On 5/5/2015 I sent out a note about my air conditioner not cooling after
being on for a long period of time. I had to drive up to the Sacramento area yesterday and meet an a/c tech during the late afternoon, when it got hot (but only 80 degrees outdoors), to demonstrate what was going on. He figured it out. I had kept outdoor/indoor/thermostat/vent temperatures for four days running, and noticed a pattern...cold air blew for a while, but after an hour or so, no matter the outside/indoor temperature, or thermostat setting, 74 degree air began to blow. Whe the a/c first goes on, it blows 58 degree air and begins to cool the house. (I hung a digital thermometer on the overhead vent.) If the house isn't too hot, it gets cooled down properly and the a/c turns itself off. If the house is hot, the a/c begins to blow 58 degree air, but after a while (maybe an hour or so), the fan continues to blow, since the thermostat is still calling to cool more, but the compressor turns off. All the while, I thought the compressor was still going, because air was blowing out of the vent, but the air was 74 degrees. Yesterday, I turned the a/c on at 2 pm, and the house began to cool with 58 degree air coming from the vent. The tech arrived at 3:15 pm, and just at that time, I showed him that the vent air was now blowing at 74 degrees. He went outside to the a/c unit, and noticed that although air was blowing out the indoor vent, the compressor was not running as noticed by the fact that the fan on top of the unit was not running. He measured all the amp/volts at the two main capacitors (start and run capacitors) and all was fine. He measured the freon, and it was up to capacity. He then measured the temperature of the compressor, and it was HOT, at 149 degrees. He called back to his company and also to the American Standard, the a/c manufacturer, for advice/trouble shooting. All were baffled. He then took the garden hose and ran water over the compressor cooling fins, and the compressor started right up and the vent air went from 74 to 71 degrees in a minute, and continued to decline. He surmised that the compressor was overheating and was shutting down, as it should. But, no one knows why the compressor gets so hot. The outdoor temperature was only 80 degrees yesterday. Even if the outdoor temperature is 75 degrees, the compressor gets hot after running for a while and shuts itself off. The a/c unit is an 18 year-old American Standard model 7A2042A100A1, R22, used to cool a 1700 sq. ft. single story home in the Sacramento area. This is my dad's house, who passed away in late 2013. Beginning in 2012, he used to call me up to figure out why the house didn't cool properly. We had techs out, and they replaced this and that, but still no luck. I replaced two thermostats, thinking that may be the issue, but still no luck. A month ago, when the tech thought the problem was with the a/c fan, because it was VERY noisy, he replaced the fan and capacitor for about $500. But, warm air still blew. So far, the tech can only explain this by saying that the unit is old, and just doens't run as efficiently. While I can buy this, I don't know why this would be. Anyone? At any rate, to replace the compressor is about $2500, which I could do, as it seems everything else is running fine, and especially since I've just replace the fan/capacitor. To replace the entire unit is about $4500, but they suggest that if I replace the entire unit, I should also replace the perfectly running furnace, since a new a/c unit uses the newer 'freon', and they like to match that with the furnace. I don't understand this. But, to replace both a/c and furnace is about $10,000. The a/c unit is about a 3.5 ton unit. I prefer to get by with the $2500 compressor, as I don't know how long I'll keep the house. Any thoughts? TIA |
#2
Posted to alt.home.repair
|
|||
|
|||
Measuring A/C Temp Solved, sort of...
On Tue, 2 Jun 2015 16:24:50 +0000 (UTC), Boris
wrote in Any thoughts? Is the outside heat exchanger dirty or blocked up? Spraying water on it lowered the temp enough for the compressor to restart. -- Web based forums are like subscribing to 10 different newspapers and having to visit 10 different news stands to pickup each one. Email list-server groups and USENET are like having all of those newspapers delivered to your door every morning. |
#3
Posted to alt.home.repair
|
|||
|
|||
Measuring A/C Temp Solved, sort of...
"Boris" wrote in message 9.88... At any rate, to replace the compressor is about $2500, which I could do, as it seems everything else is running fine, and especially since I've just replace the fan/capacitor. To replace the entire unit is about $4500, but they suggest that if I replace the entire unit, I should also replace the perfectly running furnace, since a new a/c unit uses the newer 'freon', and they like to match that with the furnace. I don't understand this. But, to replace both a/c and furnace is about $10,000. The a/c unit is about a 3.5 ton unit. I prefer to get by with the $2500 compressor, as I don't know how long I'll keep the house. Any thoughts? It does sound as if the compressor is worn out after 18 years. I don't understand why a furnace (you did not tell what type or kind) would have anything to do with the air conditioner. That statement abou tthe need because of the newer "freon" and a match seems bogus to me. I think I would be looking for a different company to do the work. I believe I would replace the whole air conditioner. That way if it does not cool correctly it would be on the installer to make it right and he could not blame the problem on anything else. |
#4
Posted to alt.home.repair
|
|||
|
|||
Measuring A/C Temp Solved, sort of...
CRNG wrote in
: On Tue, 2 Jun 2015 16:24:50 +0000 (UTC), Boris wrote in Any thoughts? Is the outside heat exchanger dirty or blocked up? Spraying water on it lowered the temp enough for the compressor to restart. Do you mean radiator looking cooling thing, that's visible when taking off a cabinet side panel? Yes, it was clean. |
#5
Posted to alt.home.repair
|
|||
|
|||
Measuring A/C Temp Solved, sort of...
On Tue, 2 Jun 2015 17:04:49 +0000 (UTC), Boris
wrote: CRNG wrote in : On Tue, 2 Jun 2015 16:24:50 +0000 (UTC), Boris wrote in Any thoughts? Is the outside heat exchanger dirty or blocked up? Spraying water on it lowered the temp enough for the compressor to restart. Do you mean radiator looking cooling thing, that's visible when taking off a cabinet side panel? Yes, it was clean. It may look clean, but can be restricting air flow through the fins. There is a chemical used to spray on the fins. It will push dirt and debris out of the fins. Then is rinsed off. Here in the Mojave Desert we have blowing sand that is like talc powder. Disclaimer Not an HVAC Tech. |
#6
Posted to alt.home.repair
|
|||
|
|||
Measuring A/C Temp Solved, sort of...
On Tuesday, June 2, 2015 at 11:49:32 AM UTC-5, CRNG wrote:
On Tue, 2 Jun 2015 16:24:50 +0000 (UTC), Boris wrote in Any thoughts? Is the outside heat exchanger dirty or blocked up? Spraying water on it lowered the temp enough for the compressor to restart. -- I have the professional chemicals and foamer that hooks to a water hose I used when I was able to work to clean condensing units. A homeowner can get aerosol cans of air conditioner cleaner from the big box stores that you can spray on the condensing coils and it will foam up penetrating the space between the fins to dissolve dirt that's interfering with air flow. Some brands claim to be self rinsing but I'd use a garden hose with the nozzle set for a wide gentle spray to rinse the coil. Don't ever use the pencil thin stream of water to rinse the coils because it will bend the fins and flatten them out which will block air flow. 8-) [8~{} Uncle AC Monster |
#7
Posted to alt.home.repair
|
|||
|
|||
Measuring A/C Temp Solved, sort of...
"Ralph Mowery" wrote in
: "Boris" wrote in message 9.88... At any rate, to replace the compressor is about $2500, which I could do, as it seems everything else is running fine, and especially since I've just replace the fan/capacitor. To replace the entire unit is about $4500, but they suggest that if I replace the entire unit, I should also replace the perfectly running furnace, since a new a/c unit uses the newer 'freon', and they like to match that with the furnace. I don't understand this. But, to replace both a/c and furnace is about $10,000. The a/c unit is about a 3.5 ton unit. I prefer to get by with the $2500 compressor, as I don't know how long I'll keep the house. Any thoughts? It does sound as if the compressor is worn out after 18 years. I don't understand why a furnace (you did not tell what type or kind) would have anything to do with the air conditioner. That statement abou tthe need because of the newer "freon" and a match seems bogus to me. I think I would be looking for a different company to do the work. The furnace is an American Standard, up-flow, housed in the hall closet. There are copper tubes (carrying what, I don't know, but they get cold when the a/c comes on)going to the furnace bonnet. I don't know the interaction, if any. I believe I would replace the whole air conditioner. That way if it does not cool correctly it would be on the installer to make it right and he could not blame the problem on anything else. You're probably right. Thanks. |
#8
Posted to alt.home.repair
|
|||
|
|||
Measuring A/C Temp Solved, sort of...
Boris wrote:
"Ralph Mowery" wrote in : "Boris" wrote in message 9.88... At any rate, to replace the compressor is about $2500, which I could do, as it seems everything else is running fine, and especially since I've just replace the fan/capacitor. To replace the entire unit is about $4500, but they suggest that if I replace the entire unit, I should also replace the perfectly running furnace, since a new a/c unit uses the newer 'freon', and they like to match that with the furnace. I don't understand this. But, to replace both a/c and furnace is about $10,000. The a/c unit is about a 3.5 ton unit. I prefer to get by with the $2500 compressor, as I don't know how long I'll keep the house. Any thoughts? It does sound as if the compressor is worn out after 18 years. I don't understand why a furnace (you did not tell what type or kind) would have anything to do with the air conditioner. That statement abou tthe need because of the newer "freon" and a match seems bogus to me. I think I would be looking for a different company to do the work. The furnace is an American Standard, up-flow, housed in the hall closet. There are copper tubes (carrying what, I don't know, but they get cold when the a/c comes on)going to the furnace bonnet. I don't know the interaction, if any. I believe I would replace the whole air conditioner. That way if it does not cool correctly it would be on the installer to make it right and he could not blame the problem on anything else. You're probably right. Thanks. Before you replace the unit , do as a couple of others have suggested and really clean the condenser coils - the radiator looking part of the outdoor unit . It can look clean and still have enough gunk on the fins to interfere with air flow and heat transfer . On the other hand , replacing a unit that old with a new more efficient one may be a good economic choice . Don't fall for that "we gotta replace the furnace too" crap . The systems are related in their handling of the air , but otherwise are independent systems . -- Snag |
#9
Posted to alt.home.repair
|
|||
|
|||
Measuring A/C Temp Solved, sort of...
"Terry Coombs" wrote in
: Boris wrote: "Ralph Mowery" wrote in : "Boris" wrote in message 9.88... At any rate, to replace the compressor is about $2500, which I could do, as it seems everything else is running fine, and especially since I've just replace the fan/capacitor. To replace the entire unit is about $4500, but they suggest that if I replace the entire unit, I should also replace the perfectly running furnace, since a new a/c unit uses the newer 'freon', and they like to match that with the furnace. I don't understand this. But, to replace both a/c and furnace is about $10,000. The a/c unit is about a 3.5 ton unit. I prefer to get by with the $2500 compressor, as I don't know how long I'll keep the house. Any thoughts? It does sound as if the compressor is worn out after 18 years. I don't understand why a furnace (you did not tell what type or kind) would have anything to do with the air conditioner. That statement abou tthe need because of the newer "freon" and a match seems bogus to me. I think I would be looking for a different company to do the work. The furnace is an American Standard, up-flow, housed in the hall closet. There are copper tubes (carrying what, I don't know, but they get cold when the a/c comes on)going to the furnace bonnet. I don't know the interaction, if any. I believe I would replace the whole air conditioner. That way if it does not cool correctly it would be on the installer to make it right and he could not blame the problem on anything else. You're probably right. Thanks. Before you replace the unit , do as a couple of others have suggested and really clean the condenser coils - the radiator looking part of the outdoor unit . Yes, thank you. I'm sure I can do that myself, as long as I'm careful and pay attention not to disturb any other components. It can look clean and still have enough gunk on the fins to interfere with air flow and heat transfer . On the other hand , replacing a unit that old with a new more efficient one may be a good economic choice . Don't fall for that "we gotta replace the furnace too" crap . The systems are related in their handling of the air , but otherwise are independent systems . Does sound like crap to me, too. Especially since he couldn't give me a good answer as to why, no matter how many ways I asked for clarification. I was also reading about cleaning the evaporative coil in the top of the furnace. http://www.handymanhowto.com/how-to-...er-evaporator- coils-part-3/ I doubt it's ever been done. |
#10
Posted to alt.home.repair
|
|||
|
|||
Measuring A/C Temp Solved, sort of...
"Boris" wrote in message 09.88... "Ralph Mowery" wrote in : "Boris" wrote in message 9.88... The furnace is an American Standard, up-flow, housed in the hall closet. There are copper tubes (carrying what, I don't know, but they get cold when the a/c comes on)going to the furnace bonnet. I don't know the interaction, if any. I guess that the furnace is either gas or oil ? The copper tubes that get cold are carring the 'freon'. If no one has explained how it works, here is a very quick explination. The compressor has a piston in it that compresses the gas to a liquid, then to the outside unit that air blows across it and takes away the heat. Then pipes it to the inside coils where the liquid goes through a small restriction in the pipe . There it absorbs heat from the air and causes the liquid to boil and turn into gas. This makes the coils feel cool. Unless you have a heat pump that reversed the flow and the tubes inside get hot in the winter it has nothing to do whit the furnace, just uses the same blower and duct work. I don't recall you saying what part of the country you are in. If in an area that does not get below 25 deg C very many days of the year, you may want to look at a heat pump. Cost should not be much more. If in a cold area of the country, then a heat pump will not be very efficent. |
#11
Posted to alt.home.repair
|
|||
|
|||
Measuring A/C Temp Solved, sort of...
"Ralph Mowery" wrote in
: "Boris" wrote in message 09.88... "Ralph Mowery" wrote in : "Boris" wrote in message 9.88... The furnace is an American Standard, up-flow, housed in the hall closet. There are copper tubes (carrying what, I don't know, but they get cold when the a/c comes on)going to the furnace bonnet. I don't know the interaction, if any. I guess that the furnace is either gas or oil ? Gas. The copper tubes that get cold are carring the 'freon'. If no one has explained how it works, here is a very quick explination. The compressor has a piston in it that compresses the gas to a liquid, then to the outside unit that air blows across it and takes away the heat. Then pipes it to the inside coils where the liquid goes through a small restriction in the pipe . There it absorbs heat from the air and causes the liquid to boil and turn into gas. This makes the coils feel cool. Unless you have a heat pump Nope. that reversed the flow and the tubes inside get hot in the winter it has nothing to do whit the furnace, just uses the same blower and duct work. Yes, that's what I've surmised. I don't recall you saying what part of the country you are in. Sacramento, CA. high 90's to low 30's If in an area that does not get below 25 deg C very many days of the year, you may want to look at a heat pump. Cost should not be much more. If in a cold area of the country, then a heat pump will not be very efficent. |
#12
Posted to alt.home.repair
|
|||
|
|||
Measuring A/C Temp Solved, sort of...
On 6/2/2015 12:24 PM, Boris wrote:
Yesterday, I turned the a/c on at 2 pm, and the house began to cool with 58 degree air coming from the vent. The tech arrived at 3:15 pm, and just at that time, I showed him that the vent air was now blowing at 74 degrees. He went outside to the a/c unit, and noticed that although air was blowing out the indoor vent, the compressor was not running as noticed by the fact that the fan on top of the unit was not running. He measured all the amp/volts at the two main capacitors (start and run capacitors) and all was fine. He measured the freon, and it was up to capacity. He then measured the temperature of the compressor, and it was HOT, at 149 degrees. He called back to his company and also to the American Standard, the a/c manufacturer, for advice/trouble shooting. All were baffled. He then took the garden hose and ran water over the compressor cooling fins, and the compressor started right up and the vent air went from 74 to 71 degrees in a minute, and continued to decline. He surmised that the compressor was overheating and was shutting down, as it should. Have the fins been properly cleaned? That would be my first step. They lose efficiency when cruded up. There is a cleaner made just for that purpose. |
#13
Posted to alt.home.repair
|
|||
|
|||
Measuring A/C Temp Solved, sort of...
Boris wrote:
"Terry Coombs" wrote in : Boris wrote: "Ralph Mowery" wrote in : "Boris" wrote in message 9.88... At any rate, to replace the compressor is about $2500, which I could do, as it seems everything else is running fine, and especially since I've just replace the fan/capacitor. To replace the entire unit is about $4500, but they suggest that if I replace the entire unit, I should also replace the perfectly running furnace, since a new a/c unit uses the newer 'freon', and they like to match that with the furnace. I don't understand this. But, to replace both a/c and furnace is about $10,000. The a/c unit is about a 3.5 ton unit. I prefer to get by with the $2500 compressor, as I don't know how long I'll keep the house. Any thoughts? It does sound as if the compressor is worn out after 18 years. I don't understand why a furnace (you did not tell what type or kind) would have anything to do with the air conditioner. That statement abou tthe need because of the newer "freon" and a match seems bogus to me. I think I would be looking for a different company to do the work. The furnace is an American Standard, up-flow, housed in the hall closet. There are copper tubes (carrying what, I don't know, but they get cold when the a/c comes on)going to the furnace bonnet. I don't know the interaction, if any. I believe I would replace the whole air conditioner. That way if it does not cool correctly it would be on the installer to make it right and he could not blame the problem on anything else. You're probably right. Thanks. Before you replace the unit , do as a couple of others have suggested and really clean the condenser coils - the radiator looking part of the outdoor unit . Yes, thank you. I'm sure I can do that myself, as long as I'm careful and pay attention not to disturb any other components. It can look clean and still have enough gunk on the fins to interfere with air flow and heat transfer . On the other hand , replacing a unit that old with a new more efficient one may be a good economic choice . Don't fall for that "we gotta replace the furnace too" crap . The systems are related in their handling of the air , but otherwise are independent systems . Does sound like crap to me, too. Especially since he couldn't give me a good answer as to why, no matter how many ways I asked for clarification. I was also reading about cleaning the evaporative coil in the top of the furnace. http://www.handymanhowto.com/how-to-...er-evaporator- coils-part-3/ I doubt it's ever been done. If you've kept up with filter changes it's probably pretty clean . Depending on how your system is put together it's probably a pure b***h to check . -- Snag |
#14
Posted to alt.home.repair
|
|||
|
|||
Measuring A/C Temp Solved, sort of...
On Tue, 2 Jun 2015 16:24:50 +0000 (UTC), Boris
wrote: At any rate, to replace the compressor is about $2500, which I could do, as it seems everything else is running fine, and especially since I've just replace the fan/capacitor. To replace the entire unit is about $4500, but they suggest that if I replace the entire unit, I should also replace the perfectly running furnace, since a new a/c unit uses the newer 'freon', and they like to match that with the furnace. I don't I like to match my date's lipstick with the color of my car, but it doesn't make the car run any better. understand this. But, to replace both a/c and furnace is about $10,000. The a/c unit is about a 3.5 ton unit. I prefer to get by with the $2500 compressor, as I don't know how long I'll keep the house. Any thoughts? I don't know enough to comment on the compressor but as you know, the furnace doesn't use freon. It's just their way of trying to get you to spend more. Do techs get a commission when customers spend money? At least more money than a simple repair? Probably. |
#15
Posted to alt.home.repair
|
|||
|
|||
Measuring A/C Temp Solved, sort of...
On Tue, 2 Jun 2015 16:24:50 +0000 (UTC), Boris
wrote: To replace the entire unit is about $4500, but they suggest that if I replace the entire unit, I should also replace the perfectly running furnace, since a new a/c unit uses the newer 'freon', and they like to match that with the furnace. I agree with the others in saying that the furnace/air handler do not necessarily need to be replaced. However, don't confuse the furnace/air handler with the inside part of the air conditioner - the evaperator coil. Those are commonly replaced when a new outside unit is installed. |
#16
Posted to alt.home.repair
|
|||
|
|||
Measuring A/C Temp Solved, sort of...
"Boris" wrote in message 09.88... I don't recall you saying what part of the country you are in. Sacramento, CA. high 90's to low 30's If in an area that does not get below 25 deg C very many days of the year, you may want to look at a heat pump. Cost should not be much more. If in a cold area of the country, then a heat pump will not be very efficent. I put in 25 deg C, should have been F. If it never got below 25 deg C you probably would never need heat.. You may want to look at a heat pump. It probably won't cost much more and may be less expensive to run than the gas for heat. |
#17
Posted to alt.home.repair
|
|||
|
|||
Measuring A/C Temp Solved, sort of...
CRNG wrote:
On Tue, 2 Jun 2015 16:24:50 +0000 (UTC), Boris wrote in Any thoughts? Is the outside heat exchanger dirty or blocked up? Spraying water on it lowered the temp enough for the compressor to restart. I wonder ODU fan is running reverse? Is the fan blowing out or sucking in the air? 3.5 ton for 1700 sq ft house? Mine is 2600 sq ft 2 story, 3 ton works just fine. 10,000.00 total cost for new system seems too high. If the compressor current draw is normal why does it OH? compressor in our unit is in a insulation jacket yet it never OH. Are the capacitors new for it? How about refrigerant oil? |
#18
Posted to alt.home.repair
|
|||
|
|||
Measuring A/C Temp Solved, sort of...
On Tuesday, June 2, 2015 at 1:52:56 PM UTC-4, Boris wrote:
"Terry Coombs" wrote in : Boris wrote: "Ralph Mowery" wrote in : "Boris" wrote in message 9.88... At any rate, to replace the compressor is about $2500, which I could do, as it seems everything else is running fine, and especially since I've just replace the fan/capacitor. To replace the entire unit is about $4500, but they suggest that if I replace the entire unit, I should also replace the perfectly running furnace, since a new a/c unit uses the newer 'freon', and they like to match that with the furnace. I don't understand this. But, to replace both a/c and furnace is about $10,000. The a/c unit is about a 3.5 ton unit. I prefer to get by with the $2500 compressor, as I don't know how long I'll keep the house. Any thoughts? It does sound as if the compressor is worn out after 18 years. I don't understand why a furnace (you did not tell what type or kind) would have anything to do with the air conditioner. That statement abou tthe need because of the newer "freon" and a match seems bogus to me. I think I would be looking for a different company to do the work. The furnace is an American Standard, up-flow, housed in the hall closet. There are copper tubes (carrying what, I don't know, but they get cold when the a/c comes on)going to the furnace bonnet. I don't know the interaction, if any. I believe I would replace the whole air conditioner. That way if it does not cool correctly it would be on the installer to make it right and he could not blame the problem on anything else. You're probably right. Thanks. Before you replace the unit , do as a couple of others have suggested and really clean the condenser coils - the radiator looking part of the outdoor unit . Yes, thank you. I'm sure I can do that myself, as long as I'm careful and pay attention not to disturb any other components. It can look clean and still have enough gunk on the fins to interfere with air flow and heat transfer . On the other hand , replacing a unit that old with a new more efficient one may be a good economic choice . Don't fall for that "we gotta replace the furnace too" crap . The systems are related in their handling of the air , but otherwise are independent systems . Does sound like crap to me, too. Especially since he couldn't give me a good answer as to why, no matter how many ways I asked for clarification. It's not exactly crap. You have an 18 year old furnace and an 18 year old AC. They both rely on the same blower and main controller board. When you're replacing the whole AC system, you're already at about 90% of the labor to replace the whole furnace. All that's left is to disconnect the gas line and the electric and chuck the old one out. Not many people are going to opt to replace most of an 18 year old system, but then leave and rely on the rest of the old equipment. And if they do it that way, then later the blower or the controller board fails, the installer has an unhappy customer. Eqpt cost, the furnace part is less than the cost of the AC part. And also if the furnace part needs to be replaced later, then you have more labor cost, because now you have to take apart the AC system again. Your symptoms could be a dying compressor. IDK why it would cost $2500 to replace just a condenser. It sounds about 2X high to me. But I'm also not sure I'd put even that into an 18 year old AC system. The cost of $10K for a whole new system sounds several thousand too high to me. When I went out for quotes a few years ago, I was getting $7K - $9K for a 5 ton AC, 120K BTU furnace and that was in The Peoples Republic of NJ, which is one of the most expensive places. If you shop around, I'll bet you can do a lot better. Also, the fact that the tech had to call around, including the manufacturer to try to diagnose the problem, wouldn't leave me with so much confidence in them. |
#19
Posted to alt.home.repair
|
|||
|
|||
Measuring A/C Temp Solved, sort of...
On 6/2/15 12:24 PM, Boris wrote:
Any thoughts? TIA I'd check the temperature of the tube taking the liquid freon out of the compressor unit with an infrared thermometer. The copper probably won't give you a good reading, but if you wrap it with electrical tape, you should be able to get a good IR reading from the tape. If it's not much above the outdoor air temperature, the compressor radiator isn't the problem. I'd be interested in the temperature between the compressor and the radiator. First, I'd google to try to find out what a reasonable temperature is. On my compressor, I don't think I could get an IR reading with the compressor running. I'd tape the probe from an indoor-outdoor thermometer to the tube. (Actually, I'd use the probe that came with my multimeter because it's smaller.) I'd tape insulating material over it to keep air from cooling the probe. If the freon going into the radiator is abnormally hot but it's good coming out, I'd suspect a restriction on the flow of freon somewhere in the system. I'm vague about air conditioning, but I believe there's a thermostatic valve on the evaporator. If it malfunctioned, I imagine that restriction could be severe enough to overheat your compressor. |
#20
Posted to alt.home.repair
|
|||
|
|||
Measuring A/C Temp Solved, sort of...
On 6/2/15 3:23 PM, J Burns wrote:
On 6/2/15 12:24 PM, Boris wrote: Any thoughts? TIA I'd check the temperature of the tube taking the liquid freon out of the compressor unit with an infrared thermometer. The copper probably won't give you a good reading, but if you wrap it with electrical tape, you should be able to get a good IR reading from the tape. If it's not much above the outdoor air temperature, the compressor radiator isn't the problem. I'd be interested in the temperature between the compressor and the radiator. First, I'd google to try to find out what a reasonable temperature is. On my compressor, I don't think I could get an IR reading with the compressor running. I'd tape the probe from an indoor-outdoor thermometer to the tube. (Actually, I'd use the probe that came with my multimeter because it's smaller.) I'd tape insulating material over it to keep air from cooling the probe. If the freon going into the radiator is abnormally hot but it's good coming out, I'd suspect a restriction on the flow of freon somewhere in the system. I'm vague about air conditioning, but I believe there's a thermostatic valve on the evaporator. If it malfunctioned, I imagine that restriction could be severe enough to overheat your compressor. Come to think of it, I wouldn't bother to check the temperature of the tube coming out of the compressor. If the condenser is cooling properly and the compressor is too hot, I'd suspect a malfunction in a valve at the evaporator. |
#21
Posted to alt.home.repair
|
|||
|
|||
Measuring A/C Temp Solved, sort of...
trader_4 wrote:
On Tuesday, June 2, 2015 at 1:52:56 PM UTC-4, Boris wrote: "Terry Coombs" wrote in : Boris wrote: "Ralph Mowery" wrote in : "Boris" wrote in message 9.88... At any rate, to replace the compressor is about $2500, which I could do, as it seems everything else is running fine, and especially since I've just replace the fan/capacitor. To replace the entire unit is about $4500, but they suggest that if I replace the entire unit, I should also replace the perfectly running furnace, since a new a/c unit uses the newer 'freon', and they like to match that with the furnace. I don't understand this. But, to replace both a/c and furnace is about $10,000. The a/c unit is about a 3.5 ton unit. I prefer to get by with the $2500 compressor, as I don't know how long I'll keep the house. Any thoughts? It does sound as if the compressor is worn out after 18 years. I don't understand why a furnace (you did not tell what type or kind) would have anything to do with the air conditioner. That statement abou tthe need because of the newer "freon" and a match seems bogus to me. I think I would be looking for a different company to do the work. The furnace is an American Standard, up-flow, housed in the hall closet. There are copper tubes (carrying what, I don't know, but they get cold when the a/c comes on)going to the furnace bonnet. I don't know the interaction, if any. I believe I would replace the whole air conditioner. That way if it does not cool correctly it would be on the installer to make it right and he could not blame the problem on anything else. You're probably right. Thanks. Before you replace the unit , do as a couple of others have suggested and really clean the condenser coils - the radiator looking part of the outdoor unit . Yes, thank you. I'm sure I can do that myself, as long as I'm careful and pay attention not to disturb any other components. It can look clean and still have enough gunk on the fins to interfere with air flow and heat transfer . On the other hand , replacing a unit that old with a new more efficient one may be a good economic choice . Don't fall for that "we gotta replace the furnace too" crap . The systems are related in their handling of the air , but otherwise are independent systems . Does sound like crap to me, too. Especially since he couldn't give me a good answer as to why, no matter how many ways I asked for clarification. It's not exactly crap. You have an 18 year old furnace and an 18 year old AC. They both rely on the same blower and main controller board. When you're replacing the whole AC system, you're already at about 90% of the labor to replace the whole furnace. All that's left is to disconnect the gas line and the electric and chuck the old one out. Not many people are going to opt to replace most of an 18 year old system, but then leave and rely on the rest of the old equipment. And if they do it that way, then later the blower or the controller board fails, the installer has an unhappy customer. Eqpt cost, the furnace part is less than the cost of the AC part. And also if the furnace part needs to be replaced later, then you have more labor cost, because now you have to take apart the AC system again. Your symptoms could be a dying compressor. IDK why it would cost $2500 to replace just a condenser. It sounds about 2X high to me. But I'm also not sure I'd put even that into an 18 year old AC system. The cost of $10K for a whole new system sounds several thousand too high to me. When I went out for quotes a few years ago, I was getting $7K - $9K for a 5 ton AC, 120K BTU furnace and that was in The Peoples Republic of NJ, which is one of the most expensive places. If you shop around, I'll bet you can do a lot better. Also, the fact that the tech had to call around, including the manufacturer to try to diagnose the problem, wouldn't leave me with so much confidence in them. New furnace will have more efficient blower, probably VS or X13 type DC motor driven blower which is whole lot more efficient than old PSC type AC motor. |
#22
Posted to alt.home.repair
|
|||
|
|||
Measuring A/C Temp Solved, sort of...
On 6/2/15 3:33 PM, J Burns wrote:
On 6/2/15 3:23 PM, J Burns wrote: On 6/2/15 12:24 PM, Boris wrote: Any thoughts? TIA I'd check the temperature of the tube taking the liquid freon out of the compressor unit with an infrared thermometer. The copper probably won't give you a good reading, but if you wrap it with electrical tape, you should be able to get a good IR reading from the tape. If it's not much above the outdoor air temperature, the compressor radiator isn't the problem. I'd be interested in the temperature between the compressor and the radiator. First, I'd google to try to find out what a reasonable temperature is. On my compressor, I don't think I could get an IR reading with the compressor running. I'd tape the probe from an indoor-outdoor thermometer to the tube. (Actually, I'd use the probe that came with my multimeter because it's smaller.) I'd tape insulating material over it to keep air from cooling the probe. If the freon going into the radiator is abnormally hot but it's good coming out, I'd suspect a restriction on the flow of freon somewhere in the system. I'm vague about air conditioning, but I believe there's a thermostatic valve on the evaporator. If it malfunctioned, I imagine that restriction could be severe enough to overheat your compressor. Come to think of it, I wouldn't bother to check the temperature of the tube coming out of the compressor. If the condenser is cooling properly and the compressor is too hot, I'd suspect a malfunction in a valve at the evaporator. How about your drier? Many times, a drier will last the life of the system, but not always. They can get clogged. I've read that the water in freon can cause all kinds of problems. I wonder if one problem could be a buildup of ice in the valve on the evaporator that separates the high side from the low side. When the compressor wasn't running, the ice would melt. Then the air conditioner would run normally until a buildup of ice blocked the valve. You'd lose your cooling, and I imagine the compressor would overheat. |
#23
Posted to alt.home.repair
|
|||
|
|||
Measuring A/C Temp Solved, sort of...
That doesn't sound like all that hot a temperature for teh compressor
to me. But I'm just guessing. I know I've had compressors in the past that would run all day long and be so hot that you couldn't touch them without getting burned but they never stopped running. So maybe it's overheat protection is a little too touchy. I also got the impression from my AC guy that part of having a proper amount of refrigerant in the system is so that there is a certain amount of COLD refrigerant that for whatever reason trickles into the compressor to keep it from getting too hot. I got the impression that a low charge meant there wasn't enough of the "left over cold refrigerant" to cool down the compressor and that could make the compressor run hot. Sooooo... if there is any truth to that I would hypothesize that if you were to have your AC guy shove some additional "freon" into your system, whether he thinks it needs it or not, that it might make the compressor run cooler and solve your problem. On Tue, 2 Jun 2015 16:24:50 +0000 (UTC), Boris wrote: On 5/5/2015 I sent out a note about my air conditioner not cooling after being on for a long period of time. I had to drive up to the Sacramento area yesterday and meet an a/c tech during the late afternoon, when it got hot (but only 80 degrees outdoors), to demonstrate what was going on. He figured it out. I had kept outdoor/indoor/thermostat/vent temperatures for four days running, and noticed a pattern...cold air blew for a while, but after an hour or so, no matter the outside/indoor temperature, or thermostat setting, 74 degree air began to blow. Whe the a/c first goes on, it blows 58 degree air and begins to cool the house. (I hung a digital thermometer on the overhead vent.) If the house isn't too hot, it gets cooled down properly and the a/c turns itself off. If the house is hot, the a/c begins to blow 58 degree air, but after a while (maybe an hour or so), the fan continues to blow, since the thermostat is still calling to cool more, but the compressor turns off. All the while, I thought the compressor was still going, because air was blowing out of the vent, but the air was 74 degrees. Yesterday, I turned the a/c on at 2 pm, and the house began to cool with 58 degree air coming from the vent. The tech arrived at 3:15 pm, and just at that time, I showed him that the vent air was now blowing at 74 degrees. He went outside to the a/c unit, and noticed that although air was blowing out the indoor vent, the compressor was not running as noticed by the fact that the fan on top of the unit was not running. He measured all the amp/volts at the two main capacitors (start and run capacitors) and all was fine. He measured the freon, and it was up to capacity. He then measured the temperature of the compressor, and it was HOT, at 149 degrees. He called back to his company and also to the American Standard, the a/c manufacturer, for advice/trouble shooting. All were baffled. He then took the garden hose and ran water over the compressor cooling fins, and the compressor started right up and the vent air went from 74 to 71 degrees in a minute, and continued to decline. He surmised that the compressor was overheating and was shutting down, as it should. But, no one knows why the compressor gets so hot. The outdoor temperature was only 80 degrees yesterday. Even if the outdoor temperature is 75 degrees, the compressor gets hot after running for a while and shuts itself off. The a/c unit is an 18 year-old American Standard model 7A2042A100A1, R22, used to cool a 1700 sq. ft. single story home in the Sacramento area. This is my dad's house, who passed away in late 2013. Beginning in 2012, he used to call me up to figure out why the house didn't cool properly. We had techs out, and they replaced this and that, but still no luck. I replaced two thermostats, thinking that may be the issue, but still no luck. A month ago, when the tech thought the problem was with the a/c fan, because it was VERY noisy, he replaced the fan and capacitor for about $500. But, warm air still blew. So far, the tech can only explain this by saying that the unit is old, and just doens't run as efficiently. While I can buy this, I don't know why this would be. Anyone? At any rate, to replace the compressor is about $2500, which I could do, as it seems everything else is running fine, and especially since I've just replace the fan/capacitor. To replace the entire unit is about $4500, but they suggest that if I replace the entire unit, I should also replace the perfectly running furnace, since a new a/c unit uses the newer 'freon', and they like to match that with the furnace. I don't understand this. But, to replace both a/c and furnace is about $10,000. The a/c unit is about a 3.5 ton unit. I prefer to get by with the $2500 compressor, as I don't know how long I'll keep the house. Any thoughts? TIA |
#24
Posted to alt.home.repair
|
|||
|
|||
Measuring A/C Temp Solved, sort of...
Tony Hwang wrote in news:%Imbx.22350$bM1.18144
@fx01.iad: CRNG wrote: On Tue, 2 Jun 2015 16:24:50 +0000 (UTC), Boris wrote in Any thoughts? Is the outside heat exchanger dirty or blocked up? Spraying water on it lowered the temp enough for the compressor to restart. I wonder ODU fan is running reverse? Is the fan blowing out or sucking in the air? 3.5 ton for 1700 sq ft house? Mine is 2600 sq ft 2 story, 3 ton works just fine. 10,000.00 total cost for new system seems too high. If the compressor current draw is normal why does it OH? compressor in our unit is in a insulation jacket yet it never OH. Are the capacitors new for it? How about refrigerant oil? I guess I should have said that the tech said he'd replace with a 3.5 ton a/c unit. I assumed the current one is of similar capacity. He does know the size of the house. Is there a place online where I can calculate the size needed? |
#25
Posted to alt.home.repair
|
|||
|
|||
Measuring A/C Temp Solved, sort of...
Boris wrote in
09.88: Tony Hwang wrote in news:%Imbx.22350$bM1.18144 @fx01.iad: snip I wonder ODU fan is running reverse? Is the fan blowing out or sucking in the air? 3.5 ton for 1700 sq ft house? Mine is 2600 sq ft 2 story, 3 ton works just fine. 10,000.00 total cost for new system seems too high. If the compressor current draw is normal why does it OH? compressor in our unit is in a insulation jacket yet it never OH. Are the capacitors new for it? How about refrigerant oil? I guess I should have said that the tech said he'd replace with a 3.5 ton a/c unit. I assumed the current one is of similar capacity. He does know the size of the house. Is there a place online where I can calculate the size needed? Well, I just looked around, and some sites give me 4.5 tons, and this one gives me 3 tons. http://www.acdirect.com/ac-package-u...ter-ac-sizing- calculator |
#26
Posted to alt.home.repair
|
|||
|
|||
Measuring A/C Temp Solved, sort of...
Ashton Crusher wrote in
: That doesn't sound like all that hot a temperature for teh compressor to me. But I'm just guessing. I know I've had compressors in the past that would run all day long and be so hot that you couldn't touch them without getting burned but they never stopped running. So maybe it's overheat protection is a little too touchy. I also got the impression from my AC guy that part of having a proper amount of refrigerant in the system is so that there is a certain amount of COLD refrigerant that for whatever reason trickles into the compressor to keep it from getting too hot. I got the impression that a low charge meant there wasn't enough of the "left over cold refrigerant" to cool down the compressor and that could make the compressor run hot. Sooooo... if there is any truth to that I would hypothesize that if you were to have your AC guy shove some additional "freon" into your system, whether he thinks it needs it or not, that it might make the compressor run cooler and solve your problem. On Tue, 2 Jun 2015 16:24:50 +0000 (UTC), Boris wrote: On 5/5/2015 I sent out a note about my air conditioner not cooling after being on for a long period of time. I had to drive up to the Sacramento area yesterday and meet an a/c tech during the late afternoon, when it got hot (but only 80 degrees outdoors), to demonstrate what was going on. He figured it out. I had kept outdoor/indoor/thermostat/vent temperatures for four days running, and noticed a pattern...cold air blew for a while, but after an hour or so, no matter the outside/indoor temperature, or thermostat setting, 74 degree air began to blow. Whe the a/c first goes on, it blows 58 degree air and begins to cool the house. (I hung a digital thermometer on the overhead vent.) If the house isn't too hot, it gets cooled down properly and the a/c turns itself off. If the house is hot, the a/c begins to blow 58 degree air, but after a while (maybe an hour or so), the fan continues to blow, since the thermostat is still calling to cool more, but the compressor turns off. All the while, I thought the compressor was still going, because air was blowing out of the vent, but the air was 74 degrees. Yesterday, I turned the a/c on at 2 pm, and the house began to cool with 58 degree air coming from the vent. The tech arrived at 3:15 pm, and just at that time, I showed him that the vent air was now blowing at 74 degrees. He went outside to the a/c unit, and noticed that although air was blowing out the indoor vent, the compressor was not running as noticed by the fact that the fan on top of the unit was not running. He measured all the amp/volts at the two main capacitors (start and run capacitors) and all was fine. He measured the freon, and it was up to capacity. He then measured the temperature of the compressor, and it was HOT, at 149 degrees. He called back to his company and also to the American Standard, the a/c manufacturer, for advice/trouble shooting. All were baffled. He then took the garden hose and ran water over the compressor cooling fins, and the compressor started right up and the vent air went from 74 to 71 degrees in a minute, and continued to decline. He surmised that the compressor was overheating and was shutting down, as it should. But, no one knows why the compressor gets so hot. The outdoor temperature was only 80 degrees yesterday. Even if the outdoor temperature is 75 degrees, the compressor gets hot after running for a while and shuts itself off. The a/c unit is an 18 year-old American Standard model 7A2042A100A1, R22, used to cool a 1700 sq. ft. single story home in the Sacramento area. This is my dad's house, who passed away in late 2013. Beginning in 2012, he used to call me up to figure out why the house didn't cool properly. We had techs out, and they replaced this and that, but still no luck. I replaced two thermostats, thinking that may be the issue, but still no luck. A month ago, when the tech thought the problem was with the a/c fan, because it was VERY noisy, he replaced the fan and capacitor for about $500. But, warm air still blew. So far, the tech can only explain this by saying that the unit is old, and just doens't run as efficiently. While I can buy this, I don't know why this would be. Anyone? At any rate, to replace the compressor is about $2500, which I could do, as it seems everything else is running fine, and especially since I've just replace the fan/capacitor. To replace the entire unit is about $4500, but they suggest that if I replace the entire unit, I should also replace the perfectly running furnace, since a new a/c unit uses the newer 'freon', and they like to match that with the furnace. I don't understand this. But, to replace both a/c and furnace is about $10,000. The a/c unit is about a 3.5 ton unit. I prefer to get by with the $2500 compressor, as I don't know how long I'll keep the house. Any thoughts? TIA Yes, the tech did say that freon also cools the compressor. He checked it, and said it was fine. But...I had to ask him to check it. This company, SierraPacific (Rancho Cordova, CA), is the company that installed solar pool heat on my dad's roof 30 years ago. It's been maintained and keeps the pool between 84 and 90 in the summer. I've got an annual maintenance contract with them. With the a/c, my dad never had a contract, and would just call any old company when service was needed. I did add to the solar contract, an HVAC maintenance contract last month, and they have been very responsive when I call them out. The last two visits were about 2 hours each doing diagnostics, with no charge. They come highly rated locally, and on Angie's List (for what it's worth),and drive around in expensive, well stocked vans. However, they are always trying to sell something. I'm thinking I should clean the compressor fins and then see what happens. If no better, I may call another company out for a second opinion. As you can tell, there's a pool at this house. All this reminds me of last year when I hired a pool guy (I live two hours away in the S.F. Peninsula) to take care of the pool. The first thing he told me was I needed a new sand filter. Funny, it always worked well, even though the zeo-sand was 8 year old on a ten year life span. He wanted $1000 to put in a new filter. I knew nothing about pool maintenance (I'd rather not have a pool, but this is Sacramento), but I taught myself, and cleaned up the filter for about $50. Works great now. But I digress... |
#27
Posted to alt.home.repair
|
|||
|
|||
Measuring A/C Temp Solved, sort of...
On 6/2/15 4:12 PM, J Burns wrote:
How about your drier? Many times, a drier will last the life of the system, but not always. They can get clogged. I've read that the water in freon can cause all kinds of problems. I wonder if one problem could be a buildup of ice in the valve on the evaporator that separates the high side from the low side. When the compressor wasn't running, the ice would melt. Then the air conditioner would run normally until a buildup of ice blocked the valve. You'd lose your cooling, and I imagine the compressor would overheat. Found it! http://www.freeasestudyguides.com/ac...ion-valve.html If a car drier fails, the AC will run a little while, then quit cooling when clogs the expansion valve. |
#28
Posted to alt.home.repair
|
|||
|
|||
Measuring A/C Temp Solved, sort of...
On 6/2/15 7:21 PM, J Burns wrote:
On 6/2/15 4:12 PM, J Burns wrote: How about your drier? Many times, a drier will last the life of the system, but not always. They can get clogged. I've read that the water in freon can cause all kinds of problems. I wonder if one problem could be a buildup of ice in the valve on the evaporator that separates the high side from the low side. When the compressor wasn't running, the ice would melt. Then the air conditioner would run normally until a buildup of ice blocked the valve. You'd lose your cooling, and I imagine the compressor would overheat. Found it! http://www.freeasestudyguides.com/ac...ion-valve.html If a car drier fails, the AC will run a little while, then quit cooling when clogs the expansion valve. http://www.achrnews.com/articles/91098-reasons-behind-compressor-overheating There it is. If a compressor gets too hot, it's likely to be either inadequate condenser cooling, which could be checked on the outlet side of the condenser, or a blockage. They say a blockage could be in the strainer or the drier. If it runs normally at first, I think it could be icing in the expansion valve. |
#29
Posted to alt.home.repair
|
|||
|
|||
Measuring A/C Temp Solved, sort of...
On Tuesday, June 2, 2015 at 6:21:20 PM UTC-5, J Burns wrote:
On 6/2/15 4:12 PM, J Burns wrote: How about your drier? Many times, a drier will last the life of the system, but not always. They can get clogged. I've read that the water in freon can cause all kinds of problems. I wonder if one problem could be a buildup of ice in the valve on the evaporator that separates the high side from the low side. When the compressor wasn't running, the ice would melt. Then the air conditioner would run normally until a buildup of ice blocked the valve.. You'd lose your cooling, and I imagine the compressor would overheat. Found it! http://www.freeasestudyguides.com/ac...ion-valve.html If a car drier fails, the AC will run a little while, then quit cooling when clogs the expansion valve. Many home AC systems have a calibrated orifice instead of the more efficient expansion valve and the orifice can freeze up and clog with ice if there is moisture in the refrigeration system. Most condensing units have a factory filter/dryer on the liquid line inside the condenser case. They can become clogged and need to be cut out and replaced with a short piece of copper tubing and a new dryer installed on the liquid line outside the condenser housing. Of course the refrigerant must be recovered before cutting any refrigeration lines. The freeze up can be easily diagnosed with a set of gauges if you know what readings you should look for. 8-) [8~{} Uncle AC Monster |
#30
Posted to alt.home.repair
|
|||
|
|||
Measuring A/C Temp Solved, sort of...
Boris wrote:
Tony Hwang wrote in news:%Imbx.22350$bM1.18144 @fx01.iad: CRNG wrote: On Tue, 2 Jun 2015 16:24:50 +0000 (UTC), Boris wrote in Any thoughts? Is the outside heat exchanger dirty or blocked up? Spraying water on it lowered the temp enough for the compressor to restart. I wonder ODU fan is running reverse? Is the fan blowing out or sucking in the air? 3.5 ton for 1700 sq ft house? Mine is 2600 sq ft 2 story, 3 ton works just fine. 10,000.00 total cost for new system seems too high. If the compressor current draw is normal why does it OH? compressor in our unit is in a insulation jacket yet it never OH. Are the capacitors new for it? How about refrigerant oil? I guess I should have said that the tech said he'd replace with a 3.5 ton a/c unit. I assumed the current one is of similar capacity. He does know the size of the house. Is there a place online where I can calculate the size needed? Hi, Yes, Google it, you'll find "manual J calculation method" to calculate. Over-sizing is common mistake causing short cycling system. If you decide to go for new system, replace both a/c and furnace for improved efficiency resulting cost saving in power consumption and more comfort. I am just a retired EE but I went thru the system replacement at my home(~20 yo). I let the installer do mechanical part and electrical part I did saving some $$. Going into 4th year and not an issue yet. I just replace air filter twice a year(16x25x5 size, MERV 11) Just finished cleaning condenser coil and checked Puron level as cooling season begins. |
#31
Posted to alt.home.repair
|
|||
|
|||
Measuring A/C Temp Solved, sort of...
On 6/2/2015 4:55 PM, Boris wrote:
I guess I should have said that the tech said he'd replace with a 3.5 ton a/c unit. I assumed the current one is of similar capacity. He does know the size of the house. Is there a place online where I can calculate the size needed? Well, I just looked around, and some sites give me 4.5 tons, and this one gives me 3 tons. http://www.acdirect.com/ac-package-u...ter-ac-sizing- calculator That site is giving vague averages. Fist step, did the old unit do the job? If yes,it is probably right or very close to it. The "square foot" calculations just take a lot of averages, but may be way off on some houses. Proper calculations consider: Exposed walls and direction they face. Insulation Ceiling/roof and insulation Window square footage and type Too small, you won't be cool. Too big, you won't remove the humidity and it will be cold and clammy. |
#32
Posted to alt.home.repair
|
|||
|
|||
Measuring A/C Temp Solved, sort of...
On 6/2/2015 12:24 PM, Boris wrote:
capacity. He then measured the temperature of the compressor, and it was HOT, at 149 degrees. He called back to his company and also to the American Standard, the a/c manufacturer, for advice/trouble shooting. All were baffled. He then took the garden hose and ran water over the compressor cooling fins, and the compressor started right up and the vent air went from 74 to 71 degrees in a minute, and continued to decline. He surmised that the compressor was overheating and was shutting down, as it should. But, no one knows why the compressor gets so hot. The outdoor temperature was only 80 degrees yesterday. Even if the outdoor temperature is 75 degrees, the compressor gets hot after running for a while and shuts itself off. Any thoughts? TIA The condenser is clogged with dust, and needs to be professionally cleaned. Use the purple stuff. Any good tech would have picked up on this very simple diagnosis in a few minutes. Gee whiz, you told the entire class what was wrong, wonder if I'll be the only simple minded (but excellent quality) AC tech to pick up on the answer you handed us on silver platter. Your guy and tech support "baffled". What a bunch of maroons. BTW, remit $147.50 for consultation. I also make house calls, buck a mile (one way) from western NY, USA. I have an uncle in Los Angeles who would love to have me visit. - .. Christopher A. Young learn more about Jesus .. www.lds.org .. .. |
#33
Posted to alt.home.repair
|
|||
|
|||
Measuring A/C Temp Solved, sort of...
On 6/2/2015 1:04 PM, Boris wrote:
Is the outside heat exchanger dirty or blocked up? Spraying water on it lowered the temp enough for the compressor to restart. Do you mean radiator looking cooling thing, that's visible when taking off a cabinet side panel? Yes, it was clean. More than once, I've worked on radiator looking things that looked clean, but benefitted greatly from professional cleaning. I'm really amazed the tech and tech support didn't figure it out. - .. Christopher A. Young learn more about Jesus .. www.lds.org .. .. |
#34
Posted to alt.home.repair
|
|||
|
|||
Measuring A/C Temp Solved, sort of...
On 6/2/2015 1:16 PM, Boris wrote:
I believe I would replace the whole air conditioner. That way if it does not cool correctly it would be on the installer to make it right and he could not blame the problem on anything else. You're probably right. Thanks. Hey, tell you want. If you decide to replace the entire unit, let me know what the quote is. I'll fly out have my tools shipped via ground, and do the job for much less than the replacement cost. And visit my uncle in LA while I'm out. I can provide at least one reference, fellow I did work for about a year ago. He bought a trailer and heat pump. I drove to South Carolina and serviced his system. Runs fine now, and even shocked the #### out of the seller (who made my friend sign an statement that the heat pump was totally beyond repair). - .. Christopher A. Young learn more about Jesus .. www.lds.org .. .. |
#35
Posted to alt.home.repair
|
|||
|
|||
Measuring A/C Temp Solved, sort of...
On 6/2/2015 2:25 PM, Terry Coombs wrote:
I was also reading about cleaning the evaporative coil in the top of the furnace. http://www.handymanhowto.com/how-to-...er-evaporator- coils-part-3/ I doubt it's ever been done. If you've kept up with filter changes it's probably pretty clean . Depending on how your system is put together it's probably a pure b***h to check . The heat pump my friend Kevin had, was used by smokers. My professional cleaning did so good, you couldn't even smell the stink when I got done. And, golly did it ever stink. - .. Christopher A. Young learn more about Jesus .. www.lds.org .. .. |
#36
Posted to alt.home.repair
|
|||
|
|||
Measuring A/C Temp Solved, sort of...
On 6/2/2015 3:23 PM, J Burns wrote:
If the freon going into the radiator is abnormally hot but it's good coming out, I'd suspect a restriction on the flow of freon somewhere in the system. I'm vague about air conditioning, but I believe there's a thermostatic valve on the evaporator. If it malfunctioned, I imagine that restriction could be severe enough to overheat your compressor. Some have TXV and some have orifice (which for some reason is called a piston). If there is a restriction, the house won't cool well, but also there will be much less heat coming into the compressor. I doubt that's the problem. - .. Christopher A. Young learn more about Jesus .. www.lds.org .. .. |
#37
Posted to alt.home.repair
|
|||
|
|||
Measuring A/C Temp Solved, sort of...
On 6/2/2015 4:47 PM, Ashton Crusher wrote:
That doesn't sound like all that hot a temperature for teh compressor to me. But I'm just guessing. I know I've had compressors in the past that would run all day long and be so hot that you couldn't touch them without getting burned but they never stopped running. So maybe it's overheat protection is a little too touchy. I also got the impression from my AC guy that part of having a proper amount of refrigerant in the system is so that there is a certain amount of COLD refrigerant that for whatever reason trickles into the compressor to keep it from getting too hot. I got the impression that a low charge meant there wasn't enough of the "left over cold refrigerant" to cool down the compressor and that could make the compressor run hot. Sooooo... if there is any truth to that I would hypothesize that if you were to have your AC guy shove some additional "freon" into your system, whether he thinks it needs it or not, that it might make the compressor run cooler and solve your problem. Well, certain to happen before too long. Just add a couple pounds of that freon stuff, and it will be just fine. Someone had to say it. I stand by my original diagnosis, and also my offer to come out and fix it. - .. Christopher A. Young learn more about Jesus .. www.lds.org .. .. |
#38
Posted to alt.home.repair
|
|||
|
|||
Measuring A/C Temp Solved, sort of...
On 6/2/15 10:46 PM, Stormin Mormon wrote:
On 6/2/2015 3:23 PM, J Burns wrote: If the freon going into the radiator is abnormally hot but it's good coming out, I'd suspect a restriction on the flow of freon somewhere in the system. I'm vague about air conditioning, but I believe there's a thermostatic valve on the evaporator. If it malfunctioned, I imagine that restriction could be severe enough to overheat your compressor. Some have TXV and some have orifice (which for some reason is called a piston). If there is a restriction, the house won't cool well, but also there will be much less heat coming into the compressor. I doubt that's the problem. - . Christopher A. Young learn more about Jesus . www.lds.org . . This page says a blockage will overheat the compressor. http://www.achrnews.com/articles/91098-reasons-behind-compressor-overheating |
#39
Posted to alt.home.repair
|
|||
|
|||
Measuring A/C Temp Solved, sort of...
On 6/2/15 10:34 PM, Stormin Mormon wrote:
On 6/2/2015 12:24 PM, Boris wrote: capacity. He then measured the temperature of the compressor, and it was HOT, at 149 degrees. He called back to his company and also to the American Standard, the a/c manufacturer, for advice/trouble shooting. All were baffled. He then took the garden hose and ran water over the compressor cooling fins, and the compressor started right up and the vent air went from 74 to 71 degrees in a minute, and continued to decline. He surmised that the compressor was overheating and was shutting down, as it should. But, no one knows why the compressor gets so hot. The outdoor temperature was only 80 degrees yesterday. Even if the outdoor temperature is 75 degrees, the compressor gets hot after running for a while and shuts itself off. Any thoughts? TIA The condenser is clogged with dust, and needs to be professionally cleaned. Use the purple stuff. Any good tech would have picked up on this very simple diagnosis in a few minutes. Gee whiz, you told the entire class what was wrong, wonder if I'll be the only simple minded (but excellent quality) AC tech to pick up on the answer you handed us on silver platter. Your guy and tech support "baffled". What a bunch of maroons. Maybe he was baffled because he knew the condenser was cooling properly. Don't you think he checked the temperature of the outlet, with a thermometer or by touch? If the condenser were dirty enough to overheat the compressor, how would he get a 16F drop when it was restarted? Why would it work fine for an hour or so? If there's moisture in the freon, most would probably pass through the expansion orifice. It might take an hour for enough ice to build up, to block it enough to overheat the compressor. As soon as the compressor stops, the indoor blower heats the evaporator to 74. No more ice. The tech starts it can can't find anything wrong. BTW, remit $247.50 for insultation by insinuation. |
#40
Posted to alt.home.repair
|
|||
|
|||
Measuring A/C Temp Solved, sort of...
On 6/2/2015 2:59 PM, trader_4 wrote:
that was in The Peoples Republic of NJ, which is one of the most expensive places. If you shop around, I'll bet you can do a lot better. Also, the fact that the tech had to call around, including the manufacturer to try to diagnose the problem, wouldn't leave me with so much confidence in them. CA is total expensive, also. I'm astounded that the tech (and telephone tech support) could not diagnose some thing so obvious. Me, I'm a fat, balding old guy who is running out of teeth. I'm no one special, just a common sense retread (polyester belted with suspenders) who thinks in simple terms. - .. Christopher A. Young learn more about Jesus .. www.lds.org .. .. |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Measuring A/C Air Temp | Home Repair | |||
Measuring colour temp at home | UK diy | |||
measuring small dia. bores with low temp alloy | Metalworking | |||
low temp snap action temp switch needed | Electronics Repair | |||
Designing a circuit to control heater output temp depending on temp of an input | Electronics |