Home |
Search |
Today's Posts |
|
Home Repair (alt.home.repair) For all homeowners and DIYers with many experienced tradesmen. Solve your toughest home fix-it problems. |
Reply |
|
|
LinkBack | Thread Tools | Display Modes |
#1
Posted to alt.home.repair
|
|||
|
|||
Dish washer and garbage disposal
A friend is remodeling and wanted me to wire-in a garbage disposal and
dish washer. May I assume both should be on a GFC breaker? |
#2
Posted to alt.home.repair
|
|||
|
|||
Dish washer and garbage disposal
philo wrote:
A friend is remodeling and wanted me to wire-in a garbage disposal and dish washer. May I assume both should be on a GFC breaker? Hi, I wonder why? |
#3
Posted to alt.home.repair
|
|||
|
|||
Dish washer and garbage disposal
On Mon, 17 Nov 2014 17:21:26 -0600, philo* wrote:
A friend is remodeling and wanted me to wire-in a garbage disposal and dish washer. May I assume both should be on a GFC breaker? Certainly. You have water at the unit. Kitchens require a GFCI in modern times? |
#4
Posted to alt.home.repair
|
|||
|
|||
Dish washer and garbage disposal
On 11/17/2014 6:21 PM, philo wrote:
A friend is remodeling and wanted me to wire-in a garbage disposal and dish washer. May I assume both should be on a GFC breaker? Something to consider. If you hard wire, they have to be disconnected if moved out for service. I put a receptacle under the sink Short cord and plug makes it easy to handle. |
#5
Posted to alt.home.repair
|
|||
|
|||
Dish washer and garbage disposal
On 11/17/2014 06:17 PM, Oren wrote:
On Mon, 17 Nov 2014 17:21:26 -0600, philo wrote: A friend is remodeling and wanted me to wire-in a garbage disposal and dish washer. May I assume both should be on a GFC breaker? Certainly. You have water at the unit. Kitchens require a GFCI in modern times? I was pretty sure. Thanks for the confirmation. This should not be too bad, the wall has been partially removed and it's only about 12 feet from the breaker box. Will p/u two GFC breakers tomorrow |
#6
Posted to alt.home.repair
|
|||
|
|||
Dish washer and garbage disposal
On 11/17/2014 06:22 PM, Ed Pawlowski wrote:
On 11/17/2014 6:21 PM, philo wrote: A friend is remodeling and wanted me to wire-in a garbage disposal and dish washer. May I assume both should be on a GFC breaker? Something to consider. If you hard wire, they have to be disconnected if moved out for service. I put a receptacle under the sink Short cord and plug makes it easy to handle. That occurred to me but if I leave enough wire for the washer to be pulled out for service, that should be OK I think. |
#7
Posted to alt.home.repair
|
|||
|
|||
Dish washer and garbage disposal
On 11/17/2014 7:23 PM, philo wrote:
On 11/17/2014 06:17 PM, Oren wrote: On Mon, 17 Nov 2014 17:21:26 -0600, philo wrote: A friend is remodeling and wanted me to wire-in a garbage disposal and dish washer. May I assume both should be on a GFC breaker? Certainly. You have water at the unit. Kitchens require a GFCI in modern times? I was pretty sure. Thanks for the confirmation. This should not be too bad, the wall has been partially removed and it's only about 12 feet from the breaker box. Will p/u two GFC breakers tomorrow It's been years, but I've found GFCI breakers are far more expensive than GFCI socket. I'd consider a GFCI socket and short cord, as mentioned. -- .. Christopher A. Young Learn about Jesus www.lds.org .. |
#8
Posted to alt.home.repair
|
|||
|
|||
Dish washer and garbage disposal
On Mon, 17 Nov 2014 17:21:26 -0600, philo* wrote:
A friend is remodeling and wanted me to wire-in a garbage disposal and dish washer. May I assume both should be on a GFC breaker? To be odd man out, my house used 1979 rules, but I have separate breakers for the D\W. the washer, and the disposale, and none are GFC. The kitchen, bathroom, and outdoor receptacles are. |
#9
Posted to alt.home.repair
|
|||
|
|||
Dish washer and garbage disposal
On 11/17/2014 07:03 PM, micky wrote:
On Mon, 17 Nov 2014 17:21:26 -0600, philo wrote: A friend is remodeling and wanted me to wire-in a garbage disposal and dish washer. May I assume both should be on a GFC breaker? To be odd man out, my house used 1979 rules, but I have separate breakers for the D\W. the washer, and the disposale, and none are GFC. The kitchen, bathroom, and outdoor receptacles are. I'm going with the present code |
#10
Posted to alt.home.repair
|
|||
|
|||
Dish washer and garbage disposal
On 11/17/2014 8:03 PM, micky wrote:
To be odd man out, my house used 1979 rules, but I have separate breakers for the D\W. the washer, and the disposale, and none are GFC. The kitchen, bathroom, and outdoor receptacles are. You should use 1967 rules, and give up about 2/3 of your house to Palestine. You'll love em! Really knock you dead. A real blast. - .. Christopher A. Young Learn about Jesus www.lds.org .. |
#11
Posted to alt.home.repair
|
|||
|
|||
Dish washer and garbage disposal
On 11/17/2014 8:05 PM, philo wrote:
To be odd man out, my house used 1979 rules, but I have separate breakers for the D\W. the washer, and the disposale, and none are GFC. The kitchen, bathroom, and outdoor receptacles are. I'm going with the present code You might get sentenced to jail in 1979.... - .. Christopher A. Young Learn about Jesus www.lds.org .. |
#12
Posted to alt.home.repair
|
|||
|
|||
Dish washer and garbage disposal
On 11/17/2014 6:41 PM, Stormin Mormon wrote:
On 11/17/2014 7:23 PM, philo wrote: [snip] This should not be too bad, the wall has been partially removed and it's only about 12 feet from the breaker box. Will p/u two GFC breakers tomorrow It's been years, but I've found GFCI breakers are far more expensive than GFCI socket. I'd consider a GFCI socket and short cord, as mentioned. Depends on the load of course but I agree about the GFCI outlet being the cheaper route to go. Consider also, that if you have access to the wall and outlet box, you could tie in there with a BX or Romex pig tail to the DW or the Disposal. Everything downwind of the GFCI is protected as well. That's another nice feature of the cheaper CFCI outlets... install in the first outlet in that circuit in the kitchen or bath and the others that follow can be the normal outlets. Only thing you need to consider is the total load on that circuit. |
#13
Posted to alt.home.repair
|
|||
|
|||
Dish washer and garbage disposal
On 11/17/2014 8:36 PM, Unquestionably Confused wrote:
It's been years, but I've found GFCI breakers are far more expensive than GFCI socket. I'd consider a GFCI socket and short cord, as mentioned. Depends on the load of course but I agree about the GFCI outlet being the cheaper route to go. Consider also, that if you have access to the wall and outlet box, you could tie in there with a BX or Romex pig tail to the DW or the Disposal. Everything downwind of the GFCI is protected as well. That's another nice feature of the cheaper CFCI outlets... install in the first outlet in that circuit in the kitchen or bath and the others that follow can be the normal outlets. Only thing you need to consider is the total load on that circuit. Now, that sounds like the voice of experience. Nothing like a RX pt down from the GFCI, KWIM? -- .. Christopher A. Young Learn about Jesus www.lds.org .. |
#14
Posted to alt.home.repair
|
|||
|
|||
Dish washer and garbage disposal
Ed Pawlowski wrote:
On 11/17/2014 6:21 PM, philo wrote: A friend is remodeling and wanted me to wire-in a garbage disposal and dish washer. May I assume both should be on a GFC breaker? Something to consider. If you hard wire, they have to be disconnected if moved out for service. I put a receptacle under the sink Short cord and plug makes it easy to handle. Hi, Both are installed with plugs in our kitchen too. The possibility is both having inductive load(motors) it can falsely trigger GFCI sensor and shut the unit specially when starting. Like wise fridge is not on GFCI. |
#15
Posted to alt.home.repair
|
|||
|
|||
Dish washer and garbage disposal
On Mon, 17 Nov 2014 19:05:35 -0600, philo* wrote:
On 11/17/2014 07:03 PM, micky wrote: On Mon, 17 Nov 2014 17:21:26 -0600, philo wrote: A friend is remodeling and wanted me to wire-in a garbage disposal and dish washer. May I assume both should be on a GFC breaker? To be odd man out, my house used 1979 rules, but I have separate breakers for the D\W. the washer, and the disposale, and none are GFC. The kitchen, bathroom, and outdoor receptacles are. I'm going with the present code You're call. (Has it changed?) |
#16
Posted to alt.home.repair
|
|||
|
|||
Dish washer and garbage disposal
On Monday, November 17, 2014 6:21:32 PM UTC-5, philo* wrote:
A friend is remodeling and wanted me to wire-in a garbage disposal and dish washer. May I assume both should be on a GFC breaker? *2014 National Electrical Code requires that the dishwasher be GFI protected (210.8(D). You can install a GFI outlet under the counter for this, but it must be reasonably accessible for servicing. There is no requirement that the garbage disposal be GFI protected. If it is plugged into an outlet under the counter instead of being hardwired, the outlet would need to be GFI (210.8(A)(7). John Grabowski http://www.MrElectrician.TV |
#17
Posted to alt.home.repair
|
|||
|
|||
Dish washer and garbage disposal
|
#18
Posted to alt.home.repair
|
|||
|
|||
Dish washer and garbage disposal
On 11/17/2014 08:51 PM, John G wrote:
On Monday, November 17, 2014 6:21:32 PM UTC-5, philo wrote: A friend is remodeling and wanted me to wire-in a garbage disposal and dish washer. May I assume both should be on a GFC breaker? *2014 National Electrical Code requires that the dishwasher be GFI protected (210.8(D). You can install a GFI outlet under the counter for this, but it must be reasonably accessible for servicing. There is no requirement that the garbage disposal be GFI protected. If it is plugged into an outlet under the counter instead of being hardwired, the outlet would need to be GFI (210.8(A)(7). John Grabowski http://www.MrElectrician.TV The more I think about this I realize that since both units will have water in them that it makes sense to put on a GFI breaker. (even if not needed for the disposal) I plan to do this by direct wiring and not by the use of receptacles. Originally I was thinking of running two, 15 amp circuits but think a single 20 Amp should suffice. |
#19
Posted to alt.home.repair
|
|||
|
|||
Dish washer and garbage disposal
|
#20
Posted to alt.home.repair
|
|||
|
|||
Dish washer and garbage disposal
On Mon, 17 Nov 2014 21:15:58 -0600, philo* wrote:
Originally I was thinking of running two, 15 amp circuits but think a single 20 Amp should suffice. Here in NYC they have to be on dedicated circuits. Don. www.donwiss.com (e-mail link at home page bottom). |
#21
Posted to alt.home.repair
|
|||
|
|||
Dish washer and garbage disposal
Two separate circuits seems unreasonable, since you rarely would be starting to use the disposal at the exact same time as the dishwasher motor is starting up. The outlet route with a short cord and plug is definitely the way togo for ease of current use and future repairs.
|
#22
Posted to alt.home.repair
|
|||
|
|||
Dish washer and garbage disposal
|
#23
Posted to alt.home.repair
|
|||
|
|||
Dish washer and garbage disposal
A friend is remodeling and wanted me to wire-in a garbage disposal and dish washer. May I assume both should be on a GFC breaker? *2014 National Electrical Code requires that the dishwasher be GFI protected (210.8(D). You can install a GFI outlet under the counter for this, but it must be reasonably accessible for servicing. There is no requirement that the garbage disposal be GFI protected. If it is plugged into an outlet under the counter instead of being hardwired, the outlet would need to be GFI (210.8(A)(7). John Grabowski http://www.MrElectrician.TV 2014? Eeek! We are still waiting until they decide when the 11 will be approved. *New Jersey should have the 2014 adopted by January. I had my mandatory 2014 code update class last February. |
#25
Posted to alt.home.repair
|
|||
|
|||
Dish washer and garbage disposal
On 11/17/2014 10:31 PM, philo wrote:
On 11/17/2014 09:28 PM, wrote: O In a dwelling; There is no requirement to put the dish washer, disposal or fridge on GFCI circuits, only "where the receptacles are installed to serve the countertop surfaces" 210.52(G)(6) OK, so you are saying no GFC is needed if there is no receptacle? I looked at the NEC and see 210.52 (G) but no subsection (6) 210.8(A)(6) Sorry. Brain fart. Thanks Also, not that the codes are real strict here in western NC, neither the DW or disposal have any type ground fault protection, other than a hard wired ground. The house was built 5 years ago. It does have arc fault detection for the bedrooms, though, plus GFCIs for all kitchen, bath, unfinished basement, and exterior outlets. Also, you'd never want any protectors on the fridge or freezer for obvious reasons. |
#26
Posted to alt.home.repair
|
|||
|
|||
Dish washer and garbage disposal
On 11/18/2014 07:41 AM, Art Todesco wrote:
snip Thanks Also, not that the codes are real strict here in western NC, neither the DW or disposal have any type ground fault protection, other than a hard wired ground. The house was built 5 years ago. It does have arc fault detection for the bedrooms, though, plus GFCIs for all kitchen, bath, unfinished basement, and exterior outlets. Also, you'd never want any protectors on the fridge or freezer for obvious reasons. Thanks to you and everyone for the advice I'll soon be heading out to get parts. After I finally brought my own house up to code I see that I've used up most of my electrical supplies. |
#27
Posted to alt.home.repair
|
|||
|
|||
Dish washer and garbage disposal
On 11/18/2014 05:56 AM, John G wrote:
A friend is remodeling and wanted me to wire-in a garbage disposal and dish washer. May I assume both should be on a GFC breaker? *2014 National Electrical Code requires that the dishwasher be GFI protected (210.8(D). You can install a GFI outlet under the counter for this, but it must be reasonably accessible for servicing. There is no requirement that the garbage disposal be GFI protected. If it is plugged into an outlet under the counter instead of being hardwired, the outlet would need to be GFI (210.8(A)(7). John Grabowski http://www.MrElectrician.TV 2014? Eeek! We are still waiting until they decide when the 11 will be approved. *New Jersey should have the 2014 adopted by January. I had my mandatory 2014 code update class last February. Well, one problem solved. Went to two suppliers and could not find an Eaton/Cutler Hammer GFCI breaker so will use the GFCI outlet method. Will be better when the need arises for removing the washer. |
#28
Posted to alt.home.repair
|
|||
|
|||
Dish washer and garbage disposal
=?windows-1252?Q?philo=A0?= writes:
On 11/18/2014 05:56 AM, John G wrote: A friend is remodeling and wanted me to wire-in a garbage disposal and dish washer. May I assume both should be on a GFC breaker? *2014 National Electrical Code requires that the dishwasher be GFI protected (210.8(D). You can install a GFI outlet under the counter for this, but it must be reasonably accessible for servicing. There is no requirement that the garbage disposal be GFI protected. If it is plugged into an outlet under the counter instead of being hardwired, the outlet would need to be GFI (210.8(A)(7). John Grabowski http://www.MrElectrician.TV 2014? Eeek! We are still waiting until they decide when the 11 will be approved. *New Jersey should have the 2014 adopted by January. I had my mandatory 2014 code update class last February. Well, one problem solved. Went to two suppliers and could not find an Eaton/Cutler Hammer GFCI breaker so will use the GFCI outlet method. http://www.homedepot.com/p/Eaton-20-...GFCS/100210432 |
#29
Posted to alt.home.repair
|
|||
|
|||
Dish washer and garbage disposal
On 11/18/2014 12:04 PM, Scott Lurndal wrote:
=?windows-1252?Q?philo=A0?= writes: O http://www.homedepot.com/p/Eaton-20-...GFCS/100210432 yep, I went to Home Depot's website and that's the one I found... only the closest Home Depot to my house no longer carries any Cutler Hammer products. Considering the price, it was cheaper to just get a standard breaker (elsewhere) and a GFCI outlet. Plus as was mentioned...the dishwasher can just be unplugged if it needs to be pulled out and worked on. |
#31
Posted to alt.home.repair
|
|||
|
|||
Dish washer and garbage disposal
On 11/18/2014 5:32 PM, VinnyB wrote:
On Tue, 18 Nov 2014 12:24:05 -0500, wrote in That GFCI on the dish washer is a new requirement in the 2014 code. Just curious: so dishwashers have been installed without GFCI for 60 or so years. Now they need to have GFCI. What has changed to require the code intrusion? Are a lot of people suddenly getting electrocuted or have a lot of people always been getting electrocuted and the code writers just deciding to do something about it? Or were the code writers just bored this year? I suspect the code writers got paid off by the GFCI lobbyists, who took them to Vegas for all drinks paid weekend at the Mustang Ranch. Cynical, much? - .. Christopher A. Young Learn about Jesus www.lds.org .. |
#32
Posted to alt.home.repair
|
|||
|
|||
Dish washer and garbage disposal
On Mon, 17 Nov 2014 21:34:08 -0800 (PST), "
wrote: Two separate circuits seems unreasonable, since you rarely would be starting to use the disposal at the exact same time as the dishwasher motor is starting up. The outlet route with a short cord and plug is definitely the way togo for ease of current use and future repairs. I don't know why that would be -- I'm often cleaning the dishes, loading up the dishwasher, and as I finish loading, put the soap in, and start the dishwasher, I either continue washing pots and pans, or realize I didn't run the disposal and need to before the dishwasher starts draining, so I run it then, right as the dishwasher is cycling. I can't be the only one. Having said that, our current 1955 house has the dishwasher, disposal, all of the counter outlets and many of the lights on the same circuit. But that doesn't mean it's a good idea. Josh |
#33
Posted to alt.home.repair
|
|||
|
|||
Dish washer and garbage disposal
On 11/18/2014 04:32 PM, VinnyB wrote:
On Tue, 18 Nov 2014 12:24:05 -0500, wrote in That GFCI on the dish washer is a new requirement in the 2014 code. Just curious: so dishwashers have been installed without GFCI for 60 or so years. Now they need to have GFCI. What has changed to require the code intrusion? Are a lot of people suddenly getting electrocuted or have a lot of people always been getting electrocuted and the code writers just deciding to do something about it? Or were the code writers just bored this year? It's just a matter of safety. GFCI Back 60 years ago houses did not even have grounded outlets much less GFCI ( Invention date 1961 according to a Google search) I just recalled that my grandparents' house was built in 1948 and had a dishwasher. As I kid I really thought that was hi tech. Even though my grandmother had a dish washer I still recall that her toaster was one of those old-fashioned kind that toasted one side of the bread at a time |
#34
Posted to alt.home.repair
|
|||
|
|||
Dish washer and garbage disposal
On 11/18/2014 05:25 PM, Josh wrote:
On Mon, 17 Nov 2014 21:34:08 -0800 (PST), " wrote: Two separate circuits seems unreasonable, since you rarely would be starting to use the disposal at the exact same time as the dishwasher motor is starting up. The outlet route with a short cord and plug is definitely the way togo for ease of current use and future repairs. I don't know why that would be -- I'm often cleaning the dishes, loading up the dishwasher, and as I finish loading, put the soap in, and start the dishwasher, I either continue washing pots and pans, or realize I didn't run the disposal and need to before the dishwasher starts draining, so I run it then, right as the dishwasher is cycling. I can't be the only one. Having said that, our current 1955 house has the dishwasher, disposal, all of the counter outlets and many of the lights on the same circuit. But that doesn't mean it's a good idea. Josh Since the garbage disposal usually just runs a few seconds, it's not likely to cause a problem. I suppose that if something lodged in it and it locked up, it could draw a bit of current though. In my own house I have neither garbage disposal or dish washer... however I did re-wire the kitchen so that the coffee maker, microwave and toaster are all on their own circuits. Even two on the same circuit would very likely be an over-load or close to it. |
#35
Posted to alt.home.repair
|
|||
|
|||
Dish washer and garbage disposal
That GFCI on the dish washer is a new requirement in the 2014 code.
Just curious: so dishwashers have been installed without GFCI for 60 or so years. Now they need to have GFCI. What has changed to require the code intrusion? Are a lot of people suddenly getting electrocuted or have a lot of people always been getting electrocuted and the code writers just deciding to do something about it? Or were the code writers just bored this year? *The explanation given in my code class (If I remember correctly) was that the controls for dishwashers are becoming more and more electronic and less and less mechanical. The electronic components insulating ability breaks down over time and current can leak to the metal frame thereby creating a shock hazard. |
#36
Posted to alt.home.repair
|
|||
|
|||
Dish washer and garbage disposal
Josh wrote:
On Mon, 17 Nov 2014 21:34:08 -0800 (PST), " wrote: Two separate circuits seems unreasonable, since you rarely would be starting to use the disposal at the exact same time as the dishwasher motor is starting up. The outlet route with a short cord and plug is definitely the way togo for ease of current use and future repairs. I don't know why that would be -- I'm often cleaning the dishes, loading up the dishwasher, and as I finish loading, put the soap in, and start the dishwasher, I either continue washing pots and pans, or realize I didn't run the disposal and need to before the dishwasher starts draining, so I run it then, right as the dishwasher is cycling. I can't be the only one. Having said that, our current 1955 house has the dishwasher, disposal, all of the counter outlets and many of the lights on the same circuit. But that doesn't mean it's a good idea. Josh Hmm, In our kitchen DW and disposal unit is on different circuit. Fridge, MW also. All counter top duplex outlets are independent, each fed by different circuit, lighting is all pot LEDs on dimmer. Sub panel for kitchen is located on the pantry wall. Never had problem. |
#37
Posted to alt.home.repair
|
|||
|
|||
Dish washer and garbage disposal
"philo " wrote in message
... On 11/18/2014 12:04 PM, Scott Lurndal wrote: =?windows-1252?Q?philo=A0?= writes: O http://www.homedepot.com/p/Eaton-20-...GFCS/100210432 yep, I went to Home Depot's website and that's the one I found... only the closest Home Depot to my house no longer carries any Cutler Hammer products. Considering the price, it was cheaper to just get a standard breaker (elsewhere) and a GFCI outlet. Plus as was mentioned...the dishwasher can just be unplugged if it needs to be pulled out and worked on. I am curious where the GFCI outlet for the dishwasher will be located -- maybe in a cabinet space next to the dishwasher? -- similar to how an over-the-range microwave outlet is often located in a cabinet space above the microwave? I am assuming that the dishwasher GFCI outlet would need to be located someplace where it could be reset if it trips without having to pull the dishwasher out first to reset the GFCI. |
#38
Posted to alt.home.repair
|
|||
|
|||
Dish washer and garbage disposal
On 11/18/2014 08:33 PM, TomR wrote:
snip I am curious where the GFCI outlet for the dishwasher will be located -- maybe in a cabinet space next to the dishwasher? -- similar to how an over-the-range microwave outlet is often located in a cabinet space above the microwave? I am assuming that the dishwasher GFCI outlet would need to be located someplace where it could be reset if it trips without having to pull the dishwasher out first to reset the GFCI. I am going to put the outlet in the cabinet under the sink. It will be easy to access in the event it trips. The home owner will of course be informed. |
#39
Posted to alt.home.repair
|
|||
|
|||
Dish washer and garbage disposal
"philo " wrote in message
... On 11/18/2014 08:33 PM, TomR wrote: snip I am curious where the GFCI outlet for the dishwasher will be located -- maybe in a cabinet space next to the dishwasher? -- similar to how an over-the-range microwave outlet is often located in a cabinet space above the microwave? I am assuming that the dishwasher GFCI outlet would need to be located someplace where it could be reset if it trips without having to pull the dishwasher out first to reset the GFCI. I am going to put the outlet in the cabinet under the sink. It will be easy to access in the event it trips. The home owner will of course be informed. Got it. |
#40
Posted to alt.home.repair
|
|||
|
|||
Dish washer and garbage disposal
On Tuesday, November 18, 2014 7:13:01 PM UTC-5, John G wrote:
That GFCI on the dish washer is a new requirement in the 2014 code. Just curious: so dishwashers have been installed without GFCI for 60 or so years. Now they need to have GFCI. What has changed to require the code intrusion? Are a lot of people suddenly getting electrocuted or have a lot of people always been getting electrocuted and the code writers just deciding to do something about it? Or were the code writers just bored this year? *The explanation given in my code class (If I remember correctly) was that the controls for dishwashers are becoming more and more electronic and less and less mechanical. The electronic components insulating ability breaks down over time and current can leak to the metal frame thereby creating a shock hazard. It's not much of a shock hazard if the metal frame is grounded, which has been a code requirement for a very long time. The poster raises a good question.. It would be interesting to see if they have any real world data that justifies making this GFCI or if they have no data to back it up. |
Reply |
|
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Garbage disposal | Home Repair | |||
Garbage disposal | Home Repair | |||
Garbage disposal | Home Repair | |||
Garbage disposal | Home Repair | |||
garbage disposal | Home Repair |