Generator Cord Sizing 100' Run: Stay With 10-Gauge?
Been using a 10-gauge cord to connect my little 2kw gennie in the garden
shed to the transfer switch in the garage. No problems in maybe 20 hours total usage and the numbers look right per http://tinyurl.com/nvkyq32, which says the voltage drop will be 2.5% at full load. My understanding being that the voltage drop should be less than 5% at full load. Now I am going to add a second 2kw and run them in parallel. (Honda EU2000i + EU2000i Companion). viz: http://tinyurl.com/pjwqxbp In outage mode, the house cruises on 800-1200 watts so 95% of the second gennie's function will be redundant backup in case there's a problem with one unit during an outage. But since I will have two.... why not? Then we could fire up both during mealtimes and accommodate a toaster or a coffee maker... or the kitchen's big microwave. With the two units connected in parallel, the power cord interface changes from a regular 3-prong plug to a 30-amp L5-30 twist-lock plug. Running the numbers (Copper wire, 10 AWG, 120v, AC single phase, single set of conductors, 100' distance, load current 30 Amps) into http://tinyurl.com/nvkyq32, I get a voltage drop of 5.99 (4.99 percent). Less than the 5% limit - and, real-world, not just .1% less because the two gennies will never be putting out a full 30 amps. I'm thinking I can keep using the current 10-gauge cord by making up an adapter with a female 3-prong receptacle on one end and an L5-30 male plug on the other end. That way, one cord does it whether I use one gennie or two; cord winding/storage remains merely inconvenient instead of becoming difficult; and I avoid shelling out $250-$300. Anybody see a flaw in this reasoning? -- Pete Cresswell |
#2
Posted to alt.home.repair
|
|||
|
|||
Generator Cord Sizing 100' Run: Stay With 10-Gauge?
Per (PeteCresswell):
Running the numbers (Copper wire, 10 AWG, 120v, AC single phase, single set of conductors, 100' distance, load current 30 Amps) into http://tinyurl.com/nvkyq32, I get a voltage drop of 5.99 (4.99 percent). Correction: Looking at a photo of the actual outlet on the Companion, I see it is labeled "26.6" amps..... so the voltage drop is 4.43% instead of 4.99%. -- Pete Cresswell |
#3
Posted to alt.home.repair
|
|||
|
|||
Generator Cord Sizing 100' Run: Stay With 10-Gauge?
On Sunday, July 27, 2014 12:06:56 PM UTC-4, (PeteCresswell) wrote:
Been using a 10-gauge cord to connect my little 2kw gennie in the garden shed to the transfer switch in the garage. No problems in maybe 20 hours total usage and the numbers look right per http://tinyurl.com/nvkyq32, which says the voltage drop will be 2.5% at full load. My understanding being that the voltage drop should be less than 5% at full load. Now I am going to add a second 2kw and run them in parallel. (Honda EU2000i + EU2000i Companion). viz: http://tinyurl.com/pjwqxbp In outage mode, the house cruises on 800-1200 watts so 95% of the second gennie's function will be redundant backup in case there's a problem with one unit during an outage. But since I will have two.... why not? Then we could fire up both during mealtimes and accommodate a toaster or a coffee maker... or the kitchen's big microwave. With the two units connected in parallel, the power cord interface changes from a regular 3-prong plug to a 30-amp L5-30 twist-lock plug. Running the numbers (Copper wire, 10 AWG, 120v, AC single phase, single set of conductors, 100' distance, load current 30 Amps) into http://tinyurl.com/nvkyq32, I get a voltage drop of 5.99 (4.99 percent). Less than the 5% limit - and, real-world, not just .1% less because the two gennies will never be putting out a full 30 amps. I'm thinking I can keep using the current 10-gauge cord by making up an adapter with a female 3-prong receptacle on one end and an L5-30 male plug on the other end. That way, one cord does it whether I use one gennie or two; cord winding/storage remains merely inconvenient instead of becoming difficult; and I avoid shelling out $250-$300. Anybody see a flaw in this reasoning? -- Pete Cresswell Maybe I'm wrong, but I don't think you can do 30 amps. You have two identical generators that together put out 4KW. I may be wrong, but I'm betting that a generator that's rated at 4KW can only do that 4KW with a balanced load, ie either 16A @ 240V or 16A on each leg supplying 120V. In either case it's not thg 32A that you're anticipating. To do that it would have to be supplying 32A at 120V all to one leg and I don't think it does that, is rated to do it etc. So, I think the voltage drop is actually half what you think it is. And even if it wasn't I'd still be OK with the 10g. Another note, since it's likely to come up. You brought up running these two generators in parallel before and they can be used that way because they are inverter type and specifically designed to allow it. You couldn't do it with typical generators, so thought I'd point that out before you get 6 other replies telling you that you can't hook them up that way. |
#4
Posted to alt.home.repair
|
|||
|
|||
Generator Cord Sizing 100' Run: Stay With 10-Gauge?
"trader_4" wrote in message ... Maybe I'm wrong, but I don't think you can do 30 amps. You have two identical generators that together put out 4KW. I may be wrong, but I'm betting that a generator that's rated at 4KW can only do that 4KW with a balanced load, ie either 16A @ 240V or 16A on each leg supplying 120V. In either case it's not thg 32A that you're anticipating. To do that it would have to be supplying 32A at 120V all to one leg and I don't think it does that, is rated to do it etc. So, I think the voltage drop is actually half what you think it is. And even if it wasn't I'd still be OK with the 10g. Another note, since it's likely to come up. You brought up running these two generators in parallel before and they can be used that way because they are inverter type and specifically designed to allow it. You couldn't do it with typical generators, so thought I'd point that out before you get 6 other replies telling you that you can't hook them up that way. I am also thinking that about 16 amps is the max that can be delivered by the generators if they are paralled for 4 kw total. For generators in parallel, yes there are some inverter types that can be paralleled with out any problem. I have two generators rated at 5 kw each that just have the generators and not inverters.. I have often wondered if they could be paralled for more power. I know how to place them in parallel safely but wonder if they will stay synced up for a long period of time. Where I worked we did that all the time with motor/generator sets. As it cost lots of money to shut down some equipment, we used motor/genertor sets to vary the speed of some motors. We had a bank of about 20 sets, and one spare set. We would run both in parallel for a short time and then switch one off. |
#5
Posted to alt.home.repair
|
|||
|
|||
Generator Cord Sizing 100' Run: Stay With 10-Gauge?
Per trader_4: do it with typical generators, so thought I'd point that out before you get 6 other replies telling you that you can't hook them up that way. Per Ralph Mowery: I am also thinking that about 16 amps is the max that can be delivered by the generators if they are paralled for 4 kw total. I am too clueless to explain how or why, but these things are specifically engineered to work together and deliver 4000 watts peak and 3200 continuous. -- Pete Cresswell |
#7
Posted to alt.home.repair
|
|||
|
|||
Generator Cord Sizing 100' Run: Stay With 10-Gauge?
On Sunday, July 27, 2014 2:21:41 PM UTC-4, (PeteCresswell) wrote:
Per trader_4: do it with typical generators, so thought I'd point that out before you get 6 other replies telling you that you can't hook them up that way. Per Ralph Mowery: I am also thinking that about 16 amps is the max that can be delivered by the generators if they are paralled for 4 kw total. I am too clueless to explain how or why, but these things are specifically engineered to work together and deliver 4000 watts peak and 3200 continuous. -- Pete Cresswell I was using your full 4KW number in the numbers in my reply, treating it just like one 4KW generator. By my analysis a 4KW generator can only supply 16 amps on any conductor. If you have only 240V loads, it delivers 16 amps. If you have balanced 120V loads it delivers a max of 16 amps, ie 120V @ 16 amps and 120V @ 16 amps. And if you try to do an unbalanced 120V greater than 16 amps, eg put 30 amps on just one 120V leg, I don't think it can deliver it. Essentially you're only using part of the generator winding at that point. |
#8
Posted to alt.home.repair
|
|||
|
|||
Generator Cord Sizing 100' Run: Stay With 10-Gauge?
On Sun, 27 Jul 2014 12:06:56 -0400, "(PeteCresswell)"
wrote: Been using a 10-gauge cord to connect my little 2kw gennie in the garden shed to the transfer switch in the garage. No problems in maybe 20 hours total usage and the numbers look right per http://tinyurl.com/nvkyq32, which says the voltage drop will be 2.5% at full load. My understanding being that the voltage drop should be less than 5% at full load. Now I am going to add a second 2kw and run them in parallel. (Honda EU2000i + EU2000i Companion). viz: http://tinyurl.com/pjwqxbp In outage mode, the house cruises on 800-1200 watts so 95% of the second gennie's function will be redundant backup in case there's a problem with one unit during an outage. But since I will have two.... why not? Then we could fire up both during mealtimes and accommodate a toaster or a coffee maker... or the kitchen's big microwave. With the two units connected in parallel, the power cord interface changes from a regular 3-prong plug to a 30-amp L5-30 twist-lock plug. Running the numbers (Copper wire, 10 AWG, 120v, AC single phase, single set of conductors, 100' distance, load current 30 Amps) into http://tinyurl.com/nvkyq32, I get a voltage drop of 5.99 (4.99 percent). Less than the 5% limit - and, real-world, not just .1% less because the two gennies will never be putting out a full 30 amps. I'm thinking I can keep using the current 10-gauge cord by making up an adapter with a female 3-prong receptacle on one end and an L5-30 male plug on the other end. That way, one cord does it whether I use one gennie or two; cord winding/storage remains merely inconvenient instead of becoming difficult; and I avoid shelling out $250-$300. Anybody see a flaw in this reasoning? As long as you are never drwing 30 amps from the generator the cord will be "adequate". If I was setting up fresh I would buy a heavier cord - but what you have will continue to do the job. |
#9
Posted to alt.home.repair
|
|||
|
|||
Generator Cord Sizing 100' Run: Stay With 10-Gauge?
On Sun, 27 Jul 2014 13:01:27 -0400, "Ralph Mowery"
wrote: "trader_4" wrote in message ... Maybe I'm wrong, but I don't think you can do 30 amps. You have two identical generators that together put out 4KW. I may be wrong, but I'm betting that a generator that's rated at 4KW can only do that 4KW with a balanced load, ie either 16A @ 240V or 16A on each leg supplying 120V. In either case it's not thg 32A that you're anticipating. To do that it would have to be supplying 32A at 120V all to one leg and I don't think it does that, is rated to do it etc. So, I think the voltage drop is actually half what you think it is. And even if it wasn't I'd still be OK with the 10g. That is EXACTLY what paralleled inverter generators do. They parallel synch and put out double the output of one generator into a single 120 volt line - unless they are connected "series synch" which gives you a 220/120 center tapped output which puts 15 amps max on each "leg". Another note, since it's likely to come up. You brought up running these two generators in parallel before and they can be used that way because they are inverter type and specifically designed to allow it. You couldn't do it with typical generators, so thought I'd point that out before you get 6 other replies telling you that you can't hook them up that way. I am also thinking that about 16 amps is the max that can be delivered by the generators if they are paralled for 4 kw total. For generators in parallel, yes there are some inverter types that can be paralleled with out any problem. I have two generators rated at 5 kw each that just have the generators and not inverters.. I have often wondered if they could be paralled for more power. I know how to place them in parallel safely but wonder if they will stay synced up for a long period of time. They won't synch - period. Where I worked we did that all the time with motor/generator sets. As it cost lots of money to shut down some equipment, we used motor/genertor sets to vary the speed of some motors. We had a bank of about 20 sets, and one spare set. We would run both in parallel for a short time and then switch one off. These "motor geerator sets" were "ward leonard" drives - AC motor running DC generator to run variable speed DC motors bu varying the field current of the DC generator. Parallelling DC generators is not a serious problem Parralleling AC generators is a lot of fun, unless one of them is a synchronous generator (like an overdriven induction motor) |
#10
Posted to alt.home.repair
|
|||
|
|||
Generator Cord Sizing 100' Run: Stay With 10-Gauge?
On Sun, 27 Jul 2014 14:21:41 -0400, "(PeteCresswell)"
wrote: Per trader_4: do it with typical generators, so thought I'd point that out before you get 6 other replies telling you that you can't hook them up that way. Per Ralph Mowery: I am also thinking that about 16 amps is the max that can be delivered by the generators if they are paralled for 4 kw total. I am too clueless to explain how or why, but these things are specifically engineered to work together and deliver 4000 watts peak and 3200 continuous. The inverters "link" - the pwm signal from the one inverter bank drives the other bank as well. It is more than just the outputs connected. In the one's I've seen the second unit (partner) is switched to the "partner" mode instead of the "stand-alone" mode and it picks up the synch signal from the output of the "master" to run the inverter on the "partner". Basically the "smarts " of the partner unit are shut off and it gets the timing signal from the master. |
#11
Posted to alt.home.repair
|
|||
|
|||
Generator Cord Sizing 100' Run: Stay With 10-Gauge?
|
#12
Posted to alt.home.repair
|
|||
|
|||
Generator Cord Sizing 100' Run: Stay With 10-Gauge?
Parallelling DC generators is not a serious problem Parralleling AC generators is a lot of fun, unless one of them is a synchronous generator (like an overdriven induction motor) https://en.wikipedia.org/wiki/Synchr...ing_current%29 -- Snag |
#13
Posted to alt.home.repair
|
|||
|
|||
Generator Cord Sizing 100' Run: Stay With 10-Gauge?
|
#14
Posted to alt.home.repair
|
|||
|
|||
Generator Cord Sizing 100' Run: Stay With 10-Gauge?
On Sunday, July 27, 2014 3:25:32 PM UTC-4, wrote:
On Sun, 27 Jul 2014 13:01:27 -0400, "Ralph Mowery" wrote: "trader_4" wrote in message ... Maybe I'm wrong, but I don't think you can do 30 amps. You have two identical generators that together put out 4KW. I may be wrong, but I'm betting that a generator that's rated at 4KW can only do that 4KW with a balanced load, ie either 16A @ 240V or 16A on each leg supplying 120V. In either case it's not thg 32A that you're anticipating. To do that it would have to be supplying 32A at 120V all to one leg and I don't think it does that, is rated to do it etc. So, I think the voltage drop is actually half what you think it is. And even if it wasn't I'd still be OK with the 10g. That is EXACTLY what paralleled inverter generators do. They parallel synch and put out double the output of one generator into a single 120 volt line - unless they are connected "series synch" which gives you a 220/120 center tapped output which puts 15 amps max on each "leg". I don't see why paralled generators would be paralled into just one 120V line. Seems more logical to just parallel both legs. If you can parallel one, why can't you parallel both legs? And regardless, it doesn't change what I posted about his voltage drop issue, ie the amperage on the conductors being 16A max, which is half of what he thinks it is. |
#15
Posted to alt.home.repair
|
|||
|
|||
Generator Cord Sizing 100' Run: Stay With 10-Gauge?
On Sunday, July 27, 2014 3:17:32 PM UTC-4, wrote:
On Sun, 27 Jul 2014 12:06:56 -0400, "(PeteCresswell)" wrote: Been using a 10-gauge cord to connect my little 2kw gennie in the garden shed to the transfer switch in the garage. No problems in maybe 20 hours total usage and the numbers look right per http://tinyurl.com/nvkyq32, which says the voltage drop will be 2.5% at full load. My understanding being that the voltage drop should be less than 5% at full load. Now I am going to add a second 2kw and run them in parallel. (Honda EU2000i + EU2000i Companion). viz: http://tinyurl.com/pjwqxbp In outage mode, the house cruises on 800-1200 watts so 95% of the second gennie's function will be redundant backup in case there's a problem with one unit during an outage. But since I will have two.... why not? Then we could fire up both during mealtimes and accommodate a toaster or a coffee maker... or the kitchen's big microwave. With the two units connected in parallel, the power cord interface changes from a regular 3-prong plug to a 30-amp L5-30 twist-lock plug. Running the numbers (Copper wire, 10 AWG, 120v, AC single phase, single set of conductors, 100' distance, load current 30 Amps) into http://tinyurl.com/nvkyq32, I get a voltage drop of 5.99 (4.99 percent). Less than the 5% limit - and, real-world, not just .1% less because the two gennies will never be putting out a full 30 amps. I'm thinking I can keep using the current 10-gauge cord by making up an adapter with a female 3-prong receptacle on one end and an L5-30 male plug on the other end. That way, one cord does it whether I use one gennie or two; cord winding/storage remains merely inconvenient instead of becoming difficult; and I avoid shelling out $250-$300. Anybody see a flaw in this reasoning? As long as you are never drwing 30 amps from the generator the cord will be "adequate". If I was setting up fresh I would buy a heavier cord - but what you have will continue to do the job. Again, I don't see how you could ever draw 30 amps from a 4KW generator on any one conductor. AFAIK, you can only do half of that. |
#16
Posted to alt.home.repair
|
|||
|
|||
Generator Cord Sizing 100' Run: Stay With 10-Gauge?
On Sunday, July 27, 2014 4:02:53 PM UTC-4, trader_4 wrote:
On Sunday, July 27, 2014 3:25:32 PM UTC-4, wrote: On Sun, 27 Jul 2014 13:01:27 -0400, "Ralph Mowery" wrote: "trader_4" wrote in message ... Maybe I'm wrong, but I don't think you can do 30 amps. You have two identical generators that together put out 4KW. I may be wrong, but I'm betting that a generator that's rated at 4KW can only do that 4KW with a balanced load, ie either 16A @ 240V or 16A on each leg supplying 120V. In either case it's not thg 32A that you're anticipating. To do that it would have to be supplying 32A at 120V all to one leg and I don't think it does that, is rated to do it etc. So, I think the voltage drop is actually half what you think it is. And even if it wasn't I'd still be OK with the 10g. That is EXACTLY what paralleled inverter generators do. They parallel synch and put out double the output of one generator into a single 120 volt line - unless they are connected "series synch" which gives you a 220/120 center tapped output which puts 15 amps max on each "leg". I don't see why paralled generators would be paralled into just one 120V line. Seems more logical to just parallel both legs. If you can parallel one, why can't you parallel both legs? And regardless, it doesn't change what I posted about his voltage drop issue, ie the amperage on the conductors being 16A max, which is half of what he thinks it is. I just looked at the specs of the Honda EU200i which I think is the unit he actually has. It's strictly 120V, no 240V and it's rated at 13 amps continous. So there are not two legs involved like you;d have with a generator that's 240/120V and if you parallel two of them, you'd get 26 amps on the conductors. So, I agree with Pete's analysis of the current and voltage drop. As I said, I'd be OK with it and use 10g cable. Especially if he already has it. |
#17
Posted to alt.home.repair
|
|||
|
|||
Generator Cord Sizing 100' Run: Stay With 10-Gauge?
wrote in message ... These "motor geerator sets" were "ward leonard" drives - AC motor running DC generator to run variable speed DC motors bu varying the field current of the DC generator. Parallelling DC generators is not a serious problem Parralleling AC generators is a lot of fun, unless one of them is a synchronous generator (like an overdriven induction motor) The MG sets we were using were 3 phase 480 volt systems. We often used the light bulb or voltmeter system to put them in parallel. When the bulbs went out or the volt metes went to 0, then the switch was flipped. They then drove a bank of about 16 motors that were around 3 or 5 HP at 480 volt, 3 phase. |
#18
Posted to alt.home.repair
|
|||
|
|||
Generator Cord Sizing 100' Run: Stay With 10-Gauge?
"Rick" wrote in message b.com... On 07/27/2014 03:29 PM, wrote: The inverters "link" - the pwm signal from the one inverter bank drives the other bank as well. It is more than just the outputs connected. In the one's I've seen the second unit (partner) is switched to the "partner" mode instead of the "stand-alone" mode and it picks up the synch signal from the output of the "master" to run the inverter on the "partner". Basically the "smarts " of the partner unit are shut off and it gets the timing signal from the master. Would that make it single-phase 240 or two-phase 240? We don't even need to get that started again. It would be whatever one of the generators put out. Call it whatever you want. |
#19
Posted to alt.home.repair
|
|||
|
|||
Generator Cord Sizing 100' Run: Stay With 10-Gauge?
"trader_4" wrote in message ... I just looked at the specs of the Honda EU200i which I think is the unit he actually has. It's strictly 120V, no 240V and it's rated at 13 amps continous. So there are not two legs involved like you;d have with a generator that's 240/120V and if you parallel two of them, you'd get 26 amps on the conductors. So, I agree with Pete's analysis of the current and voltage drop. As I said, I'd be OK with it and use 10g cable. Especially if he already has it. I guess that we jumped the gun and assumed it was a 120/240 volt unit instead of a single 120 volt unit. So that would be correct that he could get 26 amps at 120 volts. Even at that the # 10 wire should be large enough , especially as it is already installed. |
#20
Posted to alt.home.repair
|
|||
|
|||
Generator Cord Sizing 100' Run: Stay With 10-Gauge?
On Sun, 27 Jul 2014 14:40:02 -0500, "Terry Coombs"
wrote: Parallelling DC generators is not a serious problem Parralleling AC generators is a lot of fun, unless one of them is a synchronous generator (like an overdriven induction motor) https://en.wikipedia.org/wiki/Synchr...ing_current%29 Hey, I didn't say it was impossible - but not something the average homeowner is going to want to have to do every time there is a power outage. |
#21
Posted to alt.home.repair
|
|||
|
|||
Generator Cord Sizing 100' Run: Stay With 10-Gauge?
On Sun, 27 Jul 2014 15:59:25 -0400, Rick
wrote: On 07/27/2014 03:29 PM, wrote: The inverters "link" - the pwm signal from the one inverter bank drives the other bank as well. It is more than just the outputs connected. In the one's I've seen the second unit (partner) is switched to the "partner" mode instead of the "stand-alone" mode and it picks up the synch signal from the output of the "master" to run the inverter on the "partner". Basically the "smarts " of the partner unit are shut off and it gets the timing signal from the master. Would that make it single-phase 240 or two-phase 240? It would give you exactly what you get on a typical north american power line. Center tapped single phase 240. You won't get me into any arguement/discussion of whether it is single or 2 phase. |
#22
Posted to alt.home.repair
|
|||
|
|||
Generator Cord Sizing 100' Run: Stay With 10-Gauge?
On Sun, 27 Jul 2014 16:44:52 -0400, "Ralph Mowery"
wrote: wrote in message .. . These "motor geerator sets" were "ward leonard" drives - AC motor running DC generator to run variable speed DC motors bu varying the field current of the DC generator. Parallelling DC generators is not a serious problem Parralleling AC generators is a lot of fun, unless one of them is a synchronous generator (like an overdriven induction motor) The MG sets we were using were 3 phase 480 volt systems. We often used the light bulb or voltmeter system to put them in parallel. When the bulbs went out or the volt metes went to 0, then the switch was flipped. They then drove a bank of about 16 motors that were around 3 or 5 HP at 480 volt, 3 phase. OK, so basically mechanical phase converters? The input was single phase AC? How did you vary the speed of the prime mover?Mechanical variable speed drive? |
#23
Posted to alt.home.repair
|
|||
|
|||
Generator Cord Sizing 100' Run: Stay With 10-Gauge?
wrote:
On Sun, 27 Jul 2014 14:40:02 -0500, "Terry Coombs" wrote: Parallelling DC generators is not a serious problem Parralleling AC generators is a lot of fun, unless one of them is a synchronous generator (like an overdriven induction motor) https://en.wikipedia.org/wiki/Synchr...ing_current%29 Hey, I didn't say it was impossible - but not something the average homeowner is going to want to have to do every time there is a power outage. Well , there is that ... -- Snag |
#24
Posted to alt.home.repair
|
|||
|
|||
Generator Cord Sizing 100' Run: Stay With 10-Gauge?
wrote in message ... The MG sets we were using were 3 phase 480 volt systems. We often used the light bulb or voltmeter system to put them in parallel. When the bulbs went out or the volt metes went to 0, then the switch was flipped. They then drove a bank of about 16 motors that were around 3 or 5 HP at 480 volt, 3 phase. OK, so basically mechanical phase converters? The input was single phase AC? How did you vary the speed of the prime mover?Mechanical variable speed drive? I did not get into the prime mover that much, but I think it was a DC electronic drive that powered the motor part. The main power fed to the varitable speed part was 60 Hz 480 volt 3 phase. I think it was converted to DC to drive the motor part that controls the speed and then to the generator part that puts out lower frequency ( probably lower voltage also) 3 phase AC. I know it had a knob on it so we could change the speed of the motor driving the AC generator. When I needed to put one on line, I hooked a box up to some plugs on the speed control drive and adjusted the speed so the bulbs went out and threw a switch. I was not too concerned about the actual speed control part as others repaired that. My part of that job was just to get the MG sets on and off line without causing prblems. My main job was instrumentation, but had to know a little about most everything so I could fill in for the electrician that worked on each shift when they went on vacation. We also had a newer part of the plant that did the same thing except it was with all electronic controls and no MG sets. We had a box with meters on it that we used to sync the inverters to put the spare on and off line when we worked on the main speed control inverter. This setup was at a plant that made polyester. The 'small' motors powered gear pumps that forced the melted plastic out of a die. This speed had to be constant so the plastic comming out of the die would be the same thickness. There were 16 small motors being driven at the same time. We could shut off one or two of the small motors and not cause much of a problem,but if the whole thing shut off very long (much over 2 minuits) it would cause a major problem and loss of production. That is why we had a spare MG set for about 20 of the other MG sets. |
#25
Posted to alt.home.repair
|
|||
|
|||
Generator Cord Sizing 100' Run: Stay With 10-Gauge?
On 07/27/2014 02:59 PM, Rick wrote:
[snipp] Would that make it single-phase 240 or two-phase 240? "two-phase 240" sounds like you'd get 480 across the whole thing. These things are relative to ground, so it's a matter of what you do with the point that's between the generators. |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
extension cord 12 gauge 75 ft vs 100 ft for lawn mower | Home Repair | |||
generator extension cord | Home Repair | |||
generator extension cord | Home Ownership | |||
What gauge is this extension cord | Home Repair | |||
110v extension cord sizing | Woodworking |