A friend is having a heated pool installed. He has a breaker panel outside
near the pool. He was told that per NYS code, the wires that go run through
his basement from the exterior panel to the main panel must be run inside
rigid conduit. He said that they didn't use individual wires, they used
some type of jacketed cable that contains 4(?) wires and they ran that
inside grey plastic conduit. I haven't seen it, but I assume it's Schedule
40 PVC.

Another friend had a heated pool installed last year (also in NYS) and he
said that they didn't use conduit through his basement. They just stabled a
large cable to the joists.

So what's the story? Is the conduit required? If it is, is it specifically
related to the pool or is it because there's another panel involved?

Thanks.
  #2   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 22,192
Default Pool Wiring Question

On Tue, 27 May 2014 18:55:20 +0000 (UTC), DerbyDad03
wrote:

A friend is having a heated pool installed. He has a breaker panel outside
near the pool. He was told that per NYS code, the wires that go run through
his basement from the exterior panel to the main panel must be run inside
rigid conduit. He said that they didn't use individual wires, they used
some type of jacketed cable that contains 4(?) wires and they ran that
inside grey plastic conduit. I haven't seen it, but I assume it's Schedule
40 PVC.

Another friend had a heated pool installed last year (also in NYS) and he
said that they didn't use conduit through his basement. They just stabled a
large cable to the joists.

So what's the story? Is the conduit required? If it is, is it specifically
related to the pool or is it because there's another panel involved?

Thanks.


I'm not an electrician so cannot offer advice. I suspect this is
related to 220V, exposed wire and water. My pool wires are in a
specific type of PVC pipe that has water tight fittings. They run
along the outside wall just below ground, the length of the house, to
the pump area. I'm sure the wires are in conduit to prevent any
possible cutting by say a shovel, etc.

In Nevada, a contractor must have an additional contractor license to
install a pool. Based on codes for pool construction. Meaning, a
contractor has a license to build a house, but needs an additional
license for pool construction.
  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 14,845
Default Pool Wiring Question

Oren wrote:
On Tue, 27 May 2014 18:55:20 +0000 (UTC), DerbyDad03
wrote:

A friend is having a heated pool installed. He has a breaker panel outside
near the pool. He was told that per NYS code, the wires that go run through
his basement from the exterior panel to the main panel must be run inside
rigid conduit. He said that they didn't use individual wires, they used
some type of jacketed cable that contains 4(?) wires and they ran that
inside grey plastic conduit. I haven't seen it, but I assume it's Schedule
40 PVC.

Another friend had a heated pool installed last year (also in NYS) and he
said that they didn't use conduit through his basement. They just stabled a
large cable to the joists.

So what's the story? Is the conduit required? If it is, is it specifically
related to the pool or is it because there's another panel involved?

Thanks.


I'm not an electrician so cannot offer advice. I suspect this is
related to 220V, exposed wire and water. My pool wires are in a
specific type of PVC pipe that has water tight fittings. They run
along the outside wall just below ground, the length of the house, to
the pump area. I'm sure the wires are in conduit to prevent any
possible cutting by say a shovel, etc.


I was asking about the wires that run _inside_ the house from where they
enter through the wall and run back to the main interior panel, not the
wires that run underground or from the exterior panel to pump/heater/etc.
  #4   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 15,279
Default Pool Wiring Question

On Tuesday, May 27, 2014 3:25:41 PM UTC-4, DerbyDad03 wrote:
Oren wrote:

On Tue, 27 May 2014 18:55:20 +0000 (UTC), DerbyDad03


wrote:




A friend is having a heated pool installed. He has a breaker panel outside


near the pool. He was told that per NYS code, the wires that go run through


his basement from the exterior panel to the main panel must be run inside


rigid conduit. He said that they didn't use individual wires, they used


some type of jacketed cable that contains 4(?) wires and they ran that


inside grey plastic conduit. I haven't seen it, but I assume it's Schedule


40 PVC.




Another friend had a heated pool installed last year (also in NYS) and he


said that they didn't use conduit through his basement. They just stabled a


large cable to the joists.




So what's the story? Is the conduit required? If it is, is it specifically


related to the pool or is it because there's another panel involved?




Thanks.




I'm not an electrician so cannot offer advice. I suspect this is


related to 220V, exposed wire and water. My pool wires are in a


specific type of PVC pipe that has water tight fittings. They run


along the outside wall just below ground, the length of the house, to


the pump area. I'm sure the wires are in conduit to prevent any


possible cutting by say a shovel, etc.




I was asking about the wires that run _inside_ the house from where they

enter through the wall and run back to the main interior panel, not the

wires that run underground or from the exterior panel to pump/heater/etc.



There isn't anything in NEC that differentiates how a subpanel for
a pool is connected versus any other subpanel. There is no reason I
know of that says wires for a pool or anything else have to be run
in rigid conduit for a subpanel. Here, NJ, very typical to use
appropriate sized cable to go from the basement panel
to the pool subpanel, on the side of the house. If they had an
existing code compliant subpanel that the pool could run off, no
reason to go rework that with conduit inside the house, which is
what it looks like you;re saying they did.
  #5   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 14,845
Default Pool Wiring Question

trader_4 wrote:
On Tuesday, May 27, 2014 3:25:41 PM UTC-4, DerbyDad03 wrote:
Oren wrote:

On Tue, 27 May 2014 18:55:20 +0000 (UTC), DerbyDad03


wrote:




A friend is having a heated pool installed. He has a breaker panel outside


near the pool. He was told that per NYS code, the wires that go run through


his basement from the exterior panel to the main panel must be run inside


rigid conduit. He said that they didn't use individual wires, they used


some type of jacketed cable that contains 4(?) wires and they ran that


inside grey plastic conduit. I haven't seen it, but I assume it's Schedule


40 PVC.




Another friend had a heated pool installed last year (also in NYS) and he


said that they didn't use conduit through his basement. They just stabled a


large cable to the joists.




So what's the story? Is the conduit required? If it is, is it specifically


related to the pool or is it because there's another panel involved?




Thanks.




I'm not an electrician so cannot offer advice. I suspect this is


related to 220V, exposed wire and water. My pool wires are in a


specific type of PVC pipe that has water tight fittings. They run


along the outside wall just below ground, the length of the house, to


the pump area. I'm sure the wires are in conduit to prevent any


possible cutting by say a shovel, etc.




I was asking about the wires that run _inside_ the house from where they

enter through the wall and run back to the main interior panel, not the

wires that run underground or from the exterior panel to pump/heater/etc.



There isn't anything in NEC that differentiates how a subpanel for
a pool is connected versus any other subpanel. There is no reason I
know of that says wires for a pool or anything else have to be run
in rigid conduit for a subpanel. Here, NJ, very typical to use
appropriate sized cable to go from the basement panel
to the pool subpanel, on the side of the house. If they had an
existing code compliant subpanel that the pool could run off, no
reason to go rework that with conduit inside the house, which is
what it looks like you;re saying they did.


Sorry if I wasn't clear. He did not have a panel outside the house until
the pool was installed. The panel was installed as part of the pool
installation. At the time the panel was installed, he was told that conduit
was required for the wires from that panel to the main panel.

I can say upfront that he wasn't being ripped off by the installer because
the installer is doing everything he can to save the homeowner some money.
The installer told my friend "if I buy the conduit, I have to mark it up.
Take this list. If all these conduit parts are here when I run the wires,
then I'll use it."


  #6   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 296
Default Pool Wiring Question

On Tuesday, May 27, 2014 4:01:07 PM UTC-4, DerbyDad03 wrote:
trader_4 wrote:

On Tuesday, May 27, 2014 3:25:41 PM UTC-4, DerbyDad03 wrote:


Oren wrote:




On Tue, 27 May 2014 18:55:20 +0000 (UTC), DerbyDad03




wrote:








A friend is having a heated pool installed. He has a breaker panel outside




near the pool. He was told that per NYS code, the wires that go run through




his basement from the exterior panel to the main panel must be run inside




rigid conduit. He said that they didn't use individual wires, they used




some type of jacketed cable that contains 4(?) wires and they ran that




inside grey plastic conduit. I haven't seen it, but I assume it's Schedule




40 PVC.








Another friend had a heated pool installed last year (also in NYS) and he




said that they didn't use conduit through his basement. They just stabled a




large cable to the joists.








So what's the story? Is the conduit required? If it is, is it specifically




related to the pool or is it because there's another panel involved?








Thanks.








I'm not an electrician so cannot offer advice. I suspect this is




related to 220V, exposed wire and water. My pool wires are in a




specific type of PVC pipe that has water tight fittings. They run




along the outside wall just below ground, the length of the house, to




the pump area. I'm sure the wires are in conduit to prevent any




possible cutting by say a shovel, etc.








I was asking about the wires that run _inside_ the house from where they




enter through the wall and run back to the main interior panel, not the




wires that run underground or from the exterior panel to pump/heater/etc.






There isn't anything in NEC that differentiates how a subpanel for


a pool is connected versus any other subpanel. There is no reason I


know of that says wires for a pool or anything else have to be run


in rigid conduit for a subpanel. Here, NJ, very typical to use


appropriate sized cable to go from the basement panel


to the pool subpanel, on the side of the house. If they had an


existing code compliant subpanel that the pool could run off, no


reason to go rework that with conduit inside the house, which is


what it looks like you;re saying they did.




Sorry if I wasn't clear. He did not have a panel outside the house until

the pool was installed. The panel was installed as part of the pool

installation. At the time the panel was installed, he was told that conduit

was required for the wires from that panel to the main panel.



I can say upfront that he wasn't being ripped off by the installer because

the installer is doing everything he can to save the homeowner some money..

The installer told my friend "if I buy the conduit, I have to mark it up.

Take this list. If all these conduit parts are here when I run the wires,

then I'll use it."


There may have been other circumstances in the situation. He has to protect the wire from the main to the sub-panel from damage. One way is conduit. Another way is to run it inside a wall. Possibly the conduit was cheaper.. That's not specific to pools, you have to protect any exposed wire.
  #7   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 15,279
Default Pool Wiring Question

On Tuesday, May 27, 2014 4:01:07 PM UTC-4, DerbyDad03 wrote:
trader_4 wrote:

On Tuesday, May 27, 2014 3:25:41 PM UTC-4, DerbyDad03 wrote:


Oren wrote:




On Tue, 27 May 2014 18:55:20 +0000 (UTC), DerbyDad03




wrote:








A friend is having a heated pool installed. He has a breaker panel outside




near the pool. He was told that per NYS code, the wires that go run through




his basement from the exterior panel to the main panel must be run inside




rigid conduit. He said that they didn't use individual wires, they used




some type of jacketed cable that contains 4(?) wires and they ran that




inside grey plastic conduit. I haven't seen it, but I assume it's Schedule




40 PVC.








Another friend had a heated pool installed last year (also in NYS) and he




said that they didn't use conduit through his basement. They just stabled a




large cable to the joists.








So what's the story? Is the conduit required? If it is, is it specifically




related to the pool or is it because there's another panel involved?








Thanks.








I'm not an electrician so cannot offer advice. I suspect this is




related to 220V, exposed wire and water. My pool wires are in a




specific type of PVC pipe that has water tight fittings. They run




along the outside wall just below ground, the length of the house, to




the pump area. I'm sure the wires are in conduit to prevent any




possible cutting by say a shovel, etc.








I was asking about the wires that run _inside_ the house from where they




enter through the wall and run back to the main interior panel, not the




wires that run underground or from the exterior panel to pump/heater/etc.






There isn't anything in NEC that differentiates how a subpanel for


a pool is connected versus any other subpanel. There is no reason I


know of that says wires for a pool or anything else have to be run


in rigid conduit for a subpanel. Here, NJ, very typical to use


appropriate sized cable to go from the basement panel


to the pool subpanel, on the side of the house. If they had an


existing code compliant subpanel that the pool could run off, no


reason to go rework that with conduit inside the house, which is


what it looks like you;re saying they did.




Sorry if I wasn't clear. He did not have a panel outside the house until

the pool was installed. The panel was installed as part of the pool

installation. At the time the panel was installed, he was told that conduit

was required for the wires from that panel to the main panel.



I can say upfront that he wasn't being ripped off by the installer because

the installer is doing everything he can to save the homeowner some money.

The installer told my friend "if I buy the conduit, I have to mark it up.

Take this list. If all these conduit parts are here when I run the wires,

then I'll use it."


Well shiver me timbers, I got this wrong. Special rules do apply
for a pool subpanel. NEC 680.25 states that any
feeders supplying a pool panel must be in conduit, either EMT, PVC,
liquidtight, etc. So, the installers are correct.
  #8   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 22,192
Default Pool Wiring Question

On Tue, 27 May 2014 19:25:41 +0000 (UTC), DerbyDad03
wrote:

I was asking about the wires that run _inside_ the house from where they
enter through the wall and run back to the main interior panel, not the
wires that run underground or from the exterior panel to pump/heater/etc.


I appreciate that. I was simply trying to say conduit may be needed
to protect 220V wires, reduce potential for water intrusion, and from
possible accidental damage. Worth a look into the codes. I can't say.
I'm not in NYS.
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Wiring a pool Terry Home Repair 1 June 1st 07 03:32 PM
Pool timer wiring dilemma RakeKiller Home Repair 9 April 25th 07 12:29 PM
Wiring 220 V pool Timer - HElp John W Home Repair 3 April 8th 07 07:40 PM
Pool wiring Kim Borchers Electronics Repair 3 August 23rd 06 06:34 PM
Pool Filter Wiring Size Ron in NY Home Repair 1 June 28th 05 01:02 AM


All times are GMT +1. The time now is 07:09 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"