Burnt Outlet
Had a potential fire hazard occur a few days ago when a plug for an electric baseboard heater (the outlet is behind some furniture) apparently developed a bad connection. Perhaps the plug was not seated properly or was dislodged by a tug on the cord? Anyway at some point things got hot. Two smoke alarms failed to go off and in the morning I was told by a family member that "the heater isn't working and apparently has fried itself."
There was a heavy smell that something had fried. Upon inspection the outlet and heater plug was fried and there was a burnt spot on the back of the furniture. The white wire insulation inside the outlet was totally crunchy, so there was considerable heat at the connection and the heat conducted up the white wire. I guess an AFCI breaker might have shut this down, and I see one company sells temperature sensing outlets. I wish the outlets were more commonly available. The breakers would never fit my old box. |
#2
Posted to alt.home.repair
|
|||
|
|||
Burnt Outlet
On 2/16/2014 1:27 PM, Davej wrote:
Had a potential fire hazard occur a few days ago when a plug for an electric baseboard heater (the outlet is behind some furniture) apparently developed a bad connection. Perhaps the plug was not seated properly or was dislodged by a tug on the cord? ... You were well past a "potential" hazard at that point. More likely there was a loose connection on the outlet...isn't the "backstabbed" type by any chance't? That sounds like a very risky installation/usage pattern, anyway, of placing an electric heater behind furniture... -- |
#3
Posted to alt.home.repair
|
|||
|
|||
Burnt Outlet
On Sun, 16 Feb 2014 13:46:31 -0600, dpb wrote:
On 2/16/2014 1:27 PM, Davej wrote: Had a potential fire hazard occur a few days ago when a plug for an electric baseboard heater (the outlet is behind some furniture) apparently developed a bad connection. Perhaps the plug was not seated properly or was dislodged by a tug on the cord? ... You were well past a "potential" hazard at that point. Yes indeed. Congratulations Davej. You dodged a bullet More likely there was a loose connection on the outlet...isn't the "backstabbed" type by any chance't? That sounds like a very risky installation/usage pattern, anyway, of placing an electric heater behind furniture... I think only the plug and cord were behind the sofa. When I had this problem, it wasn't behind furniture, but I was sleeping. I also had a very old receptacle. Mine was covered by 20 layers of paint, but in the case of Davej, if it was more than 10 years old, maybe he should have replaced the receptacle before using it for this, certainly if it was at all loose or more than 15. I presume you've replaced it now. Make sure it grips it firmly and after the heater has been running for 20 minutes, hold the plug in your hand to see if it is warm. It shouldn't be at all warm. I've also seen clamps to hold a plug into a recept. Held on by the screw in the center. Or you can make one |
#4
Posted to alt.home.repair
|
|||
|
|||
Burnt Outlet
On 2/16/2014 2:46 PM, dpb wrote:
On 2/16/2014 1:27 PM, Davej wrote: Had a potential fire hazard occur a few days ago when a plug for an electric baseboard heater (the outlet is behind some furniture) apparently developed a bad connection. Perhaps the plug was not seated properly or was dislodged by a tug on the cord? ... You were well past a "potential" hazard at that point. More likely there was a loose connection on the outlet...isn't the "backstabbed" type by any chance't? That sounds like a very risky installation/usage pattern, anyway, of placing an electric heater behind furniture... -- I read the OUTLET was behind furniture. The heater, not clear. -- .. Christopher A. Young Learn about Jesus www.lds.org .. |
#5
Posted to alt.home.repair
|
|||
|
|||
Burnt Outlet
On Sunday, February 16, 2014 3:58:50 PM UTC-6, Stormin Mormon wrote:
On 2/16/2014 2:46 PM, dpb wrote: On 2/16/2014 1:27 PM, Davej wrote: Had a potential fire hazard occur a few days ago when a plug for an electric baseboard heater (the outlet is behind some furniture) apparently developed a bad connection. Perhaps the plug was not seated properly or was dislodged by a tug on the cord? ... You were well past a "potential" hazard at that point. More likely there was a loose connection on the outlet...isn't the "backstabbed" type by any chance't? That sounds like a very risky installation/usage pattern, anyway, of placing an electric heater behind furniture... I read the OUTLET was behind furniture. The heater, not clear. The outlet was old, perhaps 20+ years, but not coated with paint. The outlet is behind furniture but the heater isn't. The cord is not in a place where it would normally be touched or tugged. I remember unplugging the heater last Spring but I believe a family member plugged it back in this Fall, and that I suspect may have been the problem. Perhaps they did not plug it in carefully and fully? I never use the "backstab" holes in outlets because I don't feel they provide a reliable connection. I think I will be installing a dedicated outlet for this heater in the near future. Thanks for the comments. |
#6
Posted to alt.home.repair
|
|||
|
|||
Burnt Outlet
On 2/16/2014 11:16 PM, Davej wrote:
The outlet was old, perhaps 20+ years, but not coated with paint. The outlet is behind furniture but the heater isn't. The cord is not in a place where it would normally be touched or tugged. I remember unplugging the heater last Spring but I believe a family member plugged it back in this Fall, and that I suspect may have been the problem. Perhaps they did not plug it in carefully and fully? I never use the "backstab" holes in outlets because I don't feel they provide a reliable connection. I think I will be installing a dedicated outlet for this heater in the near future. Thanks for the comments. I'm pleased the outlet did not catch fire, and you and your family are safe. Might be a good socket to install a two dollar socket, not the bargain basket 59 center. Cheaper than rebuilding. -- .. Christopher A. Young Learn about Jesus www.lds.org .. |
#7
Posted to alt.home.repair
|
|||
|
|||
Burnt Outlet
On 2/16/2014 1:27 PM, Davej wrote:
Had a potential fire hazard occur a few days ago when a plug for an electric baseboard heater (the outlet is behind some furniture) apparently developed a bad connection. Perhaps the plug was not seated properly or was dislodged by a tug on the cord? Anyway at some point things got hot. Two smoke alarms failed to go off and in the morning I was told by a family member that "the heater isn't working and apparently has fried itself." The smell produced by overheating was probably not smoke. Not exactly reassuring, but if there had been an actual fire the smoke alarms should have gone off. There was a heavy smell that something had fried. Upon inspection the outlet and heater plug was fried and there was a burnt spot on the back of the furniture. The white wire insulation inside the outlet was totally crunchy, so there was considerable heat at the connection and the heat conducted up the white wire. I guess an AFCI breaker might have shut this down, and I see one company sells temperature sensing outlets. There can be a loose connection that produces a "glowing connection" that is stable, and an AFCI won't trip on arc detection because there is no arc. In 2001 UL did testing for Cutler-Hammer on glowing connections. Steel connection screws (plated)were the easiest to create a glowing connection. A few amps could produce a glowing connection. The heat can, obviously, start fires. And the heat can carbonize the plastic, which can create a leakage path to a ground terminal or the yoke. Since AFCIs also have a ground fault detector (at 30 mA), that can cause an AFCI trip. Of 16 receptacle trials, 9 tripped the AFCI. (In 6 the wire burned open, and in 1 the test was ended after 35 hours.) A glowing connection might also eventually become an arc. The earliest AFCIs would only detect high current arcs - between wires. They would not detect a loose connection, which is lower current than the circuit breaker rating. More sensitive AFCIs were required in the 2002 NEC, and they can detect a series arc (?above 5 amps). The older ones will still trip on a ground fault. I wish the outlets were more commonly available. The breakers would never fit my old box. As gfretwell wrote, AFCI receptacles are now available. In addition to installing them as in his post, you could put AFCI receptacles next to the panel and use the wire-through feature to protect existing circuits. |
#8
Posted to alt.home.repair
|
|||
|
|||
Burnt Outlet
"bud--" wrote in message news:53025e07$0$47887$c3e8da3
stuff snipped As gfretwell wrote, AFCI receptacles are now available. In addition to installing them as in his post, you could put AFCI receptacles next to the panel and use the wire-through feature to protect existing circuits. I wired in three new 20A circuits to service two space heaters and a convection combo oven. Since I knew where the first outlets were on the branch circuits I simply replaced those outlets with Leviton AFTR2-W SmartlockPro Outlet Branch Circuit Arc-Fault Circuit Interrupter Receptacle, 20-Amp units ($25 each at Amazon) and connected the downstream outlets through the load connections. The only real downside of doing that is that when an AFCI outlet trips, you have to roam around the house looking for it. I've made an addendum to the ever-growing list of notations inside the panel door of where they are (along with GFCI's wired the same way) but it still complicates things. There are circuits I'd like to protect where I don't necessarily know where the first outlet in the chain happens to be (is there a way to determine that?) so they would have to be protected by AFCI breakers instead of AFCI outlets. The circuit breaker AFCI's are almost twice as expensive and require a neutral pigtail connection in the circuit breaker panel. Since my neutral bar is already at capacity, the outlets seemed to make more sense cost-wise and installation-wise. I have a question for you. Is it "code" to use two neutral buss bars in a circuit breaker panel? The one I just bought is rated for putting two 12 gauge wires under one screw but I don't like to do that if I can avoid it. I could remove the old one and replace it with the one rated for two wires per terminal and double up all the neutrals but I would rather install a second one on the opposite side of the panel and still connect one wire per terminal. Just not sure that two separate neutral buss bars is permissible. I have to admit since reading about what you wrote about the UL tests I am not sure arc fault protection devices are worth all the effort. I've had two meltdowns already from plugs that were either not fully plugged in or had come loose and one because an six-outlet adapter's crimped internal buss bar worked itself loose. It would be nice to know if the AFCI could have detected any of those events. I am beginning to think they might not have. -- Bobby G. |
#9
Posted to alt.home.repair
|
|||
|
|||
Burnt Outlet
On 2/18/2014 1:57 PM, Robert Green wrote:
"bud--" wrote in message news:53025e07$0$47887$c3e8da3 stuff snipped As gfretwell wrote, AFCI receptacles are now available. In addition to installing them as in his post, you could put AFCI receptacles next to the panel and use the wire-through feature to protect existing circuits. I wired in three new 20A circuits to service two space heaters and a convection combo oven. Since I knew where the first outlets were on the branch circuits I simply replaced those outlets with Leviton AFTR2-W SmartlockPro Outlet Branch Circuit Arc-Fault Circuit Interrupter Receptacle, 20-Amp units ($25 each at Amazon) and connected the downstream outlets through the load connections. New in the 2011 NEC - if you extend an existing circuit in an area where AFCI protection is required the extension (including wiring) must be AFCI protected. Wiring through an AFCI receptacle (as you did) is one way to provide that protection. Almost every receptacle in a dwelling must now be AFCI or GFCI protected (when originally wired or replaced). In the 2014 NEC some must be both. Also new in 2011 - replacement receptacles in areas where AFCI protection is now required have to be AFCI protected (several methods) - replacement receptacles in areas that now require tamper-resistant receptacles must be tamper-resistant (that is most of the general purpose receptacles in a dwelling)(keeps kids from putting paper-clips in the receptacle) - replacement receptacles in areas that now require weather-resistant receptacles must be weather-resistant (damp locations, like outdoors) And replacement receptacles where GFCI protection is now required must be GFCI protected AFCI or GFCI receptacles may have to be tamper-resistant or weather-resistant. The only real downside of doing that is that when an AFCI outlet trips, you have to roam around the house looking for it. I've made an addendum to the ever-growing list of notations inside the panel door of where they are (along with GFCI's wired the same way) but it still complicates things. There are circuits I'd like to protect where I don't necessarily know where the first outlet in the chain happens to be (is there a way to determine that?) so they would have to be protected by AFCI breakers instead of AFCI outlets. Or install AFCI receptacles at the panel as in my last post. The circuit breaker AFCI's are almost twice as expensive and require a neutral pigtail connection in the circuit breaker panel. Since my neutral bar is already at capacity, the outlets seemed to make more sense cost-wise and installation-wise. I have a question for you. Is it "code" to use two neutral buss bars in a circuit breaker panel? The one I just bought is rated for putting two 12 gauge wires under one screw but I don't like to do that if I can avoid it. I could remove the old one and replace it with the one rated for two wires per terminal and double up all the neutrals but I would rather install a second one on the opposite side of the panel and still connect one wire per terminal. Just not sure that two separate neutral buss bars is permissible. You can double-up wires only when the manufacturer says it is allowed. Look at the label for the panel. Neutrals are never allowed to be doubled-up - it is a code violation (408.41). It is relatively easy to add ground bars. The label for the panel should say what accessory bars can be used. If you have ground wires on the existing neutral bar they can be moved to the ground bar (and maybe doubled-up). Neutrals can not be landed on a ground bar (the enclosure can not be used as the neutral-path connection from ground bar to neutral bar in a service panel). I don't know if accessory neutral bars are available. They are not as easy to install. Other than in a service panel, they have to be insulated from the enclosure, and you have to figure out the size of the conductor to connect it to the existing neutral bar. I have to admit since reading about what you wrote about the UL tests I am not sure arc fault protection devices are worth all the effort. I've had two meltdowns already from plugs that were either not fully plugged in or had come loose and one because an six-outlet adapter's crimped internal buss bar worked itself loose. It would be nice to know if the AFCI could have detected any of those events. I am beginning to think they might not have. Was it a high resistance or arc? Some loose connections are an arc. In the research done for Cutler-Hammer about 1/2 of the high resistance connections resulted in a ground fault trip when leakage to ground resulted from the heat. The 30 mA ground fault trip in an AFCI is there for that reason. And a "glowing connection" may turn into an arc. The NEC keeps increasing the locations where AFCI protection is required. Would be nice if there was data that showed they have a major effect. But they will likely be most useful as the wiring ages. |
#10
Posted to alt.home.repair
|
|||
|
|||
Burnt Outlet
"bud--" wrote in message
eb.com... On 2/18/2014 1:57 PM, Robert Green wrote: good stuff about new 2011 requirements snipped to be moved to a new thread later The only real downside of doing that is that when an AFCI outlet trips, you have to roam around the house looking for it. I've made an addendum to the ever-growing list of notations inside the panel door of where they are (along with GFCI's wired the same way) but it still complicates things. There are circuits I'd like to protect where I don't necessarily know where the first outlet in the chain happens to be (is there a way to determine that?) so they would have to be protected by AFCI breakers instead of AFCI outlets. Or install AFCI receptacles at the panel as in my last post. There's really not room for that in my panel area. I suppose I could eventually figure out where the first outlet in a branch circuit is with a fox and hound. I could ID all the outlets in circuit that way (or by breaker switching) and then disconnecting the outlet that's the most likely candidate and testing for power at the downstream outlets but that's a lot of work and a lot of torquing around of old, cloth covered wiring that is old and doesn't like to be bothered much anymore. Just like me. (-: stuff snipped The circuit breaker AFCI's are almost twice as expensive and require a I have a question for you. Is it "code" to use two neutral buss bars in a circuit breaker panel? The one I just bought is rated for putting two 12 gauge wires under one screw but I don't like to do that if I can avoid it. I could remove the old one and replace it with the one rated for two wires per terminal and double up all the neutrals but I would rather install a second one on the opposite side of the panel and still connect one wire per terminal. Just not sure that two separate neutral buss bars is permissible. You can double-up wires only when the manufacturer says it is allowed. Look at the label for the panel. Neutrals are never allowed to be doubled-up - it is a code violation (408.41). Which clearly makes what I have ground bars. It is relatively easy to add ground bars. The label for the panel should say what accessory bars can be used. If you have ground wires on the existing neutral bar they can be moved to the ground bar (and maybe doubled-up). Neutrals can not be landed on a ground bar (the enclosure can not be used as the neutral-path connection from ground bar to neutral bar in a service panel). I was under the impression, probably wrong, that if you connected a secondary buss bar with a large gauge wire (#8) to the neutral buss bar that it was acceptable to land neutral wires on the secondary buss bar but now I am not sure where I read that or if it's true. I realize now that the OEM neutral bar on my Square D panel sits above all the breakers and looks to be isolated from the enclosure. I just looked and it seems that the small buss bar I have can be piggy-backed to the existing neutral bar, but I am going to have to look up the manual for the panel to be sure. Now a number of things have become clearer to me, which is probably good safety wise but is going to mean a lot of work and/or expense to bring it up to code. Electrically the panel is connected to the neutral conductor just because ground wires are connected to the neutral bus, correct? I think you're saying that the issue is that a secondary neutral buss can't depend on that connection. The Square D panel has mounts for ground buss bars on both sides of the panel. Even moving all the ground wires from the original neutral buss to a auxiliary ground bar won't help because there aren't many grounds (this is a two-pin outlet house, at least on all the older circuits). I installed a number of dual skinnies just to be able to take high current outlet loads off the old circuits which now primarily serve low wattage CFL lights. I also installed one AFCI breaker with a pigtail before moving on to the cheaper AFCI outlets, in part because of the lack of neutral buss bar connections. I don't know if accessory neutral bars are available. They are not as easy to install. Other than in a service panel, they have to be insulated from the enclosure, and you have to figure out the size of the conductor to connect it to the existing neutral bar. I am not sure what you mean by "other than in a service panel, they have to be insulated from the enclosure." I thought I did this correctly because I recall going out and having to buy one foot of 8 gauge wire to connect the secondary bar going alongside the rows of breakers inside the circuit breaker panel. I'll have to review my notes about that. I did notice Square D make two identical forms of the buss bar except one was tinted green, the other was all silver which made me also believe that they could be used to ":land neutrals" (I like that phrase) as well as grounds. I have to admit since reading about what you wrote about the UL tests I am not sure arc fault protection devices are worth all the effort. I've had two meltdowns already from plugs that were either not fully plugged in or had come loose and one because an six-outlet adapter's crimped internal buss bar worked itself loose. It would be nice to know if the AFCI could have detected any of those events. I am beginning to think they might not have. Was it a high resistance or arc? One was an arc because you could hear it. The others were most likely high resistance. Some loose connections are an arc. In the research done for Cutler-Hammer about 1/2 of the high resistance connections resulted in a ground fault trip when leakage to ground resulted from the heat. The 30 mA ground fault trip in an AFCI is there for that reason. And a "glowing connection" may turn into an arc. Someone mentioned thermally protected outlets that cut out when they get too hot. I've never heard of them. Are they something standard in the industry? Would they offer protection against high resistance connections that the AFCI's don't seem to provide? The NEC keeps increasing the locations where AFCI protection is required. Would be nice if there was data that showed they have a major effect. But they will likely be most useful as the wiring ages. I suppose that the data will fill in over time. Based on the number of breaker trips I've experienced in my life, I suspect that breakers have saved my life a lot more often than most other protection devices including my firearms. (-: Thanks for your input, Bud. -- Bobby G. |
#11
Posted to alt.home.repair
|
|||
|
|||
Burnt Outlet
On 2/20/2014 8:23 PM, Robert Green wrote:
"bud--" wrote in message eb.com... On 2/18/2014 1:57 PM, Robert Green wrote: good stuff about new 2011 requirements snipped to be moved to a new thread later The only real downside of doing that is that when an AFCI outlet trips, you have to roam around the house looking for it. I've made an addendum to the ever-growing list of notations inside the panel door of where they are (along with GFCI's wired the same way) but it still complicates things. There are circuits I'd like to protect where I don't necessarily know where the first outlet in the chain happens to be (is there a way to determine that?) so they would have to be protected by AFCI breakers instead of AFCI outlets. Or install AFCI receptacles at the panel as in my last post. There's really not room for that in my panel area. I suppose I could eventually figure out where the first outlet in a branch circuit is with a fox and hound. I could ID all the outlets in circuit that way (or by breaker switching) and then disconnecting the outlet that's the most likely candidate and testing for power at the downstream outlets but that's a lot of work and a lot of torquing around of old, cloth covered wiring that is old and doesn't like to be bothered much anymore. Just like me. (-: Making a map with device locations and circuit number is real useful, but a PITA. Would give you an idea where the first device is. If you AFCI the first receptacle and wire through the rest, the device protects the wiring downstream. All the load is at or downstream. The AFCI receptacle will protect the wiring back to the panel from series arcs (loose connections) by disconnecting the load that maintains the arc. stuff snipped The circuit breaker AFCI's are almost twice as expensive and require a I have a question for you. Is it "code" to use two neutral buss bars in a circuit breaker panel? The one I just bought is rated for putting two 12 gauge wires under one screw but I don't like to do that if I can avoid it. I could remove the old one and replace it with the one rated for two wires per terminal and double up all the neutrals but I would rather install a second one on the opposite side of the panel and still connect one wire per terminal. Just not sure that two separate neutral buss bars is permissible. You can double-up wires only when the manufacturer says it is allowed. Look at the label for the panel. Neutrals are never allowed to be doubled-up - it is a code violation (408.41). Which clearly makes what I have ground bars. It is relatively easy to add ground bars. The label for the panel should say what accessory bars can be used. If you have ground wires on the existing neutral bar they can be moved to the ground bar (and maybe doubled-up). Neutrals can not be landed on a ground bar (the enclosure can not be used as the neutral-path connection from ground bar to neutral bar in a service panel). I was under the impression, probably wrong, that if you connected a secondary buss bar with a large gauge wire (#8) to the neutral buss bar that it was acceptable to land neutral wires on the secondary buss bar but now I am not sure where I read that or if it's true. I realize now that the OEM neutral bar on my Square D panel sits above all the breakers and looks to be isolated from the enclosure. I assume that if there is a wire-connection that would work. You have to figure out what size wire is appropriate. Slight chance an inspector might object to using something the manufacturer calls a "ground bar" as a neutral bar. I just looked and it seems that the small buss bar I have can be piggy-backed to the existing neutral bar, but I am going to have to look up the manual for the panel to be sure. Now a number of things have become clearer to me, which is probably good safety wise but is going to mean a lot of work and/or expense to bring it up to code. Electrically the panel is connected to the neutral conductor just because ground wires are connected to the neutral bus, correct? I think you're saying that the issue is that a secondary neutral buss can't depend on that connection. The Square D panel has mounts for ground buss bars on both sides of the panel. Even moving all the ground wires from the original neutral buss to a auxiliary ground bar won't help because there aren't many grounds (this is a two-pin outlet house, at least on all the older circuits). I installed a number of dual skinnies just to be able to take high current outlet loads off the old circuits which now primarily serve low wattage CFL lights. I also installed one AFCI breaker with a pigtail before moving on to the cheaper AFCI outlets, in part because of the lack of neutral buss bar connections. A subpanel near the service panel is another possibility. (But then you will never be able to sell your house - according to one opinion. And you won't be able to get insurance. And a house inspector may say the house should be torn down. And it should be torn down. And that does not include the shame of having a subpanel.) I don't know if accessory neutral bars are available. They are not as easy to install. Other than in a service panel, they have to be insulated from the enclosure, and you have to figure out the size of the conductor to connect it to the existing neutral bar. I am not sure what you mean by "other than in a service panel, they have to be insulated from the enclosure." In a service panel the neutral and enclosure are connected together. Could be a wire. Often is a screw and looks like a mounting screw but may be green. If the neutral and enclosure are bonded, an added neutral bar would not have to be insulated from the enclosure (but may not rely on the enclosure as the electrical connection back to original neutral bar). In a subpanel, an added neutral bar must be insulated. I thought I did this correctly because I recall going out and having to buy one foot of 8 gauge wire to connect the secondary bar going alongside the rows of breakers inside the circuit breaker panel. I'll have to review my notes about that. I did notice Square D make two identical forms of the buss bar except one was tinted green, the other was all silver which made me also believe that they could be used to ":land neutrals" (I like that phrase) as well as grounds. I have to admit since reading about what you wrote about the UL tests I am not sure arc fault protection devices are worth all the effort. I've had two meltdowns already from plugs that were either not fully plugged in or had come loose and one because an six-outlet adapter's crimped internal buss bar worked itself loose. It would be nice to know if the AFCI could have detected any of those events. I am beginning to think they might not have. Was it a high resistance or arc? One was an arc because you could hear it. The others were most likely high resistance. Some loose connections are an arc. In the research done for Cutler-Hammer about 1/2 of the high resistance connections resulted in a ground fault trip when leakage to ground resulted from the heat. The 30 mA ground fault trip in an AFCI is there for that reason. And a "glowing connection" may turn into an arc. Someone mentioned thermally protected outlets that cut out when they get too hot. I've never heard of them. Are they something standard in the industry? Would they offer protection against high resistance connections that the AFCI's don't seem to provide? I have never heard of thermally protected outlets. Is that feature UL listed? And AFCIs may trip on a ground fault caused by a "glowing connection", or if a glowing connection turns into an arc. The NEC keeps increasing the locations where AFCI protection is required. Would be nice if there was data that showed they have a major effect. But they will likely be most useful as the wiring ages. I suppose that the data will fill in over time. Based on the number of breaker trips I've experienced in my life, I suspect that breakers have saved my life a lot more often than most other protection devices including my firearms. (-: |
#12
Posted to alt.home.repair
|
|||
|
|||
Burnt Outlet
"bud--" wrote in message news:53084114$0$59830$c3e8da3
stuff snipped Making a map with device locations and circuit number is real useful, but a PITA. Would give you an idea where the first device is. If you AFCI the first receptacle and wire through the rest, the device protects the wiring downstream. All the load is at or downstream. The AFCI receptacle will protect the wiring back to the panel from series arcs (loose connections) by disconnecting the load that maintains the arc. After thinking about the for a while, I realized I could use my X-10 signal strength meters to discover the first outlet on a branch circuit. If I place a test transmitter on another branch, the X-10 meter will show noticeable signal attentuation as measurements are taken at each outlet on the branch circuit in question. I often use that technique to "zero in" on noise generators. As you move closer to the noisemaker the noise reading function of my XTBM meter shows an increase in the noise signal level (in millivolts). Never thought the technique could ID the first outlet in a circuit, but I think it will. stuff snipped I was under the impression, probably wrong, that if you connected a secondary buss bar with a large gauge wire (#8) to the neutral buss bar that it was acceptable to land neutral wires on the secondary buss bar but now I am not sure where I read that or if it's true. I realize now that the OEM neutral bar on my Square D panel sits above all the breakers and looks to be isolated from the enclosure. I assume that if there is a wire-connection that would work. You have to figure out what size wire is appropriate. Slight chance an inspector might object to using something the manufacturer calls a "ground bar" as a neutral bar. I had the panel inspected after I installed the first set of dual skinnies. But I think at that time I had moved all the ground wires from the panel's legit neutral bar to the ground bar. I was mostly concerned at the time that the inspector would disallow the dual skinnies because of the potential to overload the panel. It was obvious from what I had done, though, that I was relieving the older cloth-wire circuits of heavy loads (like toasters) and using the new 12/2 romex instead. The overall load on the panel wasn't changing, just the distribution of that load. Which brings up another subject. Today with my tong meter I realized that one side of the panel was pulling way more amps than the other. I guess that's for another thread, too. What happens when a circuit panel is unbalanced and has substantially more of a load on one leg than the other? Since the last inspection I have added more circuits but the overall load is still way less than the total the panel is rated for. Unfortunately now the neutrals are connected to the auxiliary buss bar and not just the ground wires and I recall that was new work, post inspection. A subpanel near the service panel is another possibility. (But then you will never be able to sell your house - according to one opinion. And you won't be able to get insurance. And a house inspector may say the house should be torn down. And it should be torn down. And that does not include the shame of having a subpanel.) No subpanels for me! A long time ago I decided that this house would probably have to be "gutted" when sold so it's not a big issue. Part of the problem is that it was built in 1941 when there was a shortage of everything and those shortages were reflected in the materials used in the house. No building paper between the floors, badly cured wood on the roof, etc. Fortunately where I live the land's what's worth the most $ and houses like mine are often knocked down so that larger homes can be built to replace them. stuff snipped I am not sure what you mean by "other than in a service panel, they have to be insulated from the enclosure." In a service panel the neutral and enclosure are connected together. Could be a wire. Often is a screw and looks like a mounting screw but may be green. If the neutral and enclosure are bonded, an added neutral bar would not have to be insulated from the enclosure (but may not rely on the enclosure as the electrical connection back to original neutral bar). Gotcha. I may be safe after all. The question now is whether to double up all the ground wires on the buss bar I installed (with the number 8 wire connected to the panel's original neutral bar) or to install another ground bar on the left side of the panel. I am leaning toward the latter because I don't like the idea of disturbing the old wires yet again and because there's a lot more free space on the left side. In a subpanel, an added neutral bar must be insulated. Another reason not to endure the shame of a subpanel. stuff snipped Someone mentioned thermally protected outlets that cut out when they get too hot. I've never heard of them. Are they something standard in the industry? Would they offer protection against high resistance connections that the AFCI's don't seem to provide? I have never heard of thermally protected outlets. Is that feature UL listed? Dunno. I'll first have to look up where someone mentioned them here and then go on to Google to find out more. They have to be pretty simple to build - just needs a klixon internally to interrupt the circuit in case of an overheat. Look for that in a separate thread as the initial search turned up a number of likely candidates. There's probably a third thread to evolve from this. Is UL listing necessary for approval of the installation of auxiliary equipment like an X-10 coupler/repeater? Now I remember why I haven't invited the inspector back . . . And AFCIs may trip on a ground fault caused by a "glowing connection", or if a glowing connection turns into an arc. A temperature "aware" outlet seems to be the solution to glowing connections. More in a new thread. Thanks for your input, Bud. -- Bobby G. |
#13
Posted to alt.home.repair
|
|||
|
|||
Burnt Outlet
On Wednesday, February 26, 2014 5:59:43 AM UTC-5, Robert Green wrote:
I had the panel inspected after I installed the first set of dual skinnies. But I think at that time I had moved all the ground wires from the panel's legit neutral bar to the ground bar. I was mostly concerned at the time that the inspector would disallow the dual skinnies because of the potential to overload the panel. It was obvious from what I had done, though, that I was relieving the older cloth-wire circuits of heavy loads (like toasters) and using the new 12/2 romex instead. The overall load on the panel wasn't changing, just the distribution of that load. Which brings up another subject. Today with my tong meter I realized that one side of the panel was pulling way more amps than the other. How much is way much more? I guess that's for another thread, too. What happens when a circuit panel is unbalanced and has substantially more of a load on one leg than the other? Nothing unless the neutral service conductor was undersized when it was installed and you put such an unbalanced load on it that it exceeded it's rating, eg managing to put close to the full service current rating on just one leg, which is highly unlikely with typical 120V loads. In a subpanel, an added neutral bar must be insulated. Another reason not to endure the shame of a subpanel. I don't know what's shameful about using a subpanel. They are installed frequently and properly done, nothing wrong with them. It sure beats tearing out a perfectly good main panel just to add two more circuits. And having the neutral not grounded in the subpanel is trivial, they are made to do that. On the other hand, if you have an old main panel and there are other reasons to upgrade the whole thing, then I can see going to a new larger panel. stuff snipped Someone mentioned thermally protected outlets that cut out when they get too hot. I've never heard of them. Are they something standard in the industry? Would they offer protection against high resistance connections that the AFCI's don't seem to provide? I have never heard of thermally protected outlets. Is that feature UL listed? Dunno. I'll first have to look up where someone mentioned them here and then go on to Google to find out more. They have to be pretty simple to build - just needs a klixon internally to interrupt the circuit in case of an overheat. Look for that in a separate thread as the initial search turned up a number of likely candidates. There's probably a third thread to evolve from this. Is UL listing necessary for approval of the installation of auxiliary equipment like an X-10 coupler/repeater? Now I remember why I haven't invited the inspector back . . . I think it's required to be listed and while it's typically listed by UL it doesn't have to specifically be UL, just a recognized testing lab. Given the crap that most X-10 products are, and since you're worried about getting thermally protected outlets, AFCI's etc, I'd think you'd want the X10 repeater listed. Is this an active one or just a passive one? The passive ones, at least some, are just caps AFAIK. |
#14
Posted to alt.home.repair
|
|||
|
|||
Burnt Outlet
wrote in message
... On Wednesday, February 26, 2014 5:59:43 AM UTC-5, Robert Green wrote: Which brings up another subject. Today with my tong meter I realized that one side of the panel was pulling way more amps than the other. How much is way much more? From 11 to 15A What happens when a circuit panel is unbalanced and has substantially more of a load on one leg than the other? Nothing unless the neutral service conductor was undersized when it was installed and you put such an unbalanced load on it that it exceeded it's rating, eg managing to put close to the full service current rating on just one leg, which is highly unlikely with typical 120V loads. OK. I remember a long, long time ago I had problems with a Sony monitor at work that an electrician attributed to an unbalanced panel, but balancing the loads didn't solve the wavering on the monitor so while rebalancing at that site didn't help, it probably didn't hurt, either. Another reason not to endure the shame of a subpanel. I don't know what's shameful about using a subpanel. I was just "playing along" with Bud who I assumed was recapping odd comments he's seen people make about subpanels. If I misunderstood you, Bud, I apologize in advance. They are installed frequently and properly done, nothing wrong with them. It sure beats tearing out a perfectly good main panel just to add two more circuits. And having the neutral not grounded in the subpanel is trivial, they are made to do that. On the other hand, if you have an old main panel and there are other reasons to upgrade the whole thing, then I can see going to a new larger panel. A total rewire is probably what's required here but as I said, when we leave this house, it will probably be gutted and renovated into a much larger house with all new wiring. Putting in a new service panel at this late date wouldn't be cost effective. I would probably have been forced to upgrade a long time ago except that the advent of CFLs and LEDs really reduced the overall load. Same with a new fridge and AC. Much lower total current draw than the old equipment. stuff snipped I think it's required to be listed and while it's typically listed by UL it doesn't have to specifically be UL, just a recognized testing lab. Given the crap that most X-10 products are, and since you're worried about getting thermally protected outlets, AFCI's etc, I'd think you'd want the X10 repeater listed. Different concerns. I'd already melted more than one outlet with a space heater whose plug had worked slightly loose. That's a serious fire hazard. With the XTB-II repeater, I am not worried that it will start a fire. Is this an active one or just a passive one? The passive ones, at least some, are just caps AFAIK. This is an active one designed by a guy who built custom electronics for NASA for several decades. He looked into UL listing but it would have made the device impracticably expensive. He's provided detailed circuit diagrams and component lists and enough information to make me comfortable using the device. We had extensive conversations about worst-case scenarios and while I'd like it to be UL listed, I don't see it as being a dealbreaker, especially considering how useful the device has been. You can see for yourself that this is not typical Chinese made X-10 consumer stuff: http://jvde.us/xtb/XTB-II_description.htm Jeff's design and soldering work is impeccable and the XTB-II pretty much eliminates all of the typical problems X-10 faces in the world of modern switching-power supplies. Unlike other repeaters, this unit boosts the X-10 signal to over 25 volts which is usually enough to power through any interference. Investing in the XTB-II saved me from having to switch to another home automation protocol and protected my substantial investment in X-10 gear. I am sure you would change your opinion about X-10 if you saw one of these units in action and the difference it makes to an "iffy" X-10 setup. The 5 to 10 volt signal strength of standard X-10 gear is just not enough to reach across phases or fight signal attenuation. That's partly because modern electronics are pretty noisy and are often designed to choke RFI which, ironically, is what the X-10 signal looks like to many devices. A 120Khz noise spike at the zero crossing. -- Bobby G. |
#15
Posted to alt.home.repair
|
|||
|
|||
Burnt Outlet
On 2/26/2014 4:59 AM, Robert Green wrote:
I was mostly concerned at the time that the inspector would disallow the dual skinnies because of the potential to overload the panel. Panels will have a rating something like 10/16. There are 10 full size breaker positions and you can put 16 "poles" in it. A tandem breaker is 2 poles, so you could install up to 6 tandem breakers. The label should tell you the rating. The panel is tested with the maximum number of poles - 16 above - and UL does not allow installing more poles than that. That is done by only allowing tandem breakers in certain positions (6 in the example above). The label will indicate which positions tandem breakers can be installed in. In a 10/20 panel it is all positions. It may also be no positions. A SquareD tandem breaker has a bar on the bottom that has to fit into a slot through the gutter rail, which exists only in the positions where tandem breakers are allowed. These are class CTL panels and breakers (circuit limiting) and they have been around a long time. The inspector wants to know that tandem breakers were installed in positions where they are allowed. There are also non-class CTL tandem breakers that can be installed in any position - for older panels that are before CTL came out. I know no one here would ever install one of them in a class CTL panel. |
#16
Posted to alt.home.repair
|
|||
|
|||
Burnt Outlet
On 2/26/2014 1:23 PM, Robert Green wrote:
wrote in message ... On Wednesday, February 26, 2014 5:59:43 AM UTC-5, Robert Green wrote: Which brings up another subject. Today with my tong meter I realized that one side of the panel was pulling way more amps than the other. How much is way much more? From 11 to 15A Doesn't sound like much unless it is a 60A panel. It will vary depending on what is on anyway Another reason not to endure the shame of a subpanel. I don't know what's shameful about using a subpanel. I was just "playing along" with Bud who I assumed was recapping odd comments he's seen people make about subpanels. If I misunderstood you, Bud, I apologize in advance. There is a certain party here who has that opinion of subpanels, telling RBM he did schlocky work because he has a subpanel in his house. The same person has strong opinions about k&t, insurance, and some other subjects. |
#17
Posted to alt.home.repair
|
|||
|
|||
Burnt Outlet
On Wednesday, February 26, 2014 2:23:18 PM UTC-5, Robert Green wrote:
wrote in message ... On Wednesday, February 26, 2014 5:59:43 AM UTC-5, Robert Green wrote: Which brings up another subject. Today with my tong meter I realized that one side of the panel was pulling way more amps than the other. How much is way much more? From 11 to 15A Perfectly normal. I think it's required to be listed and while it's typically listed by UL it doesn't have to specifically be UL, just a recognized testing lab. Given the crap that most X-10 products are, and since you're worried about getting thermally protected outlets, AFCI's etc, I'd think you'd want the X10 repeater listed. Different concerns. I'd already melted more than one outlet with a space heater whose plug had worked slightly loose. That's a serious fire hazard. With the XTB-II repeater, I am not worried that it will start a fire. Is this an active one or just a passive one? The passive ones, at least some, are just caps AFAIK. This is an active one designed by a guy who built custom electronics for NASA for several decades. He looked into UL listing but it would have made the device impracticably expensive. He's provided detailed circuit diagrams and component lists and enough information to make me comfortable using the device. We had extensive conversations about worst-case scenarios and while I'd like it to be UL listed, I don't see it as being a dealbreaker, especially considering how useful the device has been. You can see for yourself that this is not typical Chinese made X-10 consumer stuff: http://jvde.us/xtb/XTB-II_description.htm Jeff's design and soldering work is impeccable and the XTB-II pretty much eliminates all of the typical problems X-10 faces in the world of modern switching-power supplies. Unlike other repeaters, this unit boosts the X-10 signal to over 25 volts which is usually enough to power through any interference. Investing in the XTB-II saved me from having to switch to another home automation protocol and protected my substantial investment in X-10 gear. I am sure you would change your opinion about X-10 if you saw one of these units in action and the difference it makes to an "iffy" X-10 setup. The 5 to 10 volt signal strength of standard X-10 gear is just not enough to reach across phases or fight signal attenuation. That's partly because modern electronics are pretty noisy and are often designed to choke RFI which, ironically, is what the X-10 signal looks like to many devices. A 120Khz noise spike at the zero crossing. -- Bobby G. I hear you, but I don't think it would change my overall opinion of X-10. I'm sure it helps increase the reliability and can make it work where it otherwise would not. Part of the problem is that they are not upfront about this problem. I'm sure a lot of people wind up not being able to get it to work because it really should have a bridge/repeater across the phases. Then if you want such a device, they are expensive and as you've found out, have problems of their own, ie not UL listed and there is no guarantee that they will make it all work either. Or maybe you get it to work for what you're currently doing, then want to add something else and that won't work. The other big problem is that AFAIK, no one is doing anything new with X-10. What you have now, you've pretty much had the same stuff for more than a decade, ie no new products, no improvements, etc. The outdoor sensors don't last, that's another problem. I'd still use it for a simple application, where I put $20 in it and if it works it works, but I would not choose it as a means to more extensive home automation. |
#18
Posted to alt.home.repair
|
|||
|
|||
Burnt Outlet
bud-- posted for all of us...
And I know how to SNIP I know no one here would ever install one of them in a class CTL panel. You are one funny guy! -- Tekkie |
#19
Posted to alt.home.repair
|
|||
|
|||
Burnt Outlet
"bud--" wrote in message
eb.com... On 2/26/2014 1:23 PM, Robert Green wrote: wrote in message ... On Wednesday, February 26, 2014 5:59:43 AM UTC-5, Robert Green wrote: Which brings up another subject. Today with my tong meter I realized that one side of the panel was pulling way more amps than the other. How much is way much more? From 11 to 15A Doesn't sound like much unless it is a 60A panel. It will vary depending on what is on anyway Thanks. Just wasn't sure what the parameters/problems of unbalanced loads were. Thanks to you and T4 for clearing that up. Another reason not to endure the shame of a subpanel. I don't know what's shameful about using a subpanel. I was just "playing along" with Bud who I assumed was recapping odd comments he's seen people make about subpanels. If I misunderstood you, Bud, I apologize in advance. There is a certain party here who has that opinion of subpanels, telling RBM he did schlocky work because he has a subpanel in his house. The same person has strong opinions about k&t, insurance, and some other subjects. As I thought. Thanks for being circumspect about it and not mentioning names. Things have been remarkably civil here in AHR of late. Of course, my blocked senders list is growing like kudzu . . . -- Bobby G. |
#20
Posted to alt.home.repair
|
|||
|
|||
Burnt Outlet
"bud--" wrote in message
eb.com... On 2/26/2014 4:59 AM, Robert Green wrote: I was mostly concerned at the time that the inspector would disallow the dual skinnies because of the potential to overload the panel. Panels will have a rating something like 10/16. There are 10 full size breaker positions and you can put 16 "poles" in it. A tandem breaker is 2 poles, so you could install up to 6 tandem breakers. The label should tell you the rating. Panel is a QO CAT QO BW - 20M - 100 - 5 I believe that the 20 refers to the max # of breakers and the 100 is the max current. Otherwise the catalog number don't seem to agree with the listing in the PDF. No idea what BW means. It's hard to read the label because it's a) faded, b) upside down and c) obscured by neutral and ground wires. The panel is tested with the maximum number of poles - 16 above - and UL does not allow installing more poles than that. That is done by only allowing tandem breakers in certain positions (6 in the example above). The label will indicate which positions tandem breakers can be installed in. In a 10/20 panel it is all positions. It may also be no positions. A SquareD tandem breaker has a bar on the bottom that has to fit into a slot through the gutter rail, which exists only in the positions where tandem breakers are allowed. These are class CTL panels and breakers (circuit limiting) and they have been around a long time. This has to be a pre 1985 panel and I haven't found it yet although I found a few like it in this PDF: www.farnell.com/datasheets/1626663.pdf The inspector wants to know that tandem breakers were installed in positions where they are allowed. From what I can see, that's not an issue with my panel. As I recall, the hot bar (not sure of the technical name of the alternating metal "fingers" running down the center) was the same from the top to the bottom - no specialized slots for tandems (why would there be?). The replacement breakers have a very different connection mechanism that the original ones. The ones that came with the panel have two pronged clips that make the connection to the rail but the replacements have a single claw-like "grabber" - so different looking that I was sure I bought the wrong breakers. There are also non-class CTL tandem breakers that can be installed in any position - for older panels that are before CTL came out. I know no one here would ever install one of them in a class CTL panel. I am pretty sure that at least on of the labels on the panel has the letters CTL but if it came out after 1985, then I definitely don't have a CTL panel. From what I can see of the PDF listed above, the breaker panels that support special slots for tandems look quite different from the box I have which is a series of alternating metal fingers running down the heavy black plastic "spine" of the panel. http://en.wikipedia.org/wiki/Circuit_total_limitation Talks about CTL being in place since 1969 and replacement breakers being non-CTL. Even if the panel ends up "dangerously overloaded" isn't the main breaker supposed to trip before anything bad happens? -- Bobby G. |
#21
Posted to alt.home.repair
|
|||
|
|||
Burnt Outlet
On 3/2/2014 12:55 PM, Robert Green wrote:
"bud--" wrote in message eb.com... On 2/26/2014 4:59 AM, Robert Green wrote: I was mostly concerned at the time that the inspector would disallow the dual skinnies because of the potential to overload the panel. Panels will have a rating something like 10/16. There are 10 full size breaker positions and you can put 16 "poles" in it. A tandem breaker is 2 poles, so you could install up to 6 tandem breakers. The label should tell you the rating. Panel is a QO CAT QO BW - 20M - 100 - 5 I believe that the 20 refers to the max # of breakers and the 100 is the max current. Otherwise the catalog number don't seem to agree with the listing in the PDF. No idea what BW means. It's hard to read the label because it's a) faded, b) upside down and c) obscured by neutral and ground wires. I agree with 20 and 100. M means it has a main breaker. (As in your link below.) I don't know what BW is either. Need a real old catalog. I would read "20" as not allowing tandem breakers. "2024" would allow tandems in 4 positions. But it is an old catalog number. Seems like UL had maximum number of poles depending on the panel rating. I think a 100A panel had a max of 20 poles and 200A had a max of 40 or 42 poles. That makes it harder to overload a panel, but doesn't work so good if you don't have much on each circuit (so you need more circuits). SquareD has panels with a lot more poles ("circuits") than that now. The panel is tested with the maximum number of poles - 16 above - and UL does not allow installing more poles than that. That is done by only allowing tandem breakers in certain positions (6 in the example above). The label will indicate which positions tandem breakers can be installed in. In a 10/20 panel it is all positions. It may also be no positions. A SquareD tandem breaker has a bar on the bottom that has to fit into a slot through the gutter rail, which exists only in the positions where tandem breakers are allowed. These are class CTL panels and breakers (circuit limiting) and they have been around a long time. This has to be a pre 1985 panel and I haven't found it yet although I found a few like it in this PDF: www.farnell.com/datasheets/1626663.pdf The inspector wants to know that tandem breakers were installed in positions where they are allowed. From what I can see, that's not an issue with my panel. As I recall, the hot bar (not sure of the technical name of the alternating metal "fingers" running down the center) was the same from the top to the bottom - no specialized slots for tandems (why would there be?). The replacement breakers have a very different connection mechanism that the original ones. The ones that came with the panel have two pronged clips that make the connection to the rail but the replacements have a single claw-like "grabber" - so different looking that I was sure I bought the wrong breakers. SquareD class CTL tandem breakers have the usual horizontal clip at the busbar end. At the gutter rail end they have what you describe as a claw, which fits into a slot in the gutter rail. The slot is only present at the positions where tandem breakers are allowed. Your farnell link has a crappy picture for a Homeline panel on page 9 of your link. A better picture is http://www.circuitbreakersuperstore...._8_2_5862.html where the gutter rail claw can be seen. Regular breakers just have a clip at the gutter rail end, as with your original breakers. There are also non-class CTL tandem breakers that can be installed in any position - for older panels that are before CTL came out. I know no one here would ever install one of them in a class CTL panel. I am pretty sure that at least on of the labels on the panel has the letters CTL but if it came out after 1985, then I definitely don't have a CTL panel. From what I can see of the PDF listed above, the breaker panels that support special slots for tandems look quite different from the box I have which is a series of alternating metal fingers running down the heavy black plastic "spine" of the panel. The difference is only in the gutter rail. http://en.wikipedia.org/wiki/Circuit_total_limitation Talks about CTL being in place since 1969 and replacement breakers being non-CTL. Even if the panel ends up "dangerously overloaded" isn't the main breaker supposed to trip before anything bad happens? Yes. I don't entirely agree with the limit on circuits. If I watch the connected load I might install tandems where you are not supposed to. I think one reason for the limit is to limit the heat produced in the panel. Heat can cause a breaker to trip at a lower current. Would seem like a 100A panel would only make 100A of heat no matter how many breakers. There is, in general, a limitation for fuses and circuit breakers of 80% for "continuous" loads, which are loads that are on for 3 hours or more. My understanding is this is based on panel heat, and the breaker may trip at less than 100% if the load is on for more than 3 hours. An exposed 20A breaker or fuse by itself is supposed to hold at 20A forever. |
#22
Posted to alt.home.repair
|
|||
|
|||
Burnt Outlet
circuit limit number is to protect breaker box from being overfilled. just like te limit of the number of wires in any box
|
#23
Posted to alt.home.repair
|
|||
|
|||
Burnt Outlet
"bud--" wrote in message
b.com... On 3/2/2014 12:55 PM, Robert Green wrote: "bud--" wrote in message eb.com... On 2/26/2014 4:59 AM, Robert Green wrote: I was mostly concerned at the time that the inspector would disallow the dual skinnies because of the potential to overload the panel. Panels will have a rating something like 10/16. There are 10 full size breaker positions and you can put 16 "poles" in it. A tandem breaker is 2 poles, so you could install up to 6 tandem breakers. The label should tell you the rating. Panel is a QO CAT QO BW - 20M - 100 - 5 I believe that the 20 refers to the max # of breakers and the 100 is the max current. Otherwise the catalog number don't seem to agree with the listing in the PDF. No idea what BW means. It's hard to read the label because it's a) faded, b) upside down and c) obscured by neutral and ground wires. I agree with 20 and 100. M means it has a main breaker. (As in your link below.) I don't know what BW is either. Need a real old catalog. I've found that publications printed before the internet often never make their way to the net. I don't see myself spending too much time looking for the meaning of BW. I would read "20" as not allowing tandem breakers. "2024" would allow tandems in 4 positions. But it is an old catalog number. Those tandem breakers fit just fine g. I looked at the box again and the rails are continous without interruption or anything that looks like special slotting meant to accept tandems only in one spot. Seems like UL had maximum number of poles depending on the panel rating. I think a 100A panel had a max of 20 poles and 200A had a max of 40 or 42 poles. That makes it harder to overload a panel, but doesn't work so good if you don't have much on each circuit (so you need more circuits). SquareD has panels with a lot more poles ("circuits") than that now. It would be nice to upgrade to a newer panel but it wouldn't be cost effective. This place has to be "shelled" when I am through with it. Boy will my heirs be disappointed. (-: The panel is tested with the maximum number of poles - 16 above - and UL does not allow installing more poles than that. That is done by only allowing tandem breakers in certain positions (6 in the example above). The label will indicate which positions tandem breakers can be installed in. In a 10/20 panel it is all positions. It may also be no positions. A SquareD tandem breaker has a bar on the bottom that has to fit into a slot through the gutter rail, which exists only in the positions where tandem breakers are allowed. These are class CTL panels and breakers (circuit limiting) and they have been around a long time. This has to be a pre 1985 panel and I haven't found it yet although I found a few like it in this PDF: www.farnell.com/datasheets/1626663.pdf The inspector wants to know that tandem breakers were installed in positions where they are allowed. From what I can see, that's not an issue with my panel. As I recall, the hot bar (not sure of the technical name of the alternating metal "fingers" running down the center) was the same from the top to the bottom - no specialized slots for tandems (why would there be?). The replacement breakers have a very different connection mechanism that the original ones. The ones that came with the panel have two pronged clips that make the connection to the rail but the replacements have a single claw-like "grabber" - so different looking that I was sure I bought the wrong breakers. SquareD class CTL tandem breakers have the usual horizontal clip at the busbar end. At the gutter rail end they have what you describe as a claw, which fits into a slot in the gutter rail. The slot is only present at the positions where tandem breakers are allowed. No slots in my gutter rail. All the same from top to bottom but at least now I know why they changed the clamping mechanism. Boy was I certain when I got them home that they were the wrong style breakers even though I had religiously copied down the breaker information from the one I had pulled. I also discovered that the previous owner had replaced 15A breakers with 20A ones, which I based on the fact that the same gauge wires were feeding both sizes of breaker. I replaced those 20A units with 15A ones, just to be on the safe side. I figured wiring from 1940 was not likely to be 20A capable but the idiots before me apparently found the kitchen circuits tripped less frequently with the larger capacity breaker. Sadly, you could see that the 20A breaker feed wires had evidence of overheating. That's what led me to add the tandem/dual skinnies and run new wires to the kitchen and workshop areas. Your farnell link has a crappy picture for a Homeline panel on page 9 of your link. A better picture is http://www.circuitbreakersuperstore...._8_2_5862.html where the gutter rail claw can be seen. Regular breakers just have a clip at the gutter rail end, as with your original breakers. Either kind of breaker fits into any slot on the breaker panel I have. I saw a printer's mark on one label in the box that said 1961. Of course, there's no telling if that's related to the date the panel was installed. But based on the history of this house that I know about, it's entirely possible the panel is that old. I know at one point it was a screw fuse panel because I found a bunch of fuses directly below the panel area when I pulled the old paneling off the basement. There are also non-class CTL tandem breakers that can be installed in any position - for older panels that are before CTL came out. I know no one here would ever install one of them in a class CTL panel. I am pretty sure that at least on of the labels on the panel has the letters CTL but if it came out after 1985, then I definitely don't have a CTL panel. From what I can see of the PDF listed above, the breaker panels that support special slots for tandems look quite different from the box I have which is a series of alternating metal fingers running down the heavy black plastic "spine" of the panel. The difference is only in the gutter rail. Then I don't have a CTL panel. http://en.wikipedia.org/wiki/Circuit_total_limitation Talks about CTL being in place since 1969 and replacement breakers being non-CTL. Even if the panel ends up "dangerously overloaded" isn't the main breaker supposed to trip before anything bad happens? Yes. I don't entirely agree with the limit on circuits. If I watch the connected load I might install tandems where you are not supposed to. I think the offloading of old, cloth-covered wiring to newer 12/2 NM justified the use of tandems in my case. It has to be safer using new wiring than muddling through with the old crap. I think one reason for the limit is to limit the heat produced in the panel. Heat can cause a breaker to trip at a lower current. Would seem like a 100A panel would only make 100A of heat no matter how many breakers. There are some interesting charts here about temperature, load and other factors relating to breakers and how they trip and when. http://static.schneider-electric.us/...CT9801R108.pdf There is, in general, a limitation for fuses and circuit breakers of 80% for "continuous" loads, which are loads that are on for 3 hours or more. My understanding is this is based on panel heat, and the breaker may trip at less than 100% if the load is on for more than 3 hours. An exposed 20A breaker or fuse by itself is supposed to hold at 20A forever. I saw something (not especially credible - one of those "ask me" sorts of sites) that said because of the heat generated by the electronics in AFCI breakers, they had to be mounted away from each other. I also read manufacturer info that said that heat generation was taken into account. That's where I also saw something about the NEC required that instrument controls that a user had to operate with fingers not be over 140F. That seems a little high. -- Bobby G. |
#24
Posted to alt.home.repair
|
|||
|
|||
Burnt Outlet
"bob haller" wrote in message
... circuit limit number is to protect breaker box from being overfilled. just like te limit of the number of wires in any box My panel seems to be in an oversize box - thank God - because there's at least 8" of empty space in the box below where the gutter rails end. -- Bobby G. |
#25
Posted to alt.home.repair
|
|||
|
|||
Burnt Outlet
On 3/6/2014 10:57 AM, Robert Green wrote:
"bud--" wrote in message b.com... Those tandem breakers fit just fine g. I looked at the box again and the rails are continous without interruption or anything that looks like special slotting meant to accept tandems only in one spot. Then I presume you used non-CTL tandem breakers. The difference is only in the gutter rail. Then I don't have a CTL panel. You can't tell that from the rail. The panel could just not allow any tandem breakers. Sounds like from the date you found it is not a CTL panel and it is kosher to use non-CTL tandem breakers. I am not entirely convinced that is a problem anyway. If you have a 100A panel seems like you would only get '100A of heat' no matter how many circuits/poles there are. You would have to watch how much load you connect so you don't actually overload the panel. |
#26
Posted to alt.home.repair
|
|||
|
|||
Burnt Outlet
"bud--" wrote in message
eb.com... On 3/6/2014 10:57 AM, Robert Green wrote: "bud--" wrote in message b.com... Those tandem breakers fit just fine g. I looked at the box again and the rails are continous without interruption or anything that looks like special slotting meant to accept tandems only in one spot. Then I presume you used non-CTL tandem breakers. I used what Home Depot had on the shelves that matched the QO designation and it was approved by the AHJ. Dual skinnies/tandems are a pretty popular item in this development of houses built to house the army of workers that descended on DC at the beginning of WWII. Fortunately with CFLs and more efficient motors the average load for such items has decreased substantially (although the number of plug in chargers and appliances has increased geometrically). I assume when I ultimately switch to LEDs the overall load will be reduced again. The difference is only in the gutter rail. Then I don't have a CTL panel. You can't tell that from the rail. The panel could just not allow any tandem breakers. Tell that to the four that are in there now! (-: Sounds like from the date you found it is not a CTL panel and it is kosher to use non-CTL tandem breakers. That date's not conclusive. They could have been using the same label for 20 years. There must be some other date markings inside the box. Reading all the details is getting to be like reading "War and Peace" - very arduous. I am not entirely convinced that is a problem anyway. If you have a 100A panel seems like you would only get '100A of heat' no matter how many circuits/poles there are. You would have to watch how much load you connect so you don't actually overload the panel. I do. A long time ago I installed two Hall effect sensors on the incoming feeds. For days I was calibrating them with various space heater loads (this was the springtime and it drove my wife a little crazy having me run space heaters with the windows open. She's a frugal New Englander). Those sensors feed into my HomeVision home automation controller's analog inputs. From there I can roughly gauge the total load at any one time and it very rarely exceeds 50A, and only then when it's very cold which self-limits the overheating panel problem to some extent. -- Bobby G. |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Burnt electrical outlet and plug | Home Repair | |||
is gfci outlet good replacement for two-prong non-grounded outlet ?? | Home Repair | |||
Burnt outlet / Dead circuit | Home Repair | |||
Piggy-backing new 125v outlet on existing 250v outlet? | Home Repair | |||
FS Six 20A outlet shop electrical panel, each outlet protected | Home Repair |