Home |
Search |
Today's Posts |
|
Home Repair (alt.home.repair) For all homeowners and DIYers with many experienced tradesmen. Solve your toughest home fix-it problems. |
Reply |
|
LinkBack | Thread Tools | Display Modes |
#41
Posted to alt.home.repair
|
|||
|
|||
Home Inspection Beyond the Breaker Box and with Power On
On Friday, November 1, 2013 3:15:02 PM UTC-4, wrote:
Forgot to add the extra piece of humble pie for me today: The panel did have a modification, adding wiring for the garage door opener and two garage outlets. It must have been done post the initial inspection of the house many years ago. The Romex connector was left off this modification. The three breakers were not labeled until I figured out what they powered just a little while ago. FYI, GFCI protection has been required for garage outlets for a long time, at least the 80's. So this should either be a GFCI breaker or the first outlet in the daisychain in the garage should be a GFCI outlet. That will protect it and anything downstream of it. Not sure if the garage door openers need to be on GFCI, they may be exempted. Would be interesting to see if those are there and if the inspector squaked it. Of course if it was an older home, before it was required, then it's OK. |
#42
Posted to alt.home.repair
|
|||
|
|||
Home Inspection Beyond the Breaker Box and with Power On
bud-- wrote:
On 11/1/2013 11:21 AM, TomR wrote: bud-- wrote: On 11/1/2013 9:40 AM, wrote: On Friday, November 1, 2013 10:58:27 AM UTC-4, wrote: On Fri, 1 Nov 2013 05:24:18 -0700 (PDT), " wrote: I've seen newer panels on the Holmes TV show where the upper part has it's own separate cover, that has to be removed in addition to the main cover. That is the code in Canada. You can't install a panel horizontally here. If a circuit breaker is installed vertically, "on" must be up. Half the breaker positions would be wrong. I am not sure what you meant by "here". But, if "here" means the U.S., I think that the panel can be installed horizontally (although I personally hate that). And, although I am not completely sure, I think that the code (NEC) says that the panel can be horizontal but the main service disconnect (main breaker) has to be installed such that "On" is "Up" and "Off" is "Down". I don't think that applies to each breaker -- just the main service disconnect switch. The reason why I think that is that I recently had an electrician install two new service panels. He put them both in upside down, with the main breaker on the bottom and all of the individual breakers above the main breaker. I hated that, but I looked it up and apparently that was within code. I never thought to even ask about right side up or upside down since I never saw one that was upside down. However, for my own sanity (or neurosis), I had the electrician change the panels to what I consider to be right side up -- the main breaker on top and the individual breakers below the main breaker. And, the reason why I mention this is that I am pretty sure that I was when researching this I found that the code does allow a horizontal panel as long as the main breaker's "On" position is "Up" and "Off" position is "Down". "404.7 Indicating General-use ... switches, circuit breakers, ... shall clearly indicate whether they are in the open (off) or closed (on) position. Where these switch or circuit breaker handles are operated vertically rather than rotationally or horizontally, the up position of the handle shall be the (on) position." Thanks Bud. Looks like you are right. I guess I didn't remember correctly what I had researched before. Here are the NEC citations that I just found that appear to be applicable: 404.1 Scope. The provisions of this article shall apply to all switches, switching devices, and circuit breakers where used as switches. 404.7 Indicating. General-use and motor-circuit switches, circuit breakers, and molded case switches, where mounted in an enclosure as described in 404.3, shall clearly indicate whether they are in the open (off) or closed (on) position. Where these switch or circuit breaker handles are operated vertically rather than rotationally or horizontally, the up position of the handle shall be the (on) position. Exception No. 1: Vertically operated double-throw switches shall be permitted to be in the closed (on) position with the handle in either the up or down position. Exception No. 2: On busway installations, tap switches employing a center-pivoting handle shall be permitted to be open or closed with either end of the handle in the up or down position. The switch position shall be clearly indicating and shall be visible from the floor or from the usual point of operation. 404.11 Circuit Breakers as Switches. A hand-operable circuit breaker equipped with a lever or handle, or a poweroperated circuit breaker capable of being opened by hand in the event of a power failure, shall be permitted to serve as a switch if it has the required number of poles. FPN: See the provisions contained in 240.81 and 240.83. ARTICLE 240-OVERCURRENT PROTECTION 240.33 Vertical Position. Enclosures for overcurrent devices shall be mounted in a vertical position unless that is shown to be impracticable. Circuit breaker enclosures shall be permitted to be installed horizontally where the circuit breaker is installed in accordance with 240.81. Listed busway plug-in units shall be permitted to be mounted in orientations corresponding to the busway mounting position. VII. Circuit Breakers 240.80 Method of Operation. Circuit breakers shall be trip free and capable of being closed and opened by manual operation. Their normal method of operation by other than manual means, such as electrical or pneumatic, shall be permitted if means for manual operation are also provided. 240.81 Indicating. Circuit breakers shall clearly indicate whether they are in the open "off" or closed "on" position. Where circuit breaker handles are operated vertically rather than rotationally or horizontally, the "up" position of the handle shall be the "on" position. |
#43
Posted to alt.home.repair
|
|||
|
|||
Home Inspection Beyond the Breaker Box and with Power On
|
#44
Posted to alt.home.repair
|
|||
|
|||
Home Inspection Beyond the Breaker Box and with Power On
TomR wrote:
bud-- wrote: On 11/1/2013 11:21 AM, TomR wrote: bud-- wrote: "404.7 Indicating General-use ... switches, circuit breakers, ... shall clearly indicate whether they are in the open (off) or closed (on) position. Where these switch or circuit breaker handles are operated vertically rather than rotationally or horizontally, the up position of the handle shall be the (on) position." Thanks Bud. Looks like you are right. I guess I didn't remember correctly what I had researched before. Here are the NEC citations that I just found that appear to be applicable: . . . , P.S. I think I may have been confused in the past by the last citation (240.33), the last line of which says, "Listed busway plug-in units shall be permitted to be mounted in orientations corresponding to the busway mounting position." I think I assumed that meant that "listed busway plug-in units" (circuit breakers?) could be mounted in the orientation that corresponds to how they are plugged into the busbar. But, I may have been misunderstanding what that sentence means since it seems to conflict with the sentence before it. ARTICLE 240-OVERCURRENT PROTECTION 240.33 Vertical Position. Enclosures for overcurrent devices shall be mounted in a vertical position unless that is shown to be impracticable. Circuit breaker enclosures shall be permitted to be installed horizontally where the circuit breaker is installed in accordance with 240.81. Listed busway plug-in units shall be permitted to be mounted in orientations corresponding to the busway mounting position. |
#45
Posted to alt.home.repair
|
|||
|
|||
Home Inspection Beyond the Breaker Box and with Power On
On 11/1/2013 11:38 AM, Bob_Villa wrote:
On Friday, November 1, 2013 7:39:34 AM UTC-5, Stormin Mormon wrote: And, all rapper type teens are packing? Any teen with droopy drawers, hat on sideways, flashing gang hand signs. Got to be packing a nine. Doesn't sound like Stormy? 50 plus, white, balding, wears belt and suspenders, hat on forward, when wearing one, no gang signs, no gang colors, doesn't wear sneakers or felony shoes. You be dissin me, blood, I bust cap on yo ah. -- .. Christopher A. Young Learn about Jesus www.lds.org .. |
#47
Posted to alt.home.repair
|
|||
|
|||
Home Inspection Beyond the Breaker Box and with Power On
On Fri, 01 Nov 2013 17:29:04 -0400, Stormin Mormon
wrote: And, all rapper type teens are packing? Any teen with droopy drawers, hat on sideways, flashing gang hand signs. Got to be packing a nine. Doesn't sound like Stormy? 50 plus, white, balding, wears belt and suspenders, hat on forward, when wearing one, no gang signs, no gang colors, doesn't wear sneakers or felony shoes. You be dissin me, blood, I bust cap on yo ah. Not convincing at all. Word! The funniest thing I heard from a jitterbug banger, as he told another..."nigga, yow mama got bad pussy!" I lost it, right one the spot Well, almost. ) |
#48
Posted to alt.home.repair
|
|||
|
|||
Home Inspection Beyond the Breaker Box and with Power On
dgk wrote in
: On Fri, 1 Nov 2013 05:31:09 -0700 (PDT), " wrote: On Friday, November 1, 2013 3:54:27 AM UTC-4, Ashton Crusher wrote: On Fri, 01 Nov 2013 01:16:14 -0400, wrote: On Thu, 31 Oct 2013 21:25:28 -0700 (PDT), wrote: I am in the process of selling my house. What do you all think of a home inspector who takes off the breaker box cover off (not just opens the door to expose the breakers; he had to remove four screws to get the cover off), exposes the wire connections, all the while keeping the main breaker shut and so the insides of the box remained electrically hot as he did a visual inspection and took photos? The breaker box has a prominent sticker in it that says to open the main breaker prior to removing the cover. In his report, the inspector commented: "Any electrical repairs attempted by anyone other than a licensed electrician should be approached with caution. The power to the entire house should be turned off prior to beginning any repair efforts, no matter how trivial the repair may seem. ... Missing strain relief at panel. Have a licensed electrician make further evaluation and corrections as needed." I am surprised first at how invasive this inspector was. Second at how he ignored safe practices by not securing the power. Third that he would have the gall to make judgments on the sufficiency of the internals. Fourth that he would go a step further and suggest he really does not know enough (so what's he doing in there in the first place?); get a licensed electrician to evaluate. Home inspectors dance down the fine line of marginal competence in the trades they inspect and acting like an expert. They need to put in the disclaimer that you need a professional to back up just about anything they say. And they MUST find something wrong to report in order to justify the expense of the inspection. My advise to people who are selling is to make sure at least one switch is broken and at least one easy to repair faucet leaks, or something along the lines, so the inspector won't have too look to hard to find his "justification nuggets". LOL. I've thought about that too. With an average house, the home inspection is essentially free to the buyer, because as you say, the inspector usually finds at least a few things that can take $400 of the price of the sale. But if you have a house with few problems, it's an interesting idea to leave a few simple things that you know about, that you can fix yourself later, etc, just so the inspector will find something to make the buyer feel like they did find some things. The sad ones of course are the ones where the inspector spots some trivial stuff and completely misses obvious major stuff that was readily visible. You see that on the Holmes TV show in Canada. That's pretty funny. Maybe Home Depot can sell defective washers They have other kinds? so we can replace them with good ones after the inspection. |
#49
Posted to alt.home.repair
|
|||
|
|||
Beyon de cracker Box and with Pow On. slick
On 11/1/2013 5:42 PM, Oren wrote:
Doesn't sound like Stormy? 50 plus, white, balding, wears belt and suspenders, hat on forward, when wearing one, no gang signs, no gang colors, doesn't wear sneakers or felony shoes. You be dissin me, blood, I bust cap on yo ah. Not convincing at all. Word! The funniest thing I heard from a jitterbug banger, as he told another..."nigga, yow mama got bad pussy!" I lost it, right one the spot Well, almost. ) Yo, home. Choo all calling me a bro? I ain go take it from yo, blood. You all be dissin dis hee nig won mo tahm, no ahm sayin? I ain no porch monkey, my ass be cracker to the co. http://www.ckhid.com/wp-content/uplo...ic-video_1.jpg Seff potrat. -- .. Christophe A. Yo Learn about J www.lds.o .. |
#50
Posted to alt.home.repair
|
|||
|
|||
Beyon de cracker Box and with Pow On. slick
On Fri, 01 Nov 2013 18:25:32 -0400, Stormin Mormon
wrote: On 11/1/2013 5:42 PM, Oren wrote: Doesn't sound like Stormy? 50 plus, white, balding, wears belt and suspenders, hat on forward, when wearing one, no gang signs, no gang colors, doesn't wear sneakers or felony shoes. You be dissin me, blood, I bust cap on yo ah. Not convincing at all. Word! The funniest thing I heard from a jitterbug banger, as he told another..."nigga, yow mama got bad pussy!" I lost it, right one the spot Well, almost. ) Yo, home. Choo all calling me a bro? I ain go take it from yo, blood. You all be dissin dis hee nig won mo tahm, no ahm sayin? I ain no porch monkey, my ass be cracker to the co. http://www.ckhid.com/wp-content/uplo...ic-video_1.jpg Seff potrat. Word up! I heard dat http://scrapetv.com/News/News%20Pages/Business/images-3/redneck-toilet.jpg |
#51
Posted to alt.home.repair
|
|||
|
|||
Home Inspection Beyond the Breaker Box and with Power On
|
#52
Posted to alt.home.repair
|
|||
|
|||
Home Inspection Beyond the Breaker Box and with Power On
|
#53
Posted to alt.home.repair
|
|||
|
|||
Home Inspection Beyond the Breaker Box and with Power On
|
#54
Posted to alt.home.repair
|
|||
|
|||
Beyon de cracker Box and with Pow On. slick
On 11/1/2013 7:13 PM, Oren wrote:
Yo, home. Choo all calling me a bro? I ain go take it from yo, blood. You all be dissin dis hee nig won mo tahm, no ahm sayin? I ain no porch monkey, my ass be cracker to the co. http://www.ckhid.com/wp-content/uplo...ic-video_1.jpg Seff potrat. Word up! I heard dat http://scrapetv.com/News/News%20Pages/Business/images-3/redneck-toilet.jpg Oh, bother. I kept telling my neighbor not to take that picture. But, no..... -- .. Christopher A. Young Learn about Jesus www.lds.org .. |
#55
Posted to alt.home.repair
|
|||
|
|||
Home Inspection Beyond the Breaker Box and with Power On
On Friday, November 1, 2013 2:33:08 PM UTC-7, Stormin Mormon wrote:
Sounds like a tech who knows what he's doing. I sure hope you recommend him to every one you know. I submitted my recommendation of him and the company he co-owns, and the essentials of why, to the "Services" section of my 1000+ home neighborhood's web site within an hour after he left. |
#56
Posted to alt.home.repair
|
|||
|
|||
Home Inspection Beyond the Breaker Box and with Power On
On 11/2/2013 11:00 AM, wrote:
On Friday, November 1, 2013 2:33:08 PM UTC-7, Stormin Mormon wrote: Sounds like a tech who knows what he's doing. I sure hope you recommend him to every one you know. I submitted my recommendation of him and the company he co-owns, and the essentials of why, to the "Services" section of my 1000+ home neighborhood's web site within an hour after he left. I hope he has plenty of business. And that plenty of customers have good inspections. -- .. Christopher A. Young Learn about Jesus www.lds.org .. |
#57
Posted to alt.home.repair
|
|||
|
|||
Home Inspection Beyond the Breaker Box and with Power On
|
#58
Posted to alt.home.repair
|
|||
|
|||
Home Inspection Beyond the Breaker Box and with Power On
On Monday, November 4, 2013 10:34:37 AM UTC-5, Scott Lurndal wrote:
writes: On Fri, 1 Nov 2013 12:54:25 -0700 (PDT), " wrote: On Friday, November 1, 2013 3:15:02 PM UTC-4, wrote: Forgot to add the extra piece of humble pie for me today: The panel did have a modification, adding wiring for the garage door opener and two garage outlets. It must have been done post the initial inspection of the house many years ago. The Romex connector was left off this modification. The three breakers were not labeled until I figured out what they powered just a little while ago. FYI, GFCI protection has been required for garage outlets for a long time, at least the 80's. So this should either be a GFCI breaker or the first outlet in the daisychain in the garage should be a GFCI outlet. That will protect it and anything downstream of it. Not sure if the garage door openers need to be on GFCI, they may be exempted. Would be interesting to see if those are there and if the inspector squaked it. Of course if it was an older home, before it was required, then it's OK. All 15 and 20a 120v receptacles in a garage need to be GFCI and he has been that way for several cycles. True only if the receptacle will accept a standard NEMA 5-15P/5-20P plug, if I remember the relevent code section correctly. This allows non GFCI branch circuits in the garage for stationary power tools. Such a tool might use a NEMA L5-20R (although for a good table saw, it's more likely to be a NEMA L6-20R). I pull covers without turning the main off all the time. It's not that big a deal. And I'm surprised you were missing a clamp. It's pretty obvious that there has to be one when you look at all the other existing wires. |
#59
Posted to alt.home.repair
|
|||
|
|||
Home Inspection Beyond the Breaker Box and with Power On
On Mon, 4 Nov 2013 09:36:39 -0800 (PST), jamesgang
wrote: On Monday, November 4, 2013 10:34:37 AM UTC-5, Scott Lurndal wrote: writes: On Fri, 1 Nov 2013 12:54:25 -0700 (PDT), " wrote: On Friday, November 1, 2013 3:15:02 PM UTC-4, wrote: Forgot to add the extra piece of humble pie for me today: The panel did have a modification, adding wiring for the garage door opener and two garage outlets. It must have been done post the initial inspection of the house many years ago. The Romex connector was left off this modification. The three breakers were not labeled until I figured out what they powered just a little while ago. FYI, GFCI protection has been required for garage outlets for a long time, at least the 80's. So this should either be a GFCI breaker or the first outlet in the daisychain in the garage should be a GFCI outlet. That will protect it and anything downstream of it. Not sure if the garage door openers need to be on GFCI, they may be exempted. Would be interesting to see if those are there and if the inspector squaked it. Of course if it was an older home, before it was required, then it's OK. All 15 and 20a 120v receptacles in a garage need to be GFCI and he has been that way for several cycles. True only if the receptacle will accept a standard NEMA 5-15P/5-20P plug, if I remember the relevent code section correctly. This allows non GFCI branch circuits in the garage for stationary power tools. Such a tool might use a NEMA L5-20R (although for a good table saw, it's more likely to be a NEMA L6-20R). I pull covers without turning the main off all the time. It's not that big a deal. And I'm surprised you were missing a clamp. It's pretty obvious that there has to be one when you look at all the other existing wires. You'd be surprised at what you see in houses where a "handyman" thinks he knows more than he does. When I was looking for a house 32 years ago and bought the one I now own, I saw one with a beautifully finished basement - where the whole basement was wired with 2 conductor iron core outdoor telephone wire, and there were no clamps on any of the boxes. Another one where the basement had a suspended ceiling, and all of the lights were wired with lamp cord, plugged into 2 outlet boxes hanging from the joists.With Cube Taps. Didn't look to see what the outlets were wired with. All kinds of strange und stupid stuff |
#60
Posted to alt.home.repair
|
|||
|
|||
Home Inspection Beyond the Breaker Box and with Power On
|
#61
Posted to alt.home.repair
|
|||
|
|||
GFCI Breaker? GFCI Receptacle?
On Monday, November 4, 2013 8:34:37 AM UTC-7, Scott Lurndal wrote:
gfretwell wrote: All 15 and 20a 120v receptacles in a garage need to be GFCI and he has been that way for several cycles. True only if the receptacle will accept a standard NEMA 5-15P/5-20P plug, if I remember the relevent code section correctly. This allows non GFCI branch circuits in the garage for stationary power tools. Such a tool might use a NEMA L5-20R (although for a good table saw, it's more likely to be a NEMA L6-20R). I had another home inspection today. The buyer's realtor was there and questioned why neither of the two bathrooms had GFCI receptacles. The inspector looked a little confused (the realtor was making jokes throughout the inspection, while I waited outside) but added that GFCI was recommended in the bathrooms and withdrew from the discussion. The electric panel was inspected in 1995 when the house was built and has an inspection sticker for same. What I found subsequently is that one breaker in my electrical panel is labeled "GFI - Garage." Opening this breaker shuts off power to one outlet in the garage and both bathrooms' outlets. None of these three outlets have GFCI test and reset buttons. The breaker looks the same as all the other breakers in the panel. The outlet in the garage looks like what's shown he http://www.homedepot.com/p/Leviton-D...-WMP/100684055. 1. Could a GFCI outlet have neither a test nor reset button? 2. Could a GFCI breaker in a panel be not obvious? 3. Is it worth the $15 it costs to buy a GFCI tester and test the bathroom outlets to see if there is GFCI protection of them somewhere? 4. My best guess is that the previous homeowner had a GFCI outlet in the garage but replaced it. Should I put in a new GFCI outlet in the garage. Then will I have assurance of GFCI protection in all three outlets? 15 amp or 20 amp outlet? |
#62
Posted to alt.home.repair
|
|||
|
|||
GFCI Breaker? GFCI Receptacle?
On Friday, August 29, 2014 4:19:47 PM UTC-4, wrote:
On Monday, November 4, 2013 8:34:37 AM UTC-7, Scott Lurndal wrote: gfretwell wrote: All 15 and 20a 120v receptacles in a garage need to be GFCI and he has been that way for several cycles. True only if the receptacle will accept a standard NEMA 5-15P/5-20P plug, if I remember the relevent code section correctly. This allows non GFCI branch circuits in the garage for stationary power tools. Such a tool might use a NEMA L5-20R (although for a good table saw, it's more likely to be a NEMA L6-20R). I had another home inspection today. The buyer's realtor was there and questioned why neither of the two bathrooms had GFCI receptacles. The inspector looked a little confused (the realtor was making jokes throughout the inspection, while I waited outside) but added that GFCI was recommended in the bathrooms and withdrew from the discussion. The electric panel was inspected in 1995 when the house was built and has an inspection sticker for same.. What I found subsequently is that one breaker in my electrical panel is labeled "GFI - Garage." Opening this breaker shuts off power to one outlet in the garage and both bathrooms' outlets. None of these three outlets have GFCI test and reset buttons. The breaker looks the same as all the other breakers in the panel. The outlet in the garage looks like what's shown he http://www.homedepot.com/p/Leviton-D...-WMP/100684055. 1. Could a GFCI outlet have neither a test nor reset button? An outlet that has the GFCI built into it would have to have both a test and reset button. 2. Could a GFCI breaker in a panel be not obvious? I've never seen one that isn't obvious. It has a test button for one thing and would say that it's GFCI on it. 3. Is it worth the $15 it costs to buy a GFCI tester and test the bathroom outlets to see if there is GFCI protection of them somewhere? Maybe. They aren't a bad thing to have as they also test for reversed hot/neutral, missing grounds, etc. 4. My best guess is that the previous homeowner had a GFCI outlet in the garage but replaced it. Should I put in a new GFCI outlet in the garage. Then will I have assurance of GFCI protection in all three outlets? 15 amp or 20 amp outlet? That would depend on how it's wired. If the bathrooms are downstream of the garage, then yes. If they are upstream, then no. A GFCI outlet will protect other outlets that are wired after it, but not before it in the chain. Whether it should be 15 or 20 depends on the existing breaker and wire. 15A, 14g wire, or 20A, 12g. It was common back in that period to have a bath protect a garage or vice-versa. You deduction about what might have happened about someone taking out the GFCI sounds like it could be right, but they would have had to be pretty dumb. Personally, if it were my house, I'd prefer the GFCI for the baths to be in one of the baths. Not unusual for them to trip and you want it easy to find. The garage one could be downstream of that. But if it's wired the other way around, which you think it is, then the bath can't protect the garage. So, for your solution, if it's wired the way you think, just putting a GFCI back in the garage and using it to protect everything should work. You'll have to pull the garage outlet(s) and determine where the feed to the baths originates to wire it correctly. The other and simpler option would be to replace the breaker with a GFCI one. I'm assuming that the inspector isn't going to interpret the code to mean that this is a "change" that requires everything on that circuit to now be brought up to code. |
#63
Posted to alt.home.repair
|
|||
|
|||
GFCI Breaker? GFCI Receptacle?
On Friday, August 29, 2014 2:56:24 PM UTC-6, trader_4 wrote:
On Friday, August 29, 2014 4:19:47 PM UTC-4, wrote: snip for brevity My best guess is that the previous homeowner had a GFCI outlet in the garage but replaced it. Should I put in a new GFCI outlet in the garage. Then will I have assurance of GFCI protection in all three outlets? 15 amp or 20 amp outlet? That would depend on how it's wired. If the bathrooms are downstream of the garage, then yes. If they are upstream, then no. A GFCI outlet will protect other outlets that are wired after it, but not before it in the chain. Whether it should be 15 or 20 depends on the existing breaker and wire. 15A, 14g wire, or 20A, 12g. It was common back in that period to have a bath protect a garage or vice-versa. You deduction about what might have happened about someone taking out the GFCI sounds like it could be right, but they would have had to be pretty dumb. Do you mean they were dumb to give up GFCI protection on the bathrooms and garage outlet? Or they were dumb to do so for some other reason. At this point, I think the fact that my 2003-ish home inspector (when I bought the home) said nothing on this is a bit discouraging. It's the old but thoroughly lethal electric razor or hair dryer in the bathtub death trick (and similar, and really not funny) we're trying to avoid with bathroom GFCIs in particular, right? I know this because my dad earlier today reviewed just such a case with a teenage girl where I grew up decades ago. Personally, if it were my house, I'd prefer the GFCI for the baths to be in one of the baths. Not unusual for them to trip and you want it easy to find. The garage one could be downstream of that. But if it's wired the other way around, which you think it is, then the bath can't protect the garage. So, for your solution, if it's wired the way you think, just putting a GFCI back in the garage and using it to protect everything should work. You'll have to pull the garage outlet(s) and determine where the feed to the baths originates to wire it correctly. The other and simpler option would be to replace the breaker with a GFCI one. I'm assuming that the inspector isn't going to interpret the code to mean that this is a "change" that requires everything on that circuit to now be brought up to code. Thank you for your rapid and informed response. Per your commentary, I opened the panel breaker in question, disconnected the corresponding garage receptacle (making sure no wires touched when done), and then shut the panel breaker. I had power at neither of the bathrooms' receptacles. This tells me the garage receptacle is upstream of the bathrooms' receptacles. Any objections to this approach? The micrometer-ed the wire at the garage receptacle and found it to be 14 gage, so per your note (double checked with the net), I need a 15 amp GFCI receptacle, and I am good to go. I will probably just do it and then if the buyer wants an electrician inspection of same, I will call the guy I called before. Much obliged, trader_4. |
#64
Posted to alt.home.repair
|
|||
|
|||
GFCI Breaker? GFCI Receptacle?
wrote in
: I had another home inspection today. The buyer's realtor was there and questioned why neither of the two bathrooms had GFCI receptacles. The electrical code does not require GFCI receptacles in bathrooms. It requires that receptacles in bathrooms be protected by a GFCI, which can be located anywhere. The inspector looked a little confused (the realtor was making jokes throughout the inspection, while I waited outside) but added that GFCI was recommended in the bathrooms and withdrew from the discussion. The electric panel was inspected in 1995 when the house was built and has an inspection sticker for same. Ground-fault protection for bathroom receptacles is not merely "recommended". It is *required*. However, there is no requirement that the ground fault protective device be located in the bathroom. What I found subsequently is that one breaker in my electrical panel is labeled "GFI - Garage." Opening this breaker shuts off power to one outlet in the garage and both bathrooms' outlets. That's fine, if either (a) the breaker is a GFCI breaker, or (b) the garage outlet is a GFCI outlet *and* it's wired to provide downstream protection. If neither (a) nor (b) is true, then you don't have GFCI protection despite what the label says. None of these three outlets have GFCI test and reset buttons. No, of course not. They are not GFCI receptacles. The breaker looks the same as all the other breakers in the panel. Then it's not a GFCI breaker. The outlet in the garage looks like what's shown he http://www.homedepot.com/p/Leviton-D...mper-Resistant -Duplex-Outlet-10-Pack-White-M22-T5325-WMP/100684055. That's not a GFCI outlet. 1. Could a GFCI outlet have neither a test nor reset button? A GFCI breaker provides ground-fault protections to all receptacles on that circuit. A GFCI receptacle can be -- but is not necessarily -- wired to provide GFCI protection to all receptacles "downstream" from itself. Any receptacle protected in either of these manners will have full ground fault protection, but of course the test and reset buttons exist only at the GFCI protective device itself. 2. Could a GFCI breaker in a panel be not obvious? No. GFCI breakers are *very* obvious. 3. Is it worth the $15 it costs to buy a GFCI tester and test the bathroom outlets to see if there is GFCI protection of them somewhere? Yes, absolutely. From what you have written so far, it sounds very much like you do *not* have GFCI protection. IMHO, you should do this right away. 4. My best guess is that the previous homeowner had a GFCI outlet in the garage but replaced it. Should I put in a new GFCI outlet in the garage. Then will I have assurance of GFCI protection in all three outlets? I agree on all three counts. 15 amp or 20 amp outlet? Depends on whether it's a 15A or 20A circuit. |
#66
Posted to alt.home.repair
|
|||
|
|||
GFCI Breaker? GFCI Receptacle?
|
#67
Posted to alt.home.repair
|
|||
|
|||
GFCI Breaker? GFCI Receptacle?
On Friday, August 29, 2014 5:58:25 PM UTC-4, wrote:
On Friday, August 29, 2014 2:56:24 PM UTC-6, trader_4 wrote: On Friday, August 29, 2014 4:19:47 PM UTC-4, wrote: snip for brevity My best guess is that the previous homeowner had a GFCI outlet in the garage but replaced it. Should I put in a new GFCI outlet in the garage. Then will I have assurance of GFCI protection in all three outlets? 15 amp or 20 amp outlet? That would depend on how it's wired. If the bathrooms are downstream of the garage, then yes. If they are upstream, then no. A GFCI outlet will protect other outlets that are wired after it, but not before it in the chain. Whether it should be 15 or 20 depends on the existing breaker and wire. 15A, 14g wire, or 20A, 12g. It was common back in that period to have a bath protect a garage or vice-versa. You deduction about what might have happened about someone taking out the GFCI sounds like it could be right, but they would have had to be pretty dumb. Do you mean they were dumb to give up GFCI protection on the bathrooms and garage outlet? Yes, if they did in fact replace the GFCI that was protecting everything with a standard receptacle. It's also a code violation. Or they were dumb to do so for some other reason. At this point, I think the fact that my 2003-ish home inspector (when I bought the home) said nothing on this is a bit discouraging. It's the old but thoroughly lethal electric razor or hair dryer in the bathtub death trick (and similar, and really not funny) we're trying to avoid with bathroom GFCIs in particular, right? I know this because my dad earlier today reviewed just such a case with a teenage girl where I grew up decades ago. A lot of the home inspectors out there aren't that great. Speaking of which, I guess you don't know if the home inspector who flagged this used a tester on the outlets in question? Usually they all have at least one of those and if he doubted the outlets were GFCI, the tester would give the answer. Personally, if it were my house, I'd prefer the GFCI for the baths to be in one of the baths. Not unusual for them to trip and you want it easy to find. The garage one could be downstream of that. But if it's wired the other way around, which you think it is, then the bath can't protect the garage. So, for your solution, if it's wired the way you think, just putting a GFCI back in the garage and using it to protect everything should work. You'll have to pull the garage outlet(s) and determine where the feed to the baths originates to wire it correctly. The other and simpler option would be to replace the breaker with a GFCI one. I'm assuming that the inspector isn't going to interpret the code to mean that this is a "change" that requires everything on that circuit to now be brought up to code. Thank you for your rapid and informed response. Per your commentary, I opened the panel breaker in question, disconnected the corresponding garage receptacle (making sure no wires touched when done), and then shut the panel breaker. I had power at neither of the bathrooms' receptacles. This tells me the garage receptacle is upstream of the bathrooms' receptacles. Any objections to this approach? Sounds logical. The micrometer-ed the wire at the garage receptacle and found it to be 14 gage, so per your note (double checked with the net), I need a 15 amp GFCI receptacle, and I am good to go. I will probably just do it and then if the buyer wants an electrician inspection of same, I will call the guy I called before. Much obliged, trader_4. No problemo. BTW, how did the rest of the inspection go? If this is the worst of your worries, you're in good shape! |
#68
Posted to alt.home.repair
|
|||
|
|||
GFCI Breaker? GFCI Receptacle?
On Friday, August 29, 2014 8:13:39 PM UTC-4, Terry Coombs wrote:
wrote: On Friday, August 29, 2014 2:56:24 PM UTC-6, trader_4 wrote: On Friday, August 29, 2014 4:19:47 PM UTC-4, wrote: snip for brevity My best guess is that the previous homeowner had a GFCI outlet in the garage but replaced it. Should I put in a new GFCI outlet in the garage. Then will I have assurance of GFCI protection in all three outlets? 15 amp or 20 amp outlet? That would depend on how it's wired. If the bathrooms are downstream of the garage, then yes. If they are upstream, then no. A GFCI outlet will protect other outlets that are wired after it, but not before it in the chain. Whether it should be 15 or 20 depends on the existing breaker and wire. 15A, 14g wire, or 20A, 12g. It was common back in that period to have a bath protect a garage or vice-versa. You deduction about what might have happened about someone taking out the GFCI sounds like it could be right, but they would have had to be pretty dumb. Do you mean they were dumb to give up GFCI protection on the bathrooms and garage outlet? Or they were dumb to do so for some other reason. At this point, I think the fact that my 2003-ish home inspector (when I bought the home) said nothing on this is a bit discouraging. It's the old but thoroughly lethal electric razor or hair dryer in the bathtub death trick (and similar, and really not funny) we're trying to avoid with bathroom GFCIs in particular, right? I know this because my dad earlier today reviewed just such a case with a teenage girl where I grew up decades ago. Personally, if it were my house, I'd prefer the GFCI for the baths to be in one of the baths. Not unusual for them to trip and you want it easy to find. The garage one could be downstream of that. But if it's wired the other way around, which you think it is, then the bath can't protect the garage. So, for your solution, if it's wired the way you think, just putting a GFCI back in the garage and using it to protect everything should work. You'll have to pull the garage outlet(s) and determine where the feed to the baths originates to wire it correctly. The other and simpler option would be to replace the breaker with a GFCI one. I'm assuming that the inspector isn't going to interpret the code to mean that this is a "change" that requires everything on that circuit to now be brought up to code. Thank you for your rapid and informed response. Per your commentary, I opened the panel breaker in question, disconnected the corresponding garage receptacle (making sure no wires touched when done), and then shut the panel breaker. I had power at neither of the bathrooms' receptacles. This tells me the garage receptacle is upstream of the bathrooms' receptacles. Any objections to this approach? The micrometer-ed the wire at the garage receptacle and found it to be 14 gage, so per your note (double checked with the net), I need a 15 amp GFCI receptacle, and I am good to go. I will probably just do it and then if the buyer wants an electrician inspection of same, I will call the guy I called before. Much obliged, trader_4. Do you NOT get it that the gfci in the panel gives protection to ALL the outlets that went dead when you turned it off ? There is NO NEED to add a gfci outlet , the entire circuit is protected already . I was confused on this at first too. But I went back and read it again. He isn't saying he has a GFCI breaker. He's saying it's just a regular breaker with a label that says GFI-garage. That's why he was asking if it was possible to have a GFCI breaker and for it to not be obviously identifiable as such. |
#69
Posted to alt.home.repair
|
|||
|
|||
GFCI Breaker? GFCI Receptacle?
trader_4 wrote:
On Friday, August 29, 2014 8:13:39 PM UTC-4, Terry Coombs wrote: Do you NOT get it that the gfci in the panel gives protection to ALL the outlets that went dead when you turned it off ? There is NO NEED to add a gfci outlet , the entire circuit is protected already . I was confused on this at first too. But I went back and read it again. He isn't saying he has a GFCI breaker. He's saying it's just a regular breaker with a label that says GFI-garage. That's why he was asking if it was possible to have a GFCI breaker and for it to not be obviously identifiable as such. Ah , I thought he meant that the breaker was a gfci . If it's not , he needs to determine for sure that the garage is first in the string and install one there . Or install an in-panel gfci , then it won't matter which one is first . -- Snag |
#70
Posted to alt.home.repair
|
|||
|
|||
GFCI Breaker? GFCI Receptacle?
On Friday, August 29, 2014 7:10:36 PM UTC-6, Terry Coombs wrote:
Do you NOT get it that the gfci in the panel gives protection to ALL the outlets that went dead when you turned it off ? There is NO NEED to add a gfci outlet , the entire circuit is protected already . I was confused on this at first too. But I went back and read it again. He isn't saying he has a GFCI breaker. He's saying it's just a regular breaker with a label that says GFI-garage. That's why he was asking if it was possible to have a GFCI breaker and for it to not be obviously identifiable as such. Ah , I thought he meant that the breaker was a gfci . Hi Terry, Trader_4 has it straight. To review: The breaker at issue here and in the panel has nothing that distinguishes it from the dozen or so other breakers in the panel, so I conclude this breaker is not GFCI. The taped label on the side of the breaker refers to the one outlet in the garage that should be GFCI (and soon will be). Thank you for checking in. All this discussion has clarified much in short order. At my gym tonight, I also bumped into an electrician in my neighborhood who happens to have wired many of the houses here some 20 years ago. He confirmed that there is supposed to be a GFCI outlet in the garage that also protects the bathrooms and the outdoor outlets, like all here have been saying. Doug, none of the outdoor outlets are GFCI outlets. They also all tie into the aforementioned breaker. So the outdoor outlets also lacked GFCI protection all these years. Thanks for the input on buying a GFCI tester. I am considering buying one for $15 at Sears. trader_4: The inspector did not use a GFCI tester. It was the realtor who questioned the setup. All the inspector said is that the GFCI was recommended for bathrooms, the garage, and the exterior. I agree today's finding is significant and give the realtor a lot of credit for asking the original question. I know it's not totally unsafe, but of course I agree it's unacceptable to turn the house over without GFCI protected bathrooms. I am also replacing the two other outlets (not fed by the aforementioned panel breaker but by two other breakers) in the garage currently lacking GFCI with GFCI ones. I should have known better last year, when the first evidence that some wiring in the garage had been added, based on the inspection last year. If it's not , he needs to determine for sure that the garage is first in the string and install one there . Or install an in-panel gfci , then it won't matter which one is first . Terry, correct, the one in the garage is first in the string of outlets that includes the two bathrooms and also, per discussion here, with my electrician neighbor and my further checking, the three outlets mounted on the outside of the house (with the special weather resistant covers). Trader_4, the inspector, buyer and buyer's realtor seemed pleased with all, but I count on nothing until I have it in writing. Besides, the buyer's realtor was breathing down the inspector's neck and my neck, so the inspector might have quickly reached the point that he just wanted out of there and would say anything to get back to his report picture taking and short comments. I felt bad for the inspector and the buyer. I know I would need to stay focused if I had the inspector's job. Else in writing I have that the lender has approved the buyer's "credit" and is waiting only on the inspection results. |
#71
Posted to alt.home.repair
|
|||
|
|||
GFCI Breaker? GFCI Receptacle?
|
#72
Posted to alt.home.repair
|
|||
|
|||
GFCI Breaker? GFCI Receptacle?
On Fri, 29 Aug 2014 13:19:47 -0700 (PDT), wrote:
I had another home inspection today. The buyer's realtor was there and ques= tioned why neither of the two bathrooms had GFCI receptacles. The inspector= looked a little confused (the realtor was making jokes throughout the insp= ection, while I waited outside) but added that GFCI was recommended in the = bathrooms and withdrew from the discussion. The electric panel was inspecte= d in 1995 when the house was built and has an inspection sticker for same.= =20 What I found subsequently is that one breaker in my electrical panel is lab= eled "GFI - Garage." Is this a nicely printed label? IF so maybe it was there before the breaker was replaced, and he reused it. For some reason, when my house was less than 8 years old, the GFI breaker started tripping every couple months for no reason. After I was convinced it was for no reason, I replaced it and it hasn't tripped more than twice in 27 years. I think each time I knew the reason. Opening this breaker shuts off power to one outlet in = the garage and both bathrooms' outlets. None of these three outlets have GF= CI test and reset buttons. That's the setup I have in my house built in 1979. I'm not positive they had GFI receptacles then, maybe only breakers???? My breaker controls the recept. in 2 bathrooms and a powder room, on the counter near the kitchen sink, and outside on the "patio". I suppose it controls the outlet next to the laundry sink, into which is plugged the clothes washer, but I've probably always reset the breaker long before I wanted to wwash clothes. The breaker looks the same as all the other brea= kers in the panel. But my breaker certainly doesn't look the same. A) it has a test button. It doesn't protrude and it's not very noticeable (same width and color as the breaker face) but if you push it you can see the handle of the breaker move to OFF. Then to reset, you have to move the handle back even farther (to reset, or something like that. But perhaps the words have come off for some reason) and then back to ON, The outlet in the garage looks like what's shown he = http://www.homedepot.com/p/Leviton-D...-WMP/100684055. 1. Could a GFCI outlet have neither a test nor reset button? No, but a regular outlet or a string of them can receive current from a GFI breaker, and that is just as safe. 2. Could a GFCI breaker in a panel be not obvious? No, I don't think so. Go to the hardeware store or Home Depot and look at what they sell. OTOH, it depends on how observant you are. They must be different but you might not notice. 3. Is it worth the $15 it costs to buy a GFCI tester and test the bathroom out= lets to see if there is GFCI protection of them somewhere? 4. My best guess is that the previous homeowner had a GFCI outlet in the garag= e but replaced it. My best guess is that he had a GFI breaker in the fuse box but replaced it with something that isn't GFI. Should I put in a new GFCI outlet in the garage. Then wi= ll I have assurance of GFCI protection in all three outlets? It depends on which is the most upstream breaker. 15 amp or 20 a= mp outlet? Please r ead my reply to your second post, which also takes into consideration your third post. |
#73
Posted to alt.home.repair
|
|||
|
|||
GFCI Breaker? GFCI Receptacle?
|
#74
Posted to alt.home.repair
|
|||
|
|||
GFCI Breaker? GFCI Receptacle?
micky wrote:
A lot of drivel . How about you crawl back under your rock and let the humans handle this ? -- Snag |
#76
Posted to alt.home.repair
|
|||
|
|||
GFCI Breaker? GFCI Receptacle?
On Friday, August 29, 2014 10:23:06 PM UTC-4, wrote:
On Friday, August 29, 2014 7:10:36 PM UTC-6, Terry Coombs wrote: Do you NOT get it that the gfci in the panel gives protection to ALL the outlets that went dead when you turned it off ? There is NO NEED to add a gfci outlet , the entire circuit is protected already . I was confused on this at first too. But I went back and read it again. He isn't saying he has a GFCI breaker. He's saying it's just a regular breaker with a label that says GFI-garage. That's why he was asking if it was possible to have a GFCI breaker and for it to not be obviously identifiable as such. Ah , I thought he meant that the breaker was a gfci . Hi Terry, Trader_4 has it straight. To review: The breaker at issue here and in the panel has nothing that distinguishes it from the dozen or so other breakers in the panel, so I conclude this breaker is not GFCI. The taped label on the side of the breaker refers to the one outlet in the garage that should be GFCI (and soon will be). Thank you for checking in. All this discussion has clarified much in short order. At my gym tonight, I also bumped into an electrician in my neighborhood who happens to have wired many of the houses here some 20 years ago. He confirmed that there is supposed to be a GFCI outlet in the garage that also protects the bathrooms and the outdoor outlets, like all here have been saying. Doug, none of the outdoor outlets are GFCI outlets. They also all tie into the aforementioned breaker. So the outdoor outlets also lacked GFCI protection all these years. Thanks for the input on buying a GFCI tester. I am considering buying one for $15 at Sears. trader_4: The inspector did not use a GFCI tester. It was the realtor who questioned the setup. Well, I guess that tells you something about the qualifications of the inspector. Any decent inspector, concerned about whether bathroom receptacles have GFCI, would just use his tester. I guess a $15 tester is too much for him. All the inspector said is that the GFCI was recommended for bathrooms, the garage, and the exterior. As Doug pointed out, it was also code when the house was built, which was the 90s correct? I agree today's finding is significant and give the realtor a lot of credit for asking the original question. I know it's not totally unsafe, but of course I agree it's unacceptable to turn the house over without GFCI protected bathrooms. I am also replacing the two other outlets (not fed by the aforementioned panel breaker but by two other breakers) in the garage currently lacking GFCI with GFCI ones. It's kind of unusual for a typical garage to have 3 outlets all fed by 3 separate breakers, but you're right, adding those GFCIs is what's required. I should have known better last year, when the first evidence that some wiring in the garage had been added, based on the inspection last year. Yes, I looked back in the thread and saw that. Looks like it was amature hour. If it's not , he needs to determine for sure that the garage is first in the string and install one there . Or install an in-panel gfci , then it won't matter which one is first . Terry, correct, the one in the garage is first in the string of outlets that includes the two bathrooms and also, per discussion here, with my electrician neighbor and my further checking, the three outlets mounted on the outside of the house (with the special weather resistant covers). Trader_4, the inspector, buyer and buyer's realtor seemed pleased with all, but I count on nothing until I have it in writing. That's good to hear. So the deal is going well. Besides, the buyer's realtor was breathing down the inspector's neck and my neck, so the inspector might have quickly reached the point that he just wanted out of there and would say anything to get back to his report picture taking and short comments. So the buyer's incompetent realtor actually helped you by screwing with the inspector. I felt bad for the inspector and the buyer. I know I would need to stay focused if I had the inspector's job. Else in writing I have that the lender has approved the buyer's "credit" and is waiting only on the inspection results. I wouldn't feel too bad for an inspector who can't test a bath GFCI. Sounds like he and the seller's incompetent realtor deserve each other. |
#77
Posted to alt.home.repair
|
|||
|
|||
GFCI Breaker? GFCI Receptacle?
On Friday, August 29, 2014 10:53:10 PM UTC-4, Doug Miller wrote:
wrote in : trader_4: The inspector did not use a GFCI tester. It was the realtor who questioned the setup. All the inspector said is that the GFCI was recommended for bathrooms, the garage, and the exterior. I agree today's finding is significant and give the realtor a lot of credit for asking the original question. I know it's not totally unsafe, but of course I agree it's unacceptable to turn the house over without GFCI protected bathrooms. I am also replacing the two other outlets (not fed by the aforementioned panel breaker but by two other breakers) in the garage currently lacking GFCI with GFCI ones. This is unnecessary expense and effort. *One* GFCI receptacle in the garage is sufficient to provide GFCI protection for the entire circuit. You do *not* need to have GFCI receptacles in the bathrooms if there is one in the garage, wired to provide downstream protection. The installation instructions that accompany the GFCI receptacle will show clearly how to do that. He actually said that the two other receptacles in the garage are on two separate breakers, so he does need two GFCI for those, plus one for the garage outlet that also feeds the bath and outdoors. Three total. |
#78
Posted to alt.home.repair
|
|||
|
|||
GFCI Breaker? GFCI Receptacle?
On Friday, August 29, 2014 11:37:33 PM UTC-4, micky wrote:
On Fri, 29 Aug 2014 13:19:47 -0700 (PDT), wrote: I had another home inspection today. The buyer's realtor was there and ques= tioned why neither of the two bathrooms had GFCI receptacles. The inspector= looked a little confused (the realtor was making jokes throughout the insp= ection, while I waited outside) but added that GFCI was recommended in the = bathrooms and withdrew from the discussion. The electric panel was inspecte= d in 1995 when the house was built and has an inspection sticker for same.= =20 What I found subsequently is that one breaker in my electrical panel is lab= eled "GFI - Garage." Is this a nicely printed label? IF so maybe it was there before the breaker was replaced, and he reused it. It's there so folks will see it and know that there is a GFCI in the garage. The scenario is Joe finds that some receptacle, lights, whatever aren't working. First thing Joe does is think it's the breaker. Upon looking, he sees the label, so now he knows if it involves that circuit, the other possible problem is the GFCI in the garage. For some reason, when my house was less than 8 years old, the GFI breaker started tripping every couple months for no reason. After I was convinced it was for no reason, I replaced it and it hasn't tripped more than twice in 27 years. I think each time I knew the reason. Opening this breaker shuts off power to one outlet in = the garage and both bathrooms' outlets. None of these three outlets have GF= CI test and reset buttons. That's the setup I have in my house built in 1979. I'm not positive they had GFI receptacles then, maybe only breakers???? My breaker controls the recept. in 2 bathrooms and a powder room, on the counter near the kitchen sink, and outside on the "patio". I suppose it controls the outlet next to the laundry sink, into which is plugged the clothes washer, but I've probably always reset the breaker long before I wanted to wwash clothes. That's a lot of loads for one circuit. Code today requires the laundry room have it's own circuit. Not sure the history there, but I don't think it's been code to have all that on one circuit for a very long time. The breaker looks the same as all the other brea= kers in the panel. But my breaker certainly doesn't look the same. A) it has a test button. It doesn't protrude and it's not very noticeable (same width and color as the breaker face) but if you push it you can see the handle of the breaker move to OFF. Then to reset, you have to move the handle back even farther (to reset, or something like that. That's because you have a GFCI breaker, Honda doesn't. |
#79
Posted to alt.home.repair
|
|||
|
|||
GFCI Breaker? GFCI Receptacle?
On Saturday, August 30, 2014 5:40:47 AM UTC-6, trader_4 wrote:
On Friday, August 29, 2014 10:23:06 PM UTC-4, wrote: trader_4: The inspector did not use a GFCI tester. It was the realtor who questioned the setup. Well, I guess that tells you something about the qualifications of the inspector. Any decent inspector, concerned about whether bathroom receptacles have GFCI, would just use his tester. I guess a $15 tester is too much for him. Yes, though I wonder whether it is either company, state, or current licensure policy to discourage/disallow home inspectors from getting into too much detail regarding the wiring. They're not electricians, after all. OTOH, it does seem like baloney, because in what seems my relatively simple case where a DIY-er added outlets to the garage and took out a GFCI outlet critical to several 'likely subject to moisture' circuits, the typical lay-buyer would need a licensed electrician to really study everything and get some assurance all was well GFCI-wise and in all ways. It seems to me a home inspection should really be looking for big ticket safety issues. Electrical problems have to be a leading cause of deaths, fires etc. in a house, maybe second to falling off ladders when it comes to injuries. At this point if and when I buy another house or condominium, and not needing to take a loan for same, I think I will forego a house inspection. It seems a farce for anyone with years of experience owning a home and having some electrical background. Or knowing to make inquiries on the net and of friends. :-) If there are problems, then buyer and seller can call in a licensed specialist to resolve the situation. All the inspector said is that the GFCI was recommended for bathrooms, the garage, and the exterior. As Doug pointed out, it was also code when the house was built, which was the 90s correct? Yes, the house was built in the mid-1990s. After the buyer's realtor questioned the lack of GFCI outlets in the bathroom point, the Inspector pointed out what Doug and others pointed out. What the inspector was ignorant of was the bathrooms being GFCI protected via a GFCI garage outlet upstream of the bathrooms' outlets. I agree today's finding is significant and give the realtor a lot of credit for asking the original question. I know it's not totally unsafe, but of course I agree it's unacceptable to turn the house over without GFCI protected bathrooms. I am also replacing the two other outlets (not fed by the aforementioned panel breaker but by two other breakers) in the garage currently lacking GFCI with GFCI ones. It's kind of unusual for a typical garage to have 3 outlets all fed by 3 separate breakers, but you're right, adding those GFCIs is what's required. Thanks for the reinforcement. Micky, trader_4 has things straight here, I think with all others. I should have known better last year, when the first evidence that some wiring in the garage had been added, based on the inspection last year. Yes, I looked back in the thread and saw that. Looks like it was amature hour. Yes, including my not catching this until yesterday upon the realtor's questioning and the inspector saying the baths should be GFCI protected (or similar wording). The only thing last year's report stated on this entire matter was that "GFCI outlets are recommended for installation at exterior, garage, bath rooms outlets [sic]." Anyone saying what was found yesterday was a code violation and it should have been noted as an unacceptable deficiency: I agree. What this second inspection report says will be interesting. It is due in a few days. Trader_4, the inspector, buyer and buyer's realtor seemed pleased with all, but I count on nothing until I have it in writing. That's good to hear. So the deal is going well. On paper, per what the buyer and I have signed to resuscitate the deal, and the inspections and loan approval that have gone forward, I would say it is going well. There is tenseness between the realtors and me. My realtor and I are already in the habit of double-checking and text-alerting that we each received any documents sent. Yesterday the buyer's realtor started trying this baloney double talk yesterday, and he and I had some words. He looked surprised that I would call him out for not scheduling the inspection period, resulting in a significant delay and putting the deal in peril. The buyer's realtor started talking about how he wanted a happy buyer and seller and how many deals he had done. I gave him a look and off-the-cuff said, "You want your sales commission as quickly as possible." The buyer laughed. I think the buyer's pretty savvy and just wants the house (assuming no major inspection problems). The inspector walked away, perhaps sensing the sparks. I have had it with this realtor double talk. I think realtors today are formally trained in used car sales-speak. I am not taking being pushed around by either realtor at this point. If the deal falls through, so be it. But I think all of us have enough invested that it will go through, assuming the loan is approved. Besides, the buyer's realtor was breathing down the inspector's neck and my neck, so the inspector might have quickly reached the point that he just wanted out of there and would say anything to get back to his report picture taking and short comments. So the buyer's incompetent realtor actually helped you by screwing with the inspector. I think the inspector was a bit aggravated and more likely to take it out on me. My own realtor had to cancel his presence at the last minute, whence I agreed to be there, let the inspector in, and then absent myself. Then the buyer and the buyer's realtor show up, un-announced. All were 15 minutes late. No big deal but it miffed me a bit. My realtor said the buyer had made no request to be present but of course none of us had a problem with their wanting to be there. My realtor told me the inspection was mostly a "re-inspection" for home warranty purposes and so should only take a half an hour or so. I was hanging out in the backyard, weeding, for the first hour. When I heard all the laughter and the buyer's realtor's voice leading the chatter, and not happy with the delay and joking on my time and when I needed a focused inspector, I said 'enough,' and started shadowing the group. With hindsight I am thinking I should have pulled the buyer's realtor aside and told him that I felt the inspector needed to stay focused, and please only ask technical questions without interrupting the inspector otherwise. Still, and again, I credit the buyer's realtor for calling out the GFCI situation. Like much, it's not black-and-white. Maybe he earned his commission with just this one, significant observation. I was so disgusted about how all was proceeding that I responded to the buyer's realtor, re the GFCI query, with a sarcastic "oh well." Obviously I had not dug into the GFCI situation at this point. I felt bad for the inspector and the buyer. I know I would need to stay focused if I had the inspector's job. Else in writing I have that the lender has approved the buyer's "credit" and is waiting only on the inspection results. I wouldn't feel too bad for an inspector who can't test a bath GFCI. Sounds like he and the seller's incompetent realtor deserve each other. They did make a good match, overall. Yesterday I asked me realtor to forward a note to the buyer (via the buyer's realtor) that I would be remedying the bathroom/exterior/garage GFCI situation. I do not care what the report says or whether the buyer was going to object or not. I am not turning over the house with what I personally know now is a code violation. It's costing me under $40 for parts and a few hours of labor. If the buyer says he wants a licensed electrician to check all, I do not blame him. The buyer does not know electricity from plumbing nor me from Adam. |
#80
Posted to alt.home.repair
|
|||
|
|||
GFCI Breaker? GFCI Receptacle?
On Friday, August 29, 2014 11:11:11 PM UTC-6, wrote:
The receptacle just has to be outside of the "tub space". Thanks . The receptacles are located out of the tub space in both baths, about as far as they could possibly be from the tub. I think someone asked about the outcome of the teenage girl I mentioned yesterday. I believe this happened in the late 1960s or early 1970s, when I was net yet a teenager myself. The girl was from a well-to-do family and was in the bathtub, simultaneously soaking and drying her hair with an electric dryer. Maybe one of the old fashioned hair net versions? The dryer fell in the bath water. She was electrocuted and died instantly. This was several miles from where I lived, different school district and all, but the papers reported on it amply. All the parents were talking about it. Of course they were saddened for the girls' family and went to some trouble to make sure it did not happen to their own kids. |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
home inspection | Home Ownership | |||
Home inspection | Home Repair | |||
Home Inspection? | Home Repair | |||
Home inspection window expired without home inspection | Home Ownership | |||
Would appreciate some first time home buying advice..re home inspection and negotiation | Home Repair |