Adding neutral/ground bar to Siemens S2020B1100 panel
I have a Siemens 100-amp main panel (Catalog #: S2020B1100), and it only has
one neutral/ground bar. The neutral/ground bar is on the right side of the panel. I am trying to figure out if I can add another neutral/ground bar on the left side and, if so, how to do that. The information about Siemens service panels is located at: http://www.hqs.sbt.siemens.com/gip/g..._App_Guide.pdf . This panel is a Siemens "ES" Series Load Center, and it has 20 circuits. On page 3 of the above online guide it says, "Single sided neutral on 24 circuits and below". So that explains why the panel that I have only has one neutral bar installed. My question again is, can I add another neutral/ground bar on the left side and, if so, how do I do that? Thanks. |
#2
Posted to alt.home.repair
|
|||
|
|||
Adding neutral/ground bar to Siemens S2020B1100 panel
On Apr 25, 10:27*am, "TomR" wrote:
I have a Siemens 100-amp main panel (Catalog #: S2020B1100), and it only has one neutral/ground bar. *The neutral/ground bar is on the right side of the panel. I am trying to figure out if I can add another neutral/ground bar on the left side and, if so, how to do that. The information about Siemens service panels is located at:http://www.hqs..sbt.siemens.com/gip/...ets/US/SIILV/S.... This panel is a Siemens "ES" Series Load Center, and it has 20 circuits. *On page 3 of the above online guide it says, "Single sided neutral on 24 circuits and below". *So that explains why the panel that I have only has one neutral bar installed. My question again is, can I add another neutral/ground bar on the left side and, if so, how do I do that? *Thanks. Is it just that you want a neutral/ground bus on the other side for convenience or is it that you've run out of terminals? If it's the latter, the product guide has a ECGB14, which is a ground bar that can be installed in that panel. So, one way to do it would be to add that ground bar, move some of the ground wires from the existing neutral/ground bus to it, thereby freeing up other terminals for more neutrals. If you just want another neutral/ground bus on the other side, not sure if you can do that and be code compliant. |
#4
Posted to alt.home.repair
|
|||
|
|||
Adding neutral/ground bar to Siemens S2020B1100 panel
I have a Siemens 100-amp main panel (Catalog #: S2020B1100), and it only
has one neutral/ground bar. The neutral/ground bar is on the right side of the panel. I am trying to figure out if I can add another neutral/ground bar on the left side and, if so, how to do that. The information about Siemens service panels is located at: http://www.hqs.sbt.siemens.com/gip/g..._App_Guide.pdf . This panel is a Siemens "ES" Series Load Center, and it has 20 circuits. On page 3 of the above online guide it says, "Single sided neutral on 24 circuits and below". So that explains why the panel that I have only has one neutral bar installed. My question again is, can I add another neutral/ground bar on the left side and, if so, how do I do that? Thanks. *Drill and tap two 8/32 holes. Mount the ground bar. Run a number 8 or 6 wire from the new ground bar to the existing ground/neutral bar. |
#5
Posted to alt.home.repair
|
|||
|
|||
Adding neutral/ground bar to Siemens S2020B1100 panel
On Apr 25, 4:21*pm, "John Grabowski" wrote:
I have a Siemens 100-amp main panel (Catalog #: S2020B1100), and it only has one neutral/ground bar. *The neutral/ground bar is on the right side of the panel. I am trying to figure out if I can add another neutral/ground bar on the left side and, if so, how to do that. The information about Siemens service panels is located at: http://www.hqs.sbt.siemens.com/gip/g...ets/US/SIILV/S..... This panel is a Siemens "ES" Series Load Center, and it has 20 circuits.. On page 3 of the above online guide it says, "Single sided neutral on 24 circuits and below". *So that explains why the panel that I have only has one neutral bar installed. My question again is, can I add another neutral/ground bar on the left side and, if so, how do I do that? *Thanks. *Drill and tap two 8/32 holes. *Mount the ground bar. *Run a number 8 or 6 wire from the new ground bar to the existing ground/neutral bar. if the cabinet is too thin to tap but mounted on plywood like it should be, just drill holes and use wood screws to mount the ground bar to the cabinet, then heavy copper between the old and new ground bars... |
#6
Posted to alt.home.repair
|
|||
|
|||
Adding neutral/ground bar to Siemens S2020B1100 panel
On Apr 25, 4:21*pm, "John Grabowski" wrote:
I have a Siemens 100-amp main panel (Catalog #: S2020B1100), and it only has one neutral/ground bar. *The neutral/ground bar is on the right side of the panel. I am trying to figure out if I can add another neutral/ground bar on the left side and, if so, how to do that. The information about Siemens service panels is located at: http://www.hqs.sbt.siemens.com/gip/g...ets/US/SIILV/S..... This panel is a Siemens "ES" Series Load Center, and it has 20 circuits.. On page 3 of the above online guide it says, "Single sided neutral on 24 circuits and below". *So that explains why the panel that I have only has one neutral bar installed. My question again is, can I add another neutral/ground bar on the left side and, if so, how do I do that? *Thanks. *Drill and tap two 8/32 holes. *Mount the ground bar. *Run a number 8 or 6 wire from the new ground bar to the existing ground/neutral bar.- Hide quoted text - - Show quoted text - But what he originally asked for was adding a second "ground/neutral bar" on the other side of the panel. You can add a ground bar and I don't think he needs to drill any holes, as Siemens has one for the panel, so it should already have compatible holes. But I think that's only code compliant as an additional ground bar, meaning you can't use it for neutrals..... Is that correct? If he moves some ground wires from the existing neutral/ground bus to the new bar though he would free up locations for more neutral wires. Also, can't you put more than one ground wire under a screw in at least some panels? That alone might solve the problem? |
#7
Posted to alt.home.repair
|
|||
|
|||
Adding neutral/ground bar to Siemens S2020B1100 panel
On 4/25/2013 7:13 PM, wrote:
On Apr 25, 4:21 pm, "John Grabowski" wrote: I have a Siemens 100-amp main panel (Catalog #: S2020B1100), and it only has one neutral/ground bar. The neutral/ground bar is on the right side of the panel. I am trying to figure out if I can add another neutral/ground bar on the left side and, if so, how to do that. The information about Siemens service panels is located at: http://www.hqs.sbt.siemens.com/gip/g...ets/US/SIILV/S.... This panel is a Siemens "ES" Series Load Center, and it has 20 circuits. On page 3 of the above online guide it says, "Single sided neutral on 24 circuits and below". So that explains why the panel that I have only has one neutral bar installed. My question again is, can I add another neutral/ground bar on the left side and, if so, how do I do that? Thanks. *Drill and tap two 8/32 holes. Mount the ground bar. Run a number 8 or 6 wire from the new ground bar to the existing ground/neutral bar.- Hide quoted text - - Show quoted text - But what he originally asked for was adding a second "ground/neutral bar" on the other side of the panel. You can add a ground bar and I don't think he needs to drill any holes, as Siemens has one for the panel, so it should already have compatible holes. But I think that's only code compliant as an additional ground bar, meaning you can't use it for neutrals..... Is that correct? If he moves some ground wires from the existing neutral/ground bus to the new bar though he would free up locations for more neutral wires. Also, can't you put more than one ground wire under a screw in at least some panels? That alone might solve the problem? If the bar is threaded into the panel, it would suffice as a ground bar only. If as John said, you run a #6 or 8 from it to the neutral bar, it'll work for both. You can put two grounds under one screw is some panels as well |
#8
Posted to alt.home.repair
|
|||
|
|||
Adding neutral/ground bar to Siemens S2020B1100 panel
On Apr 25, 4:13*pm, "
wrote: On Apr 25, 4:21*pm, "John Grabowski" wrote: I have a Siemens 100-amp main panel (Catalog #: S2020B1100), and it only has one neutral/ground bar. *The neutral/ground bar is on the right side of the panel. I am trying to figure out if I can add another neutral/ground bar on the left side and, if so, how to do that. The information about Siemens service panels is located at: http://www.hqs.sbt.siemens.com/gip/g...ets/US/SIILV/S..... This panel is a Siemens "ES" Series Load Center, and it has 20 circuits. On page 3 of the above online guide it says, "Single sided neutral on 24 circuits and below". *So that explains why the panel that I have only has one neutral bar installed. My question again is, can I add another neutral/ground bar on the left side and, if so, how do I do that? *Thanks. *Drill and tap two 8/32 holes. *Mount the ground bar. *Run a number 8 or 6 wire from the new ground bar to the existing ground/neutral bar.- Hide quoted text - - Show quoted text - But what he originally asked for was adding a second "ground/neutral bar" on the other side of the panel. *You can add a ground bar and I don't think he needs to drill any holes, as Siemens has one for the panel, so it should already have compatible holes. But I think that's only code compliant as an additional ground bar, meaning you can't use it for neutrals..... *Is that correct? *If he moves some ground wires from the existing neutral/ground bus to the new bar though he would free up locations for more neutral wires. Also, can't you put more than one ground wire under a screw in at least some panels? * That alone might solve the problem? I believe you can double up ground wires but neutral wires must be one per screw. |
#9
Posted to alt.home.repair
|
|||
|
|||
Adding neutral/ground bar to Siemens S2020B1100 panel
On Apr 25, 9:07*pm, DD_BobK wrote:
On Apr 25, 4:13*pm, " wrote: On Apr 25, 4:21*pm, "John Grabowski" wrote: I have a Siemens 100-amp main panel (Catalog #: S2020B1100), and it only has one neutral/ground bar. *The neutral/ground bar is on the right side of the panel. I am trying to figure out if I can add another neutral/ground bar on the left side and, if so, how to do that. The information about Siemens service panels is located at: http://www.hqs.sbt.siemens.com/gip/g...ets/US/SIILV/S.... This panel is a Siemens "ES" Series Load Center, and it has 20 circuits. On page 3 of the above online guide it says, "Single sided neutral on 24 circuits and below". *So that explains why the panel that I have only has one neutral bar installed. My question again is, can I add another neutral/ground bar on the left side and, if so, how do I do that? *Thanks. *Drill and tap two 8/32 holes. *Mount the ground bar. *Run a number 8 or 6 wire from the new ground bar to the existing ground/neutral bar.- Hide quoted text - - Show quoted text - But what he originally asked for was adding a second "ground/neutral bar" on the other side of the panel. *You can add a ground bar and I don't think he needs to drill any holes, as Siemens has one for the panel, so it should already have compatible holes. But I think that's only code compliant as an additional ground bar, meaning you can't use it for neutrals..... *Is that correct? *If he moves some ground wires from the existing neutral/ground bus to the new bar though he would free up locations for more neutral wires. Also, can't you put more than one ground wire under a screw in at least some panels? * That alone might solve the problem? I believe you can double up ground wires but neutral wires must be one per screw. Why put 2 under one screw if you dont have to? The panel will look far better if its neat and organized thats one wire per screw and definetely tie the 2 bars together... |
#10
Posted to alt.home.repair
|
|||
|
|||
Adding neutral/ground bar to Siemens S2020B1100 panel
"RBM" wrote in message
... On 4/25/2013 7:13 PM, wrote: On Apr 25, 4:21 pm, "John Grabowski" wrote: I have a Siemens 100-amp main panel (Catalog #: S2020B1100), and it only has one neutral/ground bar. The neutral/ground bar is on the right side of the panel. I am trying to figure out if I can add another neutral/ground bar on the left side and, if so, how to do that. The information about Siemens service panels is located at: http://www.hqs.sbt.siemens.com/gip/g...ets/US/SIILV/S.... This panel is a Siemens "ES" Series Load Center, and it has 20 circuits. On page 3 of the above online guide it says, "Single sided neutral on 24 circuits and below". So that explains why the panel that I have only has one neutral bar installed. My question again is, can I add another neutral/ground bar on the left side and, if so, how do I do that? Thanks. *Drill and tap two 8/32 holes. Mount the ground bar. Run a number 8 or 6 wire from the new ground bar to the existing ground/neutral bar.- Hide quoted text - - Show quoted text - But what he originally asked for was adding a second "ground/neutral bar" on the other side of the panel. You can add a ground bar and I don't think he needs to drill any holes, as Siemens has one for the panel, so it should already have compatible holes. But I think that's only code compliant as an additional ground bar, meaning you can't use it for neutrals..... Is that correct? If he moves some ground wires from the existing neutral/ground bus to the new bar though he would free up locations for more neutral wires. Also, can't you put more than one ground wire under a screw in at least some panels? That alone might solve the problem? If the bar is threaded into the panel, it would suffice as a ground bar only. If as John said, you run a #6 or 8 from it to the neutral bar, it'll work for both. Thanks. I think that is going to be the plan -- to add a ground bar and, as John said, run a #6 or 8 from it to the neutral bar so it will work as a ground and a neutral bar. And, as Trader4 siad, "the product guide has a ECGB14, which is a ground bar that can be installed in that panel", so we can use that since it is made for that panel and it is made to be threaded into the panel. You can put two grounds under one screw is some panels as well. That's good to know. I did see that the electrician who put the panel in did put two grounds under one screw is a couple of cases for the circuits that he installed; but only one neutral wire (by itself) under any screw. |
#11
Posted to alt.home.repair
|
|||
|
|||
Adding neutral/ground bar to Siemens S2020B1100 panel
I have a Siemens 100-amp main panel (Catalog #: S2020B1100), and it
only has one neutral/ground bar. The neutral/ground bar is on the right side of the panel. I am trying to figure out if I can add another neutral/ground bar on the left side and, if so, how to do that. The information about Siemens service panels is located at: http://www.hqs.sbt.siemens.com/gip/g...ets/US/SIILV/S.... This panel is a Siemens "ES" Series Load Center, and it has 20 circuits. On page 3 of the above online guide it says, "Single sided neutral on 24 circuits and below". So that explains why the panel that I have only has one neutral bar installed. My question again is, can I add another neutral/ground bar on the left side and, if so, how do I do that? Thanks. *Drill and tap two 8/32 holes. Mount the ground bar. Run a number 8 or 6 wire from the new ground bar to the existing ground/neutral bar.- Hide quoted text - - Show quoted text - But what he originally asked for was adding a second "ground/neutral bar" on the other side of the panel. You can add a ground bar and I don't think he needs to drill any holes, as Siemens has one for the panel, so it should already have compatible holes. But I think that's only code compliant as an additional ground bar, meaning you can't use it for neutrals..... Is that correct? If he moves some ground wires from the existing neutral/ground bus to the new bar though he would free up locations for more neutral wires. Also, can't you put more than one ground wire under a screw in at least some panels? That alone might solve the problem? If the bar is threaded into the panel, it would suffice as a ground bar only. If as John said, you run a #6 or 8 from it to the neutral bar, it'll work for both. Thanks. I think that is going to be the plan -- to add a ground bar and, as John said, run a #6 or 8 from it to the neutral bar so it will work as a ground and a neutral bar. And, as Trader4 siad, "the product guide has a ECGB14, which is a ground bar that can be installed in that panel", so we can use that since it is made for that panel and it is made to be threaded into the panel. You can put two grounds under one screw is some panels as well. That's good to know. I did see that the electrician who put the panel in did put two grounds under one screw is a couple of cases for the circuits that he installed; but only one neutral wire (by itself) under any screw. *If you read the label on the Siemens panel, it should tell you how many ground wires you can get under one screw. Sometimes it is more than two. Neutrals are one per screw. |
#12
Posted to alt.home.repair
|
|||
|
|||
Adding neutral/ground bar to Siemens S2020B1100 panel
On Apr 25, 7:44*pm, RBM wrote:
On 4/25/2013 7:13 PM, wrote: On Apr 25, 4:21 pm, "John Grabowski" wrote: I have a Siemens 100-amp main panel (Catalog #: S2020B1100), and it only has one neutral/ground bar. *The neutral/ground bar is on the right side of the panel. I am trying to figure out if I can add another neutral/ground bar on the left side and, if so, how to do that. The information about Siemens service panels is located at: http://www.hqs.sbt.siemens.com/gip/g...ets/US/SIILV/S..... This panel is a Siemens "ES" Series Load Center, and it has 20 circuits. On page 3 of the above online guide it says, "Single sided neutral on 24 circuits and below". *So that explains why the panel that I have only has one neutral bar installed. My question again is, can I add another neutral/ground bar on the left side and, if so, how do I do that? *Thanks. *Drill and tap two 8/32 holes. *Mount the ground bar. *Run a number 8 or 6 wire from the new ground bar to the existing ground/neutral bar.- Hide quoted text - - Show quoted text - But what he originally asked for was adding a second "ground/neutral bar" on the other side of the panel. *You can add a ground bar and I don't think he needs to drill any holes, as Siemens has one for the panel, so it should already have compatible holes. But I think that's only code compliant as an additional ground bar, meaning you can't use it for neutrals..... *Is that correct? *If he moves some ground wires from the existing neutral/ground bus to the new bar though he would free up locations for more neutral wires. Also, can't you put more than one ground wire under a screw in at least some panels? * That alone might solve the problem? If the bar is threaded into the panel, it would suffice as a ground bar only. If as John said, you run a #6 or 8 from it to the neutral bar, it'll work for both. You can put two grounds under one screw is some panels as well- Hide quoted text - - Show quoted text - But something about that doesn't seem quite right. If you just run a #6 or #8 wire between the new bar and the old bar, then you're relying on that wire to potentially carry the max current rating (100 amps) of the panel when in service, on a regular basis, as opposed to just a ground fault condition, no? Which could occur. I would think the conductor between the two would have to be rated for at least the max current of the panel, (100 amps). Isn't there a similar issue also with using an add on "ground" bar as both a ground bar and neutral? The bar in the Siemens catalog is listed for use with that panel as a ground bar, but does that mean that it has the same current rating, etc that a neutral bar would have? I realize in practice it may actually be the same bar, but who knows? |
#13
Posted to alt.home.repair
|
|||
|
|||
Adding neutral/ground bar to Siemens S2020B1100 panel
On Apr 26, 7:33*am, "
wrote: On Apr 25, 7:44*pm, RBM wrote: On 4/25/2013 7:13 PM, wrote: On Apr 25, 4:21 pm, "John Grabowski" wrote: I have a Siemens 100-amp main panel (Catalog #: S2020B1100), and it only has one neutral/ground bar. *The neutral/ground bar is on the right side of the panel. I am trying to figure out if I can add another neutral/ground bar on the left side and, if so, how to do that. The information about Siemens service panels is located at: http://www.hqs.sbt.siemens.com/gip/g...ets/US/SIILV/S.... This panel is a Siemens "ES" Series Load Center, and it has 20 circuits. On page 3 of the above online guide it says, "Single sided neutral on 24 circuits and below". *So that explains why the panel that I have only has one neutral bar installed. My question again is, can I add another neutral/ground bar on the left side and, if so, how do I do that? *Thanks. *Drill and tap two 8/32 holes. *Mount the ground bar. *Run a number 8 or 6 wire from the new ground bar to the existing ground/neutral bar.- Hide quoted text - - Show quoted text - But what he originally asked for was adding a second "ground/neutral bar" on the other side of the panel. *You can add a ground bar and I don't think he needs to drill any holes, as Siemens has one for the panel, so it should already have compatible holes. But I think that's only code compliant as an additional ground bar, meaning you can't use it for neutrals..... *Is that correct? *If he moves some ground wires from the existing neutral/ground bus to the new bar though he would free up locations for more neutral wires. Also, can't you put more than one ground wire under a screw in at least some panels? * That alone might solve the problem? If the bar is threaded into the panel, it would suffice as a ground bar only. If as John said, you run a #6 or 8 from it to the neutral bar, it'll work for both. You can put two grounds under one screw is some panels as well- Hide quoted text - - Show quoted text - But something about that doesn't seem quite right. *If you just run a #6 or #8 wire between the new bar and the old bar, then you're relying on that wire to potentially carry the max current rating (100 amps) of the panel when in service, on a regular basis, as opposed to just a ground fault condition, no? Which could occur. *I would think the conductor between the two would have to be rated for at least the max current of the panel, (100 amps). *Isn't there a similar issue also with using an add on "ground" bar as both a ground bar and neutral? * The bar in the Siemens catalog is listed for use with that panel as a ground bar, but does that mean that it has the same current rating, etc that a neutral bar would have? * I realize in practice it may actually be the same bar, but who knows? well you could run 2 heavy copper lines between the bars....... how heavy is the neutral line to the existing bar? |
#14
Posted to alt.home.repair
|
|||
|
|||
Adding neutral/ground bar to Siemens S2020B1100 panel
On Apr 26, 7:41*am, bob haller wrote:
On Apr 26, 7:33*am, " wrote: On Apr 25, 7:44*pm, RBM wrote: On 4/25/2013 7:13 PM, wrote: On Apr 25, 4:21 pm, "John Grabowski" wrote: I have a Siemens 100-amp main panel (Catalog #: S2020B1100), and it only has one neutral/ground bar. *The neutral/ground bar is on the right side of the panel. I am trying to figure out if I can add another neutral/ground bar on the left side and, if so, how to do that. The information about Siemens service panels is located at: http://www.hqs.sbt.siemens.com/gip/g...ets/US/SIILV/S.... This panel is a Siemens "ES" Series Load Center, and it has 20 circuits. On page 3 of the above online guide it says, "Single sided neutral on 24 circuits and below". *So that explains why the panel that I have only has one neutral bar installed. My question again is, can I add another neutral/ground bar on the left side and, if so, how do I do that? *Thanks. *Drill and tap two 8/32 holes. *Mount the ground bar. *Run a number 8 or 6 wire from the new ground bar to the existing ground/neutral bar.- Hide quoted text - - Show quoted text - But what he originally asked for was adding a second "ground/neutral bar" on the other side of the panel. *You can add a ground bar and I don't think he needs to drill any holes, as Siemens has one for the panel, so it should already have compatible holes. But I think that's only code compliant as an additional ground bar, meaning you can't use it for neutrals..... *Is that correct? *If he moves some ground wires from the existing neutral/ground bus to the new bar though he would free up locations for more neutral wires. Also, can't you put more than one ground wire under a screw in at least some panels? * That alone might solve the problem? If the bar is threaded into the panel, it would suffice as a ground bar only. If as John said, you run a #6 or 8 from it to the neutral bar, it'll work for both. You can put two grounds under one screw is some panels as well- Hide quoted text - - Show quoted text - But something about that doesn't seem quite right. *If you just run a #6 or #8 wire between the new bar and the old bar, then you're relying on that wire to potentially carry the max current rating (100 amps) of the panel when in service, on a regular basis, as opposed to just a ground fault condition, no? Which could occur. *I would think the conductor between the two would have to be rated for at least the max current of the panel, (100 amps). *Isn't there a similar issue also with using an add on "ground" bar as both a ground bar and neutral? * The bar in the Siemens catalog is listed for use with that panel as a ground bar, but does that mean that it has the same current rating, etc that a neutral bar would have? * I realize in practice it may actually be the same bar, but who knows? well you could run 2 heavy copper lines between the bars....... how heavy is the neutral line to the existing bar?- Hide quoted text - - Show quoted text - I think there are two seperate issues/questions here. One is what minimum things need to be in place from an electrical circuit theory perspective. And unless I'm missing something, that says the conductor between the bars better be at least the capacity of the panel, ie 100 amps. The other is what is technically allowed by code, how the panel and bar are UL listed, tested, etc. For example, it's been debated here whether you can add a simple mechanical slide lock-out for a generator to an existing panel when that slide isn't made by that panel manufacturer, hasn't been UL listed for use with that panel, etc. That slide just sits on top of the panel, doesn't even have direct electrical involvement. It just prevents two breakers from being "on" at the same time. So, thinking along those lines, we have a bar rated and listed for use with the panel as a ground bar. The installation instructions only say how to install it as a ground bar. Is it code compliant to use that for neutrals too? What's the current rating of that bar? What would an inspector say? I would think you, being very concerned that anything potentially not being done fully compliant will come back to bite you in a lawsuit from a future owner, a denied insurance claim, etc would agree that there are issues other than what will work electrically. If he installs it, uses it only for grounds, moves some of the existing grounds from the current "neutral/ground bar" over to it, he can get more neutral connections and I think we all agree it's 100% code compliant. Using that added ground bar as a neutral bar, I'm not convinced. |
#15
Posted to alt.home.repair
|
|||
|
|||
Adding neutral/ground bar to Siemens S2020B1100 panel
On Apr 25, 10:08*pm, bob haller wrote:
On Apr 25, 9:07*pm, DD_BobK wrote: On Apr 25, 4:13*pm, " wrote: On Apr 25, 4:21*pm, "John Grabowski" wrote: I have a Siemens 100-amp main panel (Catalog #: S2020B1100), and it only has one neutral/ground bar. *The neutral/ground bar is on the right side of the panel. I am trying to figure out if I can add another neutral/ground bar on the left side and, if so, how to do that. The information about Siemens service panels is located at: http://www.hqs.sbt.siemens.com/gip/g...ets/US/SIILV/S.... This panel is a Siemens "ES" Series Load Center, and it has 20 circuits. On page 3 of the above online guide it says, "Single sided neutral on 24 circuits and below". *So that explains why the panel that I have only has one neutral bar installed. My question again is, can I add another neutral/ground bar on the left side and, if so, how do I do that? *Thanks. *Drill and tap two 8/32 holes. *Mount the ground bar. *Run a number 8 or 6 wire from the new ground bar to the existing ground/neutral bar.- Hide quoted text - - Show quoted text - But what he originally asked for was adding a second "ground/neutral bar" on the other side of the panel. *You can add a ground bar and I don't think he needs to drill any holes, as Siemens has one for the panel, so it should already have compatible holes. But I think that's only code compliant as an additional ground bar, meaning you can't use it for neutrals..... *Is that correct? *If he moves some ground wires from the existing neutral/ground bus to the new bar though he would free up locations for more neutral wires. Also, can't you put more than one ground wire under a screw in at least some panels? * That alone might solve the problem? I believe you can double up ground wires but neutral wires must be one per screw. Why put 2 under one screw if you dont have to? The panel will look far better if its neat and organized thats one wire per screw and definetely tie the 2 bars together...- Hide quoted text - - Show quoted text - Well I guess if you have more ground wires than you have ground terminals, then you "have to". It's either that or go to all the added trouble of adding another ground bus. And I don't see it having anything to do with neatness and organization. You can put two wires into one terminal neatly. Or you could put two wires into two terminals and make it a mess. If two are allowed, I would do it. |
#16
Posted to alt.home.repair
|
|||
|
|||
Adding neutral/ground bar to Siemens S2020B1100 panel
I have a Siemens 100-amp main panel (Catalog #: S2020B1100), and
it only has one neutral/ground bar. The neutral/ground bar is on the right side of the panel. I am trying to figure out if I can add another neutral/ground bar on the left side and, if so, how to do that. The information about Siemens service panels is located at: http://www.hqs.sbt.siemens.com/gip/g...ets/US/SIILV/S.... This panel is a Siemens "ES" Series Load Center, and it has 20 circuits. On page 3 of the above online guide it says, "Single sided neutral on 24 circuits and below". So that explains why the panel that I have only has one neutral bar installed. My question again is, can I add another neutral/ground bar on the left side and, if so, how do I do that? Thanks. *Drill and tap two 8/32 holes. Mount the ground bar. Run a number 8 or 6 wire from the new ground bar to the existing ground/neutral bar.- Hide quoted text - - Show quoted text - But what he originally asked for was adding a second "ground/neutral bar" on the other side of the panel. You can add a ground bar and I don't think he needs to drill any holes, as Siemens has one for the panel, so it should already have compatible holes. But I think that's only code compliant as an additional ground bar, meaning you can't use it for neutrals..... Is that correct? If he moves some ground wires from the existing neutral/ground bus to the new bar though he would free up locations for more neutral wires. Also, can't you put more than one ground wire under a screw in at least some panels? That alone might solve the problem? If the bar is threaded into the panel, it would suffice as a ground bar only. If as John said, you run a #6 or 8 from it to the neutral bar, it'll work for both. You can put two grounds under one screw is some panels as well- Hide quoted text - - Show quoted text - But something about that doesn't seem quite right. If you just run a #6 or #8 wire between the new bar and the old bar, then you're relying on that wire to potentially carry the max current rating (100 amps) of the panel when in service, on a regular basis, as opposed to just a ground fault condition, no? Which could occur. I would think the conductor between the two would have to be rated for at least the max current of the panel, (100 amps). Isn't there a similar issue also with using an add on "ground" bar as both a ground bar and neutral? The bar in the Siemens catalog is listed for use with that panel as a ground bar, but does that mean that it has the same current rating, etc that a neutral bar would have? I realize in practice it may actually be the same bar, but who knows? well you could run 2 heavy copper lines between the bars....... how heavy is the neutral line to the existing bar?- Hide quoted text - - Show quoted text - I think there are two seperate issues/questions here. One is what minimum things need to be in place from an electrical circuit theory perspective. And unless I'm missing something, that says the conductor between the bars better be at least the capacity of the panel, ie 100 amps. *The neutral in the main panel is permitted to be smaller than the two hot wires because it only carries the unbalanced load. The other is what is technically allowed by code, how the panel and bar are UL listed, tested, etc. For example, it's been debated here whether you can add a simple mechanical slide lock-out for a generator to an existing panel when that slide isn't made by that panel manufacturer, hasn't been UL listed for use with that panel, etc. That slide just sits on top of the panel, doesn't even have direct electrical involvement. It just prevents two breakers from being "on" at the same time. *I've never had a problem passing inspection with an interlock kit made by a third party. I provide a copy of the installation instructions when I submit the permit application so the inspector knows ahead of time what is being used and how it is to be installed. So, thinking along those lines, we have a bar rated and listed for use with the panel as a ground bar. The installation instructions only say how to install it as a ground bar. Is it code compliant to use that for neutrals too? What's the current rating of that bar? What would an inspector say? I would think you, being very concerned that anything potentially not being done fully compliant will come back to bite you in a lawsuit from a future owner, a denied insurance claim, etc would agree that there are issues other than what will work electrically. If he installs it, uses it only for grounds, moves some of the existing grounds from the current "neutral/ground bar" over to it, he can get more neutral connections and I think we all agree it's 100% code compliant. Using that added ground bar as a neutral bar, I'm not convinced. *A phone call to the electrical inspector should resolve that concern. |
#17
Posted to alt.home.repair
|
|||
|
|||
Adding neutral/ground bar to Siemens S2020B1100 panel
I would think you, being very concerned that anything potentially not being done fully compliant will come back to bite you in a lawsuit from a future owner, a denied insurance claim, etc you bring up a interesting point. you sell your home and later something bad happens due to your poor DIY fix. Could the new owner sue you? or their insurance company? Is there a statute of limitations on how long you could be on the hook? |
#18
Posted to alt.home.repair
|
|||
|
|||
Adding neutral/ground bar to Siemens S2020B1100 panel
On Sat, 27 Apr 2013 10:33:47 -0700 (PDT), bob haller
wrote: I would think you, being very concerned that anything potentially not being done fully compliant will come back to bite you in a lawsuit from a future owner, a denied insurance claim, etc you bring up a interesting point. you sell your home and later something bad happens due to your poor DIY fix. Could the new owner sue you? or their insurance company? Is there a statute of limitations on how long you could be on the hook? MORE haller's insurance insanity. Good grief! |
#19
Posted to alt.home.repair
|
|||
|
|||
Adding neutral/ground bar to Siemens S2020B1100 panel
On Apr 27, 6:00*pm, wrote:
On Sat, 27 Apr 2013 10:33:47 -0700 (PDT), bob haller wrote: I would think you, being very concerned that anything potentially not being done fully compliant will come back to bite you in a lawsuit from a future owner, a denied insurance claim, etc you bring up a interesting point. you sell your home and later something bad happens due to your poor DIY fix. Could the new owner sue you? or their insurance company? Is there a statute of limitations on how long you could be on the hook? MORE haller's insurance insanity. *Good grief! it is a legit question....... i see you dont have a real answer... |
#20
Posted to alt.home.repair
|
|||
|
|||
Adding neutral/ground bar to Siemens S2020B1100 panel
On Sat, 27 Apr 2013 16:24:16 -0700 (PDT), bob haller
wrote: On Apr 27, 6:00*pm, wrote: On Sat, 27 Apr 2013 10:33:47 -0700 (PDT), bob haller wrote: I would think you, being very concerned that anything potentially not being done fully compliant will come back to bite you in a lawsuit from a future owner, a denied insurance claim, etc you bring up a interesting point. you sell your home and later something bad happens due to your poor DIY fix. Could the new owner sue you? or their insurance company? Is there a statute of limitations on how long you could be on the hook? MORE haller's insurance insanity. *Good grief! it is a legit question....... i see you dont have a real answer... Your life is run by your phobia of insurance companies, that's obvious. You really are a sad sack. |
#21
Posted to alt.home.repair
|
|||
|
|||
Adding neutral/ground bar to Siemens S2020B1100 panel
On Apr 27, 7:34*pm, wrote:
On Sat, 27 Apr 2013 16:24:16 -0700 (PDT), bob haller wrote: On Apr 27, 6:00*pm, wrote: On Sat, 27 Apr 2013 10:33:47 -0700 (PDT), bob haller wrote: I would think you, being very concerned that anything potentially not being done fully compliant will come back to bite you in a lawsuit from a future owner, a denied insurance claim, etc you bring up a interesting point. you sell your home and later something bad happens due to your poor DIY fix. Could the new owner sue you? or their insurance company? Is there a statute of limitations on how long you could be on the hook? MORE haller's insurance insanity. *Good grief! it is a legit question....... i see you dont have a real answer... Your life is run by your phobia of insurance companies, that's obvious. *You really are a sad sack. i have no phobia over insurance companies a buddy of mine from the 70s is a state farm agent, so i have a inside surce on some stuff....... I do wonder how long a new owner can come over a old owner if something bad happens? say the old owner installed the wrong type of gas line where it cant be seen, behind drywall.say clear plastic hose. 4 years later the home explodes when the plastic gas line finally leaks..... I havent done anything to cause a problem but have seen lots of stupid DIY repairs...... |
#22
Posted to alt.home.repair
|
|||
|
|||
Adding neutral/ground bar to Siemens S2020B1100 panel
On Apr 25, 2:36*pm, bob haller wrote:
On Apr 25, 4:21*pm, "John Grabowski" wrote: I have a Siemens 100-amp main panel (Catalog #: S2020B1100), and it only has one neutral/ground bar. *The neutral/ground bar is on the right side of the panel. I am trying to figure out if I can add another neutral/ground bar on the left side and, if so, how to do that. The information about Siemens service panels is located at: http://www.hqs.sbt.siemens.com/gip/g...ets/US/SIILV/S..... This panel is a Siemens "ES" Series Load Center, and it has 20 circuits. On page 3 of the above online guide it says, "Single sided neutral on 24 circuits and below". *So that explains why the panel that I have only has one neutral bar installed. My question again is, can I add another neutral/ground bar on the left side and, if so, how do I do that? *Thanks. *Drill and tap two 8/32 holes. *Mount the ground bar. *Run a number 8 or 6 wire from the new ground bar to the existing ground/neutral bar. if the cabinet is too thin to tap but mounted on plywood like it should be, just drill holes and use wood screws to mount the ground bar to the cabinet, then heavy copper between the old and new ground bars... use wood screws to mount the ground bar to the cabinet, then heavy copper between the old and new ground bars... this hardly seems acceptable...wood screws? |
#23
Posted to alt.home.repair
|
|||
|
|||
Adding neutral/ground bar to Siemens S2020B1100 panel
On Apr 26, 9:42*am, "
wrote: On Apr 25, 10:08*pm, bob haller wrote: On Apr 25, 9:07*pm, DD_BobK wrote: On Apr 25, 4:13*pm, " wrote: On Apr 25, 4:21*pm, "John Grabowski" wrote: I have a Siemens 100-amp main panel (Catalog #: S2020B1100), and it only has one neutral/ground bar. *The neutral/ground bar is on the right side of the panel. I am trying to figure out if I can add another neutral/ground bar on the left side and, if so, how to do that. The information about Siemens service panels is located at: http://www.hqs.sbt.siemens.com/gip/g...ets/US/SIILV/S.... This panel is a Siemens "ES" Series Load Center, and it has 20 circuits. On page 3 of the above online guide it says, "Single sided neutral on 24 circuits and below". *So that explains why the panel that I have only has one neutral bar installed. My question again is, can I add another neutral/ground bar on the left side and, if so, how do I do that? *Thanks. *Drill and tap two 8/32 holes. *Mount the ground bar. *Run a number 8 or 6 wire from the new ground bar to the existing ground/neutral bar.- Hide quoted text - - Show quoted text - But what he originally asked for was adding a second "ground/neutral bar" on the other side of the panel. *You can add a ground bar and I don't think he needs to drill any holes, as Siemens has one for the panel, so it should already have compatible holes. But I think that's only code compliant as an additional ground bar, meaning you can't use it for neutrals..... *Is that correct? *If he moves some ground wires from the existing neutral/ground bus to the new bar though he would free up locations for more neutral wires. Also, can't you put more than one ground wire under a screw in at least some panels? * That alone might solve the problem? I believe you can double up ground wires but neutral wires must be one per screw. Why put 2 under one screw if you dont have to? The panel will look far better if its neat and organized thats one wire per screw and definetely tie the 2 bars together...- Hide quoted text - - Show quoted text - Well I guess if you have more ground wires than you have ground terminals, then you "have to". *It's either that or go to all the added trouble of adding another ground bus. *And I don't see it having anything to do with neatness and organization. *You can put two wires into one terminal neatly. Or you could put two wires into two terminals and make it a mess. *If two are allowed, I would do it. +1 |
#24
Posted to alt.home.repair
|
|||
|
|||
Adding neutral/ground bar to Siemens S2020B1100 panel
wrote in message
... On Apr 25, 7:44 pm, RBM wrote: On 4/25/2013 7:13 PM, wrote: On Apr 25, 4:21 pm, "John Grabowski" wrote: I have a Siemens 100-amp main panel (Catalog #: S2020B1100), and it only has one neutral/ground bar. The neutral/ground bar is on the right side of the panel. I am trying to figure out if I can add another neutral/ground bar on the left side and, if so, how to do that. The information about Siemens service panels is located at: http://www.hqs.sbt.siemens.com/gip/g...ets/US/SIILV/S.... This panel is a Siemens "ES" Series Load Center, and it has 20 circuits. On page 3 of the above online guide it says, "Single sided neutral on 24 circuits and below". So that explains why the panel that I have only has one neutral bar installed. My question again is, can I add another neutral/ground bar on the left side and, if so, how do I do that? Thanks. But what he originally asked for was adding a second "ground/neutral bar" on the other side of the panel. You can add a ground bar and I don't think he needs to drill any holes, as Siemens has one for the panel, so it should already have compatible holes. But I think that's only code compliant as an additional ground bar, meaning you can't use it for neutrals..... Is that correct? If he moves some ground wires from the existing neutral/ground bus to the new bar though he would free up locations for more neutral wires. Also, can't you put more than one ground wire under a screw in at least some panels? That alone might solve the problem? If the bar is threaded into the panel, it would suffice as a ground bar only. If as John said, you run a #6 or 8 from it to the neutral bar, it'll work for both. You can put two grounds under one screw is some panels as well- Hide quoted text - But something about that doesn't seem quite right. If you just run a #6 or #8 wire between the new bar and the old bar, then you're relying on that wire to potentially carry the max current rating (100 amps) of the panel when in service, on a regular basis, as opposed to just a ground fault condition, no? Which could occur. I would think the conductor between the two would have to be rated for at least the max current of the panel, (100 amps). Isn't there a similar issue also with using an add on "ground" bar as both a ground bar and neutral? The bar in the Siemens catalog is listed for use with that panel as a ground bar, but does that mean that it has the same current rating, etc that a neutral bar would have? I realize in practice it may actually be the same bar, but who knows? I think that is an interesting question, and I would like to be able to figure out the correct answer to that one. Unfortunately, the Siemens panel that I have only has a neutral bar on one side since it has less than 30 circuits (30 and above have two neutral bars -- one on each side). I called Siemens technical support on Friday afternoon shortly before 5 PM. I explained that I want to be able to add a second neutral bar to my 20-circuit Siemens panel and asked if there is a way to do that. I also explained the option/idea above of adding a ground bar and connecting that to the neutral bar with an #6 or #8 wire. The call-taker entered my question into their system and created an email "ticket number", and then said that a technical representative will get back to me on Monday. I'll pass on whatever I hear back from them. |
#25
Posted to alt.home.repair
|
|||
|
|||
Adding neutral/ground bar to Siemens S2020B1100 panel
On Sat, 27 Apr 2013 20:00:52 -0700 (PDT), bob haller
wrote: On Apr 27, 7:34*pm, wrote: On Sat, 27 Apr 2013 16:24:16 -0700 (PDT), bob haller wrote: On Apr 27, 6:00*pm, wrote: On Sat, 27 Apr 2013 10:33:47 -0700 (PDT), bob haller wrote: I would think you, being very concerned that anything potentially not being done fully compliant will come back to bite you in a lawsuit from a future owner, a denied insurance claim, etc you bring up a interesting point. you sell your home and later something bad happens due to your poor DIY fix. Could the new owner sue you? or their insurance company? Is there a statute of limitations on how long you could be on the hook? MORE haller's insurance insanity. *Good grief! it is a legit question....... i see you dont have a real answer... Your life is run by your phobia of insurance companies, that's obvious. *You really are a sad sack. i have no phobia over insurance companies a buddy of mine from the 70s is a state farm agent, so i have a inside surce on some stuff....... Bull****. You're constantly worrying about insurance and telling others they can't sneeze without having their insurance canceled, or worse. I do wonder how long a new owner can come over a old owner if something bad happens? Idiot. say the old owner installed the wrong type of gas line where it cant be seen, behind drywall.say clear plastic hose. Yeah, that's what everyone has been talking about. What a moron. 4 years later the home explodes when the plastic gas line finally leaks..... I havent done anything to cause a problem but have seen lots of stupid DIY repairs...... I'm sure you haven't done jack, or you'd be cowering in the corner waiting to be sued. |
#26
Posted to alt.home.repair
|
|||
|
|||
Adding neutral/ground bar to Siemens S2020B1100 panel
On Apr 27, 11:48*pm, wrote:
On Sat, 27 Apr 2013 20:00:52 -0700 (PDT), bob haller wrote: On Apr 27, 7:34*pm, wrote: On Sat, 27 Apr 2013 16:24:16 -0700 (PDT), bob haller wrote: On Apr 27, 6:00*pm, wrote: On Sat, 27 Apr 2013 10:33:47 -0700 (PDT), bob haller wrote: I would think you, being very concerned that anything potentially not being done fully compliant will come back to bite you in a lawsuit from a future owner, a denied insurance claim, etc you bring up a interesting point. you sell your home and later something bad happens due to your poor DIY fix. Could the new owner sue you? or their insurance company? Is there a statute of limitations on how long you could be on the hook? MORE haller's insurance insanity. *Good grief! it is a legit question....... i see you dont have a real answer... Your life is run by your phobia of insurance companies, that's obvious. *You really are a sad sack. i have no phobia over insurance companies a buddy of mine from the 70s is a state farm agent, so i have a inside surce on some stuff....... Bull****. *You're constantly worrying about insurance and telling others they can't sneeze without having their insurance canceled, or worse. I do wonder how long a new owner can come over a old owner if something bad happens? Idiot. say the old owner installed the wrong type of gas line where it cant be seen, behind drywall.say clear plastic hose. Yeah, that's what everyone has been talking about. *What a moron. 4 years later the home explodes when the plastic gas line finally leaks..... I havent done anything to cause a problem but have seen lots of stupid DIY repairs...... I'm sure you haven't done jack, or you'd be cowering in the corner waiting to be sued. my insurance issues......... Its near impossible to get homeowners insurance on a home with knob and tube....... now you can deny that all you want but it doesnt change reality homeowners insurance these days often send out a inspector before writing a new policy...... they look for trash under a porch, lack of railings, bad roofs, fuse boxes, unsafe sidewalks...... all of these and more will have to be corrected before getting insurance.... I agree with these rules, since everyone wants low preminms, and all of those can and do boost losses. it might be possible to get a policy with known hazards, but it might boost premiums significantly..... incidently a customer of mine had sidewalks that were uneven. the slabs were at different levels the customer was a public school. A student got ill and grandpa was called to take the kid home. grandpa tripped on the uneven sidewalk and broke his hip. within 2 months he died, cause, the fall. the school had to pay all the medical bills, pain and suffering, etc etc. last i heard the settlement offer to grandpas family was half a million dollars.... paid by the schools liability carrier. the district replaced all the sidewalks at all the buildings and repaved parking lots etc. the insurance company required a risk inspection and repair of all possible hazards to keep their coverage. now what really caused the accident? the school board insisted on a budget cut on building maintence to save money.... the board members who voted for that cut were all gone, replaced or voted out. sadly and for practical $ reasons there are individuals doing that today. save money by no maintence... thats why insurance now inspects homes. with the stormy weather probably from global warming entire citys are being destroyed. insurance cant prevent that but can save money on preventable losses |
#27
Posted to alt.home.repair
|
|||
|
|||
Adding neutral/ground bar to Siemens S2020B1100 panel
On Apr 27, 7:55*am, "John Grabowski" wrote:
I have a Siemens 100-amp main panel (Catalog #: S2020B1100), and it only has one neutral/ground bar. The neutral/ground bar is on the right side of the panel. I am trying to figure out if I can add another neutral/ground bar on the left side and, if so, how to do that. The information about Siemens service panels is located at: http://www.hqs.sbt.siemens.com/gip/g...ets/US/SIILV/S.... This panel is a Siemens "ES" Series Load Center, and it has 20 circuits. On page 3 of the above online guide it says, "Single sided neutral on 24 circuits and below". So that explains why the panel that I have only has one neutral bar installed. My question again is, can I add another neutral/ground bar on the left side and, if so, how do I do that? Thanks. *Drill and tap two 8/32 holes. Mount the ground bar. Run a number 8 or 6 wire from the new ground bar to the existing ground/neutral bar.- Hide quoted text - - Show quoted text - But what he originally asked for was adding a second "ground/neutral bar" on the other side of the panel. You can add a ground bar and I don't think he needs to drill any holes, as Siemens has one for the panel, so it should already have compatible holes.. But I think that's only code compliant as an additional ground bar, meaning you can't use it for neutrals..... Is that correct? If he moves some ground wires from the existing neutral/ground bus to the new bar though he would free up locations for more neutral wires. Also, can't you put more than one ground wire under a screw in at least some panels? That alone might solve the problem? If the bar is threaded into the panel, it would suffice as a ground bar only. If as John said, you run a #6 or 8 from it to the neutral bar, it'll work for both. You can put two grounds under one screw is some panels as well- Hide quoted text - - Show quoted text - But something about that doesn't seem quite right. If you just run a #6 or #8 wire between the new bar and the old bar, then you're relying on that wire to potentially carry the max current rating (100 amps) of the panel when in service, on a regular basis, as opposed to just a ground fault condition, no? Which could occur. I would think the conductor between the two would have to be rated for at least the max current of the panel, (100 amps). Isn't there a similar issue also with using an add on "ground" bar as both a ground bar and neutral? The bar in the Siemens catalog is listed for use with that panel as a ground bar, but does that mean that it has the same current rating, etc that a neutral bar would have? I realize in practice it may actually be the same bar, but who knows? well you could run 2 heavy copper lines between the bars....... how heavy is the neutral line to the existing bar?- Hide quoted text - - Show quoted text - I think there are two seperate issues/questions here. *One is what minimum things need to be in place from an electrical circuit theory perspective. *And unless I'm missing something, that says the conductor between the bars better be at least the capacity of the panel, ie 100 amps. *The neutral in the main panel is permitted to be smaller than the two hot wires because it only carries the unbalanced load. But what happens if the unbalanced load happens to be larger than the conductor? Theoretically, the unbalanced load could be 100 amps. I agree that is very unlikely, but statistically, it's possible. Let's say you had some house where 8 resistance heaters are used. They could just happen to put them into outlets that are on the same leg..... 12A * 8 = 96A. Here's another point. An add-on ground bar is designed to be attached via screws to the panel metal. If you use one of those as intended, for a ground bus, then under normal conditions, no current is ever flowing in the panel metal, right? You'd only have current flow throw the panel itself if there was a ground fault of some kind. That's how it works with any metal box, right? But if you use that add-on ground bar as a neutral bar, then you do have at least part of the unbalanced current flowing through the panel metal all the time. Even with a wire connected between that neutral bar and the other neutral bar, the current will split with some of it going via the wire, some of it going via the panel metal. That doesn't seem right to me. I would think the right way to do it would be for that additional neutral bar to be installed insulated from the panel so that all the current has to flow via the wires and not through the panel metal. Not saying this is really unsafe if it's done the way you guys are saying. Just that it seems odd to me that the code is OK with using the panel metal case as a current carrying conductor. I can't think of another instance where that is allowed. |
#28
Posted to alt.home.repair
|
|||
|
|||
Adding neutral/ground bar to Siemens S2020B1100 panel
On Apr 27, 7:24*pm, bob haller wrote:
On Apr 27, 6:00*pm, wrote: On Sat, 27 Apr 2013 10:33:47 -0700 (PDT), bob haller wrote: I would think you, being very concerned that anything potentially not being done fully compliant will come back to bite you in a lawsuit from a future owner, a denied insurance claim, etc you bring up a interesting point. you sell your home and later something bad happens due to your poor DIY fix. Could the new owner sue you? Of course they could. Anyone can sue anyone for just about anything. Whether they have a real case, can they prove it, will they win, how much is it going to cost them in legal fees to find out, that's an entirely different matter. If you want to sue because the kitchen tile floor is uneven and it was clearly uneven when you bought the place, walked through it, had the opportunity to inspect it, etc, then I don't see how in any rational court of law you'd win. Of course if you were selling the place, you wouldn't have that problem because you'd tell the buyer that the floor doesn't look quite right to you, they'd say "Gee, you're right, we want $4K off for a new one." And you'd both be happy. If you find out the foundation for a room that was added on DIY is sinking because it was built on marshmallows instead of footers, that it was done by the seller, no building permit, they didn't disclose it, etc, then you probably have a decent case. or their insurance company? Sue their insurance company for a defect on a house they bought? Per the above, sure they could. But on what basis could they ever win? What did their insurance company have to do with some house defect that they later find? Is there a statute of limitations on how long you could be on the hook? I believe the last time you brought up the issue of buyers coming back to sue a seller for anything and everything that wasn't disclosed, I provided a link to the PA real estate disclosure law. Did you read it? As I recall, it said that buyers have 2 years to bring a suit. It also said that just because some housing component, say a roof or septic system is at, near or beyond it's normal expected life, that doesn't mean it's a material defect that has to be disclosed, provided that component is still functioning OK. |
#29
Posted to alt.home.repair
|
|||
|
|||
Adding neutral/ground bar to Siemens S2020B1100 panel
On Sun, 28 Apr 2013 05:29:44 -0700 (PDT), bob haller
wrote: On Apr 27, 11:48*pm, wrote: On Sat, 27 Apr 2013 20:00:52 -0700 (PDT), bob haller wrote: On Apr 27, 7:34*pm, wrote: On Sat, 27 Apr 2013 16:24:16 -0700 (PDT), bob haller wrote: On Apr 27, 6:00*pm, wrote: On Sat, 27 Apr 2013 10:33:47 -0700 (PDT), bob haller wrote: I would think you, being very concerned that anything potentially not being done fully compliant will come back to bite you in a lawsuit from a future owner, a denied insurance claim, etc you bring up a interesting point. you sell your home and later something bad happens due to your poor DIY fix. Could the new owner sue you? or their insurance company? Is there a statute of limitations on how long you could be on the hook? MORE haller's insurance insanity. *Good grief! it is a legit question....... i see you dont have a real answer... Your life is run by your phobia of insurance companies, that's obvious. *You really are a sad sack. i have no phobia over insurance companies a buddy of mine from the 70s is a state farm agent, so i have a inside surce on some stuff....... Bull****. *You're constantly worrying about insurance and telling others they can't sneeze without having their insurance canceled, or worse. I do wonder how long a new owner can come over a old owner if something bad happens? Idiot. say the old owner installed the wrong type of gas line where it cant be seen, behind drywall.say clear plastic hose. Yeah, that's what everyone has been talking about. *What a moron. 4 years later the home explodes when the plastic gas line finally leaks..... I havent done anything to cause a problem but have seen lots of stupid DIY repairs...... I'm sure you haven't done jack, or you'd be cowering in the corner waiting to be sued. my insurance issues......... Are all in your tiny little head. |
#30
Posted to alt.home.repair
|
|||
|
|||
Adding neutral/ground bar to Siemens S2020B1100 panel
On 4/26/2013 7:33 AM, wrote:
On Apr 25, 7:44 pm, RBM wrote: On 4/25/2013 7:13 PM, wrote: On Apr 25, 4:21 pm, "John Grabowski" wrote: I have a Siemens 100-amp main panel (Catalog #: S2020B1100), and it only has one neutral/ground bar. The neutral/ground bar is on the right side of the panel. I am trying to figure out if I can add another neutral/ground bar on the left side and, if so, how to do that. The information about Siemens service panels is located at: http://www.hqs.sbt.siemens.com/gip/g...ets/US/SIILV/S.... This panel is a Siemens "ES" Series Load Center, and it has 20 circuits. On page 3 of the above online guide it says, "Single sided neutral on 24 circuits and below". So that explains why the panel that I have only has one neutral bar installed. My question again is, can I add another neutral/ground bar on the left side and, if so, how do I do that? Thanks. *Drill and tap two 8/32 holes. Mount the ground bar. Run a number 8 or 6 wire from the new ground bar to the existing ground/neutral bar.- Hide quoted text - - Show quoted text - But what he originally asked for was adding a second "ground/neutral bar" on the other side of the panel. You can add a ground bar and I don't think he needs to drill any holes, as Siemens has one for the panel, so it should already have compatible holes. But I think that's only code compliant as an additional ground bar, meaning you can't use it for neutrals..... Is that correct? If he moves some ground wires from the existing neutral/ground bus to the new bar though he would free up locations for more neutral wires. Also, can't you put more than one ground wire under a screw in at least some panels? That alone might solve the problem? If the bar is threaded into the panel, it would suffice as a ground bar only. If as John said, you run a #6 or 8 from it to the neutral bar, it'll work for both. You can put two grounds under one screw is some panels as well- Hide quoted text - - Show quoted text - But something about that doesn't seem quite right. If you just run a #6 or #8 wire between the new bar and the old bar, then you're relying on that wire to potentially carry the max current rating (100 amps) of the panel when in service, on a regular basis, as opposed to just a ground fault condition, no? Which could occur. I would think the conductor between the two would have to be rated for at least the max current of the panel, (100 amps). Isn't there a similar issue also with using an add on "ground" bar as both a ground bar and neutral? The bar in the Siemens catalog is listed for use with that panel as a ground bar, but does that mean that it has the same current rating, etc that a neutral bar would have? I realize in practice it may actually be the same bar, but who knows? You are correct. A # 6 copper is all that is required to carry the full neutral load of a 100 amp service, so considering that this is a supplemental neutral bar, it's never going to carry close to the full amount. To be used as a secondary neutral bar as opposed to a ground bar, it must be connected to the original bar by something more substantial that the steel of the cabinet |
#31
Posted to alt.home.repair
|
|||
|
|||
Adding neutral/ground bar to Siemens S2020B1100 panel
On 4/28/2013 8:29 AM, bob haller wrote:
On Apr 27, 11:48 pm, wrote: On Sat, 27 Apr 2013 20:00:52 -0700 (PDT), bob haller wrote: On Apr 27, 7:34 pm, wrote: On Sat, 27 Apr 2013 16:24:16 -0700 (PDT), bob haller wrote: On Apr 27, 6:00 pm, wrote: On Sat, 27 Apr 2013 10:33:47 -0700 (PDT), bob haller wrote: I would think you, being very concerned that anything potentially not being done fully compliant will come back to bite you in a lawsuit from a future owner, a denied insurance claim, etc you bring up a interesting point. you sell your home and later something bad happens due to your poor DIY fix. Could the new owner sue you? or their insurance company? Is there a statute of limitations on how long you could be on the hook? MORE haller's insurance insanity. Good grief! it is a legit question....... i see you dont have a real answer... Your life is run by your phobia of insurance companies, that's obvious. You really are a sad sack. i have no phobia over insurance companies a buddy of mine from the 70s is a state farm agent, so i have a inside surce on some stuff....... Bull****. You're constantly worrying about insurance and telling others they can't sneeze without having their insurance canceled, or worse. I do wonder how long a new owner can come over a old owner if something bad happens? Idiot. say the old owner installed the wrong type of gas line where it cant be seen, behind drywall.say clear plastic hose. Yeah, that's what everyone has been talking about. What a moron. 4 years later the home explodes when the plastic gas line finally leaks..... I havent done anything to cause a problem but have seen lots of stupid DIY repairs...... I'm sure you haven't done jack, or you'd be cowering in the corner waiting to be sued. my insurance issues......... Its near impossible to get homeowners insurance on a home with knob and tube....... now you can deny that all you want but it doesnt change reality homeowners insurance these days often send out a inspector before writing a new policy...... they look for trash under a porch, lack of railings, bad roofs, fuse boxes, unsafe sidewalks...... all of these and more will have to be corrected before getting insurance.... I agree with these rules, since everyone wants low preminms, and all of those can and do boost losses. it might be possible to get a policy with known hazards, but it might boost premiums significantly..... incidently a customer of mine had sidewalks that were uneven. the slabs were at different levels the customer was a public school. A student got ill and grandpa was called to take the kid home. grandpa tripped on the uneven sidewalk and broke his hip. within 2 months he died, cause, the fall. the school had to pay all the medical bills, pain and suffering, etc etc. last i heard the settlement offer to grandpas family was half a million dollars.... paid by the schools liability carrier. the district replaced all the sidewalks at all the buildings and repaved parking lots etc. the insurance company required a risk inspection and repair of all possible hazards to keep their coverage. now what really caused the accident? the school board insisted on a budget cut on building maintence to save money.... the board members who voted for that cut were all gone, replaced or voted out. sadly and for practical $ reasons there are individuals doing that today. save money by no maintence... thats why insurance now inspects homes. with the stormy weather probably from global warming entire citys are being destroyed. insurance cant prevent that but can save money on preventable losses Either you live in an "alternate universe", or these insurance practices only occur when they go to your house |
#32
Posted to alt.home.repair
|
|||
|
|||
Adding neutral/ground bar to Siemens S2020B1100 panel
On Apr 28, 8:49*am, "
wrote: On Apr 27, 7:55*am, "John Grabowski" wrote: I have a Siemens 100-amp main panel (Catalog #: S2020B1100), and it only has one neutral/ground bar. The neutral/ground bar is on the right side of the panel. I am trying to figure out if I can add another neutral/ground bar on the left side and, if so, how to do that. The information about Siemens service panels is located at: http://www.hqs.sbt.siemens.com/gip/g...ets/US/SIILV/S.... This panel is a Siemens "ES" Series Load Center, and it has 20 circuits. On page 3 of the above online guide it says, "Single sided neutral on 24 circuits and below". So that explains why the panel that I have only has one neutral bar installed. My question again is, can I add another neutral/ground bar on the left side and, if so, how do I do that? Thanks. *Drill and tap two 8/32 holes. Mount the ground bar. Run a number 8 or 6 wire from the new ground bar to the existing ground/neutral bar.- Hide quoted text - - Show quoted text - But what he originally asked for was adding a second "ground/neutral bar" on the other side of the panel. You can add a ground bar and I don't think he needs to drill any holes, as Siemens has one for the panel, so it should already have compatible holes. But I think that's only code compliant as an additional ground bar, meaning you can't use it for neutrals..... Is that correct? If he moves some ground wires from the existing neutral/ground bus to the new bar though he would free up locations for more neutral wires. Also, can't you put more than one ground wire under a screw in at least some panels? That alone might solve the problem? If the bar is threaded into the panel, it would suffice as a ground bar only. If as John said, you run a #6 or 8 from it to the neutral bar, it'll work for both. You can put two grounds under one screw is some panels as well- Hide quoted text - - Show quoted text - But something about that doesn't seem quite right. If you just run a #6 or #8 wire between the new bar and the old bar, then you're relying on that wire to potentially carry the max current rating (100 amps) of the panel when in service, on a regular basis, as opposed to just a ground fault condition, no? Which could occur. I would think the conductor between the two would have to be rated for at least the max current of the panel, (100 amps). Isn't there a similar issue also with using an add on "ground" bar as both a ground bar and neutral? The bar in the Siemens catalog is listed for use with that panel as a ground bar, but does that mean that it has the same current rating, etc that a neutral bar would have? I realize in practice it may actually be the same bar, but who knows? well you could run 2 heavy copper lines between the bars....... how heavy is the neutral line to the existing bar?- Hide quoted text - - Show quoted text - I think there are two seperate issues/questions here. *One is what minimum things need to be in place from an electrical circuit theory perspective. *And unless I'm missing something, that says the conductor between the bars better be at least the capacity of the panel, ie 100 amps. *The neutral in the main panel is permitted to be smaller than the two hot wires because it only carries the unbalanced load. But what happens if the unbalanced load happens to be larger than the conductor? *Theoretically, the unbalanced load could be 100 amps. *I agree that is very unlikely, but statistically, it's possible. * Let's say you had some house where 8 resistance heaters are used. * They could just happen to put them into outlets that are on the same leg..... *12A * 8 = 96A. Here's another point. *An add-on ground bar is designed to be attached via screws to the panel metal. * If you use one of those as intended, for a ground bus, then under normal conditions, no current is ever flowing in the panel metal, right? *You'd only have current flow throw the panel itself if there was a ground fault of some kind. *That's how it works with any metal box, right? But if you use that add-on ground bar as a neutral bar, then you do have at least part of the unbalanced current flowing through the panel metal all the time. *Even with a wire connected between that neutral bar and the other neutral bar, the current will split with some of it going via the wire, some of it going via the panel metal. *That doesn't seem right to me. *I would think the right way to do it would be for that additional neutral bar to be installed insulated from the panel so that all the current has to flow via the wires and not through the panel metal. Not saying this is really unsafe if it's done the way you guys are saying. *Just that it seems odd to me that the code is OK with using the panel metal case as a current carrying conductor. *I can't think of another instance where that is allowed. well the existing bar is designed to carry current, and since its connected and actually bonded to the cabinet the cabinet would carry some current |
#33
Posted to alt.home.repair
|
|||
|
|||
Adding neutral/ground bar to Siemens S2020B1100 panel
On Apr 28, 5:51*pm, bob haller wrote:
On Apr 28, 8:49*am, " wrote: On Apr 27, 7:55*am, "John Grabowski" wrote: I have a Siemens 100-amp main panel (Catalog #: S2020B1100), and it only has one neutral/ground bar. The neutral/ground bar is on the right side of the panel. I am trying to figure out if I can add another neutral/ground bar on the left side and, if so, how to do that. The information about Siemens service panels is located at: http://www.hqs.sbt.siemens.com/gip/g...ets/US/SIILV/S.... This panel is a Siemens "ES" Series Load Center, and it has 20 circuits. On page 3 of the above online guide it says, "Single sided neutral on 24 circuits and below". So that explains why the panel that I have only has one neutral bar installed. My question again is, can I add another neutral/ground bar on the left side and, if so, how do I do that? Thanks. *Drill and tap two 8/32 holes. Mount the ground bar. Run a number 8 or 6 wire from the new ground bar to the existing ground/neutral bar.- Hide quoted text - - Show quoted text - But what he originally asked for was adding a second "ground/neutral bar" on the other side of the panel. You can add a ground bar and I don't think he needs to drill any holes, as Siemens has one for the panel, so it should already have compatible holes. But I think that's only code compliant as an additional ground bar, meaning you can't use it for neutrals..... Is that correct? If he moves some ground wires from the existing neutral/ground bus to the new bar though he would free up locations for more neutral wires. Also, can't you put more than one ground wire under a screw in at least some panels? That alone might solve the problem? If the bar is threaded into the panel, it would suffice as a ground bar only. If as John said, you run a #6 or 8 from it to the neutral bar, it'll work for both. You can put two grounds under one screw is some panels as well- Hide quoted text - - Show quoted text - But something about that doesn't seem quite right. If you just run a #6 or #8 wire between the new bar and the old bar, then you're relying on that wire to potentially carry the max current rating (100 amps) of the panel when in service, on a regular basis, as opposed to just a ground fault condition, no? Which could occur. I would think the conductor between the two would have to be rated for at least the max current of the panel, (100 amps). Isn't there a similar issue also with using an add on "ground" bar as both a ground bar and neutral? The bar in the Siemens catalog is listed for use with that panel as a ground bar, but does that mean that it has the same current rating, etc that a neutral bar would have? I realize in practice it may actually be the same bar, but who knows? well you could run 2 heavy copper lines between the bars....... how heavy is the neutral line to the existing bar?- Hide quoted text - - Show quoted text - I think there are two seperate issues/questions here. *One is what minimum things need to be in place from an electrical circuit theory perspective. *And unless I'm missing something, that says the conductor between the bars better be at least the capacity of the panel, ie 100 amps. *The neutral in the main panel is permitted to be smaller than the two hot wires because it only carries the unbalanced load. But what happens if the unbalanced load happens to be larger than the conductor? *Theoretically, the unbalanced load could be 100 amps. *I agree that is very unlikely, but statistically, it's possible. * Let's say you had some house where 8 resistance heaters are used. * They could just happen to put them into outlets that are on the same leg..... *12A * 8 = 96A. Here's another point. *An add-on ground bar is designed to be attached via screws to the panel metal. * If you use one of those as intended, for a ground bus, then under normal conditions, no current is ever flowing in the panel metal, right? *You'd only have current flow throw the panel itself if there was a ground fault of some kind. *That's how it works with any metal box, right? But if you use that add-on ground bar as a neutral bar, then you do have at least part of the unbalanced current flowing through the panel metal all the time. *Even with a wire connected between that neutral bar and the other neutral bar, the current will split with some of it going via the wire, some of it going via the panel metal. *That doesn't seem right to me. *I would think the right way to do it would be for that additional neutral bar to be installed insulated from the panel so that all the current has to flow via the wires and not through the panel metal. Not saying this is really unsafe if it's done the way you guys are saying. *Just that it seems odd to me that the code is OK with using the panel metal case as a current carrying conductor. *I can't think of another instance where that is allowed. well the existing bar is designed to carry current, and since its connected and actually bonded to the cabinet the cabinet would carry some current- Hide quoted text - - Show quoted text - No it would not, because the panel metal is not in the conductive path of the current. With the existing neutral bar, current flows from the neutral on each circuit into the neutral bar and to the service neutral which is directly connected to the existing neutral bar. There is no alternate route in the panel metal for current to go. Now let's say you add a ground bar on the other side of the panel, connect it back to the existing neutral/ground bar, and use it as a neutral. In that case you have two paths for current from that additional neutral to go to get back to the service neutral. One path is via the wire connecting the two. The other is via the panel metal. That second route didn't exist until you created it. Again, not saying this is the worst thing in the world, or that it's inherently unsafe, or that an inspector is going to fail it. I just think it's a curious situation and wonder about the code aspect of it because you're now using the panel metal as a current carrying conductor. That just doesn't seem right. If you installed that additional neutral bar as an insulated one, then you would not have current flowing in the panel metal, only the wire connecting it to the original neutral. |
#34
Posted to alt.home.repair
|
|||
|
|||
Adding neutral/ground bar to Siemens S2020B1100 panel
On Apr 28, 11:41*am, RBM wrote:
On 4/26/2013 7:33 AM, wrote: On Apr 25, 7:44 pm, RBM wrote: On 4/25/2013 7:13 PM, wrote: On Apr 25, 4:21 pm, "John Grabowski" wrote: I have a Siemens 100-amp main panel (Catalog #: S2020B1100), and it only has one neutral/ground bar. *The neutral/ground bar is on the right side of the panel. I am trying to figure out if I can add another neutral/ground bar on the left side and, if so, how to do that. The information about Siemens service panels is located at: http://www.hqs.sbt.siemens.com/gip/g...ets/US/SIILV/S.... This panel is a Siemens "ES" Series Load Center, and it has 20 circuits. On page 3 of the above online guide it says, "Single sided neutral on 24 circuits and below". *So that explains why the panel that I have only has one neutral bar installed. My question again is, can I add another neutral/ground bar on the left side and, if so, how do I do that? *Thanks. *Drill and tap two 8/32 holes. *Mount the ground bar. *Run a number 8 or 6 wire from the new ground bar to the existing ground/neutral bar.- Hide quoted text - - Show quoted text - But what he originally asked for was adding a second "ground/neutral bar" on the other side of the panel. *You can add a ground bar and I don't think he needs to drill any holes, as Siemens has one for the panel, so it should already have compatible holes. But I think that's only code compliant as an additional ground bar, meaning you can't use it for neutrals..... *Is that correct? *If he moves some ground wires from the existing neutral/ground bus to the new bar though he would free up locations for more neutral wires. Also, can't you put more than one ground wire under a screw in at least some panels? * That alone might solve the problem? If the bar is threaded into the panel, it would suffice as a ground bar only. If as John said, you run a #6 or 8 from it to the neutral bar, it'll work for both. You can put two grounds under one screw is some panels as well- Hide quoted text - - Show quoted text - But something about that doesn't seem quite right. *If you just run a #6 or #8 wire between the new bar and the old bar, then you're relying on that wire to potentially carry the max current rating (100 amps) of the panel when in service, on a regular basis, as opposed to just a ground fault condition, no? Which could occur. *I would think the conductor between the two would have to be rated for at least the max current of the panel, (100 amps). * Isn't there a similar issue also with using an add on "ground" bar as both a ground bar and neutral? * The bar in the Siemens catalog is listed for use with that panel as a ground bar, but does that mean that it has the same current rating, etc that a neutral bar would have? * I realize in practice it may actually be the same bar, but who knows? You are correct. A # 6 copper is all that is required to carry the full neutral load of a 100 amp service, so considering that this is a supplemental neutral bar, it's never going to carry close to the full amount. I still don't get how a #6 can be used to carry the full neutral load of a 100 amp service. Worse case, the full neutral load is 100 amps. You can't use #6 to connect the hots on a 100 amp sub-panel, can you? I agree the "chances" that the neutral is ever going to see the full 100 amps is small, because it's only the unbalanced portion. With 120V randomly assigned to one hot or the other, they are going to tend to cancel out and the neutral current will be small. But it is possible to put the full 100 amps on the neutral if you managed to put a bunch of large 120V loads all on the same hot leg. Like plugging in say 8 resistance heaters into 8 circuits that just happen to be all on the same hot leg. I guess maybe the answer is that even if you put 100 amps through a #6 it's not the end of the world, ie it's not going to fail or get hot enough to start a fire, etc. To be used as a secondary neutral bar as opposed to a ground bar, it must be connected to the original bar by something more substantial that the steel of the cabinet- Hide quoted text - - Show quoted text - |
#35
Posted to alt.home.repair
|
|||
|
|||
Adding neutral/ground bar to Siemens S2020B1100 panel
On Mon, 29 Apr 2013 05:46:36 -0700 (PDT), "
wrote: On Apr 28, 11:41*am, RBM wrote: On 4/26/2013 7:33 AM, wrote: On Apr 25, 7:44 pm, RBM wrote: On 4/25/2013 7:13 PM, wrote: On Apr 25, 4:21 pm, "John Grabowski" wrote: I have a Siemens 100-amp main panel (Catalog #: S2020B1100), and it only has one neutral/ground bar. *The neutral/ground bar is on the right side of the panel. I am trying to figure out if I can add another neutral/ground bar on the left side and, if so, how to do that. The information about Siemens service panels is located at: http://www.hqs.sbt.siemens.com/gip/g...ets/US/SIILV/S.... This panel is a Siemens "ES" Series Load Center, and it has 20 circuits. On page 3 of the above online guide it says, "Single sided neutral on 24 circuits and below". *So that explains why the panel that I have only has one neutral bar installed. My question again is, can I add another neutral/ground bar on the left side and, if so, how do I do that? *Thanks. *Drill and tap two 8/32 holes. *Mount the ground bar. *Run a number 8 or 6 wire from the new ground bar to the existing ground/neutral bar.- Hide quoted text - - Show quoted text - But what he originally asked for was adding a second "ground/neutral bar" on the other side of the panel. *You can add a ground bar and I don't think he needs to drill any holes, as Siemens has one for the panel, so it should already have compatible holes. But I think that's only code compliant as an additional ground bar, meaning you can't use it for neutrals..... *Is that correct? *If he moves some ground wires from the existing neutral/ground bus to the new bar though he would free up locations for more neutral wires. Also, can't you put more than one ground wire under a screw in at least some panels? * That alone might solve the problem? If the bar is threaded into the panel, it would suffice as a ground bar only. If as John said, you run a #6 or 8 from it to the neutral bar, it'll work for both. You can put two grounds under one screw is some panels as well- Hide quoted text - - Show quoted text - But something about that doesn't seem quite right. *If you just run a #6 or #8 wire between the new bar and the old bar, then you're relying on that wire to potentially carry the max current rating (100 amps) of the panel when in service, on a regular basis, as opposed to just a ground fault condition, no? Which could occur. *I would think the conductor between the two would have to be rated for at least the max current of the panel, (100 amps). * Isn't there a similar issue also with using an add on "ground" bar as both a ground bar and neutral? * The bar in the Siemens catalog is listed for use with that panel as a ground bar, but does that mean that it has the same current rating, etc that a neutral bar would have? * I realize in practice it may actually be the same bar, but who knows? You are correct. A # 6 copper is all that is required to carry the full neutral load of a 100 amp service, so considering that this is a supplemental neutral bar, it's never going to carry close to the full amount. I still don't get how a #6 can be used to carry the full neutral load of a 100 amp service. Worse case, the full neutral load is 100 amps. You can't use #6 to connect the hots on a 100 amp sub-panel, can you? There aren't the same insulation temperature issues with bare copper, clamped to the box on both ends (heat sink), inside a large enclosure (instead of threading through insulation). |
#36
Posted to alt.home.repair
|
|||
|
|||
Adding neutral/ground bar to Siemens S2020B1100 panel
On 4/29/2013 8:46 AM, wrote:
On Apr 28, 11:41 am, RBM wrote: On 4/26/2013 7:33 AM, wrote: On Apr 25, 7:44 pm, RBM wrote: On 4/25/2013 7:13 PM, wrote: On Apr 25, 4:21 pm, "John Grabowski" wrote: I have a Siemens 100-amp main panel (Catalog #: S2020B1100), and it only has one neutral/ground bar. The neutral/ground bar is on the right side of the panel. I am trying to figure out if I can add another neutral/ground bar on the left side and, if so, how to do that. The information about Siemens service panels is located at: http://www.hqs.sbt.siemens.com/gip/g...ets/US/SIILV/S.... This panel is a Siemens "ES" Series Load Center, and it has 20 circuits. On page 3 of the above online guide it says, "Single sided neutral on 24 circuits and below". So that explains why the panel that I have only has one neutral bar installed. My question again is, can I add another neutral/ground bar on the left side and, if so, how do I do that? Thanks. *Drill and tap two 8/32 holes. Mount the ground bar. Run a number 8 or 6 wire from the new ground bar to the existing ground/neutral bar.- Hide quoted text - - Show quoted text - But what he originally asked for was adding a second "ground/neutral bar" on the other side of the panel. You can add a ground bar and I don't think he needs to drill any holes, as Siemens has one for the panel, so it should already have compatible holes. But I think that's only code compliant as an additional ground bar, meaning you can't use it for neutrals..... Is that correct? If he moves some ground wires from the existing neutral/ground bus to the new bar though he would free up locations for more neutral wires. Also, can't you put more than one ground wire under a screw in at least some panels? That alone might solve the problem? If the bar is threaded into the panel, it would suffice as a ground bar only. If as John said, you run a #6 or 8 from it to the neutral bar, it'll work for both. You can put two grounds under one screw is some panels as well- Hide quoted text - - Show quoted text - But something about that doesn't seem quite right. If you just run a #6 or #8 wire between the new bar and the old bar, then you're relying on that wire to potentially carry the max current rating (100 amps) of the panel when in service, on a regular basis, as opposed to just a ground fault condition, no? Which could occur. I would think the conductor between the two would have to be rated for at least the max current of the panel, (100 amps). Isn't there a similar issue also with using an add on "ground" bar as both a ground bar and neutral? The bar in the Siemens catalog is listed for use with that panel as a ground bar, but does that mean that it has the same current rating, etc that a neutral bar would have? I realize in practice it may actually be the same bar, but who knows? You are correct. A # 6 copper is all that is required to carry the full neutral load of a 100 amp service, so considering that this is a supplemental neutral bar, it's never going to carry close to the full amount. I still don't get how a #6 can be used to carry the full neutral load of a 100 amp service. Worse case, the full neutral load is 100 amps. You can't use #6 to connect the hots on a 100 amp sub-panel, can you? I agree the "chances" that the neutral is ever going to see the full 100 amps is small, because it's only the unbalanced portion. With 120V randomly assigned to one hot or the other, they are going to tend to cancel out and the neutral current will be small. But it is possible to put the full 100 amps on the neutral if you managed to put a bunch of large 120V loads all on the same hot leg. Like plugging in say 8 resistance heaters into 8 circuits that just happen to be all on the same hot leg. I guess maybe the answer is that even if you put 100 amps through a #6 it's not the end of the world, ie it's not going to fail or get hot enough to start a fire, etc. Residential services are treated differently than feeders, so they allow the smaller size conductors |
#37
Posted to alt.home.repair
|
|||
|
|||
Adding neutral/ground bar to Siemens S2020B1100 panel
TomR wrote:
wrote in message But something about that doesn't seem quite right. If you just run a #6 or #8 wire between the new bar and the old bar, then you're relying on that wire to potentially carry the max current rating (100 amps) of the panel when in service, on a regular basis, as opposed to just a ground fault condition, no? Which could occur. I would think the conductor between the two would have to be rated for at least the max current of the panel, (100 amps). Isn't there a similar issue also with using an add on "ground" bar as both a ground bar and neutral? The bar in the Siemens catalog is listed for use with that panel as a ground bar, but does that mean that it has the same current rating, etc that a neutral bar would have? I realize in practice it may actually be the same bar, but who knows? I think that is an interesting question, and I would like to be able to figure out the correct answer to that one. Unfortunately, the Siemens panel that I have only has a neutral bar on one side since it has less than 30 circuits (30 and above have two neutral bars -- one on each side). I called Siemens technical support on Friday afternoon shortly before 5 PM. I explained that I want to be able to add a second neutral bar to my 20-circuit Siemens panel and asked if there is a way to do that. I also explained the option/idea above of adding a ground bar and connecting that to the neutral bar with an #6 or #8 wire. The call-taker entered my question into their system and created an email "ticket number", and then said that a technical representative will get back to me on Monday. I'll pass on whatever I hear back from them. Just to follow up . . , I still don't have a definite answer from Siemens on this question. Here is what I wrote to Siemens: "My question is in regard to the cat# S2020B1100 Main Breaker Load Center. It comes with only one neutral bar (on the right side). I would like to add a second neutral bar on the left side of the panel. Is there a way for me to do that? It has been suggested to me that I could possibly do this by adding a Siemens ground bar on the left side and then connecting a #6 or #8 jumper wire from the new ground bar to the original neutral bar, thus making them both useable as neutral/ground bars. Is that correct, or is there a better way to add a neutral bar on the left side?" And, this is what they wrote back yesterday: "I am checking to see if there is an offering for this. I will advise." My guess is that they are going to say that there is no option to add a second neutral bar to their cat# S2020B1100 Main Breaker Load Center. But, that I can add a ground bar to the panel. I doubt that they would want to get into giving out advice on how to create or wire a second neutral bar since that model panel does not come with a second neutral bar. Also, I went to Home Depot and I looked at the box etc. for the same model Siemens Main Breaker Load Center, and it specifically says, "Ground bar not included". I think I remember the instructions inside showing how to add a ground bar (I'm not sure). And, Home Depot does sell the ground bar and shows how to install it as a ground bar. |
#38
Posted to alt.home.repair
|
|||
|
|||
Adding neutral/ground bar to Siemens S2020B1100 panel
I added a bar to a existing cabinet once. The added bar and existing
bar both had spots for 12 gauge or smaller wire. Plus each bar had significantly larger spots for heavy conductors. perhaps a electric stove or something like it So added 2 copper heavy tie lines between the old and new bar, figuring that would never cause a problem plus the bar was bonded to the cabinet I had to get middle states to reinspect the cabinet for home sale, the inspector complimented me on my good job........ the existing bar had issues many of the screws were like welded on place, they must of been overtightened at one time and the heads would break off when loosened. i had ven tried heating some. the quick project took all day |
#39
Posted to alt.home.repair
|
|||
|
|||
Adding neutral/ground bar to Siemens S2020B1100 panel
On 4/29/2013 10:02 AM, wrote:
On Mon, 29 Apr 2013 05:46:36 -0700 (PDT), " wrote: On Apr 28, 11:41 am, wrote: On 4/26/2013 7:33 AM, wrote: On Apr 25, 7:44 pm, wrote: On 4/25/2013 7:13 PM, wrote: On Apr 25, 4:21 pm, "John wrote: I have a Siemens 100-amp main panel (Catalog #: S2020B1100), and it only has one neutral/ground bar. The neutral/ground bar is on the right side of the panel. I am trying to figure out if I can add another neutral/ground bar on the left side and, if so, how to do that. The information about Siemens service panels is located at: http://www.hqs.sbt.siemens.com/gip/g...ets/US/SIILV/S.... This panel is a Siemens "ES" Series Load Center, and it has 20 circuits. On page 3 of the above online guide it says, "Single sided neutral on 24 circuits and below". So that explains why the panel that I have only has one neutral bar installed. My question again is, can I add another neutral/ground bar on the left side and, if so, how do I do that? Thanks. *Drill and tap two 8/32 holes. Mount the ground bar. Run a number 8 or 6 wire from the new ground bar to the existing ground/neutral bar.- Hide quoted text - - Show quoted text - But what he originally asked for was adding a second "ground/neutral bar" on the other side of the panel. You can add a ground bar and I don't think he needs to drill any holes, as Siemens has one for the panel, so it should already have compatible holes. But I think that's only code compliant as an additional ground bar, meaning you can't use it for neutrals..... Is that correct? If he moves some ground wires from the existing neutral/ground bus to the new bar though he would free up locations for more neutral wires. Also, can't you put more than one ground wire under a screw in at least some panels? That alone might solve the problem? If the bar is threaded into the panel, it would suffice as a ground bar only. If as John said, you run a #6 or 8 from it to the neutral bar, it'll work for both. You can put two grounds under one screw is some panels as well- Hide quoted text - - Show quoted text - But something about that doesn't seem quite right. If you just run a #6 or #8 wire between the new bar and the old bar, then you're relying on that wire to potentially carry the max current rating (100 amps) of the panel when in service, on a regular basis, as opposed to just a ground fault condition, no? Which could occur. I would think the conductor between the two would have to be rated for at least the max current of the panel, (100 amps). Isn't there a similar issue also with using an add on "ground" bar as both a ground bar and neutral? The bar in the Siemens catalog is listed for use with that panel as a ground bar, but does that mean that it has the same current rating, etc that a neutral bar would have? I realize in practice it may actually be the same bar, but who knows? You are correct. A # 6 copper is all that is required to carry the full neutral load of a 100 amp service, so considering that this is a supplemental neutral bar, it's never going to carry close to the full amount. I still don't get how a #6 can be used to carry the full neutral load of a 100 amp service. Worse case, the full neutral load is 100 amps. You can't use #6 to connect the hots on a 100 amp sub-panel, can you? For residential, you can use #4 if the service is 100A. This is based on "diversity". You are real unlikely to have a bar total load connected to one leg that is a problem with #6, and there is also "diversity". But, as you say, it is possible. A person could be a little careful about what is connected. I would rather use a ground bar as a ground bar unless there is a good reason to have to land neutrals on it. There aren't the same insulation temperature issues with bare copper, clamped to the box on both ends (heat sink), inside a large enclosure (instead of threading through insulation). The wire is connected to the neutral bar and the ground bar. There are limits to the wire amp rating based on the connections to the wire. Unless the connections are rated for a higher temperature, in general for 100A circuits or less the wire can only use the amp rating for 60 degree C insulation. (Breakers may, for example, be marked for 75 degree C wire.) (110.14-C) |
#40
Posted to alt.home.repair
|
|||
|
|||
Adding neutral/ground bar to Siemens S2020B1100 panel
On Apr 30, 10:42*am, bud-- wrote:
On 4/29/2013 10:02 AM, wrote: On Mon, 29 Apr 2013 05:46:36 -0700 (PDT), " *wrote: On Apr 28, 11:41 am, *wrote: On 4/26/2013 7:33 AM, wrote: On Apr 25, 7:44 pm, *wrote: On 4/25/2013 7:13 PM, wrote: On Apr 25, 4:21 pm, "John *wrote: I have a Siemens 100-amp main panel (Catalog #: S2020B1100), and it only has one neutral/ground bar. *The neutral/ground bar is on the right side of the panel. I am trying to figure out if I can add another neutral/ground bar on the left side and, if so, how to do that. The information about Siemens service panels is located at: http://www.hqs.sbt.siemens.com/gip/g...ets/US/SIILV/S.... This panel is a Siemens "ES" Series Load Center, and it has 20 circuits. On page 3 of the above online guide it says, "Single sided neutral on 24 circuits and below". *So that explains why the panel that I have only has one neutral bar installed. My question again is, can I add another neutral/ground bar on the left side and, if so, how do I do that? *Thanks. *Drill and tap two 8/32 holes. *Mount the ground bar. *Run a number 8 or 6 wire from the new ground bar to the existing ground/neutral bar.- Hide quoted text - - Show quoted text - But what he originally asked for was adding a second "ground/neutral bar" on the other side of the panel. *You can add a ground bar and I don't think he needs to drill any holes, as Siemens has one for the panel, so it should already have compatible holes. But I think that's only code compliant as an additional ground bar, meaning you can't use it for neutrals..... *Is that correct? *If he moves some ground wires from the existing neutral/ground bus to the new bar though he would free up locations for more neutral wires. Also, can't you put more than one ground wire under a screw in at least some panels? * That alone might solve the problem? If the bar is threaded into the panel, it would suffice as a ground bar only. If as John said, you run a #6 or 8 from it to the neutral bar, it'll work for both. You can put two grounds under one screw is some panels as well- Hide quoted text - - Show quoted text - But something about that doesn't seem quite right. *If you just run a #6 or #8 wire between the new bar and the old bar, then you're relying on that wire to potentially carry the max current rating (100 amps) of the panel when in service, on a regular basis, as opposed to just a ground fault condition, no? Which could occur. *I would think the conductor between the two would have to be rated for at least the max current of the panel, (100 amps). * *Isn't there a similar issue also with using an add on "ground" bar as both a ground bar and neutral? * The bar in the Siemens catalog is listed for use with that panel as a ground bar, but does that mean that it has the same current rating, etc that a neutral bar would have? * I realize in practice it may actually be the same bar, but who knows? You are correct. A # 6 copper is all that is required to carry the full neutral load of a 100 amp service, so considering that this is a supplemental neutral bar, it's never going to carry close to the full amount. I still don't get how a #6 can be used to carry the full neutral load of a 100 amp service. *Worse case, the full neutral load is 100 amps.. You can't use #6 to connect the hots on a 100 amp sub-panel, can you? For residential, you can use #4 if the service is 100A. *This is based on "diversity". Which I'm sure you'd agree is an interesting concept. By diversity I assume they mean that the statistical probability of someone putting 100A of load all on one leg is low. I think we all agree, it's low, but it's not zero. You are real unlikely to have a bar total load connected to one leg that is a problem with #6, and there is also "diversity". *But, as you say, it is possible. A person could be a little careful about what is connected. Which is cool if it's a fixed installation of some known equipment. But it could be a house where someone could plug in a bunch of resistance heaters and have them by chance wind up on the same leg. I would rather use a ground bar as a ground bar unless there is a good reason to have to land neutrals on it. I agree. That was my first suggestion and everyone agrees it's 100% kosher. Use the new ground bar for grounds, move some existing grounds from the neutral/ground bar over to it, thereby freeing up more neutrals. What are your thoughts about what I pointed out about current flow through the panel itself? If you put a ground bar on the other side of the panel, it's bonded to the panel. Even if you connect it with a heavy wire back to the original neutral, you still will have current dividing, with some of it going through the panel metal. I would think the better option would be to install an insulated neutral bar. |
Reply |
|
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Adding extra ground/neutral buss bar in electrical panel or add sub-panel? | Home Repair | |||
ground wire on siemens panel | Home Repair | |||
4 gauge neutral wire doesn't fit in my neutral bus panel? | Home Repair | |||
Neutral and Ground Wires In Panel Box | Home Repair | |||
Why Is Neutral Separated Ground In Breaker Panel? | Home Repair |