I've got a Honeywell MagicStat thermostat that has 2 jumpers marked as
"A" and "B" that are opened or closed by a screw head that you tighten
(to close the jumper) or turn out (to open the jumper).

There are 2 other jumpers (C and D) - C is to set Celcius or
Farenheight, but I don't know what "D" is for (there is no screw for
that one - so it's open). I can find no reference anywhere what D could
be for.

I'm not quite sure what exact model of MagicStat I have - there is
absolutely no number or name stamped or printed on this thing. Not even
the word "MagicStat". I've seen models like 28, 1000, 2800 and 3200
from web searches. I believe this one was purchased between 1996 and
1999.

This is the most similar picture I could find of the front panel:

http://img.ehowcdn.co.uk/article-pag...10-800x800.jpg

And this is the best picture for the entire unit:

http://www.honeywellcentral.com/medi...A1001-U_lg.jpg

The thermostat is controlling a 20+ year-old GE "Whisper-heat" natural
gas furnace. This is NOT a high-efficiency (or condensing) furnace, but
it does have an electronic control module, combustion damper gate and
electronic ignition.

The furnace is cycling too often to suit me, and so I'd like to know if
the thermostat can be modified to solve that.

The written documentation for the A and B jumpers are as follows:

Warm Air Furnace: Set at the Hot Water setting (A-out, B-in)
Electric furnace: Leave at the Warm Air Furnace setting (A-in, B-in)

(the way the second line reads is confusing)

It also says:

For high efficiency (90% AFUE): A-out, B-in

On the back of the unit these instructions are stamped into the plastic
case:

Warm Air Furnace: A-in, B-in, Fuel Switch F
Hot Water Boiler: A-out, B-in, Fuel Switch F
Electric Furnace: A-in, B-out, Fuel Switch E

On my thermostat, the current settings a

Warm Air Furnace: A-in, B-in, Fuel Switch F

I believe that the only thing the Fuel Switch does is turn on the fan
when heat is called for (in the E setting) otherwise the fan is turned
on by the furnace (in the F setting).

So if anyone knows, I'd like some clarification as to how exactly the A
and B settings work or how they modify the operation of the furnace.

It would be nice if there was a SPAN or hysteresis setting so I could
force a 1 or 2 degree swing so the cycles last longer, but I see no such
setting. I'm wondering if the A and B settings can accomplish this?

And - anyone know what the D jumper does?
  #2   Report Post  
Posted to alt.home.repair,alt.hvac
external usenet poster
 
Posts: 117
Default Honeywell MagicStat thermostat - questions about jumper settingson the back

On Dec 29, 8:52*am, HVAC Guy wrote:
I've got a Honeywell MagicStat thermostat that has 2 jumpers marked as
"A" and "B" that are opened or closed by a screw head that you tighten
(to close the jumper) or turn out (to open the jumper).

There are 2 other jumpers (C and D) - C is to set Celcius or
Farenheight, but I don't know what "D" is for (there is no screw for
that one - so it's open). *I can find no reference anywhere what D could
be for.

I'm not quite sure what exact model of MagicStat I have - there is
absolutely no number or name stamped or printed on this thing. *Not even
the word "MagicStat". *I've seen models like 28, 1000, 2800 and 3200
from web searches. *I believe this one was purchased between 1996 and
1999.

This is the most similar picture I could find of the front panel:

http://img.ehowcdn.co.uk/article-pag...a08/7r/3r/inst...

And this is the best picture for the entire unit:

http://www.honeywellcentral.com/medi...3200A1001-U_lg...

The thermostat is controlling a 20+ year-old GE "Whisper-heat" natural
gas furnace. *This is NOT a high-efficiency (or condensing) furnace, but
it does have an electronic control module, combustion damper gate and
electronic ignition.

The furnace is cycling too often to suit me, and so I'd like to know if
the thermostat can be modified to solve that.

The written documentation for the A and B jumpers are as follows:

* Warm Air Furnace: *Set at the Hot Water setting (A-out, B-in)
* Electric furnace: *Leave at the Warm Air Furnace setting (A-in, B-in)

(the way the second line reads is confusing)

It also says:

* For high efficiency (90% AFUE): *A-out, B-in

On the back of the unit these instructions are stamped into the plastic
case:

* Warm Air Furnace: *A-in, *B-in, *Fuel Switch F
* Hot Water Boiler: *A-out, B-in, *Fuel Switch F
* Electric Furnace: *A-in, *B-out, Fuel Switch E

On my thermostat, the current settings a

* Warm Air Furnace: *A-in, *B-in, *Fuel Switch F

I believe that the only thing the Fuel Switch does is turn on the fan
when heat is called for (in the E setting) otherwise the fan is turned
on by the furnace (in the F setting).

So if anyone knows, I'd like some clarification as to how exactly the A
and B settings work or how they modify the operation of the furnace.

It would be nice if there was a SPAN or hysteresis setting so I could
force a 1 or 2 degree swing so the cycles last longer, but I see no such
setting. *I'm wondering if the A and B settings can accomplish this?

And - anyone know what the D jumper does?


I remember that Thermostat . The A and B screws act as a heat
anticipator does ; the more you back out the A screw with the B
screw turned all the way in....the greater the differential will be
and the greater the room temperature swing will be . It is all done
by trial and error using the screws , so, you have to set the screws
then cycle the system thru a couple times to see what kind of room
temperature drop youre getting before the next heating cycle starts.
Since the furnace has electronic ignition, youll want to set it up as
if it were a high efficiency gas furnace which ordinarily would
correspond to a .8 amp anticipator setting ; thats what you have to
shoot for by trial and error by adjusting the Magic Stat screws.
(They dont call it an 'inexpensive' thermostat for no reason !) .
If , after youve done that and you still get a rapid cycling
response...then you could install a simply spst start relay at the
furnace which would effectively reduce the heat anticipator (amp)
demand of the Magic Stat and possibly bring you within the operating
range of the A / B screws for more consise adjusting . ... the Magic
Stat would operate the added relays coil directly , with the relay
contacts making and breaking R to W at the furnace control board
strip . Good luck. ALso, theres a Honneywell Thermostat Tech 800
number for Contractors ; if you need it i can try and find it for
you.
  #3   Report Post  
Posted to alt.home.repair,alt.hvac
external usenet poster
 
Posts: 111
Default Honeywell MagicStat thermostat - questions about jumper settings on the back


"HVAC Guy" wrote in message ...
I've got a Honeywell MagicStat thermostat that has 2 jumpers marked as
"A" and "B" that are opened or closed by a screw head that you tighten
(to close the jumper) or turn out (to open the jumper).

There are 2 other jumpers (C and D) - C is to set Celcius or
Farenheight, but I don't know what "D" is for (there is no screw for
that one - so it's open). I can find no reference anywhere what D could
be for.

I'm not quite sure what exact model of MagicStat I have - there is
absolutely no number or name stamped or printed on this thing. Not even
the word "MagicStat". I've seen models like 28, 1000, 2800 and 3200
from web searches. I believe this one was purchased between 1996 and
1999.

This is the most similar picture I could find of the front panel:

http://img.ehowcdn.co.uk/article-pag...10-800x800.jpg

And this is the best picture for the entire unit:

http://www.honeywellcentral.com/medi...A1001-U_lg.jpg

The thermostat is controlling a 20+ year-old GE "Whisper-heat" natural
gas furnace. This is NOT a high-efficiency (or condensing) furnace, but
it does have an electronic control module, combustion damper gate and
electronic ignition.

The furnace is cycling too often to suit me, and so I'd like to know if
the thermostat can be modified to solve that.

The written documentation for the A and B jumpers are as follows:

Warm Air Furnace: Set at the Hot Water setting (A-out, B-in)
Electric furnace: Leave at the Warm Air Furnace setting (A-in, B-in)

(the way the second line reads is confusing)

It also says:

For high efficiency (90% AFUE): A-out, B-in

On the back of the unit these instructions are stamped into the plastic
case:

Warm Air Furnace: A-in, B-in, Fuel Switch F
Hot Water Boiler: A-out, B-in, Fuel Switch F
Electric Furnace: A-in, B-out, Fuel Switch E

On my thermostat, the current settings a

Warm Air Furnace: A-in, B-in, Fuel Switch F

I believe that the only thing the Fuel Switch does is turn on the fan
when heat is called for (in the E setting) otherwise the fan is turned
on by the furnace (in the F setting).

So if anyone knows, I'd like some clarification as to how exactly the A
and B settings work or how they modify the operation of the furnace.

It would be nice if there was a SPAN or hysteresis setting so I could
force a 1 or 2 degree swing so the cycles last longer, but I see no such
setting. I'm wondering if the A and B settings can accomplish this?

And - anyone know what the D jumper does?


Sounds like your trying to use the thermostat to mask the primary
problems.... and that would be having a furnace that is a whole lot bigger
than you need, and not enough insulation.
20 years is a normal *high* life span for a gas furnace. It would be time to
look into replacing the furnace before it becomes a problem and craps out
when its really cold.

The contractor that installs the new furnace should do a complete
room-by-room Manual J heat load/loss analysis to correctly size the new
furnace for your home. You might be surprised at the results.


  #4   Report Post  
Posted to alt.home.repair,alt.hvac
cjt cjt is offline
external usenet poster
 
Posts: 60
Default Honeywell MagicStat thermostat - questions about jumper settingson the back

On 12/29/2011 01:16 PM, Steve wrote:
"HVAC wrote in message ...
I've got a Honeywell MagicStat thermostat that has 2 jumpers marked as
"A" and "B" that are opened or closed by a screw head that you tighten
(to close the jumper) or turn out (to open the jumper).

There are 2 other jumpers (C and D) - C is to set Celcius or
Farenheight, but I don't know what "D" is for (there is no screw for
that one - so it's open). I can find no reference anywhere what D could
be for.

I'm not quite sure what exact model of MagicStat I have - there is
absolutely no number or name stamped or printed on this thing. Not even
the word "MagicStat". I've seen models like 28, 1000, 2800 and 3200
from web searches. I believe this one was purchased between 1996 and
1999.

This is the most similar picture I could find of the front panel:

http://img.ehowcdn.co.uk/article-pag...10-800x800.jpg

And this is the best picture for the entire unit:

http://www.honeywellcentral.com/medi...A1001-U_lg.jpg

The thermostat is controlling a 20+ year-old GE "Whisper-heat" natural
gas furnace. This is NOT a high-efficiency (or condensing) furnace, but
it does have an electronic control module, combustion damper gate and
electronic ignition.

The furnace is cycling too often to suit me, and so I'd like to know if
the thermostat can be modified to solve that.

The written documentation for the A and B jumpers are as follows:

Warm Air Furnace: Set at the Hot Water setting (A-out, B-in)
Electric furnace: Leave at the Warm Air Furnace setting (A-in, B-in)

(the way the second line reads is confusing)

It also says:

For high efficiency (90% AFUE): A-out, B-in

On the back of the unit these instructions are stamped into the plastic
case:

Warm Air Furnace: A-in, B-in, Fuel Switch F
Hot Water Boiler: A-out, B-in, Fuel Switch F
Electric Furnace: A-in, B-out, Fuel Switch E

On my thermostat, the current settings a

Warm Air Furnace: A-in, B-in, Fuel Switch F

I believe that the only thing the Fuel Switch does is turn on the fan
when heat is called for (in the E setting) otherwise the fan is turned
on by the furnace (in the F setting).

So if anyone knows, I'd like some clarification as to how exactly the A
and B settings work or how they modify the operation of the furnace.

It would be nice if there was a SPAN or hysteresis setting so I could
force a 1 or 2 degree swing so the cycles last longer, but I see no such
setting. I'm wondering if the A and B settings can accomplish this?

And - anyone know what the D jumper does?


Sounds like your trying to use the thermostat to mask the primary
problems.... and that would be having a furnace that is a whole lot bigger
than you need, and not enough insulation.
20 years is a normal *high* life span for a gas furnace.


I think you're assuming a LOT (like where the O.P. resides).

It would be time to
look into replacing the furnace before it becomes a problem and craps out
when its really cold.

The contractor that installs the new furnace should do a complete
room-by-room Manual J heat load/loss analysis to correctly size the new
furnace for your home. You might be surprised at the results.



  #5   Report Post  
Posted to alt.home.repair,alt.hvac
external usenet poster
 
Posts: 111
Default Honeywell MagicStat thermostat - questions about jumper settings on the back


"cjt" wrote in message
...
On 12/29/2011 01:16 PM, Steve wrote:
"HVAC wrote in message
...
I've got a Honeywell MagicStat thermostat that has 2 jumpers marked as
"A" and "B" that are opened or closed by a screw head that you tighten
(to close the jumper) or turn out (to open the jumper).

There are 2 other jumpers (C and D) - C is to set Celcius or
Farenheight, but I don't know what "D" is for (there is no screw for
that one - so it's open). I can find no reference anywhere what D could
be for.

I'm not quite sure what exact model of MagicStat I have - there is
absolutely no number or name stamped or printed on this thing. Not even
the word "MagicStat". I've seen models like 28, 1000, 2800 and 3200
from web searches. I believe this one was purchased between 1996 and
1999.

This is the most similar picture I could find of the front panel:

http://img.ehowcdn.co.uk/article-pag...10-800x800.jpg

And this is the best picture for the entire unit:

http://www.honeywellcentral.com/medi...A1001-U_lg.jpg

The thermostat is controlling a 20+ year-old GE "Whisper-heat" natural
gas furnace. This is NOT a high-efficiency (or condensing) furnace, but
it does have an electronic control module, combustion damper gate and
electronic ignition.

The furnace is cycling too often to suit me, and so I'd like to know if
the thermostat can be modified to solve that.

The written documentation for the A and B jumpers are as follows:

Warm Air Furnace: Set at the Hot Water setting (A-out, B-in)
Electric furnace: Leave at the Warm Air Furnace setting (A-in, B-in)

(the way the second line reads is confusing)

It also says:

For high efficiency (90% AFUE): A-out, B-in

On the back of the unit these instructions are stamped into the plastic
case:

Warm Air Furnace: A-in, B-in, Fuel Switch F
Hot Water Boiler: A-out, B-in, Fuel Switch F
Electric Furnace: A-in, B-out, Fuel Switch E

On my thermostat, the current settings a

Warm Air Furnace: A-in, B-in, Fuel Switch F

I believe that the only thing the Fuel Switch does is turn on the fan
when heat is called for (in the E setting) otherwise the fan is turned
on by the furnace (in the F setting).

So if anyone knows, I'd like some clarification as to how exactly the A
and B settings work or how they modify the operation of the furnace.

It would be nice if there was a SPAN or hysteresis setting so I could
force a 1 or 2 degree swing so the cycles last longer, but I see no such
setting. I'm wondering if the A and B settings can accomplish this?

And - anyone know what the D jumper does?


Sounds like your trying to use the thermostat to mask the primary
problems.... and that would be having a furnace that is a whole lot
bigger
than you need, and not enough insulation.
20 years is a normal *high* life span for a gas furnace.


I think you're assuming a LOT (like where the O.P. resides).


He still has a 20+ year old furnace.... doesn't matter where he lives... and
short cycling still indicates a grossly oversized furnace no matter where
you live.


It would be time to
look into replacing the furnace before it becomes a problem and craps out
when its really cold.

The contractor that installs the new furnace should do a complete
room-by-room Manual J heat load/loss analysis to correctly size the new
furnace for your home. You might be surprised at the results.







  #6   Report Post  
Posted to alt.home.repair,alt.hvac
external usenet poster
 
Posts: 77
Default Honeywell MagicStat thermostat - questions about jumper settings on the back

I've got the Honeywell CT3200, which matches your pictures but not your
description. My unit has 3 dip switches and a larger fuel switch.
The manual offers no suggestions about altering the duty cycle. The
furnace is expected to cycle about 5 times per hour and is meant to hold
within 1 deg F of the setpoint.

Dave M.


  #7   Report Post  
Posted to alt.home.repair,alt.hvac
external usenet poster
 
Posts: 14
Default Honeywell MagicStat thermostat - questions about jumper settings onthe back

Steve wrote:

He still has a 20+ year old furnace.... doesn't matter where he lives.
.. and short cycling still indicates a grossly oversized furnace no
matter where you live.


Why are you such a trollish Klown?

Or are you naturally stupid when it comes to furnaces and thermostats?

Any boob knows that it's the thermostat that controls the cycling of the
furnace.

You can make ANY furnace short-cycle given a tight temperature span.
  #8   Report Post  
Posted to alt.home.repair,alt.hvac
external usenet poster
 
Posts: 14
Default Honeywell MagicStat thermostat - questions about jumper settings onthe back

" wrote:

I remember that Thermostat . The A and B screws act as a heat
anticipator does ; the more you back out the A screw with the B
screw turned all the way in....the greater the differential will be
and the greater the room temperature swing will be.


Your explanation indicates that the amount of turns of the screw is
somehow sensed by the thermostat's circuitry.

This assumption is incorrect.

On this thermostat, the screw is not functioning as the core of an
inductor or coil (as per your explanation). The only function the screw
has is to bridge the wire contacts on the upper surface of a machined
plastic block. The wires connect to the PC board.

If variable operating was desired, then Honeywell would have used a
potentiometer instead of a significantly more complicated reactance
circuit.

All the printed manuals for these thermostats indicate that the screw
has basically only 2 settings: Fully turned in (tightened down) or
unscrewed (turned out) by one turn. The one turn is sufficient to raise
the underside of the screw head enough so that it is not contacting
(bridging) the wires.
  #9   Report Post  
Posted to alt.home.repair,alt.hvac
external usenet poster
 
Posts: 14
Default Honeywell MagicStat thermostat - questions about jumper settings onthe back

"Dave M." wrote:

I've got the Honeywell CT3200, which matches your pictures but not
your description. My unit has 3 dip switches and a larger fuel
switch.


I obtained the documentation for a MagicStat CT3300 and it shows a
diagram of the back of the unit that is identical to what I have. I
copied that diagram and it can be seen he

http://www.fileden.com/files/2008/7/.../Magicstat.gif

The PDF file itself can be downloaded from he

http://www.fileden.com/files/2008/7/...StatCT3300.PDF

The manual offers no suggestions about altering the duty cycle.


That appears to be the case from what I read as well.

The furnace is expected to cycle about 5 times per hour and
is meant to hold within 1 deg F of the setpoint.


That's a pretty tight temperature range and to be able to hold it within
1 degree F and keep to only 5 cycles per hour really depends on a lot of
factors (how the premesis is constructed, how drafty it is, how cold /
windy is it outside, how many BTU's the furnace puts out, etc).

This thermostat basically has 4 binary-selectable settings:

A-in / B-in Conventional warm-air (nat-gas?) furnace
A-in / B-out Electric furnace (or electric base-board?)
A-out / B-in Hot water boiler (radiant heat?)
A-out / B-out not defined (hmm...)

Just guessing here, but why would a thermostat need to know between
which of the above 3 systems is it controlling?

The speed of response of the system? Nat-gas forced-air can respond
faster than a boiler, for example. To anticpate the call for heat
(reduce the control span?)

The thermostat doesn't want the ambient temp to drop too far below the
setpoint, and it doesn't want to over-shoot the setpoint. It's not
clear which of the above options would give me a wider span (and hence
fewer cycles per unit time). I guess I'll just have to experiment - or
buy a new thermostat with a user-settable span or hysteresis setting.
  #10   Report Post  
Posted to alt.home.repair,alt.hvac
external usenet poster
 
Posts: 77
Default Honeywell MagicStat thermostat - questions about jumper settings on the back

Guy,

I agree with your conjecture that the screws (in your case) or DIP
switches (in mine) change the anticipator circuit and thus adjust the
cycling.
I suspect that experimenting with them will be harmless but unrewarding.
The settings recommended in the manual are those that will work best.
Let me know if you find better settings.

Dave M.




  #11   Report Post  
Posted to alt.home.repair,alt.hvac
external usenet poster
 
Posts: 111
Default Honeywell MagicStat thermostat - questions about jumper settings on the back


"HVAC Guy" wrote in message ...
Steve wrote:

He still has a 20+ year old furnace.... doesn't matter where he lives.
.. and short cycling still indicates a grossly oversized furnace no
matter where you live.


Why are you such a trollish Klown?

Or are you naturally stupid when it comes to furnaces and thermostats?

Any boob knows that it's the thermostat that controls the cycling of the
furnace.

You can make ANY furnace short-cycle given a tight temperature span.



Sure... go ahead on... you know what your doing, so you don't need to worry
with posting questions about ancient POS big box stats.... when you can get
a good one for $50 or so.

Just cause your "HVAC Guy" doesn't mean squat.... you should have a decent
stat on your truck that you can use instead of screwing with a POS.



  #12   Report Post  
Posted to alt.home.repair,alt.hvac
external usenet poster
 
Posts: 117
Default Honeywell MagicStat thermostat - questions about jumper settingson the back

On Dec 29, 8:44*pm, HVAC Guy wrote:
" wrote:
I remember that Thermostat . *The *A and B screws act as a heat
anticipator does ; *the more you back out the A *screw with the B
screw turned all the way in....the greater the differential will be
and the greater the room temperature swing will be.


Your explanation indicates that the amount of turns of the screw is
somehow sensed by the thermostat's circuitry.

This assumption is incorrect.

On this thermostat, the screw is not functioning as the core of an
inductor or coil (as per your explanation). *The only function the screw
has is to bridge the wire contacts on the upper surface of a machined
plastic block. *The wires connect to the PC board.

If variable operating was desired, then Honeywell would have used a
potentiometer instead of a significantly more complicated reactance
circuit.

All the printed manuals for these thermostats indicate that the screw
has basically only 2 settings: *Fully turned in (tightened down) or
unscrewed (turned out) by one turn. *The one turn is sufficient to raise
the underside of the screw head enough so that it is not contacting
(bridging) the wires.


Whenever i adjusted the 'A' screw in or out partially...it DID make a
difference on the cycle time (differential) . I wouldnt give
Honneywell too many accolaides as far as engineering goes because this
thermostat of theirs is a poor example of quality..certainly one
Engineers wet dream to flood the market with a most inexpensive
thermostat without much consideration to accuracy. A proper
electronic thermostat that is designed well, is one where the Person
can make a definitive selection between 1,2,or 3 degrees F.
differential for heating AND for cooling....and not a psuedo-
thermostat like a Honneywell Magic Stat. Sadly, these are things the
typical homeowner isnt up to par on.
  #13   Report Post  
Posted to alt.home.repair,alt.hvac
external usenet poster
 
Posts: 117
Default Honeywell MagicStat thermostat - questions about jumper settingson the back

On Dec 30, 8:50*am, "Steve" wrote:
"HVAC Guy" wrote in ....
Steve wrote:


He still has a 20+ year old furnace.... doesn't matter where he lives.
.. and short cycling still indicates a grossly oversized furnace no
matter where you live.


Why are you such a trollish Klown?


Or are you naturally stupid when it comes to furnaces and thermostats?


Any boob knows that it's the thermostat that controls the cycling of the
furnace.


You can make ANY furnace short-cycle given a tight temperature span.


Sure... go ahead on... you know what your doing, so you don't need to worry
with posting questions about ancient POS big box stats.... when you can get
a good one for $50 or so.

Just cause your "HVAC Guy" doesn't mean squat.... you should have a decent
stat on your truck that you can use instead of screwing with a POS.


The Honneywell Magic Stat was nothing but a wet dream without any
thought to accurate differential control . It shouldnt have even been
on the market and no doubt, it didnt do much for Honneywells
reputation which youd think theyd be quite interested in
maintaining.
  #14   Report Post  
Posted to alt.home.repair,alt.hvac
external usenet poster
 
Posts: 111
Default Honeywell MagicStat thermostat - questions about jumper settings on the back


" wrote in message
...
On Dec 30, 8:50 am, "Steve" wrote:
"HVAC Guy" wrote in
...
Steve wrote:


He still has a 20+ year old furnace.... doesn't matter where he lives.
.. and short cycling still indicates a grossly oversized furnace no
matter where you live.


Why are you such a trollish Klown?


Or are you naturally stupid when it comes to furnaces and thermostats?


Any boob knows that it's the thermostat that controls the cycling of the
furnace.


You can make ANY furnace short-cycle given a tight temperature span.


Sure... go ahead on... you know what your doing, so you don't need to
worry
with posting questions about ancient POS big box stats.... when you can
get
a good one for $50 or so.

Just cause your "HVAC Guy" doesn't mean squat.... you should have a decent
stat on your truck that you can use instead of screwing with a POS.


The Honneywell Magic Stat was nothing but a wet dream without any
thought to accurate differential control . It shouldnt have even been
on the market and no doubt, it didnt do much for Honneywells
reputation which youd think theyd be quite interested in
maintaining.

------------------------------------

the magic was how it lined honeywells pockets...it was in the same class as
hunter stats





  #15   Report Post  
Posted to alt.home.repair,alt.hvac
external usenet poster
 
Posts: 117
Default Honeywell MagicStat thermostat - questions about jumper settingson the back

On Dec 30, 5:48*pm, "Steve" wrote:
" wrote in message

...
On Dec 30, 8:50 am, "Steve" wrote:





"HVAC Guy" wrote in
...
Steve wrote:


He still has a 20+ year old furnace.... doesn't matter where he lives.
.. and short cycling still indicates a grossly oversized furnace no
matter where you live.


Why are you such a trollish Klown?


Or are you naturally stupid when it comes to furnaces and thermostats?


Any boob knows that it's the thermostat that controls the cycling of the
furnace.


You can make ANY furnace short-cycle given a tight temperature span.


Sure... go ahead on... you know what your doing, so you don't need to
worry
with posting questions about ancient POS big box stats.... when you can
get
a good one for $50 or so.


Just cause your "HVAC Guy" doesn't mean squat.... you should have a decent
stat on your truck that you can use instead of screwing with a POS.


The Honneywell Magic Stat was nothing but a wet dream without any
thought to accurate differential control . *It shouldnt have even been
on the market *and no doubt, it didnt do much for Honneywells
reputation *which youd think theyd be quite interested in
maintaining.

------------------------------------

the magic was how it lined honeywells pockets...it was in the same class as
hunter stats


Totally agree . The Hunter wouldnt properly control anything beyond
a .4 amp device in the heating mode.


  #16   Report Post  
Posted to alt.home.repair,alt.hvac
external usenet poster
 
Posts: 14
Default Honeywell MagicStat thermostat - questions about jumper settings onthe back

" wrote:

Whenever i adjusted the 'A' screw in or out partially...it DID
make a difference on the cycle time (differential) .


My gut feeling, based on turning out the A screw, is that the furnace
cycle time has been lengthened to a more satisfactory condition, with no
discernable change in overall ambient air temperature.

A-out / B-in Hot water boiler (radiant heat?)

So this is, in effect, telling the thermostat that instead of
controlling a conventional mid-efficiency forced-air natural gas
furnace, that it's controlling a hot water boiler.

This seems to have the effect of not turning on the furnace as often.
  #17   Report Post  
Posted to alt.home.repair,alt.hvac
external usenet poster
 
Posts: 82
Default Honeywell MagicStat thermostat - questions about jumper settings on the back

Sorry guys but some how you guys getting on my nerves
you being discussing this Fxxxxxx Magic Thermostat for past month
and I don't see positive explain what type heat does it has
is it hot water or is it hot air electrical/gas or does this thermostat controls home/buld. temp.
Or you are trying to use VW motor to drive Cad.

"HVAC Guy" wrote in message ...
" wrote:

Whenever i adjusted the 'A' screw in or out partially...it DID
make a difference on the cycle time (differential) .


My gut feeling, based on turning out the A screw, is that the furnace
cycle time has been lengthened to a more satisfactory condition, with no
discernable change in overall ambient air temperature.

A-out / B-in Hot water boiler (radiant heat?)

So this is, in effect, telling the thermostat that instead of
controlling a conventional mid-efficiency forced-air natural gas
furnace, that it's controlling a hot water boiler.

This seems to have the effect of not turning on the furnace as often.



  #18   Report Post  
Posted to alt.home.repair,alt.hvac
external usenet poster
 
Posts: 111
Default Honeywell MagicStat thermostat - questions about jumper settings on the back

I still haven't figured out why nobody has posted the link for the
instructions for this antique big box store POS stat.

Either the OP is an idiot (this is a given), and/or he's just too freakin
lazy to actually look for it, and/or hes nothing but another troll.
A simple yahoo search gets over 19,000 hits. How hard is this??

http://customer.honeywell.com/TechLi...0s/69-0653.pdf

You can also go to the Honeywell site and get it from there....



"Grumpy" wrote in message
...
Sorry guys but some how you guys getting on my nerves
you being discussing this Fxxxxxx Magic Thermostat for past month
and I don't see positive explain what type heat does it has
is it hot water or is it hot air electrical/gas or does this thermostat
controls home/buld. temp.
Or you are trying to use VW motor to drive Cad.

"HVAC Guy" wrote in message
...
" wrote:

Whenever i adjusted the 'A' screw in or out partially...it DID
make a difference on the cycle time (differential) .


My gut feeling, based on turning out the A screw, is that the furnace
cycle time has been lengthened to a more satisfactory condition, with no
discernable change in overall ambient air temperature.

A-out / B-in Hot water boiler (radiant heat?)

So this is, in effect, telling the thermostat that instead of
controlling a conventional mid-efficiency forced-air natural gas
furnace, that it's controlling a hot water boiler.

This seems to have the effect of not turning on the furnace as often.





  #19   Report Post  
Posted to alt.home.repair,alt.hvac
external usenet poster
 
Posts: 14
Default Honeywell MagicStat thermostat - questions about jumper settings onthe back

Steve wrote:

I still haven't figured out why nobody has posted the link for the
instructions for this antique big box store POS stat.

Either the OP is an idiot (this is a given), and/or he's just too
freakin lazy to actually look for it, and/or hes nothing but another
troll.


That's right.

Show what a usenet dumb-ass you are by calling everyone a troll.

A simple yahoo search gets over 19,000 hits. How hard is this??

http://customer.honeywell.com/TechLi...0s/69-0653.pdf

You can also go to the Honeywell site and get it from there....


Why the hell are you such a ****ing ass hole Steve?

I've got the ****ing pdf instructions for the stat. If you had half a
brain, you would have seen that based on my previous posts in this
thread.

If you weren't such an ass-wipe, you'd already know that the stat was
configured properly for the type of furnace it was controlling. But
even though it was properly configured, it was cycling too often to suit
my liking.

That's ****ing why I started the thread in the first place. To see if
any of you dorks know how this stat reacts when you change it's
settings. You fools obviously didn't know.

So the stat now thinks it's controlling a hot water boiler, and it's not
cycling as often as it was, and I'm satisfied with the end result. The
temperature of the space being heated is comfortable, with no real
detectible hot/cold swings because the stat's duty cycle is longer.

As for you, Grumpy, I don't know what your god damn problem is.

If you bothered to read the entire ****ing thread, you might have a clue
as to how this is going down.

Or you are trying to use VW motor to drive Cad.


What a maroon.
  #20   Report Post  
Posted to alt.home.repair,alt.hvac
external usenet poster
 
Posts: 16
Default Honeywell MagicStat thermostat - questions about jumper settingson the back

On 1/15/2012 1:26 PM, HVAC Guy wrote:
Steve wrote:
A simple yahoo search gets over 19,000 hits. How hard is this??

http://customer.honeywell.com/TechLi...0s/69-0653.pdf

You can also go to the Honeywell site and get it from there....


Why the hell are you such a ****ing ass hole Steve?


FWIW, I googled "why is steve an asshole?".

I got 207,000,000 hits

take your pick ;-)


  #21   Report Post  
Posted to alt.home.repair,alt.hvac
external usenet poster
 
Posts: 10
Default Honeywell MagicStat thermostat - questions about jumper settingson the back

On 1/15/2012 1:26 PM, HVAC Guy wrote:
Steve wrote:

I still haven't figured out why nobody has posted the link for the
instructions for this antique big box store POS stat.

Either the OP is an idiot (this is a given), and/or he's just too
freakin lazy to actually look for it, and/or hes nothing but another
troll.


That's right.

Show what a usenet dumb-ass you are by calling everyone a troll.



He's not calling everyone a troll. He's calling YOU an idiot.


He's right.










--
"OK you ****s, let's see what you can do now" -Hit Girl
http://www.youtube.com/watch?v=CjO7kBqTFqo
  #22   Report Post  
Posted to alt.home.repair,alt.hvac
external usenet poster
 
Posts: 74
Default Honeywell MagicStat thermostat - questions about jumper settings on the back


"HVAC" wrote in message
...
On 1/15/2012 1:26 PM, HVAC Guy wrote:
Steve wrote:

I still haven't figured out why nobody has posted the link for the
instructions for this antique big box store POS stat.

Either the OP is an idiot (this is a given), and/or he's just too
freakin lazy to actually look for it, and/or hes nothing but another
troll.


That's right.

Show what a usenet dumb-ass you are by calling everyone a troll.



He's not calling everyone a troll. He's calling YOU an idiot.



Person like you with such intelligence kiss my Ares does that make you happy



He's right.


"OK you ****s, let's see what you can do now" -Hit Girl
http://www.youtube.com/watch?v=CjO7kBqTFqo



  #23   Report Post  
Posted to alt.home.repair,alt.hvac
external usenet poster
 
Posts: 19
Default Honeywell MagicStat thermostat - questions about jumper settings on the back


"Steve" wrote in message
...
I still haven't figured out why nobody has posted the link for the
instructions for this antique big box store POS stat.

Either the OP is an idiot (this is a given), and/or he's just too freakin
lazy to actually look for it, and/or hes nothing but another troll.
A simple yahoo search gets over 19,000 hits. How hard is this??

http://customer.honeywell.com/TechLi...0s/69-0653.pdf

You can also go to the Honeywell site and get it from there....



Because not every Honeywell manual is perfect, especially for a cheap HwHwST

The manual for mine, a Honeywell RTH221B1000 that I got 3 of for $5 each
from the Orscheln Farm and Home bargain bin makes no mention of cycles per
hour. If you Google the model RTH221B, you get this manual:

http://www.honeywellcentral.com/ssi/...ers-Manual.pdf

However if you Google RTH221B cycles per hour you get this manual:

http://customer.honeywell.com/techli...69-2060EFS.pdf

Or Google RTH221B1000 cycles per hour and get this manual:

http://customer.honeywell.com/techli.../69-2448ES.pdf

The latter 2 manuals both explain how to press both temp arrows together for
3 seconds to enter the hidden settings menu.

If you want a real Honeywell manual you have to step up out of the HwHwST
class and into the professional class, Google Honeywell t8600d t8601d and
get:

http://www.thermostatshop.com/manual...s%20manual.pdf

Now That's what I call a manual.

HwHwST=Honeywell hardware store thermostat.


  #24   Report Post  
Posted to alt.home.repair,alt.hvac
external usenet poster
 
Posts: 14
Default Honeywell MagicStat thermostat - questions about jumper settingson the back

Daniel who wants to know wrote:

The manual for mine, a Honeywell RTH221B1000 that I got 3 of for
$5 each from the Orscheln Farm and Home bargain bin makes no
mention of cycles per hour.


Of course not.

Because the number of cycles per hour will depend on

- the temperature span or hysteresis around the desired set point
- the heat loss of the space being controlled
- the BTU capacity of the furnace

If the stat has a setting for cycles per hour, then you're going to have
a variable hysteresis, and the stat is going to take some time to learn
what that's going to be for a given set of conditions.

To make it more complicated, the heat loss of the space is going to be
affected by ambient outside weather (wind and temperature) and how well
the space is insulated. As that changes, the thermostat will have to
re-learn how to control the furnace to keep the desired set-point while
maintaining the desired cycles per hour.

It's far simpler to set the hysteresis (2 or 3 degrees instead of 1
degree) and live with what-ever cycles per hour you end up getting,
rather then aim for a set or fixed cycles-per-hour.
  #25   Report Post  
Posted to alt.home.repair,alt.hvac
external usenet poster
 
Posts: 19
Default Honeywell MagicStat thermostat - questions about jumper settings on the back

"HVAC Guy" wrote in message ...

Of course not.

Because the number of cycles per hour will depend on

- the temperature span or hysteresis around the desired set point
- the heat loss of the space being controlled
- the BTU capacity of the furnace

If the stat has a setting for cycles per hour, then you're going to have
a variable hysteresis, and the stat is going to take some time to learn
what that's going to be for a given set of conditions.

To make it more complicated, the heat loss of the space is going to be
affected by ambient outside weather (wind and temperature) and how well
the space is insulated. As that changes, the thermostat will have to
re-learn how to control the furnace to keep the desired set-point while
maintaining the desired cycles per hour.

It's far simpler to set the hysteresis (2 or 3 degrees instead of 1
degree) and live with what-ever cycles per hour you end up getting,
rather then aim for a set or fixed cycles-per-hour.


Did you read any of the PDFs?

Anyway the problem here isn't Honeywell's choice of CPH over hysteresis
degrees, it is how this stat (RTH221) seems to function, when set to 5 CPH
it calls for heat every 12 minutes as expected, but when set to 3 or 1 CPH
in my house it only drops to calling for heat every 13 minutes, and this is
after several hours to adapt. I have a 90+ condensing gas furnace and this
style is only supposed to be cycled about 3 times per hour.

Also interesting with this model is that when set to 62° F as it cycled its
reading would swing from 58° to 65° with each cycle while 3 other
thermometers, a non-connected Lux digital thermostat, a digital meat
thermometer, and an indoor/outdoor thermometer and hygrometer weather
station all placed right beside the RTH221 would all show the swing as being
from 61-63°. When the temp setting on the RTH221 was first set down to 62°
from 68° its reading quickly dropped to 61° and stayed as the 3 others
showed the normal gradual drop. When the others started to show 61° as well
the RTH221 dropped to showing 60° and shortly thereafter called for heat.

It is an odd model for sure.




  #26   Report Post  
Posted to alt.home.repair,alt.hvac
external usenet poster
 
Posts: 111
Default Honeywell MagicStat thermostat - questions about jumper settings on the back


"Daniel who wants to know" wrote in message
...
"HVAC Guy" wrote in message
...

Of course not.

Because the number of cycles per hour will depend on

- the temperature span or hysteresis around the desired set point
- the heat loss of the space being controlled
- the BTU capacity of the furnace

If the stat has a setting for cycles per hour, then you're going to have
a variable hysteresis, and the stat is going to take some time to learn
what that's going to be for a given set of conditions.

To make it more complicated, the heat loss of the space is going to be
affected by ambient outside weather (wind and temperature) and how well
the space is insulated. As that changes, the thermostat will have to
re-learn how to control the furnace to keep the desired set-point while
maintaining the desired cycles per hour.

It's far simpler to set the hysteresis (2 or 3 degrees instead of 1
degree) and live with what-ever cycles per hour you end up getting,
rather then aim for a set or fixed cycles-per-hour.


Did you read any of the PDFs?

Anyway the problem here isn't Honeywell's choice of CPH over hysteresis
degrees, it is how this stat (RTH221) seems to function, when set to 5 CPH
it calls for heat every 12 minutes as expected, but when set to 3 or 1 CPH
in my house it only drops to calling for heat every 13 minutes, and this
is after several hours to adapt. I have a 90+ condensing gas furnace and
this style is only supposed to be cycled about 3 times per hour.

Also interesting with this model is that when set to 62° F as it cycled
its reading would swing from 58° to 65° with each cycle while 3 other
thermometers, a non-connected Lux digital thermostat, a digital meat
thermometer, and an indoor/outdoor thermometer and hygrometer weather
station all placed right beside the RTH221 would all show the swing as
being from 61-63°. When the temp setting on the RTH221 was first set down
to 62° from 68° its reading quickly dropped to 61° and stayed as the 3
others showed the normal gradual drop. When the others started to show
61° as well the RTH221 dropped to showing 60° and shortly thereafter
called for heat.

It is an odd model for sure.



Yup... big box store junk..... There is a sucker born every minute that will
buy one.


  #27   Report Post  
Posted to alt.home.repair,alt.hvac
external usenet poster
 
Posts: 14
Default Honeywell MagicStat thermostat - questions about jumper settings onthe back

Grumpy full-quoted:

Ok enough of this crap apparently your cheepy Tst


Full quoting dink. Learn how to edit your posts and quote responsibly.

You can't even say "t-stat" or just "stat" ?

You have to shorten it even more?

to make it more stable you can cover Tst with something


No. I just have to dial out one screw to change the setting.

Read the ****ing thread bozo.
  #28   Report Post  
Posted to alt.home.repair,alt.hvac
external usenet poster
 
Posts: 74
Default Honeywell MagicStat thermostat - questions about jumper settings on the back

Maybe I am bozo but you Sir is professor of powder room

I do not think that explanation is required!!!




"HVAC Guy" wrote in message ...
Grumpy full-quoted:

Ok enough of this crap apparently your cheepy Tst


Full quoting dink. Learn how to edit your posts and quote responsibly.

You can't even say "t-stat" or just "stat" ?

You have to shorten it even more?

to make it more stable you can cover Tst with something


No. I just have to dial out one screw to change the setting.

Read the ****ing thread bozo.



  #29   Report Post  
Posted to alt.home.repair,alt.hvac
external usenet poster
 
Posts: 19
Default Honeywell MagicStat thermostat - questions about jumper settings on the back


"Grumpy" wrote in message
...

Ok enough of this crap apparently your cheepy Tst is much more sensitive


That's what I thought at first so I wedged some plumber's putty in the
corner where the thermistor is located (it sits epoxied into a small recess
in the bottom left corner of the plastic housing) to add thermal mass, this
showed no change. Besides have you seen how fast a meat thermometer reacts
to temp changes? In air it only takes a few seconds per degree for a small
change, in meat they don't call them "instant read" for nothing.

Than the others, to make it more stable you can cover Tst with something


I thought about also putting a clear storage bowl or one of those
anti-tamper plastic boxes over it.

To see how much of effect will have, or/and if you have forced air heating

Make sure that your duct discharge is not blowing on to Tst.


Nope, the supplies are on the other side of the room.


  #30   Report Post  
Posted to alt.home.repair,alt.hvac
external usenet poster
 
Posts: 3,761
Default Honeywell MagicStat thermostat - questions about jumper settingson the back

On 1/21/2012 9:11 PM, Daniel who wants to know wrote:
wrote in message
...

Ok enough of this crap apparently your cheepy Tst is much more sensitive


That's what I thought at first so I wedged some plumber's putty in the
corner where the thermistor is located (it sits epoxied into a small recess
in the bottom left corner of the plastic housing) to add thermal mass, this
showed no change. Besides have you seen how fast a meat thermometer reacts
to temp changes? In air it only takes a few seconds per degree for a small
change, in meat they don't call them "instant read" for nothing.

Than the others, to make it more stable you can cover Tst with something


I thought about also putting a clear storage bowl or one of those
anti-tamper plastic boxes over it.

To see how much of effect will have, or/and if you have forced air heating

Make sure that your duct discharge is not blowing on to Tst.


Nope, the supplies are on the other side of the room.


I'm afraid I didn't follow this thread that closely but did anyone
mention making sure any holes in the wall behind the T-stat were sealed?
That would be the first thing I always look for. I've found that even
the tiniest holes can let in enough air to screw with an electronic
sensor. Even air getting past/through the little plastic anchors for
the mounting screws. o_O

TDD



  #31   Report Post  
Posted to alt.home.repair,alt.hvac
external usenet poster
 
Posts: 19
Default Honeywell MagicStat thermostat - questions about jumper settings on the back

"The Daring Dufas" wrote in message
...

I'm afraid I didn't follow this thread that closely but did anyone mention
making sure any holes in the wall behind the T-stat were sealed?
That would be the first thing I always look for. I've found that even
the tiniest holes can let in enough air to screw with an electronic
sensor. Even air getting past/through the little plastic anchors for
the mounting screws. o_O

TDD


In my case that is covered too, the thermostat is mounted to a paneling wall
of the closet that the furnace is in, the walls are bare studs inside the
closet, and the furnace is direct return instead of ducted with 2 20x25
filters in an A frame shape on top (it is a downflow), IE the area behind
the thermostat is conditioned space.


  #32   Report Post  
Posted to alt.home.repair,alt.hvac
external usenet poster
 
Posts: 3,761
Default Honeywell MagicStat thermostat - questions about jumper settingson the back

On 1/23/2012 3:40 AM, Daniel who wants to know wrote:
"The Daring wrote in message
...

I'm afraid I didn't follow this thread that closely but did anyone mention
making sure any holes in the wall behind the T-stat were sealed?
That would be the first thing I always look for. I've found that even
the tiniest holes can let in enough air to screw with an electronic
sensor. Even air getting past/through the little plastic anchors for
the mounting screws. o_O

TDD


In my case that is covered too, the thermostat is mounted to a paneling wall
of the closet that the furnace is in, the walls are bare studs inside the
closet, and the furnace is direct return instead of ducted with 2 20x25
filters in an A frame shape on top (it is a downflow), IE the area behind
the thermostat is conditioned space.



Cool! No pun intended. ^_^

TDD
  #33   Report Post  
Posted to alt.home.repair,alt.hvac
external usenet poster
 
Posts: 1
Default Honeywell MagicStat thermostat - questions about jumper settings on the back

replying to HVAC Guy, Dorothy wrote:
Can you still purchase this thermostat

--
for full context, visit https://www.homeownershub.com/hvac/h...set-45521-.htm


Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Replacing old Honeywell thermostat with Honeywell 907 Kostas Kavoussanakis UK diy 7 November 3rd 07 03:25 PM
Settings For Honeywell CM67 and Old Boiler [email protected] UK diy 2 December 13th 05 05:31 PM
Rad Thermostat Settings Geoff Lane UK diy 7 June 9th 05 05:37 PM
Honeywell CT3600 Thermostat Questions Shrek Home Repair 7 November 6th 04 05:43 PM
TV does not remember channel settings, image settings, and sound settings after having been shut down Michiel Tas Electronics Repair 2 March 13th 04 02:33 AM


All times are GMT +1. The time now is 10:41 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"