Hi,
I have an old-work 20 cu in junction box. It has two sets of 14-2 cables spliced: two sets of travelers weren't long enough and had to be lengthened. The box uses Ideal connectors which take very little space. All and all, the wires already in there take about 1/4 of the available space. I need to add an outlet to that box (same circuit) which I'm technically not allowed to do. However, practically speaking, the box will hardly be half full if I do this. What would you do in this situation? Thanks! Sam |
#2
Posted to alt.home.repair
|
|||
|
|||
electrical box fill
On 09/26/2010 02:56 AM, Sam Takoy wrote:
Hi, I have an old-work 20 cu in junction box. It has two sets of 14-2 cables spliced: two sets of travelers weren't long enough and had to be lengthened. The box uses Ideal connectors which take very little space. All and all, the wires already in there take about 1/4 of the available space. I need to add an outlet to that box (same circuit) which I'm technically not allowed to do. However, practically speaking, the box will hardly be half full if I do this. What would you do in this situation? Thanks! Sam If it's an old work box why not take it out and use a deeper one? you say "travelers" but then you mention 14/2... is this a 3-way switch circuit? nate -- replace "roosters" with "cox" to reply. http://members.cox.net/njnagel |
#3
Posted to alt.home.repair
|
|||
|
|||
electrical box fill
On 9/26/2010 9:29 AM, Nate Nagel wrote:
On 09/26/2010 02:56 AM, Sam Takoy wrote: Hi, I have an old-work 20 cu in junction box. It has two sets of 14-2 cables spliced: two sets of travelers weren't long enough and had to be lengthened. The box uses Ideal connectors which take very little space. All and all, the wires already in there take about 1/4 of the available space. I need to add an outlet to that box (same circuit) which I'm technically not allowed to do. However, practically speaking, the box will hardly be half full if I do this. What would you do in this situation? Thanks! Sam If it's an old work box why not take it out and use a deeper one? you say "travelers" but then you mention 14/2... is this a 3-way switch circuit? nate OK, some clarification. I'm technically not allowed to do this because that would be too many wires/devices. 20 cu in is the deepest single gang box available. And with two sets of 14-2 wires spliced, I used up 17 cu in of nominal space (2x4x2 + 1). Yes, it's a 3-way/4-way switch circuit, but the neutral is delivered to the electrical box with the switches by a different cable that does not pass through this junction box. So: by adding a 14-2 wire and an outlet to this box, I will technically be going over the wire limit. But practically, the box will only be about half full. |
#4
Posted to alt.home.repair
|
|||
|
|||
electrical box fill
On 09/26/2010 09:34 AM, Sam Takoy wrote:
On 9/26/2010 9:29 AM, Nate Nagel wrote: On 09/26/2010 02:56 AM, Sam Takoy wrote: Hi, I have an old-work 20 cu in junction box. It has two sets of 14-2 cables spliced: two sets of travelers weren't long enough and had to be lengthened. The box uses Ideal connectors which take very little space. All and all, the wires already in there take about 1/4 of the available space. I need to add an outlet to that box (same circuit) which I'm technically not allowed to do. However, practically speaking, the box will hardly be half full if I do this. What would you do in this situation? Thanks! Sam If it's an old work box why not take it out and use a deeper one? you say "travelers" but then you mention 14/2... is this a 3-way switch circuit? nate OK, some clarification. I'm technically not allowed to do this because that would be too many wires/devices. 20 cu in is the deepest single gang box available. And with two sets of 14-2 wires spliced, I used up 17 cu in of nominal space (2x4x2 + 1). Yes, it's a 3-way/4-way switch circuit, but the neutral is delivered to the electrical box with the switches by a different cable that does not pass through this junction box. So: by adding a 14-2 wire and an outlet to this box, I will technically be going over the wire limit. But practically, the box will only be about half full. Ah, I got you. So you are going to have to pull another cable into the box, that is what I was missing. Do you have access to the backside of this wall? could you use a 1900 (4" square) box with a mud ring? nate -- replace "roosters" with "cox" to reply. http://members.cox.net/njnagel |
#5
Posted to alt.home.repair
|
|||
|
|||
electrical box fill
On 9/26/2010 9:44 AM, Nate Nagel wrote:
On 09/26/2010 09:34 AM, Sam Takoy wrote: On 9/26/2010 9:29 AM, Nate Nagel wrote: On 09/26/2010 02:56 AM, Sam Takoy wrote: Hi, I have an old-work 20 cu in junction box. It has two sets of 14-2 cables spliced: two sets of travelers weren't long enough and had to be lengthened. The box uses Ideal connectors which take very little space. All and all, the wires already in there take about 1/4 of the available space. I need to add an outlet to that box (same circuit) which I'm technically not allowed to do. However, practically speaking, the box will hardly be half full if I do this. What would you do in this situation? Thanks! Sam If it's an old work box why not take it out and use a deeper one? you say "travelers" but then you mention 14/2... is this a 3-way switch circuit? nate OK, some clarification. I'm technically not allowed to do this because that would be too many wires/devices. 20 cu in is the deepest single gang box available. And with two sets of 14-2 wires spliced, I used up 17 cu in of nominal space (2x4x2 + 1). Yes, it's a 3-way/4-way switch circuit, but the neutral is delivered to the electrical box with the switches by a different cable that does not pass through this junction box. So: by adding a 14-2 wire and an outlet to this box, I will technically be going over the wire limit. But practically, the box will only be about half full. Ah, I got you. So you are going to have to pull another cable into the box, that is what I was missing. Do you have access to the backside of this wall? could you use a 1900 (4" square) box with a mud ring? nate Yes, I have access to the back, but I can't replace the box. It's tightly between two studs. |
#6
Posted to alt.home.repair
|
|||
|
|||
electrical box fill
Sam Takoy wrote:
On 9/26/2010 9:44 AM, Nate Nagel wrote: On 09/26/2010 09:34 AM, Sam Takoy wrote: On 9/26/2010 9:29 AM, Nate Nagel wrote: On 09/26/2010 02:56 AM, Sam Takoy wrote: .... I need to add an outlet to that box (same circuit) which I'm technically not allowed to do. However, practically speaking, the box will hardly be half full if I do this. .... I'm technically not allowed to do this because that would be too many wires/devices. 20 cu in is the deepest single gang box available. And with two sets of 14-2 wires spliced, I used up 17 cu in of nominal space (2x4x2 + 1). .... So: by adding a 14-2 wire and an outlet to this box, I will technically be going over the wire limit. But practically, the box will only be about half full. Ah, I got you. So you are going to have to pull another cable into the box, that is what I was missing. Do you have access to the backside of this wall? could you use a 1900 (4" square) box with a mud ring? .... Yes, I have access to the back, but I can't replace the box. It's tightly between two studs. As another poster said, given the description and particularly that it's 14-ga wire that is so flexible, I'd in all likelihood go ahead and stretch the volume limit if it was truly near-impossible to retrofit the larger box for some reason (other than just not wanting to do so). While it might not be totally Code-compliant, if the conductors are not kinked or rubbing on mount screws, etc., it is not going to be a safety problem. I've seen many, many boxes over the years that are absolutely crammed to the limit of what could be gotten into them and none have ever been a problem owing to that capacity limit. So, it isn't quite kosher, but sometimes "ya' just gotta' do what ya' gotta' do" when it isn't really going to be anything but a technical violation, not a safety one. $0.02, etc., etc., etc., ... -- |
#7
Posted to alt.home.repair
|
|||
|
|||
electrical box fill
In article , Sam Takoy wrote:
I'm technically not allowed to do this because that would be too many wires/devices. 20 cu in is the deepest single gang box available. And with two sets of 14-2 wires spliced, I used up 17 cu in of nominal space (2x4x2 + 1). Where does that "+ 1" come from? Here's what your calculation *should* look like: 4 14ga cables @ 2 conductors each = 8 conductors add 1 for one or more equipment groundi ng conductors add 1 for each cable clamp in use (presumably at least 2) That's what you have *already*: the equivalent of 11 conductors, at 2 in^3 each, which means you're at 22 in^3 *now*. Not 17. Then add 2 more for the device yoke you're planning to add. That brings the total to 13 conductors x 2 in^3 each = 26 in^3 minimum. |
#8
Posted to alt.home.repair
|
|||
|
|||
electrical box fill
On 2010-09-26, Sam Takoy wrote:
Yes, it's a 3-way/4-way switch circuit, but the neutral is delivered to the electrical box with the switches by a different cable that does not pass through this junction box. While that is permitted with nonmetallic cable (Romex), it will cause some EMI when the light on, since the neutral is not routed with the hot conductors. It is generally a good practice to route your cables together when the neutral and the hot/travelers are in different cables. As to your OP, if I couldn't possibly fit a larger box there, I'd use an additional box for the receptacle. And I'd feed it with a hot and neutral together in the same cable. Cheers, Wayne |
#9
Posted to alt.home.repair
|
|||
|
|||
electrical box fill
On 2010-09-26, Doug Miller wrote:
I'm technically not allowed to do this because that would be too many wires/devices. 20 cu in is the deepest single gang box available. And with two sets of 14-2 wires spliced, I used up 17 cu in of nominal space (2x4x2 + 1). Where does that "+ 1" come from? That's his allowance for the EGCs, but it's not quite right. It should be (2 * 4 + 1) * 2, or 18 in^3. Here's what your calculation *should* look like: 4 14ga cables @ 2 conductors each = 8 conductors add 1 for one or more equipment groundi ng conductors add 1 for each cable clamp in use (presumably at least 2) You only need to count clamps that extend into the box, so the integral clamps on a plastic box do not need to be counted. Thus I assume he's using a plastic box. Plus, since we are talking about a one-gang box, for a plastic one-gang and NM cable, you don't need to clamp the wire to the box, as long as you secure the wire close enough to the box (I forget the requirement). Single-gang plastic boxes typically don't have cable clamps at all. Cheers, Wayne |
#10
Posted to alt.home.repair
|
|||
|
|||
electrical box fill
On 2010-09-26, Sam Takoy wrote:
20 cu in is the deepest single gang box available. You can definitely get them up to 24 in^3, although they will obviously be bigger in some dimension and so might not fit in your space. See, for example, www.aifittings.com. But you need 26 in^3 for what you want to do, and I don't know if those exist. Cheers, Wayne |
#11
Posted to alt.home.repair
|
|||
|
|||
electrical box fill
"Wayne Whitney" wrote in message ... On 2010-09-26, Doug Miller wrote: I'm technically not allowed to do this because that would be too many wires/devices. 20 cu in is the deepest single gang box available. And with two sets of 14-2 wires spliced, I used up 17 cu in of nominal space (2x4x2 + 1). Where does that "+ 1" come from? That's his allowance for the EGCs, but it's not quite right. It should be (2 * 4 + 1) * 2, or 18 in^3. Here's what your calculation *should* look like: 4 14ga cables @ 2 conductors each = 8 conductors add 1 for one or more equipment groundi ng conductors add 1 for each cable clamp in use (presumably at least 2) You only need to count clamps that extend into the box, so the integral clamps on a plastic box do not need to be counted. Thus I assume he's using a plastic box. Plus, since we are talking about a one-gang box, for a plastic one-gang and NM cable, you don't need to clamp the wire to the box, as long as you secure the wire close enough to the box (I forget the requirement). Single-gang plastic boxes typically don't have cable clamps at all. Cheers, Wayne Also, there are 22cu. in. plastic single gang boxes, or he could use a deep plastic 1900 box with single gang reducing cover. Then he can go hog wild. |
#12
Posted to alt.home.repair
|
|||
|
|||
electrical box fill
Wayne Whitney wrote:
On 2010-09-26, Sam Takoy wrote: Yes, it's a 3-way/4-way switch circuit, but the neutral is delivered to the electrical box with the switches by a different cable that does not pass through this junction box. While that is permitted with nonmetallic cable (Romex), it will cause some EMI when the light on, since the neutral is not routed with the hot conductors. It is generally a good practice to route your cables together when the neutral and the hot/travelers are in different cables. I didn't entirely follow that from Sam, but all wires for a circuit need to appear in the same cable; it seems to violate 310.3-B. I would consider that more important than too many wires in the box. Sounded like Sam was also considering adding a romex and an outlet in the box. As to your OP, if I couldn't possibly fit a larger box there, I'd use an additional box for the receptacle. And I'd feed it with a hot and neutral together in the same cable. Another possible, but ugly, is a wiremold surface extension. Anonymously ask the inspector his opinion about overfill in this box? Box now has a blank cover? Cheers, Wayne |
#13
Posted to alt.home.repair
|
|||
|
|||
electrical box fill
On 2010-09-26, bud-- wrote:
I didn't entirely follow that from Sam, but all wires for a circuit need to appear in the same cable; it seems to violate 310.3-B. I assume you mean 300.3(B). In which case see 300.3(B)(3), which basically says the requirement doesn't apply to cables with a non-metallic sheath, i.e. Romex. None the less, when circuit conductors are split between multiple cables, it is a good idea to run the cables together. Cheers, Wayne |
#14
Posted to alt.home.repair
|
|||
|
|||
electrical box fill
In article , Wayne Whitney wrote:
On 2010-09-26, Doug Miller wrote: I'm technically not allowed to do this because that would be too many wires/devices. 20 cu in is the deepest single gang box available. And with two sets of 14-2 wires spliced, I used up 17 cu in of nominal space (2x4x2 + 1). Where does that "+ 1" come from? That's his allowance for the EGCs, but it's not quite right. It should be (2 * 4 + 1) * 2, or 18 in^3. Here's what your calculation *should* look like: 4 14ga cables @ 2 conductors each = 8 conductors add 1 for one or more equipment groundi ng conductors add 1 for each cable clamp in use (presumably at least 2) You only need to count clamps that extend into the box, so the integral clamps on a plastic box do not need to be counted. Thus I assume he's using a plastic box. I, on the other hand, having observed that he didn't calculate the EGC requirement correctly, just assumed he didn't know he was supposed to count the clamps too. Plus, since we are talking about a one-gang box, for a plastic one-gang and NM cable, you don't need to clamp the wire to the box, as long as you secure the wire close enough to the box (I forget the requirement). Single-gang plastic boxes typically don't have cable clamps at all. Right, but I don't think he ever stated explicitly that it's a plastic box. OTOH, he *did* state explicitly that it's an old work box -- which makes it *very* unlikely that the cables are secured to the framing at all, let alone within the required distance (which, BTW, is 8 inches). |
#15
Posted to alt.home.repair
|
|||
|
|||
electrical box fill
Wayne Whitney wrote:
On 2010-09-26, bud-- wrote: I didn't entirely follow that from Sam, but all wires for a circuit need to appear in the same cable; it seems to violate 310.3-B. I assume you mean 300.3(B). Yes - a typo. In which case see 300.3(B)(3), which basically says the requirement doesn't apply to cables with a non-metallic sheath, i.e. Romex. None the less, when circuit conductors are split between multiple cables, it is a good idea to run the cables together. 300.3 was rewritten a few codes ago and I had a distinct recollection that California 3-ways that used 2 2-wire romexes were prohibited. Looks like the weren't. If the conductors are not together and with high current the magnetic field from the loop can affect CRTs, as in old TVs. I guess CRTs are rapidly disappearing. -- bud-- |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Convert cold fill washing machine to hot and cold fill | UK diy | |||
when you fill your 275 gallon tank does it every fill to the top? | Home Ownership | |||
Cavity walls to fill or not to fill... below a flat roof. | UK diy | |||
How to fill this gap? | Home Repair | |||
Electrical putty vs. silicone for sealing exterior electrical holes? | Home Repair |