Got a 15 amp split receptable mounted on a studded basement wall for a
washing machine and gas dryer. I want to install a laundry tub about 4 feet away. Code here says that outlet has go to be gfci (1.5 metres or about 4.5 feet from the "sink") but I cannot find any 15 amp split receptacle gfi outlets. The wire is 14/3 so I can't do like the kitchen 20 amp near the sinks... are there 15 amp gfi split receptacle outlets? I see none available in my juistiction (ontario)... Is this because it has to be gfi at the breaker and not allowed at the outlet? |
#2
Posted to alt.home.repair
|
|||
|
|||
Split Receptacle GFI outlet. Do they exist?
"The Henchman" wrote in message ... Got a 15 amp split receptable mounted on a studded basement wall for a washing machine and gas dryer. I want to install a laundry tub about 4 feet away. Code here says that outlet has go to be gfci (1.5 metres or about 4.5 feet from the "sink") but I cannot find any 15 amp split receptacle gfi outlets. The wire is 14/3 so I can't do like the kitchen 20 amp near the sinks... are there 15 amp gfi split receptacle outlets? I see none available in my juistiction (ontario)... Is this because it has to be gfi at the breaker and not allowed at the outlet? It's probably because they can't fit all the electronics into the size of a receptacle. You could change the box to a double and install two gfci outlets, or if you have piles of money to blow, you could get a double pole 15 amp gfci with neutral circuit breaker |
#3
Posted to alt.home.repair
|
|||
|
|||
Split Receptacle GFI outlet. Do they exist?
On Sep 16, 8:50*pm, "The Henchman" wrote:
Got a 15 amp split receptable mounted on a studded basement wall for a washing machine and gas dryer. * I want to install a laundry tub about 4 feet away. *Code here says that outlet has go to be gfci *(1.5 metres or about 4.5 feet from the "sink") but I cannot find any 15 amp split receptacle gfi outlets. * The wire is 14/3 so I can't do like the kitchen 20 amp near the sinks... are there 15 amp gfi split receptacle outlets? *I see none available in my juistiction (ontario)... * Is this because it has to be gfi at the breaker and not allowed at the outlet? As far as I know, they don't exist. Here are some thoughts: 1 - Any reason you can't use one GFCI for both? Why is the current outlet split? I've been running a washing machine and gas dryer off of a single 15 amp receptacle for years. It's on the same circuit as the receptacle we use to iron. We've never had a problem using all three appliances at the same time. 2 - How hard would it be to add a second receptacle (2 GFCI's) in the same location? 3 - Why not leave the current receptacle in place and use a 2 pole GFCI breaker? http://www.electricsuppliesonline.co...t-breaker.html 4 - I've heard of this solution, although I'll say right up front that I don't know if it's code compliant - or could be made code compliant by ganging 2 breakers: Install 2 GFCI's someplace else and wire the top of the split to one GFCI and the bottom to the other. Again, I don't know if that is doable per code, but I've heard of it being done to split receptacles in a kitchen. |
#4
Posted to alt.home.repair
|
|||
|
|||
Split Receptacle GFI outlet. Do they exist?
"RBM" wrote in message ... "The Henchman" wrote in message ... Got a 15 amp split receptable mounted on a studded basement wall for a washing machine and gas dryer. I want to install a laundry tub about 4 feet away. Code here says that outlet has go to be gfci (1.5 metres or about 4.5 feet from the "sink") but I cannot find any 15 amp split receptacle gfi outlets. The wire is 14/3 so I can't do like the kitchen 20 amp near the sinks... are there 15 amp gfi split receptacle outlets? I see none available in my juistiction (ontario)... Is this because it has to be gfi at the breaker and not allowed at the outlet? It's probably because they can't fit all the electronics into the size of a receptacle. You could change the box to a double and install two gfci outlets, or if you have piles of money to blow, you could get a double pole 15 amp gfci with neutral circuit breaker It's a single 14/3 wire. How do I wire that single splt receptacle into two receptacle in a single double box? |
#5
Posted to alt.home.repair
|
|||
|
|||
Split Receptacle GFI outlet. Do they exist?
"The Henchman" wrote in message ... "RBM" wrote in message ... "The Henchman" wrote in message ... Got a 15 amp split receptable mounted on a studded basement wall for a washing machine and gas dryer. I want to install a laundry tub about 4 feet away. Code here says that outlet has go to be gfci (1.5 metres or about 4.5 feet from the "sink") but I cannot find any 15 amp split receptacle gfi outlets. The wire is 14/3 so I can't do like the kitchen 20 amp near the sinks... are there 15 amp gfi split receptacle outlets? I see none available in my juistiction (ontario)... Is this because it has to be gfi at the breaker and not allowed at the outlet? It's probably because they can't fit all the electronics into the size of a receptacle. You could change the box to a double and install two gfci outlets, or if you have piles of money to blow, you could get a double pole 15 amp gfci with neutral circuit breaker It's a single 14/3 wire. How do I wire that single splt receptacle into two receptacle in a single double box? You share the neutral between both receptacles, typically by using pigtails |
#6
Posted to alt.home.repair
|
|||
|
|||
Split Receptacle GFI outlet. Do they exist?
As far as I know, they don't exist.
Here are some thoughts: 1 - Any reason you can't use one GFCI for both? Why is the current outlet split? I've been running a washing machine and gas dryer off of a single 15 amp receptacle for years. It's on the same circuit as the receptacle we use to iron. We've never had a problem using all three appliances at the same time. Too late. It's already wired 14/3. The reason this is split receptacle is the washing machine is a 4.6 cubic foot front load machine that has a 1100 w heating element as well. It's some sort of futuristic front loading NASA type bull**** appliance that claims it's more efficient to heat water while it washes rather than pull warm water from the water tank. In fairness the this washer uses 15 gallons or water per full load of laundry rather than the typical 50 gallons and it averages at least 1 hour per load instead of the typical 35 minutes per load. The washing machine calls for 11A The really large gas dryer calls for 6 A. GE appliances of Canada actually recommends in it book that these two appliances if used in a pair must either be on a 20 amp circuit or two 15 amp circuits. 2 - How hard would it be to add a second receptacle (2 GFCI's) in the same location? Not hard. Would have to find a current circuit and have it end for the dryer maybe since it only maxes 6 amps (I can do this myself) or easily;\ snake new wire to the panel box for one of the many empty breakers but I am deathly afraid of touching wires in my own panel boxes and would have to call an electrician to wire into the box because of my fear. However it is currently 14-3 wire right now at the split. What do I do with the red wire 3 - Why not leave the current receptacle in place and use a 2 pole GFCI breaker? http://www.electricsuppliesonline.co...t-breaker.html easiest solution at this point. 4 - I've heard of this solution, although I'll say right up front that I don't know if it's code compliant - or could be made code compliant by ganging 2 breakers: Install 2 GFCI's someplace else and wire the top of the split to one GFCI and the bottom to the other. Again, I don't know if that is doable per code, but I've heard of it being done to split receptacles in a kitchen. Our panel box is getting changed as we speak. An electrical inspector is inspecting all work \before the utility is allow to turn electricity back on. If it's grey area for code, we could be in trouble.... Number 3 is the best bet right now...... |
#7
Posted to alt.home.repair
|
|||
|
|||
Split Receptacle GFI outlet. Do they exist?
On Sep 16, 9:18*pm, "RBM" wrote:
"The Henchman" wrote in message ... Got a 15 amp split receptable mounted on a studded basement wall for a washing machine and gas dryer. * I want to install a laundry tub about 4 feet away. *Code here says that outlet has go to be gfci *(1.5 metres or about 4.5 feet from the "sink") but I cannot find any 15 amp split receptacle gfi outlets. * The wire is 14/3 so I can't do like the kitchen 20 amp near the sinks... are there 15 amp gfi split receptacle outlets? *I see none available in my juistiction (ontario)... * Is this because it has to be gfi at the breaker and not allowed at the outlet? It's probably because they can't fit all the electronics into the size of a receptacle. You could change the box to a double and install two gfci outlets, or if you have piles of money to blow, you could get a double pole 15 amp gfci with neutral circuit breaker "if you have piles of money to blow, you could get a double pole 15 amp gfci with neutral circuit breaker" RBM...serious question...since you know a lot more about this than me... Everybody's idea of a "pile" is different. This link shows a 15 amp 2 pole GFCI breaker for $25. http://www.electricsuppliesonline.co...t-breaker.html Do you consider that a "pile of money" or is that not the type of breaker you were referring to? Wouldn't 2 GFCI's, a double box and face plate cost close to that - and take a lot more work to install? |
#8
Posted to alt.home.repair
|
|||
|
|||
Split Receptacle GFI outlet. Do they exist?
It's a single 14/3 wire. How do I wire that single splt receptacle into two receptacle in a single double box? You share the neutral between both receptacles, typically by using pigtails neutral is white correct? so I run a shoirt pig tail from one recpet to the other. Red wire goes hot onto first recept and black wire goes hot into recpt number 2? anything about the grounding I would have to consider? I can use gfi outlets using this scenario? |
#9
Posted to alt.home.repair
|
|||
|
|||
Split Receptacle GFI outlet. Do they exist?
"The Henchman" wrote in message ... It's a single 14/3 wire. How do I wire that single splt receptacle into two receptacle in a single double box? You share the neutral between both receptacles, typically by using pigtails neutral is white correct? so I run a shoirt pig tail from one recpet to the other. Red wire goes hot onto first recept and black wire goes hot into recpt number 2? anything about the grounding I would have to consider? I can use gfi outlets using this scenario? You got it, and just ground both receptacles as you would normally |
#10
Posted to alt.home.repair
|
|||
|
|||
Split Receptacle GFI outlet. Do they exist?
"DerbyDad03" wrote in message ... On Sep 16, 9:18 pm, "RBM" wrote: "The Henchman" wrote in message ... Got a 15 amp split receptable mounted on a studded basement wall for a washing machine and gas dryer. I want to install a laundry tub about 4 feet away. Code here says that outlet has go to be gfci (1.5 metres or about 4.5 feet from the "sink") but I cannot find any 15 amp split receptacle gfi outlets. The wire is 14/3 so I can't do like the kitchen 20 amp near the sinks... are there 15 amp gfi split receptacle outlets? I see none available in my juistiction (ontario)... Is this because it has to be gfi at the breaker and not allowed at the outlet? It's probably because they can't fit all the electronics into the size of a receptacle. You could change the box to a double and install two gfci outlets, or if you have piles of money to blow, you could get a double pole 15 amp gfci with neutral circuit breaker "if you have piles of money to blow, you could get a double pole 15 amp gfci with neutral circuit breaker" RBM...serious question...since you know a lot more about this than me... Everybody's idea of a "pile" is different. This link shows a 15 amp 2 pole GFCI breaker for $25. http://www.electricsuppliesonline.co...t-breaker.html Do you consider that a "pile of money" or is that not the type of breaker you were referring to? Wouldn't 2 GFCI's, a double box and face plate cost close to that - and take a lot more work to install? The breaker you link to is just a standard 2 pole 15 amp. If you scrounge around that site, you'll find the 2 pole 15 amp gfci, which is $145 |
#11
Posted to alt.home.repair
|
|||
|
|||
Split Receptacle GFI outlet. Do they exist?
"The Henchman" wrote in message ... Got a 15 amp split receptable mounted on a studded basement wall for a washing machine and gas dryer. I want to install a laundry tub about 4 feet away. Code here says that outlet has go to be gfci (1.5 metres or about 4.5 feet from the "sink") but I cannot find any 15 amp split receptacle gfi outlets. The wire is 14/3 so I can't do like the kitchen 20 amp near the sinks... are there 15 amp gfi split receptacle outlets? I see none available in my juistiction (ontario)... Is this because it has to be gfi at the breaker and not allowed at the outlet? Moot point I just found out. Ge Appliances of Canada answered my email in 35 minutes time about the use of GFI/GFCI for their gas dryer. They do NOT recommend any of their large appliances, esp gas stoves, gas ranges and gas dryers be used with gfi because the igniters in these appliances will always have a small "leak to ground" that will trip the gfi. In their email they also included water softeners, microwaves and teevee monitors not be connected to gfi. so much for all of our ideas. Sorry for getting everyone all worked up on my question.... |
#12
Posted to alt.home.repair
|
|||
|
|||
Split Receptacle GFI outlet. Do they exist?
"The Henchman" wrote in message ... "The Henchman" wrote in message ... Got a 15 amp split receptable mounted on a studded basement wall for a washing machine and gas dryer. I want to install a laundry tub about 4 feet away. Code here says that outlet has go to be gfci (1.5 metres or about 4.5 feet from the "sink") but I cannot find any 15 amp split receptacle gfi outlets. The wire is 14/3 so I can't do like the kitchen 20 amp near the sinks... are there 15 amp gfi split receptacle outlets? I see none available in my juistiction (ontario)... Is this because it has to be gfi at the breaker and not allowed at the outlet? Moot point I just found out. Ge Appliances of Canada answered my email in 35 minutes time about the use of GFI/GFCI for their gas dryer. They do NOT recommend any of their large appliances, esp gas stoves, gas ranges and gas dryers be used with gfi because the igniters in these appliances will always have a small "leak to ground" that will trip the gfi. In their email they also included water softeners, microwaves and teevee monitors not be connected to gfi. so much for all of our ideas. Sorry for getting everyone all worked up on my question.... Does the CEC require the outlet in that location to be gfci protected? I know in the US, the NEC couldn't give a hoot about any appliance manufacturers recommendations |
#13
Posted to alt.home.repair
|
|||
|
|||
Split Receptacle GFI outlet. Do they exist?
Does the CEC require the outlet in that location to be gfci protected? I know in the US, the NEC couldn't give a hoot about any appliance manufacturers recommendations The only code I could find was that any outlet within 4.5 feet (1.5 meters) near a sink or tub must be gfci protected. There are specific instructions for small bathrooms. The new laundry tub is 3 foot 6 from the outlet, whatever that is in the metric system they use here. |
#14
Posted to alt.home.repair
|
|||
|
|||
Split Receptacle GFI outlet. Do they exist?
On 9/16/2010 9:20 PM, The Henchman wrote:
"The Henchman" wrote in message ... Got a 15 amp split receptable mounted on a studded basement wall for a washing machine and gas dryer. I want to install a laundry tub about 4 feet away. Code here says that outlet has go to be gfci (1.5 metres or about 4.5 feet from the "sink") but I cannot find any 15 amp split receptacle gfi outlets. The wire is 14/3 so I can't do like the kitchen 20 amp near the sinks... are there 15 amp gfi split receptacle outlets? I see none available in my juistiction (ontario)... Is this because it has to be gfi at the breaker and not allowed at the outlet? Moot point I just found out. Ge Appliances of Canada answered my email in 35 minutes time about the use of GFI/GFCI for their gas dryer. They do NOT recommend any of their large appliances, esp gas stoves, gas ranges and gas dryers be used with gfi because the igniters in these appliances will always have a small "leak to ground" that will trip the gfi. In their email they also included water softeners, microwaves and teevee monitors not be connected to gfi. so much for all of our ideas. Sorry for getting everyone all worked up on my question.... actually, anything with a motor should not be plugged into a gfci. -- Steve Barker remove the "not" from my address to email |
#15
Posted to alt.home.repair
|
|||
|
|||
Split Receptacle GFI outlet. Do they exist?
On Sep 16, 10:12*pm, "RBM" wrote:
"DerbyDad03" wrote in message ... On Sep 16, 9:18 pm, "RBM" wrote: "The Henchman" wrote in message ... Got a 15 amp split receptable mounted on a studded basement wall for a washing machine and gas dryer. I want to install a laundry tub about 4 feet away. Code here says that outlet has go to be gfci (1.5 metres or about 4.5 feet from the "sink") but I cannot find any 15 amp split receptacle gfi outlets. The wire is 14/3 so I can't do like the kitchen 20 amp near the sinks... are there 15 amp gfi split receptacle outlets? I see none available in my juistiction (ontario)... Is this because it has to be gfi at the breaker and not allowed at the outlet? It's probably because they can't fit all the electronics into the size of a receptacle. You could change the box to a double and install two gfci outlets, or if you have piles of money to blow, you could get a double pole 15 amp gfci with neutral circuit breaker "if you have piles of money to blow, you could get a double pole 15 amp gfci with neutral circuit breaker" RBM...serious question...since you know a lot more about this than me... Everybody's idea of a "pile" is different. This link shows a 15 amp 2 pole GFCI breaker for $25. http://www.electricsuppliesonline.co...t-breaker.html Do you consider that a "pile of money" or is that not the type of breaker you were referring to? Wouldn't 2 GFCI's, a double box and face plate cost close to that - and take a lot more work to install? The breaker you link to is just a standard 2 pole 15 amp. If you scrounge around that site, you'll find the 2 pole 15 amp gfci, which is $145 Crabby website! The page for the GFCI breaker shows a picture and specs on the GFCI breaker on top and then a table of part numbers just below that. I clicked on the 15 amp 1-pack and didn't even realize it had taken me to a totally different page. |
#16
Posted to alt.home.repair
|
|||
|
|||
Split Receptacle GFI outlet. Do they exist?
On Sep 16, 10:43*pm, "The Henchman" wrote:
Does the CEC require the outlet in that location to be gfci protected? I know in the US, the NEC couldn't give a hoot about any appliance manufacturers recommendations The only code I could find was that any outlet within 4.5 feet (1.5 meters) near a sink or tub must be gfci protected. *There are specific instructions for small bathrooms. * The new laundry tub is 3 foot 6 from the outlet, whatever that is in the metric system they use here. Stupid question...if you move the outlet 1 foot will the cords still reach? |
#17
Posted to alt.home.repair
|
|||
|
|||
Split Receptacle GFI outlet. Do they exist?
On 2010-09-17, Steve Barker wrote:
actually, anything with a motor should not be plugged into a gfci. Outdated conventional wisdom. Current version: motor appliance manufacturers need to build their motors so that the leakage current is low enough not to trip a 5ma GFCI. I think the UL standard may be 0.5ma allowable leakage current, not sure. Cheers, Wayne |
#18
Posted to alt.home.repair
|
|||
|
|||
Split Receptacle GFI outlet. Do they exist?
"Wayne Whitney" wrote in message ... On 2010-09-17, Steve Barker wrote: actually, anything with a motor should not be plugged into a gfci. Outdated conventional wisdom. Current version: motor appliance manufacturers need to build their motors so that the leakage current is low enough not to trip a 5ma GFCI. I think the UL standard may be 0.5ma allowable leakage current, not sure. Cheers, Wayne GE's email response seem to focus on the gas igniters of their appliance more than anything maybe maybe that's because they custom answered my question. Here's a question for you. I have a 15 amp outdoor gfi outlet that I want to use power tools on such as 13 amp table saws and 15 cicrular saws and the like. what potential leak to ground can be from those motors? |
#19
Posted to alt.home.repair
|
|||
|
|||
Split Receptacle GFI outlet. Do they exist?
"The Henchman" wrote in message ... "Wayne Whitney" wrote in message ... On 2010-09-17, Steve Barker wrote: actually, anything with a motor should not be plugged into a gfci. Outdated conventional wisdom. Current version: motor appliance manufacturers need to build their motors so that the leakage current is low enough not to trip a 5ma GFCI. I think the UL standard may be 0.5ma allowable leakage current, not sure. Cheers, Wayne GE's email response seem to focus on the gas igniters of their appliance more than anything maybe maybe that's because they custom answered my question. Here's a question for you. I have a 15 amp outdoor gfi outlet that I want to use power tools on such as 13 amp table saws and 15 cicrular saws and the like. what potential leak to ground can be from those motors? If they're in proper working condition, there shouldn't be any. This is also Wayne's point, at least in the US, the manufacturers are responsible for building their stuff to the latest safety standards, so they will work reliably with gfci protection |
#20
Posted to alt.home.repair
|
|||
|
|||
Split Receptacle GFI outlet. Do they exist?
On Sep 17, 5:30*am, "The Henchman" wrote:
"Wayne Whitney" wrote in message ... On 2010-09-17, Steve Barker wrote: actually, anything with a motor should not be plugged into a gfci. Outdated conventional wisdom. Current version: motor appliance manufacturers need to build their motors so that the leakage current is low enough not to trip a 5ma GFCI. *I think the UL standard may be 0.5ma allowable leakage current, not sure. Cheers, Wayne GE's email response seem to focus on the gas igniters of their appliance more than anything maybe maybe that's because they custom answered my question. Here's a question for you. * *I have a 15 amp outdoor gfi outlet that I want to use power tools on such as 13 amp table saws and 15 cicrular saws and the like. * what potential leak to ground can be from those motors? "use power tools on such as 13 amp table saws and 15 cicrular saws" You have 15 circular saws? Wow! ;-) I've been using corded hand tools on GFCI's for a couple of decades and as far as I recall, none of them have ever tripped the receptacle. |
#21
Posted to alt.home.repair
|
|||
|
|||
Split Receptacle GFI outlet. Do they exist?
On Thu, 16 Sep 2010 20:50:17 -0400, "The Henchman"
wrote: Got a 15 amp split receptable mounted on a studded basement wall for a washing machine and gas dryer. I want to install a laundry tub about 4 feet away. Code here says that outlet has go to be gfci (1.5 metres or about 4.5 feet from the "sink") but I cannot find any 15 amp split receptacle gfi outlets. The wire is 14/3 so I can't do like the kitchen 20 amp near the sinks... are there 15 amp gfi split receptacle outlets? I see none available in my juistiction (ontario)... Is this because it has to be gfi at the breaker and not allowed at the outlet? Not sure of current codes, but code used to allow a dedicated (single) outlet to serve utilization equipment in a GFI mandated distance. Code also used to require a 20 amp laundry circuit. Your inspector will have the required information. -- Mr.E |
#22
Posted to alt.home.repair
|
|||
|
|||
Split Receptacle GFI outlet. Do they exist?
RBM wrote:
"The Henchman" wrote in message ... "Wayne Whitney" wrote in message ... On 2010-09-17, Steve Barker wrote: actually, anything with a motor should not be plugged into a gfci. Outdated conventional wisdom. Current version: motor appliance manufacturers need to build their motors so that the leakage current is low enough not to trip a 5ma GFCI. I think the UL standard may be 0.5ma allowable leakage current, not sure. Cheers, Wayne GE's email response seem to focus on the gas igniters of their appliance more than anything maybe maybe that's because they custom answered my question. Here's a question for you. I have a 15 amp outdoor gfi outlet that I want to use power tools on such as 13 amp table saws and 15 cicrular saws and the like. what potential leak to ground can be from those motors? If they're in proper working condition, there shouldn't be any. This is also Wayne's point, at least in the US, the manufacturers are responsible for building their stuff to the latest safety standards, so they will work reliably with gfci protection Or, conversely, the code probably wouldn't be changed to not work with the way equipment is built. I agree with RBM and Wayne. Temporary receptacles at construction sites generally have to be GFCI protected. The power tools used by construction workers better not trip a GFCI. Receptacles for 15/20A 120V refrigerators and freezers in commercial kitchens have to be GFCI protected. It would be easy to construct a spark ignitor on the secondary of a transformer, so there is no ground leakage on the supply wires. -- bud-- |
#23
Posted to alt.home.repair
|
|||
|
|||
Split Receptacle GFI outlet. Do they exist?
On Sep 16, 10:50*pm, Steve Barker wrote:
On 9/16/2010 9:20 PM, The Henchman wrote: "The Henchman" wrote in message ... Got a 15 amp split receptable mounted on a studded basement wall for a washing machine and gas dryer. I want to install a laundry tub about 4 feet away. Code here says that outlet has go to be gfci (1.5 metres or about 4.5 feet from the "sink") but I cannot find any 15 amp split receptacle gfi outlets. The wire is 14/3 so I can't do like the kitchen 20 amp near the sinks... are there 15 amp gfi split receptacle outlets? I see none available in my juistiction (ontario)... Is this because it has to be gfi at the breaker and not allowed at the outlet? Moot point I just found out. Ge Appliances of Canada answered my email in 35 minutes time about the use of GFI/GFCI for their gas dryer. They do NOT recommend any of their large appliances, esp gas stoves, gas ranges and gas dryers be used with gfi because the igniters in these appliances will always have a small "leak to ground" that will trip the gfi. In their email they also included water softeners, microwaves and teevee monitors not be connected to gfi. so much for all of our ideas. Sorry for getting everyone all worked up on my question.... actually, anything with a motor should not be plugged into a gfci. -- Steve Barker remove the "not" from my address to email- Hide quoted text - - Show quoted text - The NEC specifically calls for pool pump motors to be GFCI protected. Some of those are used on cords/plugs to facilitate easy removal. |
#24
Posted to alt.home.repair
|
|||
|
|||
Split Receptacle GFI outlet. Do they exist?
On Sep 17, 10:33*am, bud-- wrote:
RBM wrote: "The Henchman" wrote in message ... "Wayne Whitney" wrote in message ... On 2010-09-17, Steve Barker wrote: actually, anything with a motor should not be plugged into a gfci. Outdated conventional wisdom. Current version: motor appliance manufacturers need to build their motors so that the leakage current is low enough not to trip a 5ma GFCI. *I think the UL standard may be 0.5ma allowable leakage current, not sure. Cheers, Wayne GE's email response seem to focus on the gas igniters of their appliance more than anything maybe maybe that's because they custom answered my question. Here's a question for you. * *I have a 15 amp outdoor gfi outlet that I want to use power tools on such as 13 amp table saws and 15 cicrular saws and the like. * what potential leak to ground can be from those motors? If they're in proper working condition, there shouldn't be any. This is also Wayne's point, at least in the US, the manufacturers are responsible for building their stuff to the latest safety standards, so they will work reliably with gfci protection Or, conversely, the code probably wouldn't be changed to not work with the way equipment is built. I agree with RBM and Wayne. Temporary receptacles at construction sites generally have to be GFCI protected. The power tools used by construction workers better not trip a GFCI. Receptacles for 15/20A 120V refrigerators and freezers in commercial kitchens have to be GFCI protected. It would be easy to construct a spark ignitor on the secondary of a transformer, so there is no ground leakage on the supply wires. -- bud--- Hide quoted text - - Show quoted text - Or just use a hot surface ignitor. I don't see why an appliance manufacturer can't build a dryer within leakage current limits of GFCI either. |
#25
Posted to alt.home.repair
|
|||
|
|||
Split Receptacle GFI outlet. Do they exist?
On Sep 17, 10:08*am, wrote:
On Sep 17, 10:33*am, bud-- wrote: RBM wrote: "The Henchman" wrote in message ... "Wayne Whitney" wrote in message ... On 2010-09-17, Steve Barker wrote: actually, anything with a motor should not be plugged into a gfci. Outdated conventional wisdom. Current version: motor appliance manufacturers need to build their motors so that the leakage current is low enough not to trip a 5ma GFCI. *I think the UL standard may be 0.5ma allowable leakage current, not sure. Cheers, Wayne GE's email response seem to focus on the gas igniters of their appliance more than anything maybe maybe that's because they custom answered my question. Here's a question for you. * *I have a 15 amp outdoor gfi outlet that I want to use power tools on such as 13 amp table saws and 15 cicrular saws and the like. * what potential leak to ground can be from those motors? If they're in proper working condition, there shouldn't be any. This is also Wayne's point, at least in the US, the manufacturers are responsible for building their stuff to the latest safety standards, so they will work reliably with gfci protection Or, conversely, the code probably wouldn't be changed to not work with the way equipment is built. I agree with RBM and Wayne. Temporary receptacles at construction sites generally have to be GFCI protected. The power tools used by construction workers better not trip a GFCI. Receptacles for 15/20A 120V refrigerators and freezers in commercial kitchens have to be GFCI protected. It would be easy to construct a spark ignitor on the secondary of a transformer, so there is no ground leakage on the supply wires. -- bud--- Hide quoted text - - Show quoted text - Or just use a hot surface ignitor. *I don't see why an appliance manufacturer can't build a dryer within leakage current limits of GFCI either. They can, if the customer uses a 4-wire connection. Otherwise, any 120V stuff in the dryer is connected to ground and there will be (a lot of) leakage. 3-Wire (hot, hot, ground) used to be code, but now 4- wire connections (hot-hot-neutral-ground) are required where any 120V circuits are used. The 3-wire connections are grandfathered for existing structures. |
#26
Posted to alt.home.repair
|
|||
|
|||
Split Receptacle GFI outlet. Do they exist?
|
#27
Posted to alt.home.repair
|
|||
|
|||
Split Receptacle GFI outlet. Do they exist?
On Sep 17, 11:53*am, keith wrote:
On Sep 17, 10:08*am, wrote: On Sep 17, 10:33*am, bud-- wrote: RBM wrote: "The Henchman" wrote in message ... "Wayne Whitney" wrote in message ... On 2010-09-17, Steve Barker wrote: actually, anything with a motor should not be plugged into a gfci. Outdated conventional wisdom. Current version: motor appliance manufacturers need to build their motors so that the leakage current is low enough not to trip a 5ma GFCI. *I think the UL standard may be 0.5ma allowable leakage current, not sure. Cheers, Wayne GE's email response seem to focus on the gas igniters of their appliance more than anything maybe maybe that's because they custom answered my question. Here's a question for you. * *I have a 15 amp outdoor gfi outlet that I want to use power tools on such as 13 amp table saws and 15 cicrular saws and the like. * what potential leak to ground can be from those motors? If they're in proper working condition, there shouldn't be any. This is also Wayne's point, at least in the US, the manufacturers are responsible for building their stuff to the latest safety standards, so they will work reliably with gfci protection Or, conversely, the code probably wouldn't be changed to not work with the way equipment is built. I agree with RBM and Wayne. Temporary receptacles at construction sites generally have to be GFCI protected. The power tools used by construction workers better not trip a GFCI. Receptacles for 15/20A 120V refrigerators and freezers in commercial kitchens have to be GFCI protected. It would be easy to construct a spark ignitor on the secondary of a transformer, so there is no ground leakage on the supply wires. -- bud--- Hide quoted text - - Show quoted text - Or just use a hot surface ignitor. *I don't see why an appliance manufacturer can't build a dryer within leakage current limits of GFCI either. They can, if the customer uses a 4-wire connection. *Otherwise, any 120V stuff in the dryer is connected to ground and there will be (a lot of) leakage. *3-Wire (hot, hot, ground) used to be code, but now 4- wire connections (hot-hot-neutral-ground) are required where any 120V circuits are used. *The 3-wire connections are grandfathered for existing structures.- Hide quoted text - - Show quoted text - In the context of the discussion, clearly it's a gas dryer we're talking about that uses 120V. But broadening the discussion, why does there have to be any 120V "stuff" in a dryer, including a 240V electric one? I see you're point regarding backward compatibility to an existing 3 wire dryer circuit. But in any dryer there is a heating element if it's an electric one, a motor, and some control circuitry. I can design all of that using just 240V. The only thing I can think of that would ordinarily be a 120v load would be a light inside the dryer. But it would seem someone must make a 240V appliance bulb, no? |
#28
Posted to alt.home.repair
|
|||
|
|||
Split Receptacle GFI outlet. Do they exist?
On Sep 17, 2:51*pm, wrote:
On Sep 17, 11:53*am, keith wrote: On Sep 17, 10:08*am, wrote: On Sep 17, 10:33*am, bud-- wrote: RBM wrote: "The Henchman" wrote in message ... "Wayne Whitney" wrote in message ... On 2010-09-17, Steve Barker wrote: actually, anything with a motor should not be plugged into a gfci. Outdated conventional wisdom. Current version: motor appliance manufacturers need to build their motors so that the leakage current is low enough not to trip a 5ma GFCI. *I think the UL standard may be 0.5ma allowable leakage current, not sure. Cheers, Wayne GE's email response seem to focus on the gas igniters of their appliance more than anything maybe maybe that's because they custom answered my question. Here's a question for you. * *I have a 15 amp outdoor gfi outlet that I want to use power tools on such as 13 amp table saws and 15 cicrular saws and the like. * what potential leak to ground can be from those motors? If they're in proper working condition, there shouldn't be any. This is also Wayne's point, at least in the US, the manufacturers are responsible for building their stuff to the latest safety standards, so they will work reliably with gfci protection Or, conversely, the code probably wouldn't be changed to not work with the way equipment is built. I agree with RBM and Wayne. Temporary receptacles at construction sites generally have to be GFCI protected. The power tools used by construction workers better not trip a GFCI. Receptacles for 15/20A 120V refrigerators and freezers in commercial kitchens have to be GFCI protected. It would be easy to construct a spark ignitor on the secondary of a transformer, so there is no ground leakage on the supply wires. -- bud--- Hide quoted text - - Show quoted text - Or just use a hot surface ignitor. *I don't see why an appliance manufacturer can't build a dryer within leakage current limits of GFCI either. They can, if the customer uses a 4-wire connection. *Otherwise, any 120V stuff in the dryer is connected to ground and there will be (a lot of) leakage. *3-Wire (hot, hot, ground) used to be code, but now 4- wire connections (hot-hot-neutral-ground) are required where any 120V circuits are used. *The 3-wire connections are grandfathered for existing structures.- Hide quoted text - - Show quoted text - In the context of the discussion, clearly it's a gas dryer we're talking about that uses 120V. * *But broadening the discussion, why does there have to be any 120V "stuff" in a dryer, including a 240V electric one? *I see you're point regarding backward compatibility to an existing 3 wire dryer circuit. *But in any dryer there is a heating element if it's an electric one, a motor, and some control circuitry. * I can design all of that using just 240V. *The only thing I can think of that would ordinarily be a 120v load would be a light inside the dryer. * But it would seem someone must make a 240V appliance bulb, no?- Hide quoted text - - Show quoted text - Bulb, "I'm done" Buzzer, Timer/Control, LEDs, Liquid Crystal display, things that go 'beep" when you turn the knob, etc. While all of them can be implemented with 240V, I'll bet it's cheaper to design and implement for 120V and then use the same circuity for both gas and electric. You gotta have 120V dryers for those of us who use gas and don't have 240V in the laundry area. |
#29
Posted to alt.home.repair
|
|||
|
|||
Split Receptacle GFI outlet. Do they exist?
On Sep 16, 8:50*pm, "The Henchman" wrote:
Got a 15 amp split receptable mounted on a studded basement wall for a washing machine and gas dryer. * I want to install a laundry tub about 4 feet away. *Code here says that outlet has go to be gfci *(1.5 metres or about 4.5 feet from the "sink") but I cannot find any 15 amp split receptacle gfi outlets. * The wire is 14/3 so I can't do like the kitchen 20 amp near the sinks... are there 15 amp gfi split receptacle outlets? *I see none available in my juistiction (ontario)... * Is this because it has to be gfi at the breaker and not allowed at the outlet? I would find where the outlets are being fed from. If from another outlet then change that one to GFCI. If directly from the panel install a GFCI breaker in the panel.. Jimmie |
#30
Posted to alt.home.repair
|
|||
|
|||
Split Receptacle GFI outlet. Do they exist?
|
#31
Posted to alt.home.repair
|
|||
|
|||
Split Receptacle GFI outlet. Do they exist?
On Sep 17, 3:12*pm, DerbyDad03 wrote:
On Sep 17, 2:51*pm, wrote: On Sep 17, 11:53*am, keith wrote: On Sep 17, 10:08*am, wrote: On Sep 17, 10:33*am, bud-- wrote: RBM wrote: "The Henchman" wrote in message ... "Wayne Whitney" wrote in message ... On 2010-09-17, Steve Barker wrote: actually, anything with a motor should not be plugged into a gfci. Outdated conventional wisdom. Current version: motor appliance manufacturers need to build their motors so that the leakage current is low enough not to trip a 5ma GFCI. *I think the UL standard may be 0.5ma allowable leakage current, not sure. Cheers, Wayne GE's email response seem to focus on the gas igniters of their appliance more than anything maybe maybe that's because they custom answered my question. Here's a question for you. * *I have a 15 amp outdoor gfi outlet that I want to use power tools on such as 13 amp table saws and 15 cicrular saws and the like. * what potential leak to ground can be from those motors? If they're in proper working condition, there shouldn't be any. This is also Wayne's point, at least in the US, the manufacturers are responsible for building their stuff to the latest safety standards, so they will work reliably with gfci protection Or, conversely, the code probably wouldn't be changed to not work with the way equipment is built. I agree with RBM and Wayne. Temporary receptacles at construction sites generally have to be GFCI protected. The power tools used by construction workers better not trip a GFCI. Receptacles for 15/20A 120V refrigerators and freezers in commercial kitchens have to be GFCI protected. It would be easy to construct a spark ignitor on the secondary of a transformer, so there is no ground leakage on the supply wires. -- bud--- Hide quoted text - - Show quoted text - Or just use a hot surface ignitor. *I don't see why an appliance manufacturer can't build a dryer within leakage current limits of GFCI either. They can, if the customer uses a 4-wire connection. *Otherwise, any 120V stuff in the dryer is connected to ground and there will be (a lot of) leakage. *3-Wire (hot, hot, ground) used to be code, but now 4- wire connections (hot-hot-neutral-ground) are required where any 120V circuits are used. *The 3-wire connections are grandfathered for existing structures.- Hide quoted text - - Show quoted text - In the context of the discussion, clearly it's a gas dryer we're talking about that uses 120V. * *But broadening the discussion, why does there have to be any 120V "stuff" in a dryer, including a 240V electric one? *I see you're point regarding backward compatibility to an existing 3 wire dryer circuit. *But in any dryer there is a heating element if it's an electric one, a motor, and some control circuitry. * I can design all of that using just 240V. *The only thing I can think of that would ordinarily be a 120v load would be a light inside the dryer. * But it would seem someone must make a 240V appliance bulb, no?- Hide quoted text - - Show quoted text - Bulb, "I'm done" Buzzer, Timer/Control, LEDs, Liquid Crystal display, things that go 'beep" when you turn the knob, etc. While all of them can be implemented with 240V, I'll bet it's cheaper to design and implement for 120V and then use the same circuity for both gas and electric. You gotta have 120V dryers for those of us who use gas and don't have 240V in the laundry area.- Hide quoted text - - Show quoted text - Most of the stuff on that list, ie LEDs, display, beepers, etc aren't powered by 240V or 120V anyway. You have a transformer that powers them, microprocessor boards, etc. So, if it;s a common design you seek, you could have the same design for 120V gas and 240V electric, just substitute a different transformer. Or use a transformer with multiple taps that would support either. However, I think the design differences between a gas dryer and an electric one are so substantial that you would have so many other design differences that it would render the point moot anyway. |
#32
Posted to alt.home.repair
|
|||
|
|||
Split Receptacle GFI outlet. Do they exist?
|
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Switch + Receptacle thru to Receptacle | Home Repair | |||
is gfci outlet good replacement for two-prong non-grounded outlet ?? | Home Repair | |||
Replacing 1 15 amp Receptacle With 1 20 Receptacle | Home Repair | |||