Higgs Boson wrote:
Lately, one circuit on my box blows. It covers the microwave and regular oven. I could understand it blowing when another heat-using appliance, like toaster oven or toaster runs at same time as microwave. But now it's blowing all on its own. Last time, today, only the micro was being used, to "reduce" a glass dish of chicken drippings. Can one circuit go bad all on its own? If so, why? And what should I do about it. Any info appreciated. Can't you just measure the load? Count how long it takes the wheel on the power meter to go around. Turn on the suspect appliance. Count the wheel again. Calculate the load difference. |
#42
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
On Thu, 5 Aug 2010 12:47:23 -0700 (PDT), Higgs Boson
wrote: all kinds of previou stuff snipped - Is it a 15 amp breaker/circuit? What else is on that circuit. Can he easily avoid any additional load on the MW circuit by moving any other loads to a different circuit, eg plug the toaster into a different outlet. Â*He has answered the second half or your question several times - the clock of the gas oven (which likely draws less than 200 Ma), and the toaster opr toaster oven if he has it plugged in - If he ONLY uses the Microwave, or ONLY uses the toaster, the 15 amp breaker should hold. The only thing to do is to replace the breaker and see what happens. A dedicated 20 amp split countertop receptacle should be installed in the kitchen replacing whatever he is plugging the toaster into, leaving the Microwave and gas oven on the existing circuit. This would give him 2 20 amp circuits to handle toasters, coffeemakers, toaster ovens, etc without danger of tripping breakers from inadvertent overloads - and would get him almost code compliant. (which adding a separate circuit for the microwave would not). The countertop receptacles should be on GFCI protected circuits whereas the microwave and oven are not so critical that way. OMG, now I am more anxious than ever. Why would "adding a separate circuit for the microwave" not get me code compliant? This is a civilian talking, who doesn't know from code. Current code requires split receptacles on the countertop - at least here in Kitchener/Waterloo Ontario. Adding a dedicated line to the microwave won't give you that - while adding the split will give you a "dedicated" line for the microwave (which is allowed, I believe, to also service the gas oven) Also, can you explain "split countertop receptacle"? What is the "split" about? It is a duplex receptacle that has been fed with a 3 wire 220 volt feed, split to 2 110 volt (nominal - I know, generally 230 and 115, but that's just semantics) circuits - also referred to by some on the group as an "edison" circuit, I believe. I went on-line to get a definition, but never did find one as such. Found a number of sites, but all too technical for me. Whatever the job turns out to be, I will have to hire a qualified electrician; this is not a DIY, even with help. Also: You say "The countertop receptacles should be on GFCI protected circuits whereas the microwave and oven are not so critical that way." Can you explain the reason? The microwave and oven are permanetly (more or less) in one place, and generally not within teach of the sink or water taps, whereas the countertop receptacles can feet things like portable mixers etc that can get within reach of the sink - where you could hold a (leaky) appliance in one hand and touch the sink or tap with the other. Without a GFCI you could get a nasty shock. With a GFCI the breaker will trip and you usually will not even get a tickle. Also: Someone in this thread suggested refrigerator cycling on might be causing the trips. I just checked by disabling the breaker governing MW and gas oven, and it does NOT govern the refrig. Last: Would doing the "split countertop receptacle" obviate the necessity of replacing what might be a defective breaker controlling the MW and gas oven, leading to repeated trips? No, like I said, replace the breaker FIRST as it is about 99.999% likely that it is defective, given the scenario described. What make panel do you have? Certain brands are much more succeptible to failure. TIA to all for your continued help! Much appreciated. HB |
#43
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
On Thu, 5 Aug 2010 16:09:27 -0400, "RBM" wrote:
"Higgs Boson" wrote in message ... On Aug 4, 6:14 pm, wrote: On Wed, 4 Aug 2010 11:08:47 -0700 (PDT), wrote: On Aug 4, 8:32 am, jamesgangnc wrote: On Aug 4, 12:37 am, Higgs Boson wrote: On Aug 2, 4:14 am, "RBM" wrote: "Higgs Boson" wrote in message ... On Aug 1, 10:11 am, jeff_wisnia wrote: Higgs Boson wrote: Lately, one circuit on my box blows. It covers the microwave and regular oven. I could understand it blowing when another heat-using appliance, like toaster oven or toaster runs at same time as microwave. But now it's blowing all on its own. Last time, today, only the micro was being used, to "reduce" a glass dish of chicken drippings. Can one circuit go bad all on its own? If so, why? And what should I do about it. Any info appreciated. Since nobody has mentioned this yet and it sounds like it's a kitchen circuit, is the breaker perchance a GFI one? The microwave may have marginal "hot to ground" leakage which sometimes becomes high enough to trip a GFI breaker. If it's not a GFI breaker, then I'll side with those who say, "change the breaker. The breaker box was installed many years ago and I don't have any paper work on it. Is there a way for a non-techie to ascertain whether it is a GFI breaker? Also, is it normal for a near-new MW to have the "marginal "hot to ground" leakage? How do I ascertain this? (Starts to look like an expensive electrician visit...sob...) Jeff -- Jeffry Wisnia (W1BSV + Brass Rat '57 EE) The speed of light is 1.8*10e12 furlongs per fortnight. From your two replies, it sounds like this circuit is not dedicated to the microwave. Is it a 15 or 20 amp circuit? What is the wattage of the microwave? If there is truly nothing else operating simultaneously on the circuit, and it trips, it's most likely a problem with the microwave, or a bad breaker. Have you checked to see if anything else goes out when that circuit trips, such as the refrigerator or something in another room? The microwave is only a few months old, as I mentioned earlier. It is a Sears Kenmore Elite. Here are the specs: Power Supply: 120 V AC, 60 Hz Rated Power Consumption: 1,600 W Microwave Output: 1,200 W Rated Current: 14.0 A You are correct; the circuit is not dedicated to the microwave. As another poster mentioned, older houses don't always have dedicated MW circuits. How do I find out whether it is a 15 or 20 amp circuit? Is this relevant if, as it appears, I will have to have a dedicated MW circuit installed? ******QUESTION: What should such an electrician visit cost, including parts. This is a fairly expensive area, and I am not a fairly expensive homeowner, so I need to budget ahead. Estimates appreciated. In answer to your q. if anything else goes out when the circuit trips: No, just the light panel on the wall oven and the toaster and/or toaster oven IF either happens to be on and pulling juice. Nothing in another room. Your advice much appreciated. As another poster mentioned, older houses don't always have dedic- Hide quoted text - - Show quoted text - By reading the breaker handle. If it is a 15amp circuit then it would be helpful to know how much of the rest of the kitchen is on it. That microwave is going to pull around 12 to 13 amps based on it's 1600 watt label. If you are on a 15amp circuit and the fridge is also on it then your problem is probably that the fridge tries to start up while the microwave is running. I'm also inclined to guess you had a less powerfull microwave before. You can not use other stuff in the kitchen while microwaving but you can't really easily control when the fridge will try to kick in. Upgrading the circuit to 20 amp is not very practical. Running a new dedicated circuit for the microwave would be your simplest solution. How much that costs depends on a lot of variables like distance from the breaker panel and how difficult it will be to run the wire. Where you are factors in as well, some locations are only going to allow a licensed electrician or the homeowner to perform this work. In that case an economical alternative solution is to get a more knowledgable friend to help you diy it. You'd be better off getting some local quotes as far as possible prices go than asking here.- Hide quoted text - - Show quoted text - Agree with the above. The MW is rated at 14 amps, 1600 watts. If it's on a 15 amp breaker, that doesn't leave much for any other load. Which is why with new wiring there is a dedicated circuit for the microwave. Another possible alternative that would be a lot less expensive is finding a MW that is lower power. But first he needs to determine: Is it a 15 amp breaker/circuit? What else is on that circuit. Can he easily avoid any additional load on the MW circuit by moving any other loads to a different circuit, eg plug the toaster into a different outlet. He has answered the second half or your question several times - the clock of the gas oven (which likely draws less than 200 Ma), and the toaster opr toaster oven if he has it plugged in - If he ONLY uses the Microwave, or ONLY uses the toaster, the 15 amp breaker should hold. The only thing to do is to replace the breaker and see what happens. A dedicated 20 amp split countertop receptacle should be installed in the kitchen replacing whatever he is plugging the toaster into, leaving the Microwave and gas oven on the existing circuit. This would give him 2 20 amp circuits to handle toasters, coffeemakers, toaster ovens, etc without danger of tripping breakers from inadvertent overloads - and would get him almost code compliant. (which adding a separate circuit for the microwave would not). The countertop receptacles should be on GFCI protected circuits whereas the microwave and oven are not so critical that way. OMG, now I am more anxious than ever. Why would "adding a separate circuit for the microwave" not get me code compliant? This is a civilian talking, who doesn't know from code. Also, can you explain "split countertop receptacle"? What is the "split" about? I went on-line to get a definition, but never did find one as such. Found a number of sites, but all too technical for me. Whatever the job turns out to be, I will have to hire a qualified electrician; this is not a DIY, even with help. Also: You say "The countertop receptacles should be on GFCI protected circuits whereas the microwave and oven are not so critical that way." Can you explain the reason? Also: Someone in this thread suggested refrigerator cycling on might be causing the trips. I just checked by disabling the breaker governing MW and gas oven, and it does NOT govern the refrig. Last: Would doing the "split countertop receptacle" obviate the necessity of replacing what might be a defective breaker controlling the MW and gas oven, leading to repeated trips? TIA to all for your continued help! Much appreciated. HB A split receptacle is what they do in kitchens in Canada. It's two circuits to one outlet. It's not typically done in the U.S. In the U.S. all kitchen counter top outlets are supposed to be GFCI protected, regardless of what they're used for. All you really need to do to remedy your problem, is run a dedicated 20 amp circuit and outlet for this microwave. Which still leaves him with only one countertop receptacle, which cannot handle both a toaster and a tea kettle - there is a reason Canadian codes are more stringent than US - They make a lot more sense. To remedy the problem and live with the same restrictions he now has, just replace the breaker. If spending the money to add a new circuit - get 2 for just a bit more than the one - the labour will be virtually identical, and the material cost negligibly higher (14/3 or 12/3 instead of 14/2 or 12/2 cable is MABEE 30% more expensive - more likely 15% or so. |
#44
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
Also, can you explain "split countertop receptacle"? What is the
"split" about? I went on-line to get a definition, but never did find one as such. Found a number of sites, but all too technical for me. Whatever the job turns out to be, I will have to hire a qualified electrician; this is not a DIY, even with help. Also: You say "The countertop receptacles should be on GFCI protected circuits whereas the microwave and oven are not so critical that way." Can you explain the reason? Also: Someone in this thread suggested refrigerator cycling on might be causing the trips. I just checked by disabling the breaker governing MW and gas oven, and it does NOT govern the refrig. Last: Would doing the "split countertop receptacle" obviate the necessity of replacing what might be a defective breaker controlling the MW and gas oven, leading to repeated trips? TIA to all for your continued help! Much appreciated. HB A split receptacle is what they do in kitchens in Canada. It's two circuits to one outlet. It's not typically done in the U.S. In the U.S. all kitchen counter top outlets are supposed to be GFCI protected, regardless of what they're used for. All you really need to do to remedy your problem, is run a dedicated 20 amp circuit and outlet for this microwave. Which still leaves him with only one countertop receptacle, which cannot handle both a toaster and a tea kettle - there is a reason Canadian codes are more stringent than US - They make a lot more sense. To remedy the problem and live with the same restrictions he now has, just replace the breaker. If spending the money to add a new circuit - get 2 for just a bit more than the one - the labour will be virtually identical, and the material cost negligibly higher (14/3 or 12/3 instead of 14/2 or 12/2 cable is MABEE 30% more expensive - more likely 15% or so. You have no idea how many receptacles , circuits, or countertops the OP has. What the OP should do, is determine exactly what his problem is, then fix it and not willy nilly replacing parts like a bad mechanic |
#45
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
On Aug 5, 10:57*pm, wrote:
On Thu, 5 Aug 2010 16:09:27 -0400, "RBM" wrote: "Higgs Boson" wrote in message .... On Aug 4, 6:14 pm, wrote: On Wed, 4 Aug 2010 11:08:47 -0700 (PDT), wrote: On Aug 4, 8:32 am, jamesgangnc wrote: On Aug 4, 12:37 am, Higgs Boson wrote: On Aug 2, 4:14 am, "RBM" wrote: "Higgs Boson" wrote in message ... On Aug 1, 10:11 am, jeff_wisnia wrote: Higgs Boson wrote: Lately, one circuit on my box blows. It covers the microwave and regular oven. I could understand it blowing when another heat-using appliance, like toaster oven or toaster runs at same time as microwave. But now it's blowing all on its own. Last time, today, only the micro was being used, to "reduce" a glass dish of chicken drippings. Can one circuit go bad all on its own? If so, why? And what should I do about it. Any info appreciated. Since nobody has mentioned this yet and it sounds like it's a kitchen circuit, is the breaker perchance a GFI one? The microwave may have marginal "hot to ground" leakage which sometimes becomes high enough to trip a GFI breaker. If it's not a GFI breaker, then I'll side with those who say, "change the breaker. The breaker box was installed many years ago and I don't have any paper work on it. Is there a way for a non-techie to ascertain whether it is a GFI breaker? Also, is it normal for a near-new MW to have the "marginal "hot to ground" leakage? How do I ascertain this? (Starts to look like an expensive electrician visit...sob...) Jeff -- Jeffry Wisnia (W1BSV + Brass Rat '57 EE) The speed of light is 1.8*10e12 furlongs per fortnight. From your two replies, it sounds like this circuit is not dedicated to the microwave. Is it a 15 or 20 amp circuit? What is the wattage of the microwave? If there is truly nothing else operating simultaneously on the circuit, and it trips, it's most likely a problem with the microwave, or a bad breaker. Have you checked to see if anything else goes out when that circuit trips, such as the refrigerator or something in another room? The microwave is only a few months old, as I mentioned earlier. It is a Sears Kenmore Elite. Here are the specs: Power Supply: 120 V AC, 60 Hz Rated Power Consumption: 1,600 W Microwave Output: 1,200 W Rated Current: 14.0 A You are correct; the circuit is not dedicated to the microwave. As another poster mentioned, older houses don't always have dedicated MW circuits. How do I find out whether it is a 15 or 20 amp circuit? Is this relevant if, as it appears, I will have to have a dedicated MW circuit installed? ******QUESTION: What should such an electrician visit cost, including parts. This is a fairly expensive area, and I am not a fairly expensive homeowner, so I need to budget ahead. Estimates appreciated. In answer to your q. if anything else goes out when the circuit trips: No, just the light panel on the wall oven and the toaster and/or toaster oven IF either happens to be on and pulling juice. Nothing in another room. Your advice much appreciated. As another poster mentioned, older houses don't always have dedic- Hide quoted text - - Show quoted text - By reading the breaker handle. If it is a 15amp circuit then it would be helpful to know how much of the rest of the kitchen is on it. That microwave is going to pull around 12 to 13 amps based on it's 1600 watt label. If you are on a 15amp circuit and the fridge is also on it then your problem is probably that the fridge tries to start up while the microwave is running. I'm also inclined to guess you had a less powerfull microwave before. You can not use other stuff in the kitchen while microwaving but you can't really easily control when the fridge will try to kick in. Upgrading the circuit to 20 amp is not very practical. Running a new dedicated circuit for the microwave would be your simplest solution.. How much that costs depends on a lot of variables like distance from the breaker panel and how difficult it will be to run the wire. Where you are factors in as well, some locations are only going to allow a licensed electrician or the homeowner to perform this work. In that case an economical alternative solution is to get a more knowledgable friend to help you diy it. You'd be better off getting some local quotes as far as possible prices go than asking here.- Hide quoted text - - Show quoted text - Agree with the above. The MW is rated at 14 amps, 1600 watts. If it's on a 15 amp breaker, that doesn't leave much for any other load. Which is why with new wiring there is a dedicated circuit for the microwave. Another possible alternative that would be a lot less expensive is finding a MW that is lower power. But first he needs to determine: Is it a 15 amp breaker/circuit? What else is on that circuit. Can he easily avoid any additional load on the MW circuit by moving any other loads to a different circuit, eg plug the toaster into a different outlet. He has answered the second half or your question several times - the clock of the gas oven (which likely draws less than 200 Ma), and the toaster opr toaster oven if he has it plugged in - If he ONLY uses the Microwave, or ONLY uses the toaster, the 15 amp breaker should hold. The only thing to do is to replace the breaker and see what happens. A dedicated 20 amp split countertop receptacle should be installed in the kitchen replacing whatever he is plugging the toaster into, leaving the Microwave and gas oven on the existing circuit. This would give him 2 20 amp circuits to handle toasters, coffeemakers, toaster ovens, etc without danger of tripping breakers from inadvertent overloads - and would get him almost code compliant. (which adding a separate circuit for the microwave would not). The countertop receptacles should be on GFCI protected circuits whereas the microwave and oven are not so critical that way. OMG, now I am more anxious than ever. *Why would "adding a separate circuit for the microwave" not get me code compliant? *This is a civilian talking, who doesn't know from code. Also, can you explain "split countertop receptacle"? *What is the "split" about? I went on-line to get a definition, but never did find one as such. Found a number of sites, but all too technical for me. *Whatever the job turns out to be, I will have to hire a qualified electrician; this is not a DIY, even with help. Also: *You say "The countertop receptacles should be on GFCI protected circuits whereas the microwave and oven are not so critical that way." *Can you explain the reason? Also: *Someone in this thread suggested refrigerator cycling on might be causing the trips. I just checked by disabling the breaker governing MW and gas oven, and it does NOT govern the refrig. Last: *Would doing the "split countertop receptacle" obviate the necessity of replacing what might be a defective breaker controlling the MW and gas oven, leading to repeated trips? TIA to all for your continued help! *Much appreciated. HB A split receptacle is what they do in kitchens in Canada. It's two circuits to one outlet. It's not typically done in the U.S. In the U.S. all kitchen counter top outlets are supposed to be GFCI protected, regardless of what they're used for. All you really need to do to remedy your problem, is run a dedicated 20 amp circuit and outlet for this microwave. Which still leaves him with only one countertop receptacle, which cannot handle both a toaster and a tea kettle - there is a reason Canadian codes are more stringent than US - They make a lot more sense. To remedy the problem and live with the same restrictions he now has, just replace the breaker. If spending the money to add a new circuit - get 2 for just a bit *more than the one - the labour will be virtually identical, and the material cost negligibly higher (14/3 or 12/3 instead of 14/2 or 12/2 cable is MABEE 30% more expensive - more likely 15% or so. 12/3 (forget 14/n for this application) is about 60% more but it's still a trivial amount of money compared to the labor of adding another circuit. |
#46
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
On Aug 6, 6:02*am, "RBM" wrote:
Also, can you explain "split countertop receptacle"? *What is the "split" about? I went on-line to get a definition, but never did find one as such. Found a number of sites, but all too technical for me. *Whatever the job turns out to be, I will have to hire a qualified electrician; this is not a DIY, even with help. Also: *You say "The countertop receptacles should be on GFCI protected circuits whereas the microwave and oven are not so critical that way." *Can you explain the reason? Also: *Someone in this thread suggested refrigerator cycling on might be causing the trips. I just checked by disabling the breaker governing MW and gas oven, and it does NOT govern the refrig. Last: *Would doing the "split countertop receptacle" obviate the necessity of replacing what might be a defective breaker controlling the MW and gas oven, leading to repeated trips? TIA to all for your continued help! *Much appreciated. HB A split receptacle is what they do in kitchens in Canada. It's two circuits to one outlet. It's not typically done in the U.S. In the U.S. all kitchen counter top outlets are supposed to be GFCI protected, regardless of what they're used for. All you really need to do to remedy your problem, is run a dedicated 20 amp circuit and outlet for this microwave. Which still leaves him with only one countertop receptacle, which cannot handle both a toaster and a tea kettle - there is a reason Canadian codes are more stringent than US - They make a lot more sense. To remedy the problem and live with the same restrictions he now has, just replace the breaker. If spending the money to add a new circuit - get 2 for just a bit *more than the one - the labour will be virtually identical, and the material cost negligibly higher (14/3 or 12/3 instead of 14/2 or 12/2 cable is MABEE 30% more expensive - more likely 15% or so. You have no idea how many receptacles , circuits, or countertops the OP has. What the OP should do, is determine exactly what his problem is, then fix it and not willy nilly replacing parts like a bad mechanic Often replacing parts is the cheapest solution. If parts cost is trivial compared to labor it's the way to go. It's a lot better advice to give long-distance, too. |
#47
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
On Aug 5, 3:47*pm, Higgs Boson wrote:
On Aug 4, 6:14*pm, wrote: On Wed, 4 Aug 2010 11:08:47 -0700 (PDT), wrote: On Aug 4, 8:32*am, jamesgangnc wrote: On Aug 4, 12:37*am, Higgs Boson wrote: On Aug 2, 4:14*am, "RBM" wrote: "Higgs Boson" wrote in message ... On Aug 1, 10:11 am, jeff_wisnia wrote: Higgs Boson wrote: Lately, one circuit on my box blows. It covers the microwave and regular oven. I could understand it blowing when another heat-using appliance, like toaster oven or toaster runs at same time as microwave. But now it's blowing all on its own. Last time, today, only the micro was being used, to "reduce" a glass dish of chicken drippings. Can one circuit go bad all on its own? If so, why? And what should I do about it. Any info appreciated. Since nobody has mentioned this yet and it sounds like it's a kitchen circuit, is the breaker perchance a GFI one? The microwave may have marginal "hot to ground" leakage which sometimes becomes high enough to trip a GFI breaker. If it's not a GFI breaker, then I'll side with those who say, "change the breaker. The breaker box was installed many years ago and I don't have any paper work on it. *Is there a way for a *non-techie to ascertain whether it is a GFI breaker? Also, is it normal for a near-new MW to have the "marginal "hot to ground" leakage? * How do I ascertain this? (Starts to look like an expensive electrician visit...sob...) Jeff -- Jeffry Wisnia (W1BSV + Brass Rat '57 EE) The speed of light is 1.8*10e12 furlongs per fortnight. From your two replies, it sounds like this circuit is not dedicated to the microwave. Is it a 15 or 20 amp circuit? What is the wattage of the microwave? If there is truly nothing else operating simultaneously on the circuit, and it trips, it's most likely a problem with the microwave, or a bad breaker. Have you checked to see if anything else goes out when that circuit trips, such as the refrigerator or something in another room? The microwave is only a few months old, as I mentioned earlier. *It is a Sears Kenmore Elite. *Here are the specs: Power Supply: * *120 V AC, 60 Hz Rated Power Consumption: *1,600 W Microwave Output: *1,200 W Rated Current: 14.0 A You are correct; the circuit is not dedicated to the microwave. *As another poster mentioned, older houses don't always have dedicated MW circuits. How do I find out whether it is a *15 or 20 amp circuit? *Is this relevant if, as it appears, I will have to have a dedicated MW circuit installed? ******QUESTION: *What should such an electrician visit cost, including parts. This is a fairly expensive area, and I am not a fairly expensive homeowner, so I need to budget ahead. Estimates appreciated. In answer to your q. if anything else goes out when the circuit trips: *No, just the light panel on the wall oven and the toaster and/or toaster oven IF either happens to be on and pulling juice. *Nothing in another room. Your advice much appreciated. As another poster mentioned, older houses don't always have dedic- Hide quoted text - - Show quoted text - By reading the breaker handle. *If it is a 15amp circuit then it would be helpful to know how much of the rest of the kitchen is on it. *That microwave is going to pull around 12 to 13 amps based on it's 1600 watt label. *If you are on a 15amp circuit and the fridge is also on it then your problem is probably that the fridge tries to start up while the microwave is running. *I'm also inclined to guess you had a less powerfull microwave before. *You can not use other stuff in the kitchen while microwaving but you can't really easily control when the fridge will try to kick in. Upgrading the circuit to 20 amp is not very practical. *Running a new dedicated circuit for the microwave would be your simplest solution. How much that costs depends on a lot of variables like distance from the breaker panel and how difficult it will be to run the wire. *Where you are factors in as well, some locations are only going to allow a licensed electrician or the homeowner to perform this work. *In that case an economical alternative solution is to get a more knowledgable friend to help you diy it. *You'd be better off getting some local quotes as far as possible prices go than asking here.- Hide quoted text - - Show quoted text - Agree with the above. *The MW is rated at 14 amps, 1600 watts. * If it's on a 15 amp breaker, that doesn't leave much for any other load. Which is why with new wiring there is a dedicated circuit for the microwave. * Another possible alternative that would be a lot less expensive is finding a MW that is lower power. But first he needs to determine: Is it a 15 amp breaker/circuit? What else is on that circuit. Can he easily avoid any additional load on the MW circuit by moving any other loads to a different circuit, eg plug the toaster into a different outlet. *He has answered the second half or your question several times - the clock of the gas oven (which likely draws less than 200 Ma), and the toaster opr toaster oven if he has it plugged in - If he ONLY uses the Microwave, or ONLY uses the toaster, the 15 amp breaker should hold. The only thing to do is to replace the breaker and see what happens. A dedicated 20 amp split countertop receptacle should be installed in the kitchen replacing whatever he is plugging the toaster into, leaving the Microwave and gas oven on the existing circuit. This would give him 2 20 amp circuits to handle toasters, coffeemakers, toaster ovens, etc without danger of tripping breakers from inadvertent overloads - and would get him almost code compliant. (which adding a separate circuit for the microwave would not). The countertop receptacles should be on GFCI protected circuits whereas the microwave and oven are not so critical that way. OMG, now I am more anxious than ever. *Why would "adding a separate circuit for the microwave" not get me code compliant? *This is a civilian talking, who doesn't know from code. Also, can you explain "split countertop receptacle"? *What is the "split" about? I went on-line to get a definition, but never did find one as such. Found a number of sites, but all too technical for me. *Whatever the job turns out to be, I will have to hire a qualified electrician; this is not a DIY, even with help. Also: *You say "The countertop receptacles should be on GFCI protected circuits whereas the microwave and oven are not so critical that way." *Can you explain the reason? Also: *Someone in this thread suggested refrigerator cycling on might be causing the trips. I just checked by disabling the breaker governing MW and gas oven, and it does NOT govern the refrig. Last: *Would doing the "split countertop receptacle" obviate the necessity of replacing what might be a defective breaker controlling the MW and gas oven, leading to repeated trips? TIA to all for your continued help! *Much appreciated. HB- Hide quoted text - - Show quoted text - If the fridge is not on your breaker then I'm leaning towards a weak breaker. Have you figured out what else is on that circuit? Turn it off and check everything; all the outlets in the kitchen and adjacent rooms. If the fridge is on a different circuit then you may be able to manage your usage to avoid the problem. Don't turn on other things on that circuit while you are microwaving. A few lights won't matter. If you do decide to add a dedicated circuit for the microwave you should be able to do that without messing around with the rest of the existing wiring. However adding the gfci capability is often easy. It's just a matter of figuring out which outlet in the kitchen is first on the chain of outlets from the box. That outlet would be replaced with a gfci outlet. Even if the kitchen has two circuits in it you simply will need 2 gfci outlets. |
#48
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
On 7/31/2010 11:48 PM, Higgs Boson wrote:
Lately, one circuit on my box blows. It covers the microwave and regular oven. I could understand it blowing when another heat-using appliance, like toaster oven or toaster runs at same time as microwave. But now it's blowing all on its own. Last time, today, only the micro was being used, to "reduce" a glass dish of chicken drippings. Can one circuit go bad all on its own? If so, why? And what should I do about it. Any info appreciated. I'm in the process of rebuilding a refrigeration unit in a restaurant right now and I'm having to replace the plug, outlet and some other wiring because it got toasted. The plug got wet and the connection got worse over time because of the heat produced. It's a destructive cycle that happens over time until the wiring is destroyed or equipment stops running. When the voltage drops, the current goes up and heat is produced at the point of every marginal connection and there can be more than one. The spring tension of the electrical outlet contacts is one of the first things destroyed by heat and that leads to a problem connection which can cascade from there by burning up the plug and cord. The Mark-1 eyeball and SM-3-b nose are often the only tools needed to detect the damaged components. In a home kitchen, folks often spray cleaner on a wall to wipe off splatters and such. The spray often gets into the electrical outlets and onto the plugs which can cause corrosion. The spray can run down the wall and get into the outlet even if there is a plug in it. TDD |
#49
![]()
Posted to alt.home.repair
|
|||
|
|||
![]() "keith" wrote in message ... On Aug 6, 6:02 am, "RBM" wrote: Also, can you explain "split countertop receptacle"? What is the "split" about? I went on-line to get a definition, but never did find one as such. Found a number of sites, but all too technical for me. Whatever the job turns out to be, I will have to hire a qualified electrician; this is not a DIY, even with help. Also: You say "The countertop receptacles should be on GFCI protected circuits whereas the microwave and oven are not so critical that way." Can you explain the reason? Also: Someone in this thread suggested refrigerator cycling on might be causing the trips. I just checked by disabling the breaker governing MW and gas oven, and it does NOT govern the refrig. Last: Would doing the "split countertop receptacle" obviate the necessity of replacing what might be a defective breaker controlling the MW and gas oven, leading to repeated trips? TIA to all for your continued help! Much appreciated. HB A split receptacle is what they do in kitchens in Canada. It's two circuits to one outlet. It's not typically done in the U.S. In the U.S. all kitchen counter top outlets are supposed to be GFCI protected, regardless of what they're used for. All you really need to do to remedy your problem, is run a dedicated 20 amp circuit and outlet for this microwave. Which still leaves him with only one countertop receptacle, which cannot handle both a toaster and a tea kettle - there is a reason Canadian codes are more stringent than US - They make a lot more sense. To remedy the problem and live with the same restrictions he now has, just replace the breaker. If spending the money to add a new circuit - get 2 for just a bit more than the one - the labour will be virtually identical, and the material cost negligibly higher (14/3 or 12/3 instead of 14/2 or 12/2 cable is MABEE 30% more expensive - more likely 15% or so. You have no idea how many receptacles , circuits, or countertops the OP has. What the OP should do, is determine exactly what his problem is, then fix it and not willy nilly replacing parts like a bad mechanic Often replacing parts is the cheapest solution. If parts cost is trivial compared to labor it's the way to go. It's a lot better advice to give long-distance, too. I'm not disagreeing with you, however if it's a solution, and it's cheap, great, but if it doesn't solve the problem, it's jus a waste of time. In many of these situations, if the OP would just answer a few questions, a lot can be determined. In this case the OP has a near new microwave that draws 14 amps. He has a house built in the forties. He does know that the circuit is not dedicated to the microwave, but it's still not clear how many other outlets might be on that circuit. Outlets that may be in other rooms, and drawing current that the OP doesn't know about. It's also not clear if it's a 15 or 20 amp circuit. If it's 15 amp, and not dedicated, and the microwave draws 14 amps, you can change breakers all day, and your not going to solve the problem. |
#50
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
On Fri, 6 Aug 2010 16:38:17 -0400, "RBM" wrote:
"keith" wrote in message ... On Aug 6, 6:02 am, "RBM" wrote: Also, can you explain "split countertop receptacle"? What is the "split" about? I went on-line to get a definition, but never did find one as such. Found a number of sites, but all too technical for me. Whatever the job turns out to be, I will have to hire a qualified electrician; this is not a DIY, even with help. Also: You say "The countertop receptacles should be on GFCI protected circuits whereas the microwave and oven are not so critical that way." Can you explain the reason? Also: Someone in this thread suggested refrigerator cycling on might be causing the trips. I just checked by disabling the breaker governing MW and gas oven, and it does NOT govern the refrig. Last: Would doing the "split countertop receptacle" obviate the necessity of replacing what might be a defective breaker controlling the MW and gas oven, leading to repeated trips? TIA to all for your continued help! Much appreciated. HB A split receptacle is what they do in kitchens in Canada. It's two circuits to one outlet. It's not typically done in the U.S. In the U.S. all kitchen counter top outlets are supposed to be GFCI protected, regardless of what they're used for. All you really need to do to remedy your problem, is run a dedicated 20 amp circuit and outlet for this microwave. Which still leaves him with only one countertop receptacle, which cannot handle both a toaster and a tea kettle - there is a reason Canadian codes are more stringent than US - They make a lot more sense. To remedy the problem and live with the same restrictions he now has, just replace the breaker. If spending the money to add a new circuit - get 2 for just a bit more than the one - the labour will be virtually identical, and the material cost negligibly higher (14/3 or 12/3 instead of 14/2 or 12/2 cable is MABEE 30% more expensive - more likely 15% or so. You have no idea how many receptacles , circuits, or countertops the OP has. What the OP should do, is determine exactly what his problem is, then fix it and not willy nilly replacing parts like a bad mechanic Often replacing parts is the cheapest solution. If parts cost is trivial compared to labor it's the way to go. It's a lot better advice to give long-distance, too. I'm not disagreeing with you, however if it's a solution, and it's cheap, great, but if it doesn't solve the problem, it's jus a waste of time. That's kinda redundant, no? "If it works, it works but if it doesn't, you should have done something else", sort of argument. In many of these situations, if the OP would just answer a few questions, a lot can be determined. In this case the OP has a near new microwave that draws 14 amps. He has a house built in the forties. He does know that the circuit is not dedicated to the microwave, but it's still not clear how many other outlets might be on that circuit. Outlets that may be in other rooms, and drawing current that the OP doesn't know about. It's also not clear if it's a 15 or 20 amp circuit. If it's 15 amp, and not dedicated, and the microwave draws 14 amps, you can change breakers all day, and your not going to solve the problem. Others have brought this up. Others have also, rightly, pointed out that circuit breakers weaken after multiple trips. It should be replaced anyway. If that solves the problem, all done. If not, you're right; the problem was something else. |
#51
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
On Aug 6, 9:50*pm, "
wrote: On Fri, 6 Aug 2010 16:38:17 -0400, "RBM" wrote: "keith" wrote in message .... On Aug 6, 6:02 am, "RBM" wrote: Also, can you explain "split countertop receptacle"? What is the "split" about? I went on-line to get a definition, but never did find one as such. Found a number of sites, but all too technical for me. Whatever the job turns out to be, I will have to hire a qualified electrician; this is not a DIY, even with help. Also: You say "The countertop receptacles should be on GFCI protected circuits whereas the microwave and oven are not so critical that way." Can you explain the reason? Also: Someone in this thread suggested refrigerator cycling on might be causing the trips. I just checked by disabling the breaker governing MW and gas oven, and it does NOT govern the refrig. Last: Would doing the "split countertop receptacle" obviate the necessity of replacing what might be a defective breaker controlling the MW and gas oven, leading to repeated trips? TIA to all for your continued help! Much appreciated. HB A split receptacle is what they do in kitchens in Canada. It's two circuits to one outlet. It's not typically done in the U.S. In the U.S. all kitchen counter top outlets are supposed to be GFCI protected, regardless of what they're used for. All you really need to do to remedy your problem, is run a dedicated 20 amp circuit and outlet for this microwave. Which still leaves him with only one countertop receptacle, which cannot handle both a toaster and a tea kettle - there is a reason Canadian codes are more stringent than US - They make a lot more sense. To remedy the problem and live with the same restrictions he now has, just replace the breaker. If spending the money to add a new circuit - get 2 for just a bit more than the one - the labour will be virtually identical, and the material cost negligibly higher (14/3 or 12/3 instead of 14/2 or 12/2 cable is MABEE 30% more expensive - more likely 15% or so. You have no idea how many receptacles , circuits, or countertops the OP has. What the OP should do, is determine exactly what his problem is, then fix it and not willy nilly replacing parts like a bad mechanic Often replacing parts is the cheapest solution. *If parts cost is trivial compared to labor it's the way to go. *It's a lot better advice to give long-distance, too. I'm not disagreeing with you, however if it's a solution, and it's cheap, great, but if it doesn't solve the problem, it's jus a waste of time. That's kinda redundant, no? *"If it works, it works but if it doesn't, you should have done something else", sort of argument. In many of these situations, if the OP would just answer a few questions, a lot can be determined. In this case the OP has a near new microwave that draws 14 amps. He has a house built in the forties. He does know that the circuit is not dedicated to the microwave, but it's still not clear how many other outlets might be on that circuit. Outlets that may be in other rooms, and drawing current that the OP doesn't know about. It's also not clear if it's a 15 or 20 amp circuit. If it's 15 amp, and not dedicated, and the microwave draws 14 amps, you can change breakers all day, and your not going to solve the problem. Others have brought this up. *Others have also, rightly, pointed out that circuit breakers weaken after multiple trips. Now THAT is interesting! Just as a matter of intellectual curiosity, what makes the breaker "weaken after multiple trips". Inquiring minds... *It should be replaced anyway. If that solves the problem, all done. *If not, you're right; the problem was something else. That seems to be the consensus, so here goes finding an electrician, fingers crossed. Don't forget to explain about weakening after multiple trips TIA HB |
#52
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
On Aug 6, 1:38*pm, "RBM" wrote:
"keith" wrote in message ... On Aug 6, 6:02 am, "RBM" wrote: Also, can you explain "split countertop receptacle"? What is the "split" about? I went on-line to get a definition, but never did find one as such. Found a number of sites, but all too technical for me. Whatever the job turns out to be, I will have to hire a qualified electrician; this is not a DIY, even with help. Also: You say "The countertop receptacles should be on GFCI protected circuits whereas the microwave and oven are not so critical that way." Can you explain the reason? Also: Someone in this thread suggested refrigerator cycling on might be causing the trips. I just checked by disabling the breaker governing MW and gas oven, and it does NOT govern the refrig. Last: Would doing the "split countertop receptacle" obviate the necessity of replacing what might be a defective breaker controlling the MW and gas oven, leading to repeated trips? TIA to all for your continued help! Much appreciated. HB A split receptacle is what they do in kitchens in Canada. It's two circuits to one outlet. It's not typically done in the U.S. In the U.S. all kitchen counter top outlets are supposed to be GFCI protected, regardless of what they're used for. All you really need to do to remedy your problem, is run a dedicated 20 amp circuit and outlet for this microwave. Which still leaves him with only one countertop receptacle, which cannot handle both a toaster and a tea kettle - there is a reason Canadian codes are more stringent than US - They make a lot more sense. To remedy the problem and live with the same restrictions he now has, just replace the breaker. If spending the money to add a new circuit - get 2 for just a bit more than the one - the labour will be virtually identical, and the material cost negligibly higher (14/3 or 12/3 instead of 14/2 or 12/2 cable is MABEE 30% more expensive - more likely 15% or so. You have no idea how many receptacles , circuits, or countertops the OP has. What the OP should do, is determine exactly what his problem is, then fix it and not willy nilly replacing parts like a bad mechanic Often replacing parts is the cheapest solution. *If parts cost is trivial compared to labor it's the way to go. *It's a lot better advice to give long-distance, too. I'm not disagreeing with you, however if it's a solution, and it's cheap, great, but if it doesn't solve the problem, it's jus a waste of time. In many of these situations, if the OP would just answer a few questions, a lot can be determined. In this case the OP has a near new microwave that draws 14 amps. He has a house built in the forties. He does know that the circuit is not dedicated to the microwave, but it's still not clear how many other outlets might be on that circuit. Outlets that may be in other rooms, and drawing current that the OP doesn't know about. It's also not clear if it's a 15 or 20 amp circuit. If it's 15 amp, and not dedicated, and the microwave draws 14 amps, you can change breakers all day, and your not going to solve the problem. I wrote a reply but guess it didn't make it. I DID "answer a few questions" multiple times. Made it clear that no other outlets on that circuit, and no outlets in other rooms draw current worth a damn. |
#53
![]()
Posted to alt.home.repair
|
|||
|
|||
![]() "Higgs Boson" wrote in message ... On Aug 6, 1:38 pm, "RBM" wrote: "keith" wrote in message ... On Aug 6, 6:02 am, "RBM" wrote: Also, can you explain "split countertop receptacle"? What is the "split" about? I went on-line to get a definition, but never did find one as such. Found a number of sites, but all too technical for me. Whatever the job turns out to be, I will have to hire a qualified electrician; this is not a DIY, even with help. Also: You say "The countertop receptacles should be on GFCI protected circuits whereas the microwave and oven are not so critical that way." Can you explain the reason? Also: Someone in this thread suggested refrigerator cycling on might be causing the trips. I just checked by disabling the breaker governing MW and gas oven, and it does NOT govern the refrig. Last: Would doing the "split countertop receptacle" obviate the necessity of replacing what might be a defective breaker controlling the MW and gas oven, leading to repeated trips? TIA to all for your continued help! Much appreciated. HB A split receptacle is what they do in kitchens in Canada. It's two circuits to one outlet. It's not typically done in the U.S. In the U.S. all kitchen counter top outlets are supposed to be GFCI protected, regardless of what they're used for. All you really need to do to remedy your problem, is run a dedicated 20 amp circuit and outlet for this microwave. Which still leaves him with only one countertop receptacle, which cannot handle both a toaster and a tea kettle - there is a reason Canadian codes are more stringent than US - They make a lot more sense. To remedy the problem and live with the same restrictions he now has, just replace the breaker. If spending the money to add a new circuit - get 2 for just a bit more than the one - the labour will be virtually identical, and the material cost negligibly higher (14/3 or 12/3 instead of 14/2 or 12/2 cable is MABEE 30% more expensive - more likely 15% or so. You have no idea how many receptacles , circuits, or countertops the OP has. What the OP should do, is determine exactly what his problem is, then fix it and not willy nilly replacing parts like a bad mechanic Often replacing parts is the cheapest solution. If parts cost is trivial compared to labor it's the way to go. It's a lot better advice to give long-distance, too. I'm not disagreeing with you, however if it's a solution, and it's cheap, great, but if it doesn't solve the problem, it's jus a waste of time. In many of these situations, if the OP would just answer a few questions, a lot can be determined. In this case the OP has a near new microwave that draws 14 amps. He has a house built in the forties. He does know that the circuit is not dedicated to the microwave, but it's still not clear how many other outlets might be on that circuit. Outlets that may be in other rooms, and drawing current that the OP doesn't know about. It's also not clear if it's a 15 or 20 amp circuit. If it's 15 amp, and not dedicated, and the microwave draws 14 amps, you can change breakers all day, and your not going to solve the problem. I wrote a reply but guess it didn't make it. I DID "answer a few questions" multiple times. Made it clear that no other outlets on that circuit, and no outlets in other rooms draw current worth a damn. HB, you never said if the circuit is 15 or 20 amp. The number is written on the breaker handle. If it is a 15 amp circuit, and your micro draws 14 amps, anything else that may be on that circuit only needs to draw 1 amp to reach the capacity of the breaker. |
#54
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
Well mine is fixed, it began tripping often then wouldnt reset.
So I used a spare breaker and all is well, a 15 minute fix mostly moving stuff to get to the main panel.......... |
#55
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
On Sun, 8 Aug 2010 00:41:14 -0700 (PDT), Higgs Boson
wrote: On Aug 6, 9:50*pm, " wrote: On Fri, 6 Aug 2010 16:38:17 -0400, "RBM" wrote: "keith" wrote in message ... On Aug 6, 6:02 am, "RBM" wrote: Also, can you explain "split countertop receptacle"? What is the "split" about? I went on-line to get a definition, but never did find one as such. Found a number of sites, but all too technical for me. Whatever the job turns out to be, I will have to hire a qualified electrician; this is not a DIY, even with help. Also: You say "The countertop receptacles should be on GFCI protected circuits whereas the microwave and oven are not so critical that way." Can you explain the reason? Also: Someone in this thread suggested refrigerator cycling on might be causing the trips. I just checked by disabling the breaker governing MW and gas oven, and it does NOT govern the refrig. Last: Would doing the "split countertop receptacle" obviate the necessity of replacing what might be a defective breaker controlling the MW and gas oven, leading to repeated trips? TIA to all for your continued help! Much appreciated. HB A split receptacle is what they do in kitchens in Canada. It's two circuits to one outlet. It's not typically done in the U.S. In the U.S. all kitchen counter top outlets are supposed to be GFCI protected, regardless of what they're used for. All you really need to do to remedy your problem, is run a dedicated 20 amp circuit and outlet for this microwave. Which still leaves him with only one countertop receptacle, which cannot handle both a toaster and a tea kettle - there is a reason Canadian codes are more stringent than US - They make a lot more sense. To remedy the problem and live with the same restrictions he now has, just replace the breaker. If spending the money to add a new circuit - get 2 for just a bit more than the one - the labour will be virtually identical, and the material cost negligibly higher (14/3 or 12/3 instead of 14/2 or 12/2 cable is MABEE 30% more expensive - more likely 15% or so. You have no idea how many receptacles , circuits, or countertops the OP has. What the OP should do, is determine exactly what his problem is, then fix it and not willy nilly replacing parts like a bad mechanic Often replacing parts is the cheapest solution. *If parts cost is trivial compared to labor it's the way to go. *It's a lot better advice to give long-distance, too. I'm not disagreeing with you, however if it's a solution, and it's cheap, great, but if it doesn't solve the problem, it's jus a waste of time. That's kinda redundant, no? *"If it works, it works but if it doesn't, you should have done something else", sort of argument. In many of these situations, if the OP would just answer a few questions, a lot can be determined. In this case the OP has a near new microwave that draws 14 amps. He has a house built in the forties. He does know that the circuit is not dedicated to the microwave, but it's still not clear how many other outlets might be on that circuit. Outlets that may be in other rooms, and drawing current that the OP doesn't know about. It's also not clear if it's a 15 or 20 amp circuit. If it's 15 amp, and not dedicated, and the microwave draws 14 amps, you can change breakers all day, and your not going to solve the problem. Others have brought this up. *Others have also, rightly, pointed out that circuit breakers weaken after multiple trips. Now THAT is interesting! Just as a matter of intellectual curiosity, what makes the breaker "weaken after multiple trips". Inquiring minds... *It should be replaced anyway. If that solves the problem, all done. *If not, you're right; the problem was something else. That seems to be the consensus, so here goes finding an electrician, fingers crossed. Don't forget to explain about weakening after multiple trips Not sure, but I think it's wear on the mechanical parts (springs, friction surfaces to determine trip levels, etc.). These things, unless rated as switches, aren't intended to be cycled manually either. |