Default When bulb blows, earth leakage circuit breaker is tripped

Sometimes when a bulb blows (ceiling light) it causes the ELCB for the
circuit to trip. That is, if the bulb is in one of the upstairs rooms,
only the upstairs lighting ELCB is tripped. The power points are
unaffected, as are the power points and lighting circuits downstairs.

Is this just because modern wiring is so much more "safe" than once
was the case? This house was built in 2004.

MM
  #2   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 9,045
Default When bulb blows, earth leakage circuit breaker is tripped

MM wrote:
Sometimes when a bulb blows (ceiling light) it causes the ELCB for the
circuit to trip. That is, if the bulb is in one of the upstairs rooms,
only the upstairs lighting ELCB is tripped. The power points are
unaffected, as are the power points and lighting circuits downstairs.

Is this just because modern wiring is so much more "safe" than once
was the case? This house was built in 2004.

MM


I suspect you don't mean earth leakage trips..its uncommon to have those
on lighting circuits alone..

Yes, its very common for bulbs to trip a standard MCB.. as they arc on
failure and draw quite large currents before burning out. Mine do it
every time..I s'pose I could replace then with slower acting ones..but I
can't be arsed..

RCD's can also trip if they are marginal, and there is a lot
ofcapaicatbce between live or neutral and ground..
  #3   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 17
Default When bulb blows, earth leakage circuit breaker is tripped

I suspect you don't mean earth leakage trips..its uncommon to have those
on lighting circuits alone..

Yes, its very common for bulbs to trip a standard MCB.. as they arc on
failure and draw quite large currents before burning out. Mine do it
every time..I s'pose I could replace then with slower acting ones..but I
can't be arsed..


Out of interest, how do they specify slower acting ones ? I've never
seen them, but then for a twice-a-year event (the MCB tripping on bulb
blowing) I also fall into the CBA category ...

  #4   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 43,017
Default When bulb blows, earth leakage circuit breaker is tripped

In article ,
MM wrote:
Sometimes when a bulb blows (ceiling light) it causes the ELCB for the
circuit to trip. That is, if the bulb is in one of the upstairs rooms,
only the upstairs lighting ELCB is tripped. The power points are
unaffected, as are the power points and lighting circuits downstairs.


Are you sure you mean ELCB? It would be an unusual domestic installation
which had these on individual lighting circuits. Sure you don't mean MCB?

Is this just because modern wiring is so much more "safe" than once
was the case? This house was built in 2004.


Standard MCBs trip in a shorter time than a wire fuse takes to blow, and
bulbs often draw excessive current at the instant when they blow. Plenty
of theories on why - you'd probably find them by Googling.

--
*Pride is what we have. Vanity is what others have.

Dave Plowman London SW
To e-mail, change noise into sound.
  #5   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 2,120
Default When bulb blows, earth leakage circuit breaker is tripped

The message
from The Natural Philosopher contains these words:

Yes, its very common for bulbs to trip a standard MCB.. as they arc on
failure and draw quite large currents before burning out. Mine do it
every time..I s'pose I could replace then with slower acting ones..but I
can't be arsed..


They also are supposed to have fast-blow fuses inside each bulb these
days to stop this happening. Does it? Does it hell!

--
Skipweasel
Pay no attention to that man behind the curtain.


  #10   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 9,045
Default When bulb blows, earth leakage circuit breaker is tripped

Guy King wrote:
The message
from The Natural Philosopher contains these words:

Yes, its very common for bulbs to trip a standard MCB.. as they arc on
failure and draw quite large currents before burning out. Mine do it
every time..I s'pose I could replace then with slower acting ones..but I
can't be arsed..


They also are supposed to have fast-blow fuses inside each bulb these
days to stop this happening. Does it? Does it hell!

Not all do. Candle bulbs are the worst offenders..


  #12   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,730
Default When bulb blows, earth leakage circuit breaker is tripped


MM wrote:
Sometimes when a bulb blows (ceiling light) it causes the ELCB for the
circuit to trip. That is, if the bulb is in one of the upstairs rooms,
only the upstairs lighting ELCB is tripped. The power points are
unaffected, as are the power points and lighting circuits downstairs.

Is this just because modern wiring is so much more "safe" than once
was the case? This house was built in 2004.

MM


Like the rest I reckon you've got ELCB's and MCB's muddled. If the
ELCB went then the whole house would in all likelihood go down. As
you've got a modern house I suspect you will have a split consumer unit
in which the lights are NOT off the ELCB so that if an earth leakage
occurs in an item on the power circuits and does trip the ELCB, then
the lights will remain on.

Having said all, thanks for asking the question as I've recently done a
CU replacement and was heading towards asking the same one due to the
nuisance trips when a bulb fused. I'm surprised at one contributor who
reckoned he only got 1 or 2 a year - he must buy better quality
filament bulbs than me as I get one every couple of months.

Rob

  #13   Report Post  
Posted to uk.d-i-y
MM MM is offline
external usenet poster
 
Posts: 2,172
Default When bulb blows, earth leakage circuit breaker is tripped

On Tue, 12 Dec 2006 11:20:13 +0000, The Natural Philosopher
wrote:

MM wrote:
Sometimes when a bulb blows (ceiling light) it causes the ELCB for the
circuit to trip. That is, if the bulb is in one of the upstairs rooms,
only the upstairs lighting ELCB is tripped. The power points are
unaffected, as are the power points and lighting circuits downstairs.

Is this just because modern wiring is so much more "safe" than once
was the case? This house was built in 2004.

MM


I suspect you don't mean earth leakage trips..its uncommon to have those
on lighting circuits alone..


I mean the switches in place of the fuses of yore. My consumer unit
contains a whole row of them. Mostly black, some red.

MM
  #16   Report Post  
Posted to uk.d-i-y
MM MM is offline
external usenet poster
 
Posts: 2,172
Default When bulb blows, earth leakage circuit breaker is tripped

On Tue, 12 Dec 2006 13:25:17 +0000 (GMT), "Dave Plowman (News)"
wrote:

In article ,
MM wrote:
Sometimes when a bulb blows (ceiling light) it causes the ELCB for the
circuit to trip. That is, if the bulb is in one of the upstairs rooms,
only the upstairs lighting ELCB is tripped. The power points are
unaffected, as are the power points and lighting circuits downstairs.


Are you sure you mean ELCB? It would be an unusual domestic installation
which had these on individual lighting circuits. Sure you don't mean MCB?


Yeah, probably I do! I just mean the switches fitted as standard
nowadays where my old 1947 council house had push-in fuse holders.

MM
  #17   Report Post  
Posted to uk.d-i-y
MM MM is offline
external usenet poster
 
Posts: 2,172
Default When bulb blows, earth leakage circuit breaker is tripped

On 12 Dec 2006 08:52:39 -0800, "robgraham"
wrote:


MM wrote:
Sometimes when a bulb blows (ceiling light) it causes the ELCB for the
circuit to trip. That is, if the bulb is in one of the upstairs rooms,
only the upstairs lighting ELCB is tripped. The power points are
unaffected, as are the power points and lighting circuits downstairs.

Is this just because modern wiring is so much more "safe" than once
was the case? This house was built in 2004.

MM


Like the rest I reckon you've got ELCB's and MCB's muddled. If the
ELCB went then the whole house would in all likelihood go down. As
you've got a modern house I suspect you will have a split consumer unit
in which the lights are NOT off the ELCB so that if an earth leakage
occurs in an item on the power circuits and does trip the ELCB, then
the lights will remain on.

Having said all, thanks for asking the question as I've recently done a
CU replacement and was heading towards asking the same one due to the
nuisance trips when a bulb fused. I'm surprised at one contributor who
reckoned he only got 1 or 2 a year - he must buy better quality
filament bulbs than me as I get one every couple of months.


Well, I only buy the cheapest bulbs, Tesco's or ASDA's Smart Price
brand. They seem to last as long as any other and are dirt cheap. I
reckon I replace two or three a year, tops. Most bedrooms, however,
never have them switched on from one month to the next.

MM
  #18   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 2,120
Default When bulb blows, earth leakage circuit breaker is tripped

The message
from The Natural Philosopher contains these words:

internal fuses
Not all do. Candle bulbs are the worst offenders..


Don't have any handy to peep at.

--
Skipweasel
Pay no attention to that man behind the curtain.
  #20   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 3,356
Default When bulb blows, earth leakage circuit breaker is tripped

On Tue, 12 Dec 2006 13:25:17 +0000 (GMT) someone who may be "Dave
Plowman (News)" wrote this:-

Standard MCBs trip in a shorter time than a wire fuse takes to blow,


That rather depends on the situation.




--
David Hansen, Edinburgh
I will *always* explain revoked encryption keys, unless RIP prevents me
http://www.opsi.gov.uk/acts/acts2000/00023--e.htm#54


  #21   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 25,191
Default When bulb blows, earth leakage circuit breaker is tripped

wrote:

Really I need to get one which only trips if the current drawn exceeds
the limit for (say) more than a millisecond or two.


Its called a fuse! ;-)

--
Cheers,

John.

/================================================== ===============\
| Internode Ltd -
http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/
  #22   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 2,120
Default When bulb blows, earth leakage circuit breaker is tripped

The message
from contains these words:

This used to happen /many/ years ago with fuses. Then they came along with
bulbs that had a built in fuse to prevent this happening.


Well, the incandescent bulbs[1] we use here appear to have fuses in and
it still happens - so do you have another explanation? I suspect the
fuse still doesn't react as fast as the MCB.

[1]I think we've got two left - apart from those in the cooker hood. Got
several live spares in the cupboard though.

--
Skipweasel
Pay no attention to that man behind the curtain.
  #24   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 3,356
Default When bulb blows, earth leakage circuit breaker is tripped

On Wed, 13 Dec 2006 12:47:21 GMT someone who may be Guy King
wrote this:-

I suspect the
fuse still doesn't react as fast as the MCB.


Do you? Why?

A generalisation is that a fuse reacts much faster than an MCB
during a high current fault, but an MCB reacts faster than a fuse
during a low current fault (an overload).


--
David Hansen, Edinburgh
I will *always* explain revoked encryption keys, unless RIP prevents me
http://www.opsi.gov.uk/acts/acts2000/00023--e.htm#54
  #25   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 2,120
Default When bulb blows, earth leakage circuit breaker is tripped

The message
from David Hansen contains these words:

I suspect the fuse still doesn't react as fast as the MCB.


Do you? Why?


Because when the lamp blows it still takes out the MCB even when there's
an internal fuse. For all your cunning reasoning, real life experience
suggests that having a fuse in the bulb doesn't prevent the breaker
breaking.

--
Skipweasel
Pay no attention to that man behind the curtain.


  #26   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 3,356
Default When bulb blows, earth leakage circuit breaker is tripped

On Wed, 13 Dec 2006 18:49:50 GMT someone who may be Guy King
wrote this:-

Because when the lamp blows it still takes out the MCB even when there's
an internal fuse.


As others have said, fuses (in consumer units) can also be "taken
out" in such circumstances.

For all your cunning reasoning, real life experience
suggests that having a fuse in the bulb doesn't prevent the breaker
breaking.


I made no comment on fuses in bulbs. The comparison is between fuses
in consumer units and MCBs in consumer units.


--
David Hansen, Edinburgh
I will *always* explain revoked encryption keys, unless RIP prevents me
http://www.opsi.gov.uk/acts/acts2000/00023--e.htm#54
  #27   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 2,120
Default When bulb blows, earth leakage circuit breaker is tripped

The message
from David Hansen contains these words:

Because when the lamp blows it still takes out the MCB even when there's
an internal fuse.


As others have said, fuses (in consumer units) can also be "taken
out" in such circumstances.


For all your cunning reasoning, real life experience
suggests that having a fuse in the bulb doesn't prevent the breaker
breaking.


I made no comment on fuses in bulbs. The comparison is between fuses
in consumer units and MCBs in consumer units.


Sorry, I thought you were saying that MCBs no longer pop when a light
bulb blows because bulbs now have fuses.

I was actually answering "B Thumbs" who said in reply to me saying that
blowing bulbs take out MCBs "This used to happen /many/ years ago with
fuses. Then they came along with bulbs that had a built in fuse to
prevent this happening. Do incandescent lamps no longer incorporate a
fuse, or is it just the halogen ones?"

So my reply /was/ about bulbs with fuses though it may not have been
aimed at you.

--
Skipweasel
Pay no attention to that man behind the curtain.
  #28   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 11,175
Default When bulb blows, earth leakage circuit breaker is tripped

In article ,
David Hansen writes:
On Wed, 13 Dec 2006 12:47:21 GMT someone who may be Guy King
wrote this:-

I suspect the
fuse still doesn't react as fast as the MCB.


Do you? Why?

A generalisation is that a fuse reacts much faster than an MCB
during a high current fault, but an MCB reacts faster than a fuse
during a low current fault (an overload).


Hum,
It's sufficiently more complex than that I don't think any
such generalisation can be valid (and if you look at the trip
curves, _in general_ I would say it's the other way around).
For example, what to you mean by "react"? Actually detect
the error condition, or finish clearing the error condition,
because those two are quite different between MCBs and fuses,
and even quite different between different types of fuses.

Lamp base fuses seem mostly to be of the bare wire type, which
are going to be similar response to a BS3036 semi-enclosed
(a.k.a rewirable) fuse. Occasionally, ballotini fuses are used,
which have different error detection and clearing times, more
like that of a cartridge fuse.

Once an open wire fuse melts, it can take a number of mains
cycles before the vapour has dispersed sufficiently for the
arc to be quenched. Meanwhile, an MCB can operate in less than
a half cycle, whilst the fuse arc is still running. If you look
at a lamp which has tripped an MCB, you will see its fuses are
blown, but they were unable to quench the arc before the MCB
tripped. It's a case of a current which grossly exceeds both
the fault current ratings of both protective devices, and they
both trip. I've never seen a lamp with fuses trip an MCB without
also blowing its lamp base fuses (both of them if is has two).

--
Andrew Gabriel
  #30   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 6,020
Default When bulb blows, earth leakage circuit breaker is tripped

On Thu, 14 Dec 2006 21:08:10 +0000, David Hansen wrote:

There is a saying, if you think you
understand something then try writing computer software to model it.
If the software works then you really do understand the subject.


That's ********. I've written several computer models, all of them modeling
with varying degrees of accuracy systems of assorted complexities. I can't
pretend to have understood the subject well for every model.

And no, I wasn't coding someone else's models.


  #31   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 402
Default When bulb blows, earth leakage circuit breaker is tripped

David Hansen wrote:

At the risk of starting a, "mine is bigger then yours", discussion,
not something I am keen on. There is a saying, if you think you
understand something then try writing computer software to model it.
If the software works then you really do understand the subject.


The principles here are fairly straightforward, it's obtaining and
applying the relevant data that's the problem.

At a particular fault current:

(i) if the operating I^2*t of the MCB is less than the pre-arcing
I^2*t of the fuse then the MCB will discriminate in favour of
the fuse (i.e. breaker trips, fuse does not blow);

(ii) if the operating I^2*t of the MCB exceeds the total clearing
I^2*t of the fuse (pre-arcing and arcing) then the fuse will
discriminate in favour of the MCB (fuse blows, breaker does
not trip);

(iii) if the operating I^2*t of the MCB exceeds the pre-arcing I^2*t
of the fuse, but does not exceed its total clearing I^2*t then
both devices will operate (no discrimination, fuse element melts
but the arc is extinguished by the MCB).

Now all you need is the relevant I^2*t curves and knowledge of the fault
level. I^2*t data for MCBs should be fairly readily available from the
manufacturers, but for lamp fuses... (I've never seen any published).

--
Andy
  #32   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 519
Default When bulb blows, earth leakage circuit breaker is tripped

Steve Firth wrote:
On Thu, 14 Dec 2006 21:08:10 +0000, David Hansen wrote:

There is a saying, if you think you
understand something then try writing computer software to model it.
If the software works then you really do understand the subject.


That's ********. I've written several computer models, all of them modeling
with varying degrees of accuracy systems of assorted complexities. I can't
pretend to have understood the subject well for every model.


Not to mention that unless you actually do understand the model, and
have verified it against underlying facts, you can come up with a model
that seems to work, but doesn't except in the test cases.

Modelling something doesn't help, if your understanding is flawed, and
you are just modelling your understanding, if your understanding of the
system is self-consistent.
  #33   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 307
Default When bulb blows, earth leakage circuit breaker is tripped

Andy Wade wrote:

At a particular fault current:

(i) if the operating I^2*t of the MCB is less than the pre-arcing
I^2*t of the fuse then the MCB will discriminate in favour of
the fuse (i.e. breaker trips, fuse does not blow);

(ii) if the operating I^2*t of the MCB exceeds the total clearing
I^2*t of the fuse (pre-arcing and arcing) then the fuse will
discriminate in favour of the MCB (fuse blows, breaker does
not trip);

(iii) if the operating I^2*t of the MCB exceeds the pre-arcing I^2*t
of the fuse, but does not exceed its total clearing I^2*t then
both devices will operate (no discrimination, fuse element melts
but the arc is extinguished by the MCB).


To add a bit more detail...

I^2*t (pron: "I-squared-T") is a measure of the electrical energy that
is let through the fuse or MCB during a current surge. Some of that
energy is absorbed by the device itself, either to heat the wire in a
fuse, or to give an electromechanical kick to the moving parts in an
MCB.

In a fuse, the pre-arcing I^2*t represents a "point of no return", where
enough heat has been absorbed to melt the wire, so it is definitely
destined to break. However, it takes a while longer for the molten metal
to flow, and for surface tension to pull the ends apart.

Thus you can easily have a situation like Andy's case (iii) where the
current surge takes the fuse beyond its point of no return while also
operating the MCB. Then, as Andy says, it is often the MCB that breaks
the circuit, before the fuse has time to pull apart... but the fuse is
still found to be melted.



--
Ian White
  #34   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 3,356
Default When bulb blows, earth leakage circuit breaker is tripped

On Thu, 14 Dec 2006 23:13:50 +0000 someone who may be Steve Firth
wrote this:-

There is a saying, if you think you
understand something then try writing computer software to model it.
If the software works then you really do understand the subject.


That's ********.


Ah, proof by assertion and rudeness in three words. Excellent.

I've written several computer models, all of them modeling
with varying degrees of accuracy systems of assorted complexities. I can't
pretend to have understood the subject well for every model.


Noted.


--
David Hansen, Edinburgh
I will *always* explain revoked encryption keys, unless RIP prevents me
http://www.opsi.gov.uk/acts/acts2000/00023--e.htm#54
  #35   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 3,356
Default When bulb blows, earth leakage circuit breaker is tripped

On Thu, 14 Dec 2006 23:59:30 +0000 someone who may be Andy Wade
wrote this:-

I^2*t data for MCBs should be fairly readily available from the
manufacturers,


It is.

but for lamp fuses... (I've never seen any published).


Fuses built into lamps are not something I have discussed, not the
least because I have never seen data on them.


--
David Hansen, Edinburgh
I will *always* explain revoked encryption keys, unless RIP prevents me
http://www.opsi.gov.uk/acts/acts2000/00023--e.htm#54


  #36   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 255
Default When bulb blows, earth leakage circuit breaker is tripped

In article ,
Andrew Gabriel wrote:
[snip]
Once an open wire fuse melts, it can take a number of mains
cycles before the vapour has dispersed sufficiently for the
arc to be quenched. Meanwhile, an MCB can operate in less than
a half cycle, whilst the fuse arc is still running. If you look
at a lamp which has tripped an MCB, you will see its fuses are
blown, but they were unable to quench the arc before the MCB
tripped. It's a case of a current which grossly exceeds both
the fault current ratings of both protective devices, and they
both trip. I've never seen a lamp with fuses trip an MCB without
also blowing its lamp base fuses (both of them if is has two).


I was going to do a post earlier on in this thread
to say that we've never had a blown bulb trip the
MCB. That was, until last night, when it happened
with an almost new 100W bulb (about 10 days old).

I've just knocked it apart. As you say, destruction
is complete. The support wires are there, but the
filament has disappeared, as have both fusewires in
the stem of the bulb.

SWMBO did note that it didn't do the normal 'plink'
as it went, it did a nasty-sounding 'splat'. That
could have been the arcing.

--
Tony Williams.
  #37   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 131
Default When bulb blows, earth leakage circuit breaker is tripped

"MM" wrote in message
...
Sometimes when a bulb blows (ceiling light) it causes the ELCB for the
circuit to trip. That is, if the bulb is in one of the upstairs rooms,
only the upstairs lighting ELCB is tripped. The power points are
unaffected, as are the power points and lighting circuits downstairs.

Is this just because modern wiring is so much more "safe" than once
was the case? This house was built in 2004.

Two solutions :-

1. Change MCB (I am sure you meant MCB not ELCB) to type C.
(www.tlc-direct.co.uk) as this has a higher over-load/time trip. This worked
for me in my hall lights (4 x 60W). Got fed up of coming home, turn on hall
lights and flash and still in dark. In fact very dark as the IR triggered
outside light is on same circuit, so is the garage lights which makes
getting to the breaker very hard.

2. Change to low enrgy bulbs.


  #38   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 6,020
Default When bulb blows, earth leakage circuit breaker is tripped

On Fri, 15 Dec 2006 08:44:09 +0000, David Hansen wrote:

On Thu, 14 Dec 2006 23:13:50 +0000 someone who may be Steve Firth
wrote this:-

There is a saying, if you think you
understand something then try writing computer software to model it.
If the software works then you really do understand the subject.


That's ********.


Ah, proof by assertion and rudeness in three words. Excellent.


Life must be so difficult for you, blubbering every time someone says boo!
  #39   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 25,191
Default When bulb blows, earth leakage circuit breaker is tripped

Ian_m wrote:

Two solutions :-

1. Change MCB (I am sure you meant MCB not ELCB) to type C.
(www.tlc-direct.co.uk) as this has a higher over-load/time trip. This worked
for me in my hall lights (4 x 60W). Got fed up of coming home, turn on hall
lights and flash and still in dark. In fact very dark as the IR triggered
outside light is on same circuit, so is the garage lights which makes
getting to the breaker very hard.



1.5) install a non maintained emergency light at the CU and anyplace
enroute to it that may prove difficult to navigate when dark.

(and to be fair 1) is not a total solution - you can still trip those on
bulb failure - just not as often.

2. Change to low enrgy bulbs.




--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/
  #40   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 3,356
Default When bulb blows, earth leakage circuit breaker is tripped

On Fri, 15 Dec 2006 16:45:04 +0000 someone who may be Steve Firth
wrote this:-

Life must be so difficult for you, blubbering every time someone says boo!


Ah, someone else trying to give the impression that they can read my
mind. Don't give up the day job and take up mind reading, you are
not any good at it.


--
David Hansen, Edinburgh
I will *always* explain revoked encryption keys, unless RIP prevents me
http://www.opsi.gov.uk/acts/acts2000/00023--e.htm#54
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
bulb blow causes circuit breaker to trip [email protected] UK diy 9 November 20th 06 07:50 PM
Circuit breaker tripped while on vacation, how to get smell out of refrigerator? Dan K Home Repair 9 December 10th 04 04:30 PM
Should this have tripped the breaker? Ged UK diy 5 February 18th 04 07:52 PM
Help -- Power out in one area but circuit breaker not tripped Joseph Meehan Home Repair 0 June 27th 03 02:29 AM


All times are GMT +1. The time now is 08:17 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"