Default Extending multiple BX cables: with multiple bx cables or multiple wires in greenfield?

Awl --

I've posted on aspects of this before, and d-day is coming.

The situation is this:
A fuse panel upstairs is being eliminated, and the #14 bx cable extended
down about 10-15 feet to a new surface mounted breaker panel downstairs.
Thirteen separate bx cables, 7 of which are 3 wire (Edison), for a total of
20 circuits.

Should I extend each bx cable with its own extension bx (or romex), or get
one or two 3/4-1" greenfield cables with sufficient #14 conductors pulled
through?

I'm leaning toward the greenfield, as it's just neater, less bulky, fewer
knock-out connections, and I believe a lot more economical.

Opinions? Pros/cons of either strategy?
tia.

--
EA




  #2   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,746
Default Extending multiple BX cables: with multiple bx cables or multiplewires in greenfield?


Existential Angst wrote:

Awl --

I've posted on aspects of this before, and d-day is coming.

The situation is this:
A fuse panel upstairs is being eliminated, and the #14 bx cable extended
down about 10-15 feet to a new surface mounted breaker panel downstairs.
Thirteen separate bx cables, 7 of which are 3 wire (Edison), for a total of
20 circuits.

Should I extend each bx cable with its own extension bx (or romex), or get
one or two 3/4-1" greenfield cables with sufficient #14 conductors pulled
through?

I'm leaning toward the greenfield, as it's just neater, less bulky, fewer
knock-out connections, and I believe a lot more economical.

Opinions? Pros/cons of either strategy?
tia.

--
EA


I use 2" EMT between the connection pull box and the panel, but normally
it's located just a few feet above the panel.
  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,934
Default Extending multiple BX cables: with multiple bx cables or multiple wires in greenfield?


I've posted on aspects of this before, and d-day is coming.

The situation is this:
A fuse panel upstairs is being eliminated, and the #14 bx cable extended
down about 10-15 feet to a new surface mounted breaker panel downstairs.
Thirteen separate bx cables, 7 of which are 3 wire (Edison), for a total
of 20 circuits.

Should I extend each bx cable with its own extension bx (or romex), or get
one or two 3/4-1" greenfield cables with sufficient #14 conductors pulled
through?

I'm leaning toward the greenfield, as it's just neater, less bulky, fewer
knock-out connections, and I believe a lot more economical.

Opinions? Pros/cons of either strategy?




*I'd go with 3- 3/4" or 2-1" flexible conduits since you will have a total
of 33 conductors plus a grounding conductor in each conduit. Using the
conduits will make it easy to pull additional circuits in the future if
needed. Single conductor wire is cheaper than BX cable.

Check tables C.3, 310.15(B)(2)(a) and 310.16 for more information.

  #4   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 539
Default Extending multiple BX cables: with multiple bx cables or multiple wires in greenfield?

"John Grabowski" wrote in message
...

I've posted on aspects of this before, and d-day is coming.

The situation is this:
A fuse panel upstairs is being eliminated, and the #14 bx cable
extended down about 10-15 feet to a new surface mounted breaker panel
downstairs. Thirteen separate bx cables, 7 of which are 3 wire (Edison),
for a total of 20 circuits.

Should I extend each bx cable with its own extension bx (or romex), or
get one or two 3/4-1" greenfield cables with sufficient #14 conductors
pulled through?

I'm leaning toward the greenfield, as it's just neater, less bulky, fewer
knock-out connections, and I believe a lot more economical.

Opinions? Pros/cons of either strategy?




*I'd go with 3- 3/4" or 2-1" flexible conduits since you will have a total
of 33 conductors plus a grounding conductor in each conduit. Using the
conduits will make it easy to pull additional circuits in the future if
needed. Single conductor wire is cheaper than BX cable.

Check tables C.3, 310.15(B)(2)(a) and 310.16 for more information.


Yeah, this is how I'm leaning.
"Flexible conduit" is what I'm calling Greenfield, right?

They make an aluminum and a steel greenfield, and also sell bx cable with
aluminum armour as "MC lite", iiuc.

Does steel greenfield require a ground wire? I assume the aluminum version
does.
--
EA







  #5   Report Post  
Posted to alt.home.repair
N8N N8N is offline
external usenet poster
 
Posts: 1,192
Default Extending multiple BX cables: with multiple bx cables or multiplewires in greenfield?

On Nov 13, 7:42*am, "John Grabowski" wrote:
I've posted on aspects of this before, and d-day is coming.


The situation is this:
* A fuse panel upstairs is being eliminated, and the #14 bx cable extended
down about 10-15 feet to a new surface mounted breaker panel downstairs..
Thirteen separate bx cables, 7 of which are 3 wire (Edison), for a total
of 20 circuits.


Should I extend each bx cable with its own extension bx (or romex), or get
one or two 3/4-1" greenfield cables with sufficient #14 conductors pulled
through?


I'm leaning toward the greenfield, as it's just neater, less bulky, fewer
knock-out connections, and I believe a lot more economical.


Opinions? *Pros/cons of either strategy?


*I'd go with 3- 3/4" or 2-1" flexible conduits since you will have a total
of 33 conductors plus a grounding conductor in each conduit. *Using the
conduits will make it easy to pull additional circuits in the future if
needed. *Single conductor wire is cheaper than BX cable.

Check tables C.3, *310.15(B)(2)(a) and 310.16 for more information.- Hide quoted text -

- Show quoted text -



in that scenario would you really need individual grounds? I'm
thinking that you'd have one large grounding conductor between the
panel and the trough and have a terminal strip in the trough to land
all your existing "field" grounds. Is there some reason why that
wouldn't work?

nate


  #6   Report Post  
Posted to alt.home.repair
N8N N8N is offline
external usenet poster
 
Posts: 1,192
Default Extending multiple BX cables: with multiple bx cables or multiplewires in greenfield?

On Nov 13, 8:30*am, "Existential Angst"
wrote:
"John Grabowski" wrote in message

...







I've posted on aspects of this before, and d-day is coming.


The situation is this:
* A fuse panel upstairs is being eliminated, and the #14 bx cable
extended down about 10-15 feet to a new surface mounted breaker panel
downstairs. Thirteen separate bx cables, 7 of which are 3 wire (Edison),
for a total of 20 circuits.


Should I extend each bx cable with its own extension bx (or romex), or
get one or two 3/4-1" greenfield cables with sufficient #14 conductors
pulled through?


I'm leaning toward the greenfield, as it's just neater, less bulky, fewer
knock-out connections, and I believe a lot more economical.


Opinions? *Pros/cons of either strategy?


*I'd go with 3- 3/4" or 2-1" flexible conduits since you will have a total
of 33 conductors plus a grounding conductor in each conduit. *Using the
conduits will make it easy to pull additional circuits in the future if
needed. *Single conductor wire is cheaper than BX cable.


Check tables C.3, *310.15(B)(2)(a) and 310.16 for more information.


Yeah, this is how I'm leaning.
"Flexible conduit" is what I'm calling Greenfield, right?

They make an aluminum and a steel greenfield, and also sell bx cable with
aluminum armour as "MC lite", iiuc.

Does steel greenfield require a ground wire? *I assume the aluminum version
does.
--
EA


I ASSume the steel version does as well, I bought some premade fixture
whips a while back and they had ground wires in them despite being
basically steel Greenfield.

Now the really really old BX in my house, that just has a bonding
strip inside the armor, no ground conductor, but that also has cloth
covered wiring in it...

There are a couple locations where I'm really really tempted to try to
use the two old wires to pull two plus ground new THHN through the BX
armor, because it would save SO much work rewiring. However, I don't
have a "plan B" if things go wrong...

nate
  #7   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,934
Default Extending multiple BX cables: with multiple bx cables or multiple wires in greenfield?



I've posted on aspects of this before, and d-day is coming.

The situation is this:
A fuse panel upstairs is being eliminated, and the #14 bx cable
extended down about 10-15 feet to a new surface mounted breaker panel
downstairs. Thirteen separate bx cables, 7 of which are 3 wire (Edison),
for a total of 20 circuits.

Should I extend each bx cable with its own extension bx (or romex), or
get one or two 3/4-1" greenfield cables with sufficient #14 conductors
pulled through?

I'm leaning toward the greenfield, as it's just neater, less bulky,
fewer knock-out connections, and I believe a lot more economical.

Opinions? Pros/cons of either strategy?




*I'd go with 3- 3/4" or 2-1" flexible conduits since you will have a
total of 33 conductors plus a grounding conductor in each conduit. Using
the conduits will make it easy to pull additional circuits in the future
if needed. Single conductor wire is cheaper than BX cable.

Check tables C.3, 310.15(B)(2)(a) and 310.16 for more information.


Yeah, this is how I'm leaning.
"Flexible conduit" is what I'm calling Greenfield, right?

They make an aluminum and a steel greenfield, and also sell bx cable with
aluminum armour as "MC lite", iiuc.

Does steel greenfield require a ground wire? I assume the aluminum
version does.




*A grounding conductor is required for Type FMC (Flexible Metallic Conduit,
AKA Greenfield) regardless of the metal composition for anything over six
feet. Check 348.60, 250.134, 250.118(5)

I believe that a grounding conductor is required for each conduit run even
though one ground may be sufficient. Someone else can probably confirm or
refute this.

  #8   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,981
Default Extending multiple BX cables: with multiple bx cables or multiplewires in greenfield?

John Grabowski wrote:

I've posted on aspects of this before, and d-day is coming.

The situation is this:
A fuse panel upstairs is being eliminated, and the #14 bx cable
extended down about 10-15 feet to a new surface mounted breaker panel
downstairs. Thirteen separate bx cables, 7 of which are 3 wire
(Edison), for a total of 20 circuits.

Should I extend each bx cable with its own extension bx (or romex), or
get one or two 3/4-1" greenfield cables with sufficient #14 conductors
pulled through?

I'm leaning toward the greenfield, as it's just neater, less bulky,
fewer knock-out connections, and I believe a lot more economical.

Opinions? Pros/cons of either strategy?




*I'd go with 3- 3/4" or 2-1" flexible conduits since you will have a
total of 33 conductors plus a grounding conductor in each conduit.
Using the conduits will make it easy to pull additional circuits in the
future if needed. Single conductor wire is cheaper than BX cable.

Check tables C.3, 310.15(B)(2)(a) and 310.16 for more information.


310.16 gives the allowable "ampacity" for the wire. Assuming it is #14
with *THHN* insulation the ampacity is 20A (but cannot be used at over 15A).

310.15(B)(2)(a) requires the ampacity to be reduced if there are more
than 3 wires in a conduit. If you have 6 "current-carrying" wires, the
ampacity is reduced to 80%. For #14 *THHN* the ampacity is then 16A and
you can still use it on a 15A circuit. You can not have more than 6
"current-carrying" #14 *THHN* wires in a conduit and connect them to a
15A breaker.

310.15(B)(4) says that the neutral of a 3 wire "Edison" circuit does not
count as one of the "current-carrying" conductors.

310.15(B)(5) says that ground wires do not count as "current-carrying"
conductors.

You can run 3 "Edison" circuits, 9 - #14 *THHN* wires (6
"current-carrying" conductors) in a single conduit. Add a #14 ground wire.

Appendix C.3 says the 10 - #14 conductors can be run in a 1/2"
Greenfield (aka flex).

For 2 wire circuits (if you do not combine them to be "Edison"
circuits), you can run 3 - #14 *THHN* circuits in the same conduit - 6
"current-carrying" wires plus ground = 7 wires.

The rules are somewhat more complicated, but this is what should apply
to what you are doing, assuming the installation complies with the NEC.

Since you are posting fairly often, do you have a copy of the NEC?
Are you reasonably proficient at reading it?

--
bud--
  #9   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,981
Default Extending multiple BX cables: with multiple bx cables or multiplewires in greenfield?

N8N wrote:
On Nov 13, 7:42 am, "John Grabowski" wrote:
I've posted on aspects of this before, and d-day is coming.
The situation is this:
A fuse panel upstairs is being eliminated, and the #14 bx cable extended
down about 10-15 feet to a new surface mounted breaker panel downstairs.
Thirteen separate bx cables, 7 of which are 3 wire (Edison), for a total
of 20 circuits.
Should I extend each bx cable with its own extension bx (or romex), or get
one or two 3/4-1" greenfield cables with sufficient #14 conductors pulled
through?
I'm leaning toward the greenfield, as it's just neater, less bulky, fewer
knock-out connections, and I believe a lot more economical.
Opinions? Pros/cons of either strategy?

*I'd go with 3- 3/4" or 2-1" flexible conduits since you will have a total
of 33 conductors plus a grounding conductor in each conduit. Using the
conduits will make it easy to pull additional circuits in the future if
needed. Single conductor wire is cheaper than BX cable.

Check tables C.3, 310.15(B)(2)(a) and 310.16 for more information.-


in that scenario would you really need individual grounds? I'm
thinking that you'd have one large grounding conductor between the
panel and the trough and have a terminal strip in the trough to land
all your existing "field" grounds. Is there some reason why that
wouldn't work?


For multiple circuits in one conduit you only need one ground wire for
each conduit (where the conduit can not be used as the grounding
conductor). The ground wire is sized for the maximum circuit breaker amp
rating for any circuit (#14 for 15A) (NEC250.122). If circuit conductors
are increased (such as to limit voltage drop) the size of the ground
wire must also be increased.

--
bud--
  #10   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 539
Default Extending multiple BX cables: with multiple bx cables or multiple wires in greenfield?

"bud--" wrote in message
.. .
John Grabowski wrote:

I've posted on aspects of this before, and d-day is coming.

The situation is this:
A fuse panel upstairs is being eliminated, and the #14 bx cable
extended down about 10-15 feet to a new surface mounted breaker panel
downstairs. Thirteen separate bx cables, 7 of which are 3 wire (Edison),
for a total of 20 circuits.

Should I extend each bx cable with its own extension bx (or romex), or
get one or two 3/4-1" greenfield cables with sufficient #14 conductors
pulled through?

I'm leaning toward the greenfield, as it's just neater, less bulky,
fewer knock-out connections, and I believe a lot more economical.

Opinions? Pros/cons of either strategy?




*I'd go with 3- 3/4" or 2-1" flexible conduits since you will have a
total of 33 conductors plus a grounding conductor in each conduit. Using
the conduits will make it easy to pull additional circuits in the future
if needed. Single conductor wire is cheaper than BX cable.

Check tables C.3, 310.15(B)(2)(a) and 310.16 for more information.


310.16 gives the allowable "ampacity" for the wire. Assuming it is #14
with *THHN* insulation the ampacity is 20A (but cannot be used at over
15A).

310.15(B)(2)(a) requires the ampacity to be reduced if there are more than
3 wires in a conduit. If you have 6 "current-carrying" wires, the ampacity
is reduced to 80%. For #14 *THHN* the ampacity is then 16A and you can
still use it on a 15A circuit. You can not have more than 6
"current-carrying" #14 *THHN* wires in a conduit and connect them to a 15A
breaker.

310.15(B)(4) says that the neutral of a 3 wire "Edison" circuit does not
count as one of the "current-carrying" conductors.

310.15(B)(5) says that ground wires do not count as "current-carrying"
conductors.

You can run 3 "Edison" circuits, 9 - #14 *THHN* wires (6
"current-carrying" conductors) in a single conduit. Add a #14 ground wire.

Appendix C.3 says the 10 - #14 conductors can be run in a 1/2" Greenfield
(aka flex).

For 2 wire circuits (if you do not combine them to be "Edison" circuits),
you can run 3 - #14 *THHN* circuits in the same conduit - 6
"current-carrying" wires plus ground = 7 wires.

The rules are somewhat more complicated, but this is what should apply to
what you are doing, assuming the installation complies with the NEC.

Since you are posting fairly often, do you have a copy of the NEC?
Are you reasonably proficient at reading it?


Very helpful info, thank you.
I have a 1996 NEC, and I *could* be proficient at reading it if the
essentials weren't drowned in thousands of other words. But yeah, the
tables in App. B and C do get to the point.

It seems that many others have trouble reading the NEC, as there is a whole
cottage industry of workbooks and guides in how to read, understand, and use
the NEC. wow....

I just came home with 100 ft of 3/4 greenfield, two 500 ft rolls of #14
wire -- which, btw, just jumped $5 a roll in the past 3 days. Man, I hate
gving money to HD -- who nevertheless charge in some cases quite a bit less
than electrical supply houses for wire -- but a hair more for greenfield.
--
EA


--
bud--





  #11   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,934
Default Extending multiple BX cables: with multiple bx cables or multiple wires in greenfield?


I've posted on aspects of this before, and d-day is coming.

The situation is this:
A fuse panel upstairs is being eliminated, and the #14 bx cable
extended down about 10-15 feet to a new surface mounted breaker panel
downstairs. Thirteen separate bx cables, 7 of which are 3 wire
(Edison), for a total of 20 circuits.

Should I extend each bx cable with its own extension bx (or romex), or
get one or two 3/4-1" greenfield cables with sufficient #14 conductors
pulled through?

I'm leaning toward the greenfield, as it's just neater, less bulky,
fewer knock-out connections, and I believe a lot more economical.

Opinions? Pros/cons of either strategy?



*I'd go with 3- 3/4" or 2-1" flexible conduits since you will have a
total of 33 conductors plus a grounding conductor in each conduit.
Using the conduits will make it easy to pull additional circuits in the
future if needed. Single conductor wire is cheaper than BX cable.

Check tables C.3, 310.15(B)(2)(a) and 310.16 for more information.


310.16 gives the allowable "ampacity" for the wire. Assuming it is #14
with *THHN* insulation the ampacity is 20A (but cannot be used at over
15A).

310.15(B)(2)(a) requires the ampacity to be reduced if there are more
than 3 wires in a conduit. If you have 6 "current-carrying" wires, the
ampacity is reduced to 80%. For #14 *THHN* the ampacity is then 16A and
you can still use it on a 15A circuit. You can not have more than 6
"current-carrying" #14 *THHN* wires in a conduit and connect them to a
15A breaker.

310.15(B)(4) says that the neutral of a 3 wire "Edison" circuit does not
count as one of the "current-carrying" conductors.

310.15(B)(5) says that ground wires do not count as "current-carrying"
conductors.

You can run 3 "Edison" circuits, 9 - #14 *THHN* wires (6
"current-carrying" conductors) in a single conduit. Add a #14 ground
wire.

Appendix C.3 says the 10 - #14 conductors can be run in a 1/2" Greenfield
(aka flex).

For 2 wire circuits (if you do not combine them to be "Edison" circuits),
you can run 3 - #14 *THHN* circuits in the same conduit - 6
"current-carrying" wires plus ground = 7 wires.

The rules are somewhat more complicated, but this is what should apply to
what you are doing, assuming the installation complies with the NEC.

Since you are posting fairly often, do you have a copy of the NEC?
Are you reasonably proficient at reading it?


Very helpful info, thank you.
I have a 1996 NEC, and I *could* be proficient at reading it if the
essentials weren't drowned in thousands of other words. But yeah, the
tables in App. B and C do get to the point.

It seems that many others have trouble reading the NEC, as there is a
whole cottage industry of workbooks and guides in how to read, understand,
and use the NEC. wow....

I just came home with 100 ft of 3/4 greenfield, two 500 ft rolls of #14
wire -- which, btw, just jumped $5 a roll in the past 3 days. Man, I hate
gving money to HD -- who nevertheless charge in some cases quite a bit
less than electrical supply houses for wire -- but a hair more for
greenfield.




*The supply houses that I deal with adjust their wire prices daily according
to the market. Home Depot does it I presume as they replenish. I have
found Home Depot higher and lower depending on which way copper is going.
Unfortunately I don't always have time to shop around.

  #12   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,981
Default Extending multiple BX cables: with multiple bx cables or multiplewires in greenfield?

Existential Angst wrote:
"bud--" wrote in message

Since you are posting fairly often, do you have a copy of the NEC?
Are you reasonably proficient at reading it?


Very helpful info, thank you.
I have a 1996 NEC, and I *could* be proficient at reading it if the
essentials weren't drowned in thousands of other words. But yeah, the
tables in App. B and C do get to the point.

It seems that many others have trouble reading the NEC, as there is a whole
cottage industry of workbooks and guides in how to read, understand, and use
the NEC. wow....


The NEC has been revised 4 times since your 1996 copy. Revisions can
change often used sections. And numbering in some articles has been
changed, so references may not match your copy.

The NEC is not laid out to be easy to learn (it is a reference).
Information on installing an outlet, for instance, is in buried in
several articles. Good reason for the cottage industries.


I just came home with 100 ft of 3/4 greenfield, two 500 ft rolls of #14
wire -- which, btw, just jumped $5 a roll in the past 3 days. Man, I hate
gving money to HD -- who nevertheless charge in some cases quite a bit less
than electrical supply houses for wire -- but a hair more for greenfield.


What I wrote was based on THHN insulation. That is probably what you
bought, but not necessarily. The wire is probably marked THHN/THWN. If
not, the number of wires in a conduit is likely different.

But I managed to read the wrong column for ampacity. Particularly
annoying because the value I read was not what I remembered. What I
wrote is revised below.

310.16 gives the allowable "ampacity" for the wire. Assuming it is #14
with *THHN* insulation the ampacity is 25A (but cannot be used at over 15A).

310.15(B)(2)(a) requires the ampacity to be reduced if there are more
than 3 wires in a conduit. If you have 7-9 "current-carrying" wires, the
ampacity is reduced to 70%. For #14 *THHN* the ampacity is then 17.5A
and you can still use it on a 15A circuit. You can not have more than 9
"current-carrying" #14 *THHN* wires in a conduit and connect them to a
15A breaker.

310.15(B)(4) says that the neutral of a 3 wire "Edison" circuit does not
count as one of the "current-carrying" conductors.

310.15(B)(5) says that ground wires do not count as "current-carrying"
conductors.

You can run 4 "Edison" circuits, 12 - #14 *THHN* wires (8
"current-carrying" conductors) in a single conduit. Add a #14 ground wire.

Appendix C.3 says the 13 - #14 conductors can be run in a 1/2"
Greenfield. It is the maximum number and you would have to pull the wire
carefully. With 3/4" Greenfield you shouldn't have a problem

For 2 wire circuits (if you do not combine them to be "Edison"
circuits), you can run 4 - #14 *THHN* circuits in the same conduit - 8
"current-carrying" wires plus ground = 9 wires.

--
bud--
  #13   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 2,679
Default Extending multiple BX cables: with multiple bx cables or multiplewires in greenfield?

wrote:
On Sat, 14 Nov 2009 09:07:07 -0600, bud--
wrote:

But I managed to read the wrong column for ampacity. Particularly
annoying because the value I read was not what I remembered. What I
wrote is revised below.

310.16 gives the allowable "ampacity" for the wire. Assuming it is #14
with *THHN* insulation the ampacity is 25A (but cannot be used at over 15A).

310.15(B)(2)(a) requires the ampacity to be reduced if there are more
than 3 wires in a conduit. If you have 7-9 "current-carrying" wires, the
ampacity is reduced to 70%. For #14 *THHN* the ampacity is then 17.5A
and you can still use it on a 15A circuit. You can not have more than 9
"current-carrying" #14 *THHN* wires in a conduit and connect them to a
15A breaker.

310.15(B)(4) says that the neutral of a 3 wire "Edison" circuit does not
count as one of the "current-carrying" conductors.

310.15(B)(5) says that ground wires do not count as "current-carrying"
conductors.

You can run 4 "Edison" circuits, 12 - #14 *THHN* wires (8
"current-carrying" conductors) in a single conduit. Add a #14 ground wire.

Appendix C.3 says the 13 - #14 conductors can be run in a 1/2"
Greenfield. It is the maximum number and you would have to pull the wire
carefully. With 3/4" Greenfield you shouldn't have a problem

For 2 wire circuits (if you do not combine them to be "Edison"
circuits), you can run 4 - #14 *THHN* circuits in the same conduit - 8
"current-carrying" wires plus ground = 9 wires.



When you are talking about 14, 12 and 10 gauge, don't forget 240.4(D)
that effectively limits that to 15a, 20a and 30a respectively, except
for certain fixed loads. You always have to use 240.4(D) if
receptacles or lamp holder are involved since the installer has no
control over what the user will attach..


right, but he's talking about derating because of all the wires running
in a single pipe, which uses the "real" ampacity

when the ampacity drops below 15A then you just can't put any more wires
in the pipe

nate

--
replace "roosters" with "cox" to reply.
http://members.cox.net/njnagel
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
How many 12/3 cables in 1/2" (trade) Greenfield? blueman Home Repair 6 September 3rd 08 12:20 AM
multiple RCDs Richard Tobin UK diy 16 July 3rd 08 12:12 PM
Multiple long cables in parallel. Ian Stirling UK diy 8 April 16th 06 02:38 AM
multiple roofs MarkK Home Repair 7 November 4th 05 11:32 AM
Multiple use nailer. PVR Home Repair 2 July 17th 03 11:46 AM


All times are GMT +1. The time now is 08:23 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"