Does electric box have to be right next to fixture?

The first electrician (provided by the HOA) who installed a floodlight
on my wall didn't use any electric box, afaicr. He just screwed the
fixture to the T1-11 and ran the wire through a hole in the T1, behind
the fixture.

Even though T1-11 is not very flammable???, or is it?, I presume that
is a violation of code?????


Ten years later when the fixture burned out, I suspect it was a
different electrician (although maybe from the same company) replaced
it and installed a box on the the ouside wall and then the fixture on
the box.

I need to both replace and move the fixture, and it may be much easier
to do it myself than have the HOA electician do it.

(I could put the box on the outside like it is now, but) it would be a
lot easier if I could put it on the inside, either with a hole just
big enough for the Romex, or a hole almost as big as the box, between
the fixture and the box. Are either or both of these Okay?

Thanks a lot.



  #2   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 14,845
Default Does electric box have to be right next to fixture?

On Sep 1, 2:14*pm, mm wrote:
Does electric box have to be right next to fixture?

The first electrician (provided by the HOA) who installed a floodlight
on my wall didn't use any electric box, afaicr. *He just screwed the
fixture to the T1-11 and ran the wire through a hole in the T1, behind
the fixture. *

Even though T1-11 is not very flammable???, or is it?, I presume that
is a violation of code?????

Ten years later when the fixture burned out, I suspect it was a
different electrician (although maybe from the same company) replaced
it and installed a box on the the ouside wall and then the fixture on
the box.

I need to both replace and move the fixture, and it may be much easier
to do it myself than have the HOA electician do it.

(I could put the box on the outside like it is now, but) it would be a
lot easier if I could put it on the inside, either with a hole just
big enough for the Romex, or a hole almost as big as the box, between
the fixture and the box. *Are either or both of these Okay?

Thanks a lot.


Is there a cover on the back of the fixture or is it open to the
elements?
  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,563
Default Does electric box have to be right next to fixture?


"mm" wrote in message
news
Does electric box have to be right next to fixture?

The first electrician (provided by the HOA) who installed a floodlight
on my wall didn't use any electric box, afaicr. He just screwed the
fixture to the T1-11 and ran the wire through a hole in the T1, behind
the fixture.

Even though T1-11 is not very flammable???, or is it?, I presume that
is a violation of code?????


Ten years later when the fixture burned out, I suspect it was a
different electrician (although maybe from the same company) replaced
it and installed a box on the the ouside wall and then the fixture on
the box.

I need to both replace and move the fixture, and it may be much easier
to do it myself than have the HOA electician do it.

(I could put the box on the outside like it is now, but) it would be a
lot easier if I could put it on the inside, either with a hole just
big enough for the Romex, or a hole almost as big as the box, between
the fixture and the box. Are either or both of these Okay?

Thanks a lot.


Some fixtures have integral splice boxes and can be mounted directly to
the building surface. Some fixtures require an electrical box to mount to.
If your cable will reach the location where you want to mount the fixture,
you can cut a box into the siding and mount it flush



  #4   Report Post  
Posted to alt.home.repair
mm mm is offline
external usenet poster
 
Posts: 7,824
Default Does electric box have to be right next to fixture?

On Tue, 1 Sep 2009 16:00:27 -0400, "RBM" wrote:


"mm" wrote in message
news
Does electric box have to be right next to fixture?

The first electrician (provided by the HOA) who installed a floodlight
on my wall didn't use any electric box, afaicr. He just screwed the
fixture to the T1-11 and ran the wire through a hole in the T1, behind
the fixture.

Even though T1-11 is not very flammable???, or is it?, I presume that
is a violation of code?????


Ten years later when the fixture burned out, I suspect it was a
different electrician (although maybe from the same company) replaced
it and installed a box on the the ouside wall and then the fixture on
the box.

I need to both replace and move the fixture, and it may be much easier
to do it myself than have the HOA electician do it.

(I could put the box on the outside like it is now, but) it would be a
lot easier if I could put it on the inside, either with a hole just
big enough for the Romex, or a hole almost as big as the box, between
the fixture and the box. Are either or both of these Okay?

Thanks a lot.


Derby Dad, the base of the floodlight is like a little dome, no
openings on the front, and it backs up against the wall or the
electric box. Nothing open to the elements.


Some fixtures have integral splice boxes and can be mounted directly to
the building surface. Some fixtures require an electrical box to mount to.
If your cable will reach the location where you want to mount the fixture,
you can cut a box into the siding and mount it flush


That would be hard for a couple reasons. I figured out a one-step way
I can install this from inside the attic, without borrowing a ladder,
but it requires at least a ring of T1-11 between the box and the
fixture. At least a half inch smaller than that the box or fixture
base is big. Would that be okay?


(Long tedious background not needed to answer my question: I was going
to have the HOA electrician replace the broken floodlight fixture, but
I realized I could replace bulbs or fixtures myself with a borrowed
ladder if I lowered the fixture as much as possible, 4 or 5 feet, from
shoulder or head high in the attic, to foot level. I asked for it to
be as high as it is, but I didn't foresee having to call an
electrician every time there was a problem. I can only borrow a 16
foot ladder, I think it is, and right now it needs a 20 foot ladder
just to change a bulb. I can't expect the HOA to pay to move it.

I couldn't ask the electrician to do all this, including caulk the old
holes, or let him charge the HOA for moving the fixture, so I thought
of doing the first part myself, and then thought I could do the second
part too!

I'll have to patch the 1" hole and two little screw holes that are at
the first location. I think I can unscrew the screws with a pliers
from the inside, tie a string to the fixture, cut the romex, lower the
fixture to the ground. (It's broken but the bulbs are good.) Drill
new holes at the base of the wall (just one layer of T1), lower a
string, put machine screws through the new fixture and a nut so the
screws don't come out, tie a nylon string to the fixture and lift the
fixture to the attic, maniuplate the wires through the big hole and
the screws into the two pre-drilled screw holes (this is the tricky
part) than put on washers and nuts. And I think I could do a box at
this time, but not if the hole is as big as the box.

I'm going to caulk the old holes without a ladder as follows: From
the inside, maybe I can stick my finger through the big hole to caulk
the little screw holes (I don't remember how big the hole is, etc.) If
not, I'll make some tool. To caulk the big hole, I'll get a small
piece of scrap T1-11 and make a hole of the same size. I'll put
vaseline on the edge and a little on the back. I'll clamp it to a one
foot square piece of 3/4" wood and I'll caulk the hole. Then I'll
separate the two pieces of wood and mount the 1 foot square piece to
the inside of my wall, probably with white glue with the caulk in the
original hole.

This all won't take as long as it sounds.

20 years ago, using a long flexible drill bit, to drill a hole so I
could run a piece of romex down an outside wall, from inside the
attic, which has very little eaves, and thus very little vertical
leeway, I drilled wrong and the drill came out the out side of the
house. When I had a ladder, I caulked it, from the outside, with
brown latex caulk that matched my russet brown house perfectly.
Twenty years later, the patch still hasn't shrunk and from the ground,
I can't even see where it is.
  #5   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 634
Default Does electric box have to be right next to fixture?

On 2009-09-02, mm wrote:

I can install this from inside the attic, without borrowing a ladder,
but it requires at least a ring of T1-11 between the box and the
fixture. At least a half inch smaller than that the box or fixture
base is big. Would that be okay?


No. 2008 NEC section 314.20 says "In walls and ceilings constructed
of wood or other combustible surface material, boxes, plaster rings,
extension rings, or listed extenders shall be flush with the finished
surface or project therefrom."

Cheers, Wayne


  #6   Report Post  
Posted to alt.home.repair
mm mm is offline
external usenet poster
 
Posts: 7,824
Default Does electric box have to be right next to fixture?

On Wed, 2 Sep 2009 15:59:53 +0000 (UTC), Wayne Whitney
wrote:

On 2009-09-02, mm wrote:

I can install this from inside the attic, without borrowing a ladder,
but it requires at least a ring of T1-11 between the box and the
fixture. At least a half inch smaller than that the box or fixture
base is big. Would that be okay?


No. 2008 NEC section 314.20 says "In walls and ceilings constructed
of wood or other combustible surface material, boxes, plaster rings,
extension rings, or listed extenders shall be flush with the finished
surface or project therefrom."

Cheers, Wayne


Okay. Thank you. I'll do it right, even if it requires borrowing a
ladder for the second half. I drive a LeBaron convertible, that
only takes a class 1 hitch, or whatever is the least strong. I got it
mostly to hold a bicycle rack, and I bought a one that has a square
upright-holder that screws on to the draw bar. Then with angle iron I
made a fork shaped upright with only 2 tines about 18 inches apart,
and I used a big piece of foam rubber on top of the windshield, and I
can borrow the ladder now without making my friend deliver it. At
least when the weather is good enough to put the top down. I start
off trying to make a canoe rack, and ended up with a much less
impressive ladder and pipe rack. I had no place to keep a canoe,

I bought the hitch for the first Lebaron, but I've used it on all 3
for a total of 20 years so far. I could use it on other cars too if
the struts holding the rear bumper are the same distance apart, or if
I can somehow drill another hole in the horizontal hitch bar, which is
3/8" or 1/2" thick and looks very hard.
  #7   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 130
Default Does electric box have to be right next to fixture?

In article , (mm) writes:

| I think I can unscrew the screws with a pliers
| from the inside, tie a string to the fixture, cut the romex, lower the
| fixture to the ground. (It's broken but the bulbs are good.) Drill
| new holes at the base of the wall (just one layer of T1), lower a
| string, put machine screws through the new fixture and a nut so the
| screws don't come out, tie a nylon string to the fixture and lift the
| fixture to the attic, maniuplate the wires through the big hole and
| the screws into the two pre-drilled screw holes (this is the tricky
| part) than put on washers and nuts. And I think I could do a box at
| this time, but not if the hole is as big as the box.

How about this? Fully attach the fixture to a box in advance, sealing
the unused openings with plugs and bringing a UF cable out the back with
a weather resistant clamp. Put the above machine screws through the
mounting tabs on the box. Lower the string through the central hole
(which you have made large enough to accommodate the clamp on the back of
the box) and attach it to the UF cable. Lift and position the assembly
as above. Add a splice box in the attic to connect the feed cable to
your new piece of UF.

If you really want the fixture flush you are going to have to make a
much bigger hole and you can pull the whole box in. People use non-
weather-resistant boxes in such installations but I wouldn't.

Dan Lanciani
ddl@danlan.*com
  #8   Report Post  
Posted to alt.home.repair
mm mm is offline
external usenet poster
 
Posts: 7,824
Default Does electric box have to be right next to fixture?

On 2 Sep 2009 20:45:45 GMT, ddl@danlan.*com (Dan Lanciani) wrote:

In article , (mm) writes:

| I think I can unscrew the screws with a pliers
| from the inside, tie a string to the fixture, cut the romex, lower the
| fixture to the ground. (It's broken but the bulbs are good.) Drill


Actually, everything is good except the circuit in the sensor (that
turns the light off at dawn), and for the previous fixture, that is
good but the light socket is burned. So I can combine the two to make
one.
| new holes at the base of the wall (just one layer of T1), lower a
| string, put machine screws through the new fixture and a nut so the
| screws don't come out, tie a nylon string to the fixture and lift the
| fixture to the attic, maniuplate the wires through the big hole and
| the screws into the two pre-drilled screw holes (this is the tricky
| part) than put on washers and nuts. And I think I could do a box at
| this time, but not if the hole is as big as the box.

How about this? Fully attach the fixture to a box in advance, sealing
the unused openings with plugs and bringing a UF cable out the back with
a weather resistant clamp. Put the above machine screws through the
mounting tabs on the box. Lower the string through the central hole
(which you have made large enough to accommodate the clamp on the back of
the box) and attach it to the UF cable. Lift and position the assembly
as above. Add a splice box in the attic to connect the feed cable to
your new piece of UF.


This is very good. I may do just this. Thanks. Except instead of
nuts on the screws that I suggested to hold them in place, I may put
a splinter or a split kitchen match in the hole before I shove the
screw in. That will hold the screw for a while, and I'll be providing
my own screws so if I lose one, I'll have more. And it will tighten
down better.

Or maybe a speed nut, one of those pieces of spring steel with a hole
in them that are less than a milliter thick, not counting their curve.
I save them when I take apart something that uses them.

I can screw the interior box right behind the outside box. BTW, I
think the first fixture once fell over, down, because it was only
screwed into T1-11. And the first electrician actually went up in my
attic to run the romex to my ceiling fixture, but installed no inside,
or outside, box.

Now I'm so enthusiastic I want to do this tommorrow, but first I have
to make a path to the attic hatch!

If you really want the fixture flush you are going to have to make a
much bigger hole and you can pull the whole box in. People use non-
weather-resistant boxes in such installations but I wouldn't.

Dan Lanciani
ddl@danlan.*com


  #9   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 5,040
Default Does electric box have to be right next to fixture?

In article ,
mm wrote:

I can only borrow a 16
foot ladder, I think it is, and right now it needs a 20 foot ladder
just to change a bulb.


Is there some reason a light bulb changing pole won't work? If you're
only going through this exercise to make changing light bulbs easier, it
seems like serious overkill.
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Electric fixture not working Slain Home Repair 6 April 27th 08 04:12 PM
Light/Fan Fixture Brian Staff Home Repair 5 November 13th 06 12:22 PM
fluorescent fixture Patt Home Repair 6 January 16th 06 06:42 PM
adding electric circuit for air con + general electric questions James UK diy 5 January 25th 05 10:00 PM


All times are GMT +1. The time now is 06:27 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"