I have a question that I can't seem to find an answer to.
The task is adding a new sub-panel in an outbuilding. I understand that new sub-panels now require a 4-wire feeder line, however this feeder will be coming from the service disconnect. Specifically, it will be coming from a small lug box on the side of the service disconnect; because this is how the existing outbuildings are being fed. So, my quesiton is: Is the fourth wire required in this situation, coming off the disconnect. If it is required, what is it connected to?? Thanks in advance for any advice! scrapwood. ----------------------------------- ##-----------------------------------------------## Delivered via http://www.thestuccocompany.com/ Building Construction and Maintenance Forum Web and RSS access to your favorite newsgroup - alt.home.repair - 317306 messages and counting! ##-----------------------------------------------## |
#2
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
On Oct 8, 9:36*am, (scrapwood)
wrote: I have a question that I can't seem to find an answer to. The task is adding a new sub-panel in an outbuilding. *I understand that new sub-panels now require a 4-wire feeder line, ... Run four. It never hurts to upgrade and it is always far more bother and expense to change it later when the need, that you thought would never happen, happens. |
#3
![]()
Posted to alt.home.repair
|
|||
|
|||
![]() "scrapwood" wrote in message ... I have a question that I can't seem to find an answer to. The task is adding a new sub-panel in an outbuilding. I understand that new sub-panels now require a 4-wire feeder line, however this feeder will be coming from the service disconnect. Specifically, it will be coming from a small lug box on the side of the service disconnect; because this is how the existing outbuildings are being fed. So, my quesiton is: Is the fourth wire required in this situation, coming off the disconnect. If it is required, what is it connected to?? Thanks in advance for any advice! scrapwood. ----------------------------------- ##-----------------------------------------------## Delivered via http://www.thestuccocompany.com/ Building Construction and Maintenance Forum Web and RSS access to your favorite newsgroup - alt.home.repair - 317306 messages and counting! ##-----------------------------------------------## I'm not completely sure I understand your situation, however, if this feeder to the outbuilding is connected to the "load" side of the service disconnect, it will require four wires for a 120/240 volt feeder. Two hot legs, one neutral, and one ground. You may have to drive additional ground rods at the outbuilding as well |
#4
![]()
Posted to alt.home.repair
|
|||
|
|||
![]() "RBM" wrote in message ... "scrapwood" wrote in message ... I have a question that I can't seem to find an answer to. The task is adding a new sub-panel in an outbuilding. I understand that new sub-panels now require a 4-wire feeder line, however this feeder will be coming from the service disconnect. Specifically, it will be coming from a small lug box on the side of the service disconnect; because this is how the existing outbuildings are being fed. So, my quesiton is: Is the fourth wire required in this situation, coming off the disconnect. If it is required, what is it connected to?? Thanks in advance for any advice! scrapwood. ----------------------------------- ##-----------------------------------------------## Delivered via http://www.thestuccocompany.com/ Building Construction and Maintenance Forum Web and RSS access to your favorite newsgroup - alt.home.repair - 317306 messages and counting! ##-----------------------------------------------## I'm not completely sure I understand your situation, however, if this feeder to the outbuilding is connected to the "load" side of the service disconnect, it will require four wires for a 120/240 volt feeder. Two hot legs, one neutral, and one ground. You may have to drive additional ground rods at the outbuilding as well The ground line can be bare and is sometimes wrapped around the others to make a sturdy cable. But there's another possibility if you have heavy motor loads. What you heard could apply to a 3-phase system and, specifically, a 3-phase "Y" system which has 4 wires. TKM |
#5
![]()
Posted to alt.home.repair
|
|||
|
|||
![]() "TKM" wrote in message ... "RBM" wrote in message ... "scrapwood" wrote in message ... I have a question that I can't seem to find an answer to. The task is adding a new sub-panel in an outbuilding. I understand that new sub-panels now require a 4-wire feeder line, however this feeder will be coming from the service disconnect. Specifically, it will be coming from a small lug box on the side of the service disconnect; because this is how the existing outbuildings are being fed. So, my quesiton is: Is the fourth wire required in this situation, coming off the disconnect. If it is required, what is it connected to?? Thanks in advance for any advice! scrapwood. ----------------------------------- ##-----------------------------------------------## Delivered via http://www.thestuccocompany.com/ Building Construction and Maintenance Forum Web and RSS access to your favorite newsgroup - alt.home.repair - 317306 messages and counting! ##-----------------------------------------------## I'm not completely sure I understand your situation, however, if this feeder to the outbuilding is connected to the "load" side of the service disconnect, it will require four wires for a 120/240 volt feeder. Two hot legs, one neutral, and one ground. You may have to drive additional ground rods at the outbuilding as well The ground line can be bare and is sometimes wrapped around the others to make a sturdy cable. That is not the ground. It is the neutral conductor of an "SEU" type cable But there's another possibility if you have heavy motor loads. What you heard could apply to a 3-phase system and, specifically, a 3-phase "Y" system which has 4 wires. Even if the OP had a 3 phase wye service, it would still require a fifth conductor as it would require three hot legs, one neutral, and one ground TKM |
#6
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
On Oct 8, 6:01�pm, "RBM" wrote:
"TKM" wrote in message ... "RBM" wrote in message ... "scrapwood" wrote in message .. . I have a question that I can't seem to find an answer to. The task is adding a new sub-panel in an outbuilding. �I understand that new sub-panels now require a 4-wire feeder line, however this feeder will be coming from the service disconnect. �Specifically, it will be coming from a small lug box on the side of the service disconnect; because this is how the existing outbuildings are being fed. So, my quesiton is: Is the fourth wire required in this situation, coming off the disconnect. �If it is required, what is it connected to?? Thanks in advance for any advice! scrapwood. ----------------------------------- ##-----------------------------------------------## Delivered via �http://www.thestuccocompany.com/ Building Construction and Maintenance Forum Web and RSS access to your favorite newsgroup - alt.home.repair - 317306 messages and counting! ##-----------------------------------------------## I'm not completely sure I understand your situation, however, if this feeder to the outbuilding is connected to the "load" side of the service disconnect, it will require four wires for a 120/240 volt feeder. Two hot legs, one neutral, and one ground. You may have to drive additional ground rods at the outbuilding as well The ground line can be bare and is sometimes wrapped around the others to make a sturdy cable. That is not the ground. It is the neutral conductor of an "SEU" type cable But there's another possibility if you have heavy motor loads. �What you heard could apply to a 3-phase system and, specifically, a 3-phase "Y" system which has 4 wires. Even if the OP had a 3 phase wye service, it would still require a fifth conductor as it would require three hot legs, one neutral, and one ground TKM- Hide quoted text - - Show quoted text -- Hide quoted text - - Show quoted text - or run a empty conduit for a future use. cheap choice |
#7
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
scrapwood had written this in response to
http://www.thestuccocompany.com/main...ne-335437-.htm : Thanks for all the suggestion guys. After doing further research today, and consulting a knowledgable electrician, I think I have my answer. First, I have to change out the breaker box and put a load center there so I can have three breakers. The two existing ones plus the new one. Run 3-wire with equipment ground to the new barn. Grounding rod at the sub-panel in the barn. Apparently, grounding rod at the other end is not required. . . unless of course the inspector says it is ![]() Thanks for all the suggesitons guys. I sure do appreciate it! scrapwood. ------------------------------------- ##-----------------------------------------------## Delivered via http://www.thestuccocompany.com/ Building Construction and Maintenance Forum Web and RSS access to your favorite newsgroup - alt.home.repair - 317432 messages and counting! ##-----------------------------------------------## |
#8
![]()
Posted to alt.home.repair
|
|||
|
|||
![]() "TKM" wrote in message ... "RBM" wrote in message ... "scrapwood" wrote in message ... I have a question that I can't seem to find an answer to. The task is adding a new sub-panel in an outbuilding. I understand that new sub-panels now require a 4-wire feeder line, however this feeder will be coming from the service disconnect. Specifically, it will be coming from a small lug box on the side of the service disconnect; because this is how the existing outbuildings are being fed. So, my quesiton is: Is the fourth wire required in this situation, coming off the disconnect. If it is required, what is it connected to?? Thanks in advance for any advice! scrapwood. ----------------------------------- ##-----------------------------------------------## Delivered via http://www.thestuccocompany.com/ Building Construction and Maintenance Forum Web and RSS access to your favorite newsgroup - alt.home.repair - 317306 messages and counting! ##-----------------------------------------------## I'm not completely sure I understand your situation, however, if this feeder to the outbuilding is connected to the "load" side of the service disconnect, it will require four wires for a 120/240 volt feeder. Two hot legs, one neutral, and one ground. You may have to drive additional ground rods at the outbuilding as well The ground line can be bare and is sometimes wrapped around the others to make a sturdy cable. But there's another possibility if you have heavy motor loads. What you heard could apply to a 3-phase system and, specifically, a 3-phase "Y" system which has 4 wires. TKM So, what would a delta have? My house has 240V 3 Phase Delta service, four wires come from the pole to the house. Three are standard single phase, two hot, one common. The other is the so called "wild" leg. No ground. Ground is bonded to the water line and tied to a ground rod just under the meter. Al |
#9
![]()
Posted to alt.home.repair
|
|||
|
|||
![]() Big Al wrote: "TKM" wrote in message ... "RBM" wrote in message ... "scrapwood" wrote in message ... I have a question that I can't seem to find an answer to. The task is adding a new sub-panel in an outbuilding. I understand that new sub-panels now require a 4-wire feeder line, however this feeder will be coming from the service disconnect. Specifically, it will be coming from a small lug box on the side of the service disconnect; because this is how the existing outbuildings are being fed. So, my quesiton is: Is the fourth wire required in this situation, coming off the disconnect. If it is required, what is it connected to?? Thanks in advance for any advice! scrapwood. ----------------------------------- ##-----------------------------------------------## Delivered via http://www.thestuccocompany.com/ Building Construction and Maintenance Forum Web and RSS access to your favorite newsgroup - alt.home.repair - 317306 messages and counting! ##-----------------------------------------------## I'm not completely sure I understand your situation, however, if this feeder to the outbuilding is connected to the "load" side of the service disconnect, it will require four wires for a 120/240 volt feeder. Two hot legs, one neutral, and one ground. You may have to drive additional ground rods at the outbuilding as well The ground line can be bare and is sometimes wrapped around the others to make a sturdy cable. But there's another possibility if you have heavy motor loads. What you heard could apply to a 3-phase system and, specifically, a 3-phase "Y" system which has 4 wires. TKM So, what would a delta have? My house has 240V 3 Phase Delta service, four wires come from the pole to the house. Three are standard single phase, two hot, one common. The other is the so called "wild" leg. No ground. Ground is bonded to the water line and tied to a ground rod just under the meter. Al You'd still have 5 wires feeding a sub panel, your three hots (including the "wild" one), your neutral a.k.a. your common, and the ground which is bonded to your neutral at your service entrance. The key thing here is we're talking about what is required to be feeding a sub panel, not what is feeding from the utility to your service disconnecting means. |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
![]() |
||||
Thread | Forum | |||
feeder wire for a subpanel | Home Repair | |||
in-line automatic chlorine feeder does not put in enough | Home Repair | |||
I want to wire a new line to my bathroom | Home Repair | |||
wire feeder on Tig/stick welder | Metalworking | |||
Best for Aluminum FS: Cobramatic Wire Feeder | Metalworking |