Default Electric water heater problem?????

OK folks I have repaired many electric water heaters in my 18 years as a
handyman and have never ran into one that I couldn't fix. The best part is I
am doing this for free for a friend that is out of work.

First I replaced both elements and upper/lower thermostats and flushed the
water heater because it would not make hot water. It still didn't heat the
water. I went back over today and changed them all out again and it still
doesn't work. Yes it has power to it , right up to the top element. What am
I missing?

Thanks

cm


  #2   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 75
Default Electric water heater problem?????

Most electric hot water heaters are 220, are both 110 legs providing
power? I have seen it where one 110 leg trips and the other is still
hot. You could try jumping the thermostat and see if you have hot
water. If you do, then it is a thermostat issue, if not it is power.
How is the continuity of the heater elements?
  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 120
Default Electric water heater problem?????


"CM" wrote in message
...
OK folks I have repaired many electric water heaters in my 18 years as a
handyman and have never ran into one that I couldn't fix. The best part is
I am doing this for free for a friend that is out of work.

First I replaced both elements and upper/lower thermostats and flushed the
water heater because it would not make hot water. It still didn't heat
the water. I went back over today and changed them all out again and it
still doesn't work. Yes it has power to it , right up to the top element.
What am I missing?

Thanks


I know this sounds like I am questioning your ability, but if you disconnect
the line (coming from the panel) from the heater, are you definitely getting
208/240?

Just a suggestion.....

cm


  #4   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,563
Default Electric water heater problem?????

I'm not trying to beat on you either, but the first part of a repair is to
determine what's broken. As the others have said, you need to verify 240
volts across the two upper element terminals. My guess is that you've got a
dead leg feeding the heater, which may have been the original problem. If
you do have 240 volts across the upper element, it'll heat or you have a bad
element, which is unlikely




"CM" wrote in message
...
OK folks I have repaired many electric water heaters in my 18 years as a
handyman and have never ran into one that I couldn't fix. The best part is
I am doing this for free for a friend that is out of work.

First I replaced both elements and upper/lower thermostats and flushed the
water heater because it would not make hot water. It still didn't heat
the water. I went back over today and changed them all out again and it
still doesn't work. Yes it has power to it , right up to the top element.
What am I missing?

Thanks

cm



  #5   Report Post  
Posted to alt.home.repair
cm cm is offline
external usenet poster
 
Posts: 278
Default Electric water heater problem?????

Dr.

I have not tested the power with the wires disconnected, only at the
thermostat and at the upper element and I get 220 volts. I did not think it
to test the wires while disconnected. Is that necessary??

You question my abilities/ - ha ha - Right now I question my abilities.

cm


"Dr. Hardcrab" wrote in message
news:V7chj.182919$TO.180126@trnddc01...

"CM" wrote in message
...
OK folks I have repaired many electric water heaters in my 18 years as a
handyman and have never ran into one that I couldn't fix. The best part
is I am doing this for free for a friend that is out of work.

First I replaced both elements and upper/lower thermostats and flushed
the water heater because it would not make hot water. It still didn't
heat the water. I went back over today and changed them all out again and
it still doesn't work. Yes it has power to it , right up to the top
element. What am I missing?

Thanks


I know this sounds like I am questioning your ability, but if you
disconnect the line (coming from the panel) from the heater, are you
definitely getting 208/240?

Just a suggestion.....

cm






  #6   Report Post  
Posted to alt.home.repair
cm cm is offline
external usenet poster
 
Posts: 278
Default Electric water heater problem?????


"komobu" wrote in message
...
Most electric hot water heaters are 220, are both 110 legs providing
power? I have seen it where one 110 leg trips and the other is still
hot. You could try jumping the thermostat and see if you have hot
water. If you do, then it is a thermostat issue, if not it is power.
How is the continuity of the heater elements?


komobu,

I have 220 volts at the thermostat and at the upper element so I assume 1/2
the breaker is not tripped. I will try jumping the thermostat.

Thanks,

cm


  #7   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 120
Default Electric water heater problem?????


"RBM" wrote in message
...
I'm not trying to beat on you either, but the first part of a repair is to
determine what's broken. As the others have said, you need to verify 240
volts across the two upper element terminals. My guess is that you've got
a dead leg feeding the heater, which may have been the original problem.
If you do have 240 volts across the upper element, it'll heat or you have
a bad element, which is unlikely



You explained better than I did.

I've seen many techs take out their meters and check one termimal to ground
("Hmmmm....120....that's good...") and then check the other and get the same
thing and think everything is hunky dorey (What exactly *IS* a dorey and how
did it get so hunky?)






"CM" wrote in message
...
OK folks I have repaired many electric water heaters in my 18 years as a
handyman and have never ran into one that I couldn't fix. The best part
is I am doing this for free for a friend that is out of work.

First I replaced both elements and upper/lower thermostats and flushed
the water heater because it would not make hot water. It still didn't
heat the water. I went back over today and changed them all out again and
it still doesn't work. Yes it has power to it , right up to the top
element. What am I missing?

Thanks

cm




  #8   Report Post  
Posted to alt.home.repair
cm cm is offline
external usenet poster
 
Posts: 278
Default Electric water heater problem?????

RBM,

I have 220 volts at the t-stat and the upper element. I removed the upper
element earlier today to check its condition and continuity and it was fine.

Thanks,

Craig


"RBM" wrote in message
...
I'm not trying to beat on you either, but the first part of a repair is to
determine what's broken. As the others have said, you need to verify 240
volts across the two upper element terminals. My guess is that you've got
a dead leg feeding the heater, which may have been the original problem.
If you do have 240 volts across the upper element, it'll heat or you have
a bad element, which is unlikely




"CM" wrote in message
...
OK folks I have repaired many electric water heaters in my 18 years as a
handyman and have never ran into one that I couldn't fix. The best part
is I am doing this for free for a friend that is out of work.

First I replaced both elements and upper/lower thermostats and flushed
the water heater because it would not make hot water. It still didn't
heat the water. I went back over today and changed them all out again and
it still doesn't work. Yes it has power to it , right up to the top
element. What am I missing?

Thanks

cm





  #9   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,563
Default Electric water heater problem?????

Forget the thermostat. There are two terminals on the element. When you test
across those two terminals, do you get 240 volts?




"CM" wrote in message
news
RBM,

I have 220 volts at the t-stat and the upper element. I removed the upper
element earlier today to check its condition and continuity and it was
fine.

Thanks,

Craig


"RBM" wrote in message
...
I'm not trying to beat on you either, but the first part of a repair is
to determine what's broken. As the others have said, you need to verify
240 volts across the two upper element terminals. My guess is that you've
got a dead leg feeding the heater, which may have been the original
problem. If you do have 240 volts across the upper element, it'll heat or
you have a bad element, which is unlikely




"CM" wrote in message
...
OK folks I have repaired many electric water heaters in my 18 years as a
handyman and have never ran into one that I couldn't fix. The best part
is I am doing this for free for a friend that is out of work.

First I replaced both elements and upper/lower thermostats and flushed
the water heater because it would not make hot water. It still didn't
heat the water. I went back over today and changed them all out again
and it still doesn't work. Yes it has power to it , right up to the top
element. What am I missing?

Thanks

cm







  #10   Report Post  
Posted to alt.home.repair
cm cm is offline
external usenet poster
 
Posts: 278
Default Electric water heater problem?????

Yup.

cm


"RBM" wrote in message
...
Forget the thermostat. There are two terminals on the element. When you
test across those two terminals, do you get 240 volts?




"CM" wrote in message
news
RBM,

I have 220 volts at the t-stat and the upper element. I removed the upper
element earlier today to check its condition and continuity and it was
fine.

Thanks,

Craig


"RBM" wrote in message
...
I'm not trying to beat on you either, but the first part of a repair is
to determine what's broken. As the others have said, you need to verify
240 volts across the two upper element terminals. My guess is that
you've got a dead leg feeding the heater, which may have been the
original problem. If you do have 240 volts across the upper element,
it'll heat or you have a bad element, which is unlikely




"CM" wrote in message
...
OK folks I have repaired many electric water heaters in my 18 years as
a handyman and have never ran into one that I couldn't fix. The best
part is I am doing this for free for a friend that is out of work.

First I replaced both elements and upper/lower thermostats and flushed
the water heater because it would not make hot water. It still didn't
heat the water. I went back over today and changed them all out again
and it still doesn't work. Yes it has power to it , right up to the
top element. What am I missing?

Thanks

cm











  #11   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,563
Default Electric water heater problem?????

It would be good if you had an ammeter, which would tell you if there is any
current flowing. I had a situation one time very similar to yours. The wires
in the heater go from the junction box on top of the heater through foam
insulation to the upper thermostat. One of the two wires burned in half
imbedded in the foam insulation. Through the moisture and carbonized copper
I got a 240 volt reading at the upper thermostat and element, but the
element of course wouldn't heat. Barring a bad meter, I would try to
physically check the condition of the wires inside the heater

"CM" wrote in message
...
Yup.

cm


"RBM" wrote in message
...
Forget the thermostat. There are two terminals on the element. When you
test across those two terminals, do you get 240 volts?




"CM" wrote in message
news
RBM,

I have 220 volts at the t-stat and the upper element. I removed the
upper element earlier today to check its condition and continuity and it
was fine.

Thanks,

Craig


"RBM" wrote in message
...
I'm not trying to beat on you either, but the first part of a repair is
to determine what's broken. As the others have said, you need to verify
240 volts across the two upper element terminals. My guess is that
you've got a dead leg feeding the heater, which may have been the
original problem. If you do have 240 volts across the upper element,
it'll heat or you have a bad element, which is unlikely




"CM" wrote in message
...
OK folks I have repaired many electric water heaters in my 18 years as
a handyman and have never ran into one that I couldn't fix. The best
part is I am doing this for free for a friend that is out of work.

First I replaced both elements and upper/lower thermostats and flushed
the water heater because it would not make hot water. It still didn't
heat the water. I went back over today and changed them all out again
and it still doesn't work. Yes it has power to it , right up to the
top element. What am I missing?

Thanks

cm











  #12   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,563
Default Electric water heater problem?????

Another thing CM, we out here in the ether, have no idea of how you are
testing . Like Dr. Hardcrab said. you could be testing each terminal to
ground and getting 120 volts on each, multiply that time 2, you get 240




"CM" wrote in message
...
OK folks I have repaired many electric water heaters in my 18 years as a
handyman and have never ran into one that I couldn't fix. The best part is
I am doing this for free for a friend that is out of work.

First I replaced both elements and upper/lower thermostats and flushed the
water heater because it would not make hot water. It still didn't heat
the water. I went back over today and changed them all out again and it
still doesn't work. Yes it has power to it , right up to the top element.
What am I missing?

Thanks

cm



  #13   Report Post  
Posted to alt.home.repair
cm cm is offline
external usenet poster
 
Posts: 278
Default Electric water heater problem?????

RBM,

I will check them in the morning.

I just got off the phone with the home owner and she says there is a warm
spot on the vinyl covered concrete floor near her kitchen sink. I think she
may have a leaking hot water pipe under the slab. I'll check all this out in
the morning.

Thanks so much,

cm


"RBM" wrote in message
...
It would be good if you had an ammeter, which would tell you if there is
any current flowing. I had a situation one time very similar to yours. The
wires in the heater go from the junction box on top of the heater through
foam insulation to the upper thermostat. One of the two wires burned in
half imbedded in the foam insulation. Through the moisture and carbonized
copper I got a 240 volt reading at the upper thermostat and element, but
the element of course wouldn't heat. Barring a bad meter, I would try to
physically check the condition of the wires inside the heater

"CM" wrote in message
...
Yup.

cm


"RBM" wrote in message
...
Forget the thermostat. There are two terminals on the element. When you
test across those two terminals, do you get 240 volts?




"CM" wrote in message
news RBM,

I have 220 volts at the t-stat and the upper element. I removed the
upper element earlier today to check its condition and continuity and
it was fine.

Thanks,

Craig


"RBM" wrote in message
...
I'm not trying to beat on you either, but the first part of a repair
is to determine what's broken. As the others have said, you need to
verify 240 volts across the two upper element terminals. My guess is
that you've got a dead leg feeding the heater, which may have been the
original problem. If you do have 240 volts across the upper element,
it'll heat or you have a bad element, which is unlikely




"CM" wrote in message
...
OK folks I have repaired many electric water heaters in my 18 years
as a handyman and have never ran into one that I couldn't fix. The
best part is I am doing this for free for a friend that is out of
work.

First I replaced both elements and upper/lower thermostats and
flushed the water heater because it would not make hot water. It
still didn't heat the water. I went back over today and changed them
all out again and it still doesn't work. Yes it has power to it ,
right up to the top element. What am I missing?

Thanks

cm













  #14   Report Post  
Posted to alt.home.repair
cm cm is offline
external usenet poster
 
Posts: 278
Default Electric water heater problem?????

I am testing across the terminal - not to ground so I am getting 220 volts
on my digital meter. I will also take a back up meter tomorrow.

If it is fact an under slab leak the water could just be running through the
water heater and not sitting long enough to heat. Should be easy to check.

cm


"RBM" wrote in message
...
Another thing CM, we out here in the ether, have no idea of how you are
testing . Like Dr. Hardcrab said. you could be testing each terminal to
ground and getting 120 volts on each, multiply that time 2, you get 240




"CM" wrote in message
...
OK folks I have repaired many electric water heaters in my 18 years as a
handyman and have never ran into one that I couldn't fix. The best part
is I am doing this for free for a friend that is out of work.

First I replaced both elements and upper/lower thermostats and flushed
the water heater because it would not make hot water. It still didn't
heat the water. I went back over today and changed them all out again and
it still doesn't work. Yes it has power to it , right up to the top
element. What am I missing?

Thanks

cm





  #15   Report Post  
Posted to alt.home.repair
cm cm is offline
external usenet poster
 
Posts: 278
Default Electric water heater problem?????



When you check the voltage, what kind of meter are you using? Are you
testing it with it connected to the heating element and with the
thermostat calling for heat?

Have you checked power to the lower thermostat?


--
Joseph Meehan

Dia 's Muire duit




Joseph,

I am using a Greenlee multimeter (digital) and have only tested voltage with
the wires connected to the element as well as the thermostat and it shows
220 volts at the upper thermostat and the upper heating element and no power
to the lower thermostat or lower element. I assume the upper thermostat is
calling for heat since the tank is not hot. The top thermostat is not
sending power to the lower since upper thermostat is not satisfied.

I am going to check the voltage coming into the water heater with the wires
disconnected tomorrow and will do the same to the wires that go to the upper
element. I will also check the water meter and see if it is spinning with
all faucets shut off to see if there is a possibility of an under slab pipe
leak.

Thanks for your help on this,

Craig




  #16   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 674
Default Electric water heater problem?????


"CM" wrote in message
...
I am testing across the terminal - not to ground so I am getting 220 volts
on my digital meter. I will also take a back up meter tomorrow.

If it is fact an under slab leak the water could just be running through
the water heater and not sitting long enough to heat. Should be easy to
check.

cm


"RBM" wrote in message
...
Another thing CM, we out here in the ether, have no idea of how you are
testing . Like Dr. Hardcrab said. you could be testing each terminal to
ground and getting 120 volts on each, multiply that time 2, you get 240




"CM" wrote in message
...
OK folks I have repaired many electric water heaters in my 18 years as a
handyman and have never ran into one that I couldn't fix. The best part
is I am doing this for free for a friend that is out of work.

First I replaced both elements and upper/lower thermostats and flushed
the water heater because it would not make hot water. It still didn't
heat the water. I went back over today and changed them all out again
and it still doesn't work. Yes it has power to it , right up to the top
element. What am I missing?

Thanks

cm





A leak under the slab is a common cause of all of your symptoms. The warm
spot on the floor is a sure sign. If at all feasible, replace under-slab
plumbing with plumbing above the slab.

Don Young


  #17   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 216
Default Electric water heater problem?????

On Wed, 09 Jan 2008 23:22:32 GMT, "Dr. Hardcrab"
wrote:


"RBM" wrote in message
...
I'm not trying to beat on you either, but the first part of a repair is to
determine what's broken. As the others have said, you need to verify 240
volts across the two upper element terminals. My guess is that you've got
a dead leg feeding the heater, which may have been the original problem.
If you do have 240 volts across the upper element, it'll heat or you have
a bad element, which is unlikely



You explained better than I did.

I've seen many techs take out their meters and check one termimal to ground
("Hmmmm....120....that's good...") and then check the other and get the same
thing and think everything is hunky dorey (What exactly *IS* a dorey and how
did it get so hunky?)


A dorey is a small boat.






"CM" wrote in message
...
OK folks I have repaired many electric water heaters in my 18 years as a
handyman and have never ran into one that I couldn't fix. The best part
is I am doing this for free for a friend that is out of work.

First I replaced both elements and upper/lower thermostats and flushed
the water heater because it would not make hot water. It still didn't
heat the water. I went back over today and changed them all out again and
it still doesn't work. Yes it has power to it , right up to the top
element. What am I missing?

Thanks

cm



  #18   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 165
Default Electric water heater problem?????

A slab leak is a possibility, which should not be that hard to
determine. If large enough to cause the problem, you should probably be
able to hear water running through the pipes and tank. Otherwise, see if
the water meter is turning with everything off, or the pump cycling if
it is on a well. I ran into a similar situation some years ago with a
friend's gas WH. Turned out the Moen cartridge at the bathtub was bad.
The water would take the path of least resistance, so any time a hot
water faucet was opened, the water would feed through that cartridge
rather than the WH. He had already bought a new WH, and I was going to
install it for him. I turned the valve off in the cold water inlet to
the WH and opened the drain valve. Not only was the water in the tank
hot, but the pressure in it never dropped. Finally took the hot water
line loose at the WH, and water was coming out of the line, but not out
of the WH. He took the new WH back and got a refund on it. Good luck
Larry

  #19   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 120
Default Electric water heater problem?????


"Sam E" wrote in message
...
On Wed, 09 Jan 2008 23:22:32 GMT, "Dr. Hardcrab"
wrote:


"RBM" wrote in message
...
I'm not trying to beat on you either, but the first part of a repair is
to
determine what's broken. As the others have said, you need to verify 240
volts across the two upper element terminals. My guess is that you've
got
a dead leg feeding the heater, which may have been the original problem.
If you do have 240 volts across the upper element, it'll heat or you
have
a bad element, which is unlikely



You explained better than I did.

I've seen many techs take out their meters and check one termimal to
ground
("Hmmmm....120....that's good...") and then check the other and get the
same
thing and think everything is hunky dorey (What exactly *IS* a dorey and
how
did it get so hunky?)


A dorey is a small boat.


Hmmmmm.......so that's why my wife laughs and points
and.......nevermind.......

  #20   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 120
Default Electric water heater problem?????

Damn! Let us know what you find out. I'm curious as hell now!!

(Ghosts in the machine)


"CM" wrote in message
...


When you check the voltage, what kind of meter are you using? Are you
testing it with it connected to the heating element and with the
thermostat calling for heat?

Have you checked power to the lower thermostat?


--
Joseph Meehan

Dia 's Muire duit




Joseph,

I am using a Greenlee multimeter (digital) and have only tested voltage
with the wires connected to the element as well as the thermostat and it
shows 220 volts at the upper thermostat and the upper heating element and
no power to the lower thermostat or lower element. I assume the upper
thermostat is calling for heat since the tank is not hot. The top
thermostat is not sending power to the lower since upper thermostat is not
satisfied.

I am going to check the voltage coming into the water heater with the
wires disconnected tomorrow and will do the same to the wires that go to
the upper element. I will also check the water meter and see if it is
spinning with all faucets shut off to see if there is a possibility of an
under slab pipe leak.

Thanks for your help on this,

Craig


Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Electric Water Heater Grounded to Copper Water Pipes? [email protected] Home Repair 4 October 30th 05 06:23 PM
Problem with new water heater (electric) - please advice Robert Home Repair 8 February 19th 04 05:27 AM
Problem with new water heater (electric) - please advice Robert Home Ownership 8 February 19th 04 05:27 AM
Electric Water Heater Problem, Repair or Buy new, please help Robert Home Repair 10 January 10th 04 01:09 AM
Electric Water Heater Problem, Repair or Buy new, please help Robert Home Ownership 9 January 10th 04 01:09 AM


All times are GMT +1. The time now is 06:49 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"