We recently remodeled my in-laws bathroom and, as per code, the entire 20
amp bathroom circuit is protected by a 20A GFCI outlet. Everything was inspected and functions as it should. Unfortunately, the GFCI is tripping occasionally when the bathroom vent fan is turned "off". It never trips when turning on the fan, only when turning it off. And, it may go a few weeks before it trips, and then suddenly trip three times in a row. Then it'll work fine again for a few weeks. I suspected a bad GFCI, so I replaced it with a new one, and also replaced the switch that controls the fan. It doesn't seem to trip as often now, but it tripped for me again last night when we were visiting. The only remaining item seems to be the fan itself, but I'm curious if there's some other possible cause I might be overlooking? The fan has been installed for a few months now, so I probably can't return it at this point. I thought maybe condensation from moisture draining back through the vent pipe (it had to be routed up over a beam to get out through the side wall). But, the tripping doesn't really seem to be related to when the shower was used recently. Thoughts? Anthony |
#2
Posted to alt.home.repair
|
|||
|
|||
GFCI Tripping Repeatedly?
HerHusband wrote:
We recently remodeled my in-laws bathroom and, as per code, the entire 20 amp bathroom circuit is protected by a 20A GFCI outlet. Everything was inspected and functions as it should. Unfortunately, the GFCI is tripping occasionally when the bathroom vent fan is turned "off". It never trips when turning on the fan, only when turning it off. And, it may go a few weeks before it trips, and then suddenly trip three times in a row. Then it'll work fine again for a few weeks. I suspected a bad GFCI, so I replaced it with a new one, and also replaced the switch that controls the fan. It doesn't seem to trip as often now, but it tripped for me again last night when we were visiting. The only remaining item seems to be the fan itself, but I'm curious if there's some other possible cause I might be overlooking? The fan has been installed for a few months now, so I probably can't return it at this point. I thought maybe condensation from moisture draining back through the vent pipe (it had to be routed up over a beam to get out through the side wall). But, the tripping doesn't really seem to be related to when the shower was used recently. Thoughts? Anthony Hi, Probably motor body and fan enclosure does not have or have poor ground? |
#3
Posted to alt.home.repair
|
|||
|
|||
GFCI Tripping Repeatedly?
On Dec 24, 7:30 am, HerHusband wrote:
We recently remodeled my in-laws bathroom and, as per code, the entire 20 amp bathroom circuit is protected by a 20A GFCI outlet. Everything was inspected and functions as it should. Unfortunately, the GFCI is tripping occasionally when the bathroom vent fan is turned "off". It never trips when turning on the fan, only when turning it off. And, it may go a few weeks before it trips, and then suddenly trip three times in a row. Then it'll work fine again for a few weeks. I suspected a bad GFCI, so I replaced it with a new one, and also replaced the switch that controls the fan. It doesn't seem to trip as often now, but it tripped for me again last night when we were visiting. The only remaining item seems to be the fan itself, but I'm curious if there's some other possible cause I might be overlooking? The fan has been installed for a few months now, so I probably can't return it at this point. I thought maybe condensation from moisture draining back through the vent pipe (it had to be routed up over a beam to get out through the side wall). But, the tripping doesn't really seem to be related to when the shower was used recently. Thoughts? Anthony I have had trouble with motor loads tripping GFI's. The fact that it trips when the fan is turned "off" leads me to believe what you're seeing is not a true ground fault (current leakage to ground) but "merely" a difference between the instantaneous currents on the hot & neutral wires. I'm an ME but I did study some motor & circuit stuff in school.......here's my best attempt at an explanation, when the fan is turned off, the magnetic field of the windings of the motor collapses & induces a current back thru the neutral (since the hot lead is switched & therefore open). The GFI senses this slight current as mismatch between hot & neutral currents & trios. cheers Bob |
#4
Posted to alt.home.repair
|
|||
|
|||
GFCI Tripping Repeatedly?
On 2007-12-24, BobK207 wrote:
I have had trouble with motor loads tripping GFI's. The fact that it trips when the fan is turned "off" leads me to believe what you're seeing is not a true ground fault (current leakage to ground) but "merely" a difference between the instantaneous currents on the hot & neutral wires. I'm an ME but I did study some motor & circuit stuff in school.......here's my best attempt at an explanation, when the fan is turned off, the magnetic field of the windings of the motor collapses & induces a current back thru the neutral (since the hot lead is switched & therefore open). The GFI senses this slight current as mismatch between hot & neutral currents & trios. Hi Bob, If this is the story, what is the proper way to deal with this? Is there a type of motor that can be specified and which would minimize this effect? Would it be acceptable practice to switch both the neutral and hot to the motor? If so do double pole switches break both connections sufficiently close to simultaneously to avoid the induced current imbalance? Thanks, Wayne |
#5
Posted to alt.home.repair
|
|||
|
|||
GFCI Tripping Repeatedly?
"HerHusband" wrote in message ... We recently remodeled my in-laws bathroom and, as per code, the entire 20 amp bathroom circuit is protected by a 20A GFCI outlet. Everything was inspected and functions as it should. Unfortunately, the GFCI is tripping occasionally when the bathroom vent fan is turned "off". It never trips when turning on the fan, only when turning it off. And, it may go a few weeks before it trips, and then suddenly trip three times in a row. Then it'll work fine again for a few weeks. I suspected a bad GFCI, so I replaced it with a new one, and also replaced the switch that controls the fan. It doesn't seem to trip as often now, but it tripped for me again last night when we were visiting. The only remaining item seems to be the fan itself, but I'm curious if there's some other possible cause I might be overlooking? The fan has been installed for a few months now, so I probably can't return it at this point. I thought maybe condensation from moisture draining back through the vent pipe (it had to be routed up over a beam to get out through the side wall). But, the tripping doesn't really seem to be related to when the shower was used recently. The fan isn't required to be on a GFI protected circuit unless it is in the shower/tub space. I'm not sure what could be causing your problem. Maybe try installing a two pole switch so that the hot and the neutral are being disconnected at the same time. |
#6
Posted to alt.home.repair
|
|||
|
|||
GFCI Tripping Repeatedly?
"HerHusband" wrote in message ... We recently remodeled my in-laws bathroom and, as per code, the entire 20 amp bathroom circuit is protected by a 20A GFCI outlet. Everything was inspected and functions as it should. Unfortunately, the GFCI is tripping occasionally when the bathroom vent fan is turned "off". It never trips when turning on the fan, only when turning it off. And, it may go a few weeks before it trips, and then suddenly trip three times in a row. Then it'll work fine again for a few weeks. I suspected a bad GFCI, so I replaced it with a new one, and also replaced the switch that controls the fan. It doesn't seem to trip as often now, but it tripped for me again last night when we were visiting. The only remaining item seems to be the fan itself, but I'm curious if there's some other possible cause I might be overlooking? The fan has been installed for a few months now, so I probably can't return it at this point. I thought maybe condensation from moisture draining back through the vent pipe (it had to be routed up over a beam to get out through the side wall). But, the tripping doesn't really seem to be related to when the shower was used recently. Thoughts? Anthony Why connect the fan to the GFI at all? Is it a requirement in your locality? |
#7
Posted to alt.home.repair
|
|||
|
|||
GFCI Tripping Repeatedly?
This is not an uncommon anomaly. As others have said, the NEC doesn't
require GFCI protection for the fan unless it's located over the tub, and the manufacturer requires it "HerHusband" wrote in message ... We recently remodeled my in-laws bathroom and, as per code, the entire 20 amp bathroom circuit is protected by a 20A GFCI outlet. Everything was inspected and functions as it should. Unfortunately, the GFCI is tripping occasionally when the bathroom vent fan is turned "off". It never trips when turning on the fan, only when turning it off. And, it may go a few weeks before it trips, and then suddenly trip three times in a row. Then it'll work fine again for a few weeks. I suspected a bad GFCI, so I replaced it with a new one, and also replaced the switch that controls the fan. It doesn't seem to trip as often now, but it tripped for me again last night when we were visiting. The only remaining item seems to be the fan itself, but I'm curious if there's some other possible cause I might be overlooking? The fan has been installed for a few months now, so I probably can't return it at this point. I thought maybe condensation from moisture draining back through the vent pipe (it had to be routed up over a beam to get out through the side wall). But, the tripping doesn't really seem to be related to when the shower was used recently. Thoughts? Anthony |
#8
Posted to alt.home.repair
|
|||
|
|||
GFCI Tripping Repeatedly?
On Dec 24, 10:30*am, HerHusband wrote:
We recently remodeled my in-laws bathroom and, as per code, the entire 20 amp bathroom circuit is protected by a 20A GFCI outlet. Everything was inspected and functions as it should. Unfortunately, the GFCI is tripping occasionally when the bathroom vent fan is turned "off". It never trips when turning on the fan, only when turning it off. And, it may go a few weeks before it trips, and then suddenly trip three times in a row. Then it'll work fine again for a few weeks. I suspected a bad GFCI, so I replaced it with a new one, and also replaced the switch that controls the fan. It doesn't seem to trip as often now, but it tripped for me again last night when we were visiting. The only remaining item seems to be the fan itself, but I'm curious if there's some other possible cause I might be overlooking? The fan has been installed for a few months now, so I probably can't return it at this point. I thought maybe condensation from moisture draining back through the vent pipe (it had to be routed up over a beam to get out through the side wall).. But, the tripping doesn't really seem to be related to when the shower was used recently. Thoughts? Anthony I had this same problem a while back with my bath fan. The problem was a minor leak from the roof vent. Fixed leak. Haven't had this problem since. |
#9
Posted to alt.home.repair
|
|||
|
|||
GFCI Tripping Repeatedly?
On Dec 24, 11:34 am, "HeyBub" wrote:
BobK207 wrote: I have had trouble with motor loads tripping GFI's. The fact that it trips when the fan is turned "off" leads me to believe what you're seeing is not a true ground fault (current leakage to ground) but "merely" a difference between the instantaneous currents on the hot & neutral wires. I'm an ME but I did study some motor & circuit stuff in school.......here's my best attempt at an explanation, when the fan is turned off, the magnetic field of the windings of the motor collapses & induces a current back thru the neutral (since the hot lead is switched & therefore open). The field collapses 60 times a second when running... yeah but BOTH the hot & the neutral are still connected when the fan is running..... I believe it is the "collapse" with the hot open & the neutral still connected that causes the problem for the GFI current sensing circuit. My comments were meant to provide a plausible reason for the behavior "GFI trip on fan shutdown" & your theory is? Sounds like Doug's comment that its ok to switch both should solve the issue. OP- Is the fan / switch wiring such that you can easily install a DPST switch and switch the hot & the neutral to the fan? cheers Bob |
#10
Posted to alt.home.repair
|
|||
|
|||
GFCI Tripping Repeatedly?
I have had trouble with motor loads tripping GFI's.
The fact that it trips when the fan is turned "off" leads me to believe what you're seeing is not a true ground fault (current leakage to ground) but "merely" a difference between the instantaneous currents on the hot & neutral wires. I was afraid of something like that. At this point, there's not much I can do to rewire the fan to be off the GFCI. Is the fan / switch wiring such that you can easily install a DPST switch and switch the hot & the neutral to the fan? Yes, I could install a DPST, but I can't say I've seen them in stores? Then again, I've never really been looking for them. Anthony |
#11
Posted to alt.home.repair
|
|||
|
|||
GFCI Tripping Repeatedly?
This is not an uncommon anomaly. As others have said, the NEC doesn't
require GFCI protection for the fan unless it's located over the tub, and the manufacturer requires it Well, good to know, but a little too late. It had been my understanding that the entire bathroom circuit needed to be protected by the GFCI. But the inspector mentioned a couple of things that didn't need to be on it also. Oh well, no harm done, except for the fan nuisance. The DPST switch idea sounds like my best option if I can find one. Anthony |
#12
Posted to alt.home.repair
|
|||
|
|||
GFCI Tripping Repeatedly?
Roger,
I had this same problem a while back with my bath fan. The problem was a minor leak from the roof vent. Fixed leak. Haven't had this problem since. My in-laws just had a new roof installed, so I didn't want to cut any holes and risk causing a leak. So we routed the duct out through a sidewall. Except for a short bump up over a beam, the 8' duct slopes mostly towards the outside wall vent. So, there's no chance of a leak, other than maybe condensation working it's way back. However, the tripping doesn't seem to be related to shower usage, which makes me doubtful of a moisture related cause. Anthony |
#13
Posted to alt.home.repair
|
|||
|
|||
GFCI Tripping Repeatedly?
On Dec 25, 9:08 am, HerHusband wrote:
I have had trouble with motor loads tripping GFI's. The fact that it trips when the fan is turned "off" leads me to believe what you're seeing is not a true ground fault (current leakage to ground) but "merely" a difference between the instantaneous currents on the hot & neutral wires. I was afraid of something like that. At this point, there's not much I can do to rewire the fan to be off the GFCI. Is the fan / switch wiring such that you can easily install a DPST switch and switch the hot & the neutral to the fan? Yes, I could install a DPST, but I can't say I've seen them in stores? Then again, I've never really been looking for them. Anthony Anthony- If you have a Home Depot near by, they probably have the DPST here's a link to listing of the Leviton double pole products (white), HD (at least in my area) stocks Leviton products http://www.leviton.com/OA_HTML/xxlcf...20&st=kw&cpg=0 the 1202-2W switch looks to be the one you'd want. The DPST solution will only work IF the neutral to the fan comes from the switch box & can be safely broken there. cheers Bob |
#14
Posted to alt.home.repair
|
|||
|
|||
GFCI Tripping Repeatedly?
Bob,
Thanks for the info! If you have a Home Depot near by, they probably have the DPST We have a couple of HD's and a Lowes nearby. I'll have a look next time I'm there. I've never had a need for them before, so I've probably looked over them and didn't know it. The DPST solution will only work IF the neutral to the fan comes from the switch box & can be safely broken there. Yep, the power comes into the 3-gang switch box, then separate cables run to the fans and lights. It'll be no problem switching to the DPST switch. I'll have to wait and see if changing the switch will prevent the GFCI from tripping when the fan is turned off, but it's a relatively simple and inexpensive thing to try. Thanks for the tip. Anthony |
#15
Posted to alt.home.repair
|
|||
|
|||
GFCI Tripping Repeatedly?
On Mon, 24 Dec 2007 16:23:28 GMT, Wayne Whitney
wrote: Hi Bob, If this is the story, what is the proper way to deal with this? Is there a type of motor that can be specified and which would minimize this effect? Would it be acceptable practice to switch both the neutral and hot to the motor? If so do double pole switches break both connections sufficiently close to simultaneously to avoid the induced current imbalance? Thanks, Wayne An easy "try this" will be to swap out the washroom fan with a new one or one from another bathroom. The puzzling thing is the exhaust fan motor draws so little power that even stopping the motor by hand should not cause any circuit hiccups (and will not cause the motor to overheat.) |
#16
Posted to alt.home.repair
|
|||
|
|||
GFCI Tripping Repeatedly?
"HerHusband" wrote in message ... Bob, Thanks for the info! If you have a Home Depot near by, they probably have the DPST We have a couple of HD's and a Lowes nearby. I'll have a look next time I'm there. I've never had a need for them before, so I've probably looked over them and didn't know it. The DPST solution will only work IF the neutral to the fan comes from the switch box & can be safely broken there. Yep, the power comes into the 3-gang switch box, then separate cables run to the fans and lights. It'll be no problem switching to the DPST switch. I'll have to wait and see if changing the switch will prevent the GFCI from tripping when the fan is turned off, but it's a relatively simple and inexpensive thing to try. Thanks for the tip. If the GFCI is in the same three gang box as the switch for the fan and lights you should be able to reconfigure the wiring to eliminate the light and fan from the GFCI protection. |
#17
Posted to alt.home.repair
|
|||
|
|||
GFCI Tripping Repeatedly?
HerHusband wrote:
We recently remodeled my in-laws bathroom and, as per code, the entire 20 amp bathroom circuit is protected by a 20A GFCI outlet. Everything was inspected and functions as it should. Unfortunately, the GFCI is tripping occasionally when the bathroom vent fan is turned "off". It never trips when turning on the fan, only when turning it off. And, it may go a few weeks before it trips, and then suddenly trip three times in a row. Then it'll work fine again for a few weeks. I suspected a bad GFCI, so I replaced it with a new one, and also replaced the switch that controls the fan. It doesn't seem to trip as often now, but it tripped for me again last night when we were visiting. The only remaining item seems to be the fan itself, but I'm curious if there's some other possible cause I might be overlooking? The fan has been installed for a few months now, so I probably can't return it at this point. I thought maybe condensation from moisture draining back through the vent pipe (it had to be routed up over a beam to get out through the side wall). But, the tripping doesn't really seem to be related to when the shower was used recently. Thoughts? Anthony I am skeptical that a properly working fan should trip a properly working GFCI when the fan is turned off. If there is no ground fault in the fan or switch, there can be no imbalance of currents (conservation of electrons). A double pole switch should not make a difference. I might suggest an intermittent ground fault in the fan or switch when the fan is turned off. Please let us know what the problem is/was when/if you figure it out. |
#18
Posted to alt.home.repair
|
|||
|
|||
GFCI Tripping Repeatedly?
HerHusband wrote:
Bob, Thanks for the info! If you have a Home Depot near by, they probably have the DPST We have a couple of HD's and a Lowes nearby. I'll have a look next time I'm there. I've never had a need for them before, so I've probably looked over them and didn't know it. The DPST solution will only work IF the neutral to the fan comes from the switch box & can be safely broken there. Yep, the power comes into the 3-gang switch box, then separate cables run to the fans and lights. It'll be no problem switching to the DPST switch. I'll have to wait and see if changing the switch will prevent the GFCI from tripping when the fan is turned off, but it's a relatively simple and inexpensive thing to try. Thanks for the tip. Anthony I think you'll be shocked at what they charge for a DPST. -- The e-mail address in our reply-to line is reversed in an attempt to minimize spam. Our true address is of the form . |
#19
Posted to alt.home.repair
|
|||
|
|||
GFCI Tripping Repeatedly?
On Dec 26, 1:06 pm, M Q wrote:
HerHusband wrote: We recently remodeled my in-laws bathroom and, as per code, the entire 20 amp bathroom circuit is protected by a 20A GFCI outlet. Everything was inspected and functions as it should. Unfortunately, the GFCI is tripping occasionally when the bathroom vent fan is turned "off". It never trips when turning on the fan, only when turning it off. And, it may go a few weeks before it trips, and then suddenly trip three times in a row. Then it'll work fine again for a few weeks. I suspected a bad GFCI, so I replaced it with a new one, and also replaced the switch that controls the fan. It doesn't seem to trip as often now, but it tripped for me again last night when we were visiting. The only remaining item seems to be the fan itself, but I'm curious if there's some other possible cause I might be overlooking? The fan has been installed for a few months now, so I probably can't return it at this point. I thought maybe condensation from moisture draining back through the vent pipe (it had to be routed up over a beam to get out through the side wall). But, the tripping doesn't really seem to be related to when the shower was used recently. Thoughts? Anthony I am skeptical that a properly working fan should trip a properly working GFCI when the fan is turned off. If there is no ground fault in the fan or switch, there can be no imbalance of currents (conservation of electrons). A double pole switch should not make a difference. I might suggest an intermittent ground fault in the fan or switch when the fan is turned off. Please let us know what the problem is/was when/if you figure it out. Anthony- Give MQ's theory a try. I would agree with his suggestion that you might have an intermittent ground fault in the switch itself. Cheap & easy to try it out. Just swap the switch with another SPST from somewhere else in the house. cheers Bob |
#20
Posted to alt.home.repair
|
|||
|
|||
GFCI Tripping Repeatedly?
In article , BobK207 wrote:
On Dec 26, 1:06 pm, M Q wrote: HerHusband wrote: I am skeptical that a properly working fan should trip a properly working GFCI when the fan is turned off. If there is no ground fault in the fan or switch, there can be no imbalance of currents (conservation of electrons). This is incorrect; see an earlier post regarding the collapse of the magnetic field in the motor windings when power is switched off. The consequent backcurrent generated does indeed produce a brief, slight current imbalance. This is evidently of sufficient magnitude and duration to exceed the GFCI's trip threshold. A double pole switch should not make a difference. Of course it should. By opening both the neutral and the hot, a DPST switch prevents the backcurrent from reaching the GFCI, thus preventing the GFCI from ever seeing the imbalance. I might suggest an intermittent ground fault in the fan or switch when the fan is turned off. Perhaps; but the explanation referenced above is IMO much more likely to be correct. Please let us know what the problem is/was when/if you figure it out. Give MQ's theory a try. I would agree with his suggestion that you might have an intermittent ground fault in the switch itself. Very doubtful. Given that it's a single-pole switch, this would require an intermittent, high-resistance short to ground that doesn't draw enough current to make an audible arc. Hard to imagine how that could happen. Cheap & easy to try it out. Just swap the switch with another SPST from somewhere else in the house. Easy enough to test -- but the results are predictable: it won't make any difference. It's possible that this particular GFCI is a little more sensitive than it should be, and swapping it with a different one may cure the problem. Switching both the hot and the neutral through a double-pole switch is almost certain to fix it. -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. |
#21
Posted to alt.home.repair
|
|||
|
|||
GFCI Tripping Repeatedly?
If the GFCI is in the same three gang box as the switch for the fan
and lights you should be able to reconfigure the wiring to eliminate the light and fan from the GFCI protection. No, the GFCI is in a different box on a different wall. Power comes from the GFCI over to the 3-gang box, then three cables exit the switch box to go to the fixtures (ceiling lights, vanity lights, bath fan). There wouldn't be an easy way to take the fan off the GFCI. I wired both bathrooms in our own house the same way, with the fan on the GFCI, and we've never had a GFCI trip. So it has been odd that my in-laws GFCI trips so often with the same wiring scheme. Anthony |
#22
Posted to alt.home.repair
|
|||
|
|||
GFCI Tripping Repeatedly?
you might have an intermittent ground fault in the switch itself.
Just swap the switch with another SPST from somewhere else As I mentioned in my original post, I already replaced the switch and GFCI with new ones, thinking the switch was bad or the GFCI was faulty. It seemed to reduce the tripping slightly, but did not eliminate it. Replacing the fan is kind of my last resort. Anthony |
#23
Posted to alt.home.repair
|
|||
|
|||
GFCI Tripping Repeatedly?
Doug Miller wrote:
In article , BobK207 wrote: On Dec 26, 1:06 pm, M Q wrote: HerHusband wrote: I am skeptical that a properly working fan should trip a properly working GFCI when the fan is turned off. If there is no ground fault in the fan or switch, there can be no imbalance of currents (conservation of electrons). This is incorrect; see an earlier post regarding the collapse of the magnetic field in the motor windings when power is switched off. The consequent backcurrent generated does indeed produce a brief, slight current imbalance. This is evidently of sufficient magnitude and duration to exceed the GFCI's trip threshold. Only if there is leakage to ground. The leakage could be capacitive currents from winding to motor poles. Else, as M Q wrote, how could the current be different in the 2 wires? Field collapse can create a high voltage spike but it creates a current in the circuit through both wires. Could be high voltage produces current from high side (hot) to grounded motor poles by capacitive current?. Spike is short duration (high frequency) increasing the capacitive current. Size of voltage spike depends on where in the current sine wave the switch opens. A double pole switch should not make a difference. Of course it should. By opening both the neutral and the hot, a DPST switch prevents the backcurrent from reaching the GFCI, thus preventing the GFCI from ever seeing the imbalance. Assuming timing of both poles opening is close enough together that the GFCI doesn't trip. I might suggest an intermittent ground fault in the fan or switch when the fan is turned off. Perhaps; but the explanation referenced above is IMO much more likely to be correct. Please let us know what the problem is/was when/if you figure it out. Give MQ's theory a try. I would agree with his suggestion that you might have an intermittent ground fault in the switch itself. Very doubtful. Given that it's a single-pole switch, this would require an intermittent, high-resistance short to ground that doesn't draw enough current to make an audible arc. Hard to imagine how that could happen. Yea, seems remote. -- bud-- |
#24
Posted to alt.home.repair
|
|||
|
|||
GFCI Tripping Repeatedly?
In article , bud-- wrote:
Doug Miller wrote: In article , BobK207 wrote: On Dec 26, 1:06 pm, M Q wrote: HerHusband wrote: I am skeptical that a properly working fan should trip a properly working GFCI when the fan is turned off. If there is no ground fault in the fan or switch, there can be no imbalance of currents (conservation of electrons). This is incorrect; see an earlier post regarding the collapse of the magnetic field in the motor windings when power is switched off. The consequent backcurrent generated does indeed produce a brief, slight current imbalance. This is evidently of sufficient magnitude and duration to exceed the GFCI's trip threshold. Only if there is leakage to ground. NOT correct. A GFCI trips any time there is an imbalance between the hot and neutral currents, that exceeds the thresholds for duration and current. It is NOT necessary for there to be ANY leakage to ground. The leakage could be capacitive currents from winding to motor poles. Else, as M Q wrote, how could the current be different in the 2 wires? Field collapse can create a high voltage spike but it creates a current in the circuit through both wires. Yes, it does -- and with current reaching the motor through an SPST switch, *one* of those two wires is disconnected from the GFCI when the switch is opened, but the other is not. And that's why the GFCI sees an imbalance -- and why I think a DPST switch will eliminate the problem. Could be high voltage produces current from high side (hot) to grounded motor poles by capacitive current?. Spike is short duration (high frequency) increasing the capacitive current. Size of voltage spike depends on where in the current sine wave the switch opens. Possible, I suppose... but I'm not convinced. A double pole switch should not make a difference. Of course it should. By opening both the neutral and the hot, a DPST switch prevents the backcurrent from reaching the GFCI, thus preventing the GFCI from ever seeing the imbalance. Assuming timing of both poles opening is close enough together that the GFCI doesn't trip. Pretty good assumption, I'd say. -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. |
#25
Posted to alt.home.repair
|
|||
|
|||
GFCI Tripping Repeatedly?
"HerHusband" wrote in message ... If the GFCI is in the same three gang box as the switch for the fan and lights you should be able to reconfigure the wiring to eliminate the light and fan from the GFCI protection. No, the GFCI is in a different box on a different wall. Power comes from the GFCI over to the 3-gang box, then three cables exit the switch box to go to the fixtures (ceiling lights, vanity lights, bath fan). There wouldn't be an easy way to take the fan off the GFCI. Sure there would. Just disconnect the cable coming from the load side of the GFCI outlet, and connect it to the line side . There is no need to connect any of the loads you have through a gfci I wired both bathrooms in our own house the same way, with the fan on the GFCI, and we've never had a GFCI trip. So it has been odd that my in-laws GFCI trips so often with the same wiring scheme. Anthony |
#26
Posted to alt.home.repair
|
|||
|
|||
GFCI Tripping Repeatedly?
RBM wrote:
"HerHusband" wrote in message ... If the GFCI is in the same three gang box as the switch for the fan and lights you should be able to reconfigure the wiring to eliminate the light and fan from the GFCI protection. No, the GFCI is in a different box on a different wall. Power comes from the GFCI over to the 3-gang box, then three cables exit the switch box to go to the fixtures (ceiling lights, vanity lights, bath fan). There wouldn't be an easy way to take the fan off the GFCI. Sure there would. Just disconnect the cable coming from the load side of the GFCI outlet, and connect it to the line side . There is no need to connect any of the loads you have through a gfci I wired both bathrooms in our own house the same way, with the fan on the GFCI, and we've never had a GFCI trip. So it has been odd that my in-laws GFCI trips so often with the same wiring scheme. Anthony Some exhaust fans are specifically listed to be installed with a GFCI protected supply. The concern is that the vibration of the fan is more likely to cause a fault and a person who is standing in a shower is particularly vulnerable to electric shock. Removing the GFCI protection from the shower fan may be a violation of the electric code requirement for installing all devices in conformity with the instructions included in the listing or labeling. You can purchase a combination device that has the switch and a GFCI on the same yoke and use that to control the fan. It would make a lot more sense however to open the neutral splice in the three gang box and test for a ground fault on each of the cables that are not the supply. The one that shows a measurable resistance to ground from the load side of the switch with the switch open and the neutral splices open is the one that is ground faulted. If you cannot get the fault to read a measurable resistance with the circuits thus disconnected from the supply you can either open and inspect all three load outlets for a pinched wire or an over tightened cable clamp or you can rent an insulation tester and subject the three cable's insulated conductors to three hundred volts. Insulation testers give the resistance of the conductors insulation under a specific test voltage. If you use any higher setting than three hundred volts you are likely to cause faults rather than locate the existing fault. -- Tom Horne |
#27
Posted to alt.home.repair
|
|||
|
|||
GFCI Tripping Repeatedly?
Doug Miller wrote:
In article , bud-- wrote: Doug Miller wrote: In article , BobK207 wrote: On Dec 26, 1:06 pm, M Q wrote: HerHusband wrote: I am skeptical that a properly working fan should trip a properly working GFCI when the fan is turned off. If there is no ground fault in the fan or switch, there can be no imbalance of currents (conservation of electrons). This is incorrect; see an earlier post regarding the collapse of the magnetic field in the motor windings when power is switched off. The consequent backcurrent generated does indeed produce a brief, slight current imbalance. This is evidently of sufficient magnitude and duration to exceed the GFCI's trip threshold. Only if there is leakage to ground. NOT correct. A GFCI trips any time there is an imbalance between the hot and neutral currents, that exceeds the thresholds for duration and current. It is NOT necessary for there to be ANY leakage to ground. Of course. But how do you get a different current in the wires of a bath fan without ground leakage. The leakage could be capacitive currents from winding to motor poles. Else, as M Q wrote, how could the current be different in the 2 wires? Field collapse can create a high voltage spike but it creates a current in the circuit through both wires. Yes, it does -- and with current reaching the motor through an SPST switch, *one* of those two wires is disconnected from the GFCI when the switch is opened, but the other is not. And that's why the GFCI sees an imbalance -- and why I think a DPST switch will eliminate the problem. Still not explained - how is the current not the same in both wires unless there is some form of leakage to ground. The current is the same in both wires for a light bulb. Why not the fan. Could be high voltage produces current from high side (hot) to grounded motor poles by capacitive current?. Spike is short duration (high frequency) increasing the capacitive current. Size of voltage spike depends on where in the current sine wave the switch opens. Possible, I suppose... but I'm not convinced. A double pole switch should not make a difference. Of course it should. By opening both the neutral and the hot, a DPST switch prevents the backcurrent from reaching the GFCI, thus preventing the GFCI from ever seeing the imbalance. Assuming timing of both poles opening is close enough together that the GFCI doesn't trip. Pretty good assumption, I'd say. Wall switches generally operate slowly - apparently intentionally. (You can typically move the handle to a position that causes the contacts to arc - not that arcing is relevant.) I have read the intent is that the contact break be slow enough to reduce inductive kick from magnetic field collapse. GFCIs may operate in 1/2 cycle. It is not obvious to me that slow operation and random variation would not result in timing difference between poles of 1/2 cycle in some switches. -- bud-- |
#28
Posted to alt.home.repair
|
|||
|
|||
GFCI Tripping Repeatedly?
On Dec 24, 2:34*pm, "HeyBub" wrote:
BobK207 wrote: I have had trouble with motor loads tripping GFI's. The fact that it trips when the fan is turned "off" leads me to believe what you're seeing is not a true ground fault (current leakage to ground) but "merely" a difference between the instantaneous currents on the hot & neutral wires. I'm an ME but I did study some motor & circuit stuff in school.......here's my best attempt at an explanation, *when the fan is turned off, *the magnetic field of the windings of the motor collapses & induces a current back thru the neutral (since the hot lead is switched & therefore open). The field collapses 60 times a second when running... 120 times per second |
#29
Posted to alt.home.repair
|
|||
|
|||
GFCI Tripping Repeatedly?
"Tom Horne" wrote in message news:6XXcj.13589$1q4.5129@trnddc06... RBM wrote: "HerHusband" wrote in message ... If the GFCI is in the same three gang box as the switch for the fan and lights you should be able to reconfigure the wiring to eliminate the light and fan from the GFCI protection. No, the GFCI is in a different box on a different wall. Power comes from the GFCI over to the 3-gang box, then three cables exit the switch box to go to the fixtures (ceiling lights, vanity lights, bath fan). There wouldn't be an easy way to take the fan off the GFCI. Sure there would. Just disconnect the cable coming from the load side of the GFCI outlet, and connect it to the line side . There is no need to connect any of the loads you have through a gfci I wired both bathrooms in our own house the same way, with the fan on the GFCI, and we've never had a GFCI trip. So it has been odd that my in-laws GFCI trips so often with the same wiring scheme. Anthony Some exhaust fans are specifically listed to be installed with a GFCI protected supply. The concern is that the vibration of the fan is more likely to cause a fault and a person who is standing in a shower is particularly vulnerable to electric shock. Removing the GFCI protection from the shower fan may be a violation of the electric code requirement for installing all devices in conformity with the instructions included in the listing or labeling. In his case, the fan is not located over the shower or tub You can purchase a combination device that has the switch and a GFCI on the same yoke and use that to control the fan. It would make a lot more sense however to open the neutral splice in the three gang box and test for a ground fault on each of the cables that are not the supply. The one that shows a measurable resistance to ground from the load side of the switch with the switch open and the neutral splices open is the one that is ground faulted. If you cannot get the fault to read a measurable resistance with the circuits thus disconnected from the supply you can either open and inspect all three load outlets for a pinched wire or an over tightened cable clamp or you can rent an insulation tester and subject the three cable's insulated conductors to three hundred volts. Insulation testers give the resistance of the conductors insulation under a specific test voltage. If you use any higher setting than three hundred volts you are likely to cause faults rather than locate the existing fault. -- Tom Horne |
#30
Posted to alt.home.repair
|
|||
|
|||
GFCI Tripping Repeatedly?
In article , bud-- wrote:
Doug Miller wrote: In article , bud-- wrote: Doug Miller wrote: In article , BobK207 wrote: On Dec 26, 1:06 pm, M Q wrote: HerHusband wrote: I am skeptical that a properly working fan should trip a properly working GFCI when the fan is turned off. If there is no ground fault in the fan or switch, there can be no imbalance of currents (conservation of electrons). This is incorrect; see an earlier post regarding the collapse of the magnetic field in the motor windings when power is switched off. The consequent backcurrent generated does indeed produce a brief, slight current imbalance. This is evidently of sufficient magnitude and duration to exceed the GFCI's trip threshold. Only if there is leakage to ground. NOT correct. A GFCI trips any time there is an imbalance between the hot and neutral currents, that exceeds the thresholds for duration and current. It is NOT necessary for there to be ANY leakage to ground. Of course. But how do you get a different current in the wires of a bath fan without ground leakage. As noted above, see an earlier post in this thread (not mine) regarding magnetic field collapse and back-EMF. The leakage could be capacitive currents from winding to motor poles. Else, as M Q wrote, how could the current be different in the 2 wires? Field collapse can create a high voltage spike but it creates a current in the circuit through both wires. Yes, it does -- and with current reaching the motor through an SPST switch, *one* of those two wires is disconnected from the GFCI when the switch is opened, but the other is not. And that's why the GFCI sees an imbalance -- and why I think a DPST switch will eliminate the problem. Still not explained - how is the current not the same in both wires unless there is some form of leakage to ground. As noted above, see an earlier post in this thread, etc. The current is the same in both wires for a light bulb. Why not the fan. Because a light bulb is a resistive load, and a fan is an inductive load, at least in part. -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. |
#31
Posted to alt.home.repair
|
|||
|
|||
GFCI Tripping Repeatedly?
In article , Terry wrote:
On Dec 24, 2:34=A0pm, "HeyBub" wrote: BobK207 wrote: I have had trouble with motor loads tripping GFI's. The fact that it trips when the fan is turned "off" leads me to believe what you're seeing is not a true ground fault (current leakage to ground) but "merely" a difference between the instantaneous currents on the hot & neutral wires. I'm an ME but I did study some motor & circuit stuff in school.......here's my best attempt at an explanation, =A0when the fan is turned off, =A0the magnetic field of the windings of the motor collapses & induces a current back thru the neutral (since the hot lead is switched & therefore open). The field collapses 60 times a second when running... 120 times per second Whether it collapses 60, 120, or a thousand times a second when running is not relevant, because when the fan is running, both wires are connected to the GFCI. With power to the fan routed through a single-pole switch so that only the hot conductor is opened by the switch, only *one* wire is connected to the GFCI, thus making it possible for the collapsing field to cause imbalanced hot and neutral currents at the GFCI. -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. |
#32
Posted to alt.home.repair
|
|||
|
|||
GFCI Tripping Repeatedly?
On Dec 28, 9:14*pm, (Doug Miller) wrote:
In article , Terry wrote: On Dec 24, 2:34=A0pm, "HeyBub" wrote: BobK207 wrote: I have had trouble with motor loads tripping GFI's. The fact that it trips when the fan is turned "off" leads me to believe what you're seeing is not a true ground fault (current leakage to ground) but "merely" a difference between the instantaneous currents on the hot & neutral wires. I'm an ME but I did study some motor & circuit stuff in school.......here's my best attempt at an explanation, =A0when the fan is turned off, =A0the magnetic field of the windings of the motor collapses & induces a current back thru the neutral (since the hot lead is switched & therefore open). The field collapses 60 times a second when running... 120 times per second Whether it collapses 60, 120, or a thousand times a second when running is not relevant, because when the fan is running, both wires are connected to the GFCI. With power to the fan routed through a single-pole switch so that only the hot conductor is opened by the switch, only *one* wire is connected to the GFCI, thus making it possible for the collapsing field to cause imbalanced hot and neutral currents at the GFCI. With only "one" wire connected to the GFI there is no difference of potential either. It kind of makes induced currents impossible too, but run with it. Want to bet on the double pole switch? |
#33
Posted to alt.home.repair
|
|||
|
|||
GFCI Tripping Repeatedly?
In article , Terry wrote:
On Dec 28, 9:14=A0pm, (Doug Miller) wrote: Whether it collapses 60, 120, or a thousand times a second when running is not relevant, because when the fan is running, both wires are connected to the GFCI. With power to the fan routed through a single-pole switch so that only the hot conductor is opened by the switch, only *one* wire is connected to the GFCI, thus making it possible for the collapsing field to cause imbalanced hot and neutral currents at the GFCI. With only "one" wire connected to the GFI there is no difference of potential either. It kind of makes induced currents impossible too, but run with it. Maybe you ought to spend a little more time thinking about that... Want to bet on the double pole switch? Sure. -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. |
#34
Posted to alt.home.repair
|
|||
|
|||
GFCI Tripping Repeatedly?
Whether it collapses 60, 120, or a thousand times a second when
running is not relevant, because when the fan is running, both wires are connected to the GFCI. With power to the fan routed through a single-pole switch so that only the hot conductor is opened by the switch, only *one* wire is connected to the GFCI, thus making it possible for the collapsing field to cause imbalanced hot and neutral currents at the GFCI. With only "one" wire connected to the GFI there is no difference of potential either. It kind of makes induced currents impossible too, but run with it. Maybe you ought to spend a little more time thinking about that... Want to bet on the double pole switch? Sure. I have to admit, I'm a little skeptical about the double-pole switch. Whether resistive or inductive, how can you have current flow unless the circuit is completed? Open the hot wire and current shouldn't flow through the neutral either, unless there really was a fault in the wiring somewhere? I was an electronic tech MANY years ago, so maybe I've just been away from this stuff too long. In any case, my own attempts at solving the problem have failed, so I'm willing to give it a try. I bought a double-pole switch yesterday ($9) and plan to install it in the next day or two. Unfortunately, due to the erratic nature of the problem, I may not know for a month or more whether it solved the tripping problem. But, if it does trip again, at least I can rule out the switch once and for all. Thanks for the feedback! Anthony |
#35
Posted to alt.home.repair
|
|||
|
|||
GFCI Tripping Repeatedly?
On Dec 27, 11:22*am, bud-- wrote:
Doug Miller wrote: In article , BobK207 wrote: On Dec 26, 1:06 pm, M Q wrote: HerHusband wrote: I am skeptical that a properly working fan should trip a properly working GFCI when the fan is turned off. *If there is no ground fault in the fan or switch, there can be no imbalance of currents (conservation of electrons). This is incorrect; see an earlier post regarding the collapse of the magnetic field in the motor windings when power is switched off. The consequent backcurrent generated does indeed produce a brief, slight current imbalance. This is evidently of sufficient magnitude and duration to exceed the GFCI's trip threshold. Only if there is leakage to ground. The leakage could be capacitive currents from winding to motor poles. Else, as M Q wrote, how could the current be different in the 2 wires? Field collapse can create a high voltage spike but it creates a current in the circuit through both wires. Could be high voltage produces current from high side (hot) to grounded motor poles by capacitive current?. Spike is short duration (high frequency) increasing the capacitive current. Size of voltage spike depends on where in the current sine wave the switch opens. A double pole switch should not make a difference. Of course it should. By opening both the neutral and the hot, a DPST switch prevents the backcurrent from reaching the GFCI, thus preventing the GFCI from ever seeing the imbalance. Assuming timing of both poles opening is close enough together that the GFCI doesn't trip. I might suggest an intermittent ground fault in the fan or switch when the fan is turned off. Perhaps; but the explanation referenced above is IMO much more likely to be correct. Please let us know what the problem is/was when/if you figure it out. Give MQ's theory a try. * I would agree with his suggestion that you might have an intermittent ground fault in the switch itself. Very doubtful. Given that it's a single-pole switch, this would require an intermittent, high-resistance short to ground that doesn't draw enough current to make an audible arc. Hard to imagine how that could happen. Yea, seems remote. -- bud-- check and see if the positve(black) and neg(white) wires are connected to the coresponding black and white wires in the fan, if they are reversed u will trip a gfci |
#36
Posted to alt.home.repair
|
|||
|
|||
GFCI Tripping Repeatedly?
In article , HerHusband wrote:
Whether it collapses 60, 120, or a thousand times a second when running is not relevant, because when the fan is running, both wires are connected to the GFCI. With power to the fan routed through a single-pole switch so that only the hot conductor is opened by the switch, only *one* wire is connected to the GFCI, thus making it possible for the collapsing field to cause imbalanced hot and neutral currents at the GFCI. With only "one" wire connected to the GFI there is no difference of potential either. It kind of makes induced currents impossible too, but run with it. Maybe you ought to spend a little more time thinking about that... Want to bet on the double pole switch? Sure. I have to admit, I'm a little skeptical about the double-pole switch. So test it. Whether resistive or inductive, how can you have current flow unless the circuit is completed? Back-EMF can flow through the neutral wire because the neutral is connected to ground at the breaker box. Open the hot wire and current shouldn't flow through the neutral either, unless there really was a fault in the wiring somewhere? Back-EMF from the collapsing magnetic field in the motor windings when it's switched off. I was an electronic tech MANY years ago, so maybe I've just been away from this stuff too long. In any case, my own attempts at solving the problem have failed, so I'm willing to give it a try. I bought a double-pole switch yesterday ($9) and plan to install it in the next day or two. Unfortunately, due to the erratic nature of the problem, I may not know for a month or more whether it solved the tripping problem. But, if it does trip again, at least I can rule out the switch once and for all. Yep. Let us know what happens. -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. |
#37
Posted to alt.home.repair
|
|||
|
|||
GFCI Tripping Repeatedly?
|
#38
Posted to alt.home.repair
|
|||
|
|||
GFCI Tripping Repeatedly?
Doug Miller wrote:
In article , HerHusband wrote: Whether resistive or inductive, how can you have current flow unless the circuit is completed? Back-EMF can flow through the neutral wire because the neutral is connected to ground at the breaker box. Open the hot wire and current shouldn't flow through the neutral either, unless there really was a fault in the wiring somewhere? Back-EMF from the collapsing magnetic field in the motor windings when it's switched off. You basically have a 2 wire inductor. You are saying that when the circuit is broken, magnetic field collapse produces a current flow in one wire that is not equal to the current flow in the other wire. You may be in line for a Nobel Prize. Or maybe not. -- bud-- |
#40
Posted to alt.home.repair
|
|||
|
|||
GFCI Tripping Repeatedly?
In article 6cRdj.559$jX4.196@trnddc07, M Q wrote:
In the wire that is not connected we can agree that the current is zero? Of course. In the wire that is connected, what do you think the current is? Small, but non-zero. If it is zero, they are equal and the GFCI should not trip. Correct. If it is not zero, where do you think that current is going? To ground, obviously, at the service entrance. Those electrons have to go (come from) somewhere. They are not getting stored in the fan. Electric current is the movement of electric *charge*. The current is generated by the collapsing magnetic field. They could be going to ground, True. but only if you have a ground fault. False. All current in the neutral wire ultimately goes to ground at the service panel. -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. |