I recently bought an older home with a newer addition. The original
portion of the house has 2 conductor wire with no ground. The addition
and recently wired parts of the basement use 3 conductor wire and all
the outlets are grounded and appear to be wired correctly (when tested
with a $5 outlet tester from the hardware store).

I need to plug in some computer equipment to two older outlets in the
original part of the house. I understand that I need a "real" ground
wire back to the panel for surge protectors / computer equipment (no
GFC or ground tied to water pipes etc).

Here is what I want to do - I would like to know if there are any
concerns with this approach:

The new wiring for the basement and the addition are easily accessible
in the basement and each has a junction box located near the older
outlets I want to add ground to. I plan to run a ground wire from the
two older outlets where I need to connect my computer to the juction
boxes with the newer wiring in the basement, and connect them to the
ground wires in the juction boxes.

Assuming that the ground wires in the newer wiring are properly
connected back at the panel, will this present any sort of problem?
Will the two older outlets be properly grounded for use with computer
equipment?

Ben

  #2   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 548
Default Adding Separate Ground Wire to 2-wire Circuit

wrote:
I recently bought an older home with a newer addition. The original
portion of the house has 2 conductor wire with no ground. The addition
and recently wired parts of the basement use 3 conductor wire and all
the outlets are grounded and appear to be wired correctly (when tested
with a $5 outlet tester from the hardware store).

I need to plug in some computer equipment to two older outlets in the
original part of the house. I understand that I need a "real" ground
wire back to the panel for surge protectors / computer equipment (no
GFC or ground tied to water pipes etc).

Here is what I want to do - I would like to know if there are any
concerns with this approach:

The new wiring for the basement and the addition are easily accessible
in the basement and each has a junction box located near the older
outlets I want to add ground to. I plan to run a ground wire from the
two older outlets where I need to connect my computer to the juction
boxes with the newer wiring in the basement, and connect them to the
ground wires in the juction boxes.

Assuming that the ground wires in the newer wiring are properly
connected back at the panel, will this present any sort of problem?
Will the two older outlets be properly grounded for use with computer
equipment?

Ben



That green wire should run all the way back to the electrical panel, or to
one of the grounding electrode conductors if that is easier. "Borrowing" a
ground from another nearby circuit isn't Kosher (even though it works,
wink, wink, nudge, nudge)

Best regards,
Bob
  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 557
Default Adding Separate Ground Wire to 2-wire Circuit

On 30 Dec 2006 09:09:56 -0800, wrote:

I recently bought an older home with a newer addition. The original
portion of the house has 2 conductor wire with no ground. The addition
and recently wired parts of the basement use 3 conductor wire and all
the outlets are grounded and appear to be wired correctly (when tested
with a $5 outlet tester from the hardware store).

I need to plug in some computer equipment to two older outlets in the
original part of the house. I understand that I need a "real" ground
wire back to the panel for surge protectors / computer equipment (no
GFC or ground tied to water pipes etc).

Here is what I want to do - I would like to know if there are any
concerns with this approach:

The new wiring for the basement and the addition are easily accessible
in the basement and each has a junction box located near the older
outlets I want to add ground to. I plan to run a ground wire from the
two older outlets where I need to connect my computer to the juction
boxes with the newer wiring in the basement, and connect them to the
ground wires in the juction boxes.

Assuming that the ground wires in the newer wiring are properly
connected back at the panel, will this present any sort of problem?
Will the two older outlets be properly grounded for use with computer
equipment?

Ben


imho:

Too many words.

First check if you have an existing grounding method. See if the
receptacle boxes are metal and the wiring method is AC (BX). Now if
you aren't a qualified electrician then get one to do the work.
Cheaper than replacing computers, and such.

Good luck,

tom @
www.Consolidated-Loans.info

  #4   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 4
Default Adding Separate Ground Wire to 2-wire Circuit

zxcvbob wrote:


That green wire should run all the way back to the electrical panel, or to
one of the grounding electrode conductors if that is easier. "Borrowing" a
ground from another nearby circuit isn't Kosher (even though it works,
wink, wink, nudge, nudge)

Best regards,
Bob


Thanks Bob. After looking at it some more, running a ground to the
panel isn't that bad. It's only about 30 feet, 2 outlets, and there
are plenty of ground lugs in the panel, so that is what I will do.

Ben

  #6   Report Post  
Posted to alt.home.repair
RBM RBM is offline
external usenet poster
 
Posts: 1,690
Default Adding Separate Ground Wire to 2-wire Circuit

The NEC requires it to be connected to any point along the grounding
electrode system, but if you really can't do that, I agree with Bob



wrote in message
ps.com...
I recently bought an older home with a newer addition. The original
portion of the house has 2 conductor wire with no ground. The addition
and recently wired parts of the basement use 3 conductor wire and all
the outlets are grounded and appear to be wired correctly (when tested
with a $5 outlet tester from the hardware store).

I need to plug in some computer equipment to two older outlets in the
original part of the house. I understand that I need a "real" ground
wire back to the panel for surge protectors / computer equipment (no
GFC or ground tied to water pipes etc).

Here is what I want to do - I would like to know if there are any
concerns with this approach:

The new wiring for the basement and the addition are easily accessible
in the basement and each has a junction box located near the older
outlets I want to add ground to. I plan to run a ground wire from the
two older outlets where I need to connect my computer to the juction
boxes with the newer wiring in the basement, and connect them to the
ground wires in the juction boxes.

Assuming that the ground wires in the newer wiring are properly
connected back at the panel, will this present any sort of problem?
Will the two older outlets be properly grounded for use with computer
equipment?

Ben



  #7   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 66
Default Adding Separate Ground Wire to 2-wire Circuit

All things considered if you have the extra capacity in your panel, or if
you have access to the old line feeding the outlet for the computer, I'd
pull a new line, with a ground, to some central point, where you can put a
junction box and feed the computer outlet, including the ground. This can
then be the point to pull grounds for any other outlets that were on that
same circuit.

wrote in message
ups.com...

Tom The Great wrote:
On 30 Dec 2006 09:09:56 -0800, wrote:
imho:

Too many words.


I agree. I get too wordy sometimes for a simple question

First check if you have an existing grounding method. See if the
receptacle boxes are metal and the wiring method is AC (BX).


The boxes are metal, but the wiring is not armored. Even if it were, I
would not rely on it as grounding.

Now if
you aren't a qualified electrician then get one to do the work.
Cheaper than replacing computers, and such.


When it comes to electrical I do feel that one needs to know what they
are doing, be safe, and be comfortable with the job. I do not feel
every task requires putting hundreds of dollars in someone else's
pocket, however. If I needed to replace my panel, I'd hire an expert.
If I'm just installing a new outlet or running a ground wire, I feel
quite capable.



  #8   Report Post  
Posted to alt.home.repair
 
Posts: n/a
Default Adding Separate Ground Wire to 2-wire Circuit


"Mark" wrote in message
...
All things considered if you have the extra capacity in your panel, or if
you have access to the old line feeding the outlet for the computer, I'd
pull a new line, with a ground, to some central point, where you can put a
junction box and feed the computer outlet, including the ground. This can
then be the point to pull grounds for any other outlets that were on that
same circuit.

wrote in message
ups.com...

Tom The Great wrote:
On 30 Dec 2006 09:09:56 -0800, wrote:
imho:

Too many words.


I agree. I get too wordy sometimes for a simple question

First check if you have an existing grounding method. See if the
receptacle boxes are metal and the wiring method is AC (BX).


The boxes are metal, but the wiring is not armored. Even if it were, I
would not rely on it as grounding.

Now if
you aren't a qualified electrician then get one to do the work.
Cheaper than replacing computers, and such.


When it comes to electrical I do feel that one needs to know what they
are doing, be safe, and be comfortable with the job. I do not feel
every task requires putting hundreds of dollars in someone else's
pocket, however. If I needed to replace my panel, I'd hire an expert.
If I'm just installing a new outlet or running a ground wire, I feel
quite capable.

Mark came closest, but I wouldn't even mess with the existing outlets. Add a
new 2-gang outlet behind the computer desk, tied to any convenient
non-switched grounded circuit in the basement. Modern computers don't draw
much. If OP is comfortable fishing wires, a length of 12-3 or 14-3 (for a
single outlet) would be about as quick to fish as the seperate ground. And
if he has an easy road to the service panel, and an open breaker socket, a
dedicated string wouldn't take much longer to run. If an old-work box and
fishing through the wall is a problem, a baseboard- level surface-mount box
and bushed conduit running through the floor wouldn't look that bad, and
could easily be moved or removed, if needed in the future, with only a tiny
hole to plug with a hardwood dowel. For that matter, they sell raised
floor-mount boxes (aka 'couch outlets') that could go through the floor
under the desk.

aem sends...


  #9   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 4
Default Adding Separate Ground Wire to 2-wire Circuit

"Mark" wrote in message
Mark came closest, but I wouldn't even mess with the existing outlets. Add a
new 2-gang outlet behind the computer desk, tied to any convenient
non-switched grounded circuit in the basement. Modern computers don't draw
much. If OP is comfortable fishing wires, a length of 12-3 or 14-3 (for a
single outlet) would be about as quick to fish as the seperate ground.
aem sends...


Thanks everyone for the replys. This is actually what I'm going to do.
The addition is really just a mud room, and the _only_ thing we use in
that room is two lights - we have never even used the outlets. I'm
just going to fish a short line up to the new outlet I need.

Not to mention when I took the cover off one outlets in the mud room I
was shocked (haha, not literally), at what I saw. Hots with 2" of bare
copper, and not screwed onto the outlet securely, and the whole outlet
wrapped with tape around the outside, almost as if it's to keep the
wires on there. I had to look because in the older part of the house
the guy just put in 3 prong outlets with no ground connection at all
and didn't fill in the ground hole.

Every time I look at a new project in this house I find something like
this, just below the surface.

  #10   Report Post  
Posted to alt.home.repair
 
Posts: n/a
Default Adding Separate Ground Wire to 2-wire Circuit


wrote in message
ups.com...
"Mark" wrote in message
Mark came closest, but I wouldn't even mess with the existing outlets.
Add a
new 2-gang outlet behind the computer desk, tied to any convenient
non-switched grounded circuit in the basement. Modern computers don't
draw
much. If OP is comfortable fishing wires, a length of 12-3 or 14-3 (for
a
single outlet) would be about as quick to fish as the seperate ground.
aem sends...


Thanks everyone for the replys. This is actually what I'm going to do.
The addition is really just a mud room, and the _only_ thing we use in
that room is two lights - we have never even used the outlets. I'm
just going to fish a short line up to the new outlet I need.

Not to mention when I took the cover off one outlets in the mud room I
was shocked (haha, not literally), at what I saw. Hots with 2" of bare
copper, and not screwed onto the outlet securely, and the whole outlet
wrapped with tape around the outside, almost as if it's to keep the
wires on there. I had to look because in the older part of the house
the guy just put in 3 prong outlets with no ground connection at all
and didn't fill in the ground hole.

Every time I look at a new project in this house I find something like
this, just below the surface.

Don't feel like the lone ranger- I keep finding stupids like that in this
house, too. Miswired outlets, open junction boxes in attic with loose
connections, buried floating butt splices, etc. I'm no pro electrician, but
I can do simple stuff, and what I put back is safer than what I found.

aem sends...




  #11   Report Post  
Posted to alt.home.repair
RBM RBM is offline
external usenet poster
 
Posts: 1,690
Default Adding Separate Ground Wire to 2-wire Circuit

Just to clarify for the OP, 14-2 (nm) has two wires +ground, 14-3 (nm) has
three wires + ground



wrote in message
...

"Mark" wrote in message
...
All things considered if you have the extra capacity in your panel, or if
you have access to the old line feeding the outlet for the computer, I'd
pull a new line, with a ground, to some central point, where you can put
a junction box and feed the computer outlet, including the ground. This
can then be the point to pull grounds for any other outlets that were on
that same circuit.

wrote in message
ups.com...

Tom The Great wrote:
On 30 Dec 2006 09:09:56 -0800, wrote:
imho:

Too many words.


I agree. I get too wordy sometimes for a simple question

First check if you have an existing grounding method. See if the
receptacle boxes are metal and the wiring method is AC (BX).

The boxes are metal, but the wiring is not armored. Even if it were, I
would not rely on it as grounding.

Now if
you aren't a qualified electrician then get one to do the work.
Cheaper than replacing computers, and such.


When it comes to electrical I do feel that one needs to know what they
are doing, be safe, and be comfortable with the job. I do not feel
every task requires putting hundreds of dollars in someone else's
pocket, however. If I needed to replace my panel, I'd hire an expert.
If I'm just installing a new outlet or running a ground wire, I feel
quite capable.

Mark came closest, but I wouldn't even mess with the existing outlets. Add
a new 2-gang outlet behind the computer desk, tied to any convenient
non-switched grounded circuit in the basement. Modern computers don't draw
much. If OP is comfortable fishing wires, a length of 12-3 or 14-3 (for a
single outlet) would be about as quick to fish as the seperate ground. And
if he has an easy road to the service panel, and an open breaker socket, a
dedicated string wouldn't take much longer to run. If an old-work box and
fishing through the wall is a problem, a baseboard- level surface-mount
box and bushed conduit running through the floor wouldn't look that bad,
and could easily be moved or removed, if needed in the future, with only a
tiny hole to plug with a hardwood dowel. For that matter, they sell raised
floor-mount boxes (aka 'couch outlets') that could go through the floor
under the desk.

aem sends...



  #12   Report Post  
Posted to alt.home.repair
 
Posts: n/a
Default Adding Separate Ground Wire to 2-wire Circuit


"RBM" rbm2(remove wrote in message
...
Just to clarify for the OP, 14-2 (nm) has two wires +ground, 14-3 (nm) has
three wires + ground


You are right, of course- my bad. My mind was still on the wiring at my
father's place, where an unused 3-wire run for a future 240 outlet had been
pressed into service for a 110 outlet.

aem sends...


Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Bonded ground wires vs. earth ground wire Eigenvector Home Repair 21 December 28th 06 05:31 PM
Adding a GFCI outlet with two-wire (duplex) wire android Home Repair 22 August 21st 06 12:29 AM
ground wire extension (anti-static ground) toronado455 Electronics Repair 5 July 18th 06 08:44 AM
Adding separate light to ceiling fan circuit...need wiring help JaxDawg Home Ownership 2 January 18th 05 02:42 PM
Adding a ground wire Dan Home Repair 16 December 1st 04 12:18 PM


All times are GMT +1. The time now is 02:13 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"