I would like to replace a two prong outlet in the kitchen of my 1950's home
with a GFCI outlet. The conductor is two-wire (no ground). Will a GFCI
outlet work (will I be able to "reset" it)without replacing the wiring?
  #2   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 87
Default Adding a GFCI outlet with two-wire (duplex) wire


"android" wrote in message
news:a7684266647e2c4fee315231fdd0689c@homerepairli ve.com...
I would like to replace a two prong outlet in the kitchen of my 1950's home
with a GFCI outlet. The conductor is two-wire (no ground). Will a GFCI
outlet work (will I be able to "reset" it)without replacing the wiring?


Is the house wired with Romex (armored cable)? If so that is your ground so
the screws holding it to the box will give you the ground or you could run
an extra wire from the box to the ground terminal. Also check to make sure
you have 110 volts from hot to the box and nothing from neutral to the box
this will confirm that you do have a ground just not a separate one like
modern wiring.

Rich



  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 4,500
Default Adding a GFCI outlet with two-wire (duplex) wire


Rich wrote:
"android" wrote in message
news:a7684266647e2c4fee315231fdd0689c@homerepairli ve.com...
I would like to replace a two prong outlet in the kitchen of my 1950's home
with a GFCI outlet. The conductor is two-wire (no ground). Will a GFCI
outlet work (will I be able to "reset" it)without replacing the wiring?


Is the house wired with Romex (armored cable)? If so that is your ground so
the screws holding it to the box will give you the ground or you could run
an extra wire from the box to the ground terminal. Also check to make sure
you have 110 volts from hot to the box and nothing from neutral to the box
this will confirm that you do have a ground just not a separate one like
modern wiring.

Rich



You can install a GFCI on a circuit with no ground and it will work,
trip, reset with no problem.

  #4   Report Post  
Posted to alt.home.repair
EXT EXT is offline
external usenet poster
 
Posts: 1,661
Default Adding a GFCI outlet with two-wire (duplex) wire

Please note that Romex is a generic name for non-metalic sheathed cable, not
steel or aluminum armored cable which is generically known as BX cable.

"Rich" wrote in message
. ..

"android" wrote in message
news:a7684266647e2c4fee315231fdd0689c@homerepairli ve.com...
I would like to replace a two prong outlet in the kitchen of my 1950's
home
with a GFCI outlet. The conductor is two-wire (no ground). Will a GFCI
outlet work (will I be able to "reset" it)without replacing the wiring?


Is the house wired with Romex (armored cable)? If so that is your ground
so the screws holding it to the box will give you the ground or you could
run an extra wire from the box to the ground terminal. Also check to make
sure you have 110 volts from hot to the box and nothing from neutral to
the box this will confirm that you do have a ground just not a separate
one like modern wiring.

Rich





  #5   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,963
Default Adding a GFCI outlet with two-wire (duplex) wire

On Sat, 19 Aug 2006 11:18:22 -0500, "android"
wrote:

I would like to replace a two prong outlet in the kitchen of my 1950's home
with a GFCI outlet. The conductor is two-wire (no ground). Will a GFCI
outlet work (will I be able to "reset" it)without replacing the wiring?


Yes. The "ground" in GFCI refers to the unintentional ground that
occurs when something goes wrong. There is no need for a ground wire.
--
Mark Lloyd
http://notstupid.laughingsquid.com

"Democracy is two wolves and a lamb voting on what
to have for lunch. Liberty is a well armed lamb
contesting the vote." - Benjamin Franklin


  #6   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,199
Default Adding a GFCI outlet with two-wire (duplex) wire

I would add a ground wire if at all possible. GFCI is good but ground
with GFCI is better.

the ungrounded GFCI will be noted at home resale time.

might be easier to run a new dedicated 20 amp circuit just for kitchen,
abandon old receptable remove and use blank cover

  #8   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,300
Default Adding a GFCI outlet with two-wire (duplex) wire

android wrote:
I would like to replace a two prong outlet in the kitchen of my 1950's home
with a GFCI outlet. The conductor is two-wire (no ground). Will a GFCI
outlet work (will I be able to "reset" it)without replacing the wiring?



Yes, it will work fine and do the shock protection job as intended, and
test or reset without problems.

When you buy a new GFCI outlet it will come with a stick-on label saying
"Ground Not Connected" which you should place on the outlet plate for
that receptical.

I haven't yet learned just why that notice is needed, but I suppose
there's a valid reason. It's hard to imagine why someone would want to
use the ground pin of a receptical to ground something that's not being
powered by that same receptical, maybe someone here will explain that part.

Jeff

--
Jeffry Wisnia
(W1BSV + Brass Rat '57 EE)
"What do you expect from a pig but a grunt?"
  #9   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,963
Default Adding a GFCI outlet with two-wire (duplex) wire

On Sat, 19 Aug 2006 19:46:53 -0400, Jeff Wisnia
wrote:

android wrote:
I would like to replace a two prong outlet in the kitchen of my 1950's home
with a GFCI outlet. The conductor is two-wire (no ground). Will a GFCI
outlet work (will I be able to "reset" it)without replacing the wiring?



Yes, it will work fine and do the shock protection job as intended, and
test or reset without problems.

When you buy a new GFCI outlet it will come with a stick-on label saying
"Ground Not Connected" which you should place on the outlet plate for
that receptical.

I haven't yet learned just why that notice is needed, but I suppose
there's a valid reason. It's hard to imagine why someone would want to
use the ground pin of a receptical to ground something that's not being
powered by that same receptical, maybe someone here will explain that part.

Jeff


It doesn't have to be something else. It could be an appliance with a
3-prong cord. Some people will see a 3-hole receptacle (as GFCIs are)
and think there's a ground there. If there's no ground (and a GFCI in
no way CREATES one), it's somewhat safer to have that fact indicated.
--
Mark Lloyd
http://notstupid.laughingsquid.com

"Democracy is two wolves and a lamb voting on what
to have for lunch. Liberty is a well armed lamb
contesting the vote." - Benjamin Franklin
  #10   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,199
Default Adding a GFCI outlet with two-wire (duplex) wire

if a ground wasnt better than a GFCI grounds wouldnt be required, and
GFCIs do fail, I found a bad one and replaced it, after testing it with
one of those plug in testers, it didnt trip.

in a kitchen with water that could kill.......



  #12   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 109
Default Adding a GFCI outlet with two-wire (duplex) wire


I haven't yet learned just why that notice is needed, but I suppose
there's a valid reason. It's hard to imagine why someone would want to
use the ground pin of a receptical to ground something that's not being
powered by that same receptical, maybe someone here will explain that part.

Jeff


It doesn't have to be something else. It could be an appliance with a
3-prong cord. Some people will see a 3-hole receptacle (as GFCIs are)
and think there's a ground there. If there's no ground (and a GFCI in
no way CREATES one), it's somewhat safer to have that fact indicated.
--



You can still get a nasty shock from an ungrounded GFCI protected
circuit if all the current leaking into your body through a hotwire
fault goes back into the neutral wire. This is not uncommon, and is
as easy as gripping the metal prongs of an outlet when inserting or
removing a plug from a socket.

GFCI's protect by sensing an imbalance between the hot and neutral
wires and tripping OFF when this get to be 5 ma. or greater. During
the type of fault described above, there is no imbalance and therefore
no protection from this type of shock.

As stated by other posters, a ground wire is not required, but if you
want to be protected, you hope that the fault leakage will find a path
to ground through a cold water piper, damp basement floor, moist
earth, etc.

Before the GFCI's were invented, electrical safety was predicated on a
good ground being connected to the metal frame of a motor, for
example.

Under such circumstances, a hot-to-frame fault would normally result
in a near short circuit and hopefully trip the breaker or blow the
fuse serving the motor.

GFCI's augment, but do not completely replace the protection that a
good grounding system offers.

Beachcomber



  #14   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 4,500
Default Adding a GFCI outlet with two-wire (duplex) wire


Joshua Putnam wrote:
In article . com,
says...
if a ground wasnt better than a GFCI grounds wouldnt be required, and
GFCIs do fail, I found a bad one and replaced it, after testing it with
one of those plug in testers, it didnt trip.



There is no way that a ground is better than a GFCI. Given the choice
of one or the other, I would take the GFCI in a minute. Most of the
items one plugs in today don't even have a ground wire, whether it's a
hair dryer, toaster, or electric drill. Get any of those wet or with
an exposed conductor and grab it while grounded and it can kill you
whether it's plugged into a grounded outlet or not. But if it's
plugged into a GFCI, it will trip at 5ma in a fraction of a second,
whether the appliance has a ground or not, which is much less than the
current required to kill you.

Sure, GFCI's can fail. But so can grounds. Haven't we seen plenty of
posts on here of folks with all kinds of situations with missing
grounds? All you need for a ground to be ineffective is an
interruption in the daisy chain of wiring. So, without actual data, I
would not conclude that grounds are any more or less reliable than a
GFCI.








Just a side-note, if you have a GFCI without a ground, some testers
won't work even if the GFCI is perfectly good.

Why?

Because they test the GFCI by leaking current to ground, but the ground
pin isn't connected to a ground, so the tester does not create a ground
fault.

That's one reason you should have the "no equipment ground" sticker on
ungrounded GFCIs. It's also there for equipment that expects a ground,
like electronics, or a tool with a grounded housing for protection.

--
is Joshua Putnam
http://www.phred.org/~josh/
Books for Bicycle Mechanics and Tinkerers:
http://www.phred.org/~josh/bike/bikebooks.html


  #15   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,300
Default Adding a GFCI outlet with two-wire (duplex) wire

wrote:

Joshua Putnam wrote:



snipped
There is no way that a ground is better than a GFCI. Given the choice
of one or the other, I would take the GFCI in a minute. Most of the
items one plugs in today don't even have a ground wire, whether it's a
hair dryer, toaster, or electric drill. Get any of those wet or with
an exposed conductor and grab it while grounded and it can kill you
whether it's plugged into a grounded outlet or not. But if it's
plugged into a GFCI, it will trip at 5ma in a fraction of a second,
whether the appliance has a ground or not, which is much less than the
current required to kill you.

Sure, GFCI's can fail. But so can grounds. Haven't we seen plenty of
posts on here of folks with all kinds of situations with missing
grounds? All you need for a ground to be ineffective is an
interruption in the daisy chain of wiring. So, without actual data, I
would not conclude that grounds are any more or less reliable than a
GFCI.



Since I think I was the first poster on this thread to remind the OP to
apply that "No Ground Connection" sticker, I wasn't against it, just
pondering about the average citizen not even understand what it means.
Well, maybe a techie or perhaps someone trying to test the GFCI with an
artificially created external leak to the ground pin hole. When GFCIs
first began to appearI once stuck the leads of a 10K one watt carbon
resistor between the hot and ground pins on a GFCI to "test" its tripping.

I'm sure that the manufacturers of GFCI outlets are more than willing to
include that sticker to maximize their CYA potential.

And I'd agree that a belt and suspenders approach, with a properly
grounded GFCI would have advantages over an ungrounded one in unlikely
and arcane situations.

Jeff

--
Jeffry Wisnia
(W1BSV + Brass Rat '57 EE)
"What do you expect from a pig but a grunt?"


  #16   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,199
Default Adding a GFCI outlet with two-wire (duplex) wire


wrote:
Joshua Putnam wrote:
In article . com,
says...
if a ground wasnt better than a GFCI grounds wouldnt be required, and
GFCIs do fail, I found a bad one and replaced it, after testing it with
one of those plug in testers, it didnt trip.



There is no way that a ground is better than a GFCI. Given the choice
of one or the other, I would take the GFCI in a minute. Most of the
items one plugs in today don't even have a ground wire, whether it's a
hair dryer, toaster, or electric drill. Get any of those wet or with
an exposed conductor and grab it while grounded and it can kill you
whether it's plugged into a grounded outlet or not. But if it's
plugged into a GFCI, it will trip at 5ma in a fraction of a second,
whether the appliance has a ground or not, which is much less than the
current required to kill you.

Sure, GFCI's can fail. But so can grounds. Haven't we seen plenty of
posts on here of folks with all kinds of situations with missing
grounds? All you need for a ground to be ineffective is an
interruption in the daisy chain of wiring. So, without actual data, I
would not conclude that grounds are any more or less reliable than a
GFCI.



Ahh all TWO prong devices today with ANY exposed outside conductive
surfaces are DOUBLE INSULATED with 2 layers of protection between
conductor and shell.

GFCI with ground is safer, lets imagine your drilling a hole in a wall
and happen to hit a active conductor. the GFCI wouldnt know your
getting shocked, whilew a ground will.

if you ask me all electric drills should be 3 prong for this reason.

  #17   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,963
Default Adding a GFCI outlet with two-wire (duplex) wire

On 20 Aug 2006 06:13:57 -0700, wrote:


Joshua Putnam wrote:
In article . com,
says...
if a ground wasnt better than a GFCI grounds wouldnt be required, and
GFCIs do fail, I found a bad one and replaced it, after testing it with
one of those plug in testers, it didnt trip.



There is no way that a ground is better than a GFCI. Given the choice
of one or the other, I would take the GFCI in a minute. Most of the
items one plugs in today don't even have a ground wire, whether it's a
hair dryer, toaster, or electric drill. Get any of those wet or with
an exposed conductor and grab it while grounded and it can kill you
whether it's plugged into a grounded outlet or not. But if it's
plugged into a GFCI, it will trip at 5ma in a fraction of a second,
whether the appliance has a ground or not, which is much less than the
current required to kill you.

Sure, GFCI's can fail. But so can grounds. Haven't we seen plenty of
posts on here of folks with all kinds of situations with missing
grounds? All you need for a ground to be ineffective is an
interruption in the daisy chain of wiring. So, without actual data, I
would not conclude that grounds are any more or less reliable than a
GFCI.


It sounds like people often want to do one OR the other. Not such a
good idea.








Just a side-note, if you have a GFCI without a ground, some testers
won't work even if the GFCI is perfectly good.

Why?

Because they test the GFCI by leaking current to ground, but the ground
pin isn't connected to a ground, so the tester does not create a ground
fault.

That's one reason you should have the "no equipment ground" sticker on
ungrounded GFCIs. It's also there for equipment that expects a ground,
like electronics, or a tool with a grounded housing for protection.

--
is Joshua Putnam
http://www.phred.org/~josh/
Books for Bicycle Mechanics and Tinkerers:
http://www.phred.org/~josh/bike/bikebooks.html

--
Mark Lloyd
http://notstupid.laughingsquid.com

"Democracy is two wolves and a lamb voting on what
to have for lunch. Liberty is a well armed lamb
contesting the vote." - Benjamin Franklin
  #18   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,199
Default Adding a GFCI outlet with two-wire (duplex) wire



It sounds like people often want to do one OR the other. Not such a
good idea.



lazy dont want to open walls, basically make do decision that does NOT
address the larger issues with the fire risk of K&T the most common
ungrounded cause

  #19   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,963
Default Adding a GFCI outlet with two-wire (duplex) wire

On 20 Aug 2006 10:34:30 -0700, "
wrote:



It sounds like people often want to do one OR the other. Not such a
good idea.



lazy dont want to open walls,


Yes, laziness is too common.

basically make do decision that does NOT
address the larger issues with the fire risk of K&T the most common
ungrounded cause


Not the only one. My house is too new for K&T (built around 1969), but
there are still no ground wires (except to laundry area). I do have
several GFCIs in use.

BTW, that includes the one that had to be replaces because it was full
of ants (eggs and feces too).
--
Mark Lloyd
http://notstupid.laughingsquid.com

"Democracy is two wolves and a lamb voting on what
to have for lunch. Liberty is a well armed lamb
contesting the vote." - Benjamin Franklin
  #20   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,199
Default Adding a GFCI outlet with two-wire (duplex) wire




Not the only one. My house is too new for K&T (built around 1969), but
there are still no ground wires (except to laundry area). I do have
several GFCIs in use.


1969 what kind of cable in your home?

If its BX its grounded by the cables metal shell........



  #21   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,963
Default Adding a GFCI outlet with two-wire (duplex) wire

On 20 Aug 2006 12:27:16 -0700, "
wrote:




Not the only one. My house is too new for K&T (built around 1969), but
there are still no ground wires (except to laundry area). I do have
several GFCIs in use.


1969 what kind of cable in your home?

If its BX its grounded by the cables metal shell........


It's 2-conductor Romex (all 120V circuits except the laundry room
one), nonmetallic jacket, no ground.

The receptacles themselves are all 3-contact, but no ground
connection.
--
Mark Lloyd
http://notstupid.laughingsquid.com

"Democracy is two wolves and a lamb voting on what
to have for lunch. Liberty is a well armed lamb
contesting the vote." - Benjamin Franklin
  #22   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,199
Default Adding a GFCI outlet with two-wire (duplex) wire


Mark Lloyd wrote:
On 20 Aug 2006 12:27:16 -0700, "
wrote:




Not the only one. My house is too new for K&T (built around 1969), but
there are still no ground wires (except to laundry area). I do have
several GFCIs in use.


1969 what kind of cable in your home?

If its BX its grounded by the cables metal shell........


It's 2-conductor Romex (all 120V circuits except the laundry room
one), nonmetallic jacket, no ground.

The receptacles themselves are all 3-contact, but no ground
connection.
--
Mark Lloyd
http://notstupid.laughingsquid.com


sad it passed inspection

If I were you I would add ground lines, not hard just time consuming...

  #23   Report Post  
Posted to alt.home.repair
 
Posts: n/a
Default Adding a GFCI outlet with two-wire (duplex) wire


"Mark Lloyd" wrote in message
...
On 20 Aug 2006 12:27:16 -0700, "
wrote:




Not the only one. My house is too new for K&T (built around 1969), but
there are still no ground wires (except to laundry area). I do have
several GFCIs in use.


1969 what kind of cable in your home?

If its BX its grounded by the cables metal shell........


It's 2-conductor Romex (all 120V circuits except the laundry room
one), nonmetallic jacket, no ground.

The receptacles themselves are all 3-contact, but no ground
connection.

Wow- even in flyover country in southern Indiana, 3-wire circuits were
standard practice, and I assume required, by the early to mid 60s. My
Grandmother's 1961 house was 100-amp 2-wire, my Fathers 1966 folly just down
the street was 200-amp 3-wire. This SW Michigan 1960 cookie cutter was wired
with 3-wire and grounded metal boxes, but 2-hole outlets, which I have since
switched. (Yes, I assume current code requires a ground pigtail to the
outlet, but the test meter is happy, so I'm happy. That old wire is way too
stiff, and there is no slack, so I wasn't about to try fishing the copper
from under the clamps. At least I got the polarity right, unlike the last
guy on half of them.)

aem sends...


Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
GFCI Outlet Wiring Question Alan Home Repair 7 August 7th 05 05:42 PM
adding an outlet next to two switches Jim Home Repair 12 July 10th 05 04:47 AM
Red Wire in Ceiling Light Outlet Unknown Home Repair 11 March 28th 05 08:19 PM
GFCI outlet / automated sprinkler system that plugs in it Vince Home Ownership 3 November 27th 04 04:26 AM
automotive wire size calculator CampinGazz Electronics 1 January 5th 04 07:02 PM


All times are GMT +1. The time now is 11:54 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"