  #1   Report Post  
Posted to alt.home.repair
RPN RPN is offline
external usenet poster
 
Posts: 2
Default Smoke Detector Woes

My neighbors are having a smoke detector problem. It recently started
beeping every 30 seconds or so. The obvious solution is that the beep
is a low battery indication and you should replace the battery, but that
apparently is not the case. The facts as I know them are as follows.

1. The building is a modular home of recent construction with
one floor and a basement.

2. There are a total of 5 smoke detectors. There is one in each
of the bedrooms (3), one in the hallway, and one in the basement.

3. The smoke detectors on the first floor are all BRK 2002RAC. I
forgot to check the model of the one in the basement, but it is
different. I cannot say for sure it is even a BRK unit, but based
on appearance and memory, it was probably BRK 9120B.

4. According to the drawings, the four first floor detectors
were put in by the modular home manufacturer. The one in the
cellar appears to have put by the builder when they were putting
it up. They are all interconnected.

5. The first thing I did was to turn of the breaker (green LED in
unit went out confirming loss of AC) and check the battery in each
of the five units. I replaced four marginal ones. Testing was
done with DVOM and a battery tester that added some load. The
one good battery tested 8.99 V under load. The rest, the were
replaced, were typically 8.5 V. The beeping remained on through
out the process and did not stop even after all units were back in
place with known good batteries and the power restored.

6. The beeps did not always come from the same location, so I
could not tell which unit was the problem one. As a result, I
turned off the AC again, and took all five units down.

7. This is where it gets strange. With all five units out and the
AC power off, the beeps continued from different locations at
different times, and they seemed to be coming from the original
locations in the ceiling, not the units.

8. I then removed the battery from all five units, so none were
powered, just to be sure the units were not beeping. That did not
help as the beeping continued.


I know large value capacitors can can keep things running for a long
time if the load is small, but there were four of us there, including my
wife and the two neighbors, and we all confirmed that the beeping
appeared to be coming from the ceiling mount point, and not the
disconnected units on the floor that had no batteries in them.

Based on this I have a few questions, besides the obvious one of
how to stop the beeping.

1. I realize the smoke detectors are tied together so if one
detects smoke and alarms, they all alarm. Does the same hold true
for the low battery beep, and does it round robin through the
other units?

2. Is it possible that there are transducers or other audio
transmitters near the mount point as well as on the unit?

I have never heard of such a thing, but I could see where someone
might of thought it was great idea so that you would still know a
remote sensor was alarming, even if the local unit was completely dead.
The mounting bracket for the detector covered the electrical box
behind it preventing a thorough inspection of what else might might be
in the box besides the wiring.

3. If the sound is coming from the ceiling location, and not the
units themselves, what is the source of the beep and where is the
power for it coming from?

All the units are on the floor, with no batteries in them, and the AC
power has been turned off. The only thing I can think of is that there
is a detector that we have not located that is still connected and it
has a low battery, but if that is the case, it is not shown on the
electrical drawing for the house as constructed, and I can not locate
it. You would think it would not be buried out of sight.

I have looked around the archives for other postings that might be
similar in scope as mine, but could not find any. If I missed one, my
apologies, and please feel free to send me a URL rather than compose a
similar response.

Thanks for your help,

RPN
  #2   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 229
Default Smoke Detector Woes

RPN wrote:
My neighbors are having a smoke detector problem. It recently started
beeping every 30 seconds or so. The obvious solution is that the beep
is a low battery indication and you should replace the battery, but
that apparently is not the case. The facts as I know them are as
follows.

1. The building is a modular home of recent construction with
one floor and a basement.

2. There are a total of 5 smoke detectors. There is one in each
of the bedrooms (3), one in the hallway, and one in the basement.

3. The smoke detectors on the first floor are all BRK 2002RAC. I
forgot to check the model of the one in the basement, but it is
different. I cannot say for sure it is even a BRK unit, but based
on appearance and memory, it was probably BRK 9120B.

4. According to the drawings, the four first floor detectors
were put in by the modular home manufacturer. The one in the
cellar appears to have put by the builder when they were putting
it up. They are all interconnected.

5. The first thing I did was to turn of the breaker (green LED in
unit went out confirming loss of AC) and check the battery in each
of the five units. I replaced four marginal ones. Testing was
done with DVOM and a battery tester that added some load. The
one good battery tested 8.99 V under load. The rest, the were
replaced, were typically 8.5 V. The beeping remained on through
out the process and did not stop even after all units were back in
place with known good batteries and the power restored.

6. The beeps did not always come from the same location, so I
could not tell which unit was the problem one. As a result, I
turned off the AC again, and took all five units down.

7. This is where it gets strange. With all five units out and the
AC power off, the beeps continued from different locations at
different times, and they seemed to be coming from the original
locations in the ceiling, not the units.

8. I then removed the battery from all five units, so none were
powered, just to be sure the units were not beeping. That did not
help as the beeping continued.


I know large value capacitors can can keep things running for a long
time if the load is small, but there were four of us there, including
my wife and the two neighbors, and we all confirmed that the beeping
appeared to be coming from the ceiling mount point, and not the
disconnected units on the floor that had no batteries in them.

Based on this I have a few questions, besides the obvious one of
how to stop the beeping.

1. I realize the smoke detectors are tied together so if one
detects smoke and alarms, they all alarm. Does the same hold true
for the low battery beep, and does it round robin through the
other units?

2. Is it possible that there are transducers or other audio
transmitters near the mount point as well as on the unit?

I have never heard of such a thing, but I could see where someone
might of thought it was great idea so that you would still know a
remote sensor was alarming, even if the local unit was completely
dead. The mounting bracket for the detector covered the electrical box
behind it preventing a thorough inspection of what else might might be
in the box besides the wiring.

3. If the sound is coming from the ceiling location, and not the
units themselves, what is the source of the beep and where is the
power for it coming from?

All the units are on the floor, with no batteries in them, and the AC
power has been turned off. The only thing I can think of is that
there is a detector that we have not located that is still connected
and it has a low battery, but if that is the case, it is not shown on
the electrical drawing for the house as constructed, and I can not
locate it. You would think it would not be buried out of sight.

I have looked around the archives for other postings that might be
similar in scope as mine, but could not find any. If I missed one, my
apologies, and please feel free to send me a URL rather than compose a
similar response.

Thanks for your help,

RPN



You might want to consider that smoke detectors become less sensitive
with age. How old are these detectors? Maybe it might be good just to
replace them all. I just replaced all mine about six months ago. They were
all about 8 years old and I believe the recommendation was like 5-6 years.

--
Joseph Meehan

Dia 's Muire duit



  #3   Report Post  
Posted to alt.home.repair
RBM RBM is offline
external usenet poster
 
Posts: 1,690
Default Smoke Detector Woes

I've had customers with similar situations. First of all I find it
impossible to detect which unit is beeping, so I remove them all to an
outside location. Typically the beeping continues and I have found it to be:
Units mounted in the attic that no one knew about. Units in boiler rooms
that no one knew about, and carbon monoxide detectors that people had
plugged into wall outlets and never suspected


"RPN" wrote in message
...
My neighbors are having a smoke detector problem. It recently started
beeping every 30 seconds or so. The obvious solution is that the beep
is a low battery indication and you should replace the battery, but that
apparently is not the case. The facts as I know them are as follows.

1. The building is a modular home of recent construction with
one floor and a basement.

2. There are a total of 5 smoke detectors. There is one in each
of the bedrooms (3), one in the hallway, and one in the basement.

3. The smoke detectors on the first floor are all BRK 2002RAC. I
forgot to check the model of the one in the basement, but it is
different. I cannot say for sure it is even a BRK unit, but based
on appearance and memory, it was probably BRK 9120B.

4. According to the drawings, the four first floor detectors
were put in by the modular home manufacturer. The one in the
cellar appears to have put by the builder when they were putting
it up. They are all interconnected.

5. The first thing I did was to turn of the breaker (green LED in
unit went out confirming loss of AC) and check the battery in each
of the five units. I replaced four marginal ones. Testing was
done with DVOM and a battery tester that added some load. The
one good battery tested 8.99 V under load. The rest, the were
replaced, were typically 8.5 V. The beeping remained on through
out the process and did not stop even after all units were back in
place with known good batteries and the power restored.

6. The beeps did not always come from the same location, so I
could not tell which unit was the problem one. As a result, I
turned off the AC again, and took all five units down.

7. This is where it gets strange. With all five units out and the
AC power off, the beeps continued from different locations at
different times, and they seemed to be coming from the original
locations in the ceiling, not the units.

8. I then removed the battery from all five units, so none were
powered, just to be sure the units were not beeping. That did not
help as the beeping continued.


I know large value capacitors can can keep things running for a long
time if the load is small, but there were four of us there, including my
wife and the two neighbors, and we all confirmed that the beeping
appeared to be coming from the ceiling mount point, and not the
disconnected units on the floor that had no batteries in them.

Based on this I have a few questions, besides the obvious one of
how to stop the beeping.

1. I realize the smoke detectors are tied together so if one
detects smoke and alarms, they all alarm. Does the same hold true
for the low battery beep, and does it round robin through the
other units?

2. Is it possible that there are transducers or other audio
transmitters near the mount point as well as on the unit?

I have never heard of such a thing, but I could see where someone
might of thought it was great idea so that you would still know a
remote sensor was alarming, even if the local unit was completely dead.
The mounting bracket for the detector covered the electrical box
behind it preventing a thorough inspection of what else might might be
in the box besides the wiring.

3. If the sound is coming from the ceiling location, and not the
units themselves, what is the source of the beep and where is the
power for it coming from?

All the units are on the floor, with no batteries in them, and the AC
power has been turned off. The only thing I can think of is that there
is a detector that we have not located that is still connected and it
has a low battery, but if that is the case, it is not shown on the
electrical drawing for the house as constructed, and I can not locate
it. You would think it would not be buried out of sight.

I have looked around the archives for other postings that might be
similar in scope as mine, but could not find any. If I missed one, my
apologies, and please feel free to send me a URL rather than compose a
similar response.

Thanks for your help,

RPN



  #4   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,743
Default Smoke Detector Woes


"RBM" rbm2(remove wrote in message
...
I've had customers with similar situations. First of all I find it
impossible to detect which unit is beeping, so I remove them all to an
outside location. Typically the beeping continues and I have found it to
be: Units mounted in the attic that no one knew about. Units in boiler
rooms that no one knew about, and carbon monoxide detectors that people
had plugged into wall outlets and never suspected


Second that. The frequency of the beep disguises its location.

We had a similar situation. After disarming the smoke detectors - and
continuing to hear the beep - we were convinced it was the burglar/fire
alarm system. The alarm company mechanic found it: a carbon monoxide
detector two rooms down the hall (it was plugged into a switched outlet and
its backup batteries had failed)!

Just make a list of things that go beep. It's got to be one. Don't forget
cell phones.


  #5   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 674
Default Smoke Detector Woes


"HeyBub" wrote in message
...

"RBM" rbm2(remove wrote in message
...
I've had customers with similar situations. First of all I find it
impossible to detect which unit is beeping, so I remove them all to an
outside location. Typically the beeping continues and I have found it to
be: Units mounted in the attic that no one knew about. Units in boiler
rooms that no one knew about, and carbon monoxide detectors that people
had plugged into wall outlets and never suspected


Second that. The frequency of the beep disguises its location.

We had a similar situation. After disarming the smoke detectors - and
continuing to hear the beep - we were convinced it was the burglar/fire
alarm system. The alarm company mechanic found it: a carbon monoxide
detector two rooms down the hall (it was plugged into a switched outlet
and its backup batteries had failed)!

Just make a list of things that go beep. It's got to be one. Don't forget
cell phones.

A funnel and a piece of hose makes a pretty good directional sound locator,
if you want to try it.

Don Young




Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Mains Smoke Alarm thankyousam UK diy 17 June 6th 06 04:53 PM
question about interconnected smoke detectors autonut843 Home Repair 13 December 17th 05 12:44 AM
Smoke (and other) Alarms - best suppliers of compatible ranges? [email protected] UK diy 33 December 6th 04 09:48 AM
Smoke smell from A/C? Eyes burning. jan Home Repair 7 November 18th 03 03:04 AM
Ultimate smoke alarm - never need to change batteries! Daniel Morrow Electronics 10 October 10th 03 11:08 PM


All times are GMT +1. The time now is 05:40 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"