Home Repair (alt.home.repair) For all homeowners and DIYers with many experienced tradesmen. Solve your toughest home fix-it problems.

Reply
 
LinkBack Thread Tools Search this Thread Display Modes
  #1   Report Post  
Posted to alt.home.repair
autonut843
 
Posts: n/a
Default question about interconnected smoke detectors

Hi,
I have noticed in newer homes that they have smoke detectors that take
both a battery and are plugged in to the AC. I think the wires running
between them seem to have an additional conductor and if one smoke
detector goes off and starts beeping, shortly thereafter, the other
ones start beeping as well. How does this work? If you were to mix
and match between different smoke detector vendors (all having the
interconnect feature, of course), would they all work the same? Is
this an industry standard connection? I assume it is an additional
conductor that either gets shorted to ground or hot by the tripped
smoke detector and when the other ones detect that short to ground/hot,
they start beeping as well.

Does any company make something that could tap in to that extra wire so
that, say, if I wanted to turn on emergency lighting or something like
that, it could trip a relay to do that? I'm thinking something that
wires in like a door bell transformer where the line voltage AC is all
in the box and the relay contact screws are outside where they belong,
not sharing a box with the line voltage at all.

Of course, if company XYZcorp makes an "interconnect smoke detector
relay module" that is UL etc approved and can be legally connected to
the smoke detector wiring harness in a standard single gang box and
will trip a NO/NC relay when the detectors are beeping, I'd like to
know about that.

Since IMO, smoke detectors are life safety, I'm not thinking about
modifying anything or experimenting on my own. It is more just a
curiosity on how the thing works and if there is an industry standard
or not. I am sure some of you have modified smoke detectors to do
something like this, but I would prefer if these mods were kept out of
this thread since I think there are many that feel this is no problem
and there are many that feel that modifying a smoke detector is a
dangerous thing to do. I, personally, would rather not be lead away in
handcuffs after explaining to the fire investigator the cool mod I did
to my smoke detectors that caused them not to work when I needed them
most and, golly, I don't see why it didn't work right, should I get a
lawyer now? the circuit really should have worked....

Thanks

  #2   Report Post  
Posted to alt.home.repair
Ken
 
Posts: n/a
Default question about interconnected smoke detectors


autonut843 wrote:
Hi,
I have noticed in newer homes that they have smoke detectors that take
both a battery and are plugged in to the AC. I think the wires running
between them seem to have an additional conductor and if one smoke
detector goes off and starts beeping, shortly thereafter, the other
ones start beeping as well. How does this work? If you were to mix
and match between different smoke detector vendors (all having the
interconnect feature, of course), would they all work the same? Is
this an industry standard connection? I assume it is an additional
conductor that either gets shorted to ground or hot by the tripped
smoke detector and when the other ones detect that short to ground/hot,
they start beeping as well.

Does any company make something that could tap in to that extra wire so
that, say, if I wanted to turn on emergency lighting or something like
that, it could trip a relay to do that? I'm thinking something that
wires in like a door bell transformer where the line voltage AC is all
in the box and the relay contact screws are outside where they belong,
not sharing a box with the line voltage at all.

Of course, if company XYZcorp makes an "interconnect smoke detector
relay module" that is UL etc approved and can be legally connected to
the smoke detector wiring harness in a standard single gang box and
will trip a NO/NC relay when the detectors are beeping, I'd like to
know about that.

Since IMO, smoke detectors are life safety, I'm not thinking about
modifying anything or experimenting on my own. It is more just a
curiosity on how the thing works and if there is an industry standard
or not. I am sure some of you have modified smoke detectors to do
something like this, but I would prefer if these mods were kept out of
this thread since I think there are many that feel this is no problem
and there are many that feel that modifying a smoke detector is a
dangerous thing to do. I, personally, would rather not be lead away in
handcuffs after explaining to the fire investigator the cool mod I did
to my smoke detectors that caused them not to work when I needed them
most and, golly, I don't see why it didn't work right, should I get a
lawyer now? the circuit really should have worked....

Thanks


You would think that they would make an industry standard for that sort
of thing, but unfortunately, not only is there no industry standard,
the interconnect specs are different between different smoke detector
models from the same manufacturer. There are low voltage
interconnects, and line voltage interconnects. And ther eare different
standards for the low voltage interconnects. I wired up 9 smoke alarms
with interconnects in our house, went and bought 1 hardwired detector
w/ battery backup for each floor of the house, and the remaining ones
were hardwired models without battery backup. (I figured that one
battery backup per floor was sufficient.) Well, after installing
everything and testing it, I discovered that the battery backup ones
will only remotely sound the other battery backup ones, and the
no-battery-backup ones will sound other no-battery-backup ones. After
reading the fine print buried in the instructions, it does in fact say
that you have to have the exact same model for the interconnect to
work. Oh well. I assume that there is some modulated signal that is
sent over the interconnect line as opposed to a simple high/low voltage
to signal the other units, although this is just speculation on my
part, and I've never tested it out. (I'd have to borrow an
oscilloscope from work if I wanted to try out that theory.)

Ken

  #3   Report Post  
Posted to alt.home.repair
RBM
 
Posts: n/a
Default question about interconnected smoke detectors

There are relay modules made for smoke detectors. I used to have one
interrupt the power to my oil burner if the alarm went off. I would look at
the website of your particular smoke detector manufacturer



"Ken" wrote in message
ups.com...

autonut843 wrote:
Hi,
I have noticed in newer homes that they have smoke detectors that take
both a battery and are plugged in to the AC. I think the wires running
between them seem to have an additional conductor and if one smoke
detector goes off and starts beeping, shortly thereafter, the other
ones start beeping as well. How does this work? If you were to mix
and match between different smoke detector vendors (all having the
interconnect feature, of course), would they all work the same? Is
this an industry standard connection? I assume it is an additional
conductor that either gets shorted to ground or hot by the tripped
smoke detector and when the other ones detect that short to ground/hot,
they start beeping as well.

Does any company make something that could tap in to that extra wire so
that, say, if I wanted to turn on emergency lighting or something like
that, it could trip a relay to do that? I'm thinking something that
wires in like a door bell transformer where the line voltage AC is all
in the box and the relay contact screws are outside where they belong,
not sharing a box with the line voltage at all.

Of course, if company XYZcorp makes an "interconnect smoke detector
relay module" that is UL etc approved and can be legally connected to
the smoke detector wiring harness in a standard single gang box and
will trip a NO/NC relay when the detectors are beeping, I'd like to
know about that.

Since IMO, smoke detectors are life safety, I'm not thinking about
modifying anything or experimenting on my own. It is more just a
curiosity on how the thing works and if there is an industry standard
or not. I am sure some of you have modified smoke detectors to do
something like this, but I would prefer if these mods were kept out of
this thread since I think there are many that feel this is no problem
and there are many that feel that modifying a smoke detector is a
dangerous thing to do. I, personally, would rather not be lead away in
handcuffs after explaining to the fire investigator the cool mod I did
to my smoke detectors that caused them not to work when I needed them
most and, golly, I don't see why it didn't work right, should I get a
lawyer now? the circuit really should have worked....

Thanks


You would think that they would make an industry standard for that sort
of thing, but unfortunately, not only is there no industry standard,
the interconnect specs are different between different smoke detector
models from the same manufacturer. There are low voltage
interconnects, and line voltage interconnects. And ther eare different
standards for the low voltage interconnects. I wired up 9 smoke alarms
with interconnects in our house, went and bought 1 hardwired detector
w/ battery backup for each floor of the house, and the remaining ones
were hardwired models without battery backup. (I figured that one
battery backup per floor was sufficient.) Well, after installing
everything and testing it, I discovered that the battery backup ones
will only remotely sound the other battery backup ones, and the
no-battery-backup ones will sound other no-battery-backup ones. After
reading the fine print buried in the instructions, it does in fact say
that you have to have the exact same model for the interconnect to
work. Oh well. I assume that there is some modulated signal that is
sent over the interconnect line as opposed to a simple high/low voltage
to signal the other units, although this is just speculation on my
part, and I've never tested it out. (I'd have to borrow an
oscilloscope from work if I wanted to try out that theory.)

Ken



  #4   Report Post  
Posted to alt.home.repair
SQLit
 
Posts: n/a
Default question about interconnected smoke detectors


"autonut843" wrote in message
ups.com...
Hi,
I have noticed in newer homes that they have smoke detectors that take
both a battery and are plugged in to the AC. I think the wires running
between them seem to have an additional conductor and if one smoke
detector goes off and starts beeping, shortly thereafter, the other
ones start beeping as well. How does this work? If you were to mix
and match between different smoke detector vendors (all having the
interconnect feature, of course), would they all work the same? Is
this an industry standard connection? I assume it is an additional
conductor that either gets shorted to ground or hot by the tripped
smoke detector and when the other ones detect that short to ground/hot,
they start beeping as well.

Does any company make something that could tap in to that extra wire so
that, say, if I wanted to turn on emergency lighting or something like
that, it could trip a relay to do that? I'm thinking something that
wires in like a door bell transformer where the line voltage AC is all
in the box and the relay contact screws are outside where they belong,
not sharing a box with the line voltage at all.

Of course, if company XYZcorp makes an "interconnect smoke detector
relay module" that is UL etc approved and can be legally connected to
the smoke detector wiring harness in a standard single gang box and
will trip a NO/NC relay when the detectors are beeping, I'd like to
know about that.

Since IMO, smoke detectors are life safety, I'm not thinking about
modifying anything or experimenting on my own. It is more just a
curiosity on how the thing works and if there is an industry standard
or not. I am sure some of you have modified smoke detectors to do
something like this, but I would prefer if these mods were kept out of
this thread since I think there are many that feel this is no problem
and there are many that feel that modifying a smoke detector is a
dangerous thing to do. I, personally, would rather not be lead away in
handcuffs after explaining to the fire investigator the cool mod I did
to my smoke detectors that caused them not to work when I needed them
most and, golly, I don't see why it didn't work right, should I get a
lawyer now? the circuit really should have worked....

Thanks


What you want is available and in production. Just not on the low end
interconnected ones.


  #5   Report Post  
Posted to alt.home.repair
autonut843
 
Posts: n/a
Default question about interconnected smoke detectors

Once again, I should have Googled first and I would have found my
answer. The Firex manual for one of their interconnected smoke
detectors says...


This smoke alarm should be installed in accordance with the NFPA's Standard 72 (National Fire Protection Association,
Batterymarch Park, Quincy, MA 02269) and any local codes that apply.

When interconnecting, use #18 AWG minimum solid or stranded wire. Maximum wire length between any two is 1,500
feet for #18 AWG or 4,000 feet for #14 AWG (20 OHMS loop resistance).

DO NOT connect to any other type or model of heat or smoke alarm. Connect smoke or heat alarms to a single AC
branch circuit. If local codes do not permit, be sure the neutral wire is common to both phases.


So, I think that explains why I haven't found a commercially available
relay module to do what I was looking for.

Does anybody have a good idea for a passive way to monitor if the smoke
detector is going off? I guess I'm thinking something like a sound
pressure level sensor or something like that. Obviously it wouldn't be
foolproof. Any other ideas?



  #6   Report Post  
Posted to alt.home.repair
Thomas D. Horne, FF EMT
 
Posts: n/a
Default question about interconnected smoke detectors

autonut843 wrote:
Once again, I should have Googled first and I would have found my
answer. The Firex manual for one of their interconnected smoke
detectors says...


This smoke alarm should be installed in accordance with the NFPA's Standard 72 (National Fire Protection Association,
Batterymarch Park, Quincy, MA 02269) and any local codes that apply.

When interconnecting, use #18 AWG minimum solid or stranded wire. Maximum wire length between any two is 1,500
feet for #18 AWG or 4,000 feet for #14 AWG (20 OHMS loop resistance).

DO NOT connect to any other type or model of heat or smoke alarm. Connect smoke or heat alarms to a single AC
branch circuit. If local codes do not permit, be sure the neutral wire is common to both phases.



So, I think that explains why I haven't found a commercially available
relay module to do what I was looking for.

Does anybody have a good idea for a passive way to monitor if the smoke
detector is going off? I guess I'm thinking something like a sound
pressure level sensor or something like that. Obviously it wouldn't be
foolproof. Any other ideas?


You can buy smoke detectors that provide dry contact closure on
activation. They are available in interconnected models but they are
not cheap. If you want smoke detectors that can be reliably monitored
from a remote location you should install a listed automatic fire
detection system. Since that is work I have done as an electrician I
can assure you that it would be both cheaper and more reliable then
anything you would jury rig. Systems are available that are wireless.
Those systems meet the requirements for interconnected detectors.
--
Tom Horne

Well we aren't no thin blue heroes and yet we aren't no blackguards to.
We're just working men and woman most remarkable like you.
  #7   Report Post  
Posted to alt.home.repair
mm
 
Posts: n/a
Default question about interconnected smoke detectors

On 14 Dec 2005 14:53:05 -0800, "autonut843"
wrote:

Once again, I should have Googled first and I would have found my
answer. The Firex manual for one of their interconnected smoke
detectors says...


This smoke alarm should be installed in accordance with the NFPA's Standard 72 (National Fire Protection Association,
Batterymarch Park, Quincy, MA 02269) and any local codes that apply.

When interconnecting, use #18 AWG minimum solid or stranded wire. Maximum wire length between any two is 1,500
feet for #18 AWG or 4,000 feet for #14 AWG (20 OHMS loop resistance).

DO NOT connect to any other type or model of heat or smoke alarm. Connect smoke or heat alarms to a single AC
branch circuit. If local codes do not permit, be sure the neutral wire is common to both phases.


So, I think that explains why I haven't found a commercially available
relay module to do what I was looking for.

Does anybody have a good idea for a passive way to monitor if the smoke
detector is going off? I guess I'm thinking something like a sound
pressure level sensor or something like that. Obviously it wouldn't be
foolproof. Any other ideas?


The only other idea I have is what you said you didn't want to do, but
after some hesistation, I did it.

I have, the house came with 110 volt smoke detector in the hall
outside my bedroom. In parallel with the noisemaker thing inside the
detector, I put a relay that connects to my burglar alarm which sounds
a constant noise, not the pulsating noise that breaking into the house
causes. I used a fairly large relay but it was still small enough to
stuff into the original hole in the ceiling.

It says on the smoke detector not to fiddle with it, of course, but my
relay uses less than the noisemaker, and the it's all 110 volts so
it's not going to overdraw from a battery. I've tested it more than
once. Although it is so loud that I only do it in the middle of a
weekday when my neighbors mostly aren't home.

When I sell the house, I'll give them notes about everything I've done
to it.



Remove NOPSAM to email me. Please let
me know if you have posted also.
  #8   Report Post  
Posted to alt.home.repair
autonut843
 
Posts: n/a
Default question about interconnected smoke detectors

Thanks for the input.

One thing your realtor may request. Instead of the notes, just swap
out the modified smoke detector with the correct one so nothing has to
be declared. It'll make the sale go easier. You really don't want to
mess it up. It's not like your mod will be the deal clencher that
makes the buyer choose your home. It very well could be the thing that
makes the buyer walk away.

Think about it, if you were buying a house from, say, Steve Wozniak (a
known good electrical guy, think Apple computer) and he said, 'by the
way, I modified the smoke detector so it would...' Would you trust
the life and safety of your family with it or would you want it swapped
out?

Also, considering all the horror stories there are about the 'buyer
from hell' (I know someone personally that had such a buyer, what a
major hassle it was and it cost lots in legal fees but that is another
story. Their buyer just wanted to back out after the time frame but it
still cost the seller legal fees just to clear up the mess.) do you
really want that in the mix?

Let's say your buyer gets your notes, is a dream buyer, all is well,
and then 3 months later the house burns or something like that. Now
you have given them written descriptions of what you did. Who do you
think the law/insurance is going to come after? What if they aren't
such a dream buyer and they modify your mod and it burns. Now what?
Now their insurance company and your insurance company have you on the
stand and you say, 'I just added *this* relay, I didn't do *that* to
it!". I just don't see the gain here.

  #9   Report Post  
Posted to alt.home.repair
Steve Kraus
 
Posts: n/a
Default question about interconnected smoke detectors

What about those detectors with the built-in emergency light? I presume
that's just a flashlight type bulb (not an LED light) and if it can drive a
bulb it could drive a small reed relay. Wiring a relay in place of the
bulb is a pretty minimal alteration.

Rather than fooling with the noisemaker in each detector you could buy such
things (Sonalert or whatever) and place them next to each detector or
wherever you feel like so that there is good audio coverage around the
house (best place for a detector isn't necessarily the best place for the
alarm horns). Run Class 2 3 wire cable around the house. One wire is the
feed from some central power source...a battery...a DC supply or a doorbell
tranformer (depending on the needs of your alarm horns)...feeding the
relays in each detector. 2nd wire is what the other side of each relay is
connected to and is also what the horns are connecte to. 3rd wire is
common return.

Now when any detector goes off the alarm horns everywhere go off though
they won't be the ones inside the other detectors. You could wire them up
so they are the horns that sound but I figure it's best to leave them be so
that if your whole system fails for some reason (short circuit) at least
the one detector nearest the smoke will still sound even if the others
don't.
  #10   Report Post  
Posted to alt.home.repair
mm
 
Posts: n/a
Default question about interconnected smoke detectors

On 15 Dec 2005 13:25:15 -0800, "autonut843"
wrote:

Thanks for the input.

One thing your realtor may request. Instead of the notes, just swap
out the modified smoke detector with the correct one so nothing has to
be declared. It'll make the sale go easier. You really don't want to
mess it up. It's not like your mod will be the deal clencher that
makes the buyer choose your home. It very well could be the thing that
makes the buyer walk away.

Think about it, if you were buying a house from, say, Steve Wozniak (a
known good electrical guy, think Apple computer) and he said, 'by the
way, I modified the smoke detector so it would...' Would you trust
the life and safety of your family with it or would you want it swapped
out?

Also, considering all the horror stories there are about the 'buyer
from hell' (I know someone personally that had such a buyer, what a
major hassle it was and it cost lots in legal fees but that is another
story. Their buyer just wanted to back out after the time frame but it
still cost the seller legal fees just to clear up the mess.) do you
really want that in the mix?

Let's say your buyer gets your notes, is a dream buyer, all is well,
and then 3 months later the house burns or something like that. Now
you have given them written descriptions of what you did. Who do you


I agreed with t he rest of your post, but you really got me with this
part. How about if I cut the two wires I soldered to the original
smoke detector, and cut off any stubs on the detector itself, and tape
the relay wires and roll them up and stuff them away. That puts
everything back the way I found it, eletrically at least. Do you
think that will leave me safe?

Then what if I leave a note about what I did, so the new owner can put
it back the way I made it. Or is that looking for trouble?

think the law/insurance is going to come after? What if they aren't
such a dream buyer and they modify your mod and it burns. Now what?
Now their insurance company and your insurance company have you on the
stand and you say, 'I just added *this* relay, I didn't do *that* to
it!". I just don't see the gain here.


It's idealism, believe it or not, and I guess some vanity.. I've
improved on the original, and I'd like to see the improvement last.

The warning on the smoke detector is to keep the smoke detector people
from being sued, in the case of those who don't know how to do a
proper modification. But I started doing stuff like this 50 years ago
when I was 8, and after model trains, wall switches, radio, tv, house
wiring, more tv and a little bit of other various things, by now I
know how to do something simple like this..




Remove NOPSAM to email me. Please let
me know if you have posted also.


  #11   Report Post  
Posted to alt.home.repair
mm
 
Posts: n/a
Default question about interconnected smoke detectors

On Thu, 15 Dec 2005 23:38:19 GMT, Steve Kraus
wrote:

What about those detectors with the built-in emergency light? I presume
that's just a flashlight type bulb (not an LED light) and if it can drive a
bulb it could drive a small reed relay. Wiring a relay in place of the
bulb is a pretty minimal alteration.


No comment on your post, but it reminds me of another thing I did that
was rather interesting. Couldn't hear the doorbell upstairs when the
computer and radio are running, and couldn't figure out an easy way to
run a wire from the existing doorbell**

So I took the 3 dollar wireless door buzzer that my mother used before
she died (cement walls in her apartment building.) and I took the
button half, and soldered a jumper across the button switch on the
circuit board.

Then I connected the 9 volt connector of the button par sort of to the
doorbell transformer, that is, in parallel with the current doorbell,
with a diode in the circuit to give DC from the 18?** volt AC
transformer. And screwed the thing to a ceiling joist in the basement.

Now when someone rings the front doorbell, it also powers the button
half, the LED lights, and it causes the buzzer in the hallway upstairs
to sound.

** (I'm done running wires through the stack. I should have put in
some spares but dudn't.)

***The transformer is 18 volts because 12 wasn't enough when I got the
seocnd doorbell for the basement. But I think rectified 12 volts,
which would have been about 6 volts, might have been enough to power
the 9 volt button half of the wireless doorbell. If not, a full wave
or bridge rectifier could have been used to get closer to 9 volts.


Remove NOPSAM to email me. Please let
me know if you have posted also.
  #12   Report Post  
Posted to alt.home.repair
buffalobill
 
Posts: n/a
Default question about interconnected smoke detectors

wow you're getting some interesting replies. some thoughts from buffalo
ny: you may play with extra smoke detectors only in addition to the
dedicated approved systems and devices in your home, not interconnect
them to the minimum required devices in your building.
not permitted to connect other items to the inspected dedicated red
electrical smoke detector box circuit or its devices.
not permitted: altering a lifesaving safety device. you are creating a
hazard for yourself and others. especially if you die from smoke
inhalation, where only the stupidity will live on.

  #13   Report Post  
Posted to alt.home.repair
autonut843
 
Posts: n/a
Default question about interconnected smoke detectors

Obviously, it's your choice.
I live in CA and when houses change hands there is a specific item on
one of the forms regarding smoke detectors in the house. They have to
be there. I don't know if this is federal or not. If we were talking
electronic door strikes or extra doorbells or something like that, I
can understand messing with it. But on something that is specifically
called out on one of the forms of the transaction. Obviously some
people think it is important.

I've seen other posts that call out, houses built after a certain date
and houses built before a certain date regarding if they have to have
interconnected smokes or not. Or doing additions to an older house and
having to upgrade the smoke detectors from individual to interconnected
in order to meet current law. I am not familiar with those laws at all
but if they do exist, obviously it is pretty important to some people.

Regarding cutting the wires and putting it back. I work for a company
that makes products that customers buy. We get customer returns. It
is obvious when people mess with them. How much do you think we should
stand behind products that have obviously been worked on by a customer?
And our products have nothing at all to do with life safety. I've got
to believe that FirstAlert or Firex or whoever else, have legions of
really good lawyers that have crossed this bridge before. How much
idealism can stand up to that? how much vanity can stand up to that?
You said, 'That puts everything back the way I found it, electrically
at least. Do you think that will leave me safe?" I am sure you are a
great solderer, but I am also sure that there is a pretty good chance
that the original manufacturer can detect modifications. How much is a
new replacement smoke detector? $10, $60 max? Just change it out with
a good one installed. Leave the modified one in a box with
instructions on the kitchen counter if you just have to but let the
buyer re-install it themselves, not you. Another way to look at it,
let's say there is no fire. The buyer doesn't clearly understand the
change you did and, during the transaction, says, 'hey, that's great,
thanks!'. Then, a month later they read what you did, don't want it,
and someone tells them this is a big deal so they overreact and they
have a lawyer write you a letter asking you to put a good one in or
else. What are you going to do? why hassle with it. Just buy a new
one and sell the house with the new good one installed and your
modified one in a box on the counter with instructions.

Another poster on this thread mentioned not messing with the originally
installed interconnected smokes at all but just dinking around on a
separate set of interconnected smokes. I think that is a great idea.
the best idea. Have your sandbox to play in, but have the one that
counts in perfect condition, unaffected by the sandbox. Build your own
sandbox exactly how you want to, play to your heart's content.
install, experiment, test, debug, have fun. But leave the original one
intact.

You mention you are 58 and have been doing this for 50 years. Surely
you can afford two or three or a dozen smokes from Home Depot to play
with. Obviously you are smart enough to design your own
interconnected system out of those smokes. So do it that way and be
safe.

Hopefully I didn't step on any toes.
Have a good holday!

  #14   Report Post  
Posted to alt.home.repair
mm
 
Posts: n/a
Default question about interconnected smoke detectors

On 16 Dec 2005 00:32:11 -0800, "buffalobill"
wrote:

wow you're getting some interesting replies. some thoughts from buffalo
ny: you may play with extra smoke detectors only in addition to the
dedicated approved systems and devices in your home, not interconnect
them to the minimum required devices in your building.
not permitted to connect other items to the inspected dedicated red
electrical smoke detector box circuit or its devices.
not permitted: altering a lifesaving safety device. you are creating a
hazard for yourself and others. especially if you die from smoke
inhalation, where only the stupidity will live on.



Darn, my last ditch plan to solve the problem autonut pointed out was
to live here until I died. Then the new owner probably couldn't sue
me.

But now you point out that wouldn't be right either.

Remove NOPSAM to email me. Please let
me know if you have posted also.
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
OT Guns more Guns Cliff Metalworking 519 December 12th 04 05:52 AM
Question on smoke alarms Matt Home Ownership 2 August 16th 04 08:41 PM
Simple question regarding Ceiling tiles and sound? lbbs UK diy 5 March 26th 04 01:36 AM
Alarm advice with cats in mind. Mortimer UK diy 73 January 19th 04 08:39 AM
CLOSE CALL - SMOKE ALARM IN THE SHOP? T. Woodworking 47 December 6th 03 04:35 AM


All times are GMT +1. The time now is 06:02 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"