Default 12-3 Double Circuit Run Length - Should I Split the Circuit?

Hello

I just finished wiring my basement with 12/3 wire. I was planning on
using a double pole breaker with two circuits and a shared neutral
(alternating circuits between outlets). My run is around the
perimeter of my basement inside wood framing studs. After all was said
and done with the requried routing, I've used about 250ft of wire.

I'm concerned that I may have too long of a run and that, instead of
creating one big 250ft run with alternating circuits on a double pole
20A breaker, I should just have two 125ft circuits on separate 20A
breakers. I guess now's the time to make my decision before I go into
my panel. I've already run the 12-3 wire but I don't mind using only
2 of the 3 wires if that will make these circuits better performing and
safer.

The reading I have done so far and the 13.6% voltage drop at 20A
calculated using this website:

http://www.powerstream.com/Wire_Size.htm

has me leaning heavily toward two separate 125ft circuits.

Any feedback is apprecaited. Thanks!

Kevin

  #2   Report Post  
Posted to alt.home.repair
Toller
 
Posts: n/a
Default 12-3 Double Circuit Run Length - Should I Split the Circuit?


wrote in message
ups.com...
Hello

I just finished wiring my basement with 12/3 wire. I was planning on
using a double pole breaker with two circuits and a shared neutral
(alternating circuits between outlets). My run is around the
perimeter of my basement inside wood framing studs. After all was said
and done with the requried routing, I've used about 250ft of wire.

I'm concerned that I may have too long of a run and that, instead of
creating one big 250ft run with alternating circuits on a double pole
20A breaker, I should just have two 125ft circuits on separate 20A
breakers. I guess now's the time to make my decision before I go into
my panel. I've already run the 12-3 wire but I don't mind using only
2 of the 3 wires if that will make these circuits better performing and
safer.

The reading I have done so far and the 13.6% voltage drop at 20A
calculated using this website:

http://www.powerstream.com/Wire_Size.htm

has me leaning heavily toward two separate 125ft circuits.

Any feedback is apprecaited. Thanks!

A balanced multiwire circuit can be half the voltage drop because there is
no return path.
So, there are two things to consider... will you actually be using 20a on
each side, and can you get a balanced circuit.

Then you might want to rethink things; 20a is too much for a 125' run of
12/2.


  #3   Report Post  
Posted to alt.home.repair
 
Posts: n/a
Default 12-3 Double Circuit Run Length - Should I Split the Circuit?

I really don't plan on using 20A on either side. I was planning on
using the 20A mainly because I had the 12 gage wire & I was sticking
with the 12 gage because of my run length. I originally thought the
length would be about 170ft but I didn't take into account the routing
I had to do up and down to my outlet boxes and around things.

I would call the circuits light use with a TV, dehumidifier
(spring/summer) and possibly an electric space heater (occasionally) in
the winter. Maybe a computer and some lamps will eventually be down
there too but I don't plan on using really heavy draw power tools or
having a workshop down there or anything.

Lights are on a separate 15A circuit.

Thanks for your feedback!

  #4   Report Post  
Posted to alt.home.repair
 
Posts: n/a
Default 12-3 Double Circuit Run Length - Should I Split the Circuit?

Also, could you elaborate on how I can reduce the voltage drop with my
12-3 wire?

  #5   Report Post  
Posted to alt.home.repair
 
Posts: n/a
Default 12-3 Double Circuit Run Length - Should I Split the Circuit?

One other thing I forgot to mention...

If I split the circuit into two 125ft runs, most of my electrical loads
I mentioned above would end up on one of the circuits. And, naturally,
my circuit breaker box is at the opposite corner of my basement from
where most of the used outlets will be.

Thanks again for your feedback.
Kevin



  #6   Report Post  
Posted to alt.home.repair
Toller
 
Posts: n/a
Default 12-3 Double Circuit Run Length - Should I Split the Circuit?


" wrote in message
oups.com...
One other thing I forgot to mention...

If I split the circuit into two 125ft runs, most of my electrical loads
I mentioned above would end up on one of the circuits. And, naturally,
my circuit breaker box is at the opposite corner of my basement from
where most of the used outlets will be.

If all the heavy stuff will be on one of the 125' circuits, you wouldn't
gain anything that way; it will still be too much and too long.
You have to get the following right, or you risk burning your house down.
No joke; don't do it unless you are darned sure you are doing it correctly.
A multiwire circuit is essentially a 240v circuit split between two 120v
circuits. If you can get the two circuits reasonably balanced, the only
current coming back on the neutral is the difference between the two; so
there is little or no voltage drop on the neutral which reduces the total
voltage drop.
Unfortunately, the dehumidifier and the heater are both big loads and
impossible to balance. Unless you can get them at the first part of the
run, you are out of luck. You could get a 240v heater (which is
automatically balanced), but I haven't seen a 240v dehumidifier.

To be sure you would have to do a detailed analysis with specific loads and
distances, but I suspect you are looking at putting in either a #10 circuit
for the big loads or a 240v circuit.


  #7   Report Post  
Posted to alt.home.repair
 
Posts: n/a
Default 12-3 Double Circuit Run Length - Should I Split the Circuit?

OK. So what you're saying is that the more balanced the two circuits
on the double pole breaker are, the less voltage drop I will have.
Theoretically then, if I had a 250' run with two outlets at the end of
the dual pole 20A breaker (one on circuit 1 and the other on circuit 2)
and had a 15A load on BOTH of them I'd be OK. But, if I removed ONE of
the 15A loads, I could be in trouble because the voltage drop would go
up and drive the load way up. Correct?

I think I could balance the load between circuits but I can't guarantee
it would be that way all the time so that may not be the best option
for me. Also, 10AWG wire will still have a high voltage drop for a
250' run (based on the voltage drop calculator using 120v).

What if I have two separate single pole 125' circuits using my 12-3 and
two 15A breakers, BUT, I combine the two hots of the 12-3 to make it
12-2 inside a junction box just before going into my circuit breaker
box (12-2 would be going into the box connecting to the breaker) and,
along the run, pigtail the two hots of the 12-3 together to look like
12-2 inside the outlet boxes. I will then have a very low voltage drop
on my 125ft run because the two wires of the 12-3 are combined. It
seems this option would get me the resistance of 8 or 9AWG wire while
at the same time giving me the shorter 125ft runs.

Thoughts? Dangers? I know if one the splices where the 12-3 is
combined to look like 12-2 fails then load & resistance will go up
driving up the load. But, that would be on an outlet by outlet basis (
I could even check it with a meter) and the 15A breakers would limit
risk somewhat. This method seems safer to me than trying to guarantee
I have the balanced double pole circuit option described above but
maybe I'm missing a potential problem. Thinking about it, it looks
like I'd have to join 4 12AWG wires together with a 12AWG pigtail for
each outlet (making 5 wires) inside a wirenut. That might be a
problem?

Thanks again...and I appreciate your feedback greatly.

Kevin

  #8   Report Post  
Posted to alt.home.repair
John Grabowski
 
Posts: n/a
Default 12-3 Double Circuit Run Length - Should I Split the Circuit?


wrote in message
ups.com...
Hello

I just finished wiring my basement with 12/3 wire. I was planning on
using a double pole breaker with two circuits and a shared neutral
(alternating circuits between outlets). My run is around the
perimeter of my basement inside wood framing studs. After all was said
and done with the requried routing, I've used about 250ft of wire.

I'm concerned that I may have too long of a run and that, instead of
creating one big 250ft run with alternating circuits on a double pole
20A breaker, I should just have two 125ft circuits on separate 20A
breakers. I guess now's the time to make my decision before I go into
my panel. I've already run the 12-3 wire but I don't mind using only
2 of the 3 wires if that will make these circuits better performing and
safer.

The reading I have done so far and the 13.6% voltage drop at 20A
calculated using this website:

http://www.powerstream.com/Wire_Size.htm

has me leaning heavily toward two separate 125ft circuits.

Any feedback is apprecaited. Thanks!

Kevin


Kevin, stop worrying about the voltage drop in your basement. It won't be a
problem with the intermittent loads that you will have on your outlets. You
can have 2- 20amp circuits or 4-20 amp circuits. That decision is up to
you. Don't double up any hot wires. If you have 12/3 going to each box you
can alternate circuits in every other box. For instance box one will be fed
from the black wire, box two will be fed from the red wire, box three will
be fed from the black wire and so on. That way you will have more even use
of the circuits, but balancing them should not be a major concern of yours
either.

Now get to work. I want to see pictures of the finished product. :-)

  #9   Report Post  
Posted to alt.home.repair
Kevin Ricks
 
Posts: n/a
Default 12-3 Double Circuit Run Length - Should I Split the Circuit?


wrote in message
ups.com...
Hello

I just finished wiring my basement with 12/3 wire. I was planning on
using a double pole breaker with two circuits and a shared neutral
(alternating circuits between outlets). My run is around the
perimeter of my basement inside wood framing studs. After all was said
and done with the requried routing, I've used about 250ft of wire.

I'm concerned that I may have too long of a run and that, instead of
creating one big 250ft run with alternating circuits on a double pole
20A breaker, I should just have two 125ft circuits on separate 20A
breakers. I guess now's the time to make my decision before I go into
my panel. I've already run the 12-3 wire but I don't mind using only
2 of the 3 wires if that will make these circuits better performing and
safer.

The reading I have done so far and the 13.6% voltage drop at 20A
calculated using this website:

http://www.powerstream.com/Wire_Size.htm

has me leaning heavily toward two separate 125ft circuits.

Any feedback is apprecaited. Thanks!

Kevin


I don't know how you have done your wiring but I don't think you have any
outlets that are really 250' of wire length to the panel. Didn't you go to
a certain place and branch out? I think you would calculate the drop of each
outlet independently. The furthest one away would be the worst case
everything else would be in between. If you are really worried about it
then run 10/3 from the panel to the first junction. However I would consider
splitting things up and adding at least 2 more breakers.

FYI- I have a 1300 sf basement and have 6 circuits for outlets/lights. 3 are
20A and 3 are 15A. Not including a bathroom and furnace room which also have
there own circuits. That is for 5 rooms and a hallway. A couple of the
circuits are used for lighting as well as outlets.

I used 12/3 on the 3 rooms that I finished myself. I use the extra wire to
provide some switched outlets.

Kevin







  #10   Report Post  
Posted to alt.home.repair
 
Posts: n/a
Default 12-3 Double Circuit Run Length - Should I Split the Circuit?

Thanks again to all for your feedback. I'll try not to worry about the
voltage drop but I just want to make sure I do this right! :-) I will
be living with it for a long time. :-)

See the image below for a rough drawing of my layout. The outlets are
spaced so that they meet the spacing required by code with a couple
extra thrown in just for convenient locations.

http://img77.imageshack.us/img77/6990/layout27yn.jpg

My current plan is to separate the circuits at the 125ft corner rather
than have one big 240v split circuit with alternating outlets that I
have to balance. If anybody else has feedback I'd love to hear it.
Specifically, is there any way to reduce voltage drop on a long run
other than to use super high gage wire that is a PITA to work with?



  #11   Report Post  
Posted to alt.home.repair
Art Greenberg
 
Posts: n/a
Default 12-3 Double Circuit Run Length - Should I Split the Circuit?

On 18 May 2006 04:15:54 -0700, wrote:
OK. So what you're saying is that the more balanced the two circuits
on the double pole breaker are, the less voltage drop I will have.


That's WRONG. Look, there is no free lunch. Your fixtures and appliances will
draw their rated current, and incur the same voltage drop no matter how well
balanced the multiwire circuit is.

It is true that, if perfectly balanced, there will be no current in the
neutral wire in a multiwire circuit. But in this case, the entire load is
borne by the two hot leads. Any imbalance results in a current in the neutral
lead equal to the magnitude of the imbalance (assuming pure resistive loads).
But at ALL times, the total current is the same.

The multiwire circuit is just a "trick" to enable having two hot lines share a
single neutral that is undersized by 50%. It works because the worst-case
imbalance, where 100% of the load is on one of the hot leads, can only result
in the same current flowing in that neutral as is flowing in the hot wire.

Theoretically then, if I had a 250' run with two outlets at the end of
the dual pole 20A breaker (one on circuit 1 and the other on circuit 2)
and had a 15A load on BOTH of them I'd be OK. But, if I removed ONE of
the 15A loads, I could be in trouble because the voltage drop would go
up and drive the load way up. Correct?


Nope.

Think of it this way. You have a pair of 100W incandescent lamps, one
connected to each circuit, at the end of 250 feet of wire. (For this example,
I assume these bulbs are ideal constant resistive loads.) A 100W light bulb
looks about like a 144 ohm resistor, so it will draw about 0.83A when the
voltage across it is 120V. When both lamps are on, that current is flowing
through both lamps. No current is flowing in the neutral. The total length of
wire feeding this circuit is 500 feet (the two hot leads in series).

Now turn off one of the lamps. What happens? Now the same 0.83A is flowing
though the one hot lead, and the neutral lead. The total length of wire
feeding this circuit is exactly the same, 500 feet (one hot lead and the
neutral lead). So the total voltage drop is the same.

I'll leave the thought experiment for an partial imbalance to you. Try it with
one 200W and one 100W lamp.

--
Art

  #12   Report Post  
Posted to alt.home.repair
Art Greenberg
 
Posts: n/a
Default 12-3 Double Circuit Run Length - Should I Split the Circuit?

On Thu, 18 May 2006 04:22:16 GMT, Toller wrote:

If all the heavy stuff will be on one of the 125' circuits, you wouldn't
gain anything that way; it will still be too much and too long.
You have to get the following right, or you risk burning your house down.
No joke; don't do it unless you are darned sure you are doing it correctly.
A multiwire circuit is essentially a 240v circuit split between two 120v
circuits. If you can get the two circuits reasonably balanced, the only
current coming back on the neutral is the difference between the two; so
there is little or no voltage drop on the neutral which reduces the total
voltage drop.


Bzzzt! Wrong. That would violate some rather basic physics.

You simply don't understand what happens in a multiwire circuit.

--
Art

  #13   Report Post  
Posted to alt.home.repair
 
Posts: n/a
Default 12-3 Double Circuit Run Length - Should I Split the Circuit?

I just thought of that. If I have room in my box for two double pole
breakers, I'll try to do alternating circuits for both branches. I
think I only have 3 slots left so maybe I'll do one double pole and one
single pole.

I do have electrical service in my garage and it's at about 125'. I
believe it's a 14GA 15A circuit. I know there's a voltage drop issue
there because I can't run my little pancake air compressor there (it
will barely kick over and never actually run) but the compressor runs
fine when run off an existing outlet right by my circuit breaker (for
the sump pump).

I have a bunch of 15A breakers in my box for my house. Is there any
way to make more room in my circuit breaker box for additional breakers
or is the only solution to upgrade to a bigger box (which I have no
plan on doing)?

  #14   Report Post  
Posted to alt.home.repair
Toller
 
Posts: n/a
Default 12-3 Double Circuit Run Length - Should I Split the Circuit?


" wrote in message
ups.com...
I just thought of that. If I have room in my box for two double pole
breakers, I'll try to do alternating circuits for both branches. I
think I only have 3 slots left so maybe I'll do one double pole and one
single pole.

I do have electrical service in my garage and it's at about 125'. I
believe it's a 14GA 15A circuit. I know there's a voltage drop issue
there because I can't run my little pancake air compressor there (it
will barely kick over and never actually run) but the compressor runs
fine when run off an existing outlet right by my circuit breaker (for
the sump pump).

I have a bunch of 15A breakers in my box for my house. Is there any
way to make more room in my circuit breaker box for additional breakers
or is the only solution to upgrade to a bigger box (which I have no
plan on doing)?

I ran out of room, so I got duplex breakers. They combine two 240v circuits
in the space of one. Maybe they are available for your brand.
They don't give your box any more electrical capacity, just more room; so
don't over do it.


  #15   Report Post  
Posted to alt.home.repair
kevin
 
Posts: n/a
Default 12-3 Double Circuit Run Length - Should I Split the Circuit?

You don't need two separate double breakers. Just use a single double
breaker for both runs. The blacks on both runs go to one phase, the
reds go to the other phase.

I think you can get rid of some breakers if you like by combining two
runs into a single circuit (as long as you are careful about hidden
split circuits (where they didn't use a double breaker as they should
have). Combining two 15A circuits from one of the phases into a single
15A circuit on the same phase will in most cases be fine. Most circuits
in your house will have less than a few amps at all times (unless you
have a penchant for plugging in and turning on ALL your appliances and
lights at the same time -- and even so... last time I tripped a breaker
due to simply too much draw was at least a decade ago).

Check with some others first, and think about the circuits a little
before doing anything. Sometimes there are reasons circuits are split:
maybe they really do need that much current (space heaters, AC, larger
loads, etc.), or are required to have their own circuit for code
reasons, etc.

-Kevin



  #16   Report Post  
Posted to alt.home.repair
 
Posts: n/a
Default 12-3 Double Circuit Run Length - Should I Split the Circuit?

Toller-
I will look into the duplex breaker. Sounds like exactly what I could
use.

Kevin-
I believe that, according to code, it's against the rules to to have
two wires attached to any terminal in the box. So I think what you're
saying will technically work but is considered a 'no-no'.

Thanks again for everybody's input!

  #17   Report Post  
Posted to alt.home.repair
 
Posts: n/a
Default 12-3 Double Circuit Run Length - Should I Split the Circuit?

My circuit breaker box has Siemens Type QP single pole 15A breakers.
Any idea what the compatible duplex version of the breaker is so I can
make some more room in my box?

I'm looking on the Siemens website but it's not jumping out at me...

Thanks,
Kevin

  #18   Report Post  
Posted to alt.home.repair
John Grabowski
 
Posts: n/a
Default 12-3 Double Circuit Run Length - Should I Split the Circuit?


" wrote in message
oups.com...
My circuit breaker box has Siemens Type QP single pole 15A breakers.
Any idea what the compatible duplex version of the breaker is so I can
make some more room in my box?

I'm looking on the Siemens website but it's not jumping out at me...

Thanks,
Kevin


Look on the panel cover or inside the panel for the maximum allowed circuit
breakers for that panel. It will also tell you what breakers are approved
for that panel. I think Murray circuit breakers are compatible and approved
for use with Siemens. You can buy Murray at Home Depot.

  #19   Report Post  
Posted to alt.home.repair
 
Posts: n/a
Default 12-3 Double Circuit Run Length - Should I Split the Circuit?

Thank you very much. You all have been very helpful and I appreciate
your taking the time to give me feedback! Hopefully I can pass on what
I've learned to help others like you have helped me.

Thanks again,
Kevin

Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Grizzly G0500 8" Jointer on 220/20A circuit Seawulf Woodworking 11 November 19th 05 04:31 AM
Open Neutral indication on switched split wired receptacle circuit [email protected] Home Ownership 0 November 10th 05 02:29 PM
Interesting take on a ring circuit John Rumm UK diy 17 August 18th 05 10:09 PM
Electrician's Qualifications. RmS UK diy 9 July 28th 05 11:20 PM
Maximum Length of a ring circuit PAB UK diy 0 August 30th 03 07:10 PM


All times are GMT +1. The time now is 11:14 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"