  #1   Report Post  
Posted to alt.home.repair
FDR
 
Posts: n/a
Default Electrical panel rewiring estimate

I have an old Wadsworth panel (circa 1964) in our house. I recently got a
quote from an electrician to upgrade the panel to Square D circuit breakers.
He proposed to leave the old Wadsworth box in place, including the wiring
entering the box, removing the existing circuit breakers and bus bars as
well as the main fuses, and installing the Square D bus bars, main circuit
breakers and new circuit breakers. This would result in less labor to
remove the old box and rerunning the wires in the new box. Total cost would
be about $600 (parts and labor) to approximately 30 breakers in a 200 Amp
service. Does this sound like a reasonable approach?

Thank you.



  #2   Report Post  
Posted to alt.home.repair
Richard Blaine
 
Posts: n/a
Default Electrical panel rewiring estimate

"FDR" wrote in message
...
I have an old Wadsworth panel (circa 1964) in our house. I recently got a
quote from an electrician to upgrade the panel to Square D circuit
breakers. He proposed to leave the old Wadsworth box in place, including
the wiring entering the box, removing the existing circuit breakers and bus
bars as well as the main fuses, and installing the Square D bus bars, main
circuit breakers and new circuit breakers. This would result in less labor
to remove the old box and rerunning the wires in the new box. Total cost
would be about $600 (parts and labor) to approximately 30 breakers in a 200
Amp service. Does this sound like a reasonable approach?

Thank you.


Might be worth asking Square D...


  #3   Report Post  
Posted to alt.home.repair
Jeff
 
Posts: n/a
Default Electrical panel rewiring estimate

Considering that the breakers alone would be at least $300, you are getting
a bargain.


"FDR" wrote in message
...
I have an old Wadsworth panel (circa 1964) in our house. I recently got a
quote from an electrician to upgrade the panel to Square D circuit
breakers. He proposed to leave the old Wadsworth box in place, including
the wiring entering the box, removing the existing circuit breakers and bus
bars as well as the main fuses, and installing the Square D bus bars, main
circuit breakers and new circuit breakers. This would result in less labor
to remove the old box and rerunning the wires in the new box. Total cost
would be about $600 (parts and labor) to approximately 30 breakers in a 200
Amp service. Does this sound like a reasonable approach?

Thank you.





  #4   Report Post  
Posted to alt.home.repair
David F. Kyle III
 
Posts: n/a
Default Electrical panel rewiring estimate

Make sure you are getting QO breakers. IMO much better than the standard
Harry Home Owner Square D breakers.


"Jeff" wrote in message
...
Considering that the breakers alone would be at least $300, you are
getting a bargain.


"FDR" wrote in message
...
I have an old Wadsworth panel (circa 1964) in our house. I recently got a
quote from an electrician to upgrade the panel to Square D circuit
breakers. He proposed to leave the old Wadsworth box in place, including
the wiring entering the box, removing the existing circuit breakers and
bus bars as well as the main fuses, and installing the Square D bus bars,
main circuit breakers and new circuit breakers. This would result in less
labor to remove the old box and rerunning the wires in the new box. Total
cost would be about $600 (parts and labor) to approximately 30 breakers in
a 200 Amp service. Does this sound like a reasonable approach?

Thank you.







  #5   Report Post  
Posted to alt.home.repair
FDR
 
Posts: n/a
Default Electrical panel rewiring estimate


wrote in message
ups.com...
Is he going to use the old box as a sub panel? Then use the new panel
to feed eavch circuit in the old panel?


No, the old panel would still be the main panel.




  #6   Report Post  
Posted to alt.home.repair
Edwin Pawlowski
 
Posts: n/a
Default Electrical panel rewiring estimate


"FDR" wrote in message
...
I have an old Wadsworth panel (circa 1964) in our house. I recently got a
quote from an electrician to upgrade the panel to Square D circuit
breakers. He proposed to leave the old Wadsworth box in place, including
the wiring entering the box, removing the existing circuit breakers and bus
bars as well as the main fuses, and installing the Square D bus bars, main
circuit breakers and new circuit breakers. This would result in less labor
to remove the old box and rerunning the wires in the new box. Total cost
would be about $600 (parts and labor) to approximately 30 breakers in a 200
Amp service. Does this sound like a reasonable approach?

Thank you.


Yes, it is a sensible way to do it. The box is a box. It does nothing but
enclose stuff. If you can leave it and all the wires in place, you save a
lot of labor. 30 breakers have to be in the range of $300 to $350 alone.


  #7   Report Post  
Posted to alt.home.repair
Rich256
 
Posts: n/a
Default Electrical panel rewiring estimate

FDR wrote:
I have an old Wadsworth panel (circa 1964) in our house. I recently got a
quote from an electrician to upgrade the panel to Square D circuit breakers.
He proposed to leave the old Wadsworth box in place, including the wiring
entering the box, removing the existing circuit breakers and bus bars as
well as the main fuses, and installing the Square D bus bars, main circuit
breakers and new circuit breakers. This would result in less labor to
remove the old box and rerunning the wires in the new box. Total cost would
be about $600 (parts and labor) to approximately 30 breakers in a 200 Amp
service. Does this sound like a reasonable approach?

Thank you.



Sounds like a bargain. My neighbor just sold his house and was required
to replace the box. It cost him $1400.
  #8   Report Post  
Posted to alt.home.repair
 
Posts: n/a
Default Electrical panel rewiring estimate


Rich256 wrote:
FDR wrote:
I have an old Wadsworth panel (circa 1964) in our house. I recently got a
quote from an electrician to upgrade the panel to Square D circuit breakers.
He proposed to leave the old Wadsworth box in place, including the wiring
entering the box, removing the existing circuit breakers and bus bars as
well as the main fuses, and installing the Square D bus bars, main circuit
breakers and new circuit breakers. This would result in less labor to
remove the old box and rerunning the wires in the new box. Total cost would
be about $600 (parts and labor) to approximately 30 breakers in a 200 Amp
service. Does this sound like a reasonable approach?

Thank you.



Sounds like a bargain. My neighbor just sold his house and was required
to replace the box. It cost him $1400.


  #9   Report Post  
Posted to alt.home.repair
 
Posts: n/a
Default Electrical panel rewiring estimate

Here in the Tampa bay area of Florida that is a bargain,make sure he
has it inspected though,if he wont allow a inspection by a city or
county inspector,thats why its so cheap,even if he isnt a lic eletrical
person you should be able to pull the permit as a home owner.

  #10   Report Post  
Posted to alt.home.repair
PipeDown
 
Posts: n/a
Default Electrical panel rewiring estimate


"FDR" wrote in message
...
I have an old Wadsworth panel (circa 1964) in our house. I recently got a
quote from an electrician to upgrade the panel to Square D circuit
breakers. He proposed to leave the old Wadsworth box in place, including
the wiring entering the box, removing the existing circuit breakers and bus
bars as well as the main fuses, and installing the Square D bus bars, main
circuit breakers and new circuit breakers. This would result in less labor
to remove the old box and rerunning the wires in the new box. Total cost
would be about $600 (parts and labor) to approximately 30 breakers in a 200
Amp service. Does this sound like a reasonable approach?

Thank you.




Actualluy sounds reasonable. Thats $200- $300 in parts and will take him
2-3 hours. I bet that price does not include the permit which in my city
would cost another $150 (94 for the permit and ~50 for the SE upgrade).
Power company should not charge for the temporary disconnect but will if you
require bigger service entrance conductors.

He should stick around for the inspection but will probably split before the
power company guy gets back to reconnect.




  #11   Report Post  
Posted to alt.home.repair
John Grabowski
 
Posts: n/a
Default Electrical panel rewiring estimate


"FDR" wrote in message
...
I have an old Wadsworth panel (circa 1964) in our house. I recently got a
quote from an electrician to upgrade the panel to Square D circuit

breakers.
He proposed to leave the old Wadsworth box in place, including the wiring
entering the box, removing the existing circuit breakers and bus bars as
well as the main fuses, and installing the Square D bus bars, main circuit
breakers and new circuit breakers. This would result in less labor to
remove the old box and rerunning the wires in the new box. Total cost

would
be about $600 (parts and labor) to approximately 30 breakers in a 200 Amp
service. Does this sound like a reasonable approach?

Thank you.


Although this sounds like an economical means and as someone else said "A
box is a box", this is most certainly NOT the way to go. When Square D has
their equipment tested to get a UL listing it is with the entire package.
Removing the guts from a Square D panel and installing them in a Wadsworth
panel will void all warranties and would not pass inspection. I am
surprised that a licensed electrical contractor would even suggest something
like that. Make sure that you get an insurance certificate from him because
you will need it.

I understand that you want to save money, but the liability in such an
installation is not worth a few dollars savings on a hatchet job. I suggest
that you get a few more quotes from other electrical contractors and I also
sugest that you have the installer get a permit and inspection for the job.

When a panel is upgraded the code requires that the grounding electrode
system be upgraded as well. That means two grounds rods installed and all
interior metal piping must be bonded.


John Grabowski
http://www.mrelectrician.tv




  #12   Report Post  
Posted to alt.home.repair
RobertM
 
Posts: n/a
Default Electrical panel rewiring estimate


When a panel is upgraded the code requires that the grounding electrode
system be upgraded as well. That means two grounds rods installed and all
interior metal piping must be bonded.


John Grabowski
http://www.mrelectrician.tv


Just had my 100 amp panel upgraded to a 200 amp panel. Everyone was
involved: Electrician, power company, inspector. Passed ok. They didn't
touch the grounding, used existing ground wire. Without digging down
there, how would they have known if it was one or two rods?

Bob
  #13   Report Post  
Posted to alt.home.repair
FDR
 
Posts: n/a
Default Electrical panel rewiring estimate


"John Grabowski" wrote in message
news

"FDR" wrote in message
...
I have an old Wadsworth panel (circa 1964) in our house. I recently got
a
quote from an electrician to upgrade the panel to Square D circuit

breakers.
He proposed to leave the old Wadsworth box in place, including the wiring
entering the box, removing the existing circuit breakers and bus bars as
well as the main fuses, and installing the Square D bus bars, main
circuit
breakers and new circuit breakers. This would result in less labor to
remove the old box and rerunning the wires in the new box. Total cost

would
be about $600 (parts and labor) to approximately 30 breakers in a 200 Amp
service. Does this sound like a reasonable approach?

Thank you.


Although this sounds like an economical means and as someone else said "A
box is a box", this is most certainly NOT the way to go. When Square D
has
their equipment tested to get a UL listing it is with the entire package.
Removing the guts from a Square D panel and installing them in a Wadsworth
panel will void all warranties and would not pass inspection. I am
surprised that a licensed electrical contractor would even suggest
something
like that. Make sure that you get an insurance certificate from him
because
you will need it.

I understand that you want to save money, but the liability in such an
installation is not worth a few dollars savings on a hatchet job. I
suggest
that you get a few more quotes from other electrical contractors and I
also
sugest that you have the installer get a permit and inspection for the
job.

I didn't say anything baout saving money. The guy happened to be at my house
doing electrical work and I asked him about the Wadsworth panel; if it was
dangerous being old and fact that breakers are hard to come by. He
mentioned they aren't UL certified and I asked him to quote replacing it.
He came back with the idea of just repacing the guts. I'm just trying to
see if it really makes that much of a diffierence.


When a panel is upgraded the code requires that the grounding electrode
system be upgraded as well. That means two grounds rods installed and all
interior metal piping must be bonded.


John Grabowski
http://www.mrelectrician.tv






  #15   Report Post  
Posted to alt.home.repair
Bud--
 
Posts: n/a
Default Electrical panel rewiring estimate

FDR wrote:
"John Grabowski" wrote in message
news
"FDR" wrote in message
...

I have an old Wadsworth panel (circa 1964) in our house. I recently got
a
quote from an electrician to upgrade the panel to Square D circuit


breakers.

He proposed to leave the old Wadsworth box in place, including the wiring
entering the box, removing the existing circuit breakers and bus bars as
well as the main fuses, and installing the Square D bus bars, main
circuit
breakers and new circuit breakers. This would result in less labor to
remove the old box and rerunning the wires in the new box. Total cost


would

be about $600 (parts and labor) to approximately 30 breakers in a 200 Amp
service. Does this sound like a reasonable approach?

Thank you.


Although this sounds like an economical means and as someone else said "A
box is a box", this is most certainly NOT the way to go. When Square D
has
their equipment tested to get a UL listing it is with the entire package.
Removing the guts from a Square D panel and installing them in a Wadsworth
panel will void all warranties and would not pass inspection. I am
surprised that a licensed electrical contractor would even suggest
something
like that. Make sure that you get an insurance certificate from him
because
you will need it.

I understand that you want to save money, but the liability in such an
installation is not worth a few dollars savings on a hatchet job. I
suggest
that you get a few more quotes from other electrical contractors and I
also
sugest that you have the installer get a permit and inspection for the
job.



I didn't say anything baout saving money. The guy happened to be at my house
doing electrical work and I asked him about the Wadsworth panel; if it was
dangerous being old and fact that breakers are hard to come by. He
mentioned they aren't UL certified and I asked him to quote replacing it.
He came back with the idea of just repacing the guts. I'm just trying to
see if it really makes that much of a diffierence.


I agree with John. The Square D guts would no longer be UL listed and
the installation would be a code violation. I would be surprised if the
Wadsworth breakers/panel aren't UL listed but havn't seen one for a real
long time.

bud--


  #16   Report Post  
Posted to alt.home.repair
John Grabowski
 
Posts: n/a
Default Electrical panel rewiring estimate


"RobertM" wrote in message
...

When a panel is upgraded the code requires that the grounding electrode
system be upgraded as well. That means two grounds rods installed and

all
interior metal piping must be bonded.


John Grabowski
http://www.mrelectrician.tv


Just had my 100 amp panel upgraded to a 200 amp panel. Everyone was
involved: Electrician, power company, inspector. Passed ok. They didn't
touch the grounding, used existing ground wire. Without digging down
there, how would they have known if it was one or two rods?

Bob


It is possible to test the ground wire to determine if it is good for the
code mandated 25 ohms or less. Usually a 100 amp service has a #6 copper or
#4 aluminum (Or #8 copper armored) grounding electrode conductor. If you
have water service from the street the conductor would be connected to that.
A 200 amp service requires a #4 copper or #2 aluminum for the primary
electrode grounding conductor. The supplemental grounding electrode
conductor can be #6 copper. Your local jurisdiction may have less stringent
code requirements.

Did the electrician bond the hot and cold water pipes to the gas pipe? Did
they install a jumper from one side of the water meter to the other?

  #17   Report Post  
Posted to alt.home.repair
RobertM
 
Posts: n/a
Default Electrical panel rewiring estimate

John Grabowski wrote:
"RobertM" wrote in message
...
When a panel is upgraded the code requires that the grounding electrode
system be upgraded as well. That means two grounds rods installed and

all
interior metal piping must be bonded.


John Grabowski
http://www.mrelectrician.tv

Just had my 100 amp panel upgraded to a 200 amp panel. Everyone was
involved: Electrician, power company, inspector. Passed ok. They didn't
touch the grounding, used existing ground wire. Without digging down
there, how would they have known if it was one or two rods?

Bob


It is possible to test the ground wire to determine if it is good for the
code mandated 25 ohms or less. Usually a 100 amp service has a #6 copper or
#4 aluminum (Or #8 copper armored) grounding electrode conductor. If you
have water service from the street the conductor would be connected to that.
A 200 amp service requires a #4 copper or #2 aluminum for the primary
electrode grounding conductor. The supplemental grounding electrode
conductor can be #6 copper. Your local jurisdiction may have less stringent
code requirements.

Did the electrician bond the hot and cold water pipes to the gas pipe? Did
they install a jumper from one side of the water meter to the other?


The water meter is 40 feet from the power entrance. Everything from the
water meter to the house is PVC. No, they didn't wire anything to the
water pipes. The only gas up here on the mountain is propane. I suppose
30 feet of buried copper tubing would make a decent ground but I don't
think it would be wise to connect to that. To add to all of this, the
wires from the transformer two poles away to the house have not yet been
changed by the power company. Wires are presently not adequate for 200
amp service. Maybe the power company will upgrade the ground if and when
they upgrade their service. Having a 200 amp panel in rural Tennessee
doesn't mean the power company can supply 200 amps. And I thought the
TVA was all about abundant electricity.

Bob


  #18   Report Post  
Posted to alt.home.repair
Goedjn
 
Posts: n/a
Default Electrical panel rewiring estimate

On Thu, 02 Mar 2006 03:14:26 GMT, "FDR"
wrote:


"John Grabowski" wrote in message
news

"FDR" wrote in message
...
I have an old Wadsworth panel (circa 1964) in our house. I recently got
a
quote from an electrician to upgrade the panel to Square D circuit

breakers.
He proposed to leave the old Wadsworth box in place, including the wiring
entering the box, removing the existing circuit breakers and bus bars as
well as the main fuses, and installing the Square D bus bars, main
circuit
breakers and new circuit breakers. This would result in less labor to
remove the old box and rerunning the wires in the new box. Total cost

would
be about $600 (parts and labor) to approximately 30 breakers in a 200 Amp
service. Does this sound like a reasonable approach?

Thank you.


Although this sounds like an economical means and as someone else said "A
box is a box", this is most certainly NOT the way to go. When Square D
has
their equipment tested to get a UL listing it is with the entire package.
Removing the guts from a Square D panel and installing them in a Wadsworth
panel will void all warranties and would not pass inspection. I am
surprised that a licensed electrical contractor would even suggest
something
like that. Make sure that you get an insurance certificate from him
because
you will need it.

I understand that you want to save money, but the liability in such an
installation is not worth a few dollars savings on a hatchet job. I
suggest
that you get a few more quotes from other electrical contractors and I
also
sugest that you have the installer get a permit and inspection for the
job.


I didn't say anything baout saving money. The guy happened to be at my house
doing electrical work and I asked him about the Wadsworth panel; if it was
dangerous being old and fact that breakers are hard to come by. He
mentioned they aren't UL certified and I asked him to quote replacing it.
He came back with the idea of just repacing the guts. I'm just trying to
see if it really makes that much of a diffierence.


I'd first ask your local authority whether it's permissable, before
worrying about whether it will work. It shouldn't save you more
than a couple hours labor, and maybe $100 on the case, though,
as long as the new box has entry holes in the same places.
  #19   Report Post  
Posted to alt.home.repair
FDR
 
Posts: n/a
Default Electrical panel rewiring estimate


"volts500" wrote in message
oups.com...
FDR wrote:

I didn't say anything baout saving money. The guy happened to be at my
house
doing electrical work and I asked him about the Wadsworth panel; if it
was
dangerous being old and fact that breakers are hard to come by. He
mentioned they aren't UL certified and I asked him to quote replacing it.
He came back with the idea of just repacing the guts. I'm just trying to
see if it really makes that much of a diffierence.


It's still a hack job. Any electrician worth his salt can remove the
old panel and replace it with a new one instead of gerry rigging an old
panel. You should seriously consider finding another electrician.
Retrofitting that old Wadsworth with Sq.D guts will NOT meet NEC. That
$600 is probably about half the going rate.


What part of NEC doesn't it meet, if you don't mind answering?


  #20   Report Post  
Posted to alt.home.repair
John Grabowski
 
Posts: n/a
Default Electrical panel rewiring estimate


"FDR" wrote in message
...

"volts500" wrote in message
oups.com...
FDR wrote:

I didn't say anything baout saving money. The guy happened to be at my
house
doing electrical work and I asked him about the Wadsworth panel; if it
was
dangerous being old and fact that breakers are hard to come by. He
mentioned they aren't UL certified and I asked him to quote replacing

it.
He came back with the idea of just repacing the guts. I'm just trying

to
see if it really makes that much of a diffierence.


It's still a hack job. Any electrician worth his salt can remove the
old panel and replace it with a new one instead of gerry rigging an old
panel. You should seriously consider finding another electrician.
Retrofitting that old Wadsworth with Sq.D guts will NOT meet NEC. That
$600 is probably about half the going rate.


What part of NEC doesn't it meet, if you don't mind answering?



Articles 110.2, 110.3(A)(1), 110.3(B)

Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Electrical Panel Question James \Cubby\ Culbertson Home Repair 21 January 10th 05 06:14 AM
Onan DJE generator update (electrical panel) Jack Hayes Metalworking 3 December 12th 04 06:23 PM
Service panel upgrade question Speedy Jim Home Repair 5 December 14th 03 05:17 AM
Help upgrading Service panel from 60A to 125A, please. DaveG Home Repair 33 December 3rd 03 03:57 AM
New Electrical Regs PoP UK diy 22 September 1st 03 08:41 PM


All times are GMT +1. The time now is 11:02 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"