Posted to alt.home.repair
|
|||
|
|||
how to test gas copper line for leaks
We need to test a gas copper line for leaks and we're currently using
water at about 115 psi and a pressure gauge, but I am not sure this is the right approach. I'd like to ask what is the standard procedure to test a gas copper line for leaks. Is water or air used? At what pressure? For how long? What would be an acceptable drop in pressure in this period of time? Can an unexpensive pressure gauge ($15 or so) be used with water or air? Thanks a lot in advance. |
#2
Posted to alt.home.repair
|
|||
|
|||
how to test gas copper line for leaks
"renux" wrote in message ups.com... We need to test a gas copper line for leaks and we're currently using water at about 115 psi and a pressure gauge, but I am not sure this is the right approach. I'd like to ask what is the standard procedure to test a gas copper line for leaks. Is water or air used? At what pressure? For how long? What would be an acceptable drop in pressure in this period of time? Can an unexpensive pressure gauge ($15 or so) be used with water or air? Thanks a lot in advance. Where I live (AZ) the gas is delivered to the residence at ~ 11 ounces of pressure. We do not use copper for gas lines, black iron and galvanized are the choices we have. Tests are done with air at 30 psi. No leaks for 24 hours. What does the AHJ want you to do? What does the utility supply and what do they recommend? |
#3
Posted to alt.home.repair
|
|||
|
|||
how to test gas copper line for leaks
One older technician for our local gas company goes around to each joint
with a match. I like to use soapy water. You can also put a tee in the line with a Schrader valve and use an electronic tire pressure gauge. Any pressure drop is not acceptable. DO NOT put water inside the tubing. "renux" wrote in message ups.com... We need to test a gas copper line for leaks and we're currently using water at about 115 psi and a pressure gauge, but I am not sure this is the right approach. I'd like to ask what is the standard procedure to test a gas copper line for leaks. Is water or air used? At what pressure? For how long? What would be an acceptable drop in pressure in this period of time? Can an unexpensive pressure gauge ($15 or so) be used with water or air? Thanks a lot in advance. |
#4
Posted to alt.home.repair
|
|||
|
|||
how to test gas copper line for leaks
Copper??? Too soft to use. If you want to sweat those together with
ANY gas in there good luck! Galvanized or Black Pipe is the way to normally go for Natural gas. |
#5
Posted to alt.home.repair
|
|||
|
|||
how to test gas copper line for leaks
I don't think he said natural gas.
wrote in message oups.com... Copper??? Too soft to use. If you want to sweat those together with ANY gas in there good luck! Galvanized or Black Pipe is the way to normally go for Natural gas. |
#6
Posted to alt.home.repair
|
|||
|
|||
how to test gas copper line for leaks
|
#7
Posted to alt.home.repair
|
|||
|
|||
how to test gas copper line for leaks
He didn't say anything about sweating copper either.
"Keith Williams" wrote in message T... In article , says... I don't think he said natural gas. Ok, maybe you'd rather sweat copper with propane in there? ;-) -- Keith wrote in message oups.com... Copper??? Too soft to use. If you want to sweat those together with ANY gas in there good luck! Galvanized or Black Pipe is the way to normally go for Natural gas. |
#8
Posted to alt.home.repair
|
|||
|
|||
how to test gas copper line for leaks
"Keith Williams" wrote in message T... In article , says... I don't think he said natural gas. Ok, maybe you'd rather sweat copper with propane in there? ;-) -- Keith Propane is often done with copper, mostly compression fittings. As for sweating with propane in it, yes, it can be done. No., it won't explode. All of our natural gas lines in commercial and industrial are welded. Yes, they are sometimes welded with gas in them, but the meter shut off. |
#9
Posted to alt.home.repair
|
|||
|
|||
how to test gas copper line for leaks
Did you mean flare fittings?
"Edwin Pawlowski" wrote in message news:EkcAf.150$Jn1.122@trndny01... "Keith Williams" wrote in message T... In article , says... I don't think he said natural gas. Ok, maybe you'd rather sweat copper with propane in there? ;-) -- Keith Propane is often done with copper, mostly compression fittings. As for sweating with propane in it, yes, it can be done. No., it won't explode. All of our natural gas lines in commercial and industrial are welded. Yes, they are sometimes welded with gas in them, but the meter shut off. |
#10
Posted to alt.home.repair
|
|||
|
|||
how to test gas copper line for leaks
"Bob" wrote in message ... Did you mean flare fittings? Yeah, them things you tighten with a wrench. |
#11
Posted to alt.home.repair
|
|||
|
|||
how to test gas copper line for leaks
We use butane and "type L" copper, which is thicker than normal copper
for water. I am told that type L copper is ok for gas as long as the pipe is safe from being hit, and with the advantage that copper is more resistent to corrosion. If the pipe is exposed to physical damage, then galvanized should be used. I called my local AHJ, and they pointed me to an official norm that states to use twice the normal-use pressure for 30 min. They also pointed me to a certified expert, which I am actually going to hire to do the testing. Thanks every body that responded. Your advice was very helpful! Cheers |
#12
Posted to alt.home.repair
|
|||
|
|||
how to test gas copper line for leaks
Around here, copper can be used with propane or natural gas. It is not
allowed to have sweated fittings, nor compression fittings, they all must be flared. The copper must be flexible, not sure of the grade, but it is the thicker wall pipe. "Edwin Pawlowski" wrote in message news:EkcAf.150$Jn1.122@trndny01... "Keith Williams" wrote in message T... In article , says... I don't think he said natural gas. Ok, maybe you'd rather sweat copper with propane in there? ;-) -- Keith Propane is often done with copper, mostly compression fittings. As for sweating with propane in it, yes, it can be done. No., it won't explode. All of our natural gas lines in commercial and industrial are welded. Yes, they are sometimes welded with gas in them, but the meter shut off. |
#13
Posted to alt.home.repair
|
|||
|
|||
how to test gas copper line for leaks
I saw a wench once.
"Edwin Pawlowski" wrote in message ... "Bob" wrote in message ... Did you mean flare fittings? Yeah, them things you tighten with a wrench. |
#14
Posted to alt.home.repair
|
|||
|
|||
how to test gas copper line for leaks
Type L is normally used for water lines also. Type M is used for hydronic
heat. If you already pressure tested that gas line with water, then you should tell "certified expert". "renux" wrote in message oups.com... We use butane and "type L" copper, which is thicker than normal copper for water. I am told that type L copper is ok for gas as long as the pipe is safe from being hit, and with the advantage that copper is more resistent to corrosion. If the pipe is exposed to physical damage, then galvanized should be used. I called my local AHJ, and they pointed me to an official norm that states to use twice the normal-use pressure for 30 min. They also pointed me to a certified expert, which I am actually going to hire to do the testing. Thanks every body that responded. Your advice was very helpful! Cheers |
#15
Posted to alt.home.repair
|
|||
|
|||
how to test gas copper line for leaks
A long time ago, the only thing you could use for natural gas was black iron
pipe. Years ago, gas suppliers started putting an additive in the gas that made the use of copper ok, but some local codes were never changed. "EXT" etonks@sunstormADD-DOT-COM wrote in message anews.com... Around here, copper can be used with propane or natural gas. It is not allowed to have sweated fittings, nor compression fittings, they all must be flared. The copper must be flexible, not sure of the grade, but it is the thicker wall pipe. "Edwin Pawlowski" wrote in message news:EkcAf.150$Jn1.122@trndny01... "Keith Williams" wrote in message T... In article , says... I don't think he said natural gas. Ok, maybe you'd rather sweat copper with propane in there? ;-) -- Keith Propane is often done with copper, mostly compression fittings. As for sweating with propane in it, yes, it can be done. No., it won't explode. All of our natural gas lines in commercial and industrial are welded. Yes, they are sometimes welded with gas in them, but the meter shut off. |
#16
Posted to alt.home.repair
|
|||
|
|||
how to test gas copper line for leaks
"renux" wrote in message ups.com... We need to test a gas copper line for leaks and we're currently using water at about 115 psi and a pressure gauge, but I am not sure this is the right approach. I'd like to ask what is the standard procedure to test a gas copper line for leaks. Is water or air used? At what pressure? For how long? What would be an acceptable drop in pressure in this period of time? Can an unexpensive pressure gauge ($15 or so) be used with water or air? Thanks a lot in advance. They make a test gauge for gas it has a 3/4 female pipe thread the body has a gauge attached and a Schrader (sp) valve for a bicycle pump. 15 psi is normal for residential in my area. I would pump it up and soap the joints. I can't remember the Time to hold pressure. The PSI can vary From area to area Type of line welded . Check Local Codes. Remember it's gas so you want to do it right. test gauge http://uniweld.com/catalog/gauges_th...est_gauges.htm 3/4" FPT Hex-Body |
#17
Posted to alt.home.repair
|
|||
|
|||
how to test gas copper line for leaks
I remember when only black iron was allowed. The switch to copper came in
our area when the utility (which I worked for) decided to use copper lines from the underground to the meter because there was less damage to the service from frost heaving. The copper would just bend a bit where the black iron elbows and couplings on the meter could crack or pull loose with solid iron pipe. "Bob" wrote in message ... A long time ago, the only thing you could use for natural gas was black iron pipe. Years ago, gas suppliers started putting an additive in the gas that made the use of copper ok, but some local codes were never changed. "EXT" etonks@sunstormADD-DOT-COM wrote in message anews.com... Around here, copper can be used with propane or natural gas. It is not allowed to have sweated fittings, nor compression fittings, they all must be flared. The copper must be flexible, not sure of the grade, but it is the thicker wall pipe. "Edwin Pawlowski" wrote in message news:EkcAf.150$Jn1.122@trndny01... "Keith Williams" wrote in message T... In article , says... I don't think he said natural gas. Ok, maybe you'd rather sweat copper with propane in there? ;-) -- Keith Propane is often done with copper, mostly compression fittings. As for sweating with propane in it, yes, it can be done. No., it won't explode. All of our natural gas lines in commercial and industrial are welded. Yes, they are sometimes welded with gas in them, but the meter shut off. |
#18
Posted to alt.home.repair
|
|||
|
|||
how to test gas copper line for leaks
"EXT" etonks@sunstormADD-DOT-COM wrote in message anews.com... I remember when only black iron was allowed. The switch to copper came in our area when the utility (which I worked for) decided to use copper lines from the underground to the meter because there was less damage to the service from frost heaving. The copper would just bend a bit where the black iron elbows and couplings on the meter could crack or pull loose with solid iron pipe. Your forgot to mention something the original poster is unaware of. They tested the pipes BEFORE they buried them. Bill |
#19
Posted to alt.home.repair
|
|||
|
|||
how to test gas copper line for leaks
Sacramento Dave wrote:
"renux" wrote in message ups.com... We need to test a gas copper line for leaks and we're currently using water at about 115 psi and a pressure gauge, but I am not sure this is the right approach. I'd like to ask what is the standard procedure to test a gas copper line for leaks. Is water or air used? At what pressure? For how long? What would be an acceptable drop in pressure in this period of time? Can an unexpensive pressure gauge ($15 or so) be used with water or air? Thanks a lot in advance. They make a test gauge for gas it has a 3/4 female pipe thread the body has a gauge attached and a Schrader (sp) valve for a bicycle pump. 15 psi is normal for residential in my area. I would pump it up and soap the joints. I can't remember the Time to hold pressure. The PSI can vary From area to area Type of line welded . Check Local Codes. Remember it's gas so you want to do it right. test gauge http://uniweld.com/catalog/gauges_th...est_gauges.htm 3/4" FPT Hex-Body When I was in Arizona they pressurized to 14 psi and waited 24 hours. Here in Tennessee, they turn on the propane and soap the joints. If the house is still there 20 minutes later, they figure it's ok. Bob |
#20
Posted to alt.home.repair
|
|||
|
|||
how to test gas copper line for leaks
Either way is acceptable. I personally don't like going around with a match
or lighter, because you can miss a small leak. "RobertM" wrote in message ... Sacramento Dave wrote: "renux" wrote in message ups.com... We need to test a gas copper line for leaks and we're currently using water at about 115 psi and a pressure gauge, but I am not sure this is the right approach. I'd like to ask what is the standard procedure to test a gas copper line for leaks. Is water or air used? At what pressure? For how long? What would be an acceptable drop in pressure in this period of time? Can an unexpensive pressure gauge ($15 or so) be used with water or air? Thanks a lot in advance. They make a test gauge for gas it has a 3/4 female pipe thread the body has a gauge attached and a Schrader (sp) valve for a bicycle pump. 15 psi is normal for residential in my area. I would pump it up and soap the joints. I can't remember the Time to hold pressure. The PSI can vary From area to area Type of line welded . Check Local Codes. Remember it's gas so you want to do it right. test gauge http://uniweld.com/catalog/gauges_th...est_gauges.htm 3/4" FPT Hex-Body When I was in Arizona they pressurized to 14 psi and waited 24 hours. Here in Tennessee, they turn on the propane and soap the joints. If the house is still there 20 minutes later, they figure it's ok. Bob |
#21
Posted to alt.home.repair
|
|||
|
|||
how to test gas copper line for leaks
On Fri, 20 Jan 2006 21:09:56 GMT, Edwin Pawlowski wrote:
Propane is often done with copper, mostly compression fittings. As for sweating with propane in it, yes, it can be done. No., it won't explode. All of our natural gas lines in commercial and industrial are welded. Yes, they are sometimes welded with gas in them, but the meter shut off. My folks had a natural gas line leak killing the grass in a spot just off the side entrance. The gas company dug it up, then the repair guy cleaned off the plastic wrapping the pipe. He then took a torch to the pipe upstream of the leak, heating the pipe to red hot. Then he used a pair of pliers and crimped the pipe shut, stopping the gas flow. Leaky section of pipe cut out, new section welded in. Heat the crimped area red hot again, and finagle it with pliers to open it back up. Tested for leaks (bubble solution) and finding none, reapply protective pipe wrap and fill in the hole. Grass grows great now. Oh, this was in the drop between main line and meter, at least 50ft from the main line, and at least 75ft from the meter. sdb -- Wanted: Omnibook 800 & accessories, cheap, working or not sdbuse1 on mailhost bigfoot.com |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Weird phone wiring with new flat - help needed with BT Broadband and master socket | UK diy | |||
type of copper to use to repipe house | Home Repair | |||
Telephone Line Problems | Home Repair | |||
Copper pipe sizing. Is bigger better? | Home Repair | |||
test for Jimbo | Metalworking |