  #1   Report Post  
Posted to alt.home.repair
BiloxiBoy
 
Posts: n/a
Default Seeking Advice - New Main Breaker & Sub-Panel

Since Hurricane Katrina gutted my home - and took all the sheetrock
with it - I am upgrading ALL of the wiring (used to be "mostly"
ungrounded throughout). Consequently, I want to add a new sub-panel
inside the home to which all circuits will run. This will eliminate
the present setup of an ungrounded 4-circuit box and another grounded
(but very old) fuse panel. The home is small - only about 1,000 sq.
feet. To power that sub-panel, here's the way I've got it sketched
out:

Outside and adjacent to the meter, I will add a single 100A main
circuit breaker in a dedicated box. That breaker will then supply
power to the sub-panel (about 30 feet away) via a #4, four-wire romex
cable with two hots, a neutral, and a ground. I will bond the ground
and neutral at the main circuit breaker outside and separate them at
the sub. The sub contains 12 breakers and has no main breaker. To
ground the system, I will run #6 copper wire from the 100A breaker box
outside to an 8-foot grounding rod just below the box.

Currently, another panel is also connected to the meter and it provides
power to the A/C, a detached shop, and the two old panels listed above.
My plan is to leave it in place as is (minus the two 60A breakers for
the old panels) and wire the new 100A breaker box to the meter as well.

Can I wire both boxes to the load side of the meter, or is there a
better or another way?

Any input on my plan or the question would be appreciated.

  #2   Report Post  
Posted to alt.home.repair
Bob
 
Posts: n/a
Default Seeking Advice - New Main Breaker & Sub-Panel

Put in a whole new main panel and run all new wiring back to it.

"BiloxiBoy" wrote in message
oups.com...
Since Hurricane Katrina gutted my home - and took all the sheetrock
with it - I am upgrading ALL of the wiring (used to be "mostly"
ungrounded throughout). Consequently, I want to add a new sub-panel
inside the home to which all circuits will run. This will eliminate
the present setup of an ungrounded 4-circuit box and another grounded
(but very old) fuse panel. The home is small - only about 1,000 sq.
feet. To power that sub-panel, here's the way I've got it sketched
out:

Outside and adjacent to the meter, I will add a single 100A main
circuit breaker in a dedicated box. That breaker will then supply
power to the sub-panel (about 30 feet away) via a #4, four-wire romex
cable with two hots, a neutral, and a ground. I will bond the ground
and neutral at the main circuit breaker outside and separate them at
the sub. The sub contains 12 breakers and has no main breaker. To
ground the system, I will run #6 copper wire from the 100A breaker box
outside to an 8-foot grounding rod just below the box.

Currently, another panel is also connected to the meter and it provides
power to the A/C, a detached shop, and the two old panels listed above.
My plan is to leave it in place as is (minus the two 60A breakers for
the old panels) and wire the new 100A breaker box to the meter as well.

Can I wire both boxes to the load side of the meter, or is there a
better or another way?

Any input on my plan or the question would be appreciated.



  #3   Report Post  
Posted to alt.home.repair
BiloxiBoy
 
Posts: n/a
Default Seeking Advice - New Main Breaker & Sub-Panel

Thanks, Bob. That sounds like a great idea but I'm wondering if I can
buy a panel that has only a few spaces, and I guess I'd also have these
questions:

1. Since the entire house load calculates out to about 81 amps
(excluding central A/C), should I get a 100A main service panel, or
should I go higher? All the big appliances are gas - stove, dryer, and
central heat.
2. If I go higher, how high can I go before the service has to be
upgraded at the meter?
3. If I get a 100A panel, can I still run a sub panel to the shop (no
220) and still supply power to the central air?
4. What size main breaker would I need for the house panel, and does
it run off it's own breaker or will the main switch in the new main
panel suffice?

Sorry for all the questions, but it seems these are the kinds of things
that a lot of folks know a whole lot more about that I do...

  #4   Report Post  
Posted to alt.home.repair
Tom Horne, Electrician
 
Posts: n/a
Default Seeking Advice - New Main Breaker & Sub-Panel

BiloxiBoy wrote:
Since Hurricane Katrina gutted my home - and took all the sheetrock
with it - I am upgrading ALL of the wiring (used to be "mostly"
ungrounded throughout). Consequently, I want to add a new sub-panel
inside the home to which all circuits will run. This will eliminate
the present setup of an ungrounded 4-circuit box and another grounded
(but very old) fuse panel. The home is small - only about 1,000 sq.
feet. To power that sub-panel, here's the way I've got it sketched
out:

Outside and adjacent to the meter, I will add a single 100A main
circuit breaker in a dedicated box. That breaker will then supply
power to the sub-panel (about 30 feet away) via a #4, four-wire romex
cable with two hots, a neutral, and a ground. I will bond the ground
and neutral at the main circuit breaker outside and separate them at
the sub. The sub contains 12 breakers and has no main breaker. To
ground the system, I will run #6 copper wire from the 100A breaker box
outside to an 8-foot grounding rod just below the box.

Currently, another panel is also connected to the meter and it provides
power to the A/C, a detached shop, and the two old panels listed above.
My plan is to leave it in place as is (minus the two 60A breakers for
the old panels) and wire the new 100A breaker box to the meter as well.

Can I wire both boxes to the load side of the meter, or is there a
better or another way?

Any input on my plan or the question would be appreciated.


That existing outdoor panel is your service equipment. You will need to
answer some questions first before we can provide valid answers. How
many breakers is the existing outdoor panel, that is supplied directly
from the meter, capable of holding? What is the listed ampacity of the
existing outdoor panel? Is your service overhead or underground? What
size in amperes is the meter can? What wire gage are the Service entry
conductors that supply your meter from the end of your service drop of
lateral? Do you have the room to install a wiring trough between the
meter can and the existing service equipment? Do you have any way to
post photographs of the existing panels and meter.

I really do want to help. You folks have been through enough without
having problems with misinformation during reconstruction. I would
welcome direct Email or telephone contact. If you Email your telephone
number I will call you to save you the cost of the call or if you would
prefer you can ask for my number and I will give it to you.
--
Tom Horne

"This alternating current stuff is just a fad. It is much too dangerous
for general use." Thomas Alva Edison
  #5   Report Post  
Posted to alt.home.repair
BiloxiBoy
 
Posts: n/a
Default Seeking Advice - New Main Breaker & Sub-Panel

Wow Tom - Thanks for the reply, and for the compasion in your post. It
has, to say the least, been an interesting four months since Katrina!!
We have a loooong way to go, but every day with progress is a step in
the right direction...

In answer, here's what I have now:

The outdoor panel has four breakers; a 60A and a 30A to the two
existing sub-panels inside, a 40A for the A/C, and a 20A(??) for the
shop. There is no more room for any more breakers - at least not
double-pole.

I'm not sure on the ampacity on the existing panel outside as it is
very old and has no doubt seen its better days. No lables that I can
find!! The house was built in the 40's, and might have received a
minimal service upgrade in the 60's, but that's about it.

The service is overhead and there's a brand new meter can that I
installed in the days shortly after the storm while the power was still
off everywhere (the old one was ripped off the side of the house, and I
"straigntened" the mast out for re-use).

I'm not sure what the meter can is rated at, but here's a picture of
the meter, the existing service, and the new panel I have just wired
inside (not hot yet):
http://img.photobucket.com/albums/v4...icalIssues.jpg

Not sure on the guage of the wire from the meter to the existing panel,
but it is brand new since Katrina as I got it from the neighbor who had
it as leftovers since he had recently upgraded to 200A service. It is
bigger than what I took out - that I do know.

As for the trough, there is presently a steel conduit that connects the
two - and the present panel box is directly below the meter, but not an
integral part. There are two other unused knockouts on the bottom of
the meter can, and one on each side.

Again, I sincerely appreciate your input and your offer for assistance.
It's nice to know there are folks out there who recognize how things
are going around here.



  #6   Report Post  
Posted to alt.home.repair
BiloxiBoy
 
Posts: n/a
Default Seeking Advice - New Main Breaker & Sub-Panel

Thanks, Tom for the reply and for the compasion in your post. In
answer, here's what I have now:

There are four breakers in the outdoor panel - a 60A and a 30A for the
two existing sub-panels inside, a 40A for the A/C, and a 20A (??) for
the shop. There is no more room for any others - at least not
double-pole.

Not sure on the ampacity of the existing service panel as it is very
old and has seen its better days. No lables that I can find. It is
shown (inside cover still on) in the picture link below.

The service is overhead and the meter can is new since Katrina as the
old one was ripped off the side of the house. I bought and installed
it in the days following the storm, but I am not sure of the rating -
but is is brand new. Here's a link to the picture.
http://img.photobucket.com/albums/v4...icalIssues.jpg

The wires from the meter to the panel are new since Katrina as well. I
got the cable from a neighbor who had just recently upgraded his
service to 200A. Not sure on the size, but it is bigger than what I
took out.

As for a trough, there is presently a metal conduit connecting the
meter to the panel. There are also two other unused knockouts on the
bottom of the can and one on each side.

Again, thanks for your help and your recognition of the conditions
here. We've got a looooong way to go, but progress every day is
contributing to success in the long term.

  #7   Report Post  
Posted to alt.home.repair
Thomas D. Horne, FF EMT
 
Posts: n/a
Default Seeking Advice - New Main Breaker & Sub-Panel

BiloxiBoy wrote:
Wow Tom - Thanks for the reply, and for the compasion in your post. It
has, to say the least, been an interesting four months since Katrina!!
We have a loooong way to go, but every day with progress is a step in
the right direction...

In answer, here's what I have now:

The outdoor panel has four breakers; a 60A and a 30A to the two
existing sub-panels inside, a 40A for the A/C, and a 20A(??) for the
shop. There is no more room for any more breakers - at least not
double-pole.

I'm not sure on the ampacity on the existing panel outside as it is
very old and has no doubt seen its better days. No lables that I can
find!! The house was built in the 40's, and might have received a
minimal service upgrade in the 60's, but that's about it.

The service is overhead and there's a brand new meter can that I
installed in the days shortly after the storm while the power was still
off everywhere (the old one was ripped off the side of the house, and I
"straigntened" the mast out for re-use).

I'm not sure what the meter can is rated at, but here's a picture of
the meter, the existing service, and the new panel I have just wired
inside (not hot yet):
http://img.photobucket.com/albums/v4...icalIssues.jpg

Not sure on the guage of the wire from the meter to the existing panel,
but it is brand new since Katrina as I got it from the neighbor who had
it as leftovers since he had recently upgraded to 200A service. It is
bigger than what I took out - that I do know.

As for the trough, there is presently a steel conduit that connects the
two - and the present panel box is directly below the meter, but not an
integral part. There are two other unused knockouts on the bottom of
the meter can, and one on each side.

Again, I sincerely appreciate your input and your offer for assistance.
It's nice to know there are folks out there who recognize how things
are going around here.

George

What I would suggest is a new panel to replace your old outdoor one.
That will cost the same or less than a separate disconnect or breaker
enclosure. Your new Service Equipment should have a main breaker and
room for 12 or so load breakers. The Square D QO version of that panel
can be equipped with a manual interlock to permit generator supply to
your home. That panel will have a 200 ampere main breaker and plenty of
room for the breakers to supply your existing loads. You cannot attach
additional equipment to your existing meter's lugs unless they were
specifically designed for that service. A replacement panel will also
provide a neat and well organized layout.
--
Tom Horne

--
Tom Horne

Well we aren't no thin blue heroes and yet we aren't no blackguards to.
We're just working men and woman most remarkable like you.
  #8   Report Post  
Posted to alt.home.repair
Thomas D. Horne, FF EMT
 
Posts: n/a
Default Seeking Advice - New Main Breaker & Sub-Panel

BiloxiBoy wrote:
Thanks, Bob. That sounds like a great idea but I'm wondering if I can
buy a panel that has only a few spaces, and I guess I'd also have these
questions:

1. Since the entire house load calculates out to about 81 amps
(excluding central A/C), should I get a 100A main service panel, or
should I go higher? All the big appliances are gas - stove, dryer, and
central heat.
2. If I go higher, how high can I go before the service has to be
upgraded at the meter?
3. If I get a 100A panel, can I still run a sub panel to the shop (no
220) and still supply power to the central air?
4. What size main breaker would I need for the house panel, and does
it run off it's own breaker or will the main switch in the new main
panel suffice?

Sorry for all the questions, but it seems these are the kinds of things
that a lot of folks know a whole lot more about that I do...


I would suggest a larger service equipment panel. The difference in
price between 150 and 200 amp equipment is rather small so I'd go for
200 amps unless the existing service entry conductors will carry 150 but
are too small for 200. If the existing service entry conductors will
not carry 150 I suggest you make the jump to 200 as the difference in
cost is small. Having enough ampacity in the service for future
expansion of electrical use is a good thing. A hot tub, for instance,
would draw nearly 40 amperes.
--
Tom Horne

Well we aren't no thin blue heroes and yet we aren't no blackguards to.
We're just working men and woman most remarkable like you.
  #9   Report Post  
Posted to alt.home.repair
BiloxiBoy
 
Posts: n/a
Default Seeking Advice - New Main Breaker & Sub-Panel

Thanks, Tom... Your advice is certainly appreciated. The
single-breaker panel is going back to the store and will be replaced
with the new 200A QO model.

Many thanks again... All we gotta do now is hope another storm doesn't
grace our shores next season!! At least by then, I hope to be fully
repaired at every level - and this time with a new generator interlock
ready to go.

Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Generator transfer sub-panel: is this OK? Tman Home Repair 13 August 2nd 05 12:25 AM
Main breaker needed for subpanel???? blueman Home Repair 5 June 28th 05 09:48 AM
AC tripped at main breaker.....please advise HvacTech2 Home Repair 14 March 8th 05 01:27 AM
Help upgrading Service panel from 60A to 125A, please. DaveG Home Repair 33 December 3rd 03 03:57 AM
Drilling metal control panel advice... Alan Kamrowski II Metalworking 14 October 25th 03 05:08 AM


All times are GMT +1. The time now is 12:43 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"