Default Main breaker needed for subpanel????

We have the following series of breakers and subpanels

Mains - 200A Main breaker - 200A Subpanel with 200A breaker
-- 100A Subpanel with 100A breaker -- 30A Subpanel (but no 30A breaker)

The 30A Subpanel consists of 6 20A breakers that connect directly (via
the busses) to the 30A incoming line.

Now there is a 30A breaker on the 100A Subpanel but *no* 30A breaker
on the final 30A subpanel. The 30A subpanel is located across the
house from the other panels which are all located in the basement.

Is there any problem with not having (another) 30A breaker in the 30A
subpanel itself?

Thanks

  #2   Report Post  
RP
 
Posts: n/a
Default



blueman wrote:

We have the following series of breakers and subpanels

Mains - 200A Main breaker - 200A Subpanel with 200A breaker
-- 100A Subpanel with 100A breaker -- 30A Subpanel (but no 30A breaker)

The 30A Subpanel consists of 6 20A breakers that connect directly (via
the busses) to the 30A incoming line.

Now there is a 30A breaker on the 100A Subpanel but *no* 30A breaker
on the final 30A subpanel. The 30A subpanel is located across the
house from the other panels which are all located in the basement.

Is there any problem with not having (another) 30A breaker in the 30A
subpanel itself?

Thanks


No.

hvacrmedic


  #3   Report Post  
Olaf
 
Posts: n/a
Default


"blueman" wrote in message
...

Is there any problem with not having (another) 30A breaker in the 30A
subpanel itself?

Thanks


I believe the rule is no more than 6 circuit breakers and it doesn't need a
main breaker in the subpanel.

A 30 amp panel with 6 spaces?


  #4   Report Post  
blueman
 
Posts: n/a
Default

"Olaf" writes:

"blueman" wrote in message
...

Is there any problem with not having (another) 30A breaker in the 30A
subpanel itself?

Thanks


I believe the rule is no more than 6 circuit breakers and it doesn't need a
main breaker in the subpanel.

A 30 amp panel with 6 spaces?


Well, the panel has space for 8 20A breakers but only 6 are
filled. So, sounds like I satisfy the rule, right?
  #5   Report Post  
zxcvbob
 
Posts: n/a
Default

blueman wrote:
"Olaf" writes:


"blueman" wrote in message
...


Is there any problem with not having (another) 30A breaker in the 30A
subpanel itself?

Thanks


I believe the rule is no more than 6 circuit breakers and it doesn't need a
main breaker in the subpanel.

A 30 amp panel with 6 spaces?



Well, the panel has space for 8 20A breakers but only 6 are
filled. So, sounds like I satisfy the rule, right?



That's a "service panel" that has to have 6 or less switches (and a 2
pole breaker with the handles tied counts as only 1.) I don't think
there's any such requirement for a subpanel -- unless it is located in a
separate building (in which case it's treated like a service panel)

Bob


  #6   Report Post  
Bob Vaughan
 
Posts: n/a
Default

In article ,
zxcvbob wrote:
blueman wrote:
"Olaf" writes:


"blueman" wrote in message
...


Is there any problem with not having (another) 30A breaker in the 30A
subpanel itself?

Thanks


I believe the rule is no more than 6 circuit breakers and it doesn't need a
main breaker in the subpanel.

A 30 amp panel with 6 spaces?



Well, the panel has space for 8 20A breakers but only 6 are
filled. So, sounds like I satisfy the rule, right?



That's a "service panel" that has to have 6 or less switches (and a 2
pole breaker with the handles tied counts as only 1.) I don't think
there's any such requirement for a subpanel -- unless it is located in a
separate building (in which case it's treated like a service panel)

Bob



The "6 handle rule" basicly says that no more than 6 hand motions
shall be required to disconnect power to a building, or occupancy.

230-70(g)

The 6 handles may be fused disconnects or circuit breakers rated at 30 amps
or greater. Fire pump, and emergency lighting supplied as separate services
are excluded from the 6 handle count.

Subpanels must be protected by overcurrent protection not greater than the
rating of the subpanel.

384-16

Feeders must be protected by overcurrent protection not greater than the
capacity of the feeder.

215-4

If the overcurrent protection on the feeder is less than or equal to the
subpanel capacity, then no additional protection is required at the subpanel.

In the original example, the 200amp service disconnect would be sufficient
for the 200amp feeder supplying the 200amp subpanel, and no additional
breaker would be required at the 200amp subpanel.

The same would apply to the 100amp feeder to the 100amp subpanel, which would
be protected by the 100amp breaker in the 200amp subpanel.

If the 200 amp feeder supplied 100amp subpanel(s), then 100amp breakers would
be required to protect each subpanel.




--
-- Welcome My Son, Welcome To The Machine --
Bob Vaughan | techie @ tantivy.net |
| P.O. Box 19792, Stanford, Ca 94309 |
-- I am Me, I am only Me, And no one else is Me, What could be simpler? --
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Extra cables to the main breaker box Jag Man Home Repair 6 March 11th 05 05:30 PM
DIY Installing Whole House Transfer switch at Service Entrance Dave Morrison Home Repair 7 January 13th 05 10:34 PM
15A Circuit Breaker on a Power Tap Jajal Electronics 3 April 3rd 04 03:18 PM
boiler / central heating problem - main burner weak and cuts out SledgehammerSteve UK diy 8 March 16th 04 12:32 PM


All times are GMT +1. The time now is 09:42 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"