I have one bedroom in my house that has no power whatsoever. None of
the circuit breaker are tripped, and just to be sure, I flipped each
one to off and then back to on with no effect. I believe that most of
the circuits in the house are spread out among different lights and
outlets in different rooms, so I can't understand why only one room
would be out while everything else is working fine. The house was
built in 1972 and has had no other electrical problems. The problem
occured when the overhead light in the room was turned on. The light
went on, went off, on again, and then off completely. After that,
there was no power at all in the room. The room does not have a GFCI
in it. Does anyone have any ideas what may be wrong? Thanks for any
help you can give!

  #2   Report Post  
Posted to alt.home.repair
Jay Stootzmann
 
Posts: n/a
Default No power in one bedroom only

1972 is setting off all kinds of alarms in my head -- do you have aluminum
wiring in your house?

What you are describing is a classical case of aluminum wiring. My father's
house was built in 71-72 and about 2 months ago an entire circuit went
dead. Had to replace the entire AL circuit with copper wiring.



wrote in message
ups.com...
I have one bedroom in my house that has no power whatsoever. None of
the circuit breaker are tripped, and just to be sure, I flipped each
one to off and then back to on with no effect. I believe that most of
the circuits in the house are spread out among different lights and
outlets in different rooms, so I can't understand why only one room
would be out while everything else is working fine. The house was
built in 1972 and has had no other electrical problems. The problem
occured when the overhead light in the room was turned on. The light
went on, went off, on again, and then off completely. After that,
there was no power at all in the room. The room does not have a GFCI
in it. Does anyone have any ideas what may be wrong? Thanks for any
help you can give!



  #3   Report Post  
Posted to alt.home.repair
Kyle Boatright
 
Posts: n/a
Default No power in one bedroom only


wrote in message
ups.com...
I have one bedroom in my house that has no power whatsoever. None of
the circuit breaker are tripped, and just to be sure, I flipped each
one to off and then back to on with no effect. I believe that most of
the circuits in the house are spread out among different lights and
outlets in different rooms, so I can't understand why only one room
would be out while everything else is working fine. The house was
built in 1972 and has had no other electrical problems. The problem
occured when the overhead light in the room was turned on. The light
went on, went off, on again, and then off completely. After that,
there was no power at all in the room. The room does not have a GFCI
in it. Does anyone have any ideas what may be wrong? Thanks for any
help you can give!


Possibilities:

1) Bad connection at a breaker or in a junction box.

2) Everything in the bedroom may be wired in series, starting with one
outlet. If that outlet fails, everything else is dead too.

3) Check your GFCI's. People sometimes get lazy and pull power from
somewhere convenient instead of somewhere logical.

4) Get one of those $10 devices that senses "hot" wires and check to see if
anything in the bedroom has a hot wire. That may lead you to solve #2.

Good luck.

KB



  #4   Report Post  
Posted to alt.home.repair
Doug Kanter
 
Posts: n/a
Default No power in one bedroom only


wrote in message
ups.com...
I have one bedroom in my house that has no power whatsoever. None of
the circuit breaker are tripped, and just to be sure, I flipped each
one to off and then back to on with no effect. I believe that most of
the circuits in the house are spread out among different lights and
outlets in different rooms, so I can't understand why only one room
would be out while everything else is working fine. The house was
built in 1972 and has had no other electrical problems. The problem
occured when the overhead light in the room was turned on. The light
went on, went off, on again, and then off completely. After that,
there was no power at all in the room. The room does not have a GFCI
in it. Does anyone have any ideas what may be wrong? Thanks for any
help you can give!


Is it just the fixture that's out, or outlets in that room, too?


  #5   Report Post  
Posted to alt.home.repair
 
Posts: n/a
Default No power in one bedroom only

Thanks everyone for the advice so far. To answer your questions...I
don't believe that there is aluminum wiring in that room. The wire
appears to be copper at the light switch and in the circuit breaker
panel. We haven't opened up the outlets yet, but I think we are ok on
the wiring. Everything in the room is out...overhead light and all
outlets. There is no GFCI on that room circuit. There is only one
GFCI in the house (that I know of) which is located in the bathroom
which is on the other side of the house to where the problem is. Just
for the heck of it though, I did trip the GFCI and reset it. The GFCI
outlet is working fine, and reseting it didn't seem to make a
difference. I've started working on the idea that the room is wired in
series and that the light switch or an outlet died. I still find it
strange that the circuit breaker didn't trip, but it does seem like the
most reasonable explaination. I do have one of those hot wire testers
that I going to dig up and test the outlets with (should have done that
first, but figured the whole room was out and it wouldn't tell me
anything). Thanks again...please let me know if anyone thinks of
anything else. I'll reply as to how the search goes...



  #6   Report Post  
Posted to alt.home.repair
Jay Stootzmann
 
Posts: n/a
Default No power in one bedroom only

I use a multimeter -- very handy to have when trying to track down problems.
Ovbiously, you have an open in your circuit somewhere -- likely but not
necessiarly at one of the connectors. The reason this is usually a sign of
AL wiring is because over time the expansion of the AL wiring due to heating
will lossen even the tightest of connections. This "could" happen with CU
wiring or it could be a sign of a break in the wiring.

To check on the type of wiring you have you would need to check your breaker
panel. You may need an electrician if your not experienced in this. When I
checked my Dad's house I pulled the cover off the Breaker panel -- but I'm
an Electrical Engineer and a PE -- Unless you really know what you're doing
I would not recommend it.


wrote in message
ups.com...
Thanks everyone for the advice so far. To answer your questions...I
don't believe that there is aluminum wiring in that room. The wire
appears to be copper at the light switch and in the circuit breaker
panel. We haven't opened up the outlets yet, but I think we are ok on
the wiring. Everything in the room is out...overhead light and all
outlets. There is no GFCI on that room circuit. There is only one
GFCI in the house (that I know of) which is located in the bathroom
which is on the other side of the house to where the problem is. Just
for the heck of it though, I did trip the GFCI and reset it. The GFCI
outlet is working fine, and reseting it didn't seem to make a
difference. I've started working on the idea that the room is wired in
series and that the light switch or an outlet died. I still find it
strange that the circuit breaker didn't trip, but it does seem like the
most reasonable explaination. I do have one of those hot wire testers
that I going to dig up and test the outlets with (should have done that
first, but figured the whole room was out and it wouldn't tell me
anything). Thanks again...please let me know if anyone thinks of
anything else. I'll reply as to how the search goes...



  #7   Report Post  
Posted to alt.home.repair
 
Posts: n/a
Default No power in one bedroom only

I do have a multimeter, and we have been using that as well. So far,
we are not seeing any power anywhere in the room. We did take the
cover off of the breaker panel just to check the type of wiring, but we
aren't poking around in there. I have some basic electrical experience
(old though), and my son is currently taking courses in the electrical
field. So we have some experience, but aren't about to try something
that may be out of our league. We know just enough to be dangerous...
(just kidding of course...we are taking all due precautions).

  #9   Report Post  
Posted to alt.home.repair
 
Posts: n/a
Default No power in one bedroom only

Well, we've checked all of the outlets (wiring to the outlets) and the
light switch, and we have no power in any of the wires. I looked for
junction boxes in the basement and found none, which leads me to
believe that they are located in the attic. The last thing I can think
of to check is to remove the overhead light fixure and see if there is
any power there (I'm hoping that may also be the junction box for the
room). If that doesn't work, I'm thinking it's time to call an
electrician. Any other ideas out there?

  #10   Report Post  
Posted to alt.home.repair
Doug Kanter
 
Posts: n/a
Default No power in one bedroom only


wrote in message
ups.com...
Well, we've checked all of the outlets (wiring to the outlets) and the
light switch, and we have no power in any of the wires. I looked for
junction boxes in the basement and found none, which leads me to
believe that they are located in the attic. The last thing I can think
of to check is to remove the overhead light fixure and see if there is
any power there (I'm hoping that may also be the junction box for the
room). If that doesn't work, I'm thinking it's time to call an
electrician. Any other ideas out there?


I'd say you're on the right track, checking inside the light fixture's box.
You don't have to remove it completely - just have a 2nd person there to
support the fixture while you undo the wire nuts momentarily. However, once
you've checked for power there, and no matter what you find, turn off the
breaker before reinstalling the wire nut(s). Sometimes it's easy to remove
wire nuts with your fingertips, and not touch anything else, but putting
them back on often means getting more fingers into the box.




  #11   Report Post  
Posted to alt.home.repair
 
Posts: n/a
Default No power in one bedroom only

That is one of the things I've been trying to determine...I don't have
a wiring map for the house, and since none of the breakers tripped, I
don't know which breaker controls that room. I've be working very
carefully since wherever the problem is, it's going to be hot on one
side of it. I'm really considering running out to Home Depot and
picking up a two-part circuit tester to try and figure out which
breaker goes to which outlet. Then by a process of elimination, I can
turn off the breakers that may be going to that room.

  #12   Report Post  
Posted to alt.home.repair
SQLit
 
Posts: n/a
Default No power in one bedroom only


wrote in message
ups.com...
I have one bedroom in my house that has no power whatsoever. None of
the circuit breaker are tripped, and just to be sure, I flipped each
one to off and then back to on with no effect. I believe that most of
the circuits in the house are spread out among different lights and
outlets in different rooms, so I can't understand why only one room
would be out while everything else is working fine. The house was
built in 1972 and has had no other electrical problems. The problem
occured when the overhead light in the room was turned on. The light
went on, went off, on again, and then off completely. After that,
there was no power at all in the room. The room does not have a GFCI
in it. Does anyone have any ideas what may be wrong? Thanks for any
help you can give!


Time to investigate, I will bet on the last thing that worked,,,, i.e. the
light. Loose connections or shoddy workmanship would be good guesses.
Be careful out there


  #13   Report Post  
Posted to alt.home.repair
Joey
 
Posts: n/a
Default No power in one bedroom only

wrote:
That is one of the things I've been trying to determine...I don't have
a wiring map for the house, and since none of the breakers tripped, I
don't know which breaker controls that room. I've be working very
carefully since wherever the problem is, it's going to be hot on one
side of it. I'm really considering running out to Home Depot and
picking up a two-part circuit tester to try and figure out which
breaker goes to which outlet. Then by a process of elimination, I can
turn off the breakers that may be going to that room.


Home Depot/Lowes sells a device that senses power (AC) on the black
(hot) lead without having to physically touch the bare wire or unwrape
tape or wingnuts. Check each outlet/light box in that room and rooms
next to that room with this device. If you find the overhead fixture
has some A/C detected there, turn off your main breaker and remove each
wingnut or tape and physically check and redo the wiring there. I've
seen copper wire just break for no reason and the flicker you mentioned
makes me think this is what happened. I've also seen screws on a switch
break off leaving a continuing wire disconnected, so it can happen. The
tool I mentioned is very inexpensive and works well. Make sure you test
it first on a live circuit so you'll get used to how it works before
moving into the suspect room. I've also seen breakers (mainly old ones)
quit working. That is where the volt meter will come in handy to check
at the breaker box. If you get ANY voltage less than 115V on a standard
breaker then replace that breaker. My last job consisted of an oven
that quit working but the light worked fine. Half of that breaker
passed 115V for the light but I got about 85V on the other half which
was for the heater elements. Replacing that breaker solved the problem
but the owner of the oven was about to buy another one thinking the
thermostat and elements had went bad. Good luck.

J
  #14   Report Post  
Posted to alt.home.repair
RBM
 
Posts: n/a
Default No power in one bedroom only

You have an open circuit. Either the hot wire or neutral wire came loose
somewhere in the circuit. Since it only affects one room, its not likely a
circuit breaker problem as there is likely more things on that circuit then
just that room. I would look for a loose connection in an outlet. In the
string of daisy chained outlets, lights and switches, the problem is likely
to be in the last "live" outlet, or the first dead outlet. It sounds like
you've checked all the dead locations, now check "live" outlets in adjacent
walls of other rooms. Sometimes you can bang on the wall next to the
affected outlet and cause the circuit to flicker back on




wrote in message
ups.com...
I have one bedroom in my house that has no power whatsoever. None of
the circuit breaker are tripped, and just to be sure, I flipped each
one to off and then back to on with no effect. I believe that most of
the circuits in the house are spread out among different lights and
outlets in different rooms, so I can't understand why only one room
would be out while everything else is working fine. The house was
built in 1972 and has had no other electrical problems. The problem
occured when the overhead light in the room was turned on. The light
went on, went off, on again, and then off completely. After that,
there was no power at all in the room. The room does not have a GFCI
in it. Does anyone have any ideas what may be wrong? Thanks for any
help you can give!



  #15   Report Post  
Posted to alt.home.repair
 
Posts: n/a
Default No power in one bedroom only

For a start just pull all the breakers.

Then if you find and fix a problem you can turn on lights and attach
something to the power outlets and pull one breaker at a time to
document them.

According to my copy of the electrical code you are not supposed to use
the power outlet to connect a series of outlets. It is supposed to be
pigtailed with nuts.

While you are testing things check that the wires at the light are cold
with the switch off. I have seen some house wiring where the neutral
wire was switched.



  #16   Report Post  
Posted to alt.home.repair
Sev
 
Posts: n/a
Default No power in one bedroom only

I would get up in the attic and see if you can trace the wiring- the
problem may be up there or in outlet in nearby room on the same
circuit. I had similar problem last year, solved for me I must
sheepishly admit not by me but by my brother, who is a pro. My garage
outlet was dead- the loose wire was in outlet box of nearby bathroom.

  #17   Report Post  
Posted to alt.home.repair
Tony Hwang
 
Posts: n/a
Default No power in one bedroom only

Sev wrote:
I would get up in the attic and see if you can trace the wiring- the
problem may be up there or in outlet in nearby room on the same
circuit. I had similar problem last year, solved for me I must
sheepishly admit not by me but by my brother, who is a pro. My garage
outlet was dead- the loose wire was in outlet box of nearby bathroom.

Hi,
Quick way of sniffing live wire is to use a magnetic compass.
Near the live wire compass needle goes crazy. Have to figure out which
is the entry point of the wiring in that bedroom and start from there
backward towards breaker controlling the power in the bedroom.
Tony
  #18   Report Post  
Posted to alt.home.repair
 
Posts: n/a
Default No power in one bedroom only

Thanks again all. I did go out and buy a two-part circuit tracker and
am now in the process of mapping all of the circuits in the house.
Once I'm done doing that, I can turn off the ones that I think might be
going to the affected room, and pull down the overhead light. I'm
really thinking that I'm going to find the problem there...loose wire
or something to that effect. If not, then it's definitately time for a
pro (at least I'll have the house mapped!). Since it's starting to get
late today, and back to work tomorrow, I probably won't get much more
done until next weekend (luckily the problem is in a room that isn't
being used right now!). So, I'll post what I find next weekend. I
really appreciate all the help and words of advice...it helped point me
in the right direction. Hope everyone has a Happy New Year!

  #20   Report Post  
Posted to alt.home.repair
Doug Kanter
 
Posts: n/a
Default No power in one bedroom only


wrote in message
oups.com...
Thanks again all. I did go out and buy a two-part circuit tracker and
am now in the process of mapping all of the circuits in the house.
Once I'm done doing that, I can turn off the ones that I think might be
going to the affected room, and pull down the overhead light. I'm
really thinking that I'm going to find the problem there...loose wire
or something to that effect. If not, then it's definitately time for a
pro (at least I'll have the house mapped!). Since it's starting to get
late today, and back to work tomorrow, I probably won't get much more
done until next weekend (luckily the problem is in a room that isn't
being used right now!). So, I'll post what I find next weekend. I
really appreciate all the help and words of advice...it helped point me
in the right direction. Hope everyone has a Happy New Year!


By the way, in case this hasn't occurred to you by now, wire nuts are one of
the worst methods ever invented for putting two wires together. If that's
where you eventually find the problem, and there's enough wire to work with
(in terms of length), consider using crimp connectors. They are legal/within
code in some municipalities, and who cares, anyway? Since it's nearly
impossible to separate a *PROPERLY DONE* crimp connection, anyplace which
prohibits it in the code is a backward town run by knuckle-dragging
neanderthals and you should ignore the code.

If it sounds interesting, pick up some crimps and a good tool at HD, Lowes,
whatever, along with some wire that matches the gauge you'll be working
with, and practice with that wire. The key is to make sure that *all* bare
wire is completely within the metal sleeve, with none showing through the
transparent plastic ends.

Crimps are NOT appropriate in places where the previous wizard has cut wires
too short. To remove crimps, you have to cut the wires, so each time it
happens, they get shorter and shorter. If you're sure that one or two cuts
will still leave enough to work with, then use crimps.




  #21   Report Post  
Posted to alt.home.repair
M Q
 
Posts: n/a
Default No power in one bedroom only

Tony Hwang wrote:
....

Hi,
Quick way of sniffing live wire is to use a magnetic compass.
Near the live wire compass needle goes crazy. Have to figure out which
is the entry point of the wiring in that bedroom and start from there
backward towards breaker controlling the power in the bedroom.
Tony


No. Only if there is current flowing, which in this case it is not.
Use one of those non-contact electrical testers mentioned in
"Joey"'s message. In the attic you can also determine if a wire is
"hot" without having to open up a box.

  #22   Report Post  
Posted to alt.home.repair
Joey
 
Posts: n/a
Default No power in one bedroom only

Wing nuts are just as good as the crimp method, the secret is getting
the insulation off the wires. A wire stripper that pulls the insulation
off in one clip without nicking the wire is the best. If the bare wire
is nicked then crimping or wing nutting might very well break the wire.
The absolute best method is not used very often and that would be to
remove the insulation without nicking the wire and then soldering the
connection and then insulating it. I must admit I 've never seen one of
these break apart !

J


Doug Kanter wrote:
wrote in message
oups.com...

Thanks again all. I did go out and buy a two-part circuit tracker and
am now in the process of mapping all of the circuits in the house.
Once I'm done doing that, I can turn off the ones that I think might be
going to the affected room, and pull down the overhead light. I'm
really thinking that I'm going to find the problem there...loose wire
or something to that effect. If not, then it's definitately time for a
pro (at least I'll have the house mapped!). Since it's starting to get
late today, and back to work tomorrow, I probably won't get much more
done until next weekend (luckily the problem is in a room that isn't
being used right now!). So, I'll post what I find next weekend. I
really appreciate all the help and words of advice...it helped point me
in the right direction. Hope everyone has a Happy New Year!



By the way, in case this hasn't occurred to you by now, wire nuts are one of
the worst methods ever invented for putting two wires together. If that's
where you eventually find the problem, and there's enough wire to work with
(in terms of length), consider using crimp connectors. They are legal/within
code in some municipalities, and who cares, anyway? Since it's nearly
impossible to separate a *PROPERLY DONE* crimp connection, anyplace which
prohibits it in the code is a backward town run by knuckle-dragging
neanderthals and you should ignore the code.

If it sounds interesting, pick up some crimps and a good tool at HD, Lowes,
whatever, along with some wire that matches the gauge you'll be working
with, and practice with that wire. The key is to make sure that *all* bare
wire is completely within the metal sleeve, with none showing through the
transparent plastic ends.

Crimps are NOT appropriate in places where the previous wizard has cut wires
too short. To remove crimps, you have to cut the wires, so each time it
happens, they get shorter and shorter. If you're sure that one or two cuts
will still leave enough to work with, then use crimps.


  #23   Report Post  
Posted to alt.home.repair
HarryS
 
Posts: n/a
Default No power in one bedroom only

I agree with RBM. I had this happen once and was at a loss as to where the
problem was. The breakers were all OK but a hallway running past several
bedrooms had lost power, outlets as well as light fixtures. After a bit of
thought, I decided that there had to be a break in a string of lights and
receptacles. I started removing the closest receptacles that had power and
sure enough I found one of the chained receptacles where the hot wire had
obviously gotten hot and discolored the insulation. The person who had
wired the receptacle had elected to use the "push in" connections on the
back of the receptacle, rather than using a loop under the screws. The
connection with the push in had probably not been a good connection in the
first place and, when under power, exhibited enough resistance that it
created heat and eventually burned the connections inside the receptacle off
to the point that the rest of the circuit downstream lost power.

I've never been fond of the "push in" connections because when you push a
wire in you can tell that it's often not really tight and the wire can be
twisted around with ease inside the receptacle. This same thing can happen
with a wire under a screw, but it's not likely if the loop is formed
correctly and the screw tightened sufficiently.

Unless this one receptacle had been replaced, it's probable that most of the
rest of the house is wired in the same manner.



"RBM" rbm2(remove wrote in message
...
You have an open circuit. Either the hot wire or neutral wire came loose
somewhere in the circuit. Since it only affects one room, its not likely a
circuit breaker problem as there is likely more things on that circuit
then just that room. I would look for a loose connection in an outlet. In
the string of daisy chained outlets, lights and switches, the problem is
likely to be in the last "live" outlet, or the first dead outlet. It
sounds like you've checked all the dead locations, now check "live"
outlets in adjacent walls of other rooms. Sometimes you can bang on the
wall next to the affected outlet and cause the circuit to flicker back on




wrote in message
ups.com...
I have one bedroom in my house that has no power whatsoever. None of
the circuit breaker are tripped, and just to be sure, I flipped each
one to off and then back to on with no effect. I believe that most of
the circuits in the house are spread out among different lights and
outlets in different rooms, so I can't understand why only one room
would be out while everything else is working fine. The house was
built in 1972 and has had no other electrical problems. The problem
occured when the overhead light in the room was turned on. The light
went on, went off, on again, and then off completely. After that,
there was no power at all in the room. The room does not have a GFCI
in it. Does anyone have any ideas what may be wrong? Thanks for any
help you can give!





  #24   Report Post  
Posted to alt.home.repair
Mark Lloyd
 
Posts: n/a
Default No power in one bedroom only

On Mon, 26 Dec 2005 14:13:31 -0500, Joey
wrote:

wrote:
That is one of the things I've been trying to determine...I don't have
a wiring map for the house, and since none of the breakers tripped, I
don't know which breaker controls that room. I've be working very
carefully since wherever the problem is, it's going to be hot on one
side of it. I'm really considering running out to Home Depot and
picking up a two-part circuit tester to try and figure out which
breaker goes to which outlet. Then by a process of elimination, I can
turn off the breakers that may be going to that room.


Home Depot/Lowes sells a device that senses power (AC) on the black
(hot) lead without having to physically touch the bare wire or unwrape
tape or wingnuts.


This tester should be the same as the ones should to check Christmas
lights.

Check each outlet/light box in that room and rooms
next to that room with this device. If you find the overhead fixture
has some A/C detected there, turn off your main breaker and remove each
wingnut or tape and physically check and redo the wiring there. I've
seen copper wire just break for no reason and the flicker you mentioned
makes me think this is what happened. I've also seen screws on a switch
break off leaving a continuing wire disconnected, so it can happen. The
tool I mentioned is very inexpensive and works well. Make sure you test
it first on a live circuit so you'll get used to how it works before
moving into the suspect room. I've also seen breakers (mainly old ones)
quit working. That is where the volt meter will come in handy to check
at the breaker box. If you get ANY voltage less than 115V on a standard
breaker then replace that breaker. My last job consisted of an oven
that quit working but the light worked fine. Half of that breaker
passed 115V for the light but I got about 85V on the other half which
was for the heater elements. Replacing that breaker solved the problem
but the owner of the oven was about to buy another one thinking the
thermostat and elements had went bad. Good luck.

J

--
Mark Lloyd
http://notstupid.laughingsquid.com

"Democracy is two wolves and a lamb voting on what
to have for lunch. Liberty is a well armed lamb
contesting the vote." - Benjamin Franklin
  #25   Report Post  
Posted to alt.home.repair
Doug Kanter
 
Posts: n/a
Default No power in one bedroom only

If wire nuts were as good as crimps, they'd be used in cars, boats and the
space station.

"Joey" wrote in message
...
Wing nuts are just as good as the crimp method, the secret is getting the
insulation off the wires. A wire stripper that pulls the insulation off
in one clip without nicking the wire is the best. If the bare wire is
nicked then crimping or wing nutting might very well break the wire. The
absolute best method is not used very often and that would be to remove
the insulation without nicking the wire and then soldering the connection
and then insulating it. I must admit I 've never seen one of these break
apart !

J


Doug Kanter wrote:
wrote in message
oups.com...

Thanks again all. I did go out and buy a two-part circuit tracker and
am now in the process of mapping all of the circuits in the house.
Once I'm done doing that, I can turn off the ones that I think might be
going to the affected room, and pull down the overhead light. I'm
really thinking that I'm going to find the problem there...loose wire
or something to that effect. If not, then it's definitately time for a
pro (at least I'll have the house mapped!). Since it's starting to get
late today, and back to work tomorrow, I probably won't get much more
done until next weekend (luckily the problem is in a room that isn't
being used right now!). So, I'll post what I find next weekend. I
really appreciate all the help and words of advice...it helped point me
in the right direction. Hope everyone has a Happy New Year!



By the way, in case this hasn't occurred to you by now, wire nuts are one
of the worst methods ever invented for putting two wires together. If
that's where you eventually find the problem, and there's enough wire to
work with (in terms of length), consider using crimp connectors. They are
legal/within code in some municipalities, and who cares, anyway? Since
it's nearly impossible to separate a *PROPERLY DONE* crimp connection,
anyplace which prohibits it in the code is a backward town run by
knuckle-dragging neanderthals and you should ignore the code.

If it sounds interesting, pick up some crimps and a good tool at HD,
Lowes, whatever, along with some wire that matches the gauge you'll be
working with, and practice with that wire. The key is to make sure that
*all* bare wire is completely within the metal sleeve, with none showing
through the transparent plastic ends.

Crimps are NOT appropriate in places where the previous wizard has cut
wires too short. To remove crimps, you have to cut the wires, so each
time it happens, they get shorter and shorter. If you're sure that one or
two cuts will still leave enough to work with, then use crimps.





  #26   Report Post  
Posted to alt.home.repair
Jay Stootzmann
 
Posts: n/a
Default No power in one bedroom only


"Joey" wrote in message
...
Wing nuts are just as good as the crimp method, the secret is getting the
insulation off the wires. A wire stripper that pulls the insulation off
in one clip without nicking the wire is the best. If the bare wire is
nicked then crimping or wing nutting might very well break the wire. The
absolute best method is not used very often and that would be to remove
the insulation without nicking the wire and then soldering the connection
and then insulating it. I must admit I 've never seen one of these break
apart !


This is NOT code and would come apart if the wire was heated via load.

J


Doug Kanter wrote:
wrote in message
oups.com...

Thanks again all. I did go out and buy a two-part circuit tracker and
am now in the process of mapping all of the circuits in the house.
Once I'm done doing that, I can turn off the ones that I think might be
going to the affected room, and pull down the overhead light. I'm
really thinking that I'm going to find the problem there...loose wire
or something to that effect. If not, then it's definitately time for a
pro (at least I'll have the house mapped!). Since it's starting to get
late today, and back to work tomorrow, I probably won't get much more
done until next weekend (luckily the problem is in a room that isn't
being used right now!). So, I'll post what I find next weekend. I
really appreciate all the help and words of advice...it helped point me
in the right direction. Hope everyone has a Happy New Year!



By the way, in case this hasn't occurred to you by now, wire nuts are one
of the worst methods ever invented for putting two wires together. If
that's where you eventually find the problem, and there's enough wire to
work with (in terms of length), consider using crimp connectors. They are
legal/within code in some municipalities, and who cares, anyway? Since
it's nearly impossible to separate a *PROPERLY DONE* crimp connection,
anyplace which prohibits it in the code is a backward town run by
knuckle-dragging neanderthals and you should ignore the code.

If it sounds interesting, pick up some crimps and a good tool at HD,
Lowes, whatever, along with some wire that matches the gauge you'll be
working with, and practice with that wire. The key is to make sure that
*all* bare wire is completely within the metal sleeve, with none showing
through the transparent plastic ends.

Crimps are NOT appropriate in places where the previous wizard has cut
wires too short. To remove crimps, you have to cut the wires, so each
time it happens, they get shorter and shorter. If you're sure that one or
two cuts will still leave enough to work with, then use crimps.



  #27   Report Post  
Posted to alt.home.repair
Doug Kanter
 
Posts: n/a
Default No power in one bedroom only


"Jay Stootzmann" wrote in message
news:z2fsf.437501$084.417553@attbi_s22...

"Joey" wrote in message
...
Wing nuts are just as good as the crimp method, the secret is getting the
insulation off the wires. A wire stripper that pulls the insulation off
in one clip without nicking the wire is the best. If the bare wire is
nicked then crimping or wing nutting might very well break the wire. The
absolute best method is not used very often and that would be to remove
the insulation without nicking the wire and then soldering the connection
and then insulating it. I must admit I 've never seen one of these break
apart !


This is NOT code and would come apart if the wire was heated via load.


Soldered wires sometimes have sharp edges that will punch right through heat
shrink tubing. That leads some slobs to resort to trying to add further
protection using electrical tape, another abomination.


  #28   Report Post  
Posted to alt.home.repair
Joey
 
Posts: n/a
Default No power in one bedroom only

OK Doug, you win, I've never seen wing nuts used on these either. I
frequently do wiring on airplane avionics and very used to running wire
with no splices and crimp ring terminals. Still it sometimes happens
that a wire will break somewhere. I know we don't use them in house
wiring but stranded wiring works best in cars, planes, etc. My mention
of soldering was mainly directed at stranded wiring...so house wiring,
crimp it shall be !!!

J



Doug Kanter wrote:
If wire nuts were as good as crimps, they'd be used in cars, boats and the
space station.

"Joey" wrote in message
...

Wing nuts are just as good as the crimp method, the secret is getting the
insulation off the wires. A wire stripper that pulls the insulation off
in one clip without nicking the wire is the best. If the bare wire is
nicked then crimping or wing nutting might very well break the wire. The
absolute best method is not used very often and that would be to remove
the insulation without nicking the wire and then soldering the connection
and then insulating it. I must admit I 've never seen one of these break
apart !

J


Doug Kanter wrote:

wrote in message
egroups.com...


Thanks again all. I did go out and buy a two-part circuit tracker and
am now in the process of mapping all of the circuits in the house.
Once I'm done doing that, I can turn off the ones that I think might be
going to the affected room, and pull down the overhead light. I'm
really thinking that I'm going to find the problem there...loose wire
or something to that effect. If not, then it's definitately time for a
pro (at least I'll have the house mapped!). Since it's starting to get
late today, and back to work tomorrow, I probably won't get much more
done until next weekend (luckily the problem is in a room that isn't
being used right now!). So, I'll post what I find next weekend. I
really appreciate all the help and words of advice...it helped point me
in the right direction. Hope everyone has a Happy New Year!



By the way, in case this hasn't occurred to you by now, wire nuts are one
of the worst methods ever invented for putting two wires together. If
that's where you eventually find the problem, and there's enough wire to
work with (in terms of length), consider using crimp connectors. They are
legal/within code in some municipalities, and who cares, anyway? Since
it's nearly impossible to separate a *PROPERLY DONE* crimp connection,
anyplace which prohibits it in the code is a backward town run by
knuckle-dragging neanderthals and you should ignore the code.

If it sounds interesting, pick up some crimps and a good tool at HD,
Lowes, whatever, along with some wire that matches the gauge you'll be
working with, and practice with that wire. The key is to make sure that
*all* bare wire is completely within the metal sleeve, with none showing
through the transparent plastic ends.

Crimps are NOT appropriate in places where the previous wizard has cut
wires too short. To remove crimps, you have to cut the wires, so each
time it happens, they get shorter and shorter. If you're sure that one or
two cuts will still leave enough to work with, then use crimps.




  #29   Report Post  
Posted to alt.home.repair
g.a.miller
 
Posts: n/a
Default No power in one bedroom only

On 26 Dec 2005 08:56:53 -0800, wrote:

I have one bedroom in my house that has no power whatsoever. None of
the circuit breaker are tripped, and just to be sure, I flipped each
one to off and then back to on with no effect. I believe that most of
the circuits in the house are spread out among different lights and
outlets in different rooms, so I can't understand why only one room
would be out while everything else is working fine. The house was
built in 1972 and has had no other electrical problems. The problem
occured when the overhead light in the room was turned on. The light
went on, went off, on again, and then off completely. After that,
there was no power at all in the room. The room does not have a GFCI
in it. Does anyone have any ideas what may be wrong? Thanks for any
help you can give!



More than likely the the hot wire is loose in the circut breaker .
Check that first. If not the case remove the circut breaker and take
it with you to home depot or your local electical supplier to get
replacement. This should solve your problem. I fnot then call a well
qualified electician. It may cost more now, but in the long run you
will be more satisfied. Hope this helped!
Anthony




.................................................. ...............
Posted via TITANnews - Uncensored Newsgroups Access
at
http://www.TitanNews.com
-=Every Newsgroup - Anonymous, UNCENSORED, BROADBAND Downloads=-

  #30   Report Post  
Posted to alt.home.repair
RBM
 
Posts: n/a
Default No power in one bedroom only

It would be rare for any house built in '72 to have a bedroom on a dedicated
circuit, so a loose wire at the breaker would not be likely
Before replacing a circuit breaker, a simple volt meter or pig tail light
can determine if it is working or not



"g.a.miller" wrote in message
...
On 26 Dec 2005 08:56:53 -0800, wrote:

I have one bedroom in my house that has no power whatsoever. None of
the circuit breaker are tripped, and just to be sure, I flipped each
one to off and then back to on with no effect. I believe that most of
the circuits in the house are spread out among different lights and
outlets in different rooms, so I can't understand why only one room
would be out while everything else is working fine. The house was
built in 1972 and has had no other electrical problems. The problem
occured when the overhead light in the room was turned on. The light
went on, went off, on again, and then off completely. After that,
there was no power at all in the room. The room does not have a GFCI
in it. Does anyone have any ideas what may be wrong? Thanks for any
help you can give!



More than likely the the hot wire is loose in the circut breaker .
Check that first. If not the case remove the circut breaker and take
it with you to home depot or your local electical supplier to get
replacement. This should solve your problem. I fnot then call a well
qualified electician. It may cost more now, but in the long run you
will be more satisfied. Hope this helped!
Anthony




.................................................. ..............
Posted via TITANnews - Uncensored Newsgroups Access
at
http://www.TitanNews.com
-=Every Newsgroup - Anonymous, UNCENSORED, BROADBAND Downloads=-





  #31   Report Post  
Posted to alt.home.repair
Levon
 
Posts: n/a
Default No power in one bedroom only


wrote:
I have one bedroom in my house that has no power whatsoever.



hmm, wonder what that could be

  #32   Report Post  
Posted to alt.home.repair
Handi
 
Posts: n/a
Default No power in one bedroom only

Are the light fixtures & all the wall sockets dead?

I'd suspect a broken connection in a junction box somewhere in the
house. See if you can physically trace the wiring back to the circuit
breaker panel.

Hopefully the suspect junction box isn't behind a finished wall or
ceiling.

Handi


  #33   Report Post  
Posted to alt.home.repair
Mark Lloyd
 
Posts: n/a
Default No power in one bedroom only

On Sun, 15 Jan 2006 08:14:49 -0500, "RBM" rbm2(remove
wrote:

It would be rare for any house built in '72 to have a bedroom on a dedicated
circuit, so a loose wire at the breaker would not be likely
Before replacing a circuit breaker, a simple volt meter or pig tail light
can determine if it is working or not



This is also a case where you would benefit from having determined
what was on what circuit, before the failure.


"g.a.miller" wrote in message
.. .
On 26 Dec 2005 08:56:53 -0800, wrote:

I have one bedroom in my house that has no power whatsoever. None of
the circuit breaker are tripped, and just to be sure, I flipped each
one to off and then back to on with no effect. I believe that most of
the circuits in the house are spread out among different lights and
outlets in different rooms, so I can't understand why only one room
would be out while everything else is working fine. The house was
built in 1972 and has had no other electrical problems. The problem
occured when the overhead light in the room was turned on. The light
went on, went off, on again, and then off completely. After that,
there was no power at all in the room. The room does not have a GFCI
in it. Does anyone have any ideas what may be wrong? Thanks for any
help you can give!



More than likely the the hot wire is loose in the circut breaker .
Check that first. If not the case remove the circut breaker and take
it with you to home depot or your local electical supplier to get
replacement. This should solve your problem. I fnot then call a well
qualified electician. It may cost more now, but in the long run you
will be more satisfied. Hope this helped!
Anthony




.................................................. ..............
Posted via TITANnews - Uncensored Newsgroups Access
at
http://www.TitanNews.com
-=Every Newsgroup - Anonymous, UNCENSORED, BROADBAND Downloads=-


--
Mark Lloyd
http://notstupid.laughingsquid.com

"Democracy is two wolves and a lamb voting on what
to have for lunch. Liberty is a well armed lamb
contesting the vote." - Benjamin Franklin
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
PC power related questions [email protected] Electronics Repair 1 May 20th 05 11:28 PM
Power surges Cheryl Home Repair 54 June 25th 04 08:50 PM
POWER SAVING UNIT ? mowhoong Electronics Repair 7 May 7th 04 06:10 AM
need help tracing power circuit on laptop railroadrum Electronics Repair 7 April 16th 04 09:02 PM
Generator FAQ Gunner Metalworking 0 January 23rd 04 05:24 PM


All times are GMT +1. The time now is 01:06 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"