Home Repair (alt.home.repair) For all homeowners and DIYers with many experienced tradesmen. Solve your toughest home fix-it problems.

Reply
 
LinkBack Thread Tools Search this Thread Display Modes
  #1   Report Post  
Percival P. Cassidy
 
Posts: n/a
Default Wire and conduit size

I want to run 4 x 10-gauge conductors (Neutral, Ground, 2 Hots) from a
generator inlet box at the back of the house to a transfer panel in the
basement -- approx. 25 ft.

They will run parallel to the joists most of the way. Should I use
individual THHN conductors in conduit (metal? PVC? I understand that
3/4" is an appropriate size), or can I use 10-3WG NM-B stapled to the
sides of a joist?

Perce
  #2   Report Post  
toller
 
Posts: n/a
Default

I just did the same thing and used 10/3, so it better be okay!
It cannot run on the bottom of the joists, but on the side is fine.


  #3   Report Post  
HorneTD
 
Posts: n/a
Default

Percival P. Cassidy wrote:
I want to run 4 x 10-gauge conductors (Neutral, Ground, 2 Hots) from a
generator inlet box at the back of the house to a transfer panel in the
basement -- approx. 25 ft.

They will run parallel to the joists most of the way. Should I use
individual THHN conductors in conduit (metal? PVC? I understand that
3/4" is an appropriate size), or can I use 10-3WG NM-B stapled to the
sides of a joist?

Perce



Either approach is perfectly acceptable so use whichever one suits you.
--
Tom H
  #4   Report Post  
Percival P. Cassidy
 
Posts: n/a
Default

On 05/07/05 05:02 pm HorneTD tossed the following ingredients into the
ever-growing pot of cybersoup:

I want to run 4 x 10-gauge conductors (Neutral, Ground, 2 Hots) from a
generator inlet box at the back of the house to a transfer panel in
the basement -- approx. 25 ft.

They will run parallel to the joists most of the way. Should I use
individual THHN conductors in conduit (metal? PVC? I understand that
3/4" is an appropriate size), or can I use 10-3WG NM-B stapled to the
sides of a joist?


Either approach is perfectly acceptable so use whichever one suits you.


OK. Thanks. Now I just thought of another question: if I use NM-B and
feed it down through the back of the inlet box and a hole in the siding,
how can I staple it within 8in. of the box? (Am I remembering the Code
correctly?) I won't be able to get at it to staple it until it emerges
from between the siding and the sheetrock into the space above the
suspended ceiling.

So does this mean I *must* use separate conductors in conduit instead?

Perce
  #5   Report Post  
Calvin Henry-Cotnam
 
Posts: n/a
Default

Percival P. Cassidy ) said...

OK. Thanks. Now I just thought of another question: if I use NM-B and
feed it down through the back of the inlet box and a hole in the siding,
how can I staple it within 8in. of the box? (Am I remembering the Code
correctly?)


There should be an exception to the stapling rule for fished cable. I don't
know what part of the NEC says so, but in the CEC the rule for non-metalic
sheathed cable is 12-510(3):

Notwithstanding Subrules (1) and (2), where the cable is run as
concealed wiring such that it is impracticable to support it, the
cable shall be permitted to be fished and need not be supported
between boxes and fittings.

Subrule (1) describes the need to support the cable within 300 mm (12")
of a box or fitting and every 1.5 m (60") thereafter, and subrule (2)
states that cable run through holes in joists or studs are considered
to be supported.

--
Calvin Henry-Cotnam
"Never ascribe to malice what can equally be explained by incompetence."
- Napoleon
-------------------------------------------------------------------------
NOTE: if replying by email, remove "remove." and ".invalid"



Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Grounding, Ground loops Wayne Metalworking 14 March 24th 05 03:57 PM
Underground wiring questions... guest987 Home Repair 52 February 2nd 05 01:52 AM
? NEC and ridgid metal conduit wahzoo Home Repair 3 March 22nd 04 05:30 AM
Breaker and wire size? Tony Woodworking 15 March 5th 04 01:20 AM
automotive wire size calculator CampinGazz Electronics 1 January 5th 04 07:02 PM


All times are GMT +1. The time now is 01:27 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"