  #1   Report Post  
Elmar
 
Posts: n/a
Default No Ground in Circuit panel.

While wiring my shop, I noticed something very disturbing. My house
is not grounded. I open my main panel and there are the two hots and
one neutral.

Ground bus and neutral bus are connected and both ground and neutral
wires share the same bus.

My house is newer, only about 8 years old.

Why is there no ground? I know when I did the same work in FL I was
required to put in two ground rods.

Is this a concern or normal?
  #2   Report Post  
Dave
 
Posts: n/a
Default

Is the ground bus then hooked up to some kind of ground wire? What
happens if you insert one of those plug testers into a wall socket -- do you
get a green light indicating adequate ground?

Dave

"Elmar" wrote in message
om...
While wiring my shop, I noticed something very disturbing. My house
is not grounded. I open my main panel and there are the two hots and
one neutral.

Ground bus and neutral bus are connected and both ground and neutral
wires share the same bus.

My house is newer, only about 8 years old.

Why is there no ground? I know when I did the same work in FL I was
required to put in two ground rods.

Is this a concern or normal?



  #3   Report Post  
toller
 
Posts: n/a
Default


"Elmar" wrote in message
om...
While wiring my shop, I noticed something very disturbing. My house
is not grounded. I open my main panel and there are the two hots and
one neutral.

Ground bus and neutral bus are connected and both ground and neutral
wires share the same bus.

Yes, that is how a panel is done; ground and neutral are the same bus. On a
subpanel they are separated.

My house is newer, only about 8 years old.

Why is there no ground? I know when I did the same work in FL I was
required to put in two ground rods.


There should be a cable going from the ground bus to your ground rods/water
pipe. Look carefully. If it is not there, you have a problem; but it seems
unlikely.

Is this a concern or normal?



  #4   Report Post  
TeamCasa
 
Posts: n/a
Default

Its is correct for the main panel.
The neutral and ground share the same bus. Only in a sub-panel will the
ground be isolated from the neutral bus.

Dave


"Elmar" wrote in message
om...
While wiring my shop, I noticed something very disturbing. My house
is not grounded. I open my main panel and there are the two hots and
one neutral.

Ground bus and neutral bus are connected and both ground and neutral
wires share the same bus.

My house is newer, only about 8 years old.

Why is there no ground? I know when I did the same work in FL I was
required to put in two ground rods.

Is this a concern or normal?



  #5   Report Post  
Doug Winterburn
 
Posts: n/a
Default

On Mon, 01 Nov 2004 07:23:14 -0800, Elmar wrote:

While wiring my shop, I noticed something very disturbing. My house is
not grounded. I open my main panel and there are the two hots and one
neutral.

Ground bus and neutral bus are connected and both ground and neutral wires
share the same bus.

My house is newer, only about 8 years old.

Why is there no ground? I know when I did the same work in FL I was
required to put in two ground rods.

Is this a concern or normal?


Usually, the neutral is grounded at the transformer, and the meter and
entrance panel share a common ground with the neutral in the entrance
panel bonded to ground. Any subpanels should have the neutral isolated
from ground.

-Doug

--
"It has been a source of great pain to me to have met with so many among
[my] opponents who had not the liberality to distinguish between
political and social opposition; who transferred at once to the person,
the hatred they bore to his political opinions." --Thomas Jefferson



  #6   Report Post  
George
 
Posts: n/a
Default

Son in law discovered the same on their "new" (20yr old) house. Might have
been because the subdivision is on an old lakeside dune, and a driven rod
would have trouble gaining a ground. His dad, who works for a power
company, came up with ten feet of rod to drive. Next time the weather gets
dry, we'll see.

Guard tower they built at the airbase, also in sand, had to have an
extensive grid buried to keep St Elmo and lightning away.

"Elmar" wrote in message
om...
While wiring my shop, I noticed something very disturbing. My house
is not grounded. I open my main panel and there are the two hots and
one neutral.

Ground bus and neutral bus are connected and both ground and neutral
wires share the same bus.

My house is newer, only about 8 years old.

Why is there no ground? I know when I did the same work in FL I was
required to put in two ground rods.

Is this a concern or normal?



  #7   Report Post  
Tim Douglass
 
Posts: n/a
Default

On Mon, 01 Nov 2004 15:48:24 GMT, "toller" wrote:


"Elmar" wrote in message
. com...


Why is there no ground? I know when I did the same work in FL I was
required to put in two ground rods.


There should be a cable going from the ground bus to your ground rods/water
pipe. Look carefully. If it is not there, you have a problem; but it seems
unlikely.


If your ground goes to a water pipe check it out a bit. In my previous
house I was doing some other remodeling when I discovered that the
water line coming into the house had at some point been re-done in
plastic. I had a ground to the galvanized pipe in the house, but
effectively no real ground since what actually went into the ground
was non-conductive. I drove an 8' rod and properly grounded things -
it was amazing, both my phone system and my computer worked better
after that.

Tim Douglass

http://www.DouglassClan.com
  #8   Report Post  
Bob Peterson
 
Posts: n/a
Default


"Elmar" wrote in message
om...
While wiring my shop, I noticed something very disturbing. My house
is not grounded. I open my main panel and there are the two hots and
one neutral.

Ground bus and neutral bus are connected and both ground and neutral
wires share the same bus.


This is usually the case with service panels.


My house is newer, only about 8 years old.

Why is there no ground? I know when I did the same work in FL I was
required to put in two ground rods.

Is this a concern or normal?


There is probably a green wire snaking out to your grounding electrode,
usually a rod driven in the ground. It could also be connected to various
substitutes for a ground rod that are allowed as well.


  #9   Report Post  
Robert Galloway
 
Posts: n/a
Default

Don't know much about this but it seems like I remember that the code
most places prohibits more than one ground. Aren't you required to have
a ground for the main service or panel and no secondary ground at any
sub panel?

bob g.

Bob Peterson wrote:

"Elmar" wrote in message
om...

While wiring my shop, I noticed something very disturbing. My house
is not grounded. I open my main panel and there are the two hots and
one neutral.

Ground bus and neutral bus are connected and both ground and neutral
wires share the same bus.



This is usually the case with service panels.


My house is newer, only about 8 years old.

Why is there no ground? I know when I did the same work in FL I was
required to put in two ground rods.

Is this a concern or normal?



There is probably a green wire snaking out to your grounding electrode,
usually a rod driven in the ground. It could also be connected to various
substitutes for a ground rod that are allowed as well.


  #10   Report Post  
Greg G.
 
Posts: n/a
Default

Robert Galloway said:

Don't know much about this but it seems like I remember that the code
most places prohibits more than one ground. Aren't you required to have
a ground for the main service or panel and no secondary ground at any
sub panel?


If the sub-panel is located in a separate building from the main
panel, code generally calls for a local ground for the sub-panel.


Greg G.


  #11   Report Post  
Bob Peterson
 
Posts: n/a
Default

You cannot connect the neutral to earth except at the service point. Most
often this is done either by using the neutral bar as the earth connection
point and as a combined ground bar/neutral bar, or in newer panels via a
bonding jumper between the equipment ground bus and the neutral bus in the
service panel.

You can have as many ground rods as you want interconnected with each other
either directly or through an equipment grounding conductor.

I don't think the phrase "secondary ground" has any defined meaning in the
NEC.

A subpanel (another term that I don't recall being defined in the NEC) could
have its own ground rod but may or may not have a connection from the ground
rod to neutral at that panel. Most often in most residential settings it
would not have that connection.



"Robert Galloway" wrote in message
...
Don't know much about this but it seems like I remember that the code most
places prohibits more than one ground. Aren't you required to have a
ground for the main service or panel and no secondary ground at any sub
panel?

bob g.

Bob Peterson wrote:

"Elmar" wrote in message
om...

While wiring my shop, I noticed something very disturbing. My house
is not grounded. I open my main panel and there are the two hots and
one neutral.

Ground bus and neutral bus are connected and both ground and neutral
wires share the same bus.



This is usually the case with service panels.


My house is newer, only about 8 years old.

Why is there no ground? I know when I did the same work in FL I was
required to put in two ground rods.

Is this a concern or normal?



There is probably a green wire snaking out to your grounding electrode,
usually a rod driven in the ground. It could also be connected to
various substitutes for a ground rod that are allowed as well.



  #12   Report Post  
Bob Peterson
 
Posts: n/a
Default


Greg G. wrote in message
...
Robert Galloway said:

Don't know much about this but it seems like I remember that the code
most places prohibits more than one ground. Aren't you required to have
a ground for the main service or panel and no secondary ground at any
sub panel?


If the sub-panel is located in a separate building from the main
panel, code generally calls for a local ground for the sub-panel.


Generally you are required to have another grounding electrode (typically a
ground rod) but not necessarily a connection between earth and neutral at
that subpanel. the ground rod is for lightning protection.



Greg G.



  #13   Report Post  
Greg G.
 
Posts: n/a
Default

Bob Peterson said:


Greg G. wrote in message
.. .
Robert Galloway said:

Don't know much about this but it seems like I remember that the code
most places prohibits more than one ground. Aren't you required to have
a ground for the main service or panel and no secondary ground at any
sub panel?


If the sub-panel is located in a separate building from the main
panel, code generally calls for a local ground for the sub-panel.


Generally you are required to have another grounding electrode (typically a
ground rod) but not necessarily a connection between earth and neutral at
that subpanel. the ground rod is for lightning protection.


Err... I guess I was unclear/incomplete. It is a convoluted subject,
but here is the entire run-down as per the 2002 NEC.

When the sub-panel is located in the same building, you use the ground
provided in the main panel, and DO NOT bond the ground and neutral
together in the sub-panel - requiring a 4 wire feed.

A detached structure with no metallic paths between it and the main
building, MAY use a 3 wire feed, but MUST use a grounding electrode
with the neutral to ground UNbonded in the sub-panel.

A detached structure with no metallic paths between it and the main
building, MAY ALSO use a 4 wire feed, but MAY also use a grounding
electrode, with the neutral to ground UNbonded in the sub-panel. It
is highly recommended to have a secondary ground rod, and must NOT
bond the ground and neutral in the sub-panel when the sub-panel is
located in a separate building.

Any detached structure that has an existing non-current carrying
metallic path such as water pipes, intercoms, telephone lines, etc.
installed between the main structure and the detached structure MUST
have an equipment grounding conductor installed with the feeders
installed between the two buildings AS WELL as using the water pipe as
a ground, AND a supplementary grounding rod, even if an
interconnecting metallic water pipe is also connected as ground.
Article 250-32-B-1 & 2

It is primarily to prevent telephones, water pipes, intercoms and such
from presenting a shock hazard when they are at differing earth
potentials, aggrevated by charged atmosphere/earth conditions.

If there is no grounding electrode system serving the detached garage,
then you must install a new grounding electrode system as described in
Article 250-50. If none of those listed in Article 250-50 is
available, then you may use a made electrode as found in Article
250-52. Article 250-50 lists any metal water pipe in direct contact
with earth, any rebar in concrete, any grounding rings, and many more
as an approved grounding electrode to be combined as a grounding
electrode system. If available all of those grounding electrode
sources listed in Article 250-50 must be connected together to make
the grounding electrode system. Most likely, if you have a metal water
pipe run underground between the two buildings, then you have a water
pipe in direct contact with earth and that metal water pipe, and any
other grounding method listed in Article 250-50 must be connected
together to make that grounding electrode system. If that metal water
pipe is installed between the two buildings, then you must use that as
part of the grounding electrode system but you must also supply a
supplemental grounding electrode to back up that water pipe in case
that metal water pipe is removed at a later date. Article 250-50-A-2

Remember, if any non current carrying metal connection is existing
between that main building, and the detached building, then you must
install an equipment grounding conductor between the two buildings,
with that feeder and as a part of that feeder installed between the
two buildings. Article 250-32-B-1 & 2

Whew...


Greg G.
  #14   Report Post  
Elmar
 
Posts: n/a
Default

Thank you everyone for all of your great input. I will do some
further investigation. I am told that sometimes here in TX they will
also put the ground wire in conduit to the ground for a cleaner
appearance.

This board has been VERY valuable....
  #15   Report Post  
bob peterson
 
Posts: n/a
Default

w_tom wrote in message ...

snipped

A couple of things. Grounding (hooking up to a grounding electrode)
is really not so much a matter of human safety as it is to provide a
path for lightning and a way to equalize voltages.

The real protection for humans comes from bonding all the metal pieces
in your home that might become energized and then connecting that to
your neutral so that if the conductive pieces do become energized, a
short circuit will occur and trip the branch circuit overcurrent
protection.

Grounding (making the connection to earth) by itself really does not
provide any substantial protection.


  #17   Report Post  
w_tom
 
Posts: n/a
Default

To summarize or correct many responses. Every utility wire
entering the building must connect to same single point earth
ground before or as it enters the building. That means AC
electric neutral (one type of ground) must connect to earth
ground (what the code calls a ground electrode) where it
enters the building (called service entrance). This earthing
wire could be at meter or at breaker box with the mains (100
amp or 200 amp) circuit breaker. Meter or breaker box is
often unique to local utility requirements and typically is a
6 AWG or larger bare copper wire.

All other utilities (phone, cable TV, etc) must also make a
less than 20 foot connection to this earth ground.

This earth ground is required for human safety. NEC that
requires these earthing connections is only concerned with
human safety. However this earthing system must meet or be
enhanced to also provide transistor safety. No earth ground
is why plug-in protectors do nothing effective - another topic
beyond the scope of this discussion.

Water pipe is no longer acceptable for earthing as of 1990.
The water pipe must connect to breaker box safety ground
(where earth ground, receptacle safety ground wires, AC
neutral wire all meet) for human safety reasons - not to be an
earth ground connection. Furthermore, no wire may connect to
water pipes with the intent of dumping electricity into that
pipe. Wire connections to pipes are only to remove
electricity from those pipes - a fundamental change in code.

In addition, some jurisdictions require any metallic bathtub
be hardwired (again 6 AWG wire) from drain pipe to breaker box
safety ground. Further information on safety grounding is
summarized by volts500 in the newsgroup alt.home.repair
entitled "Grounding Rod Info" on 12 July 2003 at
http://tinyurl.com/hkjq

How to find the earth ground? Again, every utility must
connect to that earth ground. Follow the wires. All utilities
must be earthed to same grounding electrode. If not, then an
important electrical upgrade is necessary and may require an
electrician. No earth ground means no human protection and no
transistor protection.

As noted, remove sub panels - those powered by the mains
breaker box - would have safety ground and neutral wire
separate and would not connect to earth ground.

Consider geology. For example, if constructed in sandy soil
or on a boundary line between different geologies, then
consider more earthing than just a few earth ground rods.
Well pump protection may also require additional
considerations. Again, reasons involve facts beyond this
scope.

What will a plug-in ground tester report? Which ground is
it testing for? Tester can only detect bad breaker box safety
ground connection. It will not report a good safety ground
connection nor will it test for any other grounds such as
earth ground. Anyone recommending tests using "one of those
plug testers into a wall socket" should have known this before
posting.

Then another earth ground that is essential to safe home.
Note the failures exampled he
http://www.tvtower.com/fpl.html

Happy earthing. Don't get your knees too dirty.

Elmar wrote:
While wiring my shop, I noticed something very disturbing. My house
is not grounded. I open my main panel and there are the two hots and
one neutral.

Ground bus and neutral bus are connected and both ground and neutral
wires share the same bus.

My house is newer, only about 8 years old.

Why is there no ground? I know when I did the same work in FL I was
required to put in two ground rods.

Is this a concern or normal?

  #18   Report Post  
Jim Swank
 
Posts: n/a
Default

Insufficient information.... The ground might well be present, but
connected in the meter base rather than the main panel. This is common
practice - check it before you panic.

Also, if there is an outside main breaker mounted on a ppole with the
meter enclosure, the ground could be there.

Jim


Elmar wrote:
While wiring my shop, I noticed something very disturbing. My house
is not grounded. I open my main panel and there are the two hots and
one neutral.

Ground bus and neutral bus are connected and both ground and neutral
wires share the same bus.

My house is newer, only about 8 years old.

Why is there no ground? I know when I did the same work in FL I was
required to put in two ground rods.

Is this a concern or normal?

  #19   Report Post  
Dave
 
Posts: n/a
Default

Is there any way of checking for ground indirectly, rather than just
physically looking to see if a wire is connected?

Dave

"Jim Swank" wrote in message
...
Insufficient information.... The ground might well be present, but
connected in the meter base rather than the main panel. This is common
practice - check it before you panic.

Also, if there is an outside main breaker mounted on a ppole with the
meter enclosure, the ground could be there.

Jim


Elmar wrote:
While wiring my shop, I noticed something very disturbing. My house
is not grounded. I open my main panel and there are the two hots and
one neutral.

Ground bus and neutral bus are connected and both ground and neutral
wires share the same bus.

My house is newer, only about 8 years old.

Why is there no ground? I know when I did the same work in FL I was
required to put in two ground rods.

Is this a concern or normal?



  #20   Report Post  
mac davis
 
Posts: n/a
Default

On Wed, 03 Nov 2004 05:03:40 GMT, "Dave"
wrote:

your local lowes, HD, Orchard supply, etc. will have fairly
inexpensive testers available..
I think the one we carry in our rv was about $20...
(lots of rv parks have bad grounding or inverted polarity)

Is there any way of checking for ground indirectly, rather than just
physically looking to see if a wire is connected?

Dave

"Jim Swank" wrote in message
...
Insufficient information.... The ground might well be present, but
connected in the meter base rather than the main panel. This is common
practice - check it before you panic.

Also, if there is an outside main breaker mounted on a ppole with the
meter enclosure, the ground could be there.

Jim


Elmar wrote:
While wiring my shop, I noticed something very disturbing. My house
is not grounded. I open my main panel and there are the two hots and
one neutral.

Ground bus and neutral bus are connected and both ground and neutral
wires share the same bus.

My house is newer, only about 8 years old.

Why is there no ground? I know when I did the same work in FL I was
required to put in two ground rods.

Is this a concern or normal?





  #21   Report Post  
w_tom
 
Posts: n/a
Default

NEC does not care how many appliances are destroyed by
surges. It only cares about human safety which is why NEC
demands that earth ground rod. Example, in one home, the
transformer neutral failed. House did not have an earth
ground rod. So electricity used gas pipes until meter gasket
failed and house exploded. Just another reason why that earth
ground rod is essential to human safety. If earth ground was
not required for human safety, then NEC would not even require
it.

Scott. Did you include time in your wire calculations.
Furthermore, cross sectional area has less significance due to
something called skin effect. That 6 AWG wire is sufficient
to earth direct and typical lightning strikes without wire
damage. Should you think otherwise, then put up numbers to
support your speculations.

In the meantime, learn something else. How to identify
ineffective protectors. No mention of earthing and no
dedicated earth ground because they don't even claim to
protect from typically destructive transients. Protection
from lightning means that earth ground is essential. Earthing
is THE one and most critical component for lightning
protection - no way around that fact.

We earth for two reasons - human safety and transistor
safety.

Scott Lurndal wrote:
(bob peterson) writes:
w_tom wrote in message ...

snipped

A couple of things. Grounding (hooking up to a grounding electrode)
is really not so much a matter of human safety as it is to provide a
path for lightning and a way to equalize voltages.


Please calculate the the cross-sectional area of a conductor required
to carry the current from a lightning strike, and compare and contrast
that with the typical #12AWG cross-sectional area.

Grounding an electrical system will not provide a path for lightning.

scott

  #22   Report Post  
George
 
Posts: n/a
Default

Three.

To avoid dust explosions ....

"w_tom" wrote in message
...

We earth for two reasons - human safety and transistor
safety.



  #25   Report Post  
David Chamberlain
 
Posts: n/a
Default

There probably is a ground. In the main breaker box (but not in any
sub-panels), the ground and the neutral are tied together. If you look on
the neutral/ground bus bar, you will probably see one fairly large wire (#4,
#6, #8 (hopefully no smaller)) that goes into a conduit or out through a
cable clamp. That larger wire probably ends up at a good earth ground.

However, it is possible, that the electrician is relying on the utility
neutral as a ground. THAT is not a good thing.


--
dbchamber at hotmail spam dot com

Remove the spam to reach me
Elmar wrote:
While wiring my shop, I noticed something very disturbing. My house
is not grounded. I open my main panel and there are the two hots and
one neutral.

Ground bus and neutral bus are connected and both ground and neutral
wires share the same bus.

My house is newer, only about 8 years old.

Why is there no ground? I know when I did the same work in FL I was
required to put in two ground rods.

Is this a concern or normal?







  #26   Report Post  
Dave
 
Posts: n/a
Default

Is there any way to indirectly test to see if there is an adequate ground in
a system?

Dave

"David Chamberlain" wrote in message
...
There probably is a ground. In the main breaker box (but not in any
sub-panels), the ground and the neutral are tied together. If you look on
the neutral/ground bus bar, you will probably see one fairly large wire
(#4, #6, #8 (hopefully no smaller)) that goes into a conduit or out
through a cable clamp. That larger wire probably ends up at a good earth
ground.

However, it is possible, that the electrician is relying on the utility
neutral as a ground. THAT is not a good thing.


--
dbchamber at hotmail spam dot com

Remove the spam to reach me
Elmar wrote:
While wiring my shop, I noticed something very disturbing. My house
is not grounded. I open my main panel and there are the two hots and
one neutral.

Ground bus and neutral bus are connected and both ground and neutral
wires share the same bus.

My house is newer, only about 8 years old.

Why is there no ground? I know when I did the same work in FL I was
required to put in two ground rods.

Is this a concern or normal?






  #27   Report Post  
 
Posts: n/a
Default

On Fri, 05 Nov 2004 01:54:00 GMT, "Dave"
wrote:

Is there any way to indirectly test to see if there is an adequate ground in
a system?

Dave


lick it.
  #29   Report Post  
w_tom
 
Posts: n/a
Default

Dust explosions are another part of code for human safety.

George wrote:
Three.

To avoid dust explosions ....

"w_tom" wrote in message
...
We earth for two reasons - human safety and transistor
safety.

  #30   Report Post  
George
 
Posts: n/a
Default

Not really, only documented cases are with dragons....

"w_tom" wrote in message
...
Dust explosions are another part of code for human safety.

George wrote:
Three.

To avoid dust explosions ....

"w_tom" wrote in message
...
We earth for two reasons - human safety and transistor
safety.





  #31   Report Post  
David Chamberlain
 
Posts: n/a
Default

The biggest problem is finding a good earth ground to use as a reference.
If you have copper water pripe feeding the house or if you have a drilled
well, you can probably be sure of a good earth ground. You use an ohmeter
between your box ground and an actual ground. The resistance should be as
close to zero as your meter can read. The higher the resistance, the more
problems you can run into. Your box ground can start to float above zero
volts.

I miss the good old days of copper tubing and metal pipe. If you had a 100
foot run of metal pipe going out to a drilled well with 60 feet of casing,
you were pretty darn sure of a good ground. Even having 30 or 40 feet of
copper tubing going out to the water main made a pretty sure round. Now
with polybutelyne and other plastics in the system, it is harder to FIND a
good ground to use as a test.

I am not sure what the NEC requires anymore but the 2 places I built had 2
10 foot ground rounds driven 18" below grade and tied to the box with good
copper conductors.


--
dbchamber at hotmail spam dot com

Remove the spam to reach me

wrote in message
...
On Fri, 05 Nov 2004 01:54:00 GMT, "Dave"
wrote:

Is there any way to indirectly test to see if there is an adequate ground
in
a system?

Dave


lick it.



  #32   Report Post  
Bob Peterson
 
Posts: n/a
Default


"David Chamberlain" wrote in message
...
The biggest problem is finding a good earth ground to use as a reference.
If you have copper water pripe feeding the house or if you have a drilled
well, you can probably be sure of a good earth ground. You use an ohmeter
between your box ground and an actual ground. The resistance should be as
close to zero as your meter can read. The higher the resistance, the more
problems you can run into. Your box ground can start to float above zero
volts.


Just what is a "box ground" versus a "good earth ground".

The reality is you cannot test earthing with a normal voltmeter and get
anything even remotely resembling a result that is meaningful.



I miss the good old days of copper tubing and metal pipe. If you had a
100 foot run of metal pipe going out to a drilled well with 60 feet of
casing, you were pretty darn sure of a good ground. Even having 30 or 40
feet of copper tubing going out to the water main made a pretty sure
round. Now with polybutelyne and other plastics in the system, it is
harder to FIND a good ground to use as a test.

I am not sure what the NEC requires anymore but the 2 places I built had 2
10 foot ground rounds driven 18" below grade and tied to the box with good
copper conductors.


--
dbchamber at hotmail spam dot com

Remove the spam to reach me

wrote in message
...
On Fri, 05 Nov 2004 01:54:00 GMT, "Dave"
wrote:

Is there any way to indirectly test to see if there is an adequate ground
in
a system?

Dave


lick it.





  #33   Report Post  
David Chamberlain
 
Posts: n/a
Default

My meaning of a box ground is the ground bus inside your breaker box. An
earth ground is an actual ground such as a ground rod or a buried length of
pipe. An ohmeter is not the best tool but if the ohmeter measures a
difference bewtween the two points then your breaker box groun is not really
gounded.


--
dbchamber at hotmail spam dot com

Remove the spam to reach me
"Bob Peterson" wrote in message
...

"David Chamberlain" wrote in message
...
The biggest problem is finding a good earth ground to use as a reference.
If you have copper water pripe feeding the house or if you have a drilled
well, you can probably be sure of a good earth ground. You use an
ohmeter between your box ground and an actual ground. The resistance
should be as close to zero as your meter can read. The higher the
resistance, the more problems you can run into. Your box ground can
start to float above zero volts.


Just what is a "box ground" versus a "good earth ground".

The reality is you cannot test earthing with a normal voltmeter and get
anything even remotely resembling a result that is meaningful.



I miss the good old days of copper tubing and metal pipe. If you had a
100 foot run of metal pipe going out to a drilled well with 60 feet of
casing, you were pretty darn sure of a good ground. Even having 30 or 40
feet of copper tubing going out to the water main made a pretty sure
round. Now with polybutelyne and other plastics in the system, it is
harder to FIND a good ground to use as a test.

I am not sure what the NEC requires anymore but the 2 places I built had
2 10 foot ground rounds driven 18" below grade and tied to the box with
good copper conductors.


--
dbchamber at hotmail spam dot com

Remove the spam to reach me

wrote in message
...
On Fri, 05 Nov 2004 01:54:00 GMT, "Dave"
wrote:

Is there any way to indirectly test to see if there is an adequate
ground in
a system?

Dave

lick it.







Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Repairing Lightning Damaged Tv's CJ Electronics Repair 20 June 22nd 04 06:03 AM
2- vs. 3-prong outlets Suzie-Q Home Repair 30 April 19th 04 06:55 PM
Am I grounded? Electrically speaking. Anthony Diodati Home Repair 39 January 4th 04 08:11 PM
Is it a radial or ring circuit? Paul UK diy 14 September 4th 03 04:48 PM


All times are GMT +1. The time now is 06:27 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"