Today I experienced an electric shock in my house, after I touched a bare
cable, which I had foolishly left exposed. The cable touched my leg and I had a heck of a jolt up my body which pushed me out of the way. I am now wondering why the RCD did not trip. Last year a contactum split load CU was fitted, the cable which I touched is on the RCD side. Could there be a problem somewhere, or was the shock I had below the trip current? Any ideas? Thanks Andrew |
#2
|
|||
|
|||
Electric Shock with RCD
"Andrew Barnes" wrote in message .. . | Today I experienced an electric shock in my house, after I touched a bare | cable, which I had foolishly left exposed. The cable touched my leg and I | had a heck of a jolt up my body which pushed me out of the way. | | I am now wondering why the RCD did not trip. Last year a contactum split | load CU was fitted, the cable which I touched is on the RCD side. Could | there be a problem somewhere, or was the shock I had below the trip current? | | Any ideas? | | Thanks | | Andrew | Hi I'd expect that the shock was probably less than the trip current. If that's a 100mA RCD then it's hardly surprising. However, if you're worried re the RCD then best to get it tested. I assume that you have the test records from the installation which show that it was working when installed? Also, you should take more care! Shouldn't really have exposed live conductors around to touch and circuits should be isolated (and discharged) before working on them. J |
#3
|
|||
|
|||
Electric Shock with RCD
"Me" wrote in message ... "Andrew Barnes" wrote in message .. . | Today I experienced an electric shock in my house, after I touched a bare | cable, which I had foolishly left exposed. The cable touched my leg and I | had a heck of a jolt up my body which pushed me out of the way. | | I am now wondering why the RCD did not trip. Last year a contactum split | load CU was fitted, the cable which I touched is on the RCD side. Could | there be a problem somewhere, or was the shock I had below the trip current? | | Any ideas? | | Thanks | | Andrew | Hi I'd expect that the shock was probably less than the trip current. If that's a 100mA RCD then it's hardly surprising. However, if you're worried re the RCD then best to get it tested. I assume that you have the test records from the installation which show that it was working when installed? Also, you should take more care! Shouldn't really have exposed live conductors around to touch and circuits should be isolated (and discharged) before working on them. J Yep !!! This one was your warning, the next one might be worse if you carry on exposing live cables in easy reach. Always a good idea, especially if you're going to work on cables that will become live when your testing others that are connected, is to wrap a piece of insulting tape around them before you make the circuits live again for your test. --- www.basecuritysystems.no-ip.com Outgoing mail is certified Virus Free. Checked by AVG anti-virus system (http://www.grisoft.com). Version: 6.0.528 / Virus Database: 324 - Release Date: 16/10/03 |
#4
|
|||
|
|||
Electric Shock with RCD
"BigWallop" wrote in message news "Me" wrote in message ... "Andrew Barnes" wrote in message .. . | Today I experienced an electric shock in my house, after I touched a bare | cable, which I had foolishly left exposed. The cable touched my leg and I | had a heck of a jolt up my body which pushed me out of the way. | | I am now wondering why the RCD did not trip. Last year a contactum split | load CU was fitted, the cable which I touched is on the RCD side. Could | there be a problem somewhere, or was the shock I had below the trip current? | | Any ideas? | | Thanks | | Andrew | Hi You don't say what exactly you touched. If you contacted bare live and neutral, then the RCD "sees" you as a normal and legitimate load, and will not trip. This will only happen if current from either live or neutral finds an abnormal return path, normally via an earth. Charles Fearnley |
#5
|
|||
|
|||
Electric Shock with RCD
"Charles Fearnley" wrote in message ... You don't say what exactly you touched. If you contacted bare live and neutral, then the RCD "sees" you as a normal and legitimate load, and will not trip. This will only happen if current from either live or neutral finds an abnormal return path, normally via an earth. Perhaps the old description 'Earth leakage' was more informative than 'Residual Current' |
#6
|
|||
|
|||
Electric Shock with RCD
"Chris Oates" wrote in
: Perhaps the old description 'Earth leakage' was more informative than 'Residual Current' I think you're right, but the great and the good prolly thought we wouldn't get the idea and try to connect it across earth. Like Swiss bankers couldn't understand Lsd, so we had to go metric :-( mike r |
#7
|
|||
|
|||
Electric Shock with RCD
"BigWallop" wrote in message ...
a piece of insulting tape around them Heh, not heard that one before. Regards, NT |
#8
|
|||
|
|||
Electric Shock with RCD
"N. Thornton" wrote in message om... "BigWallop" wrote in message ... a piece of insulting tape around them Heh, not heard that one before. Regards, NT LOL !!! Oops !!! Insulating tape would be more appropriate, wouldn't it ? :-)) |
#9
|
|||
|
|||
Electric Shock with RCD
"BigWallop" wrote in message ...
"N. Thornton" wrote in message om... a piece of insulting tape around them Heh, not heard that one before. LOL !!! Oops !!! Insulating tape would be more appropriate, wouldn't it ? :-)) No, I'll be calling it insulting tape now Good one. Regards, NT |
#11
|
|||
|
|||
Electric Shock with RCD
In article 0, mike
ring writes "Chris Oates" wrote in : Perhaps the old description 'Earth leakage' was more informative than 'Residual Current' I think you're right, but the great and the good prolly thought we wouldn't get the idea and try to connect it across earth. Earth leakage trips are not the same as residual current trips. The principle of operation is very different (although the terms are sometimes, incorrectly, used interchangeably) -- Tim Mitchell |
#12
|
|||
|
|||
Electric Shock with RCD
In article ,
Tim Mitchell writes: In article 0, mike ring writes "Chris Oates" wrote in m: Perhaps the old description 'Earth leakage' was more informative than 'Residual Current' I think you're right, but the great and the good prolly thought we wouldn't get the idea and try to connect it across earth. Earth leakage trips are not the same as residual current trips. The principle of operation is very different (although the terms are sometimes, incorrectly, used interchangeably) Earth Leakage Circuit Breaker is generic and covers both types. RCD is a Current Operated ELCB, whereas the older ones which monitor the voltage on the CPC verses a ground spike are, unsurprisingly, called Voltage Operated ELCB's. The term RCD resulted from Which? and That's Life! suggesting that the industry adopt a common term, and it needed to be shorter than "Current Operated ELCB" which Joe Public wouldn't understand. -- Andrew Gabriel |
#13
|
|||
|
|||
Electric Shock with RCD
In article , Andrew Gabriel
writes In article , Tim Mitchell writes: In article 0, mike ring writes "Chris Oates" wrote in om: Perhaps the old description 'Earth leakage' was more informative than 'Residual Current' I think you're right, but the great and the good prolly thought we wouldn't get the idea and try to connect it across earth. Earth leakage trips are not the same as residual current trips. The principle of operation is very different (although the terms are sometimes, incorrectly, used interchangeably) Earth Leakage Circuit Breaker is generic and covers both types. RCD is a Current Operated ELCB, whereas the older ones which monitor the voltage on the CPC verses a ground spike are, unsurprisingly, called Voltage Operated ELCB's. The term RCD resulted from Which? and That's Life! suggesting that the industry adopt a common term, and it needed to be shorter than "Current Operated ELCB" which Joe Public wouldn't understand. An interesting bit of history which I didn't know (Esther Rantzen's contribution to electrical engineering. Who would have thought it) -- Tim Mitchell |
#14
|
|||
|
|||
Electric Shock with RCD
"Tim Mitchell" wrote
| The term RCD resulted from Which? and That's Life! suggesting | that the industry adopt a common term, and it needed to be shorter | than "Current Operated ELCB" which Joe Public wouldn't understand. I've never really understood what RCD actually means. I know what they do and how to use them, but Earth Leakage Circuit Breaker does exactly what it says on the BS EN IP-rated enclosure. | An interesting bit of history which I didn't know (Esther Rantzen's | contribution to electrical engineering. Who would have thought it) Well, she did play a major part in getting open-flued gas heaters (the infamous Ascot water heaters, my parents always rather liked theirs when they had one) banned in bathrooms because of the dangers of CO poisoning. Owain |
#15
|
|||
|
|||
Electric Shock with RCD
In uk.d-i-y, Owain wrote:
I've never really understood what RCD actually means. I know what they do and how to use them, but Earth Leakage Circuit Breaker does exactly what it says on the BS EN IP-rated enclosure. I guess inbetween Esther Rantzen on the one hand, and the nomenclature police at IEE ("extraneous-exposed-conductive-part" - I ask you!) they came up with this neutral no-name thang. "Differential" rather than "residual" might've been a little clearer. "Current Balance Device" would've been informative, *and* used shorter words. Ah well... no-one asked me, right? ;-) Stefek |
#16
|
|||
|
|||
Electric Shock with RCD
Stefek Zaba
| the nomenclature police at IEE ("extraneous-exposed-conductive-part" | - I ask you!) I have a sneaky suspicioun they are trying to harmonise us with something German. More bleedin' hyphens than a Twistleton-FFyffe. Could have been worse I suppose. Microsoft might have given us "My Grounded Metal Thing". Owain |
#17
|
|||
|
|||
Electric Shock with RCD
wrote in message
... "extraneous-exposed-conductive-part" No such thing! There are extraneous-conductive-parts [1] and there are exposed-conductive-parts [2]. These are different things, but the twain _should_ meet in your bathroom, via ... (you know the rest). [1] Non-electrical metalwork which may "introduce a potential, generally earth..." - e.g. metal plumbing & waste pipes. [2] Earthed metalwork of electrical appliances - e.g. wall heater, electric towel rail. -- Andy |
#18
|
|||
|
|||
Electric Shock with RCD
In uk.d-i-y, Andy Wade wrote:
"extraneous-exposed-conductive-part" No such thing! There are extraneous-conductive-parts [1] and there are exposed-conductive-parts [2]. These are different things, but the twain _should_ meet in your bathroom, via ... (you know the rest). [1] Non-electrical metalwork which may "introduce a potential, generally earth..." - e.g. metal plumbing & waste pipes. [2] Earthed metalwork of electrical appliances - e.g. wall heater, electric towel rail. Aye, I do know: and the mumpty that decided on the nomenclature, using two such similar words, deserves to spend a few thousand years in purgatory trapped in a late-1980s helpdesk dealing with Expanded vs Extended memory (come on now! quickly! summarise the differences!) ;-) Stefek |
#19
|
|||
|
|||
Electric Shock with RCD
wrote in message
... Aye, I do know: and the mumpty that decided on the nomenclature, using two such similar words, deserves to spend a few thousand years in purgatory trapped in a late-1980s helpdesk dealing with Expanded vs Extended memory Good point. Quad & Quattro LNB's provide another example in similar vein. -- Andy |
#20
|
|||
|
|||
Electric Shock with RCD
"Andy Wade" wrote in message ...
wrote in message ... "extraneous-exposed-conductive-part" No such thing! There are extraneous-conductive-parts [1] and there are exposed-conductive-parts [2]. These are different things, but the twain _should_ meet in your bathroom, via ... (you know the rest). Reminds me of a news item a few years ago about a flasher who weirded out one too many times. The lady involved had a dog apparently, and the dog decided the exposed parts were extraneous, and did something about it.... eek! Regards, NT |
#21
|
|||
|
|||
Electric Shock with RCD
purgatory trapped in a late-1980s helpdesk dealing with Expanded vs
Extended memory (come on now! quickly! summarise the differences!) ;-) Expanded memory was a system where you could set a window under the 1Mb mark into the expanded memory bank. The window could be moved to expose a different section of the memory. It was developed to help store additional information (particularly spreadsheets) that just couldn't be squeezed in. There was no virtual memory on Intel processors at this time. Extended memory was simply memory located above the 1Mb mark. This was only available on 286 processors or above, as previous processors only had a 20 bit address bus. (The 286 has a 24 bit bus, and the 386 a 32 bit one). Unfortunately, MS-DOS, the operating system of the time, did not allow the processor to be in the mode required to access this memory, so various memory extenders were required to switch the processor into and out of the mode as required. (HIMEM.SYS later helping out with this task). Expanded memory come first, when pre-286 processors were common and the 640kB limit at its worst. Extended memory took over by the time 386s came along with their fast context switches (and Windows 386 Enhanced and DOS4GW). It is far easier to work with and much less limited in size and performance (and does not require additional hardware). Christian. |
#22
|
|||
|
|||
Electric Shock with RCD
"Christian McArdle" wrote in message
t... Expanded memory came first ... .... with the Intel 'Above Board', IIRC. I remember buying one at work in 1980-something to run a upgrade release of Touchstone (1.4?) on our 12 MHz '286 PC-AT, with 20 MB HDD! The price for 1 MB ran to 4 figures. -- Andy |
#23
|
|||
|
|||
Electric Shock with RCD
On Tue, 28 Oct 2003 20:43:52 -0000, "Andy Wade"
wrote: ... with the Intel 'Above Board', IIRC. I remember buying one at work in 1980-something to run a upgrade release of Touchstone (1.4?) on our 12 MHz '286 PC-AT, with 20 MB HDD! The price for 1 MB ran to 4 figures. When you think about the prices that applied way back then, each of our PCs today would be at least half a million quid today..... PoP |
#24
|
|||
|
|||
Electric Shock with RCD
Andy Wade wrote:
on our 12 MHz '286 PC-AT, with 20 MB HDD! You exaggerate; the PC-AT was 6MHz. The later AT-X was 8MHz but that had a massive 30MB drive. -- Laurie R (IBM UK's PC Technical Product Manager 1984-2000) |
#25
|
|||
|
|||
Electric Shock with RCD
The price for 1 MB ran to 4 figures.
Yeah. I remember when a 10Mb hard disk cost 1600 quid. It was marketed as being "ideal for file server". Must have been around 1985. Christian. |
#26
|
|||
|
|||
Electric Shock with RCD
You exaggerate; the PC-AT was 6MHz. The later AT-X was 8MHz but that
had a massive 30MB drive. Ah. I remember the old AT with the really expensive EGA graphics upgrade. That was the third computer I used, after the PDP-11 and the Spectrum. The PDP-11 was fantastic. I learnt to program on it when I was five. We had two, sitting in the front room, with the teletypes sitting in the back room. I remember the excitement when the first VT100 arrived (must have been 1979). Such modern technology! You can still see the evidence of them now. My parents still have the holes in the floorboards where all the cables ran. Christian. |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Replacing electric shower - advice? | UK diy | |||
Cutting floor tiles: Electric or Hand Operated cutter? | UK diy | |||
o t ish changing gas and electric | UK diy | |||
Efficient Electric water storage heaters | UK diy | |||
Is my electric shower about to fail? | UK diy |