Electric Shock with RCD
 
Today I experienced an electric shock in my house, after I touched a bare
cable, which I had foolishly left exposed. The cable touched my leg and I
had a heck of a jolt up my body which pushed me out of the way.

I am now wondering why the RCD did not trip. Last year a contactum split
load CU was fitted, the cable which I touched is on the RCD side. Could
there be a problem somewhere, or was the shock I had below the trip current?

Any ideas?

Thanks

Andrew



Me October 18th 03 10:26 PM

Electric Shock with RCD
 

"Andrew Barnes" wrote in message
.. .
| Today I experienced an electric shock in my house, after I touched a bare
| cable, which I had foolishly left exposed. The cable touched my leg and I
| had a heck of a jolt up my body which pushed me out of the way.
|
| I am now wondering why the RCD did not trip. Last year a contactum split
| load CU was fitted, the cable which I touched is on the RCD side. Could
| there be a problem somewhere, or was the shock I had below the trip current?
|
| Any ideas?
|
| Thanks
|
| Andrew
|
Hi

I'd expect that the shock was probably less than the trip current. If that's a 100mA RCD then
it's hardly surprising.
However, if you're worried re the RCD then best to get it tested. I assume that you have the
test records from the installation which show that it was working when installed?

Also, you should take more care! Shouldn't really have exposed live conductors around to touch
and circuits should be isolated (and discharged) before working on them.

J





BigWallop October 18th 03 10:35 PM

Electric Shock with RCD
 

"Me" wrote in message
...

"Andrew Barnes" wrote in message
.. .
| Today I experienced an electric shock in my house, after I touched a

bare
| cable, which I had foolishly left exposed. The cable touched my leg and

I
| had a heck of a jolt up my body which pushed me out of the way.
|
| I am now wondering why the RCD did not trip. Last year a contactum split
| load CU was fitted, the cable which I touched is on the RCD side. Could
| there be a problem somewhere, or was the shock I had below the trip

current?
|
| Any ideas?
|
| Thanks
|
| Andrew
|
Hi

I'd expect that the shock was probably less than the trip current. If

that's a 100mA RCD then
it's hardly surprising.
However, if you're worried re the RCD then best to get it tested. I

assume that you have the
test records from the installation which show that it was working when

installed?

Also, you should take more care! Shouldn't really have exposed live

conductors around to touch
and circuits should be isolated (and discharged) before working on them.

J


Yep !!! This one was your warning, the next one might be worse if you carry
on exposing live cables in easy reach. Always a good idea, especially if
you're going to work on cables that will become live when your testing
others that are connected, is to wrap a piece of insulting tape around them
before you make the circuits live again for your test.


---
www.basecuritysystems.no-ip.com

Outgoing mail is certified Virus Free.
Checked by AVG anti-virus system (http://www.grisoft.com).
Version: 6.0.528 / Virus Database: 324 - Release Date: 16/10/03



Charles Fearnley October 19th 03 07:44 AM

Electric Shock with RCD
 

"BigWallop" wrote in message
...

"Me" wrote in message
...

"Andrew Barnes" wrote in message
.. .
| Today I experienced an electric shock in my house, after I touched a

bare
| cable, which I had foolishly left exposed. The cable touched my leg

and
I
| had a heck of a jolt up my body which pushed me out of the way.
|
| I am now wondering why the RCD did not trip. Last year a contactum

split
| load CU was fitted, the cable which I touched is on the RCD side.

Could
| there be a problem somewhere, or was the shock I had below the trip

current?
|
| Any ideas?
|
| Thanks
|
| Andrew
|
Hi


You don't say what exactly you touched. If you contacted bare live and
neutral, then the RCD "sees" you as a normal and legitimate load, and will
not trip. This will only happen if current from either live or neutral finds
an abnormal return path, normally via an earth.

Charles Fearnley



Chris Oates October 19th 03 11:02 AM

Electric Shock with RCD
 

"Charles Fearnley" wrote in
message ...

You don't say what exactly you touched. If you contacted bare live and
neutral, then the RCD "sees" you as a normal and legitimate load, and will
not trip. This will only happen if current from either live or neutral

finds
an abnormal return path, normally via an earth.


Perhaps the old description 'Earth leakage' was
more informative than 'Residual Current'



mike ring October 19th 03 12:13 PM

Electric Shock with RCD
 
"Chris Oates" wrote in
:

Perhaps the old description 'Earth leakage' was
more informative than 'Residual Current'

I think you're right, but the great and the good prolly thought we wouldn't
get the idea and try to connect it across earth.

Like Swiss bankers couldn't understand Lsd, so we had to go metric :-(

mike r

N. Thornton October 19th 03 02:36 PM

Electric Shock with RCD
 
"BigWallop" wrote in message ...

a piece of insulting tape around them


Heh, not heard that one before.

Regards, NT

BigWallop October 19th 03 03:51 PM

Electric Shock with RCD
 

"N. Thornton" wrote in message
om...
"BigWallop" wrote in message

...

a piece of insulting tape around them


Heh, not heard that one before.

Regards, NT



LOL !!!

Oops !!! Insulating tape would be more appropriate, wouldn't it ? :-))



N. Thornton October 19th 03 10:48 PM

Electric Shock with RCD
 
"BigWallop" wrote in message ...
"N. Thornton" wrote in message
om...


a piece of insulting tape around them


Heh, not heard that one before.



LOL !!!

Oops !!! Insulating tape would be more appropriate, wouldn't it ? :-))



No, I'll be calling it insulting tape now :) Good one.

Regards, NT

Gnube October 20th 03 02:35 AM

Electric Shock with RCD
 
On 19 Oct 2003 06:36:22 -0700, (N. Thornton) wrote:

"BigWallop" wrote in message ...

a piece of insulting tape around them


Heh, not heard that one before.


LOL! Is that the pink stuff[1] some Lawyers use to tie up their
briefs?

Probably would be I think.

[1] Like Red Tape but rather more effeminate!

Take Care,
Gnube
{too thick for linux}

Tim Mitchell October 20th 03 11:59 AM

Electric Shock with RCD
 
In article 0, mike
ring writes
"Chris Oates" wrote in
:

Perhaps the old description 'Earth leakage' was
more informative than 'Residual Current'

I think you're right, but the great and the good prolly thought we wouldn't
get the idea and try to connect it across earth.

Earth leakage trips are not the same as residual current trips. The
principle of operation is very different (although the terms are
sometimes, incorrectly, used interchangeably)
--
Tim Mitchell

Andrew Gabriel October 20th 03 02:10 PM

Electric Shock with RCD
 
In article ,
Tim Mitchell writes:
In article 0, mike
ring writes
"Chris Oates" wrote in
m:

Perhaps the old description 'Earth leakage' was
more informative than 'Residual Current'

I think you're right, but the great and the good prolly thought we wouldn't
get the idea and try to connect it across earth.

Earth leakage trips are not the same as residual current trips. The
principle of operation is very different (although the terms are
sometimes, incorrectly, used interchangeably)


Earth Leakage Circuit Breaker is generic and covers both types.

RCD is a Current Operated ELCB, whereas the older ones which
monitor the voltage on the CPC verses a ground spike are,
unsurprisingly, called Voltage Operated ELCB's.

The term RCD resulted from Which? and That's Life! suggesting
that the industry adopt a common term, and it needed to be shorter
than "Current Operated ELCB" which Joe Public wouldn't understand.

--
Andrew Gabriel

Tim Mitchell October 20th 03 02:38 PM

Electric Shock with RCD
 
In article , Andrew Gabriel
writes
In article ,
Tim Mitchell writes:
In article 0, mike
ring writes
"Chris Oates" wrote in
om:

Perhaps the old description 'Earth leakage' was
more informative than 'Residual Current'

I think you're right, but the great and the good prolly thought we wouldn't
get the idea and try to connect it across earth.

Earth leakage trips are not the same as residual current trips. The
principle of operation is very different (although the terms are
sometimes, incorrectly, used interchangeably)


Earth Leakage Circuit Breaker is generic and covers both types.

RCD is a Current Operated ELCB, whereas the older ones which
monitor the voltage on the CPC verses a ground spike are,
unsurprisingly, called Voltage Operated ELCB's.

The term RCD resulted from Which? and That's Life! suggesting
that the industry adopt a common term, and it needed to be shorter
than "Current Operated ELCB" which Joe Public wouldn't understand.

An interesting bit of history which I didn't know (Esther Rantzen's
contribution to electrical engineering. Who would have thought it)
--
Tim Mitchell

Owain October 20th 03 08:01 PM

Electric Shock with RCD
 
"Tim Mitchell" wrote
| The term RCD resulted from Which? and That's Life! suggesting
| that the industry adopt a common term, and it needed to be shorter
| than "Current Operated ELCB" which Joe Public wouldn't understand.

I've never really understood what RCD actually means. I know what they do
and how to use them, but Earth Leakage Circuit Breaker does exactly what it
says on the BS EN IP-rated enclosure.

| An interesting bit of history which I didn't know (Esther Rantzen's
| contribution to electrical engineering. Who would have thought it)

Well, she did play a major part in getting open-flued gas heaters (the
infamous Ascot water heaters, my parents always rather liked theirs when
they had one) banned in bathrooms because of the dangers of CO poisoning.

Owain



[email protected] October 20th 03 08:50 PM

Electric Shock with RCD
 
In uk.d-i-y, Owain wrote:

I've never really understood what RCD actually means. I know what they do
and how to use them, but Earth Leakage Circuit Breaker does exactly what it
says on the BS EN IP-rated enclosure.

I guess inbetween Esther Rantzen on the one hand, and the nomenclature
police at IEE ("extraneous-exposed-conductive-part" - I ask you!) they
came up with this neutral no-name thang. "Differential" rather than
"residual" might've been a little clearer. "Current Balance Device"
would've been informative, *and* used shorter words. Ah well... no-one
asked me, right? ;-)

Stefek

Owain October 20th 03 10:03 PM

Electric Shock with RCD
 
Stefek Zaba
| the nomenclature police at IEE ("extraneous-exposed-conductive-part"
| - I ask you!)

I have a sneaky suspicioun they are trying to harmonise us with something
German. More bleedin' hyphens than a Twistleton-FFyffe.

Could have been worse I suppose. Microsoft might have given us "My Grounded
Metal Thing".

Owain



Andy Wade October 26th 03 01:46 PM

Electric Shock with RCD
 
wrote in message
...

"extraneous-exposed-conductive-part"


No such thing! There are extraneous-conductive-parts [1] and there are
exposed-conductive-parts [2]. These are different things, but the twain
_should_ meet in your bathroom, via ... (you know the rest).

[1] Non-electrical metalwork which may "introduce a potential,
generally earth..." - e.g. metal plumbing & waste pipes.

[2] Earthed metalwork of electrical appliances - e.g. wall heater,
electric towel rail.

--
Andy



[email protected] October 26th 03 06:58 PM

Electric Shock with RCD
 
In uk.d-i-y, Andy Wade wrote:

"extraneous-exposed-conductive-part"


No such thing! There are extraneous-conductive-parts [1] and there are
exposed-conductive-parts [2]. These are different things, but the twain
_should_ meet in your bathroom, via ... (you know the rest).

[1] Non-electrical metalwork which may "introduce a potential,
generally earth..." - e.g. metal plumbing & waste pipes.

[2] Earthed metalwork of electrical appliances - e.g. wall heater,
electric towel rail.

Aye, I do know: and the mumpty that decided on the nomenclature, using
two such similar words, deserves to spend a few thousand years in
purgatory trapped in a late-1980s helpdesk dealing with Expanded vs
Extended memory (come on now! quickly! summarise the differences!) ;-)

Stefek

Andy Wade October 27th 03 12:36 AM

Electric Shock with RCD
 
wrote in message
...

Aye, I do know: and the mumpty that decided on the nomenclature,
using two such similar words, deserves to spend a few thousand years
in purgatory trapped in a late-1980s helpdesk dealing with Expanded
vs Extended memory


Good point. Quad & Quattro LNB's provide another example in similar vein.

--
Andy



N. Thornton October 27th 03 04:15 PM

Electric Shock with RCD
 
"Andy Wade" wrote in message ...
wrote in message ...


"extraneous-exposed-conductive-part"


No such thing! There are extraneous-conductive-parts [1] and there are
exposed-conductive-parts [2]. These are different things, but the twain
_should_ meet in your bathroom, via ... (you know the rest).



Reminds me of a news item a few years ago about a flasher who weirded
out one too many times. The lady involved had a dog apparently, and
the dog decided the exposed parts were extraneous, and did something
about it.... eek!

Regards, NT

Christian McArdle October 28th 03 01:17 PM

Electric Shock with RCD
 
purgatory trapped in a late-1980s helpdesk dealing with Expanded vs
Extended memory (come on now! quickly! summarise the differences!) ;-)


Expanded memory was a system where you could set a window under the 1Mb mark
into the expanded memory bank. The window could be moved to expose a
different section of the memory. It was developed to help store additional
information (particularly spreadsheets) that just couldn't be squeezed in.
There was no virtual memory on Intel processors at this time.

Extended memory was simply memory located above the 1Mb mark. This was only
available on 286 processors or above, as previous processors only had a 20
bit address bus. (The 286 has a 24 bit bus, and the 386 a 32 bit one).
Unfortunately, MS-DOS, the operating system of the time, did not allow the
processor to be in the mode required to access this memory, so various
memory extenders were required to switch the processor into and out of the
mode as required. (HIMEM.SYS later helping out with this task).

Expanded memory come first, when pre-286 processors were common and the
640kB limit at its worst. Extended memory took over by the time 386s came
along with their fast context switches (and Windows 386 Enhanced and
DOS4GW). It is far easier to work with and much less limited in size and
performance (and does not require additional hardware).

Christian.



Andy Wade October 28th 03 08:43 PM

Electric Shock with RCD
 
"Christian McArdle" wrote in message
t...

Expanded memory came first ...


.... with the Intel 'Above Board', IIRC. I remember buying one at work in
1980-something to run a upgrade release of Touchstone (1.4?) on our 12 MHz
'286 PC-AT, with 20 MB HDD! The price for 1 MB ran to 4 figures.

--
Andy



PoP October 29th 03 05:28 AM

Electric Shock with RCD
 
On Tue, 28 Oct 2003 20:43:52 -0000, "Andy Wade"
wrote:

... with the Intel 'Above Board', IIRC. I remember buying one at work in
1980-something to run a upgrade release of Touchstone (1.4?) on our 12 MHz
'286 PC-AT, with 20 MB HDD! The price for 1 MB ran to 4 figures.


When you think about the prices that applied way back then, each of
our PCs today would be at least half a million quid today..... ;)

PoP


Elessar October 29th 03 09:24 AM

Electric Shock with RCD
 
Andy Wade wrote:
on our 12 MHz '286 PC-AT, with 20 MB HDD!


You exaggerate; the PC-AT was 6MHz. The later AT-X was 8MHz but that had a
massive 30MB drive.
--
Laurie R (IBM UK's PC Technical Product Manager 1984-2000)



Christian McArdle October 29th 03 09:51 AM

Electric Shock with RCD
 
The price for 1 MB ran to 4 figures.

Yeah. I remember when a 10Mb hard disk cost 1600 quid. It was marketed as
being "ideal for file server". Must have been around 1985.

Christian.



Christian McArdle October 29th 03 10:22 AM

Electric Shock with RCD
 
You exaggerate; the PC-AT was 6MHz. The later AT-X was 8MHz but that
had a massive 30MB drive.


Ah. I remember the old AT with the really expensive EGA graphics upgrade.
That was the third computer I used, after the PDP-11 and the Spectrum. The
PDP-11 was fantastic. I learnt to program on it when I was five. We had two,
sitting in the front room, with the teletypes sitting in the back room. I
remember the excitement when the first VT100 arrived (must have been 1979).
Such modern technology! You can still see the evidence of them now. My
parents still have the holes in the floorboards where all the cables ran.

Christian.




All times are GMT +1. The time now is 09:00 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004 - 2014 DIYbanter