Woodworking (rec.woodworking) Discussion forum covering all aspects of working with wood. All levels of expertise are encouraged to particiapte.

Reply
 
LinkBack Thread Tools Search this Thread Display Modes
  #1   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 2
Default 220 volt motor wiring

Hello.
I'm sure this has been posted about in here before, but I don't know how to
find it. So I'll ask again.

I am running a 220 line for my new (used) tablesaw. What does the ground
attach to in the breaker box? Does it go to the neutral bus bar, or
elsewhere?

Thanks,

Alex


  #2   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 1,185
Default 220 volt motor wiring

Alexander Rabinovich wrote:

I am running a 220 line for my new (used) tablesaw. What does the ground
attach to in the breaker box? Does it go to the neutral bus bar, or
elsewhere?


It goes to the ground bus bar with all the other grounds.

Chris
  #3   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 311
Default 220 volt motor wiring


"Alexander Rabinovich" writes:
I am running a 220 line for my new (used) tablesaw. What does the ground
attach to in the breaker box? Does it go to the neutral bus bar, or
elsewhere?


[I am not a licensed electrician. Always follow local code and
ordinances.]

Ground (green/bare) always goes to ground. Always. Your main breaker
box may be the ground/neutral strapping point, though, in which case
both bus bars are connected together and it shouldn't matter which you
use (unless the existing wires are segregated, in which case, use the
same as as the other ground wires).

A 120v circuit uses one line to the breaker (black) and one line to
neutral (white), in addition to ground.

A 240v circuit has two options:

1. Two lines to each pole of a dual-pole breaker (supposed to be
black/red, so if you use two-conductor cable (which is black/white)
you should use a red marker to mark the white wires).

2. Two lines to each pole of a dual-pole breaker (as above) and a
third line (white) to neutral.

Table saws almost laways use #1.

Color summary:

Green/bare - ground.

White - neutral.

Black - hot (breaker or dual breaker).

Red - hot #2 (dual breaker).

Now, within the tool the colors may not be so obvious (they should be,
but they may not be). However, one wire should be physically
connected to the metal chassis or the metal case of the motor. This
wire is ground.

Any plugs/outlets you may install should have information on them
about which wires go where, but usually there's one screw that's
greenish (ground), one that's silverish (white, neutral) and one
that's bronze (black, hot). 240v outlets will have two bronze screws,
and may label them "L1" and "L2". No, it doesn't matter which hot is
which.

Other tidbits... In polarized outlets, the wider prong is neutral.
Outlets should be installed with ground "up" so if the plug is loose,
anything falling in there will hit ground first. All metal boxes and
conduits must be connected to ground, but should not be used *as*
ground. Wires should be attached to 2x4 wall studs at the center, to
avoid getting damaged by sheetrock screws.
  #4   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 931
Default 220 volt motor wiring

DJ Delorie wrote in :

*snip*

Other tidbits... In polarized outlets, the wider prong is neutral.
Outlets should be installed with ground "up" so if the plug is loose,
anything falling in there will hit ground first. All metal boxes and
conduits must be connected to ground, but should not be used *as*
ground. Wires should be attached to 2x4 wall studs at the center, to
avoid getting damaged by sheetrock screws.


So that's why they switched positions! I got used to the "face" and was
wondering why the new outlets were positioned "upside down." Is this a
NEC requirement, or just something for extra safety?

Puckdropper
--
Wise is the man who attempts to answer his question before asking it.

To email me directly, send a message to puckdropper (at) fastmail.fm
  #5   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 5,823
Default 220 volt motor wiring


"Puckdropper" wrote in message

So that's why they switched positions! I got used to the "face" and was
wondering why the new outlets were positioned "upside down." Is this a
NEC requirement, or just something for extra safety?



Not required by code, but it is becoming an accepted practice.




  #6   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 403
Default 220 volt motor wiring

On 04 Nov 2007 00:53:55 GMT, Puckdropper
wrote:

DJ Delorie wrote in :

*snip*

Other tidbits... In polarized outlets, the wider prong is neutral.
Outlets should be installed with ground "up" so if the plug is loose,
anything falling in there will hit ground first. All metal boxes and
conduits must be connected to ground, but should not be used *as*
ground. Wires should be attached to 2x4 wall studs at the center, to
avoid getting damaged by sheetrock screws.


So that's why they switched positions! I got used to the "face" and was
wondering why the new outlets were positioned "upside down." Is this a
NEC requirement, or just something for extra safety?


Annoys the **** out of me. It just looks wrong. And the "reasoning"
(loose plug/falling object) ranks right up there with dust collection
system explosions. I've yet to see or hear any actual documented
example of that happening anywhere.

Things you will never see in my house: Al Sharpton, Bill O'Reilly,
upside down receptacles, Al Sharpton (not redundant).


--
LRod

Master Woodbutcher and seasoned termite

Shamelessly whoring my website since 1999

http://www.woodbutcher.net

Proud participant of rec.woodworking since February, 1997

email addy de-spam-ified due to 1,000 spams per month.
If you can't figure out how to use it, I probably wouldn't
care to correspond with you anyway.
  #7   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 4,207
Default 220 volt motor wiring

Alexander Rabinovich wrote:
Hello.
I'm sure this has been posted about in here before, but I don't know
how to find it. So I'll ask again.

I am running a 220 line for my new (used) tablesaw. What does the
ground attach to in the breaker box? Does it go to the neutral bus
bar, or elsewhere?


If you're using three conductors plus ground, red and black go to the
breaker, white goes to the neutral bus bar, green/bare goes to the
ground bus bar.

If you're using two conductors plus ground then black and white (mark
the white conductor red at both ends with paint, tape, or heat
shrink--I forget what marking method code calls for) go to the breaker
and green/bare goes to the ground bus bar.

--
--
--John
to email, dial "usenet" and validate
(was jclarke at eye bee em dot net)


  #8   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 2
Default 220 volt motor wiring


" I am running a 220 line for my new (used) tablesaw.

Thank you everybody for your helpful responses. Now, it's time to grab the
tool belt and go down to the basement...

Alex


  #9   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 958
Default 220 volt motor wiring

On Sat, 3 Nov 2007 21:32:42 -0400, "Alexander Rabinovich"
wrote:


" I am running a 220 line for my new (used) tablesaw.

Thank you everybody for your helpful responses. Now, it's time to grab the
tool belt and go down to the basement...

Alex

After turning the breakers off, right?


mac

Please remove splinters before emailing
  #10   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 6,375
Default 220 volt motor wiring

In article , "J. Clarke" wrote:

If you're using two conductors plus ground then black and white (mark
the white conductor red at both ends with paint, tape, or heat
shrink--I forget what marking method code calls for) go to the breaker
and green/bare goes to the ground bus bar.


Code doesn't specify the marking method -- just that it must be permanent, and
encircle the conductor.

--
Regards,
Doug Miller (alphageek at milmac dot com)

It's time to throw all their damned tea in the harbor again.


  #11   Report Post  
Posted to rec.woodworking
Joe Joe is offline
external usenet poster
 
Posts: 7
Default 220 volt motor wiring

For some applications there are indeed 2 grounds, a neutral ground and
a machine ground. There is some reason the phase may be out if not
wired correctly (no im not an electrician) It is the difference
between 3 and 4 wire 220. Same voltage with different configuration...

Do yourself a favor, check with a professional or your local township
for codes...110 can kill you, but 220 likely WILL kill you if wired
wrong...

  #12   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 958
Default 220 volt motor wiring

On Sun, 04 Nov 2007 19:48:39 -0800, Joe wrote:

For some applications there are indeed 2 grounds, a neutral ground and
a machine ground. There is some reason the phase may be out if not
wired correctly (no im not an electrician) It is the difference
between 3 and 4 wire 220. Same voltage with different configuration...


Yep.. I hit this last year when we were running off of a generator..

The contractors generator didn't work very well... water pump and water heater
would not both run without blowing the breaker on the gen., so we ran one at a
time..
When we bought our own gen., I noticed that it had a 4 prong outlet, where the
contractor's had 3...
They has wires going to each hot and what I "assumed" was ground..
This was before we had electricity, obviously, and the 2 hot wires ran to lugs
in the box above where the meter would be and the ground ran to one of 2 pieces
of re-bar in the ground in front of the meter "kiosk"..

We ran the 2 hots as they did, the ground to the same place they used and the
neutral to the other grounding rod..
Everything worked well and my son & I were busy congratulating ourselves when my
wife mentioned that the breaker panel (in the kitchen pantry) was "buzzing"...
Found out it wasn't buzzing, just ARCING... oops...
Shut everything down, reversed the ground and neutral and fired up the
generator...Everything worked great for the next couple of months, until we got
"real" electricity...


mac

Please remove splinters before emailing
  #13   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 371
Default 220 volt motor wiring


"mac davis" wrote in message
...


We ran the 2 hots as they did, the ground to the same place they used and
the
neutral to the other grounding rod..
Everything worked well and my son & I were busy congratulating ourselves
when my
wife mentioned that the breaker panel (in the kitchen pantry) was
"buzzing"...
Found out it wasn't buzzing, just ARCING... oops...
Shut everything down, reversed the ground and neutral and fired up the
generator...Everything worked great for the next couple of months, until
we got
"real" electricity...


Something about this doesn't sound right mac. Both of those rods should
have been electrically the same, so it won't matter which wire you run to
which rod.

--

-Mike-



  #14   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 958
Default 220 volt motor wiring

On Mon, 5 Nov 2007 14:08:24 -0500, "Mike Marlow"
wrote:


"mac davis" wrote in message
.. .


We ran the 2 hots as they did, the ground to the same place they used and
the
neutral to the other grounding rod..
Everything worked well and my son & I were busy congratulating ourselves
when my
wife mentioned that the breaker panel (in the kitchen pantry) was
"buzzing"...
Found out it wasn't buzzing, just ARCING... oops...
Shut everything down, reversed the ground and neutral and fired up the
generator...Everything worked great for the next couple of months, until
we got
"real" electricity...


Something about this doesn't sound right mac. Both of those rods should
have been electrically the same, so it won't matter which wire you run to
which rod.


That got me, also.. I looked at my neighbor's kiosk and it only has one rod in
the ground...
Someone told me that it depended on where the ground wires went.. on the bar or
on the box, or something like that..
I'm pretty comfortable working with 110v but 220v is a now thing for me..

OH.. sort of a side thing, but might be relevant:
The house is built of insulating block and has no studs to screw the circuit
breaker panel into, so until the did the stucco work, the panel was held in
place with bailing wire twisted around a metal vent pipe and run through the
screw holes in the breaker box..
These wire were RED hot and arcing..
When we reversed the ground and neutral wires, they were fine..

Bottom line was that I should have had someone qualified hook up the generator
up but didn't really believe the bozo that the contractor sent out was an
"electrician"


mac

Please remove splinters before emailing
  #15   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 371
Default 220 volt motor wiring


"mac davis" wrote in message
...


That got me, also.. I looked at my neighbor's kiosk and it only has one
rod in
the ground...
Someone told me that it depended on where the ground wires went.. on the
bar or
on the box, or something like that..
I'm pretty comfortable working with 110v but 220v is a now thing for me..


Help me out here mac - what is this that you refer to as a kiosk?


OH.. sort of a side thing, but might be relevant:
The house is built of insulating block and has no studs to screw the
circuit
breaker panel into, so until the did the stucco work, the panel was held
in
place with bailing wire twisted around a metal vent pipe and run through
the
screw holes in the breaker box..
These wire were RED hot and arcing..
When we reversed the ground and neutral wires, they were fine..


Since your ground and your neutral are tied together in the box, it should
not matter. You can run a generator without a ground (separate ground rod
near the generator) all day long with no problems. It's done every day all
across America. That means you're only running the two hot legs and the
neutral back to the panel. You look just like the public utility at this
point. Tie the ground and the neutral together as you did by clamping to
earth ground, and tie the panel to earth ground and you've effectively done
the same thing. That of course, assumes that both of those ground rods were
indeed making good earth contact. Just being driven into the ground 8' does
not assure good earth ground. As odd as that sounds, when I was in the Air
Force they used to inspect our earth grounds every few months. Sometimes
the ground would read a high resistance and they'd pour water there to see
if that fixed it. Then of course, they'd schedule a follow up inspection to
make sure that the ground was indeed good. At home, nobody measures their
earth ground. We just sink rods and move on.

It's hard to guess in retrospect, what was wrong, but this really sounds
more like a fundamental wiring mistake - either in your cable or how you hit
the panel. Somehow you put a leg of voltage on the panel box. I'll just
about guarantee there was a wiring error in there somewhere.

--

-Mike-





Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
REPAIR 60 volt dc brushless hub scooter motor tracy Electronics Repair 1 October 3rd 07 12:55 AM
220 volt wiring question dlgeis Home Repair 10 July 28th 06 05:29 AM
190 Volt motor for phase converter. [email protected] Metalworking 2 August 17th 05 12:44 AM
12 volt motor controller Dominic Palazzola Electronics 4 May 21st 05 03:29 AM
240 volt wiring Charles Home Repair 11 December 30th 03 11:13 PM


All times are GMT +1. The time now is 10:45 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"