  #1   Report Post  
Jim Green
 
Posts: n/a
Default Kitchen circuit

My first post so please be kind!

Need to start new kitchen circuit wiring before 1st Jan. You all know why!

According to my (slightly old) DIY book I can use 2.5mm T&E with a 20amp
MCB for a maximum floor area of 20 square meters. My CU is in the
kitchen pantry so the total floor area the cable will cover is
definitely less that 20 square meters. On this circuit I plan to have:

Fridge
Dishwasher
Kettle
Microwave
Toaster
Cooker Hood

The book says unlimited sockets.

Now my question is purely theoretical as I am going to do a ring circuit
instead. But given the above why should I make it a ring circuit?


Jim
  #2   Report Post  
Lurch
 
Posts: n/a
Default

On Wed, 15 Dec 2004 10:55:03 +0000, Jim Green "nospam !!!" strung
together this:

Now my question is purely theoretical as I am going to do a ring circuit
instead. But given the above why should I make it a ring circuit?

Because you get an extra 10A for an extra length of 2.5mm. 20A might
sound ample but it isn't that much when you start putting the
dishwasher\kettle\toaster on.
It won't take much extra effort to make it a ring so I can't see any
reason not to, the only place I use a radial circuit is in a low load
area, such as bedroom or dining room.
--

SJW
Please reply to group or use 'usenet' in email subject
  #3   Report Post  
 
Posts: n/a
Default

Jim Green "nospam !!!" wrote:
My first post so please be kind!

Need to start new kitchen circuit wiring before 1st Jan. You all know why!

According to my (slightly old) DIY book I can use 2.5mm T&E with a 20amp
MCB for a maximum floor area of 20 square meters. My CU is in the


The current OSG gives a maximum recommended area of 50 sq meters.

kitchen pantry so the total floor area the cable will cover is
definitely less that 20 square meters. On this circuit I plan to have:

Fridge
Dishwasher
Kettle
Microwave
Toaster
Cooker Hood

The book says unlimited sockets.

Now my question is purely theoretical as I am going to do a ring circuit
instead. But given the above why should I make it a ring circuit?

No reason at all *except* that the loading is probably getting pretty
close to the 20 amps maximum on a 2.5sq mm radial. The kettle alone
takes 12 amps or thereabouts.

The recommendations in the OSG etc. are just that, recommendations.
For kitchens in particular the maximum load on the circuit (or
circuits) may mean that you need more circuits than would at first
seem reasonable.

That said I much prefer 2.5sq mm radial circuits to ring mains in many
cases. They have several advantages:-
No need to limit the number of spurs, the whole thing is (quite
legitimately) a multi-branched spur.

No need to check whether sockets are on spurs or 'on the ring'
when adding extra sockets.

Easier routing of cables as there's no necessity to make a ring.

Possibly more separation of different areas into separate
circuits.


I have a separate 20 amp MCB radials for the following:-

Study, lots of computers etc.

Daughter's bedroom, was an extension so added a circuit to supply
it.

Garage.

Other outdoor circuits.

If I was starting from scratch I think I'd go for all radial circuits
except possibly in the kitchen where the extra capacity of a ring
dedicated to the kitchen may be useful/necessary. (Though you could,
I suppose, go for a radial wired with 4sq mm)

--
Chris Green
  #4   Report Post  
Jim Green
 
Posts: n/a
Default

Lurch wrote:
On Wed, 15 Dec 2004 10:55:03 +0000, Jim Green "nospam !!!" strung
together this:


Now my question is purely theoretical as I am going to do a ring circuit
instead. But given the above why should I make it a ring circuit?


Because you get an extra 10A for an extra length of 2.5mm. 20A might
sound ample but it isn't that much when you start putting the
dishwasher\kettle\toaster on.
It won't take much extra effort to make it a ring so I can't see any
reason not to, the only place I use a radial circuit is in a low load
area, such as bedroom or dining room.


So unlimited sockets doesn't actually mean unlimited sockets. It means
unlimited sockets so long as the majority are turned off!


Jim
  #5   Report Post  
Jim Green
 
Posts: n/a
Default

Lurch wrote:
On Wed, 15 Dec 2004 10:55:03 +0000, Jim Green "nospam !!!" strung
together this:


Now my question is purely theoretical as I am going to do a ring circuit
instead. But given the above why should I make it a ring circuit?


Because you get an extra 10A for an extra length of 2.5mm. 20A might
sound ample but it isn't that much when you start putting the
dishwasher\kettle\toaster on.
It won't take much extra effort to make it a ring so I can't see any
reason not to, the only place I use a radial circuit is in a low load
area, such as bedroom or dining room.


So unlimited sockets doesn't actually mean unlimited sockets. It means
unlimited sockets so long as the majority are turned off!


Jim


  #6   Report Post  
Lurch
 
Posts: n/a
Default

On Wed, 15 Dec 2004 11:34:59 +0000, Jim Green "nospam !!!" strung
together this:

So unlimited sockets doesn't actually mean unlimited sockets. It means
unlimited sockets so long as the majority are turned off!

Yes, but that's the same with any circuit, ring or radial. The
limiting factor is the floor area\cable size\MCB size combination.
--

SJW
Please reply to group or use 'usenet' in email subject
  #7   Report Post  
Owain
 
Posts: n/a
Default

"Jim Green" wrote
| Now my question is purely theoretical as I am going to do a ring
| circuit instead. But given the above why should I make it a ring
| circuit?
| Because you get an extra 10A for an extra length of 2.5mm. 20A might
| sound ample but it isn't that much when you start putting the
| dishwasher\kettle\toaster on.
| So unlimited sockets doesn't actually mean unlimited sockets. It means
| unlimited sockets so long as the majority are turned off!

It means unlimited sockets assuming the majority are only used for low power
appliances - which is true in most situations. The modern kitchen is an
exception. When the 13A socket system was designed in the 1940s, deep
fryers, dishwashers, kW+ combi microwaves, etc, weren't really taken into
account :-)

You might want to run a separate, non-RCD, circuit for the fridge while
you're at it. And put in provision for an electric cooker at the same time.
Even if you don't use it, a future owner of the house might appreciate it.

Owain


  #8   Report Post  
Stefek Zaba
 
Posts: n/a
Default

Jim Green wrote:
My first post so please be kind!

Need to start new kitchen circuit wiring before 1st Jan. You all know why!

According to my (slightly old) DIY book I can use 2.5mm T&E with a 20amp
MCB for a maximum floor area of 20 square meters. My CU is in the
kitchen pantry so the total floor area the cable will cover is
definitely less that 20 square meters. On this circuit I plan to have:

Fridge
Dishwasher
Kettle
Microwave
Toaster
Cooker Hood

The book says unlimited sockets.

Now my question is purely theoretical as I am going to do a ring circuit
instead. But given the above why should I make it a ring circuit?


Jim


As I mentioned yesterday, the UK approach to wiring regs is based on
general principles and guidance on meeting them, rather than a rigid
code. The 20sqm-floor-area is an example - it's *guidance* for *typical*
loading, dating from some years ago, not a substitute for thought.

So, let's do "thought" instead. The loads you'll be putting on this
circuit aren't trivial, but they won't be drawing their full currents
for long periods. Specifically: dishwash - 1.5kW (say) while heating
water, but doesn't do it for more than 10 minutes at a time; kettle -
2kw or 2.5kw while on, doesn't stay on for more than 5 minutes at a
time; microwave - a tad under 1kW while it's on; toaster - not vast,
maybe 0.5kW while it's on. Cooker hood - minimal; fridge - 0.3kW or so,
coming on and off under thermostatic control.

So worst-case (all appliances drawing full load at once) there's 5 or
6kW; each 1kW is 4A (close enough) so that's 24A at peak. Since the
conditions under which that peak load's drawn won't last for more than a
few minutes, you could "get away" with a 20A-fused 2.5mmsq radial. And
hope you or the next householder doesn't add a washing-machine,
rice-cooker, breadmaker, or similar.

I wouldn't, though. I'd allow for "growth"/additional appliances later,
and would provide the kitchen with a dedicated 32A appliance circuit,
either as a ring with 2.5mmsq or a radial with 4mmsq. Unless there was a
long distance from kitchen to CU, the ring would be my default, as
2.5mmsq is very widely available (and full reels are always on "special
offer" at any trade counter ;-), and easier to work with (esp. if you
find it sensible to run a spur up to the FCU for the cooker hood -
stuffing 3 x 4mmsq into socket terminals and neatly into the back box
takes some doing). And for a 4mmsq radial with 32A protection, you
should really do the calcs to show the length is consistent with
tripping times...

Lastly, there's the RCD protection issue. The Regs say sockets which
it's "reasonably foreseeable" will supply outdoor appliances should have
RCD protection, and most interpretations say you should presume that all
ground-floor sockets are in such a category. (It's only a presumption in
an interpretation, mind: if, for example, the outside of the house has
several dedicated outdoor sockets at convenient locations, it's
reasonable to rebutt said presumption ;-) Perfectionists sometimes argue
for non-RCDed supplies to fridge, freezer, and maybe fixed appliances,
while providing RCD protection on sockets for the portable appliances -
kettle, mixer, and the like. For me, there's never quite so much
irreplaceable food in the fridge/freezer coupled with long periods away
from the house to want to separate the refrigeration supplies from the
others, but You May Know Different...

HTH - Stefek
  #9   Report Post  
Dave Plowman (News)
 
Posts: n/a
Default

In article ,
Jim Green nospam !!! wrote:
According to my (slightly old) DIY book I can use 2.5mm T&E with a 20amp
MCB for a maximum floor area of 20 square meters. My CU is in the
kitchen pantry so the total floor area the cable will cover is
definitely less that 20 square meters. On this circuit I plan to have:


Fridge
Dishwasher 13
Kettle 13
Microwave 05
Toaster 10
Cooker Hood

=======
41 amps

The book says unlimited sockets.


Yes. However not many sockets are fully loaded on most rings. A kitchen is
the one place in the average home where this might happen.

Now my question is purely theoretical as I am going to do a ring circuit
instead. But given the above why should I make it a ring circuit?


Think I've answered that. Unless you can guarantee you'll not use things
like the dishwasher, kettle and toaster all at once.

--
*Never miss a good chance to shut up.*

Dave Plowman London SW
To e-mail, change noise into sound.
  #10   Report Post  
John Rumm
 
Posts: n/a
Default

Jim Green wrote:

So unlimited sockets doesn't actually mean unlimited sockets. It means
unlimited sockets so long as the majority are turned off!


There is a concept called "diversity" that comes into play here. If you
think about it, a 30 amp circuit could be over loaded from a little as
three sockets feeding large 13A loads, however there may in fact be far
more than three socket outlets installed. Hence the designer of a
circuit will provide enough capacity to cope with typical and likely
loads, not the theoretical maximum load.

The wiring regs say a final ring circuit can cover an area of up to 100
sq m and have as many socket outlets as you want. However you need to
design what you actually install based on anticipated loading. Hence a
kitchen, which often has a high concentration of power hungry devices,
if often given a circuit all to itself.

--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/


  #11   Report Post  
Christian McArdle
 
Posts: n/a
Default

My CU is in the kitchen pantry so the total floor area the cable will
cover is definitely less that 20 square meters.


The square metre suggestions (which you have the wrong figure for) are only
appropriate for normal living spaces, not for kitchens. They are basically
about how much power you would need to heat the house in an emergency with
thermostatically controlled fan heaters. A kitchen, with many high powered
heating appliances requires far more capability.

You can't have all the appliances you suggest on a 20A circuit. You just
can't. It will probably trip frequently.

Also, some of the appliances should not be RCD protected, some could swing
both ways, but others should be RCD protected (not a requirement of the
regulations, just common sense).

For a kitchen, I would normally suggest 2 or 3 32A ring or radial circuits.
One ring should be RCD protected and provide all the socket outlets for
portable equipment such as kettles and non-built in microwaves. The other
ring should be not RCD protected and provide all the fixed major appliances,
such as laundry and refridgeration appliances. I would normally split this
into 2 and have an entirely separate 16A circuit just for refridgeration.
This is just to minimise the possibility of a trip on the freezer circuit
ruining all your food.

Christian.


Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Simple circuit to hold relay on after input falls John Electronics 11 November 1st 03 02:44 PM
Planit Millennium II [2 CDs] new !, and other Kitchen Design 3D programscheap software for fitted kitchen design (¯`·...ø¤°`°¤TEL4 ¤°`°¤....·´¯)tel2003@pathfinder. Woodworking 1 October 6th 03 02:22 PM
Planit Millennium II [2 CDs] new !, and other Kitchen Design 3D programscheap software for fitted kitchen design (¯`·...ø¤°`°¤TEL4 ¤°`°¤....·´¯)tel2003@pathfinder. Woodworking 0 October 6th 03 08:08 AM


All times are GMT +1. The time now is 04:46 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"