I am going to have to change out my boiler.
I had my whole house heating design done by underfloor heating company.

They sized boiler at 28kW ... (so currently have 30kW boiler)
Think it prudent to check sizing before I order replacement.

I know there are a plethora of €˜rad sizing programs, anybody able to recommend a good one (Stelrad, Castrads etc)

That would be pretty basic approach ... anybody aware of something that looks at whole house.
  #2   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 39,563
Default Heat loss calculations.

On 04/03/2021 23:05, Osprey wrote:
I am going to have to change out my boiler.
I had my whole house heating design done by underfloor heating company.

They sized boiler at 28kW ... (so currently have 30kW boiler)
Think it prudent to check sizing before I order replacement.

I know there are a plethora of €˜rad sizing programs, anybody able to recommend a good one (Stelrad, Castrads etc)

That would be pretty basic approach ... anybody aware of something that looks at whole house.


There are two things to decide first
1/. how much power you need to keep the house warm at the coldest
outside temp and wind you are likely to encounter
2/. How fast you need the place to warm up.

I sized my boiler at 1/. and forgot 2/.
This winter it was on 20 hours out of 24...

Basically an oversized boiler won't hurt - but an undersized one will
struggle

Fit the biggest that will physically fit


--
€œThose who can make you believe absurdities, can make you commit
atrocities.€

€• Voltaire, Questions sur les Miracles Ã* M. Claparede, Professeur de
Théologie Ã* Genève, par un Proposant: Ou Extrait de Diverses Lettres de
M. de Voltaire
  #3   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,159
Default Heat loss calculations.

On 04/03/2021 23:05, Osprey wrote:
I am going to have to change out my boiler.
I had my whole house heating design done by underfloor heating company.

They sized boiler at 28kW ... (so currently have 30kW boiler)
Think it prudent to check sizing before I order replacement.

I know there are a plethora of €˜rad sizing programs, anybody able to recommend a good one (Stelrad, Castrads etc)

That would be pretty basic approach ... anybody aware of something that looks at whole house.

Just fit a really big one.

Bill
  #4   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 45
Default Heat loss calculations.

On Thursday, 4 March 2021 at 23:05:31 UTC, Osprey wrote:
I am going to have to change out my boiler.
I had my whole house heating design done by underfloor heating company.

They sized boiler at 28kW ... (so currently have 30kW boiler)
Think it prudent to check sizing before I order replacement.

I'm going through the process of replacing my 26yr old boiler (14.5kW). Of the 4 quotes I have, one recommends an 18kW, two 21kW and one 24kW replacement. 4 bed detached house with loft conversion and 17 rads.
My preferred vendor had gone with 21kW (their working assumption was 1kW per rad plus 3 for the HW tank). When asked about the price difference between 21 and 24kW models it will be £50. The only further consideration for me is will the new boiler run from the 15mm supply or will it need an upgrade to 22mm. They will install the boiler and if it needs an upgraded supply they'll put in the 3m external run (£220).
  #5   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 6,938
Default Heat loss calculations.

In message , williamwright
writes
On 04/03/2021 23:05, Osprey wrote:
I am going to have to change out my boiler.
I had my whole house heating design done by underfloor heating company.
They sized boiler at 28kW ... (so currently have 30kW boiler)
Think it prudent to check sizing before I order replacement.
I know there are a plethora of €˜rad sizing programs, anybody
able to recommend a good one (Stelrad, Castrads etc)
That would be pretty basic approach ... anybody aware of something
that looks at whole house.

Just fit a really big one.


One point. I am not clear if the OP is using underfloor or radiators but
underfloor has a couple of limitations which may impact on boiler
choice.

The system has a maximum running temperature in the 40-50 deg. C range.
Excellent for operating a modern boiler in condensing mode but you still
need 65-70 for HW.

Underfloor manifolds may have temperature management to deal with this
but consideration might be given to choosing a boiler with dual
capabilities.

Our house is normally occupied 24 hrs so the underfloor system is
permanently on during the Winter months. Mostly insulated to current
standards, the consequence is that our 30kW boiler runs at the lowest of
5 possible burner settings but at a system temperature of 67 deg.C

--
Tim Lamb


  #6   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 25,191
Default Heat loss calculations.

On 04/03/2021 23:05, Osprey wrote:

I am going to have to change out my boiler.
I had my whole house heating design done by underfloor heating company.

They sized boiler at 28kW ... (so currently have 30kW boiler)
Think it prudent to check sizing before I order replacement.

I know there are a plethora of €˜rad sizing programs, anybody able to recommend a good one (Stelrad, Castrads etc)

That would be pretty basic approach ... anybody aware of something that looks at whole house.


There is the manual option:

https://web.archive.org/web/20150329...itle=Heat_loss



--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/
  #7   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 25,191
Default Heat loss calculations.

On 05/03/2021 07:50, Kevin H wrote:
On Thursday, 4 March 2021 at 23:05:31 UTC, Osprey wrote:
I am going to have to change out my boiler. I had my whole house
heating design done by underfloor heating company.

They sized boiler at 28kW ... (so currently have 30kW boiler) Think
it prudent to check sizing before I order replacement.

I'm going through the process of replacing my 26yr old boiler
(14.5kW). Of the 4 quotes I have, one recommends an 18kW, two 21kW
and one 24kW replacement.


Getting the "right" match of output power to demand is less important
these days since modern boilers have modulation - i.e. they don't have
to run flat out, and can vary their output (and hence gas rate) to match
the load.

Also there was a trend in the past to specify the heat input into the
boiler rather than output. So 14kW might only mean 10kW of output.
Whereas 18kW these days, probably means that as an actual output)

4 bed detached house with loft conversion
and 17 rads. My preferred vendor had gone with 21kW (their working
assumption was 1kW per rad plus 3 for the HW tank).


The 3kW for DHW is a bit suspect these days... it was probably about
right for an old C-plan system with a slow recovery cylinder, but for a
more modern setup with S or W plan and a fast recovery cylinder, the
cylinder will usually be able to absorb the full output of the boiler
for a sizeable part of the reheat (and hence do it in minutes rather
than hours)

When asked about
the price difference between 21 and 24kW models it will be £50. The
only further consideration for me is will the new boiler run from the
15mm supply or will it need an upgrade to 22mm. They will install the
boiler and if it needs an upgraded supply they'll put in the 3m
external run (£220).


Yup there is not much difference in pricing incrementally. In some cases
there won't even be any hardware changes to the boiler itself.



--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/
  #8   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 25,191
Default Heat loss calculations.

On 05/03/2021 08:48, Tim Lamb wrote:
In message , williamwright
writes
On 04/03/2021 23:05, Osprey wrote:
I am going to have to change out my boiler.
I had my whole house heating design done by underfloor heating company.
Â*They sized boiler at 28kW ... (so currently have 30kW boiler)
Think it prudent to check sizing before I order replacement.
Â*I know there are a plethora of €˜rad sizing programs, anybody able
to recommend a good one (Stelrad, Castrads etc)
Â*That would be pretty basic approach ... anybody aware of something
that looks at whole house.

Just fit a really big one.


One point. I am not clear if the OP is using underfloor or radiators but
underfloor has a couple of limitations which may impact on boiler choice.

The system has a maximum running temperature in the 40-50 deg. C range.
Excellent for operating a modern boiler in condensing mode but you still
need 65-70 for HW.


Yup, when researching my system some years ago it was not actually that
easy to find many boilers that supported split temperature operation to
allow different flow temps when running the rads from that used for DHW
recovery.

(I also wanted weather compensation, and multiple heating zones to make
it a bit more interesting)

Underfloor manifolds may have temperature management to deal with this
but consideration might be given to choosing a boiler with dual
capabilities.

Our house is normally occupied 24 hrs so the underfloor system is
permanently on during the Winter months. Mostly insulated to current
standards, the consequence is that our 30kW boiler runs at the lowest of
5 possible burner settings but at a system temperature of 67 deg.C


I find with weather compensation, in the milder bits of the winter, it
will run flow temps through the rads in the 40's for much of the time.
However it switches to 65/75 for DHW reheat (the higher temp on
Thursdays for an "sanitising" DHW heat to 70 rather than the normal 60.

--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/
  #9   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 937
Default Heat loss calculations.

On 05/03/2021 08:48, Tim Lamb wrote:


One point. I am not clear if the OP is using underfloor or radiators but
underfloor has a couple of limitations which may impact on boiler choice.

The system has a maximum running temperature in the 40-50 deg. C range.
Excellent for operating a modern boiler in condensing mode but you still
need 65-70 for HW.

Underfloor manifolds may have temperature management to deal with this
but consideration might be given to choosing a boiler with dual
capabilities.


It is UFH on both floors.
Only rads are heated towel rails in bathrooms (fed off DHR which is
mains pressure)

House is well insulated.

My Thermal store has Max temp of 60C though stat is low down, and
given the horizontal baffle .... top temp for DHW draw off is much higher.
Heating loop comes off low down so cannot exceed 60C (and likely a lot
less.

I gave a wrong figure in my OP .... I said Heating company stated boiler
requirement was output of 28kW ..... just checked it was only 16kW ...
in any event I have a current 30kW Baxi installed.

The boiler is fully modulating so combined with store it is working in
condensing mode. Run at about 60% of Max temp setting.
  #10   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,591
Default Heat loss calculations.

On 05/03/2021 02:27, The Natural Philosopher wrote:
On 04/03/2021 23:05, Osprey wrote:
I am going to have to change out my boiler.
I had my whole house heating design done by underfloor heating company.

They sized boiler at 28kW ... (so currently have 30kW boiler)
Think it prudent to check sizing before I order replacement.

I know there are a plethora of €˜rad sizing programs, anybody able to
recommend a good one (Stelrad, Castrads etc)

That would be pretty basic approach ... anybody aware of something
that looks at whole house.


There are two things to decide first
1/. how much power you need to keep the house warm at the coldest
outside temp and wind you are likely to encounter
2/. How fast you need the place to warm up.

I sized my boiler at 1/. and forgot 2/.
This winter it was on 20 hours out of 24...

Basically an oversized boiler won't hurt -Â* but an undersized one will
struggle

Fit the biggest that will physically fit


It's not as simple as that. Most boilers have a finite range of
modulation and the last thing you want is an idling boiler.

It is possible that the larger heat exchanger may well mean a more
efficient boiler at part loads, but I haven't seen any numbers
confirming this.


  #11   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 45
Default Heat loss calculations.

On Friday, 5 March 2021 at 12:02:00 UTC, John Rumm wrote:

Also there was a trend in the past to specify the heat input into the
boiler rather than output. So 14kW might only mean 10kW of output.
Whereas 18kW these days, probably means that as an actual output)


14kW is the output (18kW input). As you have said with modulation and similar pricing for 18/21/24kW boilers I can't see any reason not to go large (worst case having to upgrade to 22mm). Minimum output of the Greenstar 24Ri is 8kW vs 6kW for the 18Ri model which should not present any issues.

The 3kW for DHW is a bit suspect these days... it was probably about
right for an old C-plan system with a slow recovery cylinder, but for a
more modern setup with S or W plan and a fast recovery cylinder, the
cylinder will usually be able to absorb the full output of the boiler
for a sizeable part of the reheat (and hence do it in minutes rather
than hours)


We have a 250l Megaflow pressurised HW tank with a fast recovery coil. The extra output from the larger boiler should as you say help with quick re-heating. Still on a Y plan system which means all the output going through one 3 way valve. Wonder if moving to S plan would improve flow to the tank (or rads) to take advantage of the additional 10kW output that would be available?

  #12   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 25,191
Default Heat loss calculations.

On 05/03/2021 13:40, Kevin H wrote:
On Friday, 5 March 2021 at 12:02:00 UTC, John Rumm wrote:

Also there was a trend in the past to specify the heat input into
the boiler rather than output. So 14kW might only mean 10kW of
output. Whereas 18kW these days, probably means that as an actual
output)


14kW is the output (18kW input). As you have said with modulation and
similar pricing for 18/21/24kW boilers I can't see any reason not to
go large (worst case having to upgrade to 22mm). Minimum output of
the Greenstar 24Ri is 8kW vs 6kW for the 18Ri model which should not
present any issues.


IIRC, the minimum output on my Vaillant 624 (24kW) system boiler is
about 6kW

The 3kW for DHW is a bit suspect these days... it was probably
about right for an old C-plan system with a slow recovery cylinder,
but for a more modern setup with S or W plan and a fast recovery
cylinder, the cylinder will usually be able to absorb the full
output of the boiler for a sizeable part of the reheat (and hence
do it in minutes rather than hours)


We have a 250l Megaflow pressurised HW tank with a fast recovery
coil. The extra output from the larger boiler should as you say help
with quick re-heating. Still on a Y plan system which means all the
output going through one 3 way valve. Wonder if moving to S plan
would improve flow to the tank (or rads) to take advantage of the
additional 10kW output that would be available?


The 3 way is ok, but you probably want the timing set so that you don't
run CH and DHW at the same time - the the full output (or close to it)
of the boiler can go to the cylinder. I installed a 210L Unistor
unvented cylinder, and that can consume heat at up to about 22kW - so
the boiler will run close to flat out into that appart from the last 10
mins or so.



--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/
  #13   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 875
Default Heat loss calculations.

The Natural Philosopher explained :
Basically an oversized boiler won't hurt - but an undersized one will
struggle

Fit the biggest that will physically fit


Apart from in your pocket when you pay extra for it and again in poor
gas efficiency, because it is too big and constantly cycling, then the
extra wear and tear from cycling.
  #14   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 110
Default Heat loss calculations.

On 05/03/2021 16:04, Harry Bloomfield wrote:
The Natural Philosopher explained :
Basically an oversized boiler won't hurt -* but an undersized one will
struggle

Fit the biggest that will physically fit


Apart from in your pocket when you pay extra for it and again in poor
gas efficiency, because it is too big and constantly cycling, then the
extra wear and tear from cycling.

very true oversized boiler is not a good idea
  #15   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 6,213
Default Heat loss calculations.

On 05/03/2021 11:54, John Rumm wrote:
On 04/03/2021 23:05, Osprey wrote:

I am going to have to change out my boiler.
I had my whole house heating design done by underfloor heating company.

They sized boiler at 28kW ... (so currently have 30kW boiler)
Think it prudent to check sizing before I order replacement.

I know there are a plethora of €˜rad sizing programs, anybody able to
recommend a good one (Stelrad, Castrads etc)

That would be pretty basic approach ... anybody aware of something
that looks at whole house.


There is the manual option:

https://web.archive.org/web/20150329...itle=Heat_loss




I still have the Myson 1998 Heatloss application if anyone is
interested. It looks like it belongs on a Win 3.1 machine but
it seems to work (AFAIK) on a Win10 32 bit m/c

the zip file holds a file HeatLossManager98r105.exe


  #16   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 937
Default Heat loss calculations.

On 05/03/2021 19:18, Andrew wrote:


I still have the Myson 1998 Heatloss application if anyone is
interested. It looks like it belongs on a Win 3.1 machine but
it seems to work (AFAIK) on a Win10 32 bit m/c

the zip file holds a file HeatLossManager98r105.exe



Myson now have it on-line https://www.myson.co.uk/heat_loss_manager.htm
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Heat loss calculations tomahawk_pa38 UK diy 5 January 12th 07 12:43 PM
heat loss calculations - adding glass roof to kitchen larry UK diy 0 May 18th 06 09:58 AM
Heat Loss Calculations AndyHingston UK diy 10 January 18th 05 11:43 PM
heat exchanger calculations Ed Sirett UK diy 2 July 19th 03 12:49 AM
heat exchanger design calculations [repost] John Stumbles UK diy 6 July 17th 03 02:57 PM


All times are GMT +1. The time now is 07:44 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"