Default Cooker connection -

Hi,

1) Unless the manufacturer says otherwise, is it still considered the
"done thing" to use suitably sized T+E for the final connection to a
freestanding cooker, on the basis it doesn't move much?

Looking at a lumpy induction beast - 45A circuit, so 6mm2 at a pinch,
10mm2 probably better as the ambient temperature is likely to be "warm"
(=35C)



2) Some manufacturers specify H07 type cable. 6mm2 will suffice due to
higher permissible running temperature. But that's now a big fat 15mm
dia rubber cable.

Are there any cooker outlet plates that are more generous than normal,
because pretty sure 15mm isn't going to fit well in the average one.



If not, the only solution I can think of (apart from ignoring the
manufacturer) would be an external 45A joint with T+E back to the plate
and shoved behind a cupboard.

Or, possibly feeding the H07 through the 25mm conduit and jointing
directly in the isolator. Not so easy to disconnect and I'd need to make
a mask for the outlet box to protect the cable from the backbox edges.

Cheers,

Tim

  #2   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 8,019
Default Cooker connection -

On 29/01/2020 14:23, Tim Watts wrote:
Hi,

1) Unless the manufacturer says otherwise, is it still considered the
"done thing" to use suitably sized T+E for the final connection to a
freestanding cooker, on the basis it doesn't move much?

Looking at a lumpy induction beast - 45A circuit, so 6mm2 at a pinch,
10mm2 probably better as the ambient temperature is likely to be "warm"
(=35C)

That's what I have normally done (I forget the rating of my current
oven). Although ambient temperature can be high, it is relatively
accessible and easy to replace if it does degrade.



2) Some manufacturers specify H07 type cable. 6mm2 will suffice due to
higher permissible running temperature. But that's now a big fat 15mm
dia rubber cable.

Are there any cooker outlet plates that are more generous than normal,
because pretty sure 15mm isn't going to fit well in the average one.



If not, the only solution I can think of (apart from ignoring the
manufacturer) would be an external 45A joint with T+E back to the plate
and shoved behind a cupboard.

Or, possibly feeding the H07 through the 25mm conduit and jointing
directly in the isolator. Not so easy to disconnect and I'd need to make
a mask for the outlet box to protect the cable from the backbox edges.

Cheers,

Tim


  #3   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 296
Default Cooker connection -

Many many years ago, I wired up €ścooker€ť to the cooker side of a cooker & 13A socket affair. It was in a council house and €śthey€ť had installed the cooker switch and then there was a very beefy cable outlet behind the cooker.

My €ścooker€ť just required a 13A socket for its spark doobry and clock.

I was surprised to find the outlet behind the cooker
(Basically a back box, a hefty brass 3 pole in insulated chock block and a cover). Had no wire coming down from the switch unit.

From memory, I took a thin gauge flex from the cooker switch down the conduit to the connector and past the chunky choc bloc and wired straight into a surface mount 13A socket.

You could use chunky T&E down to the choc bloc (assuming these accessories are still sold) and then
Your 15mm dia stuff from there.

Cheers

Chris
  #4   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 9,066
Default Cooker connection -

On Wednesday, 29 January 2020 14:23:45 UTC, Tim Watts wrote:
Hi,

1) Unless the manufacturer says otherwise, is it still considered the
"done thing" to use suitably sized T+E for the final connection to a
freestanding cooker, on the basis it doesn't move much?

Looking at a lumpy induction beast - 45A circuit, so 6mm2 at a pinch,
10mm2 probably better as the ambient temperature is likely to be "warm"
(=35C)



2) Some manufacturers specify H07 type cable. 6mm2 will suffice due to
higher permissible running temperature. But that's now a big fat 15mm
dia rubber cable.

Are there any cooker outlet plates that are more generous than normal,
because pretty sure 15mm isn't going to fit well in the average one.



If not, the only solution I can think of (apart from ignoring the
manufacturer) would be an external 45A joint with T+E back to the plate
and shoved behind a cupboard.

Or, possibly feeding the H07 through the 25mm conduit and jointing
directly in the isolator. Not so easy to disconnect and I'd need to make
a mask for the outlet box to protect the cable from the backbox edges.




You're not likely to have everything on at once anyway.
  #5   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 4,564
Default Cooker connection -

On Wednesday, 29 January 2020 14:23:45 UTC, Tim Watts wrote:
Are there any cooker outlet plates that are more generous than normal,
because pretty sure 15mm isn't going to fit well in the average one.


Some kind soul wired my cooker point in 16mm2 cable.

Scolmore PRW217 45A says suitable for 10mm2 cable. Scolmore PRW218 is the surface pattress box if you need it.

Owain



  #7   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 63
Default Cooker connection -

On 29/01/2020 16:43, harry wrote:
On Wednesday, 29 January 2020 14:23:45 UTC, Tim Watts wrote:
Hi,

1) Unless the manufacturer says otherwise, is it still considered the
"done thing" to use suitably sized T+E for the final connection to a
freestanding cooker, on the basis it doesn't move much?

Looking at a lumpy induction beast - 45A circuit, so 6mm2 at a pinch,
10mm2 probably better as the ambient temperature is likely to be "warm"
(=35C)



2) Some manufacturers specify H07 type cable. 6mm2 will suffice due to
higher permissible running temperature. But that's now a big fat 15mm
dia rubber cable.

Are there any cooker outlet plates that are more generous than normal,
because pretty sure 15mm isn't going to fit well in the average one.



If not, the only solution I can think of (apart from ignoring the
manufacturer) would be an external 45A joint with T+E back to the plate
and shoved behind a cupboard.

Or, possibly feeding the H07 through the 25mm conduit and jointing
directly in the isolator. Not so easy to disconnect and I'd need to make
a mask for the outlet box to protect the cable from the backbox edges.




You're not likely to have everything on at once anyway.


Some hobs have a "feature" where you can restrict the maximum load
presented to match the capability of the supply, so permitting the use
of a lower rated cable, provided the MCB/RCBO is dimensioned to suit the
cable.




  #8   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 355
Default Cooker connection -

On 29/01/2020 17:26, wrote:
Scolmore PRW218


That's pretty chunky - thank you
  #9   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 12,364
Default Cooker connection -

On Wednesday, 29 January 2020 14:23:45 UTC, Tim Watts wrote:
Hi,

1) Unless the manufacturer says otherwise, is it still considered the
"done thing" to use suitably sized T+E for the final connection to a
freestanding cooker, on the basis it doesn't move much?

Looking at a lumpy induction beast - 45A circuit, so 6mm2 at a pinch,
10mm2 probably better as the ambient temperature is likely to be "warm"
(=35C)



2) Some manufacturers specify H07 type cable. 6mm2 will suffice due to
higher permissible running temperature. But that's now a big fat 15mm
dia rubber cable.

Are there any cooker outlet plates that are more generous than normal,
because pretty sure 15mm isn't going to fit well in the average one.



If not, the only solution I can think of (apart from ignoring the
manufacturer) would be an external 45A joint with T+E back to the plate
and shoved behind a cupboard.

Or, possibly feeding the H07 through the 25mm conduit and jointing
directly in the isolator. Not so easy to disconnect and I'd need to make
a mask for the outlet box to protect the cable from the backbox edges.

Cheers,

Tim


Look up 'diversity', you don't need anywhere near 15mm2.


NT
  #10   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,681
Default Cooker connection -

On 30/01/2020 13:47, wrote:
On Wednesday, 29 January 2020 14:23:45 UTC, Tim Watts wrote:
Hi,

1) Unless the manufacturer says otherwise, is it still considered the
"done thing" to use suitably sized T+E for the final connection to a
freestanding cooker, on the basis it doesn't move much?

Looking at a lumpy induction beast - 45A circuit, so 6mm2 at a pinch,
10mm2 probably better as the ambient temperature is likely to be "warm"
(=35C)



2) Some manufacturers specify H07 type cable. 6mm2 will suffice due to
higher permissible running temperature. But that's now a big fat 15mm
dia rubber cable.

Are there any cooker outlet plates that are more generous than normal,
because pretty sure 15mm isn't going to fit well in the average one.



If not, the only solution I can think of (apart from ignoring the
manufacturer) would be an external 45A joint with T+E back to the plate
and shoved behind a cupboard.

Or, possibly feeding the H07 through the 25mm conduit and jointing
directly in the isolator. Not so easy to disconnect and I'd need to make
a mask for the outlet box to protect the cable from the backbox edges.

Cheers,

Tim


Look up 'diversity', you don't need anywhere near 15mm2.


15mm is the /external/ diameter of the 6mm cable in mind for a 45A
supply; and I'd be wary of anything less than a 45A circuit without
knowing more about the cooker and the cook's habits. Some of the
all-electric stoves with induction hobs are heading for 20kW these days.
And I'm also minded to have some regard to the maker's instructions.


--
Robin
reply-to address is (intended to be) valid


  #11   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 5,061
Default Cooker connection -

In article , Robin
wrote:
On 30/01/2020 13:47, wrote:
On Wednesday, 29 January 2020 14:23:45 UTC, Tim Watts wrote:
Hi,

1) Unless the manufacturer says otherwise, is it still considered the
"done thing" to use suitably sized T+E for the final connection to a
freestanding cooker, on the basis it doesn't move much?

Looking at a lumpy induction beast - 45A circuit, so 6mm2 at a pinch,
10mm2 probably better as the ambient temperature is likely to be
"warm" (=35C)



2) Some manufacturers specify H07 type cable. 6mm2 will suffice due to
higher permissible running temperature. But that's now a big fat 15mm
dia rubber cable.

Are there any cooker outlet plates that are more generous than normal,
because pretty sure 15mm isn't going to fit well in the average one.



If not, the only solution I can think of (apart from ignoring the
manufacturer) would be an external 45A joint with T+E back to the
plate and shoved behind a cupboard.

Or, possibly feeding the H07 through the 25mm conduit and jointing
directly in the isolator. Not so easy to disconnect and I'd need to
make a mask for the outlet box to protect the cable from the backbox
edges.

Cheers,

Tim


Look up 'diversity', you don't need anywhere near 15mm2.


15mm is the /external/ diameter of the 6mm cable in mind for a 45A
supply; and I'd be wary of anything less than a 45A circuit without
knowing more about the cooker and the cook's habits. Some of the
all-electric stoves with induction hobs are heading for 20kW these days.
And I'm also minded to have some regard to the maker's instructions.


Cable is measured by conductor size, not outside diameter. When you say
15mm, electricians think of 76A rated cable.

--
from KT24 in Surrey, England
"I'd rather die of exhaustion than die of boredom" Thomas Carlyle
  #12   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,681
Default Cooker connection -

On 30/01/2020 17:39, charles wrote:
In article , Robin
wrote:
On 30/01/2020 13:47, wrote:
On Wednesday, 29 January 2020 14:23:45 UTC, Tim Watts wrote:
Hi,

1) Unless the manufacturer says otherwise, is it still considered the
"done thing" to use suitably sized T+E for the final connection to a
freestanding cooker, on the basis it doesn't move much?

Looking at a lumpy induction beast - 45A circuit, so 6mm2 at a pinch,
10mm2 probably better as the ambient temperature is likely to be
"warm" (=35C)



2) Some manufacturers specify H07 type cable. 6mm2 will suffice due to
higher permissible running temperature. But that's now a big fat 15mm
dia rubber cable.

Are there any cooker outlet plates that are more generous than normal,
because pretty sure 15mm isn't going to fit well in the average one.



If not, the only solution I can think of (apart from ignoring the
manufacturer) would be an external 45A joint with T+E back to the
plate and shoved behind a cupboard.

Or, possibly feeding the H07 through the 25mm conduit and jointing
directly in the isolator. Not so easy to disconnect and I'd need to
make a mask for the outlet box to protect the cable from the backbox
edges.

Cheers,

Tim

Look up 'diversity', you don't need anywhere near 15mm2.


15mm is the /external/ diameter of the 6mm cable in mind for a 45A
supply; and I'd be wary of anything less than a 45A circuit without
knowing more about the cooker and the cook's habits. Some of the
all-electric stoves with induction hobs are heading for 20kW these days.
And I'm also minded to have some regard to the maker's instructions.


Cable is measured by conductor size, not outside diameter. When you say
15mm, electricians think of 76A rated cable.


The only reference to 15mm was in "a big fat 15mm dia rubber cable"
which seems to be both fair and unambiguous when the OP was looking for
a suitable cable outlet.

--
Robin
reply-to address is (intended to be) valid
  #13   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 355
Default Cooker connection -

On 30/01/2020 13:47, wrote:

Look up 'diversity', you don't need anywhere near 15mm2.


NT


6mm2, 15mm diameter...
  #14   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 355
Default Cooker connection -

On 30/01/2020 17:39, charles wrote:

Cable is measured by conductor size, not outside diameter. When you say
15mm, electricians think of 76A rated cable.


Yes I know that.

However 15mm OD is the major factor when it comes to "will it fit in
this cooker connection plate" as the latter are deisgned with flat cable
in mind
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
28mm connection - hose connection asalcedo UK diy 0 September 26th 08 07:14 PM
Cooker connection ... Arfa Daily UK diy 9 June 12th 08 03:15 PM
Gas cooker connection Mo UK diy 23 May 6th 07 12:42 PM
Bayonet gas cooker connection Grumps UK diy 4 December 5th 05 09:28 PM
Electric cooker connection petek UK diy 8 March 8th 05 11:23 PM


All times are GMT +1. The time now is 08:41 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"