Does a CU on a sub-main need an integral isolator switch?
A situation that I can't found an answer to ...
There is a DP isolator before the main CU (which has an isolator). This CU will be fitted with a 50A MCB feeding a 20m sub-main to a second CU elsewhere in the house. There are therefore 3 ways to isolate the sub-main. Is there a requirement for the second CU (at the end of the sub-main) to have an integral isolator switch? |
#2
Posted to uk.d-i-y
|
|||
|
|||
Does a CU on a sub-main need an integral isolator switch?
wrote:
A situation that I can't found an answer to ... There is a DP isolator before the main CU (which has an isolator). This CU will be fitted with a 50A MCB feeding a 20m sub-main to a second CU elsewhere in the house. There are therefore 3 ways to isolate the sub-main. Is there a requirement for the second CU (at the end of the sub-main) to have an integral isolator switch? I've no idea about the regulatory position, but I'd certainly fit an isolating switch unless there was an important reason (such has not having the extra 2" where I wanted to put the CU) not to. If just for convenience. -- Roger Hayter |
#3
Posted to uk.d-i-y
|
|||
|
|||
Does a CU on a sub-main need an integral isolator switch?
On Wednesday, 13 February 2019 12:18:07 UTC, wrote:
Is there a requirement for the second CU (at the end of the sub-main) to have an integral isolator switch? It will have an integral main switch. If it doesn't have a main switch it's not a consumer unit, it's a distribution board. Owain |
#4
Posted to uk.d-i-y
|
|||
|
|||
Does a CU on a sub-main need an integral isolator switch?
|
#6
Posted to uk.d-i-y
|
|||
|
|||
Does a CU on a sub-main need an integral isolator switch?
On Thursday, 14 February 2019 11:15:49 UTC, John Rumm wrote:
2) Practical, you need some way to terminate the live of your incoming sub main on the the live bus bar(s) of the CU. The live bus bar has no terminals of its own, and relies on those of the main switch to connect the incoming feed to the bus bar. Squidging the wire under the busbar in one of the MCB terminals would be really rough wouldn't it... Owain |
#7
Posted to uk.d-i-y
|
|||
|
|||
Does a CU on a sub-main need an integral isolator switch?
John Rumm wrote:
On 13/02/2019 12:18, wrote: A situation that I can't found an answer to ... There is a DP isolator before the main CU (which has an isolator). This CU will be fitted with a 50A MCB feeding a 20m sub-main to a second CU elsewhere in the house. There are therefore 3 ways to isolate the sub-main. Is there a requirement for the second CU (at the end of the sub-main) to have an integral isolator switch? If its a CU and not a distribution board, then you will need a main switch. There are two main reasons that spring to mind: 1) Expectation - from a user's PoV they expect there to be a main switch present. A guest / future owner etc will not have the background knowledge to know its a sub CU fed from another, and might be looking for a way of killing the power in an emergency. 2) Practical, you need some way to terminate the live of your incoming sub main on the the live bus bar(s) of the CU. The live bus bar has no terminals of its own, and relies on those of the main switch to connect the incoming feed to the bus bar. I had been wondering the same question. And, now that you mention it, your point 2) is pretty conclusive. It would be a shame for an amateur such as myself to discover one had insufficient ways to fit a main switch and and no other way of putting the thing together *after* ordering the parts! -- Roger Hayter |
#8
Posted to uk.d-i-y
|
|||
|
|||
Does a CU on a sub-main need an integral isolator switch?
On 14/02/2019 11:15, John Rumm wrote:
On 13/02/2019 12:18, wrote: A situation that I can't found an answer to ... There is a DP isolator before the main CU (which has an isolator). This CU will be fitted with a 50A MCB feeding a 20m sub-main to a second CU elsewhere in the house. There are therefore 3 ways to isolate the sub-main. Is there a requirement for the second CU (at the end of the sub-main) to have an integral isolator switch? If its a CU and not a distribution board, then you will need a main I thought that, in a domestic situation, the terms "distribution board" and "CU" were interchangeable ... switch. There are two main reasons that spring to mind: 1) Expectation - from a user's PoV they expect there to be a main switch present. A guest / future owner etc will not have the background knowledge to know its a sub CU fed from another, and might be looking for a way of killing the power in an emergency. It's quite a large house and the main DP isolator (after the meter) will be both more easily accessed than this sub-board and will isolate the whole electrical system, rather than just the one segment. 2) Practical, you need some way to terminate the live of your incoming sub main on the the live bus bar(s) of the CU. The live bus bar has no terminals of its own, and relies on those of the main switch to connect the incoming feed to the bus bar. I'd planned to terminate the cable in crimped tags, bolted onto the busbar. It's only a question of spec'ing a slightly larger CU (12 way rather than 10 way) so I'll keep an isolator. Thanks, as always, for taking the time. The next question is which manufacturer: Hager, MK, BG, Wylex ... ? At the moment I'm leaning towards Hager or MK because of space for RCBOs and ease of getting parts. Are there any good deals out there? |
#9
Posted to uk.d-i-y
|
|||
|
|||
Does a CU on a sub-main need an integral isolator switch?
On Thursday, 14 February 2019 12:19:37 UTC, wrote:
On Thursday, 14 February 2019 11:15:49 UTC, John Rumm wrote: 2) Practical, you need some way to terminate the live of your incoming sub main on the the live bus bar(s) of the CU. The live bus bar has no terminals of its own, and relies on those of the main switch to connect the incoming feed to the bus bar. Squidging the wire under the busbar in one of the MCB terminals would be really rough wouldn't it... Owain I'm imagining someone discovering the cable is too thick to do that & splitting the strands over 3 MCBs NT |
#10
Posted to uk.d-i-y
|
|||
|
|||
Does a CU on a sub-main need an integral isolator switch?
|
#11
Posted to uk.d-i-y
|
|||
|
|||
Does a CU on a sub-main need an integral isolator switch?
|
#12
Posted to uk.d-i-y
|
|||
|
|||
Does a CU on a sub-main need an integral isolator switch?
On 15/02/2019 13:12, wrote:
On 14/02/2019 11:15, John Rumm wrote: On 13/02/2019 12:18, wrote: A situation that I can't found an answer to ... There is a DP isolator before the main CU (which has an isolator). This CU will be fitted with a 50A MCB feeding a 20m sub-main to a second CU elsewhere in the house. There are therefore 3 ways to isolate the sub-main. Is there a requirement for the second CU (at the end of the sub-main) to have an integral isolator switch? If its a CU and not a distribution board, then you will need a main I thought that, in a domestic situation, the terms "distribution board" and "CU" were interchangeable ... switch. There are two main reasons that spring to mind: 1) Expectation - from a user's PoV they expect there to be a main switch present. A guest / future owner etc will not have the background knowledge to know its a sub CU fed from another, and might be looking for a way of killing the power in an emergency. It's quite a large house and the main DP isolator (after the meter) will be both more easily accessed than this sub-board and will isolate the whole electrical system, rather than just the one segment. 2) Practical, you need some way to terminate the live of your incoming sub main on the the live bus bar(s) of the CU. The live bus bar has no terminals of its own, and relies on those of the main switch to connect the incoming feed to the bus bar. I'd planned to terminate the cable in crimped tags, bolted onto the busbar. It's only a question of spec'ing a slightly larger CU (12 way rather than 10 way) so I'll keep an isolator. Thanks, as always, for taking the time. The next question is which manufacturer: Hager, MK, BG, Wylex ... ? At the moment I'm leaning towards Hager or MK because of space for RCBOs and ease of getting parts. Are there any good deals out there? https://www.hager.co.uk/news-exhibit...rcbo/72306.htm are good. I just called one of my wholesalers and I would pay £27 inc VAT for them. TLC do them for £28.14 inc VAT. If you want cheaper then CPC do ProElec RCBOs for about £18 and a main switch CU with 19 spare ways for £50. I have fitted ProElec and was happy with it. And the mainswitch need not be part of the board. Although personally it would IMHO be silly not to buy one without a main switch. -- Adam |
#13
Posted to uk.d-i-y
|
|||
|
|||
Does a CU on a sub-main need an integral isolator switch?
On 16/02/2019 09:40, ARW wrote:
https://www.hager.co.uk/news-exhibit...rcbo/72306.htm are good. I just called one of my wholesalers and I would pay £27 inc VAT for them. TLC do them for £28.14 inc VAT. If you want cheaper then CPC do ProElec RCBOs for about £18 and a main switch CU with 19 spare ways for £50. I have fitted ProElec and was happy with it. And the mainswitch need not be part of the board. Although personally it would IMHO be silly not to buy one without a main switch. Any views pl. on the Contactum range which I saw from TLC's email last week they are doing for £16 incl VAT? https://www.tlc-direct.co.uk/Products/CPDD141MS.html Asking only 'cos I've long thought I ought to replace the CU with all RCBOs "when their price comes down" and wonder if I've now run out of excuse. -- Robin reply-to address is (intended to be) valid |
#14
Posted to uk.d-i-y
|
|||
|
|||
Does a CU on a sub-main need an integral isolator switch?
On 16/02/2019 10:03, Robin wrote:
On 16/02/2019 09:40, ARW wrote: https://www.hager.co.uk/news-exhibit...rcbo/72306.htm are good. I just called one of my wholesalers and I would pay £27 inc VAT for them. TLC do them for £28.14 inc VAT. If you want cheaper then CPC do ProElec RCBOs for about £18 and a main switch CU with 19 spare ways for £50. I have fitted ProElec and was happy with it. And the mainswitch need not be part of the board. Although personally it would IMHO be silly not to buy one without a main switch. Any views pl. on the Contactum range which I saw from TLC's email last week they are doing for £16 incl VAT? https://www.tlc-direct.co.uk/Products/CPDD141MS.html Asking only 'cos I've long thought I ought to replace the CU with all RCBOs "when their price comes down" and wonder if I've now run out of excuse. I would say avoid. Now I had forgotten about TLC when looking for prices. TLC are doing the BG reduced height RCBOs for £15.72 I have never had a problem with BG CUs. -- Adam |
#15
Posted to uk.d-i-y
|
|||
|
|||
Does a CU on a sub-main need an integral isolator switch?
On 16/02/2019 09:40, ARW wrote:
https://www.hager.co.uk/news-exhibit...rcbo/72306.htm are good. I just called one of my wholesalers and I would pay £27 inc VAT for them. TLC do them for £28.14 inc VAT. Sweet... -- Email does not work |
#16
Posted to uk.d-i-y
|
|||
|
|||
Does a CU on a sub-main need an integral isolator switch?
On 16/02/2019 10:40, ARW wrote:
On 16/02/2019 10:03, Robin wrote: On 16/02/2019 09:40, ARW wrote: https://www.hager.co.uk/news-exhibit...rcbo/72306.htm are good. I just called one of my wholesalers and I would pay £27 inc VAT for them. TLC do them for £28.14 inc VAT. If you want cheaper then CPC do ProElec RCBOs for about £18 and a main switch CU with 19 spare ways for £50. I have fitted ProElec and was happy with it. And the mainswitch need not be part of the board. Although personally it would IMHO be silly not to buy one without a main switch. Any views pl. on the Contactum range which I saw from TLC's email last week they are doing for £16 incl VAT? https://www.tlc-direct.co.uk/Products/CPDD141MS.html Asking only 'cos I've long thought I ought to replace the CU with all RCBOs "when their price comes down" and wonder if I've now run out of excuse. I would say avoid. Now I had forgotten about TLC when looking for prices. TLC are doing the BG reduced height RCBOs for £15.72 I have never had a problem with BG CUs. ta -- Robin reply-to address is (intended to be) valid |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Grounding conductor to sub panel from main panel & "main groundingconductor" | Home Repair | |||
Extractor fan isolator switch. | UK diy | |||
Extractor fans - is the double pole isolator switch mandatory? | UK diy | |||
isolator switch & immersion heater timer | UK diy | |||
Positioning of bathroom fan isolator switch | UK diy |