UK diy (uk.d-i-y) For the discussion of all topics related to diy (do-it-yourself) in the UK. All levels of experience and proficency are welcome to join in to ask questions or offer solutions.

Reply
 
LinkBack Thread Tools Search this Thread Display Modes
  #1   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 937
Default Anybody created a pre-heat DHW cylinder

My solar PV system, produces a significant amount of unused electricity.

I have a Thermal store based heating system .... providing mains
pressure DHW off one heat exchanger and underfloor heating from the
other ... the water content of store being circulated around the boiler
when heat demand is called.

A consideration is to install a 2nd hot water cylinder, and use the
excess PV power to feed an immersion heater .... creating a large store
of heat.

Any call for DHW will result in thye incoming cold mains being
pre-heated by this store .... when store is depleted, the normal heat
exchanger function within the Thermal store would maintain DHW supply,
topped up if necessary by boiler.


I did ask a few weeks back about just using Solar PV excess direct into
Thermal store immersion, but as this is kept 'at temp' don't really see
a way to easily do that.

This pre-heat method would seem a suitable alternative ... and using the
mass of the water as an energy store.
  #2   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 5,168
Default Anybody created a pre-heat DHW cylinder

On 03/11/2015 18:03, rick wrote:

I did ask a few weeks back about just using Solar PV excess direct into
Thermal store immersion, but as this is kept 'at temp' don't really see
a way to easily do that.


You need to reprogram it so the heat store isn't kept at full temp to
make space for the solar energy, or fit a new immersion at a lower point
so the solar energy can heat the bottom of the tank.

You could export some of the energy so others benefit.
  #3   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 39,563
Default Anybody created a pre-heat DHW cylinder

On 03/11/15 18:03, rick wrote:
My solar PV system, produces a significant amount of unused electricity.


Dont worry, it wont last. Winter is nearly here.



--
the biggest threat to humanity comes from socialism, which has utterly
diverted our attention away from what really matters to our existential
survival, to indulging in navel gazing and faux moral investigations
into what the world ought to be, whilst we fail utterly to deal with
what it actually is.
  #4   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 12,364
Default Anybody created a pre-heat DHW cylinder

On Tuesday, 3 November 2015 18:04:02 UTC, rick wrote:
My solar PV system, produces a significant amount of unused electricity.

I have a Thermal store based heating system .... providing mains
pressure DHW off one heat exchanger and underfloor heating from the
other ... the water content of store being circulated around the boiler
when heat demand is called.

A consideration is to install a 2nd hot water cylinder, and use the
excess PV power to feed an immersion heater .... creating a large store
of heat.

Any call for DHW will result in thye incoming cold mains being
pre-heated by this store .... when store is depleted, the normal heat
exchanger function within the Thermal store would maintain DHW supply,
topped up if necessary by boiler.


I did ask a few weeks back about just using Solar PV excess direct into
Thermal store immersion, but as this is kept 'at temp' don't really see
a way to easily do that.

This pre-heat method would seem a suitable alternative ... and using the
mass of the water as an energy store.


I haven't run the numbers but expect you'd be better off all round to feed the electric heat into the existing tank. The water wil go above set point, and not need other heat sources until the temp is back down again.


NT
  #5   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 9,066
Default Anybody created a pre-heat DHW cylinder

On Tuesday, 3 November 2015 18:04:02 UTC, rick wrote:
My solar PV system, produces a significant amount of unused electricity.

I have a Thermal store based heating system .... providing mains
pressure DHW off one heat exchanger and underfloor heating from the
other ... the water content of store being circulated around the boiler
when heat demand is called.

A consideration is to install a 2nd hot water cylinder, and use the
excess PV power to feed an immersion heater .... creating a large store
of heat.

Any call for DHW will result in thye incoming cold mains being
pre-heated by this store .... when store is depleted, the normal heat
exchanger function within the Thermal store would maintain DHW supply,
topped up if necessary by boiler.


I did ask a few weeks back about just using Solar PV excess direct into
Thermal store immersion, but as this is kept 'at temp' don't really see
a way to easily do that.

This pre-heat method would seem a suitable alternative ... and using the
mass of the water as an energy store.


Not worth bothering about.
There will be no heat when you need it most.
Also heat leaks away from small heat stores before you can use it.
Small thermal heat stores are a complete waste of space/money.


  #6   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 95
Default Anybody created a pre-heat DHW cylinder

A typical sub 4kw domestic array will only be generating a few kwh units each day during the winter months so economically a pointless waste of time, money and effort. You will be better doing your cooking or washing during the daytime, maybe with a slow cooker and timer.
  #8   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 937
Default Anybody created a pre-heat DHW cylinder

On 03/11/2015 18:25, dennis@home wrote:
On 03/11/2015 18:03, rick wrote:

I did ask a few weeks back about just using Solar PV excess direct into
Thermal store immersion, but as this is kept 'at temp' don't really see
a way to easily do that.


You need to reprogram it so the heat store isn't kept at full temp to
make space for the solar energy, or fit a new immersion at a lower point
so the solar energy can heat the bottom of the tank.

You could export some of the energy so others benefit.



reprogram what ? ......... there is a simple standard thermostat ...
set to 60 degrees.

I could set it to 450 and immersion stat to 60 but then tank would not
get warm enough when there is no PV power


  #9   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 937
Default Anybody created a pre-heat DHW cylinder

On 03/11/2015 19:18, The Natural Philosopher wrote:
On 03/11/15 18:03, rick wrote:
My solar PV system, produces a significant amount of unused electricity.


Dont worry, it wont last. Winter is nearly here.



today is a particularly damp, grey & gloomy day ... just looked it
produced 2.2kWh today
  #11   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 937
Default Anybody created a pre-heat DHW cylinder

On 04/11/2015 17:13, Alan Braggins wrote:


I've considered doing something similar. My thermal store is two cylinders
in parallel, with both DHW and UFH being heated by them. But the remaining
failed old Nu-Heat UFH is being replaced by radiators



How did your Nu-Heat fail ? ............ mine is Nu-Heat and runs really
well.
Although I went wit the pex system not their earlier triple pipe rubber
system.
  #13   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 9,066
Default Anybody created a pre-heat DHW cylinder

On Wednesday, 4 November 2015 18:02:40 UTC, rick wrote:
On 03/11/2015 19:18, The Natural Philosopher wrote:
On 03/11/15 18:03, rick wrote:
My solar PV system, produces a significant amount of unused electricity.


Dont worry, it wont last. Winter is nearly here.



today is a particularly damp, grey & gloomy day ... just looked it
produced 2.2kWh today


Yep .
Both of mine did 2.1 each.
  #14   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 9,066
Default Anybody created a pre-heat DHW cylinder

On Wednesday, 4 November 2015 17:13:53 UTC, Alan Braggins wrote:
In article , wrote:
A typical sub 4kw domestic array will only be generating a few kwh units each day during the winter months


He could be planning it now to use next summer.



Tch.
You don't need any heat in Summer
  #15   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 5,168
Default Anybody created a pre-heat DHW cylinder

On 04/11/2015 17:59, rick wrote:
On 03/11/2015 18:25, dennis@home wrote:
On 03/11/2015 18:03, rick wrote:

I did ask a few weeks back about just using Solar PV excess direct into
Thermal store immersion, but as this is kept 'at temp' don't really see
a way to easily do that.


You need to reprogram it so the heat store isn't kept at full temp to
make space for the solar energy, or fit a new immersion at a lower point
so the solar energy can heat the bottom of the tank.

You could export some of the energy so others benefit.



reprogram what ? ......... there is a simple standard thermostat ...
set to 60 degrees.

I could set it to 450 and immersion stat to 60 but then tank would not
get warm enough when there is no PV power



No timer so you can use solar during the day and switch in other sources
when its going dark?


  #17   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 12,364
Default Anybody created a pre-heat DHW cylinder

On Wednesday, 4 November 2015 18:04:32 UTC, rick wrote:
On 03/11/2015 22:47, nt wrote:


I haven't run the numbers but expect you'd be better off all round to feed

the electric heat into the existing tank. The water wil go above set point,
and not need other heat sources until the temp is back down again.


Can't do that ... max temp I can have store get to is 60 degree .......
any higher and you risk damage to underfloor heating pipes.


If your ufh runs off a bottom coil you can normally heat the water above it to over 60. Otherwise as you say it's a preheat tank. But a preheat tank brings a few issues:
1. water staying in the unsafe temp zone - ok for most things but not ideal for showers
2. Lots more area for heat loss, but in fairness a foot or 2 of insulation is pretty cheap.
3. Upfront costs that arent there with feeding the power into the main HW cyl.


NT
  #20   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 2,024
Default Anybody created a pre-heat DHW cylinder

On Tue, 3 Nov 2015 18:03:55 +0000, rick
wrote:


This pre-heat method would seem a suitable alternative ... and using the
mass of the water as an energy store.


I had a similar installation many years ago but using solar water as
the pre-heating. The solar tubes warmed a heavily insulated cylinder
in the attic. Incoming mains water went first to the solar cylinder
and then to the second cylinder heated by a gas boiler. It was
interesting to play with but didn't achieve much. In the summer it
provided most of the hot water, in the winter sod all.



  #21   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 12,364
Default Anybody created a pre-heat DHW cylinder

On Wednesday, 4 November 2015 21:35:08 UTC, rick wrote:
On 04/11/2015 19:48, dennis@home wrote:
On 04/11/2015 18:04, rick wrote:
On 03/11/2015 22:47, nt wrote:


I haven't run the numbers but expect you'd be better off all round to
feed
the electric heat into the existing tank. The water wil go above set
point,
and not need other heat sources until the temp is back down again.


Can't do that ... max temp I can have store get to is 60 degree ........
any higher and you risk damage to underfloor heating pipes.


They should have a mixing valve to prevent the floors getting too hot.


No the design has a mixing valve on the DHW take off, but the main feeds
off for the UFH loop is not via a mixing valve ... the main tank stat
prevents it going over 60 degree.


This extra electricity comes at times of high sun output, ie when ufh is not usually being used. So in principle you could add a stat that stops the ufh pump coming on when the cyl is too hot for it. Then you get the benefit of your extra leccy without a bunch of extra costs.


NT
  #22   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 14,085
Default Anybody created a pre-heat DHW cylinder

On Wed, 4 Nov 2015 21:35:01 +0000, rick wrote:

Can't do that ... max temp I can have store get to is 60 degree
any higher and you risk damage to underfloor heating pipes.


They should have a mixing valve to prevent the floors getting too

hot.

No the design has a mixing valve on the DHW take off, but the main feeds
off for the UFH loop is not via a mixing valve ... the main tank stat
prevents it going over 60 degree.


Strikes me as bad design then. Can't you fit a mixing valve between
the flow and return of the floor loop such that the pump circulates
via the valve when the temp approaches 60 C.

--
Cheers
Dave.



  #23   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 12,364
Default Anybody created a pre-heat DHW cylinder

On Wednesday, 4 November 2015 22:43:06 UTC, Dave Liquorice wrote:
On Wed, 4 Nov 2015 21:35:01 +0000, rick wrote:

Can't do that ... max temp I can have store get to is 60 degree
any higher and you risk damage to underfloor heating pipes.

They should have a mixing valve to prevent the floors getting too

hot.

No the design has a mixing valve on the DHW take off, but the main feeds
off for the UFH loop is not via a mixing valve ... the main tank stat
prevents it going over 60 degree.


Strikes me as bad design then. Can't you fit a mixing valve between
the flow and return of the floor loop such that the pump circulates
via the valve when the temp approaches 60 C.


60 seems unusually high for ufh


NT
  #24   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 14,085
Default Anybody created a pre-heat DHW cylinder

On Wed, 4 Nov 2015 18:36:35 -0800 (PST), wrote:

Can't do that ... max temp I can have store get to is 60 degree


any higher and you risk damage to underfloor heating pipes.

They should have a mixing valve to prevent the floors getting

too
hot.

No the design has a mixing valve on the DHW take off, but the

main
feeds off for the UFH loop is not via a mixing valve ... the main

tank
stat prevents it going over 60 degree.


Strikes me as bad design then. Can't you fit a mixing valve

between
the flow and return of the floor loop such that the pump

circulates
via the valve when the temp approaches 60 C.


60 seems unusually high for ufh


Only quoting the OP and that's the maximum to avoid damage. What
ever, to me not having some regulation of the UFH loop temperature
independant of the store temp isn't right. Limiting the store to 60 C
reduces the amount of energy it can store by about 30%.

And a store with a 60 C max must struggle to provide a decent
quantity of DHW unless the OP has that mixer valve set to the
pathtically low "safe" 43 C. Ours is set at 53 C or there abouts, hot
as in you can put your hand in it but don't want to keep it there for
more than a few tens of seconds hot. The store middle temperature is
normally about 70 to 80 C, top can get to 90+ if I miss judge the
weather and get a good burn going in the stove without the heating
coming on enough. It can deliver a bath of DHW at 53 C and 15 to
20l/min before it starts to run out heat.

--
Cheers
Dave.



  #25   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 937
Default Anybody created a pre-heat DHW cylinder

On 04/11/2015 22:19, dennis@home wrote:


60c is too high for underfloor heating IMO.
If someone collapsed on a floor that could get that hot they could die.
If it had a mixer then that would limit the temperature and allow more
heat to be stored by allowing a higher temp in the thermal store.



Agree ... but floor will never get to 60 ... each room has its own zone
with digital set back temperature control.
The max temp of water in cylinder is 60 .... there is heat exchanger
coil, with 28mm feeds to manifolds ... then individual zones .... so too
many losses to get as high as 60.

It probably would be nice to have a mixer on heating loop, wasn't in the
design ... I could retrofit.
Need to check if tank is happy being run hotter - problem will be
Nu-Heat state design temp of cylinder in 60 .... they will be unlikely
to confirm it can be run hotter - I will ask.
Without some statement that tank can be run higher my risk would be too
high to just 'chance it'


  #26   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 937
Default Anybody created a pre-heat DHW cylinder

On 05/11/2015 09:18, Dave Liquorice wrote:

Only quoting the OP and that's the maximum to avoid damage. What
ever, to me not having some regulation of the UFH loop temperature
independant of the store temp isn't right. Limiting the store to 60 C
reduces the amount of energy it can store by about 30%.

And a store with a 60 C max must struggle to provide a decent
quantity of DHW unless the OP has that mixer valve set to the
pathtically low "safe" 43 C. Ours is set at 53 C or there abouts, hot
as in you can put your hand in it but don't want to keep it there for
more than a few tens of seconds hot. The store middle temperature is
normally about 70 to 80 C, top can get to 90+ if I miss judge the
weather and get a good burn going in the stove without the heating
coming on enough. It can deliver a bath of DHW at 53 C and 15 to
20l/min before it starts to run out heat.


The regulation is done by the stat keeping tank at 60 ........ you may
deem that not enough but seems to work fine.
Stat is fitted in lower 1/3 of store.

There is never any shortage of ho****er ... this is set to 53 deg ...
and runs at full mains pressure ... on 22mm pipes.

You can run it full flow to fill a bath and still running hot when bath
is full.

Nu-Heat advise the high efficiency cross flow heat exchanger (rather
than a coil)allows this.

Flow is from mains pressure of 3.5bar at 25L/min .. and has never
once run out of ho****er when in use.
  #28   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 569
Default Anybody created a pre-heat DHW cylinder

In article , rick wrote:
On 04/11/2015 17:13, Alan Braggins wrote:


I've considered doing something similar. My thermal store is two cylinders
in parallel, with both DHW and UFH being heated by them. But the remaining
failed old Nu-Heat UFH is being replaced by radiators


How did your Nu-Heat fail ? ............ mine is Nu-Heat and runs really
well.
Although I went wit the pex system not their earlier triple pipe rubber
system.


Mine was the earlier double rubber pipe system. (Which apparently they
sold briefly after the triple, but before moving to PEX.) Failures of the
double and triple systems seem to be similar, and common.

Mostly it's perished near the manifolds, one zone leaked somewhere I
couldn't find it, and one zone (the last failure) isn't leaking, but the
rubber is gunked up and hardly any water circulates. Possibly because,
although it's had inhibitor in it, it's been repeatedly refilled because
of all the leaks.
  #30   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 12,364
Default Anybody created a pre-heat DHW cylinder

On Thursday, 5 November 2015 14:22:15 UTC, rick wrote:
On 04/11/2015 22:31, nt wrote:


This extra electricity comes at times of high sun output, ie when ufh
is not usually being used. So in principle you could add a stat that
stops the ufh pump coming on when the cyl is too hot for it. Then you
get the benefit of your extra leccy without a bunch of extra costs.


Assume you mean a manual switch in summer turning off boiler and
enabling immersion .. with it's stat set higher .,.... an idea.


that's totally different to what I suggested

In order to draw off hot water you need to run a de-stratification pump


I'm not seeing why. It's not normally how things work

I presume your pump is drawn the wrong way round on that pdf.


NT

....... existing pump does this and cycles primary (thru boiler) .. not
an issue in winter when this extra heat goes into the building fabric.

If I were to turn off control system, the de-stratification pump & zone
valve (initiated by flow switch) would not work.

I would need to install a shunt pump & one way valve .. operated by flow
switch.

This pic shows what I have .. and where shunt would go.

The system is pressurised - left out expansion chambers and much of the
other kit for clarity.

http://www.4shared.com/office/XP0ObB...al_store_.html



  #33   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 25,191
Default Anybody created a pre-heat DHW cylinder

On 05/11/2015 14:10, rick wrote:
On 05/11/2015 09:18, Dave Liquorice wrote:

Only quoting the OP and that's the maximum to avoid damage. What
ever, to me not having some regulation of the UFH loop temperature
independant of the store temp isn't right. Limiting the store to 60 C
reduces the amount of energy it can store by about 30%.

And a store with a 60 C max must struggle to provide a decent
quantity of DHW unless the OP has that mixer valve set to the
pathtically low "safe" 43 C. Ours is set at 53 C or there abouts, hot
as in you can put your hand in it but don't want to keep it there for
more than a few tens of seconds hot. The store middle temperature is
normally about 70 to 80 C, top can get to 90+ if I miss judge the
weather and get a good burn going in the stove without the heating
coming on enough. It can deliver a bath of DHW at 53 C and 15 to
20l/min before it starts to run out heat.


The regulation is done by the stat keeping tank at 60 ........ you may
deem that not enough but seems to work fine.
Stat is fitted in lower 1/3 of store.


That in itself means the upper section of the store will be able to
reach a much higher temperature.

There is never any shortage of ho****er ... this is set to 53 deg ...
and runs at full mains pressure ... on 22mm pipes.

You can run it full flow to fill a bath and still running hot when bath
is full.

Nu-Heat advise the high efficiency cross flow heat exchanger (rather
than a coil)allows this.


You have shown it as a coil in the diagram... normally there would be a
circulation pump to drive the primary of the DHW HE - that solves the
problem of cold pockets forming in the cylinder - the opt is pumped to
the inlet of the PHE primary, and the return from it go back into a
lower tapping on the cylinder.

Like:

http://wiki.diyfaq.org.uk/index.php/...Bank-Water.gif

(that shows a vented store, but the same principle can apply for unvented)

Flow is from mains pressure of 3.5bar at 25L/min .. and has never
once run out of ho****er when in use.


As long as you have adequate volume of water stored, and the PHE has
enough transfer rate, you should be fine. (you will need to shift around
80kW to keep pace with a flow rate of 25 lpm)


--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/
  #34   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 12,364
Default Anybody created a pre-heat DHW cylinder

On Thursday, 5 November 2015 20:19:43 UTC, rick wrote:
On 05/11/2015 17:38, nt wrote:


In order to draw off hot water you need to run a de-stratification pump


I'm not seeing why. It's not normally how things work

I presume your pump is drawn the wrong way round on that pdf.


The baffle in the middle of the store for one reason.
The other reason I know of is that the DHW take off is from a crossflow
plate heat exchanger, to keep up continuous high flow rate of hot water,
then need to stir the tank or it quickly would form a cold 'pocket'
around itself and flow would cool down


I'm not seeing how any of that adds up. A crossflow PHE must be external, and will run hot from the top, returning it to the bottom. The pumping inherent in that prevents cold pockets. To get best boiler efficiency & provide a cooler zone for ufh the boiler hot should enter the top of the cylinder.


NT
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Hot water cylinder heat exchanger efficiency - reheat time? MJA[_2_] UK diy 34 November 23rd 13 05:07 PM
Pitted hydraulic cylinder rod, cylinder leak poppop Metalworking 0 March 28th 12 02:06 PM
Pitted hydraulic cylinder rod, cylinder leak Ignoramus19246 Metalworking 13 March 27th 12 08:42 PM
Hot water cylinder 'robbing' radiators of heat? [email protected] UK diy 9 January 9th 06 10:17 PM
Hot water cylinder 'robbing' radiators of heat? [email protected] Home Repair 6 January 9th 06 08:00 PM


All times are GMT +1. The time now is 05:32 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"