Home |
Search |
Today's Posts |
|
UK diy (uk.d-i-y) For the discussion of all topics related to diy (do-it-yourself) in the UK. All levels of experience and proficency are welcome to join in to ask questions or offer solutions. |
Reply |
|
LinkBack | Thread Tools | Display Modes |
#1
Posted to uk.d-i-y
|
|||
|
|||
Marquee power Feedback - and more questions
Hi All, As some of my regular readers will remember, I was I/C of Electrics and PA at our church weekend camp recently and a bit concerned about only having 45A main breaker (Turned out i'd remembered wrong - It's only 40A! but we never had an issue. Anyhow, somebody said the mains distribution was a bit of a mess (a cable with blue 16A connector on and a 13 A cable reel both brought to the marquee and then distributed around using domestic 13A cable reels). I said that was about as good as it gets, but then got to thinking, at the other camp i'm involved with we generally use something similar to http://www.stagesuperstore.co.uk/32a...ets-2337-p.asp And then run 16A style cables out to the various points where power is required and just convert to 13A outlets at the very end. I asked if there might be some budget to buy the necessary "Board" and cables, but looking at the above it seems my guesstimate was seriously under what it might cost. Does anyone know of similar (reasonable quality) units at a lower price point? I suppose CPC or TLC might be my friend, but i'm not sure what to search for. TIA Chris |
#2
Posted to uk.d-i-y
|
|||
|
|||
Marquee power Feedback - and more questions
In article ,
wrote: Hi All, As some of my regular readers will remember, I was I/C of Electrics and PA at our church weekend camp recently and a bit concerned about only having 45A main breaker (Turned out i'd remembered wrong - It's only 40A! but we never had an issue. Anyhow, somebody said the mains distribution was a bit of a mess (a cable with blue 16A connector on and a 13 A cable reel both brought to the marquee and then distributed around using domestic 13A cable reels). I said that was about as good as it gets, but then got to thinking, at the other camp i'm involved with we generally use something similar to http://www.stagesuperstore.co.uk/32a...ets-2337-p.asp And then run 16A style cables out to the various points where power is required and just convert to 13A outlets at the very end. I asked if there might be some budget to buy the necessary "Board" and cables, but looking at the above it seems my guesstimate was seriously under what it might cost. Does anyone know of similar (reasonable quality) units at a lower price point? I suppose CPC or TLC might be my friend, but i'm not sure what to search for. How often is this needed? If only once in a while, I'd be inclined to hire from a film or theatrical etc lighting company. Other benefit is it will be tested before despatch. -- *He who dies with the most toys is, nonetheless, dead. Dave Plowman London SW To e-mail, change noise into sound. |
#3
Posted to uk.d-i-y
|
|||
|
|||
Marquee power Feedback - and more questions
On Friday, July 18, 2014 12:18:23 PM UTC+1, Dave Plowman (News) wrote:
In article , wrote: Stuff about marquee power distribution How often is this needed? If only once in a while, I'd be inclined to hire from a film or theatrical etc lighting company. Other benefit is it will be tested before despatch. -- *He who dies with the most toys is, nonetheless, dead. Dave Plowman London SW To e-mail, change noise into sound. Hi Dave, it's only once or twice a year, but even at the prices i've seen I think we'd soon re-coup the capital cost (can't see the lighting company wanting to write invoices for less than £150 even if we could peruade them to deal with such a small customer. But I will look into it. Cheers Chris |
#5
Posted to uk.d-i-y
|
|||
|
|||
Marquee power Feedback - and more questions
In article ,
wrote: On Friday, July 18, 2014 12:18:23 PM UTC+1, Dave Plowman (News) wrote: In article , wrote: Stuff about marquee power distribution How often is this needed? If only once in a while, I'd be inclined to hire from a film or theatrical etc lighting company. Other benefit is it will be tested before despatch. Hi Dave, it's only once or twice a year, but even at the prices i've seen I think we'd soon re-coup the capital cost (can't see the lighting company wanting to write invoices for less than £150 even if we could peruade them to deal with such a small customer. But I will look into it. I've hired from a film lighting company for a garden party, and the charges seemed pretty reasonable to me. Pro cables and fittings designed for such work are pretty robust and have a long life. Also, 150 quid won't buy very much high current flexible cable. Which would also need space to store. however, I am in London with a good choice of such places reasonably locally. Transport costs could be high. -- *I don't know what your problem is, but I'll bet it's hard to pronounce Dave Plowman London SW To e-mail, change noise into sound. |
#6
Posted to uk.d-i-y
|
|||
|
|||
Marquee power Feedback - and more questions
wrote in message
... Hi All, As some of my regular readers will remember, I was I/C of Electrics and PA at our church weekend camp recently and a bit concerned about only having 45A main breaker (Turned out i'd remembered wrong - It's only 40A! but we never had an issue. Anyhow, somebody said the mains distribution was a bit of a mess (a cable with blue 16A connector on and a 13 A cable reel both brought to the marquee and then distributed around using domestic 13A cable reels). I said that was about as good as it gets, but then got to thinking, at the other camp i'm involved with we generally use something similar to http://www.stagesuperstore.co.uk/32a...ets-2337-p.asp And then run 16A style cables out to the various points where power is required and just convert to 13A outlets at the very end. I asked if there might be some budget to buy the necessary "Board" and cables, but looking at the above it seems my guesstimate was seriously under what it might cost. Does anyone know of similar (reasonable quality) units at a lower price point? I suppose CPC or TLC might be my friend, but i'm not sure what to search for. You could make your own similar box for a lot less. -- Adam |
#7
Posted to uk.d-i-y
|
|||
|
|||
Marquee power Feedback - and more questions
On Friday, July 18, 2014 8:46:03 PM UTC+1, ARW wrote:
wrote in message ... Hi All, As some of my regular readers will remember, I was I/C of Electrics and PA at our church weekend camp recently and a bit concerned about only having 45A main breaker (Turned out i'd remembered wrong - It's only 40A! but we never had an issue. Anyhow, somebody said the mains distribution was a bit of a mess (a cable with blue 16A connector on and a 13 A cable reel both brought to the marquee and then distributed around using domestic 13A cable reels). I said that was about as good as it gets, but then got to thinking, at the other camp i'm involved with we generally use something similar to http://www.stagesuperstore.co.uk/32a...ets-2337-p.asp And then run 16A style cables out to the various points where power is required and just convert to 13A outlets at the very end. I asked if there might be some budget to buy the necessary "Board" and cables, but looking at the above it seems my guesstimate was seriously under what it might cost. Does anyone know of similar (reasonable quality) units at a lower price point? I suppose CPC or TLC might be my friend, but i'm not sure what to search for. You could make your own similar box for a lot less. -- Adam Hi Adam, That is about the descision I had come to. Thanks Chris |
#8
Posted to uk.d-i-y
|
|||
|
|||
Marquee power Feedback - and more questions
wrote in message
... On Friday, July 18, 2014 8:46:03 PM UTC+1, ARW wrote: Hi Adam, That is about the descision I had come to. Thanks Chris It should be a piece of ****. Do you need really the RCD protection and individual MCBs in the box? If the box is suppled via a 16A RCD protected supply then you clearly do not. A waterproof box with one 16A waterproof surface mounted plug and 4 x 16A surface mounted sockets is all that is needed. Do your own risk assessment as to the quality of your work. Less than £50. Good luck with it. -- Adam |
#9
Posted to uk.d-i-y
|
|||
|
|||
Marquee power Feedback - and more questions
On Tue, 22 Jul 2014 19:37:34 +0100, ARW wrote:
It should be a piece of ****. Agreed but needs a bit of thought. IIRC the supply is 40 A and presumably has to be extened to the marquee where it will be distributed. Think I'd go for Ceeform 63 A connectors and cable for that extension and rely on the supply cutout. Then have the distribution box 63 A Ceeform input and 6 x 16 A individually RCBO protected outlets. This gives diversity should kit on one feed leak a bit and trip it's RCD. Local distribution using 16 A ceeform with 16 13 adapters on the end. Not sure what to do about Protective Earth. Particularly if the 63 A extension is long, FSVO "long". All this stuff would be available from a film/tv lighting supplier as has been mentioned. http://www.provisionequipment.tv/ http://www.arrilightingrental.com/ Niether site wants to play properly with my browser, so can't tell what the hire costs are. There are other smaller companies all over the country. -- Cheers Dave. |
#10
Posted to uk.d-i-y
|
|||
|
|||
Marquee power Feedback - and more questions
On Tuesday, July 22, 2014 9:04:05 PM UTC+1, Dave Liquorice wrote:
On Tue, 22 Jul 2014 19:37:34 +0100, ARW wrote: It should be a piece of ****. Agreed but needs a bit of thought. IIRC the supply is 40 A and presumably has to be extened to the marquee where it will be distributed. Think I'd go for Ceeform 63 A connectors and cable for that extension and rely on the supply cutout. Then have the distribution box 63 A Ceeform input and 6 x 16 A individually RCBO protected outlets. This gives diversity should kit on one feed leak a bit and trip it's RCD. Local distribution using 16 A ceeform with 16 13 adapters on the end. Not sure what to do about Protective Earth. Particularly if the 63 A extension is long, FSVO "long". All this stuff would be available from a film/tv lighting supplier as has been mentioned. http://www.provisionequipment.tv/ http://www.arrilightingrental.com/ Niether site wants to play properly with my browser, so can't tell what the hire costs are. There are other smaller companies all over the country. -- Cheers Dave. Thanks for your thoughts Dave, I am having similar thoughts........ The 40A MCB is up the track and feeds a sort of Chalet type afair which has a split load CU doing all the usual domestic stuff and presently also having a 16A Ceeform for the Marquee feed. I am thinking of getting this upgraded to 32A Ceeform (& MCB)(don't search for 32A on Google kiddies, the strangest things come up! !:^*)) and running a Ceeform 32A over to the Marquee (mostly, this will run with lower than 16A through it, but i'd like to have the option to draw more if we wanted to, so am thinking 6mm will be the way to go for the cable for a 50 metre run)). This would then plug (or rather socket onto!) a plug that goes to the input on a split load CU. This would have 8 16A MCBs each feeding a 16A Ceeform socket (4 to be used to run a 16A lead to each corner of the marquee, and 2 for lighting and 2 spare) There would also be another 16A MCB feeding a number of 13A double sockets (probably 2) for any equipment which needed to be powered where the board is (Probably attached to one of the main poles of the marquee at about 4 foot off the floor). Questions? Is 6mm for the main feed adequate? or overkill? If I go for 6mm and get it in one length, will I be able to lift it when it's coiled? or would it be better as two 25 metre lengths? Would I be able to lift them? TIA Chris |
#11
Posted to uk.d-i-y
|
|||
|
|||
Marquee power Feedback - and more questions
"Dave Liquorice" wrote in message
ll.co.uk... On Tue, 22 Jul 2014 19:37:34 +0100, ARW wrote: It should be a piece of ****. Agreed but needs a bit of thought. IIRC the supply is 40 A and presumably has to be extened to the marquee where it will be distributed. Think I'd go for Ceeform 63 A connectors and cable for that extension and rely on the supply cutout. Then have the distribution box 63 A Ceeform input and 6 x 16 A individually RCBO protected outlets. This gives diversity should kit on one feed leak a bit and trip it's RCD. Local distribution using 16 A ceeform with 16 13 adapters on the end. Not sure what to do about Protective Earth. Particularly if the 63 A extension is long, FSVO "long". You might have to use a TT install with two RCDs as per a caravan set up. All points noted in your post and I like the alternative view. -- Adam |
#12
Posted to uk.d-i-y
|
|||
|
|||
Marquee power Feedback - and more questions
wrote in message
... of the main poles of the marquee at about 4 foot off the floor). Questions? Is 6mm for the main feed adequate? or overkill? It sould be fine for 32A. I would have to do calcs for 63A and I would like to see calcs for 32A. If I go for 6mm and get it in one length, will I be able to lift it when it's coiled? or would it be better as two 25 metre lengths? Would I be able to lift them? I cannot answer that one as I do not know you:-). The maximum I can carry up 3 flights of stairs is 100m of 16mm T&E (well 6 rolls of it in individual runs) and I consider that to be hardish work (it's easier than pulling in 180mm 4 core SWA) Cheers -- Adam |
#13
Posted to uk.d-i-y
|
|||
|
|||
Marquee power Feedback - and more questions
|
#14
Posted to uk.d-i-y
|
|||
|
|||
Marquee power Feedback - and more questions
On Wednesday, July 23, 2014 2:13:54 PM UTC+1, wrote:
On Tuesday, July 22, 2014 9:04:05 PM UTC+1, Dave Liquorice wrote: On Tue, 22 Jul 2014 19:37:34 +0100, ARW wrote: It should be a piece of ****. Agreed but needs a bit of thought. IIRC the supply is 40 A and presumably has to be extened to the marquee where it will be distributed. Think I'd go for Ceeform 63 A connectors and cable for that extension and rely on the supply cutout. Then have the distribution box 63 A Ceeform input and 6 x 16 A individually RCBO protected outlets. This gives diversity should kit on one feed leak a bit and trip it's RCD. Local distribution using 16 A ceeform with 16 13 adapters on the end. Not sure what to do about Protective Earth. Particularly if the 63 A extension is long, FSVO "long". All this stuff would be available from a film/tv lighting supplier as has been mentioned. http://www.provisionequipment.tv/ http://www.arrilightingrental.com/ Niether site wants to play properly with my browser, so can't tell what the hire costs are. There are other smaller companies all over the country. -- Cheers Dave. Thanks for your thoughts Dave, I am having similar thoughts........ The 40A MCB is up the track and feeds a sort of Chalet type afair which has a split load CU doing all the usual domestic stuff and presently also having a 16A Ceeform for the Marquee feed. I am thinking of getting this upgraded to 32A Ceeform (& MCB)(don't search for 32A on Google kiddies, the strangest things come up! !:^*)) and running a Ceeform 32A over to the Marquee (mostly, this will run with lower than 16A through it, but i'd like to have the option to draw more if we wanted to, so am thinking 6mm will be the way to go for the cable for a 50 metre run)). This would then plug (or rather socket onto!) a plug that goes to the input on a split load CU. This would have 8 16A MCBs each feeding a 16A Ceeform socket (4 to be used to run a 16A lead to each corner of the marquee, and 2 for lighting and 2 spare) There would also be another 16A MCB feeding a number of 13A double sockets (probably 2) for any equipment which needed to be powered where the board is (Probably attached to one of the main poles of the marquee at about 4 foot off the floor). Questions? Is 6mm for the main feed adequate? or overkill? If I go for 6mm and get it in one length, will I be able to lift it when it's coiled? or would it be better as two 25 metre lengths? Would I be able to lift them? TIA Chris BS 7909 is probably worth a look... Costs start to add up fast, for how many uses a year? 6mm X 3 core HO7 RNF typically around 4 quid a meter, 50m cable= 200 + connectors. Plus distribution and additional `borrowable, cables, and of course, testing. 30m 63A SP cable 35 quid a week, save a lot using 32A distribution. 63A 8 X 16A MCB protected 40 quid a week. http://www.pslx.co.uk/mains_distribution.htm Find any of the theatre/AV suppliers,( film and TVsuppliers can be ,er, expensive) will be able to help you with similar gear and are used to shipping hires around via courier. |
#15
Posted to uk.d-i-y
|
|||
|
|||
Marquee power Feedback - and more questions
On Wed, 23 Jul 2014 17:27:09 -0700 (PDT), Adam Aglionby wrote:
The 40A MCB is up the track and feeds a sort of Chalet type afair which has a split load CU doing all the usual domestic stuff and presently also having a 16A Ceeform for the Marquee feed. I am thinking of getting this upgraded to 32A Ceeform (& MCB) 16 A isn't a lot when you hab urns/kettles involved... B-) This would then plug (or rather socket onto!) a plug that goes to the input on a split load CU. This would have 8 16A MCBs each feeding a 16A Ceeform socket I don't see any RCD protection. This is outside possibly in the wet. In the day job any 16 A feed to anywhere is individually RCD protected. If I go for 6mm and get it in one length, will I be able to lift it when it's coiled? or would it be better as two 25 metre lengths? Longest 63 A I see at work might be 25 m. You might be able to move it but carrying any distance would be a sack truck job really. Generally these cables are kept in the load carrier section of the generator, hoiked out onto the ground and then the end and cable dragged to where it needs to be. The coil is rarely moved more than a few feet. 30m 63A SP cable 35 quid a week, save a lot using 32A distribution. Only mentioned 63 A so as to be more than ample to cope with the full 40 A supply over an unknown distance. Volt drop and earth loop impedance. If one went for two TT installs, it would mandate 100 mA time delayed RCDs. or measuring the spikes performamce at each use. Now we know the expected load and distance I think a 32 A MCB 32 A cable for the marquee feed with individual 16 A RCBO's for each 16 A distribution outlet would be fine. Means your electrically leaky urn doesn't trip the whole lot off. As Adam says do the sums for the main 32 A feed cable. 63A 8 X 16A MCB protected 40 quid a week. http://www.pslx.co.uk/mains_distribution.htm Find any of the theatre/AV suppliers,( film and TVsuppliers can be ,er, expensive) will be able to help you with similar gear and are used to shipping hires around via courier. I knew that hire would be cheap for just cables and distribution but that is cheap cheap. B-) A big advantage is that it also shifts/shares the responsibilty of testing/maintenance to a "professional organisation" who one ought to be able to rely on to do things properly. Having said that I'd be a tad wary of smaller AV suppliers. Observation has shown that they don't have knowledge much above "just plug as many 13 A plugs into as many 4 way extensions (with exposed inner cores) as required". Loading, earth loop impedance, RCD protection? Wozzat? A theatre/PA/lighting company would be a better bet, a place that hires out PA systems and lighting rigs that would eat a 13 A plug top in the quiescent state. B-) -- Cheers Dave. |
#16
Posted to uk.d-i-y
|
|||
|
|||
Marquee power Feedback - and more questions
In article ,
Adam Aglionby wrote: BS 7909 is probably worth a look... Costs start to add up fast, for how many uses a year? 6mm X 3 core HO7 RNF typically around 4 quid a meter, 50m cable= 200 + connectors. Plus distribution and additional `borrowable, cables, and of course, testing. 30m 63A SP cable 35 quid a week, save a lot using 32A distribution. 63A 8 X 16A MCB protected 40 quid a week. http://www.pslx.co.uk/mains_distribution.htm Find any of the theatre/AV suppliers,( film and TVsuppliers can be ,er, expensive) will be able to help you with similar gear and are used to shipping hires around via courier. Quite. And you don't have to find somewhere to store it all. -- *I'm not a complete idiot, some parts are missing * Dave Plowman London SW To e-mail, change noise into sound. |
#17
Posted to uk.d-i-y
|
|||
|
|||
Marquee power Feedback - and more questions
On Wed, 23 Jul 2014 19:16:02 +0100, ARW wrote:
Not sure what to do about Protective Earth. Particularly if the 63 A extension is long, FSVO "long". You might have to use a TT install with two RCDs as per a caravan set up. Aye I was thinking that but it opens another can of worms... All points noted in your post and I like the alternative view. Thank you, I'm not a spark but do keep my eyes open about how things are done in temporary installations (TV Outside Broadcasts) and around event marquees etc, if only so I feel safe plugging in mains kit. -- Cheers Dave. |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Power Deregulation - any feedback about third party suppliers? | Home Repair | |||
Power Deregulation - any feedback about third party suppliers? | Home Repair | |||
Power Deregulation - any feedback about third party suppliers? | Home Repair | |||
Power Deregulation - any feedback about third party suppliers? | Home Repair | |||
Power Deregulation - any feedback about third party suppliers? | Home Repair |