Boiler not striking up (again)!
My inherently crap Potterton Suprima 30 is on the blink again!
This time, its not sparking. The timer comes on, the pumps start up and the little green light on the boiler starts blinking, but there's no sparking and the gas valve isn't opening (I'm assuming the gas wont turn on until it starts sparking). Then a I get a SOLID green light and the red starts flashing. I'm unfamiliar with this light configuration, lockout is a flashing red with no green, but this is a solid green with a flashing red. Couple of occasions, whilst the boiler has been left on in this state, it will suddenly strike up after a time on its own (it starts sparking and the gas comes on and lights). So I'm assuming its something to do with the ignition circuit? (and yes before you ask, the thermostats are asking for heat). I had a new PCB and Gas Valve a couple of years back, so I'm hoping its neither of those. I did put a new lead on the ignition a couple of years back, so I don't think its that. Anyone give me a heads up on what I should check first? TIA -- Best Wishes Simon (Dark Angel) http://www.realmofhorror.co.uk |
#2
Posted to uk.d-i-y
|
|||
|
|||
Boiler not striking up (again)!
"Simon (Dark Angel)" darkangel5@NO SPAM lineone.net wrote in message... The timer comes on, the pumps start up and the little green light on the boiler starts blinking, but there's no sparking and the gas valve isn't opening (I'm assuming the gas wont turn on until it starts sparking). Then a I get a SOLID green light and the red starts flashing. Oh yeah, and the fan in the flue isn't coming on either. Usually, the fan starts up, then you get sparking, then the gas valve opens. None of the above is happening (though it does sometimes start up on its own after a while)/ Fan problem you think? Anyway to check for this? -- Best Wishes Simon (Dark Angel) http://www.realmofhorror.co.uk |
#3
Posted to uk.d-i-y
|
|||
|
|||
Boiler not striking up (again)!
In message , "Simon (Dark
Angel)" writes "Simon (Dark Angel)" darkangel5@NO SPAM lineone.net wrote in message... The timer comes on, the pumps start up and the little green light on the boiler starts blinking, but there's no sparking and the gas valve isn't opening (I'm assuming the gas wont turn on until it starts sparking). Then a I get a SOLID green light and the red starts flashing. Oh yeah, and the fan in the flue isn't coming on either. Usually, the fan starts up, then you get sparking, then the gas valve opens. None of the above is happening (though it does sometimes start up on its own after a while)/ Fan problem you think? Until the fan operates the air pressure switch, you won't get a spark or gas valve opening look in your manual to see what the lights mean (p22 IIRC) Do you have switched live to the pcb (WRT neutral, of course) Is the stat presenting a short circuit? Is the temp sensor OK? DO you have 230 volts to the fan? -- geoff |
#4
Posted to uk.d-i-y
|
|||
|
|||
Boiler not striking up (again)!
On 10/04/2011 20:50, Simon (Dark Angel) wrote:
"Simon (Dark Angel)" darkangel5@NO SPAM lineone.net wrote in message... The timer comes on, the pumps start up and the little green light on the boiler starts blinking, but there's no sparking and the gas valve isn't opening (I'm assuming the gas wont turn on until it starts sparking). Then a I get a SOLID green light and the red starts flashing. Oh yeah, and the fan in the flue isn't coming on either. Usually, the fan starts up, then you get sparking, then the gas valve opens. None of the above is happening (though it does sometimes start up on its own after a while)/ Fan problem you think? Anyway to check for this? Fan problem. Or possibly fan control... It won't turn on the pilot until it has air pressure. Have a chat with CET Ltd for spares. He may appear later - think yourself lucky the weather is warm so you won't freeze. Andy |
#5
Posted to uk.d-i-y
|
|||
|
|||
Boiler not striking up (again)!
On 10/04/2011 20:05, Simon (Dark Angel) wrote:
My inherently crap Potterton Suprima 30 is on the blink again! This time, its not sparking. The timer comes on, the pumps start up and the little green light on the boiler starts blinking, but there's no sparking and the gas valve isn't opening (I'm assuming the gas wont turn on until it starts sparking). Then a I get a SOLID green light and the red starts flashing. I'm unfamiliar with this light configuration, lockout is a flashing red with no green, but this is a solid green with a flashing red. Couple of occasions, whilst the boiler has been left on in this state, it will suddenly strike up after a time on its own (it starts sparking and the gas comes on and lights). So I'm assuming its something to do with the ignition circuit? (and yes before you ask, the thermostats are asking for heat). I had a new PCB and Gas Valve a couple of years back, so I'm hoping its neither of those. I did put a new lead on the ignition a couple of years back, so I don't think its that. Anyone give me a heads up on what I should check first? TIA Have you got an installation manual for your boiler. If so, there's a fault-finding chart at page 30 something. Sounds like your fan isn't working. If the pressure switch doesn't detect any pressure from the fan, it doesn't even try to light the gas. If you haven't got a manual, go to http://www.partsarena.com/baxi/ and navigate to your boiler. There you'll find a manual in html - rather than pdf - format, but better that than nothing! -- Cheers, Roger ____________ Please reply to Newsgroup. Whilst email address is valid, it is seldom checked. |
#6
Posted to uk.d-i-y
|
|||
|
|||
Boiler not striking up (again)!
"geoff" wrote in message ...
look in your manual to see what the lights mean (p22 IIRC) Ah-ha, found it this time, it says... "Blocking - Mains Frequency incorrect or Air Switch" So, something to do with the air switch then? I assume first thing to do is check to see if the fan has got power to it then, yes? It's kinda late in the evening now, so will have to tackle this again tomorrow evening when i get back from work. -- Best Wishes Simon (Dark Angel) http://www.realmofhorror.co.uk |
#7
Posted to uk.d-i-y
|
|||
|
|||
Boiler not striking up (again)!
In message , Andy Champ
writes On 10/04/2011 20:50, Simon (Dark Angel) wrote: "Simon (Dark Angel)" darkangel5@NO SPAM lineone.net wrote in message... The timer comes on, the pumps start up and the little green light on the boiler starts blinking, but there's no sparking and the gas valve isn't opening (I'm assuming the gas wont turn on until it starts sparking). Then a I get a SOLID green light and the red starts flashing. Oh yeah, and the fan in the flue isn't coming on either. Usually, the fan starts up, then you get sparking, then the gas valve opens. None of the above is happening (though it does sometimes start up on its own after a while)/ Fan problem you think? Anyway to check for this? Fan problem. Or possibly fan control... It won't turn on the pilot until it has air pressure. Have a chat with CET Ltd for spares. He may appear later Later ? I've already given him a checklist to work on -- geoff |
#8
Posted to uk.d-i-y
|
|||
|
|||
Boiler not striking up (again)!
In message , Roger Mills
writes On 10/04/2011 20:05, Simon (Dark Angel) wrote: My inherently crap Potterton Suprima 30 is on the blink again! This time, its not sparking. The timer comes on, the pumps start up and the little green light on the boiler starts blinking, but there's no sparking and the gas valve isn't opening (I'm assuming the gas wont turn on until it starts sparking). Then a I get a SOLID green light and the red starts flashing. I'm unfamiliar with this light configuration, lockout is a flashing red with no green, but this is a solid green with a flashing red. Couple of occasions, whilst the boiler has been left on in this state, it will suddenly strike up after a time on its own (it starts sparking and the gas comes on and lights). So I'm assuming its something to do with the ignition circuit? (and yes before you ask, the thermostats are asking for heat). I had a new PCB and Gas Valve a couple of years back, so I'm hoping its neither of those. I did put a new lead on the ignition a couple of years back, so I don't think its that. Anyone give me a heads up on what I should check first? TIA Have you got an installation manual for your boiler. If so, there's a fault-finding chart at page 30 something. Fault finding chart? That's for amateurs vee don't neeed no steenkin' fault finding chart -- geoff |
#9
Posted to uk.d-i-y
|
|||
|
|||
Boiler not striking up (again)!
|
#10
Posted to uk.d-i-y
|
|||
|
|||
Boiler not striking up (again)!
On 10/04/2011 22:25, geoff wrote:
In message , Roger Mills writes Have you got an installation manual for your boiler. If so, there's a fault-finding chart at page 30 something. Fault finding chart? That's for amateurs vee don't neeed no steenkin' fault finding chart You might not! But the OP *is* an amateur, and almost certainly doesn't have your detailed knowledge of the start-up sequence. There's nothing wrong with that! -- Cheers, Roger ____________ Please reply to Newsgroup. Whilst email address is valid, it is seldom checked. |
#11
Posted to uk.d-i-y
|
|||
|
|||
Boiler not striking up (again)!
In message , Roger Mills
writes On 10/04/2011 22:25, geoff wrote: In message , Roger Mills writes Have you got an installation manual for your boiler. If so, there's a fault-finding chart at page 30 something. Fault finding chart? That's for amateurs vee don't neeed no steenkin' fault finding chart You might not! But the OP *is* an amateur, and almost certainly doesn't have your detailed knowledge of the start-up sequence. There's nothing wrong with that! He doesn't need it I'm here as always -- geoff |
#12
Posted to uk.d-i-y
|
|||
|
|||
Boiler not striking up (again)!
On 11/04/2011 01:40, geoff wrote:
In message , Roger Mills writes On 10/04/2011 22:25, geoff wrote: In message , Roger Mills writes Have you got an installation manual for your boiler. If so, there's a fault-finding chart at page 30 something. Fault finding chart? That's for amateurs vee don't neeed no steenkin' fault finding chart You might not! But the OP *is* an amateur, and almost certainly doesn't have your detailed knowledge of the start-up sequence. There's nothing wrong with that! He doesn't need it I'm here as always Give a man a fish, and all that . . . -- Cheers, Roger ____________ Please reply to Newsgroup. Whilst email address is valid, it is seldom checked. |
#13
Posted to uk.d-i-y
|
|||
|
|||
Boiler not striking up (again)!
"geoff" wrote in message
news Is the temp sensor OK? Right, I think I might have made a discovery here. When I lowered the PCB housing to take a look at the wiring, the boiler suddenly clicked on and fired up OK. When I went to screw it back on to the boiler, it stopped again. So I started looking at all the plugs on the PCB, when I wiggled the yellow wires, which I believe go to the temperature sensor, it suddenly sprang to life. So I'm thinking loose connection on the temp sensor at the PCB end? -- Best Wishes Simon (Dark Angel) http://www.realmofhorror.co.uk |
#14
Posted to uk.d-i-y
|
|||
|
|||
Boiler not striking up (again)!
On 10/04/2011 22:22, geoff wrote:
Later ? I've already given him a checklist to work on Crossed posts Think of it as a free advert. Andy |
#15
Posted to uk.d-i-y
|
|||
|
|||
Boiler not striking up (again)!
On Apr 11, 1:40*am, geoff wrote:
In message , Roger Mills writes On 10/04/2011 22:25, geoff wrote: In message , Roger Mills writes Have you got an installation manual for your boiler. If so, there's a fault-finding chart at page 30 something. Fault finding chart? That's for amateurs vee don't neeed no steenkin' fault finding chart You might not! But the OP *is* an amateur, and almost certainly doesn't have your detailed knowledge of the start-up sequence. There's nothing wrong with that! He doesn't need it I'm here as always -- geoff you know**** all stick to mending fans you has make 4 replys . Still you has not told the bloke waht is wrong with his boiller You are a ****en troll you know **** all.Go and mend fans |
#16
Posted to uk.d-i-y
|
|||
|
|||
Boiler not striking up (again)!
chas wrote:
On Apr 11, 1:40 am, geoff wrote: In message , Roger Mills writes On 10/04/2011 22:25, geoff wrote: In message , Roger Mills writes Have you got an installation manual for your boiler. If so, there's a fault-finding chart at page 30 something. Fault finding chart? That's for amateurs vee don't neeed no steenkin' fault finding chart You might not! But the OP *is* an amateur, and almost certainly doesn't have your detailed knowledge of the start-up sequence. There's nothing wrong with that! He doesn't need it I'm here as always -- geoff you know**** all stick to mending fans you has make 4 replys . Still you has not told the bloke waht is wrong with his boiller You are a ****en troll you know **** all.Go and mend fans It seems Geoff has a fan club. -- Adam |
#17
Posted to uk.d-i-y
|
|||
|
|||
Boiler not striking up (again)!
In message , "Simon (Dark
Angel)" writes "geoff" wrote in message news Is the temp sensor OK? Right, I think I might have made a discovery here. When I lowered the PCB housing to take a look at the wiring, the boiler suddenly clicked on and fired up OK. When I went to screw it back on to the boiler, it stopped again. So I started looking at all the plugs on the PCB, when I wiggled the yellow wires, which I believe go to the temperature sensor, it suddenly sprang to life. So I'm thinking loose connection on the temp sensor at the PCB end? You will not find anything about this in the flow chart ... So, is it the pcb connector or the loom wire then? It wasn't a pcb from me, was it, prolly the pcb con nector -- geoff |
#18
Posted to uk.d-i-y
|
|||
|
|||
Boiler not striking up (again)!
In message
, chas writes On Apr 11, 1:40*am, geoff wrote: In message , Roger Mills writes On 10/04/2011 22:25, geoff wrote: In message , Roger Mills writes Have you got an installation manual for your boiler. If so, there's a fault-finding chart at page 30 something. Fault finding chart? That's for amateurs vee don't neeed no steenkin' fault finding chart You might not! But the OP *is* an amateur, and almost certainly doesn't have your detailed knowledge of the start-up sequence. There's nothing wrong with that! He doesn't need it I'm here as always -- geoff you know**** all stick to mending fans you has make 4 replys . Still you has not told the bloke waht is wrong with his boiller You are a ****en troll you know **** all.Go and mend fans Bloody hell, is it half term again ? -- geoff |
#19
Posted to uk.d-i-y
|
|||
|
|||
Boiler not striking up (again)!
In message , Roger Mills
writes On 10/04/2011 22:25, geoff wrote: In message , Roger Mills writes Have you got an installation manual for your boiler. If so, there's a fault-finding chart at page 30 something. Fault finding chart? That's for amateurs vee don't neeed no steenkin' fault finding chart You might not! But the OP *is* an amateur, and almost certainly doesn't have your detailed knowledge of the start-up sequence. There's nothing wrong with that! And, wouldn't have found the fault in the fault finding chart Nowhere does it say "Is your pcb falling apart?" -- geoff |
#20
Posted to uk.d-i-y
|
|||
|
|||
Boiler not striking up (again)!
In message , ARWadsworth
writes chas wrote: On Apr 11, 1:40 am, geoff wrote: In message , Roger Mills writes On 10/04/2011 22:25, geoff wrote: In message , Roger Mills writes Have you got an installation manual for your boiler. If so, there's a fault-finding chart at page 30 something. Fault finding chart? That's for amateurs vee don't neeed no steenkin' fault finding chart You might not! But the OP *is* an amateur, and almost certainly doesn't have your detailed knowledge of the start-up sequence. There's nothing wrong with that! He doesn't need it I'm here as always -- geoff you know**** all stick to mending fans you has make 4 replys . Still you has not told the bloke waht is wrong with his boiller You are a ****en troll you know **** all.Go and mend fans It seems Geoff has a fan club. He's sulking because I refused to have sex with him he doesn't have anyone to wank him off now that chas and dave have split up -- geoff |
#21
Posted to uk.d-i-y
|
|||
|
|||
Boiler not striking up (again)!
|
#22
Posted to uk.d-i-y
|
|||
|
|||
Boiler not striking up (again)!
geoff wrote:
In message , ARWadsworth writes chas wrote: On Apr 11, 1:40 am, geoff wrote: In message , Roger Mills writes On 10/04/2011 22:25, geoff wrote: In message , Roger Mills writes Have you got an installation manual for your boiler. If so, there's a fault-finding chart at page 30 something. Fault finding chart? That's for amateurs vee don't neeed no steenkin' fault finding chart You might not! But the OP *is* an amateur, and almost certainly doesn't have your detailed knowledge of the start-up sequence. There's nothing wrong with that! He doesn't need it I'm here as always -- geoff you know**** all stick to mending fans you has make 4 replys . Still you has not told the bloke waht is wrong with his boiller You are a ****en troll you know **** all.Go and mend fans It seems Geoff has a fan club. He's sulking because I refused to have sex with him he doesn't have anyone to wank him off now that chas and dave have split up I hope that his right hand is better at wanking than writing. -- Adam |
#23
Posted to uk.d-i-y
|
|||
|
|||
Boiler not striking up (again)!
"geoff" wrote in message...
So, is it the pcb connector or the loom wire then? I'm thinking loose wire in the plug. It wasn't a pcb from me, was it, prolly the pcb con nector It was one of yours yes, had it a couple of years now. I'm guessing its the plug on the end of the wire, as opposed to the PCB. I'm going to take a closer look on my next day off. -- Best Wishes Simon (Dark Angel) http://www.realmofhorror.co.uk |
#24
Posted to uk.d-i-y
|
|||
|
|||
Boiler not striking up (again)!
In message , "Simon (Dark
Angel)" writes "geoff" wrote in message... So, is it the pcb connector or the loom wire then? I'm thinking loose wire in the plug. It wasn't a pcb from me, was it, prolly the pcb con nector It was one of yours yes, had it a couple of years now. I'm guessing its the plug on the end of the wire, as opposed to the PCB. I'm going to take a closer look on my next day off. Ah well, you know where I am -- geoff |
#25
Posted to uk.d-i-y
|
|||
|
|||
Boiler not striking up (again)!
On Apr 11, 9:52*pm, geoff wrote:
In message , Roger Mills writes On 10/04/2011 22:25, geoff wrote: In message , Roger Mills writes Have you got an installation manual for your boiler. If so, there's a fault-finding chart at page 30 something. Fault finding chart? That's for amateurs vee don't neeed no steenkin' fault finding chart You might not! But the OP *is* an amateur, and almost certainly doesn't have your detailed knowledge of the start-up sequence. There's nothing wrong with that! And, wouldn't have found the fault in the fault finding chart Nowhere does it say "Is your pcb falling apart?" -- geoff you thick thick **** you did nto tell the bloke what iswrong with the boilr .. You thick thick **** |
#26
Posted to uk.d-i-y
|
|||
|
|||
Boiler not striking up (again)!
chas wrote:
On Apr 11, 9:52 pm, geoff wrote: In message , Roger Mills writes On 10/04/2011 22:25, geoff wrote: In message , Roger Mills writes Have you got an installation manual for your boiler. If so, there's a fault-finding chart at page 30 something. Fault finding chart? That's for amateurs vee don't neeed no steenkin' fault finding chart You might not! But the OP *is* an amateur, and almost certainly doesn't have your detailed knowledge of the start-up sequence. There's nothing wrong with that! And, wouldn't have found the fault in the fault finding chart Nowhere does it say "Is your pcb falling apart?" -- geoff you thick thick **** you did nto tell the bloke what iswrong with the boilr . You thick thick **** Nice spelling. Are you illiterate or a thick ****? -- Adam |
#27
Posted to uk.d-i-y
|
|||
|
|||
Boiler not striking up (again)!
"ARWadsworth" wrote in message ... you thick thick **** you did nto tell the bloke what iswrong with the boilr . You thick thick **** Nice spelling. Are you illiterate or a thick ****? Probably TNP, he spells like that when he is ****ed, and he is ****ed a lot of the time going by his spelling. |
#28
Posted to uk.d-i-y
|
|||
|
|||
Boiler not striking up (again)!
dennis@home wrote:
"ARWadsworth" wrote in message ... you thick thick **** you did nto tell the bloke what iswrong with the boilr . You thick thick **** Nice spelling. Are you illiterate or a thick ****? Probably TNP, he spells like that when he is ****ed, and he is ****ed a lot of the time going by his spelling. Did nursey help you write that? -- Adam |
#29
Posted to uk.d-i-y
|
|||
|
|||
Boiler not striking up (again)!
In message
, chas writes On Apr 11, 9:52*pm, geoff wrote: In message , Roger Mills writes On 10/04/2011 22:25, geoff wrote: In message , Roger Mills writes Have you got an installation manual for your boiler. If so, there's a fault-finding chart at page 30 something. Fault finding chart? That's for amateurs vee don't neeed no steenkin' fault finding chart You might not! But the OP *is* an amateur, and almost certainly doesn't have your detailed knowledge of the start-up sequence. There's nothing wrong with that! And, wouldn't have found the fault in the fault finding chart Nowhere does it say "Is your pcb falling apart?" -- geoff you thick thick **** you did nto tell the bloke what iswrong with the boilr . You thick thick **** Sorry, not playing ... -- geoff |
#30
Posted to uk.d-i-y
|
|||
|
|||
Boiler not striking up (again)!
"geoff" wrote in message...
Ah well, you know where I am Hope your still reading this. Well having done some tinkering today, I'm not sure but I think there might be a problem with the PCB. When I "wiggled" (for want of a better word) either of the plugs that connect the temperature sensor or the boiler thermostat control to the PCB, the boiler would strike up. Have removed the pcb and examined the solder connections, can't see anything wrong and have tested continuity between these plug and the back of the PCB and all seems well. Was wondering if there's a break somewhere on the board that was connecting when one of the connectors was "wiggled" as it were? Just trying to make head nor tail of the wiring diagram to see what else to test for (I have experience with electrics, but not electronic fault finding). -- Best Wishes Simon (Dark Angel) http://www.realmofhorror.co.uk |
#31
Posted to uk.d-i-y
|
|||
|
|||
Boiler not striking up (again)!
Quick addendum.
Removed the plug to the temperature sensor, tested the yellow wires, no continuity. Removed the plug to the Temperature control and turned it to max. There was continuity between the 2 orange wires and continuity between the 2 white wires. Removed the plug to the air pressure switch, tested the orange wires, no continuity. Any ideas? -- Best Wishes Simon (Dark Angel) http://www.realmofhorror.co.uk |
#32
Posted to uk.d-i-y
|
|||
|
|||
Boiler not striking up (again)!
In message , "Simon (Dark
Angel)" writes "geoff" wrote in message... Ah well, you know where I am Hope your still reading this. Well having done some tinkering today, I'm not sure but I think there might be a problem with the PCB. When I "wiggled" (for want of a better word) either of the plugs that connect the temperature sensor or the boiler thermostat control to the PCB, the boiler would strike up. Have removed the pcb and examined the solder connections, can't see anything wrong and have tested continuity between these plug and the back of the PCB and all seems well. Was wondering if there's a break somewhere on the board that was connecting when one of the connectors was "wiggled" as it were? Just trying to make head nor tail of the wiring diagram to see what else to test for (I have experience with electrics, but not electronic fault finding). Its only electrics where the fault lies from what you've said If the connector pins and their pads on the pcb look OK (check carefully in good light), then the next port of call has to be the loom wiring. If you have a broken wire where it attaches to a connector, you won't notice it as the insulation is also crimped to the pin. Give the wire a gentle tug to see if there is any elasticity there Also, check that one of the pads hasn't cracked away from the track it should be attached to on the solder side of the pcb. The Suprima pcb itself is a real cheap and nasty bit of kit -- geoff |
#33
Posted to uk.d-i-y
|
|||
|
|||
Boiler not striking up (again)!
In message , "Simon (Dark
Angel)" writes Quick addendum. Removed the plug to the temperature sensor, tested the yellow wires, no continuity. That's because the temperature sensor has a resistance of 1MOhm at 20C. You need to test it with a decent meter Removed the plug to the Temperature control and turned it to max. There was continuity between the 2 orange wires and continuity between the 2 white wires. The pot will go from 0 - 1MOhm, the other two wires are to the switch. Not sure why they should be short circuit when the pot is set to max though, I'll check tomorrow Removed the plug to the air pressure switch, tested the orange wires, no continuity. They are the common and normally open connections on the microswitch. When the fan operates the APS, the contacts will be short circuit Any ideas? -- geoff |
#34
Posted to uk.d-i-y
|
|||
|
|||
Boiler not striking up (again)!
"geoff" wrote in message...
That's because the temperature sensor has a resistance of 1MOhm at 20C. You need to test it with a decent meter I tested it at 2M ohm, but will check again. The pot will go from 0 - 1MOhm, the other two wires are to the switch. Not sure why they should be short circuit when the pot is set to max though, I'll check tomorrow If I read the flow chart right, its supposed to be short circuit? They are the common and normally open connections on the microswitch. When the fan operates the APS, the contacts will be short circuit I reconnected the plug and turned the power on, was getting voltage on both pins if that's of any help? -- Best Wishes Simon (Dark Angel) http://www.realmofhorror.co.uk |
#35
Posted to uk.d-i-y
|
|||
|
|||
Boiler not striking up (again)!
"geoff" wrote in message...
Its only electrics where the fault lies from what you've said If the connector pins and their pads on the pcb look OK (check carefully in good light), then the next port of call has to be the loom wiring. If you have a broken wire where it attaches to a connector, you won't notice it as the insulation is also crimped to the pin. Give the wire a gentle tug to see if there is any elasticity there Also, check that one of the pads hasn't cracked away from the track it should be attached to on the solder side of the pcb. The Suprima pcb itself is a real cheap and nasty bit of kit With the plugs connected (and the power off) I checked for continuity between where the cable terminates in the plug, and the solder joint on the back of the PCB, and got a continuity reading on all terminals. -- Best Wishes Simon (Dark Angel) http://www.realmofhorror.co.uk |
#36
Posted to uk.d-i-y
|
|||
|
|||
Boiler not striking up (again)!
"Simon (Dark Angel)" darkangel5@NO SPAM lineone.net wrote in message ... With the plugs connected (and the power off) I checked for continuity between where the cable terminates in the plug, and the solder joint on the back of the PCB, and got a continuity reading on all terminals. That tests the conductivity of the solder. A common failure on PCBs is that the pad lifts from the board and breaks the copper track that connects to the pad. You need to do the test between the pad and another on the same track and do a visual check with a magnifier. If its broken you will need to run a piece of wire to repair the track. |
#37
Posted to uk.d-i-y
|
|||
|
|||
Boiler not striking up (again)!
In message , "Simon (Dark
Angel)" writes "geoff" wrote in message... Its only electrics where the fault lies from what you've said If the connector pins and their pads on the pcb look OK (check carefully in good light), then the next port of call has to be the loom wiring. If you have a broken wire where it attaches to a connector, you won't notice it as the insulation is also crimped to the pin. Give the wire a gentle tug to see if there is any elasticity there Also, check that one of the pads hasn't cracked away from the track it should be attached to on the solder side of the pcb. The Suprima pcb itself is a real cheap and nasty bit of kit With the plugs connected (and the power off) I checked for continuity between where the cable terminates in the plug, and the solder joint on the back of the PCB, and got a continuity reading on all terminals. Well it looks like you have something not giving a good connection in that area, or your fiddling is disturbing something else in the loom It looks like its down to fiddling about and observation now There's a bad connection somewhere, you just have to find it ... no mysterious or devious electronics fault, no need to go around measuring voltages and such like -- geoff |
#38
Posted to uk.d-i-y
|
|||
|
|||
Boiler not striking up (again)!
In message , "dennis@home"
writes "Simon (Dark Angel)" darkangel5@NO SPAM lineone.net wrote in message ... With the plugs connected (and the power off) I checked for continuity between where the cable terminates in the plug, and the solder joint on the back of the PCB, and got a continuity reading on all terminals. That tests the conductivity of the solder. A common failure on PCBs is that the pad lifts from the board and breaks the copper track that connects to the pad. You need to do the test between the pad and another on the same track and do a visual check with a magnifier. If its broken you will need to run a piece of wire to repair the track. Dennis - you are entering territory where you know less than you know about most things you know **** all about I on the other hand, really do know how to get to the bottom of this so be a good boy and **** off and leave me to it -- geoff |
#39
Posted to uk.d-i-y
|
|||
|
|||
Boiler not striking up (again)!
In message , "Simon (Dark
Angel)" writes Quick addendum. Removed the plug to the temperature sensor, tested the yellow wires, no continuity. Removed the plug to the Temperature control and turned it to max. There was continuity between the 2 orange wires and continuity between the 2 white wires. Removed the plug to the air pressure switch, tested the orange wires, no continuity. Any ideas? Can you be in front of the boiler tomorrow It might be worth you giving me a ring at work and I can lead you through in real time 01923 229224 -- geoff |
#40
Posted to uk.d-i-y
|
|||
|
|||
Boiler not striking up (again)!
"geoff" wrote in message...
Can you be in front of the boiler tomorrow I appreciate the offer, however I don't get back from work till 530 pm Don't suppose you'll still be available at that time? -- Best Wishes Simon (Dark Angel) http://www.realmofhorror.co.uk |