Hello

I noticed that a light switch back box measured around 100V ac w.r.t. the
cold water tap in our recently-purchased house. I checked the earth bonding
on the metal pipework for the hot and the cold tap and the radiator; all are
at the same zero volt potential. I checked the earth of a nearby mains
socket and saw no p.d. between it and the pipework mentioned. I looked
around the house and I see lots of earth bonding that has been carried out
within the last 3-4 years.


Measuring a current flow to ground from this "dodgy" earth, I see a couple
of hundred microamps flowing (actually about 275uA). Not enough to hurt but
you can just about feel a "buzz" on your finger tip.

I shall start trying to trace the lighting ring main back, but I am puzzled
as to why this lighting ring earth should float when a nearby socket ring
main earth doesn't. I am yet to carry out furthr investigations i.e. other
looking at other ring circuits.

Maybe this is a simple fix but I'd appreciate some guidance before I get up
loads of floorboards etc.

thanks in advance

DDS


  #2   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 6,766
Default "Earth" floating at 80-120V ... why?

Duncan Di Saudelli expressed precisely :
I noticed that a light switch back box measured around 100V ac w.r.t. the
cold water tap in our recently-purchased house. I checked the earth bonding
on the metal pipework for the hot and the cold tap and the radiator; all are
at the same zero volt potential. I checked the earth of a nearby mains socket
and saw no p.d. between it and the pipework mentioned. I looked around the
house and I see lots of earth bonding that has been carried out within the
last 3-4 years.


You really need to make all measurements from one reference point and
that should be the consumer unit earth, so you probably need a long
cable of some sort to do that.

The sort of numbers you are quoting suggests the voltage is simply
induced from the live running adjacent to the earth. I would probably
be prudent to check the resistance of the earth from all lighting
switches and lights, to gain a better idea of what is wrong.

If the wiring dates back to the 1960's, it was not unusual for the
lighting circuits not to be provided with an earth. Later mods and
improvements to the circuits might mean metal boxes installed, but with
no earth.

--
Regards,
Harry (M1BYT) (L)
http://www.ukradioamateur.co.uk


  #3   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 52
Default "Earth" floating at 80-120V ... why?

The sort of numbers you are quoting suggests the voltage is simply induced
from the live running adjacent to the earth. I would probably


D'oh! Yes, an obvious contributor. Thanks - I shall pick up on your other
points (common reference via long lead etc.) and start afresh tomorrow. I
tyake your point regarding 1960s wiring and I shall look into the earthing
of the lighting rings.

thanks for the feedback. Time for some sleep!

DDS


  #4   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 2,735
Default "Earth" floating at 80-120V ... why?

Duncan Di Saudelli wrote:
The sort of numbers you are quoting suggests the voltage is simply induced
from the live running adjacent to the earth. I would probably


D'oh! Yes, an obvious contributor. Thanks - I shall pick up on your other
points (common reference via long lead etc.) and start afresh tomorrow. I
tyake your point regarding 1960s wiring and I shall look into the earthing
of the lighting rings.

thanks for the feedback. Time for some sleep!


Another thing to consider is the sensitivity of the volt meter, The more
ohms per volt, the more you are going to get confused.

Dave
  #5   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 43,017
Default "Earth" floating at 80-120V ... why?

In article ,
Duncan Di Saudelli wrote:
Measuring a current flow to ground from this "dodgy" earth, I see a
couple of hundred microamps flowing (actually about 275uA). Not enough
to hurt but you can just about feel a "buzz" on your finger tip.


I shall start trying to trace the lighting ring main back, but I am
puzzled as to why this lighting ring earth should float when a nearby
socket ring main earth doesn't. I am yet to carry out furthr
investigations i.e. other looking at other ring circuits.


For a start, lighting circuits ain't rings - they are radials.

How old is the house? Earths haven't always been required on lighting
circuits. Even although TW&E may have been used to wire them.

Most likely cause is it either isn't connected or is broken somewhere.
Especially where a ceiling rose has been replaced with an alternative
fitting which doesn't have the required terminals.

--
*Give me ambiguity or give me something else.

Dave Plowman London SW
To e-mail, change noise into sound.


  #6   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 6,766
Default "Earth" floating at 80-120V ... why?

John Rumm wrote :
To check the earth continuity you can disconnect the live at the circuit
breaker or fuse, and temporarily join it to the earth wire for the circuit.


Which would still leave the neutral connected and the neutral connected
to earth at the sub-station. One or more lights in the circuit left on
and the live will have at least some sort of connection to earth -
enough to cause some confusion when using that method.

The using a DMM on ohms range measure the live to earth resistance at each
lighting position (or switch). You should soon be able to find where in the
circuit you have a disconnection. Chances are it will be at a ceiling rose
somewhere - leaving the remainder of the circuit with a floating earth.


There were two standard methods to wire the lighting circuits using
T&E. The current method is from the Dis-board then lopped into each
ceiling rose in turn, then down from the ceiling rose to its associated
switch. The older method was similar to the above, but a joint box was
used as the central connection point for each section of the circuit.

If wired using the later joint box method it could well be that the
break in the earth is at one of these under floor joint boxes.

--
Regards,
Harry (M1BYT) (L)
http://www.ukradioamateur.co.uk


  #7   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 52
Default "Earth" floating at 80-120V ... why?

I noticed that a light switch back box measured around 100V ac w.r.t. the
cold water tap in our recently-purchased house.


Thanks everyone for your advice and a few fault-finding pointers. I did
quickly realise that the voltage measured was probably sourced from a high
impedance and that measuring with a DVM with a 20M input Z would giuve
unrealistic readings - hence my decision to measure the current and see it
as only a few hundred uA i.e. a "leakage" current.

I'll start working round the ring - sorry, the radial wiring, thanks for
putting me straight - and we'll see where we get to. Hopefully I'll find a
floating "ned" which can then be tied down.

Thanks all.

DDS


  #8   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 52
Default "Earth" floating at 80-120V ... why?

Although more focussed on socket circuits, you may find some of this
useful:

http://wiki.diyfaq.org.uk/index.php?...Circuit_Faults


Definitely useful - thankyou! More reading to be done.

DDS


  #9   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 14,085
Default "Earth" floating at 80-120V ... why?

On Sun, 14 Mar 2010 13:38:09 -0000, Duncan Di Saudelli wrote:

Hopefully I'll find a floating "ned" which can then be tied down.


Would need to be tied down if it was floating face down in the Clyde,
best place for it.

--
Cheers
Dave.



  #10   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 7,688
Default "Earth" floating at 80-120V ... why?


"John Rumm" wrote in message
o.uk...
Harry Bloomfield wrote:
John Rumm wrote :
To check the earth continuity you can disconnect the live at the circuit
breaker or fuse, and temporarily join it to the earth wire for the
circuit.


Which would still leave the neutral connected and the neutral connected
to earth at the sub-station. One or more lights in the circuit left on
and the live will have at least some sort of connection to earth - enough
to cause some confusion when using that method.


Yes, sorry I did not explicitly say - turn the CU off at the main switch.

(personally I would disconnect all the circuit wires and twist them
together - then using a low ohms meter one can do a number of other checks
as well as establish the circuit layout a bit quicker)

The using a DMM on ohms range measure the live to earth resistance at
each lighting position (or switch). You should soon be able to find
where in the circuit you have a disconnection. Chances are it will be at
a ceiling rose somewhere - leaving the remainder of the circuit with a
floating earth.


There were two standard methods to wire the lighting circuits using T&E.
The current method is from the Dis-board then lopped into each ceiling
rose in turn, then down from the ceiling rose to its associated switch.
The older method was similar to the above, but a joint box was used as
the central connection point for each section of the circuit.


There are plenty more than two out there! Loop in is the most common, but
JBs and looping through the switch positions is are also fairly frequently
found.

If wired using the later joint box method it could well be that the break
in the earth is at one of these under floor joint boxes.


Could be - but you should still be able identify in what section the fault
is from tests on what you can get access to at the light and switch
positions.

--
Cheers,

John.


Guess what job I am doing later in the week?

I got a phone call off a bloke complaining the metal backbox in the new
bathroom shaver point that he has fitted lights up his neon screwdriver. His
further tests showed that the same happens in one of his bedroom lightswitch
metal backboxes.

I am glad that he has taken his girlfriend away for a long weekend as his
words "You do not get a shock when you poke the backbox with your finger"
did worry me a little.

My first test will be an earth loop test on the new shaver socket.

My second test will probably be a resistance reading between the shaver
backbox and any available earth (eg a screw at socket front)

Cheers

Adam



  #11   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 2,640
Default "Earth" floating at 80-120V ... why?

Owain wrote:
On 14 Mar, 16:29, "ARWadsworth" wrote:
I got a phone call off a bloke complaining the metal backbox in the new
bathroom shaver point that he has fitted lights up his neon screwdriver. ...
I am glad that he has taken his girlfriend away for a long weekend as his
words "You do not get a shock when you poke the backbox with your finger"
did worry me a little.


If he doesn't use the proper tool for one job ...

Owain

I thought these days one was supposed to use insulated sleeves when
poking boxes of any orientation.

Bob
  #12   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 3,861
Default "Earth" floating at 80-120V ... why?

In message ,
ARWadsworth writes

Guess what job I am doing later in the week?

I got a phone call off a bloke complaining the metal backbox in the new
bathroom shaver point that he has fitted lights up his neon
screwdriver. His further tests showed that the same happens in one of
his bedroom lightswitch metal backboxes.

I am glad that he has taken his girlfriend away for a long weekend as
his words "You do not get a shock when you poke the backbox with your
finger" did worry me a little.


So did you ask if she did ?

--
geoff
  #13   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,154
Default "Earth" floating at 80-120V ... why?

In message ,
ARWadsworth writes

Guess what job I am doing later in the week?

I got a phone call off a bloke complaining the metal backbox in the new
bathroom shaver point that he has fitted lights up his neon
screwdriver. His further tests showed that the same happens in one of
his bedroom lightswitch metal backboxes.



I had something vaguely similar a couple of years back on my fathers
home, 200 miles away from me and in the middle of nowhere, overhead
power lines.. He was getting tingles of anything that should have been
earthed. Kitchen sink, water radiators, metal clad switches etc. It was
"interesting"

A rather fast 200 miles later........

Measuring between live and earth in the CU showed only a couple of
volts.

At the CU there was a rather old earth leakage trip, one where the earth
passed trough a separate unit to a local earth stake and any earth
current caused the trip to break the incoming supply. This had failed
and was happily still supplying the house with power.
( now replaced with something more substantial, looked like a token
gesture and probably once relied more on the lead water pipe, also new
CU with rcd now fitted )

If it had been the old days when he had a lead water pipe then it would
have either blown a fuse or warmed up the water!!

The reason for all of this was that in his green house he had trapped a
cable under a propagating frame and the VERY old rubber cable had
disintegrated inside and the live was short to the earth. There was no
separate earth to the green house it relied on the house earth via the
SWA that connected the two. The couple of volts measured at the CU were
I assume the drop in the SWA.



The moral of this is that
a) equipotential bonding works! Fine in the main house, not so sure
about the green house though with all its water and wet floors.
b) don't trust elderly, 90 year old, fathers to look after their own
electrics. c) there is a God out there looking after gardeners.

It was an interesting experience..................................
--
Bill
  #14   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 2,735
Default "Earth" floating at 80-120V ... why?

John Rumm wrote:
Bob Minchin wrote:
Owain wrote:
On 14 Mar, 16:29, "ARWadsworth" wrote:
I got a phone call off a bloke complaining the metal backbox in the new
bathroom shaver point that he has fitted lights up his neon
screwdriver. ...
I am glad that he has taken his girlfriend away for a long weekend
as his
words "You do not get a shock when you poke the backbox with your
finger"
did worry me a little.

If he doesn't use the proper tool for one job ...

Owain

I thought these days one was supposed to use insulated sleeves when
poking boxes of any orientation.


But they dramatically reduce the sensitivity of your probing
equipment... ;-)


Glad you wrote that, just remove any ambiguity.

Dave
  #15   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 2,735
Default "Earth" floating at 80-120V ... why?

geoff wrote:
In message ,
ARWadsworth writes

Guess what job I am doing later in the week?

I got a phone call off a bloke complaining the metal backbox in the
new bathroom shaver point that he has fitted lights up his neon
screwdriver. His further tests showed that the same happens in one of
his bedroom lightswitch metal backboxes.

I am glad that he has taken his girlfriend away for a long weekend as
his words "You do not get a shock when you poke the backbox with your
finger" did worry me a little.


So did you ask if she did ?


ROTFL

Nice one

Dave


  #16   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 259
Default "Earth" floating at 80-120V ... why?

geoff wrote:
In message ,
ARWadsworth writes

Guess what job I am doing later in the week?

I got a phone call off a bloke complaining the metal backbox in the
new bathroom shaver point that he has fitted lights up his neon
screwdriver. His further tests showed that the same happens in one of
his bedroom lightswitch metal backboxes.

I am glad that he has taken his girlfriend away for a long weekend as
his words "You do not get a shock when you poke the backbox with your
finger" did worry me a little.


So did you ask if she did ?


snort
  #17   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 259
Default "Earth" floating at 80-120V ... why?

Bill wrote:

It was an interesting experience..................................


Yes. What were his power bills like?
  #18   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,154
Default "Earth" floating at 80-120V ... why?

In message , Gib Bogle
writes
Bill wrote:

It was an interesting experience..................................


Yes. What were his power bills like?


Strange you should ask that. I'm not sure if it was for that period but
he did have one about then that was literally about 3X normal. He had
just invested in some new lighting in the greenhouse though. The sort
seen in cannabis factories. After he got the bill he stopped using the
lighting!

I don't think his leakage problem went on long enough to make a major
impact on the bill so it probably was the lighting.

--
Bill
  #19   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 259
Default "Earth" floating at 80-120V ... why?

Bill wrote:
In message , Gib Bogle
writes
Bill wrote:

It was an interesting experience..................................


Yes. What were his power bills like?


Strange you should ask that. I'm not sure if it was for that period but
he did have one about then that was literally about 3X normal. He had
just invested in some new lighting in the greenhouse though. The sort
seen in cannabis factories.


Is your dad an old hippie, by any chance?
  #20   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 7,688
Default "Earth" floating at 80-120V ... why?


"geoff" wrote in message
...
In message , ARWadsworth
writes

Guess what job I am doing later in the week?

I got a phone call off a bloke complaining the metal backbox in the new
bathroom shaver point that he has fitted lights up his neon screwdriver.
His further tests showed that the same happens in one of his bedroom
lightswitch metal backboxes.

I am glad that he has taken his girlfriend away for a long weekend as his
words "You do not get a shock when you poke the backbox with your finger"
did worry me a little.


So did you ask if she did ?

--
geoff


After meeting her I bet she does.

Adam



  #21   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,154
Default "Earth" floating at 80-120V ... why?

In message , Gib Bogle
writes
Bill wrote:
In message , Gib Bogle
writes
Bill wrote:

It was an interesting experience..................................

Yes. What were his power bills like?

Strange you should ask that. I'm not sure if it was for that period
but he did have one about then that was literally about 3X normal. He
had just invested in some new lighting in the greenhouse though. The
seen in cannabis factories.


Is your dad an old hippie, by any chance?


:-)

Did get me thinking though when he showed me what he was doing, actually
he hybridises fuchsias. A 45' greenhouse that can only be seen if you
are on the property and not many visitors. MMMmmmm No best
not........

--
Bill
  #22   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 336
Default "Earth" floating at 80-120V ... why?

On Sat, 13 Mar 2010 22:19:02 GMT, Harry Bloomfield
wrote:

If the wiring dates back to the 1960's, it was not unusual for the
lighting circuits not to be provided with an earth. Later mods and
improvements to the circuits might mean metal boxes installed, but with
no earth.


I've seen early 60's wiring with metal backboxes for the light
switches and no earth, the wiring being double insulated either in
singles or zip connected doubles.

Makes things interesting when you contact a switchplate fixing screw
with a finger and the backbox has been made live from a missed stray
conductor (stranded not solid conductors)


--
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT +1. The time now is 08:46 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"