"Earth" floating at 80-120V ... why?
Hello
I noticed that a light switch back box measured around 100V ac w.r.t. the cold water tap in our recently-purchased house. I checked the earth bonding on the metal pipework for the hot and the cold tap and the radiator; all are at the same zero volt potential. I checked the earth of a nearby mains socket and saw no p.d. between it and the pipework mentioned. I looked around the house and I see lots of earth bonding that has been carried out within the last 3-4 years. Measuring a current flow to ground from this "dodgy" earth, I see a couple of hundred microamps flowing (actually about 275uA). Not enough to hurt but you can just about feel a "buzz" on your finger tip. I shall start trying to trace the lighting ring main back, but I am puzzled as to why this lighting ring earth should float when a nearby socket ring main earth doesn't. I am yet to carry out furthr investigations i.e. other looking at other ring circuits. Maybe this is a simple fix but I'd appreciate some guidance before I get up loads of floorboards etc. thanks in advance DDS |
#2
Posted to uk.d-i-y
|
|||
|
|||
"Earth" floating at 80-120V ... why?
Duncan Di Saudelli expressed precisely :
I noticed that a light switch back box measured around 100V ac w.r.t. the cold water tap in our recently-purchased house. I checked the earth bonding on the metal pipework for the hot and the cold tap and the radiator; all are at the same zero volt potential. I checked the earth of a nearby mains socket and saw no p.d. between it and the pipework mentioned. I looked around the house and I see lots of earth bonding that has been carried out within the last 3-4 years. You really need to make all measurements from one reference point and that should be the consumer unit earth, so you probably need a long cable of some sort to do that. The sort of numbers you are quoting suggests the voltage is simply induced from the live running adjacent to the earth. I would probably be prudent to check the resistance of the earth from all lighting switches and lights, to gain a better idea of what is wrong. If the wiring dates back to the 1960's, it was not unusual for the lighting circuits not to be provided with an earth. Later mods and improvements to the circuits might mean metal boxes installed, but with no earth. -- Regards, Harry (M1BYT) (L) http://www.ukradioamateur.co.uk |
#3
Posted to uk.d-i-y
|
|||
|
|||
"Earth" floating at 80-120V ... why?
The sort of numbers you are quoting suggests the voltage is simply induced
from the live running adjacent to the earth. I would probably D'oh! Yes, an obvious contributor. Thanks - I shall pick up on your other points (common reference via long lead etc.) and start afresh tomorrow. I tyake your point regarding 1960s wiring and I shall look into the earthing of the lighting rings. thanks for the feedback. Time for some sleep! DDS |
#4
Posted to uk.d-i-y
|
|||
|
|||
"Earth" floating at 80-120V ... why?
Duncan Di Saudelli wrote:
The sort of numbers you are quoting suggests the voltage is simply induced from the live running adjacent to the earth. I would probably D'oh! Yes, an obvious contributor. Thanks - I shall pick up on your other points (common reference via long lead etc.) and start afresh tomorrow. I tyake your point regarding 1960s wiring and I shall look into the earthing of the lighting rings. thanks for the feedback. Time for some sleep! Another thing to consider is the sensitivity of the volt meter, The more ohms per volt, the more you are going to get confused. Dave |
#5
Posted to uk.d-i-y
|
|||
|
|||
"Earth" floating at 80-120V ... why?
On Sat, 13 Mar 2010 22:19:02 GMT, Harry Bloomfield
wrote: If the wiring dates back to the 1960's, it was not unusual for the lighting circuits not to be provided with an earth. Later mods and improvements to the circuits might mean metal boxes installed, but with no earth. I've seen early 60's wiring with metal backboxes for the light switches and no earth, the wiring being double insulated either in singles or zip connected doubles. Makes things interesting when you contact a switchplate fixing screw with a finger and the backbox has been made live from a missed stray conductor (stranded not solid conductors) -- |
#6
Posted to uk.d-i-y
|
|||
|
|||
"Earth" floating at 80-120V ... why?
In article ,
Duncan Di Saudelli wrote: Measuring a current flow to ground from this "dodgy" earth, I see a couple of hundred microamps flowing (actually about 275uA). Not enough to hurt but you can just about feel a "buzz" on your finger tip. I shall start trying to trace the lighting ring main back, but I am puzzled as to why this lighting ring earth should float when a nearby socket ring main earth doesn't. I am yet to carry out furthr investigations i.e. other looking at other ring circuits. For a start, lighting circuits ain't rings - they are radials. How old is the house? Earths haven't always been required on lighting circuits. Even although TW&E may have been used to wire them. Most likely cause is it either isn't connected or is broken somewhere. Especially where a ceiling rose has been replaced with an alternative fitting which doesn't have the required terminals. -- *Give me ambiguity or give me something else. Dave Plowman London SW To e-mail, change noise into sound. |
#7
Posted to uk.d-i-y
|
|||
|
|||
"Earth" floating at 80-120V ... why?
I noticed that a light switch back box measured around 100V ac w.r.t. the
cold water tap in our recently-purchased house. Thanks everyone for your advice and a few fault-finding pointers. I did quickly realise that the voltage measured was probably sourced from a high impedance and that measuring with a DVM with a 20M input Z would giuve unrealistic readings - hence my decision to measure the current and see it as only a few hundred uA i.e. a "leakage" current. I'll start working round the ring - sorry, the radial wiring, thanks for putting me straight - and we'll see where we get to. Hopefully I'll find a floating "ned" which can then be tied down. Thanks all. DDS |
#8
Posted to uk.d-i-y
|
|||
|
|||
"Earth" floating at 80-120V ... why?
On Sun, 14 Mar 2010 13:38:09 -0000, Duncan Di Saudelli wrote:
Hopefully I'll find a floating "ned" which can then be tied down. Would need to be tied down if it was floating face down in the Clyde, best place for it. -- Cheers Dave. |