I wish to install a 8.5KW electrical shower in the top floor of a
house. The house wiring is slightly unusual in that it is divided into three separate zones each with its own consumer unit. The top floor is unit is supplied with 16mm cable which I assume is fine for the shower. There are no other heavy duty electrical items on the top floor (there is just a couple of ring circuits and a lighting circuit) However the consumer unit has no spare fuse ways and there is no RCD protection on the top floor circuit. Therefore I would have to buy a separate consumer unit for the shower and split the incoming 16mm cable so that I can feed both the original unit and the new shower consumer unit. I’ve had a look around and I think the following items would work. For splitting the cable: http://www.allaboutelectrics.co.uk/6...ction-box.html For the consumer unit: http://www.allaboutelectrics.co.uk/c...-unit-40a.html I assume that I would then need to run either 6mm or 10mm cable to the shower. The length of the run from the new unit to the shower, via an isolator pull cord switch, would only be about 5m. As to earth bonding in the bathroom the only metal is the pipes so they are the only items that need to be bonded. I would be grateful if anybody can confirm that this is all OK and whether there is any cheaper/easy alternatives with regard the consumer unit and junction box. I am aware of part P but having installed two showers in the past feel competent enough to do it. |
#2
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
geoffr wrote:
However the consumer unit has no spare fuse ways and there is no RCD protection on the top floor circuit. Therefore I would have to buy a separate consumer unit for the shower and split the incoming 16mm cable so that I can feed both the original unit and the new shower consumer unit. I’ve had a look around and I think the following items would work. For splitting the cable: http://www.allaboutelectrics.co.uk/6...ction-box.html That would work, however there is a fair chance there will be enough terminal capacity on the main incomer switch on the existing CU to add an extra cable from there (they are built to take at least 35mm^2 normally). For the consumer unit: http://www.allaboutelectrics.co.uk/c...-unit-40a.html Yup, that's the sort of thing. You can do it without an RCD if you can be certain that the earth fault loop impedance is going to be low enough. However the RCD eliminates the doubt (not that it hurts to design as if it were not there) I assume that I would then need to run either 6mm or 10mm cable to the shower. The length of the run from the new unit to the shower, via an isolator pull cord switch, would only be about 5m. 6mm^2 ought to be ok, assuming the cable is not run in such a way as it needs to be de-rated too much. http://wiki.diyfaq.org.uk/index.php?...es#Cable_Sizes As to earth bonding in the bathroom the only metal is the pipes so they are the only items that need to be bonded. to the CPCs of the shower radial, and also probably the lighting circuit in the room. http://wiki.diyfaq.org.uk/index.php?...tary _bonding -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#3
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
John Rumm wrote:
For splitting the cable: http://www.allaboutelectrics.co.uk/6...ction-box.html That would work, however there is a fair chance there will be enough terminal capacity on the main incomer switch on the existing CU to add an extra cable from there (they are built to take at least 35mm^2 normally). Or it might be worth replacing the whole top-floor disboard, given that there are only three other circuits. An RCBO for the lighting and an RCD group with three MCBs (2 rings and the shower) would bring things up to 17th ed. standard and give a neater-looking job for not that much more cost. Then if this lighting circuit feeds the shower room the need for supplementary bonding is eliminated (provided that the main bonding for the house is OK and there are no other circuits in this shower room). [...] You can do it without an RCD if you can be certain that the earth fault loop impedance is going to be low enough. That's not an option under the 17th. All circuits feeding bath/shower room circuits must now be 30 mA RCD protected. (I'm sure you knew that, really...) However the RCD eliminates the doubt (not that it hurts to design as if it were not there) Zs needs to be watched here, given that the feeding distribution circuit is 16 mm^2 - twin & earth, quite possibly, although no specific cable type was mentioned - so possibly only a 6 mm^2 incoming CPC to the board. I'd want to take a loop reading at the board before going too much further. -- Andy |
#4
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
On 19 Aug, 16:58, Andy Wade wrote:
Thanks John and Andy for your replies. Zs needs to be watched here, given that the feeding distribution circuit is 16 mm^2 - twin & earth, quite possibly, although no specific cable type was mentioned - so possibly only a 6 mm^2 incoming CPC to the board. * The cable is T&E. I'd want to take a loop reading at the board before going too much further. The last earth loop impedance reading was taken about 2 years ago and the reading was 0.3 ohm. Is this OK or should I get it checked again? I have gone down the route of puchasing a separate RCD shower consumer unit. However there is insufficient vertical space where I would like to place the new unit and therefore can these consumer units be fixed horizontally so that in effect it will be on its side. Will this effect the operation of the MCB or the RCD? Failing that are the any regulations requiring the unit to be a certain height from the floor? Many thanks again for any replies. |
#6
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
On 25 Aug, 20:29, John Rumm wrote:
wrote: I have gone down the route of puchasing a separate RCDshowerconsumer unit. However there is insufficient vertical space where I would like to place the new unit and therefore can these consumer units be fixed horizontally so that in effect it will be on its side. Will this effect the operation of the MCB or the RCD? You would have to consult the manufacturers data sheets here. My only concern would be if adequate cooling of the MCB will be maintained in the "wrong" orientation. (while it is rare to see domestic CUs arrange the breakers horizontally, its quite common in industrial ones) Failing that are the any regulations requiring the unit to be a certain height from the floor? It ought to be accessible without a ladder etc. Other than that, use common sense. Thanks again John for your reply. I've had a re think with regard the consumer unit as allthough there are no spare fuse ways in the unit that's currently installed one of the fuse ways is just for a single double socket in the attic which is never used. Therefore would it be ok to simply wire this directly into the adjacent ring main fuse way in the cosumer unit? I then would then have a spare fuse way to use for the shower. The other issue is can I just swap the main switch on the unit for a RCD. The switch that is currently there is rated at 100A whilst the RCD I've purchased is rated at 63A. The shower will be 8.5KW otherwise there are no major loads, just a ring main, bathroom extractor fan and light circuits so I assume its OK. Thanks, Geoff |
#7
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
In article
, geoffr wrote: However the consumer unit has no spare fuse ways and there is no RCD protection on the top floor circuit. Therefore I would have to buy a separate consumer unit for the shower and split the incoming 16mm cable so that I can feed both the original unit and the new shower consumer unit. Why not just change the CU for one that does what you need - they're not that expensive and would be the better way. -- *Why is the time of day with the slowest traffic called rush hour? Dave Plowman London SW To e-mail, change noise into sound. |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
![]() |
||||
Thread | Forum | |||
Help with shower installation | UK diy | |||
Electric oven installation | UK diy | |||
Electric installation.. how old??? | UK diy | |||
Electric installation.. how old??? | UK diy | |||
Electric installation.. how old??? | UK diy |