Default catnic style lintel - point loads

Catnic style lintel opening size 1500mm. You cannot have point loads
on them, but I will effectively have a single celcon block (440 wide),
then an engineering brick padstone, then the load (end of a purlin),
so would this spread the load enough? Else I could put a concrete
lintel instead of the eng brick to spread the load a bit more, say
over 2 blocks. Of course this is thermal bridging so a balance must be
struck !
Cheers,
Simon.
  #2   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 86
Default catnic style lintel - point loads

On 29 June, 16:32, sm_jamieson wrote:
Catnic style lintel opening size 1500mm. You cannot have point loads
on them, but I will effectively have a single celcon block (440 wide),
then an engineering brick padstone, then the load (end of a purlin),
so would this spread the load enough? Else I could put a concrete
lintel instead of the eng brick to spread the load a bit more, say
over 2 blocks. Of course this is thermal bridging so a balance must be
struck !
Cheers,
Simon.


Well, for future ref, the catnic brochure says:

Do not apply point loads without prior consultation. Where the
loading or a substantial part of it is applied as concentrated
loads, each concentrated load must be supported over a
length of lintel of not less than 200mm. In such cases, the
total loading must not produce bending moments or shear
forces greater than those produced by the uniformly
distributed loads specified in the relevant data tables.

So I would imagine a purlin over a whole 440mm block is generally OK.

Simon.
  #3   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 4,010
Default catnic style lintel - point loads

Simon wrote:
On 29 June, 16:32, sm_jamieson wrote:
Catnic style lintel opening size 1500mm. You cannot have point loads
on them, but I will effectively have a single celcon block (440
wide), then an engineering brick padstone, then the load (end of a
purlin), so would this spread the load enough? Else I could put a
concrete lintel instead of the eng brick to spread the load a bit
more, say over 2 blocks. Of course this is thermal bridging so a
balance must be struck !
Cheers,
Simon.


Well, for future ref, the catnic brochure says:

Do not apply point loads without prior consultation. Where the
loading or a substantial part of it is applied as concentrated
loads, each concentrated load must be supported over a
length of lintel of not less than 200mm. In such cases, the
total loading must not produce bending moments or shear
forces greater than those produced by the uniformly
distributed loads specified in the relevant data tables.

So I would imagine a purlin over a whole 440mm block is generally OK.

Simon.


Yes, except that aircrete blocks could crush under the load, better to use a
pre-stressed concrete padstone

--
Phil L
RSRL Tipster Of The Year 2008


  #4   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 86
Default catnic style lintel - point loads

On 30 June, 17:54, "Phil L" wrote:
Simon wrote:
On 29 June, 16:32, sm_jamieson wrote:
Catnic style lintel opening size 1500mm. You cannot have point loads
on them, but I will effectively have a single celcon block (440
wide), then an engineering brick padstone, then the load (end of a
purlin), so would this spread the load enough? Else I could put a
concrete lintel instead of the eng brick to spread the load a bit
more, say over 2 blocks. Of course this is thermal bridging so a
balance must be struck !
Cheers,
Simon.


Well, for future ref, the catnic brochure says:


Do not apply point loads without prior consultation. Where the
loading or a substantial part of it is applied as concentrated
loads, each concentrated load must be supported over a
length of lintel of not less than 200mm. In such cases, the
total loading must not produce bending moments or shear
forces greater than those produced by the uniformly
distributed loads specified in the relevant data tables.


So I would imagine a purlin over a whole 440mm block is generally OK.


Simon.


Yes, except that aircrete blocks could crush under the load, better to use a
pre-stressed concrete padstone


Do you mean a padstone between the aircrete block and the purlin,
or a whole concrete block instead of the aircrete. I don't think the
BCO would like
losing a whole aircrete block for insulation reasons.
I believe a common padstone in this situation is simply an engineering
brick, which is what
I mentioned earlier.
I've no objection to putting in a prestressed concrete lintel over the
whole opening if it was
required, but I suspect this would be over-engineering !
Certainly aircrete is used for loadbearing purposes, and I've at least
seen floor joist hangers
directly on aircrete.
Cheers,
Simon.
  #5   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 4,010
Default catnic style lintel - point loads

Simon wrote:
On 30 June, 17:54, "Phil L" wrote:
Simon wrote:
On 29 June, 16:32, sm_jamieson wrote:
Catnic style lintel opening size 1500mm. You cannot have point
loads on them, but I will effectively have a single celcon block
(440 wide), then an engineering brick padstone, then the load (end
of a purlin), so would this spread the load enough? Else I could
put a concrete lintel instead of the eng brick to spread the load
a bit more, say over 2 blocks. Of course this is thermal bridging
so a balance must be struck !
Cheers,
Simon.


Well, for future ref, the catnic brochure says:


Do not apply point loads without prior consultation. Where the
loading or a substantial part of it is applied as concentrated
loads, each concentrated load must be supported over a
length of lintel of not less than 200mm. In such cases, the
total loading must not produce bending moments or shear
forces greater than those produced by the uniformly
distributed loads specified in the relevant data tables.


So I would imagine a purlin over a whole 440mm block is generally
OK.


Simon.


Yes, except that aircrete blocks could crush under the load, better
to use a pre-stressed concrete padstone


Do you mean a padstone between the aircrete block and the purlin,
or a whole concrete block instead of the aircrete. I don't think the
BCO would like
losing a whole aircrete block for insulation reasons.


A pre-stresed lintel is 75H X 100W by whatever length you want to make it -
it's not going to make one iota of difference WRT insulation.

I believe a common padstone in this situation is simply an engineering
brick, which is what
I mentioned earlier.


a brick is only 200mm long.

I've no objection to putting in a prestressed concrete lintel over the
whole opening if it was
required, but I suspect this would be over-engineering !


PS lintels come in many lengths, I was thinking say about 5 - 600mm, then it
covers more than one aircrete block in length.

Certainly aircrete is used for loadbearing purposes, and I've at least
seen floor joist hangers
directly on aircrete.


Floor joists are many and each one takes a small amount of weight, a
*single* purlin takes the weight of all the joists, which are holding up the
battens and tiles and everything else.


--
Phil L
RSRL Tipster Of The Year 2008




  #6   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 86
Default catnic style lintel - point loads

On 30 June, 21:23, "Phil L" wrote:
Simon wrote:
On 30 June, 17:54, "Phil L" wrote:
Simon wrote:
On 29 June, 16:32, sm_jamieson wrote:
Catnic style lintel opening size 1500mm. You cannot have point
loads on them, but I will effectively have a single celcon block
(440 wide), then an engineering brick padstone, then the load (end
of a purlin), so would this spread the load enough? Else I could
put a concrete lintel instead of the eng brick to spread the load
a bit more, say over 2 blocks. Of course this is thermal bridging
so a balance must be struck !
Cheers,
Simon.


Well, for future ref, the catnic brochure says:


Do not apply point loads without prior consultation. Where the
loading or a substantial part of it is applied as concentrated
loads, each concentrated load must be supported over a
length of lintel of not less than 200mm. In such cases, the
total loading must not produce bending moments or shear
forces greater than those produced by the uniformly
distributed loads specified in the relevant data tables.


So I would imagine a purlin over a whole 440mm block is generally
OK.


Simon.


Yes, except that aircrete blocks could crush under the load, better
to use a pre-stressed concrete padstone


Do you mean a padstone between the aircrete block and the purlin,
or a whole concrete block instead of the aircrete. I don't think the
BCO would like
losing a whole aircrete block for insulation reasons.


A pre-stresed lintel is 75H X 100W by whatever length you want to make it -
it's not going to make one iota of difference WRT insulation.

I believe a common padstone in this situation is simply an engineering
brick, which is what
I mentioned earlier.


a brick is only 200mm long.

I've no objection to putting in a prestressed concrete lintel over the
whole opening if it was
required, but I suspect this would be over-engineering !


PS lintels come in many lengths, I was thinking say about 5 - 600mm, then it
covers more than one aircrete block in length.

Certainly aircrete is used for loadbearing purposes, and I've at least
seen floor joist hangers
directly on aircrete.


Floor joists are many and each one takes a small amount of weight, a
*single* purlin takes the weight of all the joists, which are holding up the
battens and tiles and everything else.

--

Thanks, I understand what you're saying now.
Sounds like a good idea.
Simon.
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
brad point vs twist point Paul Fisher Woodworking 5 February 8th 09 04:17 AM
Turned Piece The End Point OR A Step To The End Point? charlieb Woodturning 14 April 9th 08 08:27 PM
VCR JVC HR-A33U loads non-existent tape and re-loads existent Viatcheslav Riabov Electronics Repair 3 October 1st 04 11:07 AM
Catnic Lintel, is this the right one? MikeT UK diy 2 August 4th 03 09:26 PM


All times are GMT +1. The time now is 01:50 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"