'Chattering' MCB
Heard a sort of chattering sound from the MCB (30A) supplying one of the ring mains in our house this afternoon. Turn of the MCB, turn it back on again, all is ok for a little while (maybe 10 minutes?) then it starts again. The circuit in question is one of four ring mains in the house, it supplies the sitting room, one bedroom , a socket in the hall, in the conservatory and the dressing room. generally lightly loaded - a few table/standard lamps, TV, VCR, DVD etc. Whilst investigating this problem I noticed that when this circuit was switched on the disc on the meter started fair whizzing round - 30 rev/minute up from the say about 3 rev/minute is was doing normally. My quick calcs indicate that 30 rev/min implies something like 10kW/h being consumed - around 40A? , or have I made some big boo-boo? Anyway, there is nothing on the circuit drawing anything like that (no we don't have any secret electric showers, or unknown immersion heaters etc.) These symptoms continue to occur once everything on the circuit has been disconnected. I've not had time today to investigate this more thoroughly, the circuit is isolated now via the MCB pending time tomorrow. So, my thought so far is that there is some fault in the fixed wiring, causing a high current draw, and that the MCB is faulty in some way, hence the noise rather than tripping. Does the above sound a reasonable diagnosis? I can check out the MCB by swopping it with others in the CU I guess, if it is faulty then I'm not sure if replacing it is going to be a problem or not. The CU is a pretty old Crabtree one, you can see a couple of piccies he http://galoka.adsl24.co.uk/temp/IMG_0085.jpg http://galoka.adsl24.co.uk/temp/IMG_0088.jpg Does anyone know if I will be able to find something to fit? Thanks -- Chris French |
#2
Posted to uk.d-i-y
|
|||
|
|||
'Chattering' MCB
"chris French" wrote in message ... .... I can check out the MCB by swopping it with others in the CU I guess, if it is faulty then I'm not sure if replacing it is going to be a problem or not. The CU is a pretty old Crabtree one, you can see a couple of piccies he http://galoka.adsl24.co.uk/temp/IMG_0085.jpg http://galoka.adsl24.co.uk/temp/IMG_0088.jpg Does anyone know if I will be able to find something to fit? They look the same type as used in a couple of my factory distribution boards and they haven't been available for the past ten years. Colin Bignell |
#3
Posted to uk.d-i-y
|
|||
|
|||
'Chattering' MCB
In article ,
chris French writes: Heard a sort of chattering sound from the MCB (30A) supplying one of the ring mains in our house this afternoon. Turn of the MCB, turn it back on again, all is ok for a little while (maybe 10 minutes?) then it starts again. The circuit in question is one of four ring mains in the house, it supplies the sitting room, one bedroom , a socket in the hall, in the conservatory and the dressing room. generally lightly loaded - a few table/standard lamps, TV, VCR, DVD etc. Whilst investigating this problem I noticed that when this circuit was switched on the disc on the meter started fair whizzing round - 30 rev/minute up from the say about 3 rev/minute is was doing normally. My quick calcs indicate that 30 rev/min implies something like 10kW/h being consumed - around 40A? , or have I made some big boo-boo? Anyway, there is nothing on the circuit drawing anything like that (no we don't have any secret electric showers, or unknown immersion heaters etc.) These symptoms continue to occur once everything on the circuit has been disconnected. I've not had time today to investigate this more thoroughly, the circuit is isolated now via the MCB pending time tomorrow. I wonder if next door's cannabis plants are now in the dark? So, my thought so far is that there is some fault in the fixed wiring, causing a high current draw, and that the MCB is faulty in some way, hence the noise rather than tripping. Does the above sound a reasonable diagnosis? It's very unlikely that a fault in the wiring dissipating 10kW will stay that way for more than a few seconds. It will quickly burn out, either sort or open circuit. Besides which, you'd be quite likely to notice 10kW of heat coming into the house from an unexpected location. I would not be surprised at a 30A breaker making a noise at 40A, and I wouldn't immediately assume something wrong with the breaker in this case. It's probably right on the virge of tripping. Seems like you need to find what the high load is, which your meter is also confirming. -- Andrew Gabriel [email address is not usable -- followup in the newsgroup] |
#4
Posted to uk.d-i-y
|
|||
|
|||
'Chattering' MCB
In article ,
chris French wrote: So, my thought so far is that there is some fault in the fixed wiring, causing a high current draw, and that the MCB is faulty in some way, hence the noise rather than tripping. Does the above sound a reasonable diagnosis? I can't really think of a fault which would result in a very high current draw on the circuit with no load applied to it. I'd say even with the smaller ECC used on early rings and one end disconnected and shorted to line (the worst possible fault condition) it should still trip the MCB. But a heavy current draw like this should be easily found with a simple DVM - after disconnecting the ring from the CU of course. -- *Great groups from little icons grow * Dave Plowman London SW To e-mail, change noise into sound. |
#5
Posted to uk.d-i-y
|
|||
|
|||
'Chattering' MCB
In message , Andrew Gabriel
writes In article , chris French writes: Heard a sort of chattering sound from the MCB (30A) supplying one of the ring mains in our house this afternoon. Turn of the MCB, turn it back on again, all is ok for a little while (maybe 10 minutes?) then it starts again. snip Whilst investigating this problem I noticed that when this circuit was switched on the disc on the meter started fair whizzing round - 30 rev/minute up from the say about 3 rev/minute is was doing normally. My quick calcs indicate that 30 rev/min implies something like 10kW/h being consumed - around 40A? , or have I made some big boo-boo? Anyway, there is nothing on the circuit drawing anything like that (no we don't have any secret electric showers, or unknown immersion heaters etc.) These symptoms continue to occur once everything on the circuit has been disconnected. I wonder if next door's cannabis plants are now in the dark? :-) Detached house, unless someone has burrowed into the house to connect something up it's pretty safe to say that it's in our property somewhere. So, my thought so far is that there is some fault in the fixed wiring, causing a high current draw, and that the MCB is faulty in some way, hence the noise rather than tripping. Does the above sound a reasonable diagnosis? It's very unlikely that a fault in the wiring dissipating 10kW will stay that way for more than a few seconds. It will quickly burn out, either sort or open circuit. Besides which, you'd be quite likely to notice 10kW of heat coming into the house from an unexpected location. TBh, that was what I was thinking. I would not be surprised at a 30A breaker making a noise at 40A, and I wouldn't immediately assume something wrong with the breaker in this case. It's probably right on the virge of tripping. Seems like you need to find what the high load is, which your meter is also confirming. Well yes, that was indeed my thought, problem is, I'm at a loss as to what/where it could be, there is nothing in the house that I can think of that could possibly be drawing that sort of current, that isn't already accounted for. OK it's an old installation, and I still haven't got my head round all of it's idiosyncrasies, but this is very odd. At the moment I'm flummoxed, but I've got the house to my self now till mid afternoon so will try and investigate some more. -- Chris French |
#6
Posted to uk.d-i-y
|
|||
|
|||
'Chattering' MCB
In message , "Dave Plowman (News)"
writes In article , chris French wrote: So, my thought so far is that there is some fault in the fixed wiring, causing a high current draw, and that the MCB is faulty in some way, hence the noise rather than tripping. Does the above sound a reasonable diagnosis? I can't really think of a fault which would result in a very high current draw on the circuit with no load applied to it. I'd say even with the smaller ECC used on early rings and one end disconnected and shorted to line (the worst possible fault condition) it should still trip the MCB. But a heavy current draw like this should be easily found with a simple DVM - after disconnecting the ring from the CU of course. OK, how would I go about it? I've got cheapy multimeter. -- Chris French |
#7
Posted to uk.d-i-y
|
|||
|
|||
'Chattering' MCB
In message , nightjar
writes "chris French" wrote in message k... ... I can check out the MCB by swopping it with others in the CU I guess, if it is faulty then I'm not sure if replacing it is going to be a problem or not. The CU is a pretty old Crabtree one, you can see a couple of piccies he http://galoka.adsl24.co.uk/temp/IMG_0085.jpg http://galoka.adsl24.co.uk/temp/IMG_0088.jpg Does anyone know if I will be able to find something to fit? They look the same type as used in a couple of my factory distribution boards and they haven't been available for the past ten years. OK, thanks Colin, I was sort of expecting that. I'll worry about that bit if I need too. -- Chris French |
#8
Posted to uk.d-i-y
|
|||
|
|||
'Chattering' MCB
On Oct 17, 10:29 am, chris French
wrote: In message , "Dave Plowman (News)" writes In article , chris French wrote: So, my thought so far is that there is some fault in the fixed wiring, causing a high current draw, and that the MCB is faulty in some way, hence the noise rather than tripping. Does the above sound a reasonable diagnosis? I can't really think of a fault which would result in a very high current draw on the circuit with no load applied to it. I'd say even with the smaller ECC used on early rings and one end disconnected and shorted to line (the worst possible fault condition) it should still trip the MCB. But a heavy current draw like this should be easily found with a simple DVM - after disconnecting the ring from the CU of course. OK, how would I go about it? I've got cheapy multimeter. -- Chris French Hi Disconnect everything from the ring, and disconnect the ring from the CU. With your multimeter set to the ohms range, do the following measurements:- LL (should read low) NN (should read low) EE (should read low) That proves your ring is intact from end to end. Next, on either of the cables measure between LE, LN, and EN. They should all read open circuit. If you get any low resistance readings, perform the same test on the other leg of the ring as whichever gives the lowest reading indicates the fault is nearer that end of the ring. Steve |
#9
Posted to uk.d-i-y
|
|||
|
|||
'Chattering' MCB
chris French wrote:
In message , "Dave Plowman (News)" writes But a heavy current draw like this should be easily found with a simple DVM - after disconnecting the ring from the CU of course. OK, how would I go about it? I've got cheapy multimeter. Personally I would prefer to start by using a clamp meter on the running circuit - clamp round the live(s) at the exit from the MCB and take a direct reading of the current. This will verify what the real load is. One test with a DVM would be to disconnect the circuit (live and neutral) at the CU and then measure the resistance between live and neutral. If the circuit was drawing 40A at 240V, then you may see a resistance as low as 6 ohms. However this does assume that the load you are seeing will be visible at the low voltage of the DVM, and also that it is purely resistive[1]. If you can see the load with the DVM like this, then it ought to be a case of just breaking the circuit at various places until you isolate where it is. So if it is a ring for example, splitting in the middle and seeing which leg of it at the CU shows the low impedance load would immediately eliminate half the circuit. [1] A large reactive load would be an interesting possibility in that it would not need to be accompanied by a large power dissipation. However your electricity meter ought not record this as power consumption. -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#10
Posted to uk.d-i-y
|
|||
|
|||
'Chattering' MCB
Have you recently moved to this house? A massive power consumption
like this would be reflected in your electricity bills. A possible explanation is that the wiring is very different to what you think it is - and a heavy load of this sort is normal (e.g. shower, cooker, storage heaters) - or the wiring is so mad that a heavy current device is actually supplied through 2 different MCB's. I would start by thoroughly mapping each circuit from the consumer unit. All mcb's off - check every single socket, light and appliance is without power (in case something has been wired before the mcb's!). Check zero consumption on the meter. Then one mcb at once, verify every single socket, light & appliance - would be a good time to use a plug-in polarity & earth tester. If the behaviour persists, and there's a massive current load on only one socket ring with no plugged in loads, and the behaviour is repeatable by switching that mcb with all others isolated - first panic, then consider opening up sockets, disconnecting parts of the ring etc. |
#11
Posted to uk.d-i-y
|
|||
|
|||
'Chattering' MCB
In message .com,
" writes Have you recently moved to this house? A massive power consumption like this would be reflected in your electricity bills. No we've been here 2 1/2 years, certainly we have not had 10Kw/h running continuously since then. Certainly the bills/my meter records don't reflect this. AFAIK this just started happening yesterday. A possible explanation is that the wiring is very different to what you think it is - and a heavy load of this sort is normal (e.g. shower, cooker, storage heaters) - or the wiring is so mad that a heavy current device is actually supplied through 2 different MCB's. Thing is we don't have many heavy loads. Cooker (which is isolated a sit is a 'spare') and Immersion Heater - which is, as it usually is, turned off. No electric shower, storage heater etc. There di use to be storage heaters before our time, and one thing I did think about was that ther was one somewhere that had sparked into life. But if there is then I certainly have never seen it. It's all very odd (and yep, if I was answering this thread I'd be saying - 'he's got somethign somewhere running he's forgotten about....). I would start by thoroughly mapping each circuit from the consumer unit. All mcb's off - check every single socket, light and appliance is without power (in case something has been wired before the mcb's!). Check zero consumption on the meter. Then one mcb at once, verify every single socket, light & appliance - would be a good time to use a plug-in polarity & earth tester. I have checked out what is on which circuit before, but as part of today's checks I'm having another check. If the behaviour persists, and there's a massive current load on only one socket ring with no plugged in loads, and the behaviour is repeatable by switching that mcb with all others isolated - first panic, then consider opening up sockets, disconnecting parts of the ring etc. Thanks for everyones comments and suggestions/instructions, Turning off now, I'll be reporting back -- Chris French |
#12
Posted to uk.d-i-y
|
|||
|
|||
'Chattering' MCB
In message . com,
stevelup writes Hi Disconnect everything from the ring, and disconnect the ring from the CU. With your multimeter set to the ohms range, do the following measurements:- LL (should read low) NN (should read low) EE (should read low) That proves your ring is intact from end to end. Next, on either of the cables measure between LE, LN, and EN. They should all read open circuit. If you get any low resistance readings, perform the same test on the other leg of the ring as whichever gives the lowest reading indicates the fault is nearer that end of the ring. Thanks for that Steve. A quick lunch break update. OK, checked over the circuits again, but could not find anything lurking in the woodpile. So been trying the above tests. Looks like a Live to Earth fault- Low resistance/continuity between Live and Earth. I think I've now managed to narrow down the section of the ring that the fault is on - there is probably a junction box lurking somewhere as there is a spur off that probably comes off this leg somewhere. I'm thinking that maybe my RCD isn't doing it's job properly? (We have a TT earth system with just one main incoming RCD - about as old looking as the CU) The test button works ok though. -- Chris French |
#13
Posted to uk.d-i-y
|
|||
|
|||
'Chattering' MCB
chris French wrote:
I'm thinking that maybe my RCD isn't doing it's job properly? (We have a TT earth system with just one main incoming RCD - about as old looking as the CU) The test button works ok though. Are you sure it is a RCD and not an older "voltage operated" ELCB? There is a picture of a common one he http://wiki.diyfaq.org.uk/index.php?title=RCD#ELCB There are also details of how to test the RCD, if it is a RCD. -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#14
Posted to uk.d-i-y
|
|||
|
|||
'Chattering' MCB
On 17 Oct, 14:27, chris French
wrote: In message . com, stevelup writes Hi Disconnect everything from the ring, and disconnect the ring from the CU. With your multimeter set to the ohms range, do the following measurements:- LL (should read low) NN (should read low) EE (should read low) That proves your ring is intact from end to end. Next, on either of the cables measure between LE, LN, and EN. They should all read open circuit. If you get any low resistance readings, perform the same test on the other leg of the ring as whichever gives the lowest reading indicates the fault is nearer that end of the ring. Thanks for that Steve. A quick lunch break update. OK, checked over the circuits again, but could not find anything lurking in the woodpile. So been trying the above tests. Looks like a Live to Earth fault- Low resistance/continuity between Live and Earth. I think I've now managed to narrow down the section of the ring that the fault is on - there is probably a junction box lurking somewhere as there is a spur off that probably comes off this leg somewhere. I'm thinking that maybe my RCD isn't doing it's job properly? (We have a TT earth system with just one main incoming RCD - about as old looking as the CU) The test button works ok though. -- Chris French- Hide quoted text - - Show quoted text - Are you sure it is an RCD and not a VOELCB? Have you or anyone else drilled any holes in walls or driven any nails into one lately? A defective immersion heater might also be a candidate for consideration. It should not be supplied from a ring final circuit but the possibility of it happening does exist. |
#15
Posted to uk.d-i-y
|
|||
|
|||
'Chattering' MCB
Hi,
I'm thinking that maybe my RCD isn't doing it's job properly? (We have a TT earth system with just one main incoming RCD - about as old looking as the CU) The test button works ok though. I would be inclined to think that as well. 10KW is a lot of energy - probably enough to meet the entire heating needs of a medium sized house at this time of year and I have to wonder where it is going without you noticing something at least getting hot and probably catching fire. One place that you might be able to loose that kind of energy for a while would be heating the ground around your earth rod. Martin. |
#16
Posted to uk.d-i-y
|
|||
|
|||
'Chattering' MCB
One place that you might be able to loose that kind of energy for a while would be heating the ground around your earth rod. Switch everything off, lift the earth connection in the CU, switch on - does fault persist? (Immediately reinstate that earth!) |
#17
Posted to uk.d-i-y
|
|||
|
|||
'Chattering' MCB
In message , John Rumm
writes chris French wrote: I'm thinking that maybe my RCD isn't doing it's job properly? (We have a TT earth system with just one main incoming RCD - about as old looking as the CU) The test button works ok though. Are you sure it is a RCD and not an older "voltage operated" ELCB? No I'm not. There is a picture of a common one he http://wiki.diyfaq.org.uk/index.php?title=RCD#ELCB In fact it looks exactly like that..... -- Chris French |
#18
Posted to uk.d-i-y
|
|||
|
|||
'Chattering' MCB
In article ,
John Rumm writes: chris French wrote: I'm thinking that maybe my RCD isn't doing it's job properly? (We have a TT earth system with just one main incoming RCD - about as old looking as the CU) The test button works ok though. Are you sure it is a RCD and not an older "voltage operated" ELCB? If that's the case, then the leak could be via a water main or similar to earth (you won't get 40A or anything like through a VOELCB). Either this water main (or whatever) is not connected to the house earthing (and has virtually full mains voltage on it), or it is connected to the house earthing but has an overlapping resistance area with the VOELCB earth rod, preventing the VOELCB from working. Another option is the VOELCB has become disconnected from the house earthing, either due to an internal fault or deliberate action (possibly to prevent tripping in the past). Probably other options too, but those two spring to mind as matching the symptoms described. Beware, as you may have live metalwork around the house. -- Andrew Gabriel [email address is not usable -- followup in the newsgroup] |
#19
Posted to uk.d-i-y
|
|||
|
|||
'Chattering' MCB
chris French wrote:
In message , John Rumm writes chris French wrote: I'm thinking that maybe my RCD isn't doing it's job properly? (We have a TT earth system with just one main incoming RCD - about as old looking as the CU) The test button works ok though. Are you sure it is a RCD and not an older "voltage operated" ELCB? No I'm not. There is a picture of a common one he http://wiki.diyfaq.org.uk/index.php?title=RCD#ELCB In fact it looks exactly like that..... Aha, the plot thickens... ;-) Like Andy said these can fail to operate for a number of reasons. So it is possible to have a live to earth fault and not have it trip. First job sounds like finding the live to earth fault. You can worry about replacing the ELCB with something else after! -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#20
Posted to uk.d-i-y
|
|||
|
|||
'Chattering' MCB
In message , John Rumm
writes chris French wrote: In message , John Rumm writes chris French wrote: I'm thinking that maybe my RCD isn't doing it's job properly? (We have a TT earth system with just one main incoming RCD - about as old looking as the CU) The test button works ok though. Are you sure it is a RCD and not an older "voltage operated" ELCB? No I'm not. There is a picture of a common one he http://wiki.diyfaq.org.uk/index.php?title=RCD#ELCB In fact it looks exactly like that..... Aha, the plot thickens... ;-) It's an old house, the plot is always thick.... At some point I did consider that it could be an ELCB, but seemed to forget about the option at this point. Like Andy said these can fail to operate for a number of reasons. So it is possible to have a live to earth fault and not have it trip. First job sounds like finding the live to earth fault. You can worry about replacing the ELCB with something else after! I think I've found the fault, after much rummaging behind sockets. A live wire in one has a small bit of damaged insulation - just like a cut or maybe getting trapped and damaged at some point - this must have been in contact with an earth wire (old-ish installation - no sleeving) or maybe the backbox. There was a little tiny bit of what looked like heat damage, but only slight, I was expecting a bit more. Just need to put everything back now, and see if it's ok. -- Chris French |
#21
Posted to uk.d-i-y
|
|||
|
|||
'Chattering' MCB
Hope you have it sorted Chris. Given the potential seriousness, a
proper wiring regs full test of all circuits might be advisable. |
#22
Posted to uk.d-i-y
|
|||
|
|||
'Chattering' MCB
On Oct 18, 12:12 pm, chris French
wrote: I think I've found the fault, after much rummaging behind sockets. A live wire in one has a small bit of damaged insulation - just like a cut or maybe getting trapped and damaged at some point - this must have been in contact with an earth wire (old-ish installation - no sleeving) or maybe the backbox. There was a little tiny bit of what looked like heat damage, but only slight, I was expecting a bit more. Just need to put everything back now, and see if it's ok. Might be worth fitting an RCD instead of the ELCB. Though Part P probably forbids doing it yourself without hassle :| cheers, Pete. |
#23
Posted to uk.d-i-y
|
|||
|
|||
'Chattering' MCB
chris French wrote:
A live wire in one has a small bit of damaged insulation - just like a cut or maybe getting trapped and damaged at some point - this must have been in contact with an earth wire (old-ish installation - no sleeving) or maybe the backbox. There was a little tiny bit of what looked like heat damage, but only slight, I was expecting a bit more. Just need to put everything back now, and see if it's ok. Given the nature of the fault I would suggest retesting with an insulation resistance tester if you can borrow one. That way you should find any other latent problems of that nature. -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#24
Posted to uk.d-i-y
|
|||
|
|||
'Chattering' MCB
In message , Andrew Gabriel
writes In article , John Rumm writes: chris French wrote: I'm thinking that maybe my RCD isn't doing it's job properly? (We have a TT earth system with just one main incoming RCD - about as old looking as the CU) The test button works ok though. Are you sure it is a RCD and not an older "voltage operated" ELCB? If that's the case, then the leak could be via a water main or similar to earth (you won't get 40A or anything like through a VOELCB). Either this water main (or whatever) is not connected to the house earthing (and has virtually full mains voltage on it), or it is connected to the house earthing but has an overlapping resistance area with the VOELCB earth rod, preventing the VOELCB from working. Another option is the VOELCB has become disconnected from the house earthing, either due to an internal fault or deliberate action (possibly to prevent tripping in the past). Probably other options too, but those two spring to mind as matching the symptoms described. Beware, as you may have live metalwork around the house. Well, thanks to everyone's help. The socket live earth fault does seem to have been the problem. Rectified the problem, all seem to be fine now. Replaced a couple of falling part 30-40 year old socket faceplates. John, you suggested borrowing an insulation tester - if I had any idea where to borrow one I might, but TBH this does seem to have been a one off, the rest of what I've seen generally seems ok Re your above comments Andrew, well the metal work around the house seemed to be ok. The isn't any main bonding of the water/gad pipes at the moment. The VOELCB seems to be connected properly, I can't see any earth connections that bypass it. It has two 'outgoing' earth connections. One, to (presumably - I need to remove the base of an old climbing plant to find it) a buried earth rod, the second looks older - connects to an external copper pipe. This looks like an old gas pipe. It rises from the solid kitchen floor, goes out through the wall, runs along the outside, goes back inside to the utility room, where it terminates in what looks like a capped off gas cock. Anyway sorting out the meter/CU area has been on the job list for a while. It's probably up to 40 years old, the main CU is chockerblock and there is the typical hotpotch of extra switch fuses etc. A new bigger CU, a main RCD, sorting out the main earth bonding etc. Probably starting with replacing the VOELCB with an RCD to give more space for the new CU, partly because that can go elsewhere on the mounting board - replacing a great big F-off metal main switch - there presumably because the house has a 3 phase supply. Though only 1 phase is used. -- Chris French |
#25
Posted to uk.d-i-y
|
|||
|
|||
'Chattering' MCB
chris French wrote:
John, you suggested borrowing an insulation tester - if I had any idea where to borrow one I might, but TBH this does seem to have been a one off, the rest of what I've seen generally seems ok I have one in SE Essex if that is any use... Failing that a hire shop may be able to help. The reason for suggesting it was that if there was one fault of this type it might indicate that other similar faults may be lurking. A high voltage resistance test will shake out the ones that a multimeter will not find. Re your above comments Andrew, well the metal work around the house seemed to be ok. The isn't any main bonding of the water/gad pipes at the moment. The VOELCB seems to be connected properly, I can't see any earth connections that bypass it. It has two 'outgoing' earth connections. There are a number of ways of hooking these things up. Some a quite sophisticated with main and sense electrodes, but more commonly you just have them inline with the main earth connection to a single electrode. One, to (presumably - I need to remove the base of an old climbing plant to find it) a buried earth rod, the second looks older - connects to an external copper pipe. This looks like an old gas pipe. It rises from the solid kitchen floor, goes out through the wall, runs along the outside, goes back inside to the utility room, where it terminates in what looks like a capped off gas cock. Using a gas pipe was not uncommon. I used to have one in my house which just used the gas pipe as a main earth. The danger is that these days they may end up replacing large swathes of pipe with plastic and this can interfere with the operation of your earthing. Anyway sorting out the meter/CU area has been on the job list for a while. It's probably up to 40 years old, the main CU is chockerblock and there is the typical hotpotch of extra switch fuses etc. A new bigger CU, a main RCD, sorting out the main earth bonding etc. Probably starting with replacing the VOELCB with an RCD to give more space for the new CU, partly because that can go elsewhere on the mounting board - replacing a great big F-off metal main switch - there presumably because the house has a 3 phase supply. Though only 1 phase is used. In circumstances like that it can often work out simpler to install two CUs fed via split tails from a main switch. You can stick an ordinary 100mA trip RCD in one for all the lights and other circuits that do not need direct contact protection, and then have a 30mA trip RCD in a second CU for the power circuits. Often works out cheaper than having a £100 time delayed RCD cascaded in the same CU as the smaller threshold one. -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#26
Posted to uk.d-i-y
|
|||
|
|||
'Chattering' MCB
In message , John Rumm
writes chris French wrote: John, you suggested borrowing an insulation tester - if I had any idea where to borrow one I might, but TBH this does seem to have been a one off, the rest of what I've seen generally seems ok I have one in SE Essex if that is any use... Failing that a hire shop may be able to help. Thanks, but we are in the middle of Cambridgeshire. I might investigate hire options. One, to (presumably - I need to remove the base of an old climbing plant to find it) a buried earth rod, the second looks older - connects to an external copper pipe. This looks like an old gas pipe. Using a gas pipe was not uncommon. I used to have one in my house which just used the gas pipe as a main earth. The danger is that these days they may end up replacing large swathes of pipe with plastic and this can interfere with the operation of your earthing. It's unlikely this bit of pipe would get replaced with plastic (more like just removed all together), but anyway, we have a proper earth rod. Anyway sorting out the meter/CU area has been on the job list for a while. It's probably up to 40 years old, the main CU is chockerblock and there is the typical hotpotch of extra switch fuses etc. A new bigger CU, a main RCD, sorting out the main earth bonding etc. Probably starting with replacing the VOELCB with an RCD to give more space for the new CU, partly because that can go elsewhere on the mounting board - replacing a great big F-off metal main switch - there presumably because the house has a 3 phase supply. Though only 1 phase is used. In circumstances like that it can often work out simpler to install two CUs fed via split tails from a main switch. You can stick an ordinary 100mA trip RCD in one for all the lights and other circuits that do not need direct contact protection, and then have a 30mA trip RCD in a second CU for the power circuits. Often works out cheaper than having a £100 time delayed RCD cascaded in the same CU as the smaller threshold one. Ahh yes, that's a good suggestion, thanks. -- Chris French |
#27
Posted to uk.d-i-y
|
|||
|
|||
'Chattering' MCB
Thanks, but we are in the middle of Cambridgeshire... Ah - you're fixing fenland wiring! This may explain much. I removed a wiring run from actually inside the trough of the rainwater guttering in my old fenland bungalow. |
#28
Posted to uk.d-i-y
|
|||
|
|||
'Chattering' MCB
wrote:
I removed a wiring run from actually inside the trough of the rainwater guttering in my old fenland bungalow. Novel approach to keeping it cool perhaps! -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#29
Posted to uk.d-i-y
|
|||
|
|||
'Chattering' MCB
In message .com,
" writes Thanks, but we are in the middle of Cambridgeshire... Ah - you're fixing fenland wiring! Not quite on the fens, we are high up (approx 10m above sea level) -- Chris French |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Chattering Sony Tape Deck | Electronics Repair | |||
Chattering selenoid valve on Boiler | UK diy | |||
Reconditioning Chattering Well Water Pump Control Box Relay? | Electronics Repair | |||
Reconditioning Chattering Well Water Pump Control Box Relay? | Electronics Repair | |||
Chattering screw-drive 3/4hp Craftsman GDO | Home Repair |