Joist strength
Steve wrote:
I have downloaded the software from Tony's website and had a quick play. But it is clear that I need to follow the advice on there and print out the instructions! I setup a beam with two loading entries: one "U" (i.e. uniform) specified as 0.8, and one "P" (point) at .7m from distance, and a load of 1.6kN. So thanks also to Tony for generously making the software available to non professionals like myself. Yup, I will second that. Coming back to the joists, I had a gut feeling that deflection would be more than desired and your results back this up although you have quite rightly taken the worst case with the load in the centre of the span. In our case most of the load will be near to a sleeper wall for each leg. But I would rather be conservative and use worst case! That also assumed the leg directly over one joist - if it were to the side a little the the load would be more spread between two (I did leave the load sharing set to 2 however) One idea was to double the joists up i.e. putting extra joists in between but in the areas of high load to have double joists joined, but I had thought of glueing them together and bolting through the neutral access. Any problems with glueing and bolting? I would be a little wary of bolting a joist that is only 100mm high. Your standard 12mm bolts would hence be taking out over 10% of the joist depth at the point. You could glue, or use the spiked timber connectors on the bolts if going that route. I would have though that just nailing the joists side by side would be enough in this circumstance. I also had an extension to this idea...I thought of cutting 8" strips of 18mm WBP, glueing two together and then sandwiching that between two joists, all glued and bolted. In effect a 'T' beam. Obviously the ply can't extend the total length because of the sleeper walls but that would probably not matter as shear is unlikely to be a problem, I think. Any comments on this idea? Doable, but possibly overkill. If you wanted a beam stronger than a pair of timbers side by side, then the next option would usually be a flitch beam[1] (i.e. a pair of beams with a steel plate sandwiched between them, and bolted together). Not sure how realistic that is on only 4" of depth though. [1] Example 8mm steel plate flitch (with red passivated coating): http://www.internode.co.uk/loft/images/flitch.jpg -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#42
Posted to uk.d-i-y
|
|||
|
|||
Joist strength
Steve wrote:
One idea was to double the joists up i.e. putting extra joists in between but in the areas of high load to have double joists joined, but I had thought of glueing them together and bolting through the neutral access. Any problems with glueing and bolting? I'm sorry but access was not what I meant to type! Neutral axis Steve |
#43
Posted to uk.d-i-y
|
|||
|
|||
Joist strength
Bolting through the neutral axis will have negligible effect on the
stiffness of the beam A 12 mm hole is about an eighth of your depth, Stiffness proportional to depth cubed, so about 0.2% reduction.. There is no need to glue the beams together (as confirmed by my structural engineer) "Steve" wrote in message .uk... Steve wrote: One idea was to double the joists up i.e. putting extra joists in between but in the areas of high load to have double joists joined, but I had thought of glueing them together and bolting through the neutral access. Any problems with glueing and bolting? I'm sorry but access was not what I meant to type! Neutral axis |
#44
Posted to uk.d-i-y
|
|||
|
|||
Joist strength
John Rumm wrote:
Coming back to the joists, I had a gut feeling that deflection would be more than desired and your results back this up although you have quite rightly taken the worst case with the load in the centre of the span. In our case most of the load will be near to a sleeper wall for each leg. But I would rather be conservative and use worst case! That also assumed the leg directly over one joist - if it were to the side a little the the load would be more spread between two (I did leave the load sharing set to 2 however) No problem, you have confirmed what I thought and unless one is a structural engineer it is better to err on the side of caution. One idea was to double the joists up i.e. putting extra joists in between but in the areas of high load to have double joists joined, but I had thought of glueing them together and bolting through the neutral access. Any problems with glueing and bolting? I would be a little wary of bolting a joist that is only 100mm high. Your standard 12mm bolts would hence be taking out over 10% of the joist depth at the point. Yes, I see that but wouldn't the fact that the beam was drilled only in the neutral axis i.e. along the centre where I believe that the beam was neither under compression or expansion make this OK? I would also clamp the edges tightly whilst the glue sets. You could glue, or use the spiked timber connectors on the bolts if going that route. I would have though that just nailing the joists side by side would be enough in this circumstance. You are right. I just have an inherent distrust of nails, even big ones! I also had an extension to this idea...I thought of cutting 8" strips of 18mm WBP, glueing two together and then sandwiching that between two joists, all glued and bolted. In effect a 'T' beam. Obviously the ply can't extend the total length because of the sleeper walls but that would probably not matter as shear is unlikely to be a problem, I think. Any comments on this idea? Doable, but possibly overkill. If you wanted a beam stronger than a pair of timbers side by side, then the next option would usually be a flitch beam[1] (i.e. a pair of beams with a steel plate sandwiched between them, and bolted together). Not sure how realistic that is on only 4" of depth though. I did not know about flitch beams. Maybe my thoughts about deep depths of plywood sandwiched between the joists are my primitive way of re-inventing the wheel :-) However that has got me thinking that this might be the neatest, most elegant and best solution. Presumably a steel stockholder would cut and 'passivate' them for me. [1] Example 8mm steel plate flitch (with red passivated coating): http://www.internode.co.uk/loft/images/flitch.jpg Yes, I see it there - what does it have to support? Thanks again John. Steve |
#45
Posted to uk.d-i-y
|
|||
|
|||
Joist strength
"Steve" wrote in message . uk... Time soon to put new floor down in lounge, but it is a bit more involved. This floor has to support a substantial dead weight or two - A Steinway Concert Grand Piano that weighs in at 480kg, or about half a tonne. The weight is, according to Steinway, evenly distributed over the three legs i.e. 160kg per leg. The other dead load is a lighter but still heavy - Boston upright piano that is probably half the weight or less and with weight on four feet, although centred on a much smaller overall area. . The remaining "live" load will be furniture etc. - normal things :-) The existing joists are 4" by 2" and are at present supported by sleeper walls at 5 foot centres, the spacing between joists is 10" with no noggins. I plan to increase the number of joists by about two, depending on arranging things to suit the Caberboards that I think will do the job. Running double joists where the dead weight will be centred. This will, obviously, make it harder for noggins if they are needed to be fitted, but the close spacing between joists should make them unnecessary I think? Am I on the right track here? Any ideas or information would be most welcome before I do it and find that our beloved piano has crashed through the floor! Thanks Steve Hi, You could of course "Test" your floor before engaging in all this work, without any Pianos being involved. You get 7 adult men, who will weigh about 14 stone (75Kg each, 525Kg total), to stand where the heavier piano is to be placed, and 3 adult men (total 225Kg) to stand where the lighter piano is to stand. If the floor survives this test without any groaning, then you can get them to jump up and down to give the floor a shock load. If you are worried about the point loading then maybe you need to fit steel plates to the floor to spread the load. Ian. |
#46
Posted to uk.d-i-y
|
|||
|
|||
Joist strength
"Ian G" wrote in message ... 18mm ply glued and screwed to the top of the joists (instead of unglued chipboard) , forming a T beam was a solution proposed by a structural engineer and adopted by me when I did a loft conversion some years ago. We didn't put a piano up there, but the purchasers of the house did install a water bed and there have been no adverse reports from neighbours whom I have remained in contact with. The increase in strength over the unglued floor was impressive, confirming in practice what the Moment of Inertia calculations indicated. We were able to jump up and down on the floor and detect very little spring. I would expect it to be even better if you fix a steel plate to the bottom and ply to the top. Steel is better in tension. Just fixing a 3mm steel plate to either side of the joists will make a huge difference as the wood stops the plate from warping and the 4" depth of steel doesn't bend much. My conservatory roof is supported in a similar way by ally strips inserted in channels in the plastic and I can walk on it and I am not thin. |
#47
Posted to uk.d-i-y
|
|||
|
|||
Joist strength
On Thu, 20 Sep 2007 23:08:32 GMT, "The Medway Handyman"
wrote: Ok great, so what do Z, B, D & I stand for? Boinggg said ZBDI - time for bed... Geo |
#49
Posted to uk.d-i-y
|
|||
|
|||
Joist strength
Steve wrote:
Yes, I see that but wouldn't the fact that the beam was drilled only in the neutral axis i.e. along the centre where I believe that the beam was neither under compression or expansion make this OK? I would also clamp the edges tightly whilst the glue sets. you have to be a little careful where you drill - i.e. not to close to the ends or you risk allowing the beam to split. You are right. I just have an inherent distrust of nails, even big ones! Plenty of houses have stood for hundreds of years held together by little else. ;-) Doable, but possibly overkill. If you wanted a beam stronger than a pair of timbers side by side, then the next option would usually be a flitch beam[1] (i.e. a pair of beams with a steel plate sandwiched between them, and bolted together). Not sure how realistic that is on only 4" of depth though. I did not know about flitch beams. Maybe my thoughts about deep depths of plywood sandwiched between the joists are my primitive way of re-inventing the wheel :-) However that has got me thinking that this might be the neatest, most elegant and best solution. Presumably a steel stockholder would cut and 'passivate' them for me. Indeed they will - they will drill them for you as well. Superbeam will model them for you as well. [1] Example 8mm steel plate flitch (with red passivated coating): http://www.internode.co.uk/loft/images/flitch.jpg Yes, I see it there - what does it have to support? The one in the photo was I believe "E": http://www.internode.co.uk/temp/beam-layout.gif Which as you can see gets a share of the load of pretty much everything at the front of the loft, including the previously pictured dwarf wall. So 0.8kN/m uniform load from the floor, a 5.7kN point load at 0.7m from beam F (stringer that carried the main front floor joists - present because getting at the existing lintle would have been too difficult), and a 11kN point load at 2.8m from beam C (triple joist) that carried two sets of floor joists, and a share of at least three partition walls.... oh and a bit of roof. So all in all about a nominal 20kN or two tonnes in total. The centre span deflection was calculated at just under 9mm. In context: http://www.internode.co.uk/loft/floor.htm -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#50
Posted to uk.d-i-y
|
|||
|
|||
Joist strength
Ian G wrote:
Bolting through the neutral axis will have negligible effect on the stiffness of the beam A 12 mm hole is about an eighth of your depth, Stiffness proportional to depth cubed, so about 0.2% reduction.. There is no need to glue the beams together (as confirmed by my structural engineer) You can stick these on each bolt between the beams: http://www.screwfix.com/sfd/i/cat/50/p1704550_x.jpg (and flat plate washers either side) -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#51
Posted to uk.d-i-y
|
|||
|
|||
Joist strength
Ian French wrote:
Am I on the right track here? Any ideas or information would be most welcome before I do it and find that our beloved piano has crashed through the floor! Thanks Steve Hi, You could of course "Test" your floor before engaging in all this work, without any Pianos being involved. I think that there is definitely some strengthening to be done. You get 7 adult men, who will weigh about 14 stone (75Kg each, 525Kg total), to stand where the heavier piano is to be placed, and 3 adult men (total 225Kg) to stand where the lighter piano is to stand. Our original plan to test the floor was to fill three 200 litre water butts to full in the strategic positions and then us and friends to jump up and down to see if the floor failed! This plan fell through, sorry!, once I started taking the floor up and found that it, most probably, would have failed catastrophically due to the poor state that the floor was in and also a lot of past bodges that needed attention. If the floor survives this test without any groaning, then you can get them to jump up and down to give the floor a shock load. If you are worried about the point loading then maybe you need to fit steel plates to the floor to spread the load. The point loading is a worry but with the proper cups under the castors and stiffened joists this does not seem to be so much of a worry as absolute strength. Steve |
#52
Posted to uk.d-i-y
|
|||
|
|||
Joist strength
John Rumm wrote:
Steve wrote: Yes, I see that but wouldn't the fact that the beam was drilled only in the neutral axis i.e. along the centre where I believe that the beam was neither under compression or expansion make this OK? I would also clamp the edges tightly whilst the glue sets. you have to be a little careful where you drill - i.e. not to close to the ends or you risk allowing the beam to split. You are right. I just have an inherent distrust of nails, even big ones! Plenty of houses have stood for hundreds of years held together by little else. ;-) Doable, but possibly overkill. If you wanted a beam stronger than a pair of timbers side by side, then the next option would usually be a flitch beam[1] (i.e. a pair of beams with a steel plate sandwiched between them, and bolted together). Not sure how realistic that is on only 4" of depth though. I did not know about flitch beams. Maybe my thoughts about deep depths of plywood sandwiched between the joists are my primitive way of re-inventing the wheel :-) However that has got me thinking that this might be the neatest, most elegant and best solution. Presumably a steel stockholder would cut and 'passivate' them for me. Indeed they will - they will drill them for you as well. Superbeam will model them for you as well. [1] Example 8mm steel plate flitch (with red passivated coating): http://www.internode.co.uk/loft/images/flitch.jpg Yes, I see it there - what does it have to support? The one in the photo was I believe "E": http://www.internode.co.uk/temp/beam-layout.gif Which as you can see gets a share of the load of pretty much everything at the front of the loft, including the previously pictured dwarf wall. So 0.8kN/m uniform load from the floor, a 5.7kN point load at 0.7m from beam F (stringer that carried the main front floor joists - present because getting at the existing lintle would have been too difficult), and a 11kN point load at 2.8m from beam C (triple joist) that carried two sets of floor joists, and a share of at least three partition walls.... oh and a bit of roof. So all in all about a nominal 20kN or two tonnes in total. The centre span deflection was calculated at just under 9mm. In context: http://www.internode.co.uk/loft/floor.htm Wow! Thanks for that John. I don't know why I have not visited your page before. Absolutely fascinating and clear straightforward information but with your knowledge clearly showing through . Bookmarked and when I have the time, I will be going through it all to get ideas for further projects! Tee Hee - expect further questions! Steve |
#53
Posted to uk.d-i-y
|
|||
|
|||
Joist strength
Steve wrote:
Wow! Thanks for that John. I don't know why I have not visited your page before. Absolutely fascinating and clear straightforward information but with your knowledge clearly showing through . Bookmarked and when I have the time, I will be going through it all to get ideas for further projects! Tee Hee - expect further questions! Beware that some of the planing and building regs related information is now out of date, and other changes are afoot. (hence if you are planning a conversion - start now, it will be harder later!) -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#54
Posted to uk.d-i-y
|
|||
|
|||
Joist strength
On 20 Sep, 16:30, Steve wrote:
Time soon to put new floor down in lounge, but it is a bit more involved. This floor has to support a substantial dead weight or two - A Steinway Concert Grand Piano that weighs in at 480kg, or about half a tonne. The weight is, according to Steinway, evenly distributed over the three legs i.e. 160kg per leg. The other dead load is a lighter but still heavy - Boston upright piano that is probably half the weight or less and with weight on four feet, although centred on a much smaller overall area. . The remaining "live" load will be furniture etc. - normal things :-) The existing joists are 4" by 2" and are at present supported by sleeper walls at 5 foot centres, the spacing between joists is 10" with no noggins. I plan to increase the number of joists by about two, depending on arranging things to suit the Caberboards that I think will do the job. Running double joists where the dead weight will be centred. This will, obviously, make it harder for noggins if they are needed to be fitted, but the close spacing between joists should make them unnecessary I think? Am I on the right track here? Any ideas or information would be most welcome before I do it and find that our beloved piano has crashed through the floor! Thanks Steve Dear Steve I suspect I am probably the man to help you here as I have a degree in timber engineering (ICST 1975 Civ Eng Dept) and have spent the last 30 plus years working on such floors in a practical fashion. No one in the group has taken into account a factor in the design of timber floors called "Duration of Load". (in essence were you to load a beam say for a fraction of a second it would take 130% of its (so called) maximum stress (derived from 5 min tests to destruction) of 100% by definition and conversely IF you were to load it to as little as 60% of its "maximum" it may well fail though it may take some years so to do. This is particularly true if the timber is green and goes through the fibre saturation point under load and vast proportional creeps are manifest... So you need to take that into account and the Codes of Practice do so. On a practical basis you need to do the following carefully identify and lift up the floorboards (marking with pencil so you know where they come from) the board in the areas of the pianos and beyond the next wall plates - staggering the cuts (if needed) to alternate joists and cutting on the joists. Use a right angle square pencil and ~Fien multi master to get neat cuts or lift all the board Once you have access to the sub floor (check ventitlation whilst you are at it) check the structure of the sleeper walls and that they are sound enought and founded well - improve if needed Consider at this point if it is worth it putting in an addtional sleeper wall - the closer to you point loads the better consider putting in INDIVIDUAL supports to the concrete as suggested by others whilst on about the concrete consider a trial pit remote from the load to see how thick it is and if it is ok fine If not spread the load on the point supports with 4" of new concrete with 142 mesh so it is over the old concrete I guess about 1 m square for each corner would be more than ample but if in doubt calculate (engineer) Next simply run more 4" joists alongside the old ones on the existing and new wall plates such as to cover the 6" of your spreader cicles - that is only likely to be 3 or at most 4 new joists between the two wall plates for each of the legs and with a bit of luck two will coincide! 4 x 2" does not cost much and it is not likely that you will need much more than 8' for each set of 3 If you are fussy screw or nail them together so you get a shared effect and avoid individual variations in strenth becoming manifest lay floor boards back down - I would use brass screws but I am fussy Any problems come back to me If you can scan and send me a plan locating point loads and existing wps I will work out a rough idea of where to go should you so want on our pro bono terms - ie FOC - you indemnify us! Chris |
#55
Posted to uk.d-i-y
|
|||
|
|||
Joist strength
wrote:
No one in the group has taken into account a factor in the design of timber floors called "Duration of Load". (in essence were you to load No need to worry, we did - at least implicitly... I used a loading duration of 1.0 (long term) on the calculation I did with superbeam. ;-) -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#56
Posted to uk.d-i-y
|
|||
|
|||
Joist strength
On Sep 21, 8:56 am, Mogga wrote:
On Fri, 21 Sep 2007 00:54:33 -0700, Robert wrote: In fact I face a related problem. I plan to put an upright piano into our 1960s house and the position it will occupy means that all the weight will be one two joists running parallelto the piano. the joists in the house are inadequate; I have alrady had problems with the floor moving when I piled a lot of books on it, so I plan to add How many books? Thousands? Yes, probably about two thousand books. Robert |
#57
Posted to uk.d-i-y
|
|||
|
|||
Joist strength
|
#58
Posted to uk.d-i-y
|
|||
|
|||
Joist strength
On Sep 21, 11:07 am, "dennis@home"
wrote: "Steve" wrote in message . uk... The finished floor will be thickened by a further 15mm as we have T&G engineered oak floor to go on top of the Caberboard. This should help with the point loading but will not help much with any bounce if there is any. Metal plates would be a good idea but would be difficult to implement with the oak floor. What will stop the piano marking the floor? 160kg on most castors is going to put grooves in a wooden floor IME. It is unlikely that the piano would be moved from the spot. There just isn't the room! I wondered what the acoustics will be like and if it will hold tune if the floor sags unevenly. Is there a mechanism to level the piano or doesn't it matter? Have you considered casting some concrete pads under the floor and building some small supporting piers in the correct places? It is probably easy if you are going to cover the floor. BTW you can get some nice electronic pianos these days that play like the real thing and don't need maintenance every six months, take up less space and are cheap(er). ....and you can set the switch so it sounds exactly like a Steinway. I am trying hard to persuade myself that I want one of these (rather than real piano) because of its ability to use headphones and not disturb others. But I am not persuaded. Robert |
#59
Posted to uk.d-i-y
|
|||
|
|||
Joist strength
RobertL wrote:
...and you can set the switch so it sounds exactly like a Steinway. I am trying hard to persuade myself that I want one of these (rather than real piano) because of its ability to use headphones and not disturb others. But I am not persuaded. LOL! No, nor are we :-) Steve |
#60
Posted to uk.d-i-y
|
|||
|
|||
Joist strength
"RobertL" wrote in message oups.com... BTW you can get some nice electronic pianos these days that play like the real thing and don't need maintenance every six months, take up less space and are cheap(er). ...and you can set the switch so it sounds exactly like a Steinway. I am trying hard to persuade myself that I want one of these (rather than real piano) because of its ability to use headphones and not disturb others. But I am not persuaded. The Yamaha baby grand is supposed to be good.. I have never seen one myself. My daughter has to put up with a cheap Korg piano and we still struggle for space. It sounds OK but its better if I connect my Yamaha synthbox to its MIDI. There are much better synths about including an add in card for mine that is supposed to be extremely good but I doubt if I could tell. |
#61
Posted to uk.d-i-y
|
|||
|
|||
Joist strength
"Steve" wrote in message news RobertL wrote: ...and you can set the switch so it sounds exactly like a Steinway. I am trying hard to persuade myself that I want one of these (rather than real piano) because of its ability to use headphones and not disturb others. But I am not persuaded. LOL! No, nor are we :-) As you suffer from someone who is pitch perfect I can see you having problems.. do you have your grand tuned frequently so it sounds excellent for a week or two a month or do you buy an electronic one that sounds OK, but not excellent, all the time? I went for the electronic one and it fits in the car too. |
#62
Posted to uk.d-i-y
|
|||
|
|||
Joist strength
On 21 Sep, 17:30, "Ian G" wrote:
The ply was glued and screwed to the top of the joists substituting for, but perhaps a couple of millimetres less deep than the more conventional chipboard. I think a difficulty in sandwiching between joists might be in maintaining the strength at the joints. Presumably glue & screw battens to the joists then glue & screw your inserts to these battens? Now if you could somehow get access to the underside of the joists with sheet plywood and complete the box, you are talking about a MAJOR increase in stiffness ;-) Kerching !! how about making up a timber box beams? A pair of new joists say 65mm deep by 50mm wide. glue & screw 18mm ply top & bottom & slot into inter joist space screwing through existing joists into new ones, or resting Does anybody (eg Tony) know if Superbeam will model such a system? I'm still working on my shed, and Superbeam tells me that the 2x3 rafters at 2' centres aren't good enough to hold a heavy green roof. On the other hand, if I glue and screw 18mm Stirling board on top that helps quite a bit, and if I fit some thin ply underneath, that would help even more. |
#63
Posted to uk.d-i-y
|
|||
|
|||
Joist strength
On 27 Sep, 14:00, Tony Bryer wrote:
On Thu, 27 Sep 2007 04:45:59 -0700 Martin Bonner wrote : Does anybody (eg Tony) know if Superbeam will model such a system? I'm still working on my shed, and Superbeam tells me that the 2x3 rafters at 2' centres aren't good enough to hold a heavy green roof. Without checking out the calcs (am drowning under work ATM), most timber calculations result in the member being sized to keep the deflection within limits, and the standard limit (0.003 x span) is really to do with preventing damage to plaster finishes and stopping floors feeling uncomfortably springy (whilst being safe). If the calculation shows the applied bending stress as being less than the permissible then all should be OK. Actually the stress was a problem with 45x70mm beams (the actual size), but was OK with 45x88mm (assuming the OSB just adds 18mm to the thickness of the beam). I /think/ I can get away with that. a) I know that OSB will not be as strong in compression as C16 timber. b) I am relying on the screw + glue transferring the entire load -but- c) I am not really adding a 45mm strip of OSB - I am adding a 590mm of the stuff (no, I don't think that will be 13 times as strong as a 45mm strip; but it ought to bring it up to C16 levels). What I was hoping was that SuperBeam would be able to model such a composite structure - but I suppose it isn't a fully blown finite element modelling package (It certainly isn't priced like one ... though you wouldn't know that from the support service :-) |
#64
Posted to uk.d-i-y
|
|||
|
|||
Joist strength
On Thu, 27 Sep 2007 04:45:59 -0700 Martin Bonner wrote :
Does anybody (eg Tony) know if Superbeam will model such a system? I'm still working on my shed, and Superbeam tells me that the 2x3 rafters at 2' centres aren't good enough to hold a heavy green roof. Without checking out the calcs (am drowning under work ATM), most timber calculations result in the member being sized to keep the deflection within limits, and the standard limit (0.003 x span) is really to do with preventing damage to plaster finishes and stopping floors feeling uncomfortably springy (whilst being safe). If the calculation shows the applied bending stress as being less than the permissible then all should be OK. -- Tony Bryer SDA UK 'Software to build on' http://www.sda.co.uk |
#65
Posted to uk.d-i-y
|
|||
|
|||
Joist strength
"Martin Bonner" wrote in message ups.com... On the other hand, if I glue and screw 18mm Stirling board on top that helps quite a bit, and if I fit some thin ply underneath, that would help even more. I think I can confirm that from experience.. I have just built a shed and used 18mm ply glued to 25mm polystyrene glued to 6mm WBP for the floor. It is very stiff even before putting it onto the 4x2 joists 5 foot span. Once its on the joists at 20" centres myself, my wife and my daughter can jump up and down on it and it hardly moves. I suspect it was a bit OTT. |
#66
Posted to uk.d-i-y
|
|||
|
|||
Joist strength
On Thu, 27 Sep 2007 05:37:20 -0700 Martin Bonner wrote :
What I was hoping was that SuperBeam would be able to model such a composite structure - but I suppose it isn't a fully blown finite element modelling package (It certainly isn't priced like one ... though you wouldn't know that from the support service :-) Afraid not since (a) I'm not that clever; and (b) over the years there have been lots of requests for enhancements that would destroy what it is - a nice simple package for nice simple beams. -- Tony Bryer SDA UK 'Software to build on' http://www.sda.co.uk |
Reply |
|
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Strength of different hardwoods | Woodworking | |||
Tenon Strength / Rail strength- Max? | Woodworking | |||
bracket strength | Metalworking | |||
0.125 Cu plate strength | Metalworking | |||
strength of timber | UK diy |