Home |
Search |
Today's Posts |
|
UK diy (uk.d-i-y) For the discussion of all topics related to diy (do-it-yourself) in the UK. All levels of experience and proficency are welcome to join in to ask questions or offer solutions. |
Reply |
|
LinkBack | Thread Tools | Display Modes |
#1
Posted to uk.d-i-y
|
|||
|
|||
Connecting an gas hob/electric oven cooker
The gas has been connected.
The electrical connection needs to be a double pole switch the feed cable needs to be H05RR-F section 3x1,1.5mm squared. It is the electrical connection that I need to have explained to me. Is it ok to connect to the 13amp circuit using a switched spur. and is there anything that I need to do. Thanks for your time. |
#2
Posted to uk.d-i-y
|
|||
|
|||
Connecting an gas hob/electric oven cooker
In article ,
"TWEEZER" writes: The gas has been connected. The electrical connection needs to be a double pole switch the feed cable needs to be H05RR-F section 3x1,1.5mm squared. It is the electrical connection that I need to have explained to me. Is it ok to connect to the 13amp circuit using a switched spur. If it was, it would have probably come with a lead with a 13A plug on the end. What's the electrical power rating of the unit? and is there anything that I need to do. Thanks for your time. -- Andrew Gabriel [email address is not usable -- followup in the newsgroup] |
#3
Posted to uk.d-i-y
|
|||
|
|||
Connecting an gas hob/electric oven cooker
"Andrew Gabriel" wrote in message ... In article , "TWEEZER" writes: The gas has been connected. The electrical connection needs to be a double pole switch the feed cable needs to be H05RR-F section 3x1,1.5mm squared. It is the electrical connection that I need to have explained to me. Is it ok to connect to the 13amp circuit using a switched spur. If it was, it would have probably come with a lead with a 13A plug on the end. What's the electrical power rating of the unit? and is there anything that I need to do. Thanks for your time. -- Andrew Gabriel [email address is not usable -- followup in the newsgroup] Hi Andrew It says on the label 12KW. 873G/H 230V- 50H 3370W Cheers. |
#4
Posted to uk.d-i-y
|
|||
|
|||
Connecting an gas hob/electric oven cooker
"TWEEZER" wrote in message ... "Andrew Gabriel" wrote in message ... In article , "TWEEZER" writes: The gas has been connected. The electrical connection needs to be a double pole switch the feed cable needs to be H05RR-F section 3x1,1.5mm squared. It is the electrical connection that I need to have explained to me. Is it ok to connect to the 13amp circuit using a switched spur. If it was, it would have probably come with a lead with a 13A plug on the end. What's the electrical power rating of the unit? and is there anything that I need to do. Thanks for your time. -- Andrew Gabriel [email address is not usable -- followup in the newsgroup] Hi Andrew It says on the label 12KW. 873G/H 230V- 50H 3370W Cheers. My cooker has it's own 6mm cable from the consumer unit via a large switch! |
#5
Posted to uk.d-i-y
|
|||
|
|||
Connecting an gas hob/electric oven cooker
In message , TWEEZER
writes "Andrew Gabriel" wrote in message . .. In article , "TWEEZER" writes: The gas has been connected. The electrical connection needs to be a double pole switch the feed cable needs to be H05RR-F section 3x1,1.5mm squared. It is the electrical connection that I need to have explained to me. Is it ok to connect to the 13amp circuit using a switched spur. If it was, it would have probably come with a lead with a 13A plug on the end. What's the electrical power rating of the unit? It says on the label 12KW. 873G/H 230V- 50H 3370W Cheers. 12KW at 230V would need ~52A. Perhaps you should tells us the make & model of the oven... -- Si |
#6
Posted to uk.d-i-y
|
|||
|
|||
Connecting an gas hob/electric oven cooker
In article ,
"TWEEZER" writes: "Andrew Gabriel" wrote in message ... In article , "TWEEZER" writes: The gas has been connected. The electrical connection needs to be a double pole switch the feed cable needs to be H05RR-F section 3x1,1.5mm squared. It is the electrical connection that I need to have explained to me. Is it ok to connect to the 13amp circuit using a switched spur. If it was, it would have probably come with a lead with a 13A plug on the end. What's the electrical power rating of the unit? Hi Andrew It says on the label 12KW. 873G/H 230V- 50H 3370W Let's assume the 12kW is the gas and the 3370W is the electricity. That's too much for a 13A plug or spur. It was probably designed for a 16A plug used in some other EU countries. -- Andrew Gabriel [email address is not usable -- followup in the newsgroup] |
#7
Posted to uk.d-i-y
|
|||
|
|||
Connecting an gas hob/electric oven cooker
"Andrew Gabriel" wrote in message ... In article , "TWEEZER" writes: "Andrew Gabriel" wrote in message ... In article , "TWEEZER" writes: The gas has been connected. The electrical connection needs to be a double pole switch the feed cable needs to be H05RR-F section 3x1,1.5mm squared. It is the electrical connection that I need to have explained to me. Is it ok to connect to the 13amp circuit using a switched spur. If it was, it would have probably come with a lead with a 13A plug on the end. What's the electrical power rating of the unit? Hi Andrew It says on the label 12KW. 873G/H 230V- 50H 3370W Let's assume the 12kW is the gas and the 3370W is the electricity. That's too much for a 13A plug or spur. It was probably designed for a 16A plug used in some other EU countries. -- Andrew Gabriel [email address is not usable -- followup in the newsgroup] Its a Delonghi DFS 903 freestanding range cooker |
#8
Posted to uk.d-i-y
|
|||
|
|||
Connecting an gas hob/electric oven cooker
TWEEZER wrote:
Is it ok to connect to the 13amp circuit using a switched spur. Probably not. If it it were a relatively lightly loaded ring circuit in the first place (which kitchen ones almost never are!) then you could just squeeze in with a connection to it allowing for diversity (which reduces to maximum 14.6A load to a typical maximum of under 12A) It says on the label 12KW. 873G/H 230V- 50H 3370W My preference would be a dedicated radial with a 16A MCB at the consumer unit (non RCD side if it is a split load one). Cable choice would depend on the length of the run, any other local factors, and what capability for expansion you want to leave for the future. Connection to the cooker end should be done via a cooker face plate switch, and cable outlet. -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#9
Posted to uk.d-i-y
|
|||
|
|||
Connecting an gas hob/electric oven cooker
On Mon, 03 Sep 2007 05:25:54 +0100, John Rumm
mused: TWEEZER wrote: Is it ok to connect to the 13amp circuit using a switched spur. Probably not. If it it were a relatively lightly loaded ring circuit in the first place (which kitchen ones almost never are!) then you could just squeeze in with a connection to it allowing for diversity (which reduces to maximum 14.6A load to a typical maximum of under 12A) It says on the label 12KW. 873G/H 230V- 50H 3370W My preference would be a dedicated radial with a 16A MCB at the consumer unit (non RCD side if it is a split load one). Cable choice would depend on the length of the run, any other local factors, and what capability for expansion you want to leave for the future. Connection to the cooker end should be done via a cooker face plate switch, and cable outlet. I'd use a 20A double pole switch, tidier and easier to wire. -- Regards, Stuart. |
#10
Posted to uk.d-i-y
|
|||
|
|||
Connecting an gas hob/electric oven cooker
Owain wrote:
John Rumm wrote: Is it ok to connect to the 13amp circuit using a switched spur. Probably not. If it it were a relatively lightly loaded ring circuit in the first place (which kitchen ones almost never are!) then you could just squeeze in with a connection to it allowing for diversity (which reduces to maximum 14.6A load to a typical maximum of under 12A) Can you apply diversity though, it's one oven which will be full load (or no load), not a collection of rings which exhibit diversity? The thermostatic control will give you a time averaged reduction in maximum current, so I expect you can[1]. Connection should be via a method that allows for the maximum current however, so a 13A FCU is out. Treating it as an unfused spur (i.e. with the cable sized to as to be adequately fault protected by the circuit MCB, and the over current limit imposed by the appliance spec) may be acceptable. (although as I said, I would not recommend doing this in the first place, and the chances that there is sufficient spare capacity on the circuit to allow for a big point load like this is probably nil anyway) [1] [311-01-01] does not have much to say on it, and the OSG (table 1B) just refers to a "Household cooking appliance" without further clarification as to whether an appliance which uses electricity for just the oven should be excluded. -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#11
Posted to uk.d-i-y
|
|||
|
|||
Connecting an gas hob/electric oven cooker
On Sun, 02 Sep 2007 18:02:18 +0100, Si wrote:
In message , TWEEZER writes "Andrew Gabriel" wrote in message .. . In article , "TWEEZER" writes: The gas has been connected. The electrical connection needs to be a double pole switch the feed cable needs to be H05RR-F section 3x1,1.5mm squared. It is the electrical connection that I need to have explained to me. Is it ok to connect to the 13amp circuit using a switched spur. If it was, it would have probably come with a lead with a 13A plug on the end. What's the electrical power rating of the unit? It says on the label 12KW. 873G/H 230V- 50H 3370W Cheers. 12KW at 230V would need ~52A. Perhaps you should tells us the make & model of the oven... The 12kW likely refers to the total of the gas burners. Then current rating is 3370/230 = 14.7A so can't quite go on a 13A plug. This needs a dedicated circuit with a 15A or 16A MCB. A double pole isolator (20A and 45A) within 2m of the oven. Without checking I would expect 2.5mm² T&E to be suitable for the fixed wiring. -- Ed Sirett - Property maintainer and registered gas fitter. The FAQ for uk.diy is at http://www.diyfaq.org.uk Gas fitting FAQ http://www.makewrite.demon.co.uk/GasFitting.html Sealed CH FAQ http://www.makewrite.demon.co.uk/SealedCH.html Choosing a Boiler FAQ http://www.makewrite.demon.co.uk/BoilerChoice.html |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|