The gas has been connected.
The electrical connection needs to be a double pole switch
the feed cable needs to be H05RR-F section 3x1,1.5mm squared.
It is the electrical connection that I need to have explained to me.
Is it ok to connect to the 13amp circuit using a switched spur.
and is there anything that I need to do.
Thanks for your time.


  #2   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 11,175
Default Connecting an gas hob/electric oven cooker

In article ,
"TWEEZER" writes:
The gas has been connected.
The electrical connection needs to be a double pole switch
the feed cable needs to be H05RR-F section 3x1,1.5mm squared.
It is the electrical connection that I need to have explained to me.
Is it ok to connect to the 13amp circuit using a switched spur.


If it was, it would have probably come with a lead with a 13A
plug on the end. What's the electrical power rating of the unit?

and is there anything that I need to do.
Thanks for your time.


--
Andrew Gabriel
[email address is not usable -- followup in the newsgroup]
  #3   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 6
Default Connecting an gas hob/electric oven cooker


"Andrew Gabriel" wrote in message
...
In article ,
"TWEEZER" writes:
The gas has been connected.
The electrical connection needs to be a double pole switch
the feed cable needs to be H05RR-F section 3x1,1.5mm squared.
It is the electrical connection that I need to have explained to me.
Is it ok to connect to the 13amp circuit using a switched spur.


If it was, it would have probably come with a lead with a 13A
plug on the end. What's the electrical power rating of the unit?

and is there anything that I need to do.
Thanks for your time.


--
Andrew Gabriel
[email address is not usable -- followup in the newsgroup]


Hi Andrew

It says on the label 12KW. 873G/H 230V- 50H 3370W
Cheers.


  #4   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 7
Default Connecting an gas hob/electric oven cooker


"TWEEZER" wrote in message
...

"Andrew Gabriel" wrote in message
...
In article ,
"TWEEZER" writes:
The gas has been connected.
The electrical connection needs to be a double pole switch
the feed cable needs to be H05RR-F section 3x1,1.5mm squared.
It is the electrical connection that I need to have explained to me.
Is it ok to connect to the 13amp circuit using a switched spur.


If it was, it would have probably come with a lead with a 13A
plug on the end. What's the electrical power rating of the unit?

and is there anything that I need to do.
Thanks for your time.


--
Andrew Gabriel
[email address is not usable -- followup in the newsgroup]


Hi Andrew

It says on the label 12KW. 873G/H 230V- 50H 3370W
Cheers.

My cooker has it's own 6mm cable from the consumer unit via a large switch!


  #5   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 369
Default Connecting an gas hob/electric oven cooker

In message , TWEEZER
writes
"Andrew Gabriel" wrote in message
. ..
In article ,
"TWEEZER" writes:
The gas has been connected.
The electrical connection needs to be a double pole switch
the feed cable needs to be H05RR-F section 3x1,1.5mm squared.
It is the electrical connection that I need to have explained to me.
Is it ok to connect to the 13amp circuit using a switched spur.


If it was, it would have probably come with a lead with a 13A
plug on the end. What's the electrical power rating of the unit?


It says on the label 12KW. 873G/H 230V- 50H 3370W
Cheers.

12KW at 230V would need ~52A.

Perhaps you should tells us the make & model of the oven...

--
Si


  #6   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 11,175
Default Connecting an gas hob/electric oven cooker

In article ,
"TWEEZER" writes:

"Andrew Gabriel" wrote in message
...
In article ,
"TWEEZER" writes:
The gas has been connected.
The electrical connection needs to be a double pole switch
the feed cable needs to be H05RR-F section 3x1,1.5mm squared.
It is the electrical connection that I need to have explained to me.
Is it ok to connect to the 13amp circuit using a switched spur.


If it was, it would have probably come with a lead with a 13A
plug on the end. What's the electrical power rating of the unit?


Hi Andrew
It says on the label 12KW. 873G/H 230V- 50H 3370W


Let's assume the 12kW is the gas and the 3370W is the electricity.

That's too much for a 13A plug or spur. It was probably designed
for a 16A plug used in some other EU countries.

--
Andrew Gabriel
[email address is not usable -- followup in the newsgroup]
  #7   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 6
Default Connecting an gas hob/electric oven cooker


"Andrew Gabriel" wrote in message
...
In article ,
"TWEEZER" writes:

"Andrew Gabriel" wrote in message
...
In article ,
"TWEEZER" writes:
The gas has been connected.
The electrical connection needs to be a double pole switch
the feed cable needs to be H05RR-F section 3x1,1.5mm squared.
It is the electrical connection that I need to have explained to me.
Is it ok to connect to the 13amp circuit using a switched spur.

If it was, it would have probably come with a lead with a 13A
plug on the end. What's the electrical power rating of the unit?


Hi Andrew
It says on the label 12KW. 873G/H 230V- 50H 3370W


Let's assume the 12kW is the gas and the 3370W is the electricity.

That's too much for a 13A plug or spur. It was probably designed
for a 16A plug used in some other EU countries.

--
Andrew Gabriel
[email address is not usable -- followup in the newsgroup]



Its a Delonghi DFS 903 freestanding range cooker



  #8   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 25,191
Default Connecting an gas hob/electric oven cooker

TWEEZER wrote:

Is it ok to connect to the 13amp circuit using a switched spur.


Probably not. If it it were a relatively lightly loaded ring circuit in
the first place (which kitchen ones almost never are!) then you could
just squeeze in with a connection to it allowing for diversity (which
reduces to maximum 14.6A load to a typical maximum of under 12A)

It says on the label 12KW. 873G/H 230V- 50H 3370W


My preference would be a dedicated radial with a 16A MCB at the consumer
unit (non RCD side if it is a split load one). Cable choice would depend
on the length of the run, any other local factors, and what capability
for expansion you want to leave for the future.

Connection to the cooker end should be done via a cooker face plate
switch, and cable outlet.

--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/
  #9   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 774
Default Connecting an gas hob/electric oven cooker

On Mon, 03 Sep 2007 05:25:54 +0100, John Rumm
mused:

TWEEZER wrote:

Is it ok to connect to the 13amp circuit using a switched spur.


Probably not. If it it were a relatively lightly loaded ring circuit in
the first place (which kitchen ones almost never are!) then you could
just squeeze in with a connection to it allowing for diversity (which
reduces to maximum 14.6A load to a typical maximum of under 12A)

It says on the label 12KW. 873G/H 230V- 50H 3370W


My preference would be a dedicated radial with a 16A MCB at the consumer
unit (non RCD side if it is a split load one). Cable choice would depend
on the length of the run, any other local factors, and what capability
for expansion you want to leave for the future.

Connection to the cooker end should be done via a cooker face plate
switch, and cable outlet.


I'd use a 20A double pole switch, tidier and easier to wire.
--
Regards,
Stuart.
  #10   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 25,191
Default Connecting an gas hob/electric oven cooker

Owain wrote:
John Rumm wrote:
Is it ok to connect to the 13amp circuit using a switched spur.

Probably not. If it it were a relatively lightly loaded ring circuit
in the first place (which kitchen ones almost never are!) then you
could just squeeze in with a connection to it allowing for diversity
(which reduces to maximum 14.6A load to a typical maximum of under 12A)


Can you apply diversity though, it's one oven which will be full load
(or no load), not a collection of rings which exhibit diversity?


The thermostatic control will give you a time averaged reduction in
maximum current, so I expect you can[1]. Connection should be via a
method that allows for the maximum current however, so a 13A FCU is out.
Treating it as an unfused spur (i.e. with the cable sized to as to be
adequately fault protected by the circuit MCB, and the over current
limit imposed by the appliance spec) may be acceptable.

(although as I said, I would not recommend doing this in the first
place, and the chances that there is sufficient spare capacity on the
circuit to allow for a big point load like this is probably nil anyway)

[1] [311-01-01] does not have much to say on it, and the OSG (table 1B)
just refers to a "Household cooking appliance" without further
clarification as to whether an appliance which uses electricity for just
the oven should be excluded.


--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/


  #11   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 2,231
Default Connecting an gas hob/electric oven cooker

On Sun, 02 Sep 2007 18:02:18 +0100, Si wrote:

In message , TWEEZER
writes
"Andrew Gabriel" wrote in message
.. .
In article ,
"TWEEZER" writes:
The gas has been connected.
The electrical connection needs to be a double pole switch
the feed cable needs to be H05RR-F section 3x1,1.5mm squared.
It is the electrical connection that I need to have explained to me.
Is it ok to connect to the 13amp circuit using a switched spur.

If it was, it would have probably come with a lead with a 13A
plug on the end. What's the electrical power rating of the unit?


It says on the label 12KW. 873G/H 230V- 50H 3370W
Cheers.

12KW at 230V would need ~52A.

Perhaps you should tells us the make & model of the oven...


The 12kW likely refers to the total of the gas burners.

Then current rating is 3370/230 = 14.7A so can't quite go on a 13A plug.

This needs a dedicated circuit with a 15A or 16A MCB. A double pole
isolator (20A and 45A) within 2m of the oven.

Without checking I would expect 2.5mm² T&E to be suitable for the fixed
wiring.



--
Ed Sirett - Property maintainer and registered gas fitter.
The FAQ for uk.diy is at http://www.diyfaq.org.uk
Gas fitting FAQ http://www.makewrite.demon.co.uk/GasFitting.html
Sealed CH FAQ http://www.makewrite.demon.co.uk/SealedCH.html
Choosing a Boiler FAQ http://www.makewrite.demon.co.uk/BoilerChoice.html
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
question on connecting gas flex hose to interior of oven HamNCheese Home Repair 1 November 17th 06 09:20 PM
Gas cooker working fine apart from oven - no gas Rob Beattie UK diy 2 October 27th 06 09:31 AM
Creda Electric Cooker - Concept Solar Plus C461 E - Oven not working [email protected] UK diy 3 June 18th 05 07:54 PM
Electrics - Replace full electric cooker with a duel fuel cooker Chi UK diy 11 December 16th 03 02:44 PM
Connecting Delinghi Gas Cooker to flexible (threaded) hose connector Ghazali UK diy 5 August 27th 03 04:43 PM


All times are GMT +1. The time now is 09:14 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"