Ring main joint - pyro to normal
Hi,
I have just had some new sockets inserted into my ring-main - or rather not. The decorator who did it turns out to have made a bit of a hash of it. The problem is that at one end the join to the old ring can be made in the outlet socket - no problem. Because of the way the old cable was removed though the new join has to happen in the middle of nowhere. To compound matters the old cable is pyro, so needs special connectors etc. I'm getting an electrician to sort it, but want to get an idea of what to tell him and what to expect. Is the following correct: I can join the cables in a junction box This junction box can be recessed into the wall and plastered over AS LONG AS the cables are soldered or crimped together If they are only screwed into terminals, they must be accessible How big a job would it be for someone to chisel out space for a junction box and make the above joint, then presumably test the ring for continuity etc. Ring mains seem deadly - they still work if they are split, but you're fuse is twice what it should be. I wouldn't know anything was wrong unless I'd happened to notice an unusual wire... Cheers, Ben |
#2
Posted to uk.d-i-y
|
|||
|
|||
Ring main joint - pyro to normal
It happens that Ben formulated :
Hi, I have just had some new sockets inserted into my ring-main - or rather not. The decorator who did it turns out to have made a bit of a hash of it. The problem is that at one end the join to the old ring can be made in the outlet socket - no problem. Because of the way the old cable was removed though the new join has to happen in the middle of nowhere. To compound matters the old cable is pyro, so needs special connectors etc. It doesn't just need special connectors, it needs a specialised method to terminate the cable itself. The insulation absorbs moisture from the air, so it needs to be sealed up air tight with a proper termination. Modern metric ones are difficult to get hold of, but imperial ones might be impossible. Also you need to make sure the electrician is familiar with terminating Pyro' - that is the old name for the type of cable BTW. -- Regards, Harry (M1BYT) (L) http://www.ukradioamateur.co.uk |
#3
Posted to uk.d-i-y
|
|||
|
|||
Ring main joint - pyro to normal
On 17 Apr, 20:12, Harry Bloomfield
wrote: It happens that Ben formulated : Hi, I have just had some new sockets inserted into my ring-main - or rather not. The decorator who did it turns out to have made a bit of a hash of it. The problem is that at one end the join to the old ring can be made in the outlet socket - no problem. Because of the way the old cable was removed though the new join has to happen in the middle of nowhere. To compound matters the old cable is pyro, so needs special connectors etc. It doesn't just need special connectors, it needs a specialised method to terminate the cable itself. The insulation absorbs moisture from the air, so it needs to be sealed up air tight with a proper termination. Modern metric ones are difficult to get hold of, but imperial ones might be impossible. Also you need to make sure the electrician is familiar with terminating Pyro' - that is the old name for the type of cable BTW. -- Regards, Harry (M1BYT) (L)http://www.ukradioamateur.co.uk Ah -ok. This could be bad... The wire will have been open to the atmosphere for a few days by the time it gets sealed - if I can find the stuff. If I can't, I'm a bit stuffed. I currently have a radial rather than a ring, with a live bit of Pyro poking through the wall... I haven't got any callipers, but the external diameter seems to be 5.5mm or 7/32". Do either of those sound like standard sizes (they don't sound it...) Ooo err. This is not good. I WISH he hadn't cut the cable! Cheers, Ben |
#4
Posted to uk.d-i-y
|
|||
|
|||
Ring main joint - pyro to normal
On 17 Apr, 20:43, Ben wrote:
On 17 Apr, 20:12, Harry Bloomfield wrote: It happens that Ben formulated : Hi, I have just had some new sockets inserted into my ring-main - or rather not. The decorator who did it turns out to have made a bit of a hash of it. The problem is that at one end the join to the old ring can be made in the outlet socket - no problem. Because of the way the old cable was removed though the new join has to happen in the middle of nowhere. To compound matters the old cable is pyro, so needs special connectors etc. It doesn't just need special connectors, it needs a specialised method to terminate the cable itself. The insulation absorbs moisture from the air, so it needs to be sealed up air tight with a proper termination. Modern metric ones are difficult to get hold of, but imperial ones might be impossible. Also you need to make sure the electrician is familiar with terminating Pyro' - that is the old name for the type of cable BTW. -- Regards, Harry (M1BYT) (L)http://www.ukradioamateur.co.uk Ah -ok. This could be bad... The wire will have been open to the atmosphere for a few days by the time it gets sealed - if I can find the stuff. If I can't, I'm a bit stuffed. I currently have a radial rather than a ring, with a live bit of Pyro poking through the wall... I haven't got any callipers, but the external diameter seems to be 5.5mm or 7/32". Do either of those sound like standard sizes (they don't sound it...) Ooo err. This is not good. I WISH he hadn't cut the cable! Cheers, Ben I have a section of the cut cable in front of me. What dimensions other than OD are used to identify it - it is 2 core, conductors look about 1mm... |
#5
Posted to uk.d-i-y
|
|||
|
|||
Ring main joint - pyro to normal
"Ben" wrote in message oups.com... On 17 Apr, 20:43, Ben wrote: On 17 Apr, 20:12, Harry Bloomfield wrote: It happens that Ben formulated : Hi, I have just had some new sockets inserted into my ring-main - or rather not. The decorator who did it turns out to have made a bit of a hash of it. The problem is that at one end the join to the old ring can be made in the outlet socket - no problem. Because of the way the old cable was removed though the new join has to happen in the middle of nowhere. To compound matters the old cable is pyro, so needs special connectors etc. It doesn't just need special connectors, it needs a specialised method to terminate the cable itself. The insulation absorbs moisture from the air, so it needs to be sealed up air tight with a proper termination. Modern metric ones are difficult to get hold of, but imperial ones might be impossible. Also you need to make sure the electrician is familiar with terminating Pyro' - that is the old name for the type of cable BTW. -- Regards, Harry (M1BYT) (L)http://www.ukradioamateur.co.uk Ah -ok. This could be bad... The wire will have been open to the atmosphere for a few days by the time it gets sealed - if I can find the stuff. If I can't, I'm a bit stuffed. I currently have a radial rather than a ring, with a live bit of Pyro poking through the wall... I haven't got any callipers, but the external diameter seems to be 5.5mm or 7/32". Do either of those sound like standard sizes (they don't sound it...) Ooo err. This is not good. I WISH he hadn't cut the cable! Cheers, Ben I have a section of the cut cable in front of me. What dimensions other than OD are used to identify it - it is 2 core, conductors look about 1mm... It is probably imperial equiv of 2L1.5 pyro. Good luck finding someone who can and has the tools to work on it. We do and are based in Portsmouth if that helps. -- Regards Stephen Dawson Fox Electrical Services Ltd |
#6
Posted to uk.d-i-y
|
|||
|
|||
Ring main joint - pyro to normal
On 17 Apr 2007 12:58:05 -0700, Ben mused:
On 17 Apr, 20:43, Ben wrote: On 17 Apr, 20:12, Harry Bloomfield wrote: It happens that Ben formulated : Hi, I have just had some new sockets inserted into my ring-main - or rather not. The decorator who did it turns out to have made a bit of a hash of it. The problem is that at one end the join to the old ring can be made in the outlet socket - no problem. Because of the way the old cable was removed though the new join has to happen in the middle of nowhere. To compound matters the old cable is pyro, so needs special connectors etc. It doesn't just need special connectors, it needs a specialised method to terminate the cable itself. The insulation absorbs moisture from the air, so it needs to be sealed up air tight with a proper termination. Modern metric ones are difficult to get hold of, but imperial ones might be impossible. Also you need to make sure the electrician is familiar with terminating Pyro' - that is the old name for the type of cable BTW. -- Regards, Harry (M1BYT) (L)http://www.ukradioamateur.co.uk Ah -ok. This could be bad... The wire will have been open to the atmosphere for a few days by the time it gets sealed - if I can find the stuff. If I can't, I'm a bit stuffed. I currently have a radial rather than a ring, with a live bit of Pyro poking through the wall... Turn it off, turn it off now. Don't stop to anything on the way, just turn it off. I haven't got any callipers, but the external diameter seems to be 5.5mm or 7/32". Do either of those sound like standard sizes (they don't sound it...) Ooo err. This is not good. I WISH he hadn't cut the cable! Cheers, Ben I have a section of the cut cable in front of me. What dimensions other than OD are used to identify it - it is 2 core, conductors look about 1mm... Depends, the OD varies amongst old and new and also throught the different grades and imperfections. -- Regards, Stuart. |
#7
Posted to uk.d-i-y
|
|||
|
|||
Ring main joint - pyro to normal
On 17 Apr, 21:30, Lurch wrote:
On 17 Apr 2007 12:58:05 -0700, Ben mused: On 17 Apr, 20:43, Ben wrote: On 17 Apr, 20:12, Harry Bloomfield wrote: It happens that Ben formulated : Hi, I have just had some new sockets inserted into my ring-main - or rather not. The decorator who did it turns out to have made a bit of a hash of it. The problem is that at one end the join to the old ring can be made in the outlet socket - no problem. Because of the way the old cable was removed though the new join has to happen in the middle of nowhere. To compound matters the old cable is pyro, so needs special connectors etc. It doesn't just need special connectors, it needs a specialised method to terminate the cable itself. The insulation absorbs moisture from the air, so it needs to be sealed up air tight with a proper termination. Modern metric ones are difficult to get hold of, but imperial ones might be impossible. Also you need to make sure the electrician is familiar with terminating Pyro' - that is the old name for the type of cable BTW. -- Regards, Harry (M1BYT) (L)http://www.ukradioamateur.co.uk Ah -ok. This could be bad... The wire will have been open to the atmosphere for a few days by the time it gets sealed - if I can find the stuff. If I can't, I'm a bit stuffed. I currently have a radial rather than a ring, with a live bit of Pyro poking through the wall... Turn it off, turn it off now. Don't stop to anything on the way, just turn it off. I haven't got any callipers, but the external diameter seems to be 5.5mm or 7/32". Do either of those sound like standard sizes (they don't sound it...) Ooo err. This is not good. I WISH he hadn't cut the cable! Cheers, Ben I have a section of the cut cable in front of me. What dimensions other than OD are used to identify it - it is 2 core, conductors look about 1mm... Depends, the OD varies amongst old and new and also throught the different grades and imperfections. -- Regards, Stuart. After a bit of detective work with the meter I have managed to isolate the exposed piece of cable so it is no longer live or in danger of shorting out. I have to watch the loading on the now radial circuits, since they are still fused as a ring, but someone is coming to look at it soon and will give their expert opinion. I'm certainly not using more than 20A at the moment anyway. Cheers, Ben |
#8
Posted to uk.d-i-y
|
|||
|
|||
Ring main joint - pyro to normal
Ben pretended :
On 17 Apr, 20:12, Harry Bloomfield wrote: It happens that Ben formulated : Hi, I have just had some new sockets inserted into my ring-main - or rather not. The decorator who did it turns out to have made a bit of a hash of it. The problem is that at one end the join to the old ring can be made in the outlet socket - no problem. Because of the way the old cable was removed though the new join has to happen in the middle of nowhere. To compound matters the old cable is pyro, so needs special connectors etc. It doesn't just need special connectors, it needs a specialised method to terminate the cable itself. The insulation absorbs moisture from the air, so it needs to be sealed up air tight with a proper termination. Modern metric ones are difficult to get hold of, but imperial ones might be impossible. Also you need to make sure the electrician is familiar with terminating Pyro' - that is the old name for the type of cable BTW. -- Regards, Harry (M1BYT) (L)http://www.ukradioamateur.co.uk Ah -ok. This could be bad... The wire will have been open to the atmosphere for a few days by the time it gets sealed - if I can find the stuff. If I can't, I'm a bit stuffed. I currently have a radial rather than a ring, with a live bit of Pyro poking through the wall... I haven't got any callipers, but the external diameter seems to be 5.5mm or 7/32". Do either of those sound like standard sizes (they don't sound it...) Ooo err. This is not good. I WISH he hadn't cut the cable! Cheers, Ben Look at the brass cable gland or seal, on both should be stamped a number which you will be able to quote to an electrical wholesaler. From memory the old imperial sizes had a number based on the diameter in thousands of an inch. The metric ones used a number based on the number and size of the cores. All is not lost, even if moisture has got in. It penetrates quite slowly, perhaps a fraction of an inch per day. The fix is to heat up the Pyro to a dull red heat, at a point beyond the damp and gradually move the heated point towards the open end - this drives the moisture out. Obviously if you don't start far enough back, or move to fast, it will make the problem even worse. Once dried out, the end can be sealed temporarily with a blob of the sealing compound, as used it the seal or 'pot'. To make the end off, you will need 2x glands, 2x pots, 2x plastic ends to suit the number of cores, sealing compound - then the special tools. Crimper, ringer and a stripper. TBH, what with all the faffing about and cost, it might be cheaper/quicker to simply replace the cable with new. FP cable does much of what the Pyro cables were once used for and you don't need any special tools or skills to be able to use it. -- Regards, Harry (M1BYT) (L) http://www.ukradioamateur.co.uk |
#9
Posted to uk.d-i-y
|
|||
|
|||
Ring main joint - pyro to normal
Ben submitted this idea :
I have a section of the cut cable in front of me. What dimensions other than OD are used to identify it - it is 2 core, conductors look about 1mm... For a ring, I think it should be 1.5mm if metric. Could you perhaps compare the size directly against a known cable? Even then it still leaves you guessing about imperial or metric as they were so close in Pyro. If it is of any help I have the tools you need for the job here in W. Yorks and the nack of making the ends off, but not the materials needed. Check the plastic sleeving, they sometimes stamp the core size it fits on that. -- Regards, Harry (M1BYT) (L) http://www.ukradioamateur.co.uk |
#10
Posted to uk.d-i-y
|
|||
|
|||
Ring main joint - pyro to normal
In article . com,
Ben wrote: I have just had some new sockets inserted into my ring-main - or rather not. The decorator who did it turns out to have made a bit of a hash of it. The problem is that at one end the join to the old ring can be made in the outlet socket - no problem. Because of the way the old cable was removed though the new join has to happen in the middle of nowhere. To compound matters the old cable is pyro, so needs special connectors etc. I'm getting an electrician to sort it, but want to get an idea of what to tell him and what to expect. Do you know when the 'pyro' was installed? It doesn't need special connectors as such but has to be properly terminated. This involves fitting a special seal to the end. If you look inside a socket etc you'll see what I mean. If it's old imperial stuff - roughly pre '70 or so - I dunno where you'll find a termination kit. And even the modern stuff might be tricky, depending on your location. Few wholesalers stock MICC these days. For reference if it's the current metric cable it will almost certainly be 2L1.5 for a final ring circuit. And you may have a problem finding an electrician who can work this stuff - it's not much used these days, and ideally needs special tools to make the termination. I do have a small stock of terminations for the common sizes but am unwilling to sell them except to someone who knows what they're doing. -- *It's a thankless job, but I've got a lot of Karma to burn off Dave Plowman London SW To e-mail, change noise into sound. |
#11
Posted to uk.d-i-y
|
|||
|
|||
Ring main joint - pyro to normal
In message , Harry Bloomfield
writes Check the plastic sleeving, they sometimes stamp the core size it fits on that. If you can find a terminated end the "pot" should also have the size embossed on it, like 2L1.5 for two core 1.5mm (If it's metric). Alternatively replace that whole bit of pyro with twin and earth if it's suitable. -- Clive Mitchell http://www.bigclive.com |
#12
Posted to uk.d-i-y
|
|||
|
|||
Ring main joint - pyro to normal
In message .com, Ben
writes I haven't got any callipers, but the external diameter seems to be 5.5mm or 7/32". Do either of those sound like standard sizes (they don't sound it...) Ooo err. This is not good. I WISH he hadn't cut the cable! Did he actually cut the pyro? So has he torn the copper back and just connected onto the wires where they come out of the chalk? If so he really shouldn't be doing electrical work. -- Clive Mitchell http://www.bigclive.com |
#13
Posted to uk.d-i-y
|
|||
|
|||
Ring main joint - pyro to normal
In message , "Dave Plowman (News)"
writes And you may have a problem finding an electrician who can work this stuff - it's not much used these days, and ideally needs special tools to make the termination. Pyro is still widely used in modern buildings for alarm systems despite the availability of other fire rated cables. It's also used in fuel stations and some entertainment venues. Pyro is an abbreviation of Pyrotenax. -- Clive Mitchell http://www.bigclive.com |
#14
Posted to uk.d-i-y
|
|||
|
|||
Ring main joint - pyro to normal
Ben wrote:
I have just had some new sockets inserted into my ring-main - or rather not. The decorator who did it turns out to have made a bit of a hash of it. If he really was a decorator what did you expect? ;-) The problem is that at one end the join to the old ring can be made in the outlet socket - no problem. Because of the way the old cable was removed though the new join has to happen in the middle of nowhere. To compound matters the old cable is pyro, so needs special connectors etc. Follow the cable back to the next accessory in line, and replace it with T&E from there. How big a job would it be for someone to chisel out space for a junction box and make the above joint, then presumably test the ring for continuity etc. Half hour tops, with normal T&E, crimps, heatshrink etc and a SDS drill - perhaps longer if including a MICC pot as well. Ring mains seem deadly - they still work if they are split, but you're fuse is twice what it should be. I wouldn't know anything was wrong unless I'd happened to notice an unusual wire... When you analyse the most likely faults that can happen, ring circuits are a pretty good compromise all things considered (much harder for one poor joint to leave the bulk of a circuit unearthed, or the full design current passing through one high resistance point). Not to mention the current carrying capacity[1] for 1.5mm^2 MICC in plaster is not far of the circuit breaker rating anyway at 28A. So you would have to try quite hard to cause damage to that during normal usage. [1] Table 4J2A in BS7671 -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#15
Posted to uk.d-i-y
|
|||
|
|||
Ring main joint - pyro to normal
In article ,
Clive Mitchell wrote: In message , "Dave Plowman (News)" writes And you may have a problem finding an electrician who can work this stuff - it's not much used these days, and ideally needs special tools to make the termination. Pyro is still widely used in modern buildings for alarm systems despite the availability of other fire rated cables. It's also used in fuel stations and some entertainment venues. Indeed - however your average jobbing domestic sparks ain't going to work in such places. Pyro is an abbreviation of Pyrotenax. Of course the Pyrotenax company no longer exists - they merged with BICC some 40 years ago. But the name tends to be generic - like hoover. -- *Do infants enjoy infancy as much as adults enjoy adultery? Dave Plowman London SW To e-mail, change noise into sound. |
#16
Posted to uk.d-i-y
|
|||
|
|||
Ring main joint - pyro to normal
On 18 Apr, 00:10, "Dave Plowman (News)" wrote:
In article . com, Ben wrote: I have just had some new sockets inserted into my ring-main - or rather not. The decorator who did it turns out to have made a bit of a hash of it. The problem is that at one end the join to the old ring can be made in the outlet socket - no problem. Because of the way the old cable was removed though the new join has to happen in the middle of nowhere. To compound matters the old cable is pyro, so needs special connectors etc. I'm getting an electrician to sort it, but want to get an idea of what to tell him and what to expect. Do you know when the 'pyro' was installed? It doesn't need special connectors as such but has to be properly terminated. This involves fitting a special seal to the end. If you look inside a socket etc you'll see what I mean. If it's old imperial stuff - roughly pre '70 or so - I dunno where you'll find a termination kit. And even the modern stuff might be tricky, depending on your location. Few wholesalers stock MICC these days. For reference if it's the current metric cable it will almost certainly be 2L1.5 for a final ring circuit. And you may have a problem finding an electrician who can work this stuff - it's not much used these days, and ideally needs special tools to make the termination. I do have a small stock of terminations for the common sizes but am unwilling to sell them except to someone who knows what they're doing. -- *It's a thankless job, but I've got a lot of Karma to burn off Dave Plowman London SW To e-mail, change noise into sound. Hi - Thanks for the reply. I have got an electrician coming around who has worked with pyro cable before, but the cable is bare unmarked brass so he'll need to work out what type it is. We then need to discuss the practicalities of joining vs rerunning (rerunning would be an arse). He also suggested just derating, but I really want to avoid that if I can! If he is able to identify the cable but unable to find the bits, perhaps I could contact you again? He can't make it around for about a week - I have isolated the offending cable, but how much of a problem will atmospheric moisture be? Should I temporarily tryt to seal it off with a blob of glue or similar? Cheers, Ben |
#17
Posted to uk.d-i-y
|
|||
|
|||
Ring main joint - pyro to normal
On 18 Apr, 09:46, "Dave Plowman (News)" wrote:
In article , Clive Mitchell wrote: In message , "Dave Plowman (News)" writes And you may have a problem finding an electrician who can work this stuff - it's not much used these days, and ideally needs special tools to make the termination. Pyro is still widely used in modern buildings for alarm systems despite the availability of other fire rated cables. It's also used in fuel stations and some entertainment venues. Indeed - however your average jobbing domestic sparks ain't going to work in such places. Pyro is an abbreviation of Pyrotenax. Of course the Pyrotenax company no longer exists - they merged with BICC some 40 years ago. But the name tends to be generic - like hoover. -- *Do infants enjoy infancy as much as adults enjoy adultery? Dave Plowman London SW To e-mail, change noise into sound. I think the original problem was this: The plan was to remove the pyro between two outlets and replace it with modern cable. But the old cable was removed before it was all exposed. It turns out that just before it reaches the second socket, it diverts to the next floor up, loops the bedroom, and then comes back down again - all in the horizontal space of a few cm. So when he had removed the cable he all of a sudden found it didn't go to an easily accesible socket, and the problems started. However, not new cable/pyro cable have been made yet (which would reform the ring) due to the lack of an electrician and of the neccesary bits. I've found someone, but he's busy this week, so fingers crossed for next. Ben Ben |
#18
Posted to uk.d-i-y
|
|||
|
|||
Ring main joint - pyro to normal
On 18 Apr, 09:46, "Dave Plowman (News)" wrote:
In article , Clive Mitchell wrote: In message , "Dave Plowman (News)" writes And you may have a problem finding an electrician who can work this stuff - it's not much used these days, and ideally needs special tools to make the termination. Pyro is still widely used in modern buildings for alarm systems despite the availability of other fire rated cables. It's also used in fuel stations and some entertainment venues. Indeed - however your average jobbing domestic sparks ain't going to work in such places. Pyro is an abbreviation of Pyrotenax. Of course the Pyrotenax company no longer exists - they merged with BICC some 40 years ago. But the name tends to be generic - like hoover. I obtained a pack of pot seals and a pack of glands for 2L1.5 from Newey and Eyre this week. The brand name Pyrotenax boldly displayrd on the packs! |
#19
Posted to uk.d-i-y
|
|||
|
|||
Ring main joint - pyro to normal
In article .com,
Ben wrote: Hi - Thanks for the reply. I have got an electrician coming around who has worked with pyro cable before, but the cable is bare unmarked brass so he'll need to work out what type it is. A termination 'pot' should have the details on it, so a look inside the socket feeding the cable should do it. And the cable outer is copper - not brass. We then need to discuss the practicalities of joining vs rerunning (rerunning would be an arse). He also suggested just derating, but I really want to avoid that if I can! That's a bit of a worry. Assuming there is about 12" of the MICC get attable, it should be possible to fit a new termination. If he is able to identify the cable but unable to find the bits, perhaps I could contact you again? Yes. But only after he's certain he can't order them from his wholesaler - as I say I keep them for my own emergencies. ;-) He can't make it around for about a week - I have isolated the offending cable, but how much of a problem will atmospheric moisture be? Should I temporarily tryt to seal it off with a blob of glue or similar? Tape it over with PVC tape. -- *Organized Crime Is Alive And Well; It's Called Auto Insurance. Dave Plowman London SW To e-mail, change noise into sound. |
#20
Posted to uk.d-i-y
|
|||
|
|||
Ring main joint - pyro to normal
In article . com,
cynic wrote: Of course the Pyrotenax company no longer exists - they merged with BICC some 40 years ago. But the name tends to be generic - like hoover. I obtained a pack of pot seals and a pack of glands for 2L1.5 from Newey and Eyre this week. The brand name Pyrotenax boldly displayrd on the packs! That's interesting - last ones I bought were 2L1 about a couple of years ago (for lighting wiring in an oak beamed room) and they were just marked BICC. -- *Why is it that to stop Windows 95, you have to click on "Start"? Dave Plowman London SW To e-mail, change noise into sound. |
#21
Posted to uk.d-i-y
|
|||
|
|||
Ring main joint - pyro to normal
Dave Plowman (News) used his keyboard to write :
He can't make it around for about a week - I have isolated the offending cable, but how much of a problem will atmospheric moisture be? Should I temporarily tryt to seal it off with a blob of glue or similar? Tape it over with PVC tape. Which would be effective, if you could get the tape to stick effectively to completely exclude air - usually it doesn't, so can I suggest a blob of silicon sealant perhaps? Another way would be to put a blob of the potting compound over the end - I assume you got some with the seals and glands? The manufacturer used to seal the cut ends with something similar to a tar like substance I seem to remember. The idea is to simply stop the white chalky substance - the insulation (aluminium oxide?) absorbing moisture from the air. -- Regards, Harry (M1BYT) (L) http://www.ukradioamateur.co.uk |
#22
Posted to uk.d-i-y
|
|||
|
|||
Ring main joint - pyro to normal
On 18 Apr, 19:16, "Dave Plowman (News)" wrote:
In article . com, cynic wrote: Of course the Pyrotenax company no longer exists - they merged with BICC some 40 years ago. But the name tends to be generic - like hoover. I obtained a pack of pot seals and a pack of glands for 2L1.5 from Newey and Eyre this week. The brand name Pyrotenax boldly displayrd on the packs! That's interesting - last ones I bought were 2L1 about a couple of years ago (for lighting wiring in an oak beamed room) and they were just marked BICC. -- *Why is it that to stop Windows 95, you have to click on "Start"? Dave Plowman London SW To e-mail, change noise into sound. I'll have a look when I get back for the type of cable it is. Last time I looked, I could see the two copper wires, which had been sheathed with black plastic. They disappeared into a larger diameter black circular pipe that was filled with some sort of resin. I can't really see the other side of the pots, as they are behind plaster. Whereabouts should I be looking for the designation (is it, in fact, on the outside edge of the box - if needs be I can always remove a bit of plaster to have a peek, since that section of wall hasn't been finished properly yet anyway) I have definitely learnt a lesson from this whole episode! Cheers, Ben |
#23
Posted to uk.d-i-y
|
|||
|
|||
Ring main joint - pyro to normal
On 18 Apr, 20:53, Ben wrote:
On 18 Apr, 19:16, "Dave Plowman (News)" wrote: In article . com, cynic wrote: Of course the Pyrotenax company no longer exists - they merged with BICC some 40 years ago. But the name tends to be generic - like hoover. I obtained a pack of pot seals and a pack of glands for 2L1.5 from Newey and Eyre this week. The brand name Pyrotenax boldly displayrd on the packs! That's interesting - last ones I bought were 2L1 about a couple of years ago (for lighting wiring in an oak beamed room) and they were just marked BICC. -- *Why is it that to stop Windows 95, you have to click on "Start"? Dave Plowman London SW To e-mail, change noise into sound. I'll have a look when I get back for the type of cable it is. Last time I looked, I could see the two copper wires, which had been sheathed with black plastic. They disappeared into a larger diameter black circular pipe that was filled with some sort of resin. I can't really see the other side of the pots, as they are behind plaster. Whereabouts should I be looking for the designation (is it, in fact, on the outside edge of the box - if needs be I can always remove a bit of plaster to have a peek, since that section of wall hasn't been finished properly yet anyway) I have definitely learnt a lesson from this whole episode! Cheers, Ben- Hide quoted text - - Show quoted text - If your electrician can't identify the size of cable you can send a sample to one of the manufacturers. They are usually helpful. I have done this with a bit of old imperial size. They sent me a pair of pot seals almost by return. (about 7 years ago now) |
#24
Posted to uk.d-i-y
|
|||
|
|||
Ring main joint - pyro to normal
In article ,
Harry Bloomfield writes: The idea is to simply stop the white chalky substance - the insulation (aluminium oxide?) absorbing moisture from the air. Magnesium oxide. -- Andrew Gabriel [email address is not usable -- followup in the newsgroup] |
#25
Posted to uk.d-i-y
|
|||
|
|||
Ring main joint - pyro to normal
In article ,
Harry Bloomfield wrote: Tape it over with PVC tape. Which would be effective, if you could get the tape to stick effectively to completely exclude air - usually it doesn't, To copper? I'd expect it to stick pretty well. so can I suggest a blob of silicon sealant perhaps? Another way would be to put a blob of the potting compound over the end - I assume you got some with the seals and glands? *I* have, but the OP hasn't. The manufacturer used to seal the cut ends with something similar to a tar like substance I seem to remember. I can't say I've seen that - although I've rarely bought a complete coil. Usually a cut length. The idea is to simply stop the white chalky substance - the insulation (aluminium oxide?) absorbing moisture from the air. Indoors it does so very slowly, though, and the act of stripping to terminate will remove the dodgy bit. -- *I couldn't repair your brakes, so I made your horn louder * Dave Plowman London SW To e-mail, change noise into sound. |
#26
Posted to uk.d-i-y
|
|||
|
|||
Ring main joint - pyro to normal
In article .com,
Ben wrote: I'll have a look when I get back for the type of cable it is. Last time I looked, I could see the two copper wires, which had been sheathed with black plastic. They disappeared into a larger diameter black circular pipe that was filled with some sort of resin. I can't really see the other side of the pots, as they are behind plaster. Whereabouts should I be looking for the designation (is it, in fact, on the outside edge of the box - if needs be I can always remove a bit of plaster to have a peek, since that section of wall hasn't been finished properly yet anyway) The material inside the pot seal is rather like putty - except that it doesn't set. It's normal to either clamp the seal in a special back box to provide the earth, or to use a compression gland which fits a standard 3/4 cutout and is fixed by a backing ring. Although I've a feeling neither of these methods is now considered satisfactory for an ECC. I have definitely learnt a lesson from this whole episode! It's a very tactile material to work with when the cable is exposed. Rather like plumbing in many ways. -- *If all is not lost, where the hell is it? Dave Plowman London SW To e-mail, change noise into sound. |
#27
Posted to uk.d-i-y
|
|||
|
|||
Ring main joint - pyro to normal
In message , "Dave Plowman (News)"
writes The material inside the pot seal is rather like putty - except that it doesn't set. It's normal to either clamp the seal in a special back box to provide the earth, or to use a compression gland which fits a standard 3/4 cutout and is fixed by a backing ring. Although I've a feeling neither of these methods is now considered satisfactory for an ECC. I prefer earth tail pots. -- Clive Mitchell http://www.bigclive.com |
#28
Posted to uk.d-i-y
|
|||
|
|||
Ring main joint - pyro to normal
In article ,
Clive Mitchell wrote: In message , "Dave Plowman (News)" writes The material inside the pot seal is rather like putty - except that it doesn't set. It's normal to either clamp the seal in a special back box to provide the earth, or to use a compression gland which fits a standard 3/4 cutout and is fixed by a backing ring. Although I've a feeling neither of these methods is now considered satisfactory for an ECC. I prefer earth tail pots. Right. Are those the preferred method these days? -- *If you don't like the news, go out and make some. Dave Plowman London SW To e-mail, change noise into sound. |
#29
Posted to uk.d-i-y
|
|||
|
|||
Ring main joint - pyro to normal
In message , "Dave Plowman (News)"
writes I prefer earth tail pots. Right. Are those the preferred method these days? Not in all cases, but they are a good reliable way of getting a solid earth bond. A pigtail of wire is bonded to the pot itself during manufacture. -- Clive Mitchell http://www.bigclive.com |