Can you get a (double) shaver socket setup with the transformer
separated, i.e. above bathroom in loft ? (that would be OK for the
regs). Or, where to get sockets without transformer and a separate
suitable transfomer (I guess you need one per socket for isolation
reasons).
I don't want to cut into the wall do bury a transformer, and want flush
mounting chrome sockets.
Cheers,
Simon.

  #2   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 9,045
Default shaver socket with separate transformer

sm_jamieson wrote:
Can you get a (double) shaver socket setup with the transformer
separated, i.e. above bathroom in loft ? (that would be OK for the
regs). Or, where to get sockets without transformer and a separate
suitable transfomer (I guess you need one per socket for isolation
reasons).
I don't want to cut into the wall do bury a transformer, and want flush
mounting chrome sockets.
Cheers,
Simon.

I managed to getr away with a simple deep backing box. Well tills SHE
wanted it moved, then I used a pushfit plastic box and cut a hole in the
back where the transformer sticks out.

But of course you could use a remote one I suppose.
  #3   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 4,555
Default shaver socket with separate transformer

sm_jamieson wrote:
Can you get a (double) shaver socket setup with the transformer
separated, i.e. above bathroom in loft ? (that would be OK for the
regs). Or, where to get sockets without transformer and a separate
suitable transfomer (I guess you need one per socket for isolation
reasons).
I don't want to cut into the wall do bury a transformer, and want flush
mounting chrome sockets.


Doubt it; but whatever you end up with it will still need to burying
surely? A shaver transformer isn't all that much deeper than a
conventional plug socket IIRC?

David
  #4   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 5,175
Default shaver socket with separate transformer


sm_jamieson wrote:

Can you get a (double) shaver socket setup with the transformer
separated, i.e. above bathroom in loft ?


Not AFAIK.

The transformer is switched by inserting the shaver plug (why they hum
and may overheat if you leave the shaver plugged in). Although it's not
impossible to do this with a split design, it's more complex than just
a supply to the transformer, then running the output to a minimal
socket.

  #5   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 131
Default shaver socket with separate transformer


sm_jamieson wrote:
Can you get a (double) shaver socket setup with the transformer
separated, i.e. above bathroom in loft ? (that would be OK for the
regs). Or, where to get sockets without transformer and a separate
suitable transfomer (I guess you need one per socket for isolation
reasons).
I don't want to cut into the wall do bury a transformer, and want flush
mounting chrome sockets.
Cheers,
Simon.


What do you want to run from this?

Most of the things that can be run from these are available in
re-chargeable form. Just charge it elsewhere in the house once a week
and happily shave/toothbrush/whatever in the bathroom or elsewhere.

Another alternative would be a shaverlight.



  #6   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 2,688
Default shaver socket with separate transformer


wrote:
sm_jamieson wrote:
Can you get a (double) shaver socket setup with the transformer
separated, i.e. above bathroom in loft ? (that would be OK for the
regs). Or, where to get sockets without transformer and a separate
suitable transfomer (I guess you need one per socket for isolation
reasons).
I don't want to cut into the wall do bury a transformer, and want flush
mounting chrome sockets.
Cheers,
Simon.


What do you want to run from this?


I would guess, shaver (recharge sometimes, and for guests) and elec
toothbrush, recharge since it won't run off mains.


Most of the things that can be run from these are available in
re-chargeable form. Just charge it elsewhere in the house once a week
and happily shave/toothbrush/whatever in the bathroom or elsewhere.


Yes of course you can. It's a question of convenience like most things
in our cushy lives.
And while I'm doing the bathroom, may as well kit it out properly. I
may only put in one socket though !


Another alternative would be a shaverlight.


No good, since the one my parents have only charged when the light was
on.
I have never seen a shaverlight that didn't look crap.

Simon.

  #7   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 43,017
Default shaver socket with separate transformer

In article . com,
sm_jamieson wrote:
Can you get a (double) shaver socket setup with the transformer
separated, i.e. above bathroom in loft ? (that would be OK for the
regs). Or, where to get sockets without transformer and a separate
suitable transfomer (I guess you need one per socket for isolation
reasons).
I don't want to cut into the wall do bury a transformer, and want flush
mounting chrome sockets.


Assuming you can source the non isolated sockets you want which conform to
regs, I think your easiest way would be to buy (cheap) isolated ones as
donors for the transformers. CPC, etc, don't appear to sell the
transformers on their own - unless I've simply not seen them.

--
*A closed mouth gathers no feet.

Dave Plowman London SW
To e-mail, change noise into sound.
  #8   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 25,191
Default shaver socket with separate transformer

sm_jamieson wrote:

Yes of course you can. It's a question of convenience like most things
in our cushy lives.
And while I'm doing the bathroom, may as well kit it out properly. I
may only put in one socket though !


What is the problem with fitting a deeper back box? (they don't need to
be taht much deeper than the one required for an non transformed socket)

Another alternative would be a shaverlight.



No good, since the one my parents have only charged when the light was
on.
I have never seen a shaverlight that didn't look crap.


Try these:

http://www.tlc-direct.co.uk/Main_Ind...s_1/index.html

They supply power to the socket without the light needing to be on, and
look a fair bit nicer than many.

--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/
  #9   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 4,555
Default shaver socket with separate transformer

sm_jamieson wrote:
I have never seen a shaverlight that didn't look crap.


I have one of these, which IMHO doesn't look bad - at least isn't the
boxy type which you're probably referring to?

http://www.tlc-direct.co.uk/Products/LL5707.html

David
  #10   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 31
Default shaver socket with separate transformer


"sm_jamieson" wrote in message
ups.com...
Can you get a (double) shaver socket setup with the transformer
separated, i.e. above bathroom in loft ? (that would be OK for the
regs). Or, where to get sockets without transformer and a separate
suitable transfomer (I guess you need one per socket for isolation
reasons).
I don't want to cut into the wall do bury a transformer, and want flush
mounting chrome sockets.
Cheers,
Simon.


We've got our electric toothbrush permanently plugged into one of these
http://tinyurl.com/yx94rn (link goes to TLC-Direct)

You say that you don't want to cut into the wall (to mount a transformer)
but you want a flush mounted socket??? There's got to be something in the
wall so it may as well be one of these as they're not much deeper than a
normal socket.

John.




  #11   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 819
Default shaver socket with separate transformer

Doubt it; but whatever you end up with it will still need to burying
surely? A shaver transformer isn't all that much deeper than a
conventional plug socket IIRC?


You are having a laugh, aren't you?

A standard shaver socket is very low profile (and single sized, rather than
double, too).

An isolating shaver outlet is the size of a double decker bus.

Christian.


  #12   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 819
Default shaver socket with separate transformer

You say that you don't want to cut into the wall (to mount a transformer)
but you want a flush mounted socket??? There's got to be something in the
wall so it may as well be one of these as they're not much deeper than a
normal socket.


A non-isolated shaver socket will normally fit within the thickness of
plaster, especially if there are tiles. There is no way an isolated type
will fit. You're lucky if it doesn't sit in the cavity of the wall.

Christian.


  #13   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 819
Default shaver socket with separate transformer

Can you get a (double) shaver socket setup with the transformer
separated, i.e. above bathroom in loft ? (that would be OK for the
regs).


Standalone BS3535 isolating transformers:

http://www.knighton-tools.co.uk/ACAT...nsformers.html

They don't have a 230V-230V, so the output would be 110V, which is probably
no hardship in this application, but check your toothbrush. 50VA should be
fine, I'd imagine, unless someone knows the regs give a minimum VA rating.

Christian.


  #14   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 819
Default shaver socket with separate transformer

They don't have a 230V-230V, so the output would be 110V, which is
probably no hardship in this application,


Note that bonding could become a bit of an issue.

Personally, I would not bond to earth through the supply cable (use 2 core
non earthed cable), but would include the fitting in the supplementary
equipotential bonding. I have no idea if that is what the regs recommend and
you may wish to check with the IET.

Christian.


  #15   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 4,555
Default shaver socket with separate transformer

Christian McArdle wrote:
Doubt it; but whatever you end up with it will still need to burying
surely? A shaver transformer isn't all that much deeper than a
conventional plug socket IIRC?


You are having a laugh, aren't you?

A standard shaver socket is very low profile (and single sized, rather than
double, too).

An isolating shaver outlet is the size of a double decker bus.


I have one of these in the bathroom, flush, in a 47mm steel backbox:
http://www.tlc-direct.co.uk/Technical/DataSheets/MK/K701.pdf

ie, not all that much deeper than a conventional plug socket - certainly
not so much more as to make it a big issue, anyway. So, still not sure
what the OP's problem is?

David


  #16   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 819
Default shaver socket with separate transformer

I have one of these in the bathroom, flush, in a 47mm steel backbox:
http://www.tlc-direct.co.uk/Technical/DataSheets/MK/K701.pdf


Exactly. A 47mm backbox ensures you need to dig out brick/block/rubble,
unlike a non-isolated socket. The double size plate is also less than
inconspicuous.

ie, not all that much deeper than a conventional plug socket - certainly
not so much more as to make it a big issue, anyway. So, still not sure
what the OP's problem is?


Doesn't want to/can't dig out the wall deeper than the plaster, presumably.

Christian.



  #17   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 11,175
Default shaver socket with separate transformer

In article ,
"Christian McArdle" writes:
Can you get a (double) shaver socket setup with the transformer
separated, i.e. above bathroom in loft ? (that would be OK for the
regs).


Standalone BS3535 isolating transformers:

http://www.knighton-tools.co.uk/ACAT...nsformers.html

They don't have a 230V-230V, so the output would be 110V, which is probably
no hardship in this application, but check your toothbrush. 50VA should be
fine, I'd imagine, unless someone knows the regs give a minimum VA rating.


Regs give a max rating for a shaver socket. I think it's
something like 25VA, but I don't have them on me to check.
The regulation is not good -- off-load, they are around
270V. The instructions usually warn to run low power
things like chargers with wide ranging voltage rating on
the 120V side. Of course, no one sees these because the
electrician chucks them out before the householder moves
in.;-)

The sockets have a self-resetting thermal trip in the
transformer windings, which in effect forms a very slow
blow fuse. This might be a requirement of the BS, as they
all seem to do it.

--
Andrew Gabriel
  #18   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 9,560
Default shaver socket with separate transformer

sm_jamieson wrote:
wrote:
sm_jamieson wrote:


Can you get a (double) shaver socket setup with the transformer
separated, i.e. above bathroom in loft ? (that would be OK for the
regs). Or, where to get sockets without transformer and a separate
suitable transfomer (I guess you need one per socket for isolation
reasons).
I don't want to cut into the wall do bury a transformer, and want flush
mounting chrome sockets.
Cheers,
Simon.


What do you want to run from this?


I would guess, shaver (recharge sometimes, and for guests) and elec
toothbrush, recharge since it won't run off mains.


Most of the things that can be run from these are available in
re-chargeable form. Just charge it elsewhere in the house once a week
and happily shave/toothbrush/whatever in the bathroom or elsewhere.


Yes of course you can. It's a question of convenience like most things
in our cushy lives.


So for reasons of convenience, rather than plug it in outside the
bathroom, you'd sooner chase out the plaster for wire and backbox,
drill into the loft, crawl into the loft and wire up an iso, wire it
into a socket in the bathroom, replaster and redecorate it all. Then
run your appliances on 240v + upto 20%, at which voltage breakdowns
will be a problem.

Maybe I just have a strange idea of convenience.


NT

  #19   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 112
Default shaver socket with separate transformer

On 23 Oct 2006 19:35:52 GMT, (Andrew
Gabriel) wrote:

In article ,
"Christian McArdle" writes:
Can you get a (double) shaver socket setup with the transformer
separated, i.e. above bathroom in loft ? (that would be OK for the
regs).


Standalone BS3535 isolating transformers:

http://www.knighton-tools.co.uk/ACAT...nsformers.html

They don't have a 230V-230V, so the output would be 110V, which is probably
no hardship in this application, but check your toothbrush. 50VA should be
fine, I'd imagine, unless someone knows the regs give a minimum VA rating.


Regs give a max rating for a shaver socket. I think it's
something like 25VA, but I don't have them on me to check.
The regulation is not good -- off-load, they are around
270V. The instructions usually warn to run low power
things like chargers with wide ranging voltage rating on
the 120V side. Of course, no one sees these because the
electrician chucks them out before the householder moves
in.;-)

The sockets have a self-resetting thermal trip in the
transformer windings, which in effect forms a very slow
blow fuse. This might be a requirement of the BS, as they
all seem to do it.


Like this ?
http://www.taps4less.com/PP/V-1010.html

Robert
Robert
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Loft power socket? - UK diy 7 July 12th 06 10:54 AM
'Moving' a socket Aldrich UK diy 4 July 4th 06 07:11 PM
Is my LT44 transformer suitable for audio (de)coupling? Andy Electronics Repair 113 May 6th 06 04:19 PM
buzzing shaver socket mike UK diy 2 December 31st 04 02:54 PM
More power from shaver socket wanted Andrew Gabriel UK diy 8 August 10th 03 04:54 PM


All times are GMT +1. The time now is 04:25 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"