Home |
Search |
Today's Posts |
|
UK diy (uk.d-i-y) For the discussion of all topics related to diy (do-it-yourself) in the UK. All levels of experience and proficency are welcome to join in to ask questions or offer solutions. |
Reply |
|
|
LinkBack | Thread Tools | Display Modes |
#1
|
|||
|
|||
Extending ring mains
Hi,
I want to extend the ring mains in my (1930's) house to add two double sockets to a room. I've got the floorboards up and know where the new cable needs to go. However, the thing that's stopping me going ahead is the fact that the existing cable appears to be ever so slightly thicker than the 2.5mm^2 that I was going to use. It is also multi(6)-stranded instead of single-stranded. Is this to be expected with older wiring (I believe a rewiring was done in the 70's)? There is a 32A MCB at the fuse box so I thought that 2.5mm^2 would do the job but having seen the existing wire I now have doubts. I don't want to weaken the installation by using wire that is too thin. After a bit of Googling it seems that 4mm^2 cable might be used in a radial installation but I disconnected the wire between two sockets in the room and they both still worked - does this allow me to conclude that I have a ring mains? Also, 4mm^2 cable doesn't seem to be available from B&Q, etc. - the next size up is 6mm^2. Maybe the fact that I'm having to ask these questions suggests that I should get in an electrician?! Cheers, Grant |
#2
|
|||
|
|||
After a bit of Googling it seems that 4mm^2 cable might be used in a
radial installation but I disconnected the wire between two sockets in the room and they both still worked - does this allow me to conclude that I have a ring mains? Also, 4mm^2 cable doesn't seem to be available from B&Q, etc. - the next size up is 6mm^2. Maybe it was a radial at some point, then was taken back to the CU and made into a ring? Are there any markings on the cable? Sparks... |
#3
|
|||
|
|||
Sparks wrote:
After a bit of Googling it seems that 4mm^2 cable might be used in a radial installation but I disconnected the wire between two sockets in the room and they both still worked - does this allow me to conclude that I have a ring mains? Also, 4mm^2 cable doesn't seem to be available from B&Q, etc. - the next size up is 6mm^2. Maybe it was a radial at some point, then was taken back to the CU and made into a ring? Are there any markings on the cable? Sparks... No markings on the cable. What I have noticed is that some of the existing cable doesn't appear to be copper - it is a silvery colour. Cheers, Grant |
#4
|
|||
|
|||
Grant wrote:
Sparks wrote: After a bit of Googling it seems that 4mm^2 cable might be used in a radial installation but I disconnected the wire between two sockets in the room and they both still worked - does this allow me to conclude that I have a ring mains? Also, 4mm^2 cable doesn't seem to be available from B&Q, etc. - the next size up is 6mm^2. Maybe it was a radial at some point, then was taken back to the CU and made into a ring? Are there any markings on the cable? .... and can you see both ends of the ring coming back to the C.U.? No markings on the cable. What I have noticed is that some of the existing cable doesn't appear to be copper - it is a silvery colour. It's tinned copper. |
#5
|
|||
|
|||
In an earlier contribution to this discussion,
Grant wrote: Hi, I want to extend the ring mains in my (1930's) house to add two double sockets to a room. I've got the floorboards up and know where the new cable needs to go. However, the thing that's stopping me going ahead is the fact that the existing cable appears to be ever so slightly thicker than the 2.5mm^2 that I was going to use. It is also multi(6)-stranded instead of single-stranded. Is this to be expected with older wiring (I believe a rewiring was done in the 70's)? There is a 32A MCB at the fuse box so I thought that 2.5mm^2 would do the job but having seen the existing wire I now have doubts. I don't want to weaken the installation by using wire that is too thin. After a bit of Googling it seems that 4mm^2 cable might be used in a radial installation but I disconnected the wire between two sockets in the room and they both still worked - does this allow me to conclude that I have a ring mains? Also, 4mm^2 cable doesn't seem to be available from B&Q, etc. - the next size up is 6mm^2. Maybe the fact that I'm having to ask these questions suggests that I should get in an electrician?! Cheers, Grant 2.5mm^2 is fine for a ring main as long as you *insert* it into the ring so as to still have a continuous ring - rather than creating spurs. My house has a mixture of older (stranded) cable and new solid stuff. Doesn't seem to be a problem! There is a limit (can't remember what it is!) to the permitted number of outlets on a single ring - but you probably won't exceed that unless the ring has already been extended. My understanding is that any such work now comes under the provisions of Part P of the Building Regs - and that, legally, the work needs to be certified by a qualified electrician - or by Building Control if they are capable! Many competent DIY-ers choose to ignore this - particularly if there's no obvious evidence as to *when* the work was carried out. But if you're not confident *and* competent, get an electrician. -- Cheers, Set Square ______ Please reply to newsgroup. Reply address is invalid. |
#6
|
|||
|
|||
No markings on the cable. What I have noticed is that some of the
existing cable doesn't appear to be copper - it is a silvery colour. Probably tinned standed cable, as used yonks ago. You can probably use the 2.5mm cable as you wish. However, you should be doing a full circuit test afterwards, which will ascertain that the circuit is a complete ring. If it really is a radial (which is unlikely), your choices are to use bigger cable, or drop the MCB to 20A, which is no hardship if the circuit just covers a few reception or bedrooms. Don't even think about it for a kitchen, though. However, if you're unlucky the test may show that the old cable isn't up to the earth loop impedence test. In that case, you probably must drop to 20A, or even rewire. You'll need an electrician to do the testing. It is probably well beyond your experience, and the test equipment costs many hundreds of pounds. Christian. |
#7
|
|||
|
|||
Set Square wrote:
My understanding is that any such work now comes under the provisions of Part P of the Building Regs - and that, legally, the work needs to be certified by a qualified electrician - or by Building Control if they are capable! Many competent DIY-ers choose to ignore this - particularly if there's no obvious evidence as to *when* the work was carried out. Effectively, it doesn't matter when it was done, as long as there isn't an exact record existing of what's there. |
#8
|
|||
|
|||
Chris Bacon wrote:
Set Square wrote: My understanding is that any such work now comes under the provisions of Part P of the Building Regs - and that, legally, the work needs to be certified by a qualified electrician - or by Building Control if they are capable! Many competent DIY-ers choose to ignore this - particularly if there's no obvious evidence as to *when* the work was carried out. Effectively, it doesn't matter when it was done, as long as there isn't an exact record existing of what's there. I'm in Scotland - I think the regs are different here aren't they? Even stricter? Cheers, Grant |
#9
|
|||
|
|||
Christian McArdle wrote:
No markings on the cable. What I have noticed is that some of the existing cable doesn't appear to be copper - it is a silvery colour. Probably tinned standed cable, as used yonks ago. You can probably use the 2.5mm cable as you wish. However, you should be doing a full circuit test afterwards, which will ascertain that the circuit is a complete ring. If it really is a radial (which is unlikely), your choices are to use bigger cable, or drop the MCB to 20A, which is no hardship if the circuit just covers a few reception or bedrooms. Don't even think about it for a kitchen, though. However, if you're unlucky the test may show that the old cable isn't up to the earth loop impedence test. In that case, you probably must drop to 20A, or even rewire. You'll need an electrician to do the testing. It is probably well beyond your experience, and the test equipment costs many hundreds of pounds. Christian. Many thanks for your reply. I think it's time for a professional! Cheers, Grant |
#10
|
|||
|
|||
Chris Bacon wrote:
Grant wrote: Sparks wrote: After a bit of Googling it seems that 4mm^2 cable might be used in a radial installation but I disconnected the wire between two sockets in the room and they both still worked - does this allow me to conclude that I have a ring mains? Also, 4mm^2 cable doesn't seem to be available from B&Q, etc. - the next size up is 6mm^2. Maybe it was a radial at some point, then was taken back to the CU and made into a ring? Are there any markings on the cable? ... and can you see both ends of the ring coming back to the C.U.? I don't really know what I'm looking for at the CU so I think, based on other advice in this thread, I should really be getting in a qualified electrician. Cheers, Grant |
#11
|
|||
|
|||
Grant wrote:
Hi, I want to extend the ring mains in my (1930's) house to add two double sockets to a room. I've got the floorboards up and know where the new cable needs to go. However, the thing that's stopping me going ahead is the fact that the existing cable appears to be ever so slightly thicker than the 2.5mm^2 that I was going to use. It is also multi(6)-stranded instead of single-stranded. Is this to be expected with older wiring (I believe a rewiring was done in the 70's)? There is a 32A MCB at the fuse box so I thought that 2.5mm^2 would do the job but having seen the existing wire I now have doubts. I don't want to weaken the installation by using wire that is too thin. After a bit of Googling it seems that 4mm^2 cable might be used in a radial installation but I disconnected the wire between two sockets in the room and they both still worked - does this allow me to conclude that I have a ring mains? Also, 4mm^2 cable doesn't seem to be available from B&Q, etc. - the next size up is 6mm^2. Maybe the fact that I'm having to ask these questions suggests that I should get in an electrician?! Cheers, Grant Grant, if it has 7 cores then it may be the old 7/029 standard. 7 cores, 0.29 something, and more tricky to work with than 2.5mm. 2.5mm came in about the late 60s/ early 70s iirc. Yes it looks like a ring, yes I'd just extend it with 2.5mm. Phil |
#12
|
|||
|
|||
P.R.Brady wrote:
Grant, if it has 7 cores then it may be the old 7/029 standard. 7 cores, 0.29 something, and more tricky to work with than 2.5mm. 2.5mm came in about the late 60s/ early 70s iirc. Yes it looks like a ring, yes I'd just extend it with 2.5mm. Phil I'm pretty sure that it has six cores, but I'll check when I get home tonight. However, based on other advice in the thread regarding full circuit & earth loop impedence tests I think I will hand this job over to a professional. Cheers, Grant |
#13
|
|||
|
|||
Christian McArdle wrote:
If it really is a radial (which is unlikely), your choices are to use bigger cable, or drop the MCB to 20A, which is no hardship if the circuit just covers a few reception or bedrooms. Don't even think about it for a kitchen, though. Flipping the 32A MCB off shows that all sockets in the house (dining room, sitting room, hall, 3 bedrooms & kitchen) are all on the same circuit. Cheers, Grant |
#14
|
|||
|
|||
Flipping the 32A MCB off shows that all sockets in the house (dining
room, sitting room, hall, 3 bedrooms & kitchen) are all on the same circuit. Ouch. You should really look into splitting the kitchen off it, unless it is a tiny kitchenette. Christian. |
#15
|
|||
|
|||
I'm pretty sure that it has six cores, but I'll check when I get home
tonight. However, based on other advice in the thread regarding full circuit & earth loop impedence tests I think I will hand this job over to a professional. Note that there is no harm in running the cables before they come. That's the long, expensive laborious bit, and I would say that there was an 80% chance of the cabling being useful. You only need the electrician for the skilled bit involving expensive equipment. Christian. |
#16
|
|||
|
|||
Christian McArdle wrote:
Flipping the 32A MCB off shows that all sockets in the house (dining room, sitting room, hall, 3 bedrooms & kitchen) are all on the same circuit. Ouch. You should really look into splitting the kitchen off it, unless it is a tiny kitchenette. Christian. No, it's a "proper" kitchen. :-( Grant |
#17
|
|||
|
|||
Christian McArdle wrote:
I'm pretty sure that it has six cores, but I'll check when I get home tonight. However, based on other advice in the thread regarding full circuit & earth loop impedence tests I think I will hand this job over to a professional. Note that there is no harm in running the cables before they come. That's the long, expensive laborious bit, and I would say that there was an 80% chance of the cabling being useful. You only need the electrician for the skilled bit involving expensive equipment. Christian. Yes, I was planning on doing that. I am now having nighmares about my house being ripped apart for a rewire (especially after having had the floors done). Not enough forward planning I suppose :-( Out of interest, maybe you could enlighten me on what a failed earth loop impedence test would signify and what dangers does it put me at risk from? Cheers, Grant |
#18
|
|||
|
|||
Out of interest, maybe you could enlighten me on what a failed earth
loop impedence test would signify and what dangers does it put me at risk from? When you have an earth to live fault, in the worst case, the current has to flow from your incoming supply, through the consumer unit, along the circuit cables to the furthest point. It then has to flow back down the earth conductor back to your incoming supply. The incoming supply will also have some resistance along its live and earth connection. The earth loop impedence is the total of all the resistances of the path that the current has to flow down. Now, a socket circuit must disconnect rapidly in the event of a fault. Using MCBs, to trip quickly enough, you must be able to guarantee that the current flowing will be 5 times the circuit rating. Therefore, a 32A circuit needs 160A to reliably flow. That requires a total earth loop impedence of 230/160 = 1.44 ohms, some of which will already come from the supply. Now, the old cables you have found, I believe, had a smaller earth conductor than modern cables. The horrendously large ring, including your entire house has more of it, too. It is quite possible that the resistance of the cable will be too much, either as is, or with your proposed extension. The danger of not fixing this potential problem is that in the event of an earth fault, it could take tens of seconds to disconnect the power, which is a fire and electrocution risk. In reality, such circuits are normally RCD protected, so provided the RCD is present and working, then the danger is not real, although it is not permitted to design circuits that rely on this, with the exception of TT earthed (earth rod) systems, where it is simply not possible to comply. Christian. |
#19
|
|||
|
|||
Christian McArdle wrote:
Out of interest, maybe you could enlighten me on what a failed earth loop impedence test would signify and what dangers does it put me at risk from? When you have an earth to live fault, in the worst case, the current has to flow from your incoming supply, through the consumer unit, along the circuit cables to the furthest point. It then has to flow back down the earth conductor back to your incoming supply. The incoming supply will also have some resistance along its live and earth connection. The earth loop impedence is the total of all the resistances of the path that the current has to flow down. Now, a socket circuit must disconnect rapidly in the event of a fault. Using MCBs, to trip quickly enough, you must be able to guarantee that the current flowing will be 5 times the circuit rating. Therefore, a 32A circuit needs 160A to reliably flow. That requires a total earth loop impedence of 230/160 = 1.44 ohms, some of which will already come from the supply. Now, the old cables you have found, I believe, had a smaller earth conductor than modern cables. The horrendously large ring, including your entire house has more of it, too. It is quite possible that the resistance of the cable will be too much, either as is, or with your proposed extension. The danger of not fixing this potential problem is that in the event of an earth fault, it could take tens of seconds to disconnect the power, which is a fire and electrocution risk. In reality, such circuits are normally RCD protected, so provided the RCD is present and working, then the danger is not real, although it is not permitted to design circuits that rely on this, with the exception of TT earthed (earth rod) systems, where it is simply not possible to comply. Christian. Christian, thanks very much for that explanation. The 1.44 ohms figure has jogged my memory - last year an engineer came to fix my washing machine and he carried out a test on the circuit. He told me that the desired figure for a sucessful test was 1.44 ohms but the figure he got from my circuit was 3-point-something (I have a note of it at home). he told me not to worry because some old houses have values above 30 ohms! So it looks like that circuit is already dangerous and I need a rewire. Thanks again, Grant |
#20
|
|||
|
|||
Christian, thanks very much for that explanation. The 1.44 ohms figure
has jogged my memory - last year an engineer came to fix my washing machine and he carried out a test on the circuit. He told me that the desired figure for a sucessful test was 1.44 ohms but the figure he got from my circuit was 3-point-something (I have a note of it at home). he told me not to worry because some old houses have values above 30 ohms! So it looks like that circuit is already dangerous and I need a rewire. Make sure the sockets are RCD protected. Although the circuit still won't be up to scratch and would still fail an inspection, this removes the main potential danger. Christian. |
#21
|
|||
|
|||
In an earlier contribution to this discussion,
Chris Bacon wrote: Set Square wrote: My understanding is that any such work now comes under the provisions of Part P of the Building Regs - and that, legally, the work needs to be certified by a qualified electrician - or by Building Control if they are capable! Many competent DIY-ers choose to ignore this - particularly if there's no obvious evidence as to *when* the work was carried out. Effectively, it doesn't matter when it was done, as long as there isn't an exact record existing of what's there. Well, on the basis of complying with the 11th commandment "Be thou not found out" - it's as well to make sure that there's no incriminating evidence which could prove that the work was done *after* the introduction of Part P. This could be important if and when you want to sell the house. For example, if the electrics are in an extension which was built this year, they *couldn't* have been done before Part P. -- Cheers, Set Square ______ Please reply to newsgroup. Reply address is invalid. |
#22
|
|||
|
|||
"Christian McArdle" wrote in message . net... Out of interest, maybe you could enlighten me on what a failed earth loop impedence test would signify and what dangers does it put me at risk from? When you have an earth to live fault, in the worst case, the current has to flow from your incoming supply, through the consumer unit, along the circuit cables to the furthest point. It then has to flow back down the earth conductor back to your incoming supply. The incoming supply will also have some resistance along its live and earth connection. The earth loop impedence is the total of all the resistances of the path that the current has to flow down. Now, a socket circuit must disconnect rapidly in the event of a fault. Using MCBs, to trip quickly enough, you must be able to guarantee that the current flowing will be 5 times the circuit rating. Therefore, a 32A circuit needs 160A to reliably flow. That requires a total earth loop impedence of 230/160 = 1.44 ohms, some of which will already come from the supply. Now, the old cables you have found, I believe, had a smaller earth conductor than modern cables. The horrendously large ring, including your entire house has more of it, too. It is quite possible that the resistance of the cable will be too much, either as is, or with your proposed extension. The danger of not fixing this potential problem is that in the event of an earth fault, it could take tens of seconds to disconnect the power, which is a fire and electrocution risk. In reality, such circuits are normally RCD protected, so provided the RCD is present and working, then the danger is not real, although it is not permitted to design circuits that rely on this, with the exception of TT earthed (earth rod) systems, where it is simply not possible to comply. Christian. Thanks, Christian- that's probably the clearest explanation of a fairly complicated (to a layman) subject I've ever seen. If only my teachers at school could have been like you......... |
#23
|
|||
|
|||
For example, if the electrics are in an extension which was built this
year, they *couldn't* have been done before Part P. And date stamps on cable etc. are becoming more common. Christian. |
#24
|
|||
|
|||
Set Square wrote:
Chris Bacon wrote: Set Square wrote: My understanding is that any such work now comes under the provisions of Part P of the Building Regs - and that, legally, the work needs to be certified by a qualified electrician - or by Building Control if they are capable! Many competent DIY-ers choose to ignore this - particularly if there's no obvious evidence as to *when* the work was carried out. Effectively, it doesn't matter when it was done, as long as there isn't an exact record existing of what's there. Well, on the basis of complying with the 11th commandment "Be thou not found out" - it's as well to make sure that there's no incriminating evidence which could prove that the work was done *after* the introduction of Part P. This could be important if and when you want to sell the house. For example, if the electrics are in an extension which was built this year, they *couldn't* have been done before Part P. There's the existing record, then - however, I shall be very interested if anyone knows what information is collected - is it simply "electrics passed", or is it "electrics passed, CU (type xxx), socket on wall X, Y, Z; lighting to points a,b,c (type xxx) (etc., etc.)". What is recorded? |
#25
|
|||
|
|||
"Christian McArdle" wrote in message
. net... Make sure the sockets are RCD protected. Although the circuit still won't be up to scratch and would still fail an inspection, this removes the main potential danger. But if it's RCD protected, don't you just need to meet ZsIn = 50V? (i.e. 1667ohm for 30mA) To me, the regs are clear that it's *preferable* to design for TN systems to disconnect on overcurrent rather than RCD, but seem to allow the use of RCD's instead. (413-02-04 (ii) and 413-02-16). What am I overlooking? Will |
#26
|
|||
|
|||
There's the existing record, then - however, I shall be very interested
if anyone knows what information is collected - is it simply "electrics passed", or is it "electrics passed, CU (type xxx), socket on wall X, Y, Z; lighting to points a,b,c (type xxx) (etc., etc.)". What is recorded? Bugger all. Your chance of being detected is between zero and nil. The only real chance of problems is if you sell the house and lie on the form, with would be regarded as fraud and could end you in prison. Your new house owner will be far more motivated at picking up infringements and evidence of new work than a BCO who is more interested in his next job where he gets to say how deep the foundations go. Christian. |
#27
|
|||
|
|||
Christian McArdle wrote:
For example, if the electrics are in an extension which was built this year, they *couldn't* have been done before Part P. And date stamps on cable etc. are becoming more common. Readers will have to refer to previous messages in this thread for context. Why not quote a bit more? Anyway: Even if date stamps are on *everything*, then what does it matter if there's no previous record of what was installed? |
#28
|
|||
|
|||
But if it's RCD protected, don't you just need to meet ZsIn = 50V? (i.e.
1667ohm for 30mA) Technically. Although they also specify a 200 ohm maximum, even this is a recommendation, I believe. To me, the regs are clear that it's *preferable* to design for TN systems to disconnect on overcurrent rather than RCD, but seem to allow the use of RCD's instead. (413-02-04 (ii) and 413-02-16). What am I overlooking? It comes under bad practice. You could certainly attempt to argue the toss, though, if it came to court or something. As I suggested, just adding an RCD to the existing system I would regard as sufficiently safe, although much over 3 ohms and you're starting to look at lighting and fixed circuits, too. However, I would not expect to see such shoddiness in a new or rewired installation and would regard such an installation as a cowboy bodge. Best practice is to always design main equipotential bonding and circuit cable sizing/resistance for TN-C-S, even on a TT or TN-S system. That way, the system can just be transferred to TN-C-S when it becomes available, which is increasingly common, even on overhead lines. Christian. |
#29
|
|||
|
|||
For example, if the electrics are in an extension which was built
this year, they *couldn't* have been done before Part P. And date stamps on cable etc. are becoming more common. Readers will have to refer to previous messages in this thread for context. Why not quote a bit more? There was enough context in what I quoted to get the gist. I don't like to quote more than necessary. It wastes the reader's time. Even if date stamps are on *everything*, then what does it matter if there's no previous record of what was installed? The fact that if the date stamps are post Part-P, there should be documentation proving that it was tested. You don't need prior documentation to see what was there before if your cables are stamped 2006, so must have been installed after the rule change. Christian. |
#30
|
|||
|
|||
Christian McArdle wrote:
The only real chance of problems is if you sell the house and lie on the form Or potentially if somebody got injured or worse as a result of the work and an investigation highlighted that the work was done illegally. |
#31
|
|||
|
|||
Christian McArdle wrote:
Christian, thanks very much for that explanation. The 1.44 ohms figure has jogged my memory - last year an engineer came to fix my washing machine and he carried out a test on the circuit. He told me that the desired figure for a sucessful test was 1.44 ohms but the figure he got from my circuit was 3-point-something (I have a note of it at home). he told me not to worry because some old houses have values above 30 ohms! So it looks like that circuit is already dangerous and I need a rewire. Make sure the sockets are RCD protected. Although the circuit still won't be up to scratch and would still fail an inspection, this removes the main potential danger. Christian. Lots of valuable advice so far - thanks everyone. So, I will protect the sockets with an RCD until I get the rewire done. Currently there is a 32A MCB for the sockets. Do I simply need to replace this MCB with an appropriate RCD or is the RCD in addition to the MCB? Do RCDs have the same kinds of ratings? In short, do I buy a 32A RCD and put it where the MCB currently is? Excuse my ignorance! Cheers, Grant |
#32
|
|||
|
|||
Grant wrote:
Christian McArdle wrote: Christian, thanks very much for that explanation. The 1.44 ohms figure has jogged my memory - last year an engineer came to fix my washing machine and he carried out a test on the circuit. He told me that the desired figure for a sucessful test was 1.44 ohms but the figure he got from my circuit was 3-point-something (I have a note of it at home). he told me not to worry because some old houses have values above 30 ohms! So it looks like that circuit is already dangerous and I need a rewire. Make sure the sockets are RCD protected. Although the circuit still won't be up to scratch and would still fail an inspection, this removes the main potential danger. Christian. Lots of valuable advice so far - thanks everyone. So, I will protect the sockets with an RCD until I get the rewire done. Currently there is a 32A MCB for the sockets. Do I simply need to replace this MCB with an appropriate RCD or is the RCD in addition to the MCB? Do RCDs have the same kinds of ratings? In short, do I buy a 32A RCD and put it where the MCB currently is? Excuse my ignorance! Cheers, Grant Its not quite as simple as that as MCBs are single pole on the live side of the circuit whereas RCDs are double pole so work on both the live and the neutral side. It may be possible, depending on your consumer unit to replace the MCB with an RCBO - which is a combined RCD and MCB in one unit that comes with the appropriate wire/teminals to connect in the neutral as well. |
#33
|
|||
|
|||
Christian McArdle wrote:
Even if date stamps are on *everything*, then what does it matter if there's no previous record of what was installed? The fact that if the date stamps are post Part-P, there should be documentation proving that it was tested. You don't need prior documentation to see what was there before if your cables are stamped 2006, so must have been installed after the rule change. Not so - nothing is recorded, as you say - so even if the cable and fittings are date marked, it doesn't matter, as replacement of fittings and damaged wiring is allowed without notification. |
#34
|
|||
|
|||
So, I will protect the sockets with an RCD until I get the rewire done.
Currently there is a 32A MCB for the sockets. Do I simply need to replace this MCB with an appropriate RCD or is the RCD in addition to the MCB? If it is an RCD, then it is in addition to the MCB. You could put it in a separate box after the MCB to just protect the socket circuit. However, you can get an RCD that replaces an MCB. It is called an RCBO. However, you may find it difficult to find a suitable device for some older boards. If you have a DIN rail system, then you should be able to find a suitable single width RCBO. These are a direct replacement. Note, that when you get the circuit sorted, you should probably install an extra few circuits in the kitchen. It is usual these days to have a separate kitchen ring that is RCD protected and to have one or more circuits for fixed appliances (washing machines/freezers/fridges/tumble dryers/dishwashers) that is not RCD protected, so that your frozen sausages are still frozen when you get back from holiday. Christian. |
#35
|
|||
|
|||
"Christian McArdle" wrote in message
. net... It comes under bad practice. You could certainly attempt to argue the toss, though, if it came to court or something. As I suggested, just adding an RCD to the existing system I would regard as sufficiently safe, although much over 3 ohms and you're starting to look at lighting and fixed circuits, too. However, I would not expect to see such shoddiness in a new or rewired installation and would regard such an installation as a cowboy bodge. But that implies that 413-02-16 is just there for the use of cowboys. I absolutely agree that one wouldn't design a new circuit like this, but I can't see how it would fail a periodic inspection. It's in compliance with the regs and the GN3 guidance. Of course, it might be a symptom of more serious problems, which *would* be failures. Best practice is to always design main equipotential bonding and circuit cable sizing/resistance for TN-C-S, even on a TT or TN-S system. That way, the system can just be transferred to TN-C-S when it becomes available, which is increasingly common, even on overhead lines. Well, it could be anyway, as long as the RCD wasn't removed. I'm really not arguing with you that it would be a good idea to look at what's really happening here, rather than sticking an RCD in and forgetting about it - I'm just always interested in what really is compliant and what isn't. Will |
#36
|
|||
|
|||
Not so - nothing is recorded, as you say - so even if the cable
and fittings are date marked, it doesn't matter, as replacement of fittings and damaged wiring is allowed without notification. It would be laughed out of court if you attempted to suggest that your entire new installation had needed every single fitting and cable replaced one at a time. Christian. |
#37
|
|||
|
|||
I absolutely agree that one wouldn't design a new circuit like this, but I
can't see how it would fail a periodic inspection. It's in compliance with the regs and the GN3 guidance. I'd expect to see it as an advisory, provided there was appropriate RCD support and a plastic consumer unit. But that implies that 413-02-16 is just there for the use of cowboys. I suspect it is written like that so that the OP can continue to use his system (with an RCD) without having the power disconnected by overzealous contractors/maintenance people. It really isn't that unsafe, provided that the circuit conductors passed their continuity tests with the expected numbers. Christian. |
#38
|
|||
|
|||
Christian McArdle wrote:
Not so - nothing is recorded, as you say - so even if the cable and fittings are date marked, it doesn't matter, as replacement of fittings and damaged wiring is allowed without notification. It would be laughed out of court if you attempted to suggest that your entire new installation had needed every single fitting and cable replaced one at a time. But in context we're talking about adding a socket to a ring, which may be exempted anyway! |
#39
|
|||
|
|||
Christian McArdle wrote:
So, I will protect the sockets with an RCD until I get the rewire done. Currently there is a 32A MCB for the sockets. Do I simply need to replace this MCB with an appropriate RCD or is the RCD in addition to the MCB? If it is an RCD, then it is in addition to the MCB. You could put it in a separate box after the MCB to just protect the socket circuit. However, you can get an RCD that replaces an MCB. It is called an RCBO. However, you may find it difficult to find a suitable device for some older boards. If you have a DIN rail system, then you should be able to find a suitable single width RCBO. These are a direct replacement. I don't know if I have a DIN rail system or not. I think I'll call an electrician ASAP and get things sorted once and for all. I am not willing to take any risks whatsoever! Note, that when you get the circuit sorted, you should probably install an extra few circuits in the kitchen. It is usual these days to have a separate kitchen ring that is RCD protected and to have one or more circuits for fixed appliances (washing machines/freezers/fridges/tumble dryers/dishwashers) that is not RCD protected, so that your frozen sausages are still frozen when you get back from holiday. Christian. Christian, I can't thank you enough for your excellent advice. I'll certainly bear this in mind when discussing my requirements with the electrician. Incidentally, how disruptive is a rewire likely to be? The two public rooms and hallway have nicely finished floors and I would prefer not to have them damaged. I know it will depend on my installation but will an electrician be able to pull through most of the new wiring using the existing stuff? None of the socket cabling is plastered in - the sockets are either behind skirting or fed via metal conduits. What about cost? £1000-ish? Cheers, Grant P.S. Anyone know a good electrician in Edinburgh? |
#40
|
|||
|
|||
"Grant" wrote in message ... Hi, I want to extend the ring mains in my (1930's) house to add two double sockets to a room. I've got the floorboards up and know where the new cable needs to go. However, the thing that's stopping me going ahead is the fact that the existing cable appears to be ever so slightly thicker than the 2.5mm^2 that I was going to use. It is also multi(6)-stranded instead of single-stranded. Is this to be expected with older wiring (I believe a rewiring was done in the 70's)? There is a 32A MCB at the fuse box so I thought that 2.5mm^2 would do the job but having seen the existing wire I now have doubts. I don't want to weaken the installation by using wire that is too thin. After a bit of Googling it seems that 4mm^2 cable might be used in a radial installation but I disconnected the wire between two sockets in the room and they both still worked - does this allow me to conclude that I have a ring mains? Also, 4mm^2 cable doesn't seem to be available from B&Q, etc. - the next size up is 6mm^2. Maybe the fact that I'm having to ask these questions suggests that I should get in an electrician?! It sounds like 7/.029 cable which was the forerunner of 2.5 solid conductor and ws usually tinned copper conductors. A simple solution of just using 2.5mm T&E to extend it is possible but ignores the ramifications of cicuit protective conductor sizing (earth conductor) and fault currents. However I suspect most of the run of the mill sparkys might do just that. 4mm cable is readily available from half decent suppliers and some wholesalers might even be willing to cut lengths for you. For a fuller answer we would need to know what earthing arrangements apply to your installation and an idea of possible cable lengths involved. You have already advised us that you have a 32A MCB but can you tell us if it a type B or otherwise? If the protection is problematic it might be possible to use a 32A RCBO but we need answers first |
Reply |
|
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Extending ring main | UK diy | |||
Extending a ring main with junction boxes | UK diy | |||
Wiring Ring mains to MCBs in consumer units | UK diy | |||
Ring mains and consumer unit | UK diy | |||
extending a ring main | UK diy |