This morning was the coldest day of the year in the Washington DC area
- a bone-chilling 21 degrees F. I stepped into my shower and lo and
behold - no hot water! I scurried to the basement, checked the main
circuit breaker and the water heater/deep well pump breaker and
everything was on - they did not trip.

I went to the water heater - a Bradford White Hydrojet that is less
than 3 years old - opened the upper panel, pushed the red reset button,
heard it click, and waited a few minutes. Later, I felt the copper tube
on top warming up again and when I checked the water faucets, the water
was starting to get warm. I had to leave for work so I didn't have a
chance to see if it would trip again. I'm now in the office for 3 hours
and the wife has not called, so I am assuming things are back to
normal.

I have done a fair amount of reading on the subject but, given the
relatively young age of this unit, I don't believe there is anything
wrong with the thermostats or the heating elements.

So my question is - is this just a fluke, an act of God, a one-time
random event that may never happen again? What could have caused it to
trip without the main breaker going off? Could the cold weather have
anything to do with it? What about the fact that our water source is a
deep well pump?

I guess I'm just looking for a rational explanation, so that I will
have peace of mind if the heater switch does not trip again.
Thanks for any insights, tips, comments, etc.

  #2   Report Post  
 
Posts: n/a
Default

On 16 Dec 2004 05:16:26 -0800, wrote:

This morning was the coldest day of the year in the Washington DC area
- a bone-chilling 21 degrees F. I stepped into my shower and lo and
behold - no hot water! I scurried to the basement, checked the main
circuit breaker and the water heater/deep well pump breaker and
everything was on - they did not trip.

I went to the water heater - a Bradford White Hydrojet that is less
than 3 years old - opened the upper panel, pushed the red reset button,
heard it click, and waited a few minutes. Later, I felt the copper tube
on top warming up again and when I checked the water faucets, the water
was starting to get warm. I had to leave for work so I didn't have a
chance to see if it would trip again. I'm now in the office for 3 hours
and the wife has not called, so I am assuming things are back to
normal.

I have done a fair amount of reading on the subject but, given the
relatively young age of this unit, I don't believe there is anything
wrong with the thermostats or the heating elements.

So my question is - is this just a fluke, an act of God, a one-time
random event that may never happen again? What could have caused it to
trip without the main breaker going off? Could the cold weather have
anything to do with it? What about the fact that our water source is a
deep well pump?

I guess I'm just looking for a rational explanation, so that I will
have peace of mind if the heater switch does not trip again.
Thanks for any insights, tips, comments, etc.



imho:
Sometimes breakers just go bad. You can verify this with a clamp on
amp meter. Which should only be done by safely trained professionals.

later,

tom @
www.FindMeShelter.com


  #3   Report Post  
Jeff Wisnia
 
Posts: n/a
Default

wrote:
On 16 Dec 2004 05:16:26 -0800,
wrote:


This morning was the coldest day of the year in the Washington DC area
- a bone-chilling 21 degrees F. I stepped into my shower and lo and
behold - no hot water! I scurried to the basement, checked the main
circuit breaker and the water heater/deep well pump breaker and
everything was on - they did not trip.

I went to the water heater - a Bradford White Hydrojet that is less
than 3 years old - opened the upper panel, pushed the red reset button,
heard it click, and waited a few minutes. Later, I felt the copper tube
on top warming up again and when I checked the water faucets, the water
was starting to get warm. I had to leave for work so I didn't have a
chance to see if it would trip again. I'm now in the office for 3 hours
and the wife has not called, so I am assuming things are back to
normal.

I have done a fair amount of reading on the subject but, given the
relatively young age of this unit, I don't believe there is anything
wrong with the thermostats or the heating elements.

So my question is - is this just a fluke, an act of God, a one-time
random event that may never happen again? What could have caused it to
trip without the main breaker going off? Could the cold weather have
anything to do with it? What about the fact that our water source is a
deep well pump?

I guess I'm just looking for a rational explanation, so that I will
have peace of mind if the heater switch does not trip again.
Thanks for any insights, tips, comments, etc.




imho:
Sometimes breakers just go bad. You can verify this with a clamp on
amp meter. Which should only be done by safely trained professionals.

later,

tom @
www.FindMeShelter.com



Tom, it appears you missed the entire point of the OPs message, the "red
button" is a THERMAL overload, not an overcurrent one. While your
statement about "breakers" is valid, the only part about it which is
pertinent is that if the OP doesn't have the skills and knowledge to
work on and/or change out a water heater thermostat then he SHOULD call
in a professional.

The "most likely" cause of it tripping is that either the upper or lower
thermostat got "sticky" and didn't open, and the temperature in the
heater rose to the point where the thermal overload tripped. I've never
seen one "trip by itself" with water in the normal temperature
range.(I'm assuming that since you mentioned opening the "upper panel",
there's a lower one too, so there's two thermostats on your water heater.

Chances are that even if the sticky operating thermostat reopened, it'll
stick again in the near future. (Things which go away by themselves
usually come back by themselves, y'know. G) The safest thing to do is
to replace the sticking if you know enough to be able to circuit trace
and catch which one is stuck, otherwise change out BOTH thermostats,
they're cheap enough.

You may very well be able to get a replacement thermostat at no cost
under warranty if you know which one it is. But, since they're
relatively cheap and available at Home Cheepo, waiting for the factory
to exchange one under warranty isn't much of an option.

HTH, and Happy Holidays,

Jeff

--
Jeffry Wisnia

(W1BSV + Brass Rat '57 EE)

"As long as there are final exams, there will be prayer in public
schools"
  #4   Report Post  
EL
 
Posts: n/a
Default

I can back-up Jeff's advice.

In the first house I owned, I had exactly the same experience with a water heater that was 2 years old. Temp safety switch
tripped for "no reason", I reset it, tripped again a couple weeks later, then it became more frequent. Along the way, I
noticed that the hot water was intermittently a lot hotter than normal.

Flipped a coin and decided to replace the upper thermostat which did not fix it, so I replaced the lower one which *did* fix
it. Like Jeff said, they're cheap and if I have the same experience again I'll just replace both.

Eric Law


  #5   Report Post  
Jeff Wisnia
 
Posts: n/a
Default

EL wrote:

I can back-up Jeff's advice.

In the first house I owned, I had exactly the same experience with a water heater that was 2 years old. Temp safety switch
tripped for "no reason", I reset it, tripped again a couple weeks later, then it became more frequent. Along the way, I
noticed that the hot water was intermittently a lot hotter than normal.

Flipped a coin and decided to replace the upper thermostat which did not fix it, so I replaced the lower one which *did* fix
it. Like Jeff said, they're cheap and if I have the same experience again I'll just replace both.

Eric Law



I wouldn't have flipped a coin... I would have gone for the lower stat,
on the theory that with typical household hot water usage vs time the
heater is probably cycling on that one most of the time and only
flipping the upper stat at those times when so much hot water is drawn
continuously that that the water at the upper stat gets cool enough to
flip it on. That would auger for the lower stat being the one to "wear
out" first, huh?

I've got a neon pilot lamp hooked to the upper element on mine, and
while I'm near the water heater frequently ('Cause it's in my basement
home workshop.) The only time I can recall seeing it lit was near the
end of one of our daughter's nerve wrackingly long showers, just before
I reached over and shut off the heater's water inlet valve. G

Happy Holidays,

jeff

--
Jeffry Wisnia

(W1BSV + Brass Rat '57 EE)

"As long as there are final exams, there will be prayer in public
schools"


  #6   Report Post  
 
Posts: n/a
Default

Thanks for all the great advice. The unit has not tripped again for the
last 48 hours after I pushed the red reset button. However, I did
notice that the water is hotter than what it used to be. I adjusted
both thermostats to the lowest level (120 degrees F - the factory
settings) but the water is still much hotter than before. So I have
made a decision to replace both thermostats on my own.

The water heater is a Bradford White Hydrojet Model No. MI65R6DS13, 65
gallon tank, double element. However, I've searched around the internet
and virtually all of the aftermarket thermostats around are generic, so
how do I know which thermostat will work with my heater? Are all upper
and lower 240 volt generic thermostats for double element electric
heaters interchangeable? The brands I found are American Water (Lowe's)
and Apcom (Home Depot) but there is no cross reference chart around
that tells me which part fits which model.

I could shut the house down, take the existing thermostats off and take
then to the hardware store as samples, but I want to avoid doing this
if I can.

I would thus appreciate any assistance/advice in this regard.
Thanks and best regards.

  #7   Report Post  
Tekkie
 
Posts: n/a
Default

posted for all of us....

Thanks for all the great advice. The unit has not tripped again for the
last 48 hours after I pushed the red reset button. However, I did
notice that the water is hotter than what it used to be. I adjusted
both thermostats to the lowest level (120 degrees F - the factory
settings) but the water is still much hotter than before. So I have
made a decision to replace both thermostats on my own.

The water heater is a Bradford White Hydrojet Model No. MI65R6DS13, 65
gallon tank, double element. However, I've searched around the internet
and virtually all of the aftermarket thermostats around are generic, so
how do I know which thermostat will work with my heater? Are all upper
and lower 240 volt generic thermostats for double element electric
heaters interchangeable? The brands I found are American Water (Lowe's)
and Apcom (Home Depot) but there is no cross reference chart around
that tells me which part fits which model.

I could shut the house down, take the existing thermostats off and take
then to the hardware store as samples, but I want to avoid doing this
if I can.

I would thus appreciate any assistance/advice in this regard.
Thanks and best regards.


Why not call up the manufacturer & have them sent to you?
--
Tekkie
  #9   Report Post  
 
Posts: n/a
Default

On Thu, 16 Dec 2004 10:19:12 -0500, Jeff Wisnia
wrote:

wrote:
On 16 Dec 2004 05:16:26 -0800, wrote:


This morning was the coldest day of the year in the Washington DC area
- a bone-chilling 21 degrees F. I stepped into my shower and lo and
behold - no hot water! I scurried to the basement, checked the main
circuit breaker and the water heater/deep well pump breaker and
everything was on - they did not trip.

I went to the water heater - a Bradford White Hydrojet that is less
than 3 years old - opened the upper panel, pushed the red reset button,
heard it click, and waited a few minutes. Later, I felt the copper tube
on top warming up again and when I checked the water faucets, the water
was starting to get warm. I had to leave for work so I didn't have a
chance to see if it would trip again. I'm now in the office for 3 hours
and the wife has not called, so I am assuming things are back to
normal.

I have done a fair amount of reading on the subject but, given the
relatively young age of this unit, I don't believe there is anything
wrong with the thermostats or the heating elements.

So my question is - is this just a fluke, an act of God, a one-time
random event that may never happen again? What could have caused it to
trip without the main breaker going off? Could the cold weather have
anything to do with it? What about the fact that our water source is a
deep well pump?

I guess I'm just looking for a rational explanation, so that I will
have peace of mind if the heater switch does not trip again.
Thanks for any insights, tips, comments, etc.




imho:
Sometimes breakers just go bad. You can verify this with a clamp on
amp meter. Which should only be done by safely trained professionals.

later,

tom @
www.FindMeShelter.com



Tom, it appears you missed the entire point of the OPs message, the "red
button" is a THERMAL overload, not an overcurrent one. While your
statement about "breakers" is valid, the only part about it which is
pertinent is that if the OP doesn't have the skills and knowledge to
work on and/or change out a water heater thermostat then he SHOULD call
in a professional.


OH! I thought I DID miss what he said. Thought it was another breaker
going bad story. Atleast I got the suggestion to have it looked at by
'trained professionals' part right.

:-P







The "most likely" cause of it tripping is that either the upper or lower
thermostat got "sticky" and didn't open, and the temperature in the
heater rose to the point where the thermal overload tripped. I've never
seen one "trip by itself" with water in the normal temperature
range.(I'm assuming that since you mentioned opening the "upper panel",
there's a lower one too, so there's two thermostats on your water heater.

Chances are that even if the sticky operating thermostat reopened, it'll
stick again in the near future. (Things which go away by themselves
usually come back by themselves, y'know. G) The safest thing to do is
to replace the sticking if you know enough to be able to circuit trace
and catch which one is stuck, otherwise change out BOTH thermostats,
they're cheap enough.

You may very well be able to get a replacement thermostat at no cost
under warranty if you know which one it is. But, since they're
relatively cheap and available at Home Cheepo, waiting for the factory
to exchange one under warranty isn't much of an option.

HTH, and Happy Holidays,

Jeff



later,

tom @ www.CarFleaMarket.com



  #11   Report Post  
Jeff Wisnia
 
Posts: n/a
Default

wrote:
On Thu, 16 Dec 2004 10:19:12 -0500, Jeff Wisnia
wrote:


The "most likely" cause of it tripping is that either the upper or lower
thermostat got "sticky" and didn't open, and the temperature in the
heater rose to the point where the thermal overload tripped. I've never
seen one "trip by itself" with water in the normal temperature
range.(I'm assuming that since you mentioned opening the "upper panel",
there's a lower one too, so there's two thermostats on your water heater.



I would tend to disagree that the heater overheated. The OP said the
water was cold in the shower in the morning. If the water was
overheated, it would still be hot, or fairly warm. I can shut off the
power to my water heater and 24 hours later still have relatively hot
water (assuming someone did not drain the tank).

Since the OP has a well, I'd check the elements. Only 3 year old tank
does not mean anything in a rural area. Sure, the tank itself should
be in good shape. BUT........

Lightning can be nasty in rural areas because of the long runs of
overhead wires and few ground points along the way. A lightning
strike last summer may have blown a tiny pin hole in one of the
elements and discharged into the water. I have fixed several of
these, and its more common that you would believe.

You could also have a high acidic water that ate a hole in an element.

You could have a combination of both of these that finally drew enough
current to go POP.


It wasn't a CURRENT overload that popped.

Pull the elements and thoroughly inspect them. Wipe them down with
one of those green pot scrubbers (scotch pad), and you should see any
pin holes or cracks. Usually they stay wet after you dry the rest of
the element.

If thats too much effort, either learn to live with the hot water
cutting off more and more in the future, or hope and pray that that
someone broke into your home while you were away, and did it just to
trip that red button. By the way, if your income is at or near any of
those political idiots in DC, just buy a new water heater and donate
the old one to charity so some needy person can fix it.


21deg.... Geeshhhhhh, I hope the shrub freezes, shrivels, and wilts
away !!!!


Mark



I won't disagree that the elements could *also* be bad, but "how the F"
will that trip a thermal breaker?

If you've ever taken a thermal breaker apart you know that it consists
of a disk of bimetal formed into a shallow "dish". When the tank shell
reaches the "overtemperature" point the dish inverts (with a snap) and
opens a set of contacts which break the line voltage feeding everything
else in the water heater.

Now, tell us how a damaged element will cause the water to heat up
enough to pop the thermal overload? And even if it in some arcane way
does so, why doesn't the operating thermostat open first and thus keep
the water from getting hot enough to pop the thermal overload?

I repeat, it has to be caused by a stuck operating thermostat, most
likely the lower one.

Happy Holidays,

Jeff


(W1BSV + Brass Rat '57 EE)

"As long as there are final exams, there will be prayer in public
schools"
  #12   Report Post  
Steve B.
 
Posts: n/a
Default

On Sat, 18 Dec 2004 13:46:50 -0500, Jeff Wisnia
wrote:

I won't disagree that the elements could *also* be bad, but "how the F"
will that trip a thermal breaker?


Some bottom thermostat setups only switch one side of the 220 going to
the element. If the element suffers a failure that allows current
leakage but isnt catastropic to the element you have a 110v potential
on one side and a nice ground path through the defect/water on the
other so the element can continue to heat at 110v with thermostat off.
Eventually it could get hot enough to pop the overheat on the top
thermostat

It would seem that the odds of this happening would be somewhere
around the odds of winning powerball but it is possible.

Steve B.
  #13   Report Post  
Jeff Wisnia
 
Posts: n/a
Default

Steve B. wrote:
On Sat, 18 Dec 2004 13:46:50 -0500, Jeff Wisnia
wrote:


I won't disagree that the elements could *also* be bad, but "how the F"
will that trip a thermal breaker?



Some bottom thermostat setups only switch one side of the 220 going to
the element. If the element suffers a failure that allows current
leakage but isnt catastropic to the element you have a 110v potential
on one side and a nice ground path through the defect/water on the
other so the element can continue to heat at 110v with thermostat off.
Eventually it could get hot enough to pop the overheat on the top
thermostat

It would seem that the odds of this happening would be somewhere
around the odds of winning powerball but it is possible.

Steve B.



You know, I thought of that, which is why I said "arcane", but I've
never heard tell of that kind of failure before. And you are correct
about the possibility that a single pole lower thermostat could let that
sort of fault keep heating the water regardless of the state of that
thermostat.

But I'm not up to visualizing what kind of mechanical/corrosion failure
would permit that sort of current flow; I'm kinda out of my element
here. G

The OP's problem *might* not be with the control thermostat, but it's
darned well the way to bet.

Happy Holidays,

Jeff

--
Jeffry Wisnia

(W1BSV + Brass Rat '57 EE)

"As long as there are final exams, there will be prayer in public
schools"
  #14   Report Post  
Stormin Mormon
 
Posts: n/a
Default

I think the lower one runs until it's satisfied, and then the upper one. Or
is it the other way around? Ah, well. Rip em both out.

--

Christopher A. Young
Learn more about Jesus
www.lds.org
www.mormons.com


"EL" wrote in message
m...
I can back-up Jeff's advice.

In the first house I owned, I had exactly the same experience with a water
heater that was 2 years old. Temp safety switch
tripped for "no reason", I reset it, tripped again a couple weeks later,
then it became more frequent. Along the way, I
noticed that the hot water was intermittently a lot hotter than normal.

Flipped a coin and decided to replace the upper thermostat which did not fix
it, so I replaced the lower one which *did* fix
it. Like Jeff said, they're cheap and if I have the same experience again
I'll just replace both.

Eric Law



  #15   Report Post  
Filipo
 
Posts: n/a
Default

This problem has defied all explanation.

I have replaced both thermostats - the upper and the lower - with the
exact same model that the unit had - and the red button tripped again!
So by process of elimination, I have to replace the elements now. I
have no problem doing both but I've never done this before. Do I just
unscrew these things or do I have to drain the tank? Any instructions
would be appreciated. Thanks once again.



  #16   Report Post  
BGBevill
 
Posts: n/a
Default

This problem has defied all explanation.

I have replaced both thermostats - the upper and the lower - with the
exact same model that the unit had - and the red button tripped again!
So by process of elimination, I have to replace the elements now. I
have no problem doing both but I've never done this before. Do I just
unscrew these things or do I have to drain the tank? Any instructions
would be appreciated. Thanks once again.


Usually, stats sticking or being out of calibration will cause the red button
to trip. I am thinking that an element could cause it, but only under certain
circumstances. Anyway, to replace the elements, cut off the power to the tank
and the incoming water. It is possible to replace the elements without
draining the tank completely, but if you have never done it, I'd recommend
draining the tank. Once you have it drained, the elements either screw out or
are attached with 4 bolts on some models I have seen.

Keep in mind that the red button is a high limit and is a safety device. Do
not continue to experiment with a solution to this problem. Ever seen on the
news what is left of a house when the water heater blows?? Not very
much....think about it.

Bobby
  #17   Report Post  
Jeff Wisnia
 
Posts: n/a
Default

Filipo wrote:
This problem has defied all explanation.

I have replaced both thermostats - the upper and the lower - with the
exact same model that the unit had - and the red button tripped again!
So by process of elimination, I have to replace the elements now. I
have no problem doing both but I've never done this before. Do I just
unscrew these things or do I have to drain the tank? Any instructions
would be appreciated. Thanks once again.


Is there ANY possibility that you might have miswired something when you
replaced the thermostats? Did you have or make an accurate diagram of
just which wire went to which terminal on the two thermostats before you
removed them?

I should have asked before, but is the "red button" you refer to
*really* on a high temperature overlimit thermostat. i.e. is it part of
the upper thermostat assembly or otherwise on something in thermal
contact with the tank shell?

I'm frustrated, 'cause I know that if I was on the scene with my
clamp-on ammeter/VOM I'd have been able to diagnose it much better.

BTW if you *are* going to change out the elements, and they are threaded
into bosses on the tank shell they'll have a large hex section on them
and you'd be well advised to pick up an "element socket wrench" to
unscrew them with unless you have a socket of the proper size already.
They usually don't like to come out if you go after them with a pair of
Channelock pliers or an adjustable wrench, and you can screw up a new
element trying to tighten it firmly without a socket wrench. Those
element socket wrenches are usually stocked right near the elements and
only cost a couple of bucks.

Good Luck,

Jeff

--
Jeffry Wisnia

(W1BSV + Brass Rat '57 EE)

"As long as there are final exams, there will be prayer in public
schools"
  #18   Report Post  
Steve B.
 
Posts: n/a
Default

On 19 Dec 2004 13:59:05 -0800, "Filipo"
wrote:

This problem has defied all explanation.

I have replaced both thermostats - the upper and the lower - with the
exact same model that the unit had - and the red button tripped again!
So by process of elimination, I have to replace the elements now. I
have no problem doing both but I've never done this before. Do I just
unscrew these things or do I have to drain the tank? Any instructions
would be appreciated. Thanks once again.


An experience plumber can sometimes replace an element without
draining the tank but I would never try it myself and I have done
about 20 over the years. Go ahead and drain the tank then replace
them and save yourself a headache.

Stee B.
  #19   Report Post  
Filipo
 
Posts: n/a
Default

The red button on the upper thermostat did not pop this morning, and
that may have been because I re-adjusted the 2 brand new thermostats to
their factory presets. Both thermostats are so-called "Apcom Style"
thermostats made as OEM by Camco. They are currently on sale at all
Home Depot stores for 3 bucks apiece, which makes me wonder if they are
crappy because they are so cheap, or they are so cheap because they are
so crappy. They are the exact same replacement models that came with my
Bradford White water heater, so I'm pretty sure my wiring is the same,
except I had a little problem tightening the screw on the black wire of
the lower stat because the screw offered some resistance so I forced it
and may have stripped it a little bit, but there is still some
electrical contact, I think.

Each thermostat has 4 settings - "Hot", "A" "B" and "C". "Hot" is the
factory preset at 120 degrees F. I turned the white knobs to "A" before
I installed them because I was guessing "A" might be at least 135
degrees F, which is supposedly the minimum temperature needed for the
clothes washer. Then I installed them. Shortly thereafter, the hot
water temp zoomed up to higher than normal and the red button tripped.
I reset the red button. Then I turned the white knobs back to "Hot" and
I heard a distinct click on the upper thermostat, as if it was closing
(or opening?) as I was turning the white knob back to "Hot" from A"".

It seems to that my act of changing the factory presets from "Hot" to
"A" prior to installation may have confused the thermostats. Perhaps I
should have installed them with the factory presets at 120 degrees F
before I decided to change anything. Just as a car needs a break-in
period, perhaps the thermostats need to be installed first before they
should be adjusted temperature-wise. Does this make sense?

Sorry for the long-winded explanation. I'm pretty happy now at the 120
degrees F factory settings, as long as they don't trip again. So I'll
suspend the element replacement project for another day. Thanks all for
your support!

Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Water heater leak? Jim Z Home Repair 1 July 18th 04 01:57 PM
Problem with new water heater (electric) - please advice Robert Home Repair 8 February 19th 04 05:27 AM
I need a little advice on running waterlines in an uninsulated crawlspace ozark Home Repair 12 January 29th 04 05:23 AM
Electric Water Heater Problem, Repair or Buy new, please help Robert Home Repair 10 January 10th 04 01:09 AM
Electric Water Heater Problem, Repair or Buy new, please help Robert Home Ownership 9 January 10th 04 01:09 AM


All times are GMT +1. The time now is 10:09 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"